Matter: Riverport Electric Light Commission Complaint - Power Poles - Martin and Wendy Tanner
8 passages 2 documents

Distribution Planning across all matters →

T-3Respondents Submission - Strum Report (redacted) 5 passages
(See Clauses 5.7.3.1 to 5.7.3.3.)
(See Clauses 5.7.3.1 to 5.7.3.3.) Minimum clear rance, m To buildings\ † To signs, billboards, lamp, and traffic sign standards, and similar plant Wire or conductor Guys, communication cables, and drop wires Horizontal to surface‡ Vertical...

AI summary The text outlines minimum clearance requirements for electrical conductors and wires relative to buildings, signs, and other structures, with specific measurements depending on voltage levels and installation methods.

(See Rule 36-110 and Appendix B.)
(See Rule 36-110 and Appendix B.) Minimum Areas acce Outdoors 1 Maximum system voltage\ , kV Indoors Light snow Heavy snow area† Areas likely to be travelled by vehicles Not exceeding 15 2.9 3.4 4.0 4.7 25 3.2 3.7 4.3 5.2 34.5 3.2 3.7 4.3...

AI summary The document provides a table outlining the maximum system voltage (in kV) for different voltage levels and conditions, including indoor and outdoor areas with varying snow conditions and vehicle traffic. It also clarifies the definition of maximum system voltage for both grounded and ungrounded systems.

Table 34 Vertical ground clearances for open line conductors\ (See Rules 36-110 and Appendix B.)
Table 34 Vertical ground clearances for open line conductors\ (See Rules 36-110 and Appendix B.) Maximum system voltage†, kV Minimum vertical clearances above ground, m Not exceeding 25.0 6.1 34.5 6.7 46 7 69 7.6 \ See Appendix B.

AI summary Table 34 outlines the minimum vertical ground clearances for open line conductors based on maximum system voltage, referencing Rules 36-110 and Appendix B for additional details.

Preamble
† See Appendix B. † For ungrounded systems, the maximum system voltage is the phase-to-phase voltage, and for grounded systems, it is the phase-to-ground voltage. † For ungrounded systems, the maximum system voltage is the phase-to-phase v...

AI summary The text outlines voltage standards for electrical systems and specifies minimum clearance requirements for overhead distribution conductors from buildings. It references the NSPI 'Overhead Distribution Standard' for safety and compliance.

SECTION - V VOLTAGES AND CLEARANCES
SECTION - V VOLTAGES AND CLEARANCES The difference between maximum conductor final sag and initial sag at the time of construction shall be added to the minimum vertical clearances shown in the chart. Sag tables are included in Section 'C'...

AI summary This section discusses voltage and clearance requirements, emphasizing the addition of conductor sag differences to minimum vertical clearances and the need for additional clearances in areas with large machinery, such as farms and industrial zones.

T-6UTILITY (NSEB) RIR-1 to RIR-7 (redacted) 3 passages
(See Clauses 5.7.3.1 to 5.7.3.3.)
(See Clauses 5.7.3.1 to 5.7.3.3.) Minimum clearance, m To buildings\ † and above- ground pipelines To signs, billboards, lamp, and traffic sign standards, and similar plant Wire or conductor Guys, communication cables, and drop wires Horiz...

AI summary The table outlines minimum clearance requirements for electrical conductors and wires relative to buildings, pipelines, and other structures, with varying distances based on voltage levels and insulation status.

SECTION - V VOLTAGES AND CLEARANCES
SECTION - V VOLTAGES AND CLEARANCES The difference between maximum conductor final sag and initial sag at the time of construction shall be added to the minimum vertical clearances shown in the chart. Sag tables are included in Section 'C'...

AI summary This section discusses voltage and clearance requirements, emphasizing the adjustment of minimum vertical clearances based on conductor sag differences and the need for additional clearances in areas with large machinery, such as farms and industrial zones.

Section 23
To increase the horizontal clearance distance from the 7.2kV conductor to the residence and its protuberances, we recommended that a 32" long epoxy insulator arm be installed on the roadside of the two (2) utility poles closest to the resi...

AI summary To increase the horizontal clearance distance from the 7.2kV conductor to the Tanner Residence, a 32" long epoxy insulator arm was recommended for installation on the two closest utility poles. This installation significantly improved the horizontal and vertical distances from the residence to the conductor, as detailed in the text.

Disclaimer: These summaries were generated by AI from the filings they describe. We take care to make them accurate, but errors are possible - and they aren't advice. Only the filings themselves are the record: if you're relying on something here, confirm it against the source documents or the Nova Scotia Energy Board's own record. Full disclaimer →