N-1Work Order - Redacted 11 passages
NSEB APPROVAL SHEET p. p. 1
NSEB APPROVAL SHEET Project Title: 92H-331 Double Circuit Peggy's Cove Rd CI Number: C0080102 Date: March 13, 2026 Expenditure Profile Type of Filing Year Budget Amount Project Estimate Capital Project Authorization X 2026 2027 1,704,973 1...

AI summary This document is an NSEB Approval Sheet for the 92H-331 Double Circuit Peggy's Cove Rd project, detailing budget amounts, project estimates, and the type of filing. It includes a capital project authorization and is submitted by Nova Scotia Power Incorporated for approval by the Nova Scotia Energy Board.

Why do this project now? p. p. 1
Why do this project now? Feeder 92H-331 has a winter peak load beyond the 325 Amp, NS Power Capital Expenditure Justification Criteria (CEJC) and has experienced cold load pickup issues, as observed during the February 4, 2024 extreme cold...

AI summary Feeder 92H-331 exceeds NS Power's 325 Amp design criterion, faces cold load pickup issues, and has a 4% annual load growth rate. Adjacent feeders are also over capacity, limiting operational flexibility. A new feeder is proposed to reduce loading, improve voltage, and enhance reliability. The project is deemed in-service after infrastructure upgrades by July 2026, with a Final Cost Date in June 2027.

Contingency Statement p. p. 1
Contingency Statement Contingency for this project has been determined using a combination of internal subject matter expert (professional engineers, capital planner and Power Line Technicians) previous experience and site-specific knowled...

AI summary The contingency for the project is set at 15% based on internal expertise, site-specific knowledge, and non-binding guidelines, classified as a Class 3 estimate. Risks covered include equipment replacement, environmental mitigation, and additional labor requirements.

Execution Year: 2026-2027 p. p. 1
Execution Year: 2026-2027 Description Unit Quantity Unit Estimate Total Estimate Cost Support Reference Completed Similar Projects (FP#'s) Regular Labour Project Management PD 382 $ 452 $ 172,730 Engineering PD 31 $ 452 $ 13,941 Planner/Sc...

AI summary The document outlines cost estimates for a project spanning the years 2026-2027, including labor, materials, contracts, and administrative overhead. It provides detailed breakdowns of expenses for various components such as project management, engineering, environmental measures, and infrastructure-related items, with a total estimated cost of $4,303,210.

Document No: XXX-XX-XXXX-XXXX p. p. 5

AI summary The document section titled 'Capital Project Detailed Estimate' outlines a regulatory proceeding related to capital expenditures in Nova Scotia. It involves the Nova Scotia Energy Board (NSEB) and Nova Scotia Power (NS Power), focusing on financial and regulatory aspects of capital projects.

EXECUTIVE SUMMARY p. pp. 6-7
EXECUTIVE SUMMARY This study evaluates capacity constraints affecting the 92H-Tidewater and 137H-Hammonds Plains substations and identifies capital investments required to maintain compliance with NS Power planning criteria and accommodate...

AI summary This study identifies capacity constraints at 92H-Tidewater and 137H-Hammonds Plains substations, recommending capital investments to meet NS Power planning criteria and accommodate load growth through 2035. Key projects include transformer replacements, new feeders, and the Stillwater Lake substation. These upgrades aim to restore compliance, improve reliability, and address forecasted overloads.

1.0 SCOPE p. pp. 9-11
1.0 SCOPE This study was initiated to address transformer and feeder overloads at the 92H-Tidewater and 137H-Hammonds Plains substations. Both substations have experienced sustained loading above planning criteria during recent winter peak...

AI summary This study addresses transformer and feeder overloads at 92H-Tidewater and 137H-Hammonds Plains substations due to sustained winter peak loading and forecasted residential growth. It evaluates alternatives to meet planning criteria (133% transformer loading, 325 A feeders) and contingency capacity (e.g., mobile transformers, load transfer) over a 15-year period, recommending capital investments to resolve overloads and ensure reliability.

6.1.1 92H-T61 Replacement p. p. 27
6.1.1 92H-T61 Replacement Winter peak load supplied by transformer 92H-T61 significantly exceeds the transformer rating when hydro is unavailable. Replacement with a new 15/20/25 MVA transformer is required. Monitoring limitations, rapid l...

AI summary Transformer 92H-T61 is overloaded during winter when hydro is unavailable, requiring replacement with a larger unit. Temporary solutions like modified hydro dispatch and mobile transformers are insufficient. Alternatives such as load transfers or adding a second transformer are infeasible due to infrastructure constraints and high costs. Replacement remains the only viable long-term solution.

