Topic/Matter Intersection

Topic:"Distribution Planning" in M03624

Matter: CI# 38847 - P-128.10 - NSPI WO - 2010 Distribution Feeder Ties - $531,609
8 passages 3 documents

Distribution Planning across all matters →

N-1Work Order - REDACTED 4 passages
p. p. 1
Project Title: 2010 D istribution Feeder Ti ies CI Number: 38847

AI summary The document references a project titled '2010 D distribution feeder ties' with a CI Number of 38847. It appears to be a regulatory proceeding related to distribution infrastructure planning.

Section 87 p. p. 1
Summary of Related Cl's +/- 2 years No other projects in 2008,2009,2010,2011 and 2012 Cl Number 38847 Distribution Feeder Ties Project Number Parent Cl Number Approved Date Cost Centre 800 - 800-Services - Admin. Budget Version 2010 09/03...

AI summary The text provides a summary of related projects, indicating no other projects were active in the years 2008 to 2012. It references a specific project (Cl Number 38847) related to Distribution Feeder Ties and includes details about a Parent Cl Number, Approved Date, and a Cost Centre with a Budget Version from 2010.

All In 2.5 Beta p. p. 1
All In 2.5 Beta Year Feeder SAIFI SAIDI CAIDI SAIFI SAIDI CAIDI 2007 1V-443 2.92 26.77 9.16 0.84 1.52 1.82 2008 1V-443 9.54 19.27 2.02 8.49 15.91 1.87 2009 1V-443 5.93 32.65 5.50 4.86 29.99 6.17 2007 79V-403 3.85 6.10 1.59 2.83 2.99 1.06 2...

AI summary The document presents data on distribution feeder performance metrics and capital expenditure plans, including variance analysis for 2010. It includes tables with metrics like SAIFI, SAIDI, and CAIDI for various feeders and details on capital expenditures and their variances.

REDACTED p. p. 1
REDACTED 1 Response IR-Dl 1: (cont'd) 2 3 c) Table 1- Breakdown of the Distribution Feeder Ties Cost Estimate.

AI summary The text includes a table labeled 'Table 1 - Breakdown of the Distribution Feeder Ties Cost Estimate' and references a continuing response from IR-Dl. The content is partially redacted and lacks detailed discussion of specific topics or arguments.

N-2Responses to Information Requests IR-1 to IR-8 1/12/2011 3 passages
NON-CONFIDENTIAL p. p. 0
NON-CONFIDENTIAL 1 Request IR-1: 2 3 For each distribution line that was included in the 2010 program please provide the 4 following information: 5 6 (a) The length of each line 7 8 (b) The peak demand loading of each line in MVA 9 10 (c)...

AI summary The document requests detailed information about distribution lines included in the 2010 program, including their length, peak demand loading, design capacity prior to upgrades, and potential load transfer to adjacent feeders.

19 p. p. 0
19 Length Peak Demand Loading Load Design Capacity Prior to Upgrade Transferable Load Capacity Location Line (km) (MVA) (MVA) (MVA) Three Mile Plains 79V-403 70 4.4 10.0 4.4 Avon 1V-443 164 4.0 10.0 0.0 Dartmouth East 113H-434 42 12.0 20.0...

AI summary The document presents a table with details about electrical lines, including their length, load demand, and capacity before and after upgrades. The table includes locations such as Three Mile Plains, Avon, and Dartmouth East, along with line identifiers and capacities.

18 p. p. 0
18 Location Line Length of Line Reconductored (km) Load Capacity Following Upgrade (MVA) Transferable Load Capacity Following Upgrade (MVA) Number of New Switches/Other Devices Added to Provide New Interconnection Points Three Mile Plains...

AI summary The table provides details on power line upgrades in Nova Scotia, including locations, line lengths, load capacities, and new switches added to support interconnection points. The data highlights specific upgrades at locations such as Three Mile Plains, Avon, and Dartmouth East.

06029Information Requests issued by Board Consultants 1 passage
Nancy cn McNeil, egulatory Affairs Officer/Clerk
Nancy cn McNeil, egulatory Affairs Officer/Clerk 1 IR-1: 2 For each distribution line that was included in the 2010 program please provide the following 3 information: 4 a. The length of each line 5 b. The peak demand loading of each line...

AI summary The document contains a series of requests for information related to distribution line upgrades, including details on line lengths, load capacities, cost breakdowns, and labor practices. These requests are part of a regulatory proceeding.

Disclaimer: These summaries were generated by AI from the filings they describe. We take care to make them accurate, but errors are possible - and they aren't advice. Only the filings themselves are the record: if you're relying on something here, confirm it against the source documents or the Nova Scotia Energy Board's own record. Full disclaimer →