GENERATION REPLACEMENT AND LOAD FOLLOWING TARIFF Page 5 of 5 p. p. 37
GENERATION REPLACEMENT AND LOAD FOLLOWING TARIFF Page 5 of 5 - (i.) Utilize dispatchable sources of generation. - (ii.) May have more than one generating unit so long as the aggregate manufacturer's nameplate rating is of not less than 2,0...

AI summary The text outlines the requirements for the Generation Replacement and Load Following Tariff. It specifies that generators must utilize dispatchable sources and may consist of multiple units provided the aggregate nameplate rating is at least 2,000 kilowatts. Customers may choose between existing points of delivery or separate approved points, with the latter incurring additional costs. Furthermore, all facilities must comply with safety and performance standards from Measurement Canada, the Canadian Electrical Code, and NSPI's interconnection guidelines.

SPECIAL CONDITIONS p. p. 37
SPECIAL CONDITIONS - (1) The Port Authority owns and is responsible for the maintenance and operation of all electrical equipment required for the supply of port electricity to docked ships other than the meters and metering transformers s...

AI summary This section outlines the special conditions for port electricity supply, defining the division of responsibilities between the Port Authority and Nova Scotia Power Inc. (NSPI). It specifies that the Port Authority maintains most electrical equipment while NSPI manages meters. Key requirements include the Port Authority providing trained staff for ship connections, submitting a two-year vessel demand schedule, and providing capital contributions for primary metering or special communication systems. It also establishes technical standards for metering, transformer loss adjustments, and minimum power factor requirements.

WHOLESALE MARKET BACKUP/TOP-UP SERVICE TARIFF Page 3 of 6 p. p. 37
WHOLESALE MARKET BACKUP/TOP-UP SERVICE TARIFF Page 3 of 6 The tariff is applicable to the scheduled backup/top-up load of participating customers under the following terms and conditions: - (1) The wholesale customer has provided written n...

AI summary This section outlines the terms and conditions for the Wholesale Market Backup/Top-Up Service Tariff. It specifies the requirements for wholesale customers applying for service, including mandatory details such as contract demand, third-party supply arrangements, and municipal utility identification. The text establishes subscription terms (minimum 12-month annual renewal or three-year forward basis depending on capacity requirements) and sets specific annual deadlines for applications based on the Capacity Contribution Factor (CCF). It also mandates the installation of metering equipment for third-party generators at the generator's expense.

AVAILABILITY p. p. 37
AVAILABILITY This tariff is available for use by, independent non-dispatchable electric generators serving the Wholesale Market. The tariff is applicable to scheduled "spill energy," under the following terms and conditions: - (1) "Spill e...

AI summary This section outlines the availability and terms of a tariff for independent non-dispatchable electric generators serving the Wholesale Market. It specifically governs 'spill energy,' defined as scheduled energy produced in excess of a wholesale customer's hourly requirements. The tariff limits compensation to the supplier's approved Maximum Spill Capacity. Suppliers are required to install company-approved metering equipment at their own expense, in accordance with the Generation Interconnection Agreement.

SPECIAL CONDITIONS p. p. 37
SPECIAL CONDITIONS (1) Suppliers must meet all conditions set forth in the Generation Interconnection Procedures and Generation Interconnection Agreement.

AI summary The document outlines a special condition requiring suppliers to comply with all terms and conditions specified in the Generation Interconnection Procedures and the Generation Interconnection Agreement.

2027 AAR Appendix E1 Page 8 of 8 REDACTED (CONFIDENTIAL INFORMATION REMOVED) p. p. 37
2027 AAR Appendix E1 Page 8 of 8 REDACTED (CONFIDENTIAL INFORMATION REMOVED) WHOLESALE MARKET NON-DISPATCHABLE SUPPLIER SPILL TARIFF Page 2 of 2 - (2) The Company reserves the right to have a separate service agreement, if in the opinion o...

AI summary The text outlines the terms for the Wholesale Market Non-Dispatchable Supplier Spill Tariff. It establishes that the Company reserves the right to enter into separate service agreements to address issues not covered in the current document. Furthermore, it mandates that suppliers must ensure their generation output does not compromise power supply system integrity, with specific requirements to be detailed in the Generation Interconnection Agreement. It lists technical criteria for assessing system integrity, including reliability, harmonic levels, voltage flicker, and stability.

SERVICE DEFINITION p. p. 37
SERVICE DEFINITION Service under this tariff consists in delivery of supplemental power to partial requirement customers who operate their own dispatchable generation equipment, as approved to be connected to the grid by the Company. The S...

AI summary The document defines the 'Service' provided under the tariff for 'customergenerators'—customers who operate their own dispatchable generation equipment connected to the grid. The service comprises three components: Generation Replacement Service (backup power during equipment outages or fuel loss), Optional Load Following Service (top-up energy when generation falls below net operating capability or load), and Spill Service (handling excess generation). Power supplied above customer generation, provided it is not below the established net operating capability, is categorized as supplementary power and billed under the full requirement tariff.

GENERATION REPLACEMENT AND LOAD FOLLOWING TARIFF Page 4 of 5 p. p. 37
GENERATION REPLACEMENT AND LOAD FOLLOWING TARIFF Page 4 of 5 (6) Customers must install metering equipment to monitor the output of the customer's generation. The equipment and installation must be approved by the Company and the costs wil...

AI summary The text specifies a requirement for customers who participate in the Generation Replacement and Load Following Tariff to install metering equipment. This equipment is necessary to monitor the output of the customer's generation. The Company retains the authority to approve the specific equipment and its installation, while the financial responsibility for these costs lies solely with the customer.

