Topic/Matter Intersection

Topic:"Performance Monitoring" in M04819

Matter: E-ENSC-R-12 - Efficiency Nova Scotia Corporation - Application for Approval of its Demand Side Management (DSM) Plan for 2013 - 2015
118 passages 16 documents

Performance Monitoring across all matters →

E-2Evidence of ENSC as DSM Administrator 11 passages
DATE FILED: February 27, 2012 Page 14 of 45 p. pp. 16-17
DATE FILED: February 27, 2012 Page 14 of 45 1  a management discussion and analysis of any major discrepancies relative 2 to the original plan's intent and forecasts 3  a summary of costs and savings for each program or target market are...

AI summary The document discusses recommendations for evaluating DSM program savings through a revised multi-year process, including ongoing tracking, free ridership surveys, and full-scale evaluations. It also proposes a trigger mechanism to ensure energy savings targets are met and outlines reporting requirements to the UARB and other stakeholders.

The table below summarizes our findings. p. p. 89
The table below summarizes our findings. CRITERIA: PERFORMANCE DRIVERS LATITUDE OVERSIGHT Components No D isin ce nti ve s Inc en tiv es Re so urc es Re sp on siv en es s Ab ilit y t o C om mi t Tra ns pa ren cy Sa feg ua rds Inf lue nc e...

AI summary The table summarizes findings related to oversight and performance drivers for ENSC, highlighting areas such as incentives, resources, and transparency. It notes that ENSC has no sales disincentive, strong reputational incentives, and challenges with long-term commitment and annual approval processes. The section will provide recommendations to address these shortcomings while maintaining current strengths.

CRITERIA: PERFORMANCE DRIVERS p. p. 89
CRITERIA: PERFORMANCE DRIVERS LATITUDE OVERSIGHT Components No D isin ce nti ve s Inc en tiv es Re so urc es Re sp on siv en es s Ab ilit y t o C om mi t Tra ns pa ren cy Sa feg ua rds Inf lue nc e Co st Examples Are profits unaffected by...

AI summary The document evaluates the performance drivers and oversight criteria for Efficiency Nova Scotia (ENSC), focusing on incentives, resources, transparency, and cost considerations. It notes that ENSC has no sales disincentives, has a budget on the higher end of the typical range, and has moved to a 3-year approval process with some long-term predictability still missing.

2.1 TMP plant flowsheets p. pp. 165-170
2.1 TMP plant flowsheets As the TMP plant is the largest electricity consuming operating unit at the FACILITY, we have included simplified process diagrams of the TMP plant in figures 2 through 5 below: - Figure 2 shows line 1 & 2 chip han...

AI summary The TMP plant is identified as the largest electricity-consuming unit at the facility, with simplified process diagrams (Figures 2-5) illustrating its operations, including chip handling, refining, bleaching, and pulp processing. Auxiliary equipment power consumption is noted as approximately 6.0 MW for Lines 1 & 2 and 9.6 MW for Lines 3, rejects refiners, and the bleach plant.

4. EVALUATION PROTOCOL & METHODOLOGY p. pp. 171-172
4. EVALUATION PROTOCOL & METHODOLOGY We have principally relied on the Superior Energy Performance (SEP) measurement & verification protocol found in Appendix-1 in conducting the M&V evaluation. We have relied on this document as it is ver...

AI summary The evaluation uses the Superior Energy Performance (SEP) and IPMVP protocols to validate NPPH's self-reported energy performance data from the INITIAL REPORT. The SEP approach requires two components to assess energy improvements, focusing on verifying preliminary estimates that lacked independent audit.

4.1Measurement Boundaries p. pp. 172-174
4.1Measurement Boundaries The measurement boundary for all projects is the whole mill. Note that the reported refining energy consumption does not include electrical consumption of any auxiliary equipment located within the TMP plant. The...

AI summary The measurement boundary for energy consumption includes the whole mill but excludes TMP plant auxiliary equipment due to lack of metering. Auxiliary consumption (11.5% of TMP load) is deemed negligible (<5% IPMVP threshold). The top-down analysis boundary includes NPPH mill (including PB3), though PB3 may be excluded in the future due to NSPI ownership.

Accuracy p. p. 181
Accuracy The electricity data reported at the whole of mill level is very accurate and has been checked against billing records from NSPI. TMP refining data is taken from motor loads and is time weighted. Paper production data is accurate...

