N-1CI C0085185 4S-332 George St Rebuild and Reconfiguration U&U - Application - Redacted
2 passages
6.2 Feeder Loading The fully loaded capacity of an NSPI 12.5 kV distribution feeder is presently the lower of the thermal capacity of the feeder circuit conductors, or 325 A (7 MVA). Under contingency operation, load on circuits can exceed...
AI summary The document discusses the capacity and loading of NSPI 12.5 kV distribution feeders, focusing on the limitations and modifications required for feeder 111S-311 to supply the Cape Breton Regional Hospital. It outlines conductor replacement and load distribution strategies to stay within operational limits.
8.0 ANALYSIS As noted, there are three alternatives included in this report for sourcing the 12.5 kV primary and secondary circuits to supply the Cape Breton Regional Hospital. Network upgrades required to increase the capacity of the prim...
AI summary The analysis outlines three alternatives for sourcing 12.5 kV circuits to supply the Cape Breton Regional Hospital. NSPI is responsible for network upgrades to increase primary supply capacity, while CBRH is responsible for subsequent secondary supply upgrades.
Disclaimer: These summaries were generated by AI from the filings they describe. We take care to make them accurate, but errors are possible - and they aren't advice. Only the filings themselves are the record: if you're relying on something here, confirm it against the source documents or the Nova Scotia Energy Board's own record. Full disclaimer →