2.0 LOCAL SUPPLY 2.1 Substation Figure 2: Substation System Operating Diagram
AI summary The document includes a section titled '2.0 LOCAL SUPPLY' with a subsection '2.1 Substation' and a figure titled 'Substation System Operating Diagram' accompanied by an image.
Function Frequency (Hz) Clearing Time (sec) OF2 > 62 0.16 OF1 > 61.2 300 UF1 < 58.5 300 UF2 < 56.5 0.16
AI summary The table outlines different functions with their corresponding frequencies and clearing times, providing technical data related to system operations. A picture is referenced, likely illustrating additional details not captured in the table.
Table 8: Limits for Rapid Voltage Changes ΔV/ V (%) Occurrences 2.5% ≤ 1 time / hr 2.0% ≤ 5 times / hr 1.0% ≤ 50 times / hr 0.5% ≤ 500 times / hr Dynamic Voltage Changes must be ≤ 2.5% 4.15 Voltage & Current Distortion
AI summary Table 8 outlines the limits for rapid voltage changes, specifying the maximum percentage change (ΔV/ V) and the allowable number of occurrences per hour. It also notes that dynamic voltage changes must not exceed 2.5%. Section 4.15 discusses voltage and current distortion.
Individual Harmonic Order h (Odd Harmonics) Total Demand 2 ≤ h < 11 11 ≤ h < 17 17 ≤ h < 23 23 ≤ h < 35 35 ≤ h ≤ 50 Distortion 4.0% 2.0% 1.5% 0.6% 0.3% 5.0% The Generating Facility must be tolerant of these harmonic distortion levels, whic...
AI summary The table presents harmonic distortion levels for different harmonic orders and total demand. The Generating Facility must be tolerant of these levels, which may be present without harmonics generated by the Interconnection Customer's facility.
REDACTED CI C0083591 Attachment 1 Page 36 of 39 REDACTED (CONFIDENTIAL INFORMATION REMOVED) Title: Reference: Date: Page: DISTRIBUTION EASEMENT AND RIGHT-OF-WAY STANDARD VM-2.01 2004 07 29 5 of 8 1.4 ROW DEVELOPMENT