AI summary The document discusses the accuracy of electricity data from NSPI, verified against billing records. TMP refining data is time-weighted, and paper production data is cross-checked by mill staff. However, TMP production data may have a ±10% error due to chip bulk density variability.

6. ANALYSIS OF PROJECT RESULTS p. p. 185
6. ANALYSIS OF PROJECT RESULTS One of the key requirements of the SEP M&V protocol is that top-down energy performance for facilities be calculated and then "sanity-checked" against aggregated bottom-up calculations of individual Energy Co...

AI summary The analysis emphasizes the SEP M&V protocol's requirement to cross-verify top-down energy performance calculations with bottom-up Energy Conservation Measure aggregations, ensuring accuracy in evaluating Nova Scotia's energy efficiency projects.

Section 299 p. pp. 188-191
on function reasonably approximates the actual real world situation. Figure 10 – Scatter plots of actual data vs linear regression model baselines, 3 reporting periods Figure 11 shows the actual reported values vs. those predicted by the m...

AI summary The analysis uses linear regression models to compare actual TMP plant energy consumption data with predicted values, showing the model's accuracy and indicating effective energy management by staff during Year 4. Figures highlight model overestimation and operational ranges, suggesting staff successfully managed energy performance.

8. CONCLUSIONS & RECOMMENDATIONS p. pp. 194-195
8. CONCLUSIONS & RECOMMENDATIONS The top-down electricity savings estimate for the whole mill described in Section-5 of this Report is consistent with the M&V requirements defined in the SEP M&V Protocol and meets all the IPMVP criteria (a...

AI summary The top-down electricity savings estimate for the NPPH mill aligns with SEP M&V Protocol and IPMVP criteria, validating its accuracy. It closely matches the initial report but may overstate savings due to limited bottom-up data. The analysis concludes the top-down method provides a reliable energy savings representation.

MARKETING p. p. 202
MARKETING ENSC will conduct marketing and outreach activities to increase awareness and confidence in Green Heating Systems. Marketing strategies would outline the key green heat systems being offered, their characteristics, as well as the...

AI summary ENSC will implement marketing strategies to promote Green Heating Systems, emphasizing system characteristics, selection factors, and case studies. Materials will encourage a holistic view of home energy performance to build customer confidence.

E-2(r)Revised ENSC Evidence 9 passages
DATE FILED: February 27, 2012 Page 14 of 45 p. pp. 16-17
DATE FILED: February 27, 2012 Page 14 of 45 1  a management discussion and analysis of any major discrepancies relative 2 to the original plan's intent and forecasts 3  a summary of costs and savings for each program or target market are...

AI summary The text discusses recommendations for evaluating and adjusting the Demand Side Management (DSM) program, including the adoption of a trigger mechanism if savings fall below 75% of forecasts and a revised evaluation approach with ongoing tracking, surveys, and reporting to the UARB.

The following table provides an overview of the oversight process we have recommended, while also indicating the extra-regulatory oversight involved. p. p. 90
The following table provides an overview of the oversight process we have recommended, while also indicating the extra-regulatory oversight involved. THREE-YEAR PLAN 2012 2013 2014 2015 2016 Q1 Q2 Q3 Q4 Q1 Q2 Q3 Q4 Q1 Q2 Q3 Q4 Q1 Q2 Q3 Q4...

AI summary The table outlines a recommended oversight process, including regulatory and extra-regulatory activities, with specific actions such as filings, hearings, meetings, and reports over a three-year period from 2012 to 2016, highlighting the sequence dependency of tasks prior to the start of the plan.

CRITERIA: PERFORMANCE DRIVERS p. p. 90
CRITERIA: PERFORMANCE DRIVERS LATITUDE OVERSIGHT Components No D isin ce nti ve s Inc en tiv es Re so urc es Re sp on siv en es s Ab ilit y t o C om mi t Tra ns pa ren cy Sa feg ua rds Inf lue nc e Co st Examples Are profits unaffected by...

AI summary This table discusses the criteria and performance drivers for ENSC (Energy Efficiency Nova Scotia), including components such as incentives, resources, responsiveness, and oversight. It outlines ENSC's current status, proposed changes, and notes on budget, flexibility, and transparency. The table also highlights the regulatory cost and long-term predictability challenges.

CONCLUSION p. pp. 90-108
CONCLUSION The regulatory framework that oversees Efficiency Nova Scotia Corporation includes a number of important strengths, including most notably a culture of focusing on results rather than micromanaging operations. Furthermore, the U...

