N-3-(b)Redacted NSPI Response to UARB IR-12 (att 7-10) to IR-17 7 passages
.10 Oil Temperature Gauges p. p. 3
.10 Oil Temperature Gauges - .1 Operational Test - .1 Test each set point and reset point for all winding temperature gauges and record the results. - .2 Record discrepancies between the listed and actual winding temperature gauge settings.

AI summary The document outlines procedures for testing and recording the operational status of oil temperature gauges, specifically focusing on testing set and reset points and documenting discrepancies in winding temperature gauge settings.

.7 Current Transformers p. p. 3
.7 Current Transformers - .1 The manufacturer shall provide one (1) bushing transformer on each Recloser bushing, both load and line side. - .2 All bushing current transformers shall have 5A nominal secondary ratings. - .3 All bushing curr...

AI summary The document outlines specifications for current transformers, including requirements for secondary ratings, primary ratings, relaying accuracy, wiring, and connection ratios.

.5 Accessories p. p. 3
.5 Accessories - .1 Group-Operating Handle (Design "A", "B" and "D" only) - .1 The Contractor shall provide the all necessary operating handle provisions, including pipe, universal joints, bearings, and operator (lockable), such as to prov...

AI summary This section outlines the specifications for the group-operating handle, including requirements for its construction, installation, and compliance with standards. Key elements include grounding terminations, mounting arrangements, sealed bearings, and padlock provisions for safety.

.2 Ratings Nameplates p. p. 3
.2 Ratings Nameplates - .1 The disconnect assembly shall be provided with an external nameplate secured next to the switch gang- operating handle containing the following information: - .1 Manufacturers Name - .2 Switch Type and Designatio...

AI summary The section outlines the requirements for the disconnect assembly's external nameplate, which must include specific information such as manufacturer name, voltage and current ratings, and applicable standards markings.

4.1 General p. pp. 20-21
4.1 General - 4.1.1 Each and every device shall be provided with a clearly visible rating plate and identifying nameplate of weatherproof material, inscribed with the minimum information defined herein. - 4.2 Warning Signs - 4.2.1 All exte...

AI summary This section outlines requirements for rating plates and warning signs on electrical devices, including specifications for nameplates, safety signs, and information to be included on external nameplates as per CSA Standards.

ISO Standards p. pp. 121-122
ISO Standards - .1 ISO 9001 Quality Systems - 1.1.2 Unless otherwise noted, CSA Standards shall be given precedence when and where conflicts arise. - 1.1.3 The Pad Mounted Transformer assembly shall meet all applicable CSA requirements. If...

AI summary The document outlines requirements for ISO 9001 Quality Systems and specifies that CSA Standards take precedence in case of conflicts. It also details the need for compliance with CSA requirements for Pad Mounted Transformer assemblies and the acceptable inspection authorities under the Nova Scotia Electrical Installation and Inspection Act.

4 DOCUMENTATION p. pp. 128-129
4 DOCUMENTATION 4.1 Manufacturers' Drawings - 4.1.1 The Pad Mounted Transformer assembly drawings submitted for review showing assembly, details, and layout showing anchor bolts, openings for cables, and all pertinent support structure loa...

AI summary This section outlines the requirements for manufacturers' drawings, specifically for Pad Mounted Transformer assemblies, including details on assembly, layout, anchor bolts, and component positioning.

Disclaimer: These summaries were generated by AI from the filings they describe. We take care to make them accurate, but errors are possible - and they aren't advice. Only the filings themselves are the record: if you're relying on something here, confirm it against the source documents or the Nova Scotia Energy Board's own record. Full disclaimer →