N-1Redacted Work Order 9/2/2010
6 passages
Project Number 0301 Approved Date 4/20/2010 Parent CI Number Cost Centre 800 800-Services - Admin. Capital Item Justification Justification Criteria: DISTRIBUTION SYSTEM Sub-Criteria: DETERIORATED CONDUCTOR Name of Report : Document Locati...
AI summary This document is a capital item justification report related to the distribution system, specifically addressing deteriorated conductor issues. It includes project number 0301, approved date 4/20/2010, and is associated with cost centre 800-Services - Admin.
3 of 6 1H-403 FEEDER PROFILE Scotia Square / Metro Center Total feeder length 7.8 km (including services) Built 1970's Route Water, Sackville, Granville, Duke, 28H, Barrington, Agryle, Grafton, Market, Brunswick, Cogswell. Installed MVA 23...
AI summary The text provides detailed information about the 1H-403 feeder profile, including its length, construction date, route, interties, load profile, and cable specifications. It also briefly mentions the 1H-405 feeder profile with its total length.
5 of 6 1H-429 FEEDER PROFILE V.G. Hospital Total feeder length 2.2 km (including services) Built 1990's Route Water, Morris, 10H Installed MVA 11.2 Interties with feeders 2H-412 Loops N/A Stepdowns 10H-T1 VG - North Bus Primary services N/...
AI summary The text provides detailed technical profiles of electrical feeders, including their lengths, construction dates, routes, and load profiles for the period ending June 1, 2008. It includes data on underground and overhead feeders, their capacities, and historical load checks from 2004 to 2008.
3.2 CONTINGENCY OPTIONS The following summaries are to give an overview of the available switching options. Contingency A options are only available for feeders with loops and only for the loop part of the feeder. This option is not shown...
AI summary This section outlines contingency options for feeders in the power grid, noting that Contingency A is limited to loop parts of feeders, while Contingency D options are shown only for feeders with limited switching options B and C. Some D-options are not fully displayed due to the complexity of switch combinations.
Table 5.1 Total Feeder Section Lengths [m] Part of Cable 1H Underground Feeders Feeder Size 403 405 419 424 429 431 Radial 750 1780 1440 3430 1600 2200 2130 500 - - - - - - Loop 750 2240 160 - - - - 500 180 - - - - - 350 1550 1380 - - - -...
AI summary Table 5.1 presents detailed data on the lengths of various feeder sections in a power distribution system, categorized by type, size, and specific segments. The table includes radial, loop, tie, and service feeders with different cable sizes and total lengths, both with and without services.
Table 5.5 Materials and Labour for Replacing Primary Service Cables Feeder Cable (refer to feeder profiles 2.2) Accessories (refer to 5.2) Labour (refer to 5.4.1) 1H-403 750 kcmil: 100 x 1.1 x 25 x 3 = $8,250 T: 27 x 3 x 239 = $19,359 LF:...
AI summary Table 5.5 presents detailed cost breakdowns for replacing primary service cables, including materials, labour, and accessories for various feeder types. The table includes calculations for different cable sizes and associated costs, with adjustments for splicing loops and waste.