HomeCost DeferralM03413Evidence
Topic/Matter Intersection

Topic:"Cost Deferral" in M03413

Matter: CI# 39323; CI# 39626; CI# 39627; & CI# 39628 - P-128.10 - NSPI WO - (Digby Wind Project) Application for approval of capital work orders  in the amount of $82.8 million for the acquisition, construction and interconnection of the Digby Wind Farm Project
5 passages 4 documents

Cost Deferral across all matters →

N-3-(b)Redacted NSPI Response to UARB IR-12 (att 7-10) to IR-17 2 passages
Section 2453 p. p. 3
- .2 CSA Standards - .1 C156.1, Ceramic and Glass Station Post Insulators - .2 G164, Hot Dipped Galvanized or Irregularly Shaped Articles - .3 W59, Welded Steel Construction (metal-ark welding) - .3 NEMA Standards - .1 Std. SG-6, Power Swi...

AI summary This document outlines the standards and submittal requirements for electrical components, including CSA, NEMA, ANSI/IEEE, and ISO standards, as well as specifications for operation and maintenance data and manufacturer drawings for disconnect switches.

Section 3458 p. p. 160
- .8 Formwork: - .1 Forms: to CSA-A23.1, plywood and lumber, clean and free of loose knots, splits or metal. - .2 Form Ties: to CSA-A23.1, removable or snap-off metal ties, fixed or adjustable length. Form ties, tie wire, spacers or other...

AI summary The text outlines specifications for formwork and concrete mix, referencing various Canadian standards and testing methods. It details requirements for materials such as form ties, release agents, and curing compounds, as well as specifications for concrete mix proportions and air content.

06537Board Decision 1 passage
VI SUMMARY OF FINDINGS p. p. 0
VI SUMMARY OF FINDINGS [161] In general, the Board finds that the acquisition of the DWP by NSPI from 324 NSL is necessary, subject to a disallowance of a $1 million bonus payment to EUS due to non-compliance with the Code and inadequate e...

AI summary The Board finds that the acquisition of the DWP by NSPI from 324 NSL is necessary, despite non-compliance with the Code in certain aspects. A $1 million bonus payment to EUS is disallowed, and construction costs are reduced. The Board also accepts the economic analysis provided by NSPI and finds the transmission interconnection contract with EUS acceptable.

05500Information Requests IR-1 to IR-20 issued to NSPI by the Consumer Advocate 1 passage
NON-CONFIDENTIAL
NON-CONFIDENTIAL 1 Request IR-5: 2 3 Please explain the meaning of the abbreviation "COPS" in Appendix 2. 4 5 Request IR-6: 6 7 Please explain the nature of the "Thermal & Hydro Contracts AO" in Appendix 2. 8 9 a. overheads, or something e...

AI summary This document contains a series of requests related to the explanation of abbreviations, the nature and derivation of specific cost allocations, and the approval status of methods used in financial calculations for the Digby Wind Project and related projects. The requests focus on overhead allocations, cost computations, and regulatory approvals.

06128Closing Submission - Avon Group 1 passage
CONCLUSION
CONCLUSION If the Board is satisfied with the P50 assumption such that the economic analysis is in favour of this project, then subject to the disallowances recommended, the Avon Group does not object to NSPI's request for approval of thes...

AI summary The Avon Group does not object to NSPI's capital expenditures request if the P50 assumption is valid, but requests a report on its validity, disallowance of the affiliate bonus and $1.5 million contingency, and submission of final costing net of these sums.

Disclaimer: These summaries were generated by AI from the filings they describe. We take care to make them accurate, but errors are possible - and they aren't advice. Only the filings themselves are the record: if you're relying on something here, confirm it against the source documents or the Nova Scotia Energy Board's own record. Full disclaimer →