7.1 Estimates p. p. 41
7.1 Estimates Below are preliminary capital cost estimates by year for capital items associated with the alternatives discussed in Sections 6.2 and 6.3. The economic analysis in Section 7.2 will determine the NPV of these alternatives. Tab...

AI summary Preliminary capital cost estimates by year are presented for alternatives discussed in Sections 6.2 and 6.3. These estimates will inform an economic analysis in Section 7.2 to determine the NPV of the alternatives, focusing on capital expenditures and cost considerations.

7.4.2 Hammonds Plains Alternative B: Second Transformer at Hammonds Plains p. pp. 43-44
7.4.2 Hammonds Plains Alternative B: Second Transformer at Hammonds Plains Adding a second transformer at 137H provides additional substation capacity and improves operational redundancy at the existing station. The 137H site was originall...

AI summary Alternative B proposes adding a second transformer at Hammonds Plains to enhance substation capacity and redundancy. While it resolves feeder capacity issues, it introduces reliability risks from long feeders, construction challenges due to heavy development along Hammonds Plains Road, and defers a Stillwater Lake substation until 2032, increasing overall costs. These factors make Alternative B less favorable than Alternative A.

7.5.1 Tidewater Alternative A: Hubley Conversion and Transfer to Stillwater Lake p. p. 45
7.5.1 Tidewater Alternative A: Hubley Conversion and Transfer to Stillwater Lake This alternative converts portions of the Hubley distribution system from 12 kV to 25 kV and transfers this load to the proposed Stillwater Lake substation. T...

AI summary Tidewater Alternative A involves upgrading Hubley's distribution system from 12 kV to 25 kV and transferring load to the Stillwater Lake substation. This reduces Tidewater substation loading, improves reliability via new feeder ties, resolves feeder overloads, and leverages existing infrastructure, making it the lowest-cost, preferred long-term solution.

N-2NSPI (NSEB) RIR-1 to RIR-15 2 passages
1 Request IR-1:
NON-CONFIDENTIAL 1 Request IR-1: 2 3 When does NS Power expect to submit C0071888 92H-T61 Transformer Replacement for 4 Board approval? 5 6 (a) Is approval of this CI contingent on Board approval of the current C0080102 92H 7 331 Double Ci...

AI summary NS Power is responding to a request regarding the submission of a transformer replacement project for Board approval. The response indicates that the project does not require approval of another capital application and that an additional feeder is required to address an overload issue independently.

1 Request IR-11:
NON-CONFIDENTIAL 1 Request IR-11: 1 Request IR-12: 2 3 (a) Most 92H feeders are adjacent to 25 kV feeders supplied from the 137H and 103H 4 substations. Please explain why under Alternative A, NS Power proposes to convert 5 only a portion...

AI summary The document contains a series of requests (IR-11 through IR-12) related to the technical and financial aspects of converting electrical feeders and transformers to 25 kV. The requests focus on feasibility, costs, and specific technical details for various infrastructure changes, with a response beginning for IR-12.

102006Board Decision Letter 2 passages
M12744 - CI C0080102 - Nova Scotia Power Inc. - 92H-331 Double Circuit Peggy's Cove Rd - $4,303,210 p. pp. 0-3
ed that the issue will be resolved by upgrading the transformer using an existing spare unit, which it expects will reduce the overall cost of the transformer replacement project to under $1 million. In response to IR-2 and IR-3, NS Power...

AI summary NSP addresses concerns about the 92H-331 feeder project, stating transformer upgrades using spare units will reduce costs below $1M. It explains load-splitting improves restoration during outages and details delayed overload detection due to rapid load growth and lack of real-time monitoring. A detailed analysis (M-AREA-2025-002) was initiated alongside preliminary design work.

CI Number: C0080102 Date: March 13, 2026 p. p. 3
CI Number: C0080102 Date: March 13, 2026 Expenditure Profile Type of Filing Year 2026 2027 Budget Amount 1,704,973 177,600 Project Estimate 3,798,558 504,652 Capital Project Authorization X Unforeseen and Unbudgeted (U&U) Planned & Advance...

AI summary The document outlines a capital project authorization and related expenditures for Nova Scotia Power Incorporated, with budget amounts for 2026 and 2027, and includes approvals from the Nova Scotia Energy Board.

101247Letter enclosing work order / request for confidentiality 2 passages
Preamble p. p. 0
March 13, 2026 Crystal Henwood Clerk of the Board Nova Scotia Energy Board 1601 Lower Water Street, 3rd Floor Halifax, NS B3J 3S3 Re: Capital Items Filed Outside the Quarter Package Dear Ms. Henwood: Enclosed for your review and approval a...