Power Factor Constant Power Factor Constant p. p. 37
Power Factor Constant Power Factor Constant 90-100% 1.0000 65-70% 1.1255 80-90% 1.0230 60-65% 1.1785 75-80% 1.0500 55-60% 1.2455 70-75% 1.0835 50-55% 1.3335 (8) Qualifying generating facility must meet the following requirements:

AI summary The document provides a table of constants used to determine the power factor requirements for qualifying generating facilities. It outlines specific constant values corresponding to various power factor ranges, ranging from 50-55% (with a constant of 1.3335) to 90-100% (with a constant of 1.0000). These values are used as technical criteria for qualifying facilities within the regulatory proceeding.

2027 AAR Appendix G1 (redline) Page 5 of 5 REDACTED (CONFIDENTIAL INFORMATION REMOVED) p. p. 37
2027 AAR Appendix G1 (redline) Page 5 of 5 REDACTED (CONFIDENTIAL INFORMATION REMOVED) GENERATION REPLACEMENT AND LOAD FOLLOWING TARIFF Page 5 of 5 - (i.) Utilize dispatchable sources of generation. - (ii.) May have more than one generatin...

AI summary This document excerpt outlines the technical and operational requirements for the Generation Replacement and Load Following Tariff. It specifies that generators must utilize dispatchable sources and meet specific nameplate rating thresholds (minimum 2,000 kilowatts) for multi-unit installations. It also details the customer's options for grid connection points, noting that any costs associated with separate points of delivery are the customer-generator's responsibility. Furthermore, facilities must comply with Measurement Canada, Canadian Electrical Code, and NSPI interconnection guidelines.

SPECIAL CONDITIONS p. p. 37
SPECIAL CONDITIONS - (1) The Port Authority owns and is responsible for the maintenance and operation of all electrical equipment required for the supply of port electricity to docked ships other than the meters and metering transformers s...

AI summary The document outlines special conditions for electricity supply to docked ships at the Port Authority. It defines ownership and maintenance responsibilities for electrical equipment and meters between the Port Authority and NSPI. Key requirements include the Port Authority's obligation to provide trained staff for interconnection, the submission of a two-year vessel demand schedule, and the customer's responsibility for capital costs associated with special metering or primary metering. It also specifies technical requirements for power factor maintenance and transformer loss adjustments.

WHOLESALE MARKET BACKUP/TOP-UP SERVICE TARIFF Page 3 of 6 p. p. 37
WHOLESALE MARKET BACKUP/TOP-UP SERVICE TARIFF Page 3 of 6 The tariff is applicable to the scheduled backup/top-up load of participating customers under the following terms and conditions: - (1) The wholesale customer has provided written n...

AI summary This section outlines the terms and conditions for the Wholesale Market Backup/Top-Up Service Tariff. It specifies the requirements for customers applying for the service, including the need for written notice detailing contract demand, third-party supply arrangements, and municipal utility information. It establishes subscription terms (minimum 12 months or three years for specific capacity types) and sets annual deadlines for applications based on Customer Capacity Factor (CCF) values. Additionally, it mandates the installation of approved metering equipment for third-party generators.

AVAILABILITY p. p. 37
AVAILABILITY This tariff is available for use by, independent non-dispatchable electric generators serving the Wholesale Market. The tariff is applicable to scheduled "spill energy," under the following terms and conditions: - (1) "Spill e...

AI summary The text outlines the terms for a tariff available to independent non-dispatchable electric generators in the Wholesale Market. It specifically addresses the compensation of 'spill energy,' defined as scheduled production exceeding a customer's hourly requirement. Compensation is capped at the supplier's Maximum Spill Capacity, which requires prior approval from NSPI and periodic review. Additionally, it mandates that suppliers bear the costs of installing company-approved metering equipment to monitor generation output.

SPECIAL CONDITIONS p. p. 37
SPECIAL CONDITIONS (1) Suppliers must meet all conditions set forth in the Generation Interconnection Procedures and Generation Interconnection Agreement.

AI summary The document specifies a special condition requiring suppliers to adhere to all requirements outlined in the Generation Interconnection Procedures and the Generation Interconnection Agreement. This ensures that any entity seeking to connect to the grid complies with established technical and procedural standards.

2027 AAR Appendix G6 (redline) Page 2 of 2 REDACTED (CONFIDENTIAL INFORMATION REMOVED) p. p. 37
2027 AAR Appendix G6 (redline) Page 2 of 2 REDACTED (CONFIDENTIAL INFORMATION REMOVED) WHOLESALE MARKET NON-DISPATCHABLE SUPPLIER SPILL TARIFF Page 2 of 2 - (2) The Company reserves the right to have a separate service agreement, if in the...

AI summary This section of the Wholesale Market Non-Dispatchable Supplier Spill Tariff outlines the rights and obligations of the Company and suppliers regarding power supply integrity. It establishes the Company's right to enter into separate service agreements for issues not covered in the primary agreement. Furthermore, it mandates that suppliers ensure their generation output does not negatively impact the power supply system's integrity, with specific requirements to be detailed in Generation Interconnection Agreements, focusing on factors such as reliability, stability, and voltage levels.

Disclaimer: These summaries were generated by AI from the filings they describe. We take care to make them accurate, but errors are possible - and they aren't advice. Only the filings themselves are the record: if you're relying on something here, confirm it against the source documents or the Nova Scotia Energy Board's own record. Full disclaimer →