Topic:"Building Efficiency" in M12104

Matter: Riverport Electric Light Commission Complaint - Power Poles - Martin and Wendy Tanner
4 passages 4 documents

Building Efficiency across all matters →

T-3Respondents Submission - Strum Report (redacted) 1 passage
4.03 Clearances to Building
4.03 Clearances to Building Minimum conductor clearances from buildings shall be in accordance with chart V-4M. Where buildings exceed three storeys (or 15 m) in height, a clear space at least 2 m wide shall be left either adjacent to the...

AI summary This section outlines the minimum conductor clearances from buildings, including requirements for multi-storey buildings, clear spaces for fire-fighting ladders, and restrictions on wires and cables rubbing against buildings or other plant.

T-6UTILITY (NSEB) RIR-1 to RIR-7 (redacted) 1 passage
4.03 Clearances to Building
4.03 Clearances to Building Minimum conductor clearances from buildings shall be in accordance with chart V-4M. Where buildings exceed three storeys (or 15 m) in height, a clear space at least 2 m wide shall be left either adjacent to the...

AI summary This section outlines the minimum conductor clearances required from buildings, including specific requirements for taller buildings and the prohibition of wires rubbing against buildings. It emphasizes the need for clear spaces to allow ladder access for firefighting and applies to all parts of a building, including fixtures and communication cables.

99194Board Decision Letter - Redacted 1 passage
BACKGROUND
2.85 meters of the upper veranda which I measured with a laser measuring device as stated in a previous email. This is less than the required 3 meters clearance code requirement. [Exhibit T-5, p. 1] In IR-6, the Board directed RELC to prov...

AI summary The document discusses a compliance issue related to safety clearance requirements for a residence, referencing a report from Strum Engineering and the implementation of a recommendation to install an insulator arm to increase horizontal clearance.

99194Board Decision Letter - Redacted 1 passage
BACKGROUND
2.85 meters of the upper veranda which I measured with a laser measuring device as stated in a previous email. This is less than the required 3 meters clearance code requirement. [Exhibit T-5, p. 1] In IR-6, the Board directed RELC to prov...

AI summary The document discusses a compliance issue related to safety clearances for electrical equipment on a property. Measurements taken by Strum Engineering show that four of five horizontal clearance measurements were non-compliant with standards. A recommendation was made to install an epoxy insulator arm to address the issue, and RELC implemented this recommendation.

Disclaimer: These summaries were generated by AI from the filings they describe. We take care to make them accurate, but errors are possible - and they aren't advice. Only the filings themselves are the record: if you're relying on something here, confirm it against the source documents or the Nova Scotia Energy Board's own record. Full disclaimer →