AI summary A letter dated March 13, 2026, from an unnamed sender to Crystal Henwood, Clerk of the Nova Scotia Energy Board, encloses capital items for review and approval outside the standard quarter package submission process.

2026 ACE Plan Capital Items for Subsequent Approval p. p. 0
2026 ACE Plan Capital Items for Subsequent Approval - CI C0068714 IT Identity & Access Management $6,756,522 2026 ACE amount $4,324,589 $2,478,826 spent as at December 31, 2025 Partially Confidential - CI C0080102 92H-331 Double Circuit Pe...

AI summary The document lists capital items under the 2026 ACE Plan, including project names, allocated funds, and spending status as of December 31, 2025. Items include IT security upgrades, power line installations, turbine refurbishment, and tidal fish passage improvements, with varying confidentiality statuses.

101403NSEB (NSPI) IR-1 to IR-15 4 passages
NOVA SCOTIA ENERGY BOARD
NOVA SCOTIA ENERGY BOARD IN THE MATTER OF: THE PUBLIC UTILITIES ACT - and - IN THE MATTER OF: AN APPLICATION by NOVA SCOTIA POWER INCORPORATED (NS Power) for Subsequent Approval of a Partially Confidential 2026 ACE Plan Capital Item CI C00...

AI summary Nova Scotia Power Inc. (NS Power) seeks subsequent approval under the Public Utilities Act for a partially confidential 2026 ACE Plan capital item related to the 92H-331 Double Circuit Peggy's Cove Rd project. The application involves regulatory approval for a specific infrastructure investment.

Request IR-1:
Request IR-1: - When does NS Power expect to submit C0071888 92H-T61 Transformer Replacement for Board - approval? - a. Is approval of this CI contingent on Board approval of the current C0080102 92H-331 Double Circuit Peggy's Cove Rd capi...

AI summary Request IR-1 seeks clarification on NS Power's timeline for submitting the 92H-T61 Transformer Replacement project for Board approval, whether its approval depends on another capital application (C0080102), and if the latter project is required if the former does not proceed.

Request IR-5:
Request IR-5: - Please provide a table outlining NS Power's cost per meter to construct three-phase feeders over each of the past five years. - a. Please identify the estimated cost per meter to construct the proposed C0080102 92H-331 Doub...

AI summary Request IR-5 seeks NS Power's historical cost-per-meter data for constructing three-phase feeders over five years, the estimated cost for a specific new feeder (C0080102 92H-331), and explanations for discrepancies between historical and projected costs.

Request IR-14:
Request IR-14: NS Power noted that the 92H substation is constructed of wood and is expected to require replacement within the next 10 years due to material deterioration. Further, in Attachment 1, section 6.3.1, NS Power stated the follow...

AI summary NS Power plans to rebuild the deteriorating 92H wooden substation by 2033, using a conservative $7M estimate. Questions focus on load redistribution during rebuilds, rebuild location (existing site vs. nearby land), transformer capacity, construction materials, and cost adjustments if relocation is needed.

102006Board Decision Letter 2 passages
M12744 - CI C0080102 - Nova Scotia Power Inc. - 92H-331 Double Circuit Peggy's Cove Rd - $4,303,210 p. pp. 0-3
ed that the issue will be resolved by upgrading the transformer using an existing spare unit, which it expects will reduce the overall cost of the transformer replacement project to under $1 million. In response to IR-2 and IR-3, NS Power...

AI summary NS Power addresses infrastructure upgrades for feeder 92H-331, citing a transformer replacement cost reduction to under $1M via spare unit use. It explains delayed overload detection due to rapid load growth and lack of real-time monitoring, and clarifies that splitting loads improved restoration outcomes during a 2024 outage. A detailed analysis (M-AREA-2025-002) was initiated alongside preliminary design work to streamline construction.

CI Number: C0080102 Date: March 13, 2026 p. p. 3
CI Number: C0080102 Date: March 13, 2026 Expenditure Profile Type of Filing Year 2026 2027 Budget Amount 1,704,973 177,600 Project Estimate 3,798,558 504,652 Capital Project Authorization X Unforeseen and Unbudgeted (U&U) Planned & Advance...

AI summary This document outlines a capital project authorization and related expenditures for Nova Scotia Power Incorporated, with approval from the Nova Scotia Energy Board. The expenditure profile includes budget amounts and project estimates for the years 2026 and 2027, along with various types of filings and approvals.

Disclaimer: These summaries were generated by AI from the filings they describe. We take care to make them accurate, but errors are possible - and they aren't advice. Only the filings themselves are the record: if you're relying on something here, confirm it against the source documents or the Nova Scotia Energy Board's own record. Full disclaimer →