- .1 stantial completion of the work. - .2 (6) months following delivery to the Place of the Installation. - .2 Owner, through the Engineer, shall promptly give the Vendor notice in writing of observed defects and deficiencies that occur d...
AI summary The text outlines warranty obligations and factory test requirements for electrical equipment, including procedures for reporting defects, correcting issues, and assigning warranties. It also specifies testing standards for circuit breakers, current transformers, and bushings.
- .2 CSA Standards - .1 C156.1, Ceramic and Glass Station Post Insulators - .2 G164, Hot Dipped Galvanized or Irregularly Shaped Articles - .3 W59, Welded Steel Construction (metal-ark welding) - .3 NEMA Standards - .1 Std. SG-6, Power Swi...
AI summary This document outlines the standards and submittal requirements for electrical components, including CSA, NEMA, ANSI/IEEE, and ISO standards, as well as specifications for operation and maintenance data and manufacturer drawings for disconnect switches.
2.1 The overall assembly enclosure(s) shall provide protection from ingress of rodents, insects, and moisture; and the possibility of arcing faults within the enclosure. - 1.12.2 The material for all external sides of the enclosure and int...
AI summary The document outlines technical specifications for the assembly enclosures, including protection against environmental factors, material requirements, grounding provisions, environmental control, and fire suppression capabilities.
9 IN-PLANT INSPECTION AND TESTING - 9.1 The Owner, Purchaser, Engineer, and/or their authorized agents shall have the privilege of inspecting and witnessing all testing at all times during the manufacture of the equipment or materials orde...
AI summary This section outlines the requirements for in-plant inspection and testing during equipment manufacturing, including the right to inspect, advance notice requirements, and the submission of test results to the Engineer.
- .8 Formwork: - .1 Forms: to CSA-A23.1, plywood and lumber, clean and free of loose knots, splits or metal. - .2 Form Ties: to CSA-A23.1, removable or snap-off metal ties, fixed or adjustable length. Form ties, tie wire, spacers or other...
AI summary The text outlines specifications for formwork and concrete mix, referencing various Canadian standards and testing methods. It details requirements for materials such as form ties, release agents, and curing compounds, as well as specifications for concrete mix proportions and air content.
06537Board Decision
3 passages
Submissions - Intervenors [133] Avon commented on the embedded costs in the overall cost of the DWP and their affect on NPV and levelized energy cost: Since the time of the filing, NSPI entered into an Operation Support Agreement with GE,...
AI summary Avon Group comments on the DWP project's embedded costs and their impact on NPV and levelized energy cost. NSPI has updated its costs, but Avon argues that using the PPA's output level results in the original PPA being more economically favorable. The Board acknowledges the use of P50 estimates but does not take a position on whether P50 or P90 should be used for future applications.
Findings [137] The Board has reviewed all the information provided and finds that NSPI customers will benefit by including the Project in the rate base. However, the amount to be included in the rate base requires reduction. The Board unde...
AI summary The Board has reviewed the DWP project and found that including it in the rate base benefits NSPI customers, though the amount requires reduction. The Project is deemed favorable compared to the PPA when considering revised construction costs, O&M savings, and higher energy output. The Board also notes that the economic analysis does not account for infrastructure benefits beyond a 20-year horizon.
contribution is not affected whether the DWP is a NSPI owned asset or developed as an IPP, selling electricity to NSPI under the PPA. [149] No submissions were made on this issue by the Intervenors. [150] The Board finds that, at the prese...
AI summary The document discusses the RES issue and the eligibility of the DWP project for the ecoEnergy incentive. The Board finds no action is required for RES, and confirms the DWP qualifies for the ecoEnergy program, which provides a $10/MWh incentive for eligible renewable projects. The ecoEnergy benefit is included in NSPI's economic analysis and flows through the Fuel Adjustment Mechanism.