AI summary The regulatory framework for Efficiency Nova Scotia Corporation (ENSC) emphasizes results over micromanagement, supported by recent UARB flexibility measures. However, the short-term approval process hampers ENSC's ability to engage market actors and meet DSM goals. Proposed solutions include annual reports and triggers to offset longer approval lags, balancing oversight and performance. The UARB retains discretion for unforeseen events.

2.1 TMP plant flowsheets p. pp. 166-171
2.1 TMP plant flowsheets As the TMP plant is the largest electricity consuming operating unit at the FACILITY, we have included simplified process diagrams of the TMP plant in figures 2 through 5 below: - Figure 2 shows line 1 & 2 chip han...

AI summary The TMP plant, the largest electricity consumer at the FACILITY, is detailed through simplified process diagrams (figures 2-5), outlining chip handling, refining, bleaching, and pulp systems. Auxiliary equipment power consumption estimates are provided for TMP lines and bleach plant operations.

4. EVALUATION PROTOCOL & METHODOLOGY p. pp. 172-173
4. EVALUATION PROTOCOL & METHODOLOGY We have principally relied on the Superior Energy Performance (SEP) measurement & verification protocol found in Appendix-1 in conducting the M&V evaluation. We have relied on this document as it is ver...

AI summary The evaluation relies on the Superior Energy Performance (SEP) and International Performance Measurement and Verification Protocol (IPMVP) to assess energy performance improvements at NPPH. The goal is to validate preliminary self-reported energy data from NPPH's INITIAL REPORT, which lacked independent auditing.

4.1Measurement Boundaries p. pp. 173-175
4.1Measurement Boundaries The measurement boundary for all projects is the whole mill. Note that the reported refining energy consumption does not include electrical consumption of any auxiliary equipment located within the TMP plant. The...

AI summary The measurement boundary for projects is the whole mill, excluding TMP plant auxiliary equipment due to lack of metering. Auxiliary consumption (15.6 MW, 11.5% of TMP plant use) is excluded as it varies ±20% but represents <5% of average load, per IPMVP guidelines. The NPPH mill facility (including PB3) is the top-down analysis boundary, with PB3 likely excluded in the future due to NSPI ownership.

Accuracy p. p. 182
Accuracy The electricity data reported at the whole of mill level is very accurate and has been checked against billing records from NSPI. TMP refining data is taken from motor loads and is time weighted. Paper production data is accurate...

AI summary The text discusses the accuracy of electricity and production data, citing checks against NSPI billing records, cross-verification by mill staff, and a ±10% error margin for TMP data due to chip bulk density variability.

Outdoor light bulbs are less common than permanent light bulbs and plug-in lamp bulbs. p. p. 228
Outdoor light bulbs are less common than permanent light bulbs and plug-in lamp bulbs. Nova Scotia residents own an average of only four outdoor light bulbs. Three-quarters of the population have fewer than five outdoor light bulbs (74%)....

AI summary Nova Scotia residents own an average of four outdoor light bulbs, with 74% having fewer than five. Only 20% have five to nine, 5% have 10-19, and 1% have 20 or more. Table A9a provides detailed distribution data.

E-3ENSC 2011 DSM Evaluation Report prepared by Econoler 44 passages
Section 3
TABLE OF CONTENTS 1 DSM PORTFOLIO PERFORMANCE ......................................................................................... 1 1.1 Overview ...........................................................................................

AI summary The document outlines the evaluation of a Demand Side Management (DSM) portfolio, covering performance analysis, achieved savings, and evaluation methodology. It includes sections on process evaluation, interviews, on-site visits, surveys, and impact assessment, concluding with overall recommendations for program improvement.

Section 10
and workplaces. For the 2011 program year, Econoler conducted impact and process evaluations for the following programs. Table 1: Type(s) of Evaluation Conducted per Program Type(s) of Evaluation Program Process Impact Appliance Retirement...

AI summary Econoler conducted impact and process evaluations for multiple programs in 2011, including appliance retirement, low-income initiatives, and energy efficiency measures. The table lists programs evaluated, with some receiving both process and impact assessments.

Section 17
2011 Evaluated 2011 Targets Results DSM PROGRAM GWh MW GWh MW RESIDENTIAL PROGRAMS a Efficient Products 42.89 4.79 49.415 8.912 b EnerGuide for Existing Houses 7.80 2.14 6.375 2.328 c Low Income 9.08 1.98 12.445 2.710 Performance Plus (New...

AI summary The document presents a 2011 evaluation of Nova Scotia's Demand Side Management (DSM) programs, comparing targets and results for residential and commercial/industrial (C&I) initiatives. Residential programs exceeded targets in energy savings (70.69 GWh vs. 62.37 GWh), while C&I programs fell slightly short (71.06 GWh vs. 96.12 GWh). Footnotes clarify program inclusions and exclusions.

Section 20
ated for 2011. Moreover, while some adjustments were applied to the unitary savings estimates used in the tracking sheet, they were in most cases revised upward. Multi-Unit Residential Renter Program The MURR program net evaluated savings...

AI summary Evaluations of 2011 DSM programs show discrepancies between tracked and evaluated savings. The Multi-Unit Residential Renter Program exceeded ENSC-tracked savings by 6%, attributed to revised unitary savings values and interactive effects. Conversely, the Efficient Products – Direct Install Program fell short by 12%, despite upward revisions to evaluation metrics.

Section 39
Efficiency Nova Scotia Corporation ECONOL:R Overall Executive Summary 2.2.5 Impact Evaluation The impact evaluations integrated findings from the telephone surveys, program data from the tracking system, on-site visits and/or interviews wi...

AI summary The impact evaluation of ENSC programs integrated data from surveys, tracking systems, on-site visits, and billing analysis. Methods included metering for ARet/ARep programs and HOT20001 simulations for EEH/Performance Plus/Low Income. Billing analysis for LIR faced limitations due to low participation, though it was recommended for future use to enhance savings verification accuracy.

Section 56
participants or units Objectives monitoring (tracked savings) Data from the program tracking system Objectives realization rate (%) Ratio between targets and tracked savings Business case Details on expected gross and net savings calculati...

AI summary The document outlines key metrics and evaluation criteria for energy efficiency programs, including objectives monitoring, realization rates, business case calculations, and types of evaluations required. It emphasizes factors such as baseline energy levels, technical distortions, free-ridership, and spillover effects in calculating net savings.

Section 67
ERGY STAR criterion and to identify the energy consumption of the appliance would ensure that savings are calculated correctly. 4.1.3 Retail Markdown Program The 2011 evaluation of the RMP demonstrated that the program used the right appro...

AI summary The 2011 evaluation of the Retail Markdown Program (RMP) showed increased participation and significant energy and demand savings. However, awareness of the program and its promotions decreased, with issues like disorganized displays and inadequate marketing materials identified as barriers to effectiveness.

Section 125
r has the following recommendations that aim at optimizing specific aspects of each program: Table 25: Recommendations for the C&IC Program No. Recommendations C&IC-R1. Clearly define the M&V requirements before signing the PDA: The Evalua...

AI summary The document recommends clearly defining Measurement and Verification (M&V) requirements before signing the Project Development Agreement (PDA) for the C&IC Program. It highlights that most projects lack a dedicated M&V plan despite being marked as complete and approved. The Evaluator suggests using M&V plan templates compliant with the International Performance Measurement and Verification Protocol (IPMVP) to standardize M&V activities.

Section 126
ams Efficiency Nova Scotia Corporation ECONOL:R Overall Executive Summary C&IC-R2. Envisage performing third-party M&V for a number of C&IC projects: ENSC should consider performing third-party M&V on projects where the implementation firm...

AI summary The Efficiency Nova Scotia Corporation (ENSC) is advised to consider third-party M&V for C&IC projects where the implementation firm also conducts M&V, to ensure compliance with IPMVP and accuracy of results. A minimum energy savings threshold may be defined to determine when third-party M&V is required.

Section 128
No. Recommendations CINC-R1. Conduct a separate complete evaluation for the CINC program: In 2010, only one new construction project was included in the C&IC program. This project was implemented using a “whole building” approach and its s...

AI summary The document recommends conducting a separate evaluation for the CINC program in 2012 to better assess its impacts and address uncertainties in savings calculations. It also suggests comparing real building consumption with design simulations to improve accuracy in M&V activities.

Section 137
e paper mill in Port Hawkesbury, Nova Scotia. The M&V report was produced by EPS and is titled “Detailed Review of Completed Energy Efficiency Projects at New Page, Port Hawkesbury,” October 17, 2011. The report methodology adhered to the...

AI summary The M&V report evaluated energy efficiency projects at a paper mill in Port Hawkesbury, using the SEP protocol based on IPMVP. The top-down analysis showed 154.2 GWh in energy savings, 26% higher than the bottom-up analysis. The evaluator concluded the savings are a fair representation of the project's impact.

Section 444
Efficiency Nova Scotia Corporation 2011 Evaluation Report should document these parameters so that the PM and the Evaluator can keep track of the assumptions used to estimate the program objectives. Moreover, the parameters should be conti...

AI summary The document outlines recommendations for improving program management and evaluation processes, including documenting parameters, refining marketing plans, and completing the program manual. It also mentions the need for more detailed tracking sheets for program administration and evaluation.

Section 585
he rationale behind the two short periods? Page 10 Q: Who provide the associate training? Q: The delivery agent? Is the same as the implementation contractor? If yes why do we use different names? C: The socket study is a very good initiat...

AI summary The text contains a series of questions and comments from a regulatory proceeding related to the Retail Markdown Program (RMP) and Efficiency Nova Scotia Corporation's 2011 evaluation report. Topics include program activities, customer service, data tracking, evaluation methods, and potential program distortions.

Section 693
list of questions and topics to include in the program partner interviews for the process evaluation was finalized. 2.2.3 In-Depth Interviews with Program Partners Interview with Delivery Agent In September, one in-depth interview was cond...

AI summary The document outlines the methodology used in evaluating the Efficient Products – Low Income Renter Program, including in-depth interviews with the program delivery agent and its subcontractor, as well as on-site visits to validate product installations and savings assumptions.

Section 912
at keeps the records? Q: Do you plan to do a post evaluation cost effectiveness test? Q: since this a new program, did you have an evaluation plan designed at the same time the program was designed? Q: Will there be a detailed program mark...

AI summary The text includes a series of questions from an evaluation process for an energy efficiency program, focusing on program design, evaluation plans, marketing strategies, and database usability. It also provides instructions for completing a questionnaire for program partners.

Section 968
y the DA to the facility manager, such as technical information regarding the use of the products installed through the program. This approach aimed to ensure that program delivery goals would be met. The methodology used for the on-site v...

AI summary The EP-DI program conducted on-site visits and a telephone survey with 70 participants to evaluate program impact and participant experiences, including motivations, barriers, and satisfaction. The survey aimed to understand program features and included data on sampling error.

Section 1080
usion between representative and delivery agent. Page 7 C: Make sure that replaced lamps where functional before replacing them (they were not burned) to get an accurate calculation of the savings. C: Interactive effects will have to be ca...

AI summary The text discusses the Efficient Products – Direct Install Program by Efficiency Nova Scotia Corporation, focusing on program evaluation, delivery agents, quality assurance, and process documentation. It includes questions about program structure, participant forms, barriers addressed, and evaluation plans.

Section 1319
Efficiency Nova Scotia Corporation 2011 Evaluation Report The logic model We proposed a modification for the logic model to include other parties beside ENSC. We sent the modification to the PM for comments. Source: General Q: Please indic...

AI summary The document outlines a process evaluation questionnaire for Efficiency Nova Scotia Corporation's EnerGuide for Existing Houses program, focusing on program partners, evaluation plans, marketing strategies, and data management challenges. It also includes questions about program barriers and cost-effectiveness testing.

Section 1380
ed to validate the new measures implemented, collect information on the previous heating and hot water system as well as gather data on the usage of the different energy sources available at the site. The methodology used for the on-site v...

AI summary The Fuel Substitution Pilot involved on-site visits and a participant survey to evaluate the pilot's impact. The survey, conducted by CRA, aimed to understand participant experiences, motivations, and the pilot's effectiveness. Sampling error data is provided for the 2011 telephone survey.

Section 1489
vities: The Evaluator recommends that outreach activities be monitored with performance indicators to evaluate the effectiveness of each activity in terms of enrolment in the program. Ref.: 5725 8 Low Income Program Efficiency Nova Scotia...

AI summary The Evaluator recommends monitoring outreach activities with performance indicators to assess program effectiveness. The program manual lacks a 'base case' for calculating gross savings and does not document parameters used to estimate program objectives, which should be based on past evaluations and adjusted annually.

Section 1660
ings evaluation, Econoler finally modified a number of energy savings per prescriptive measure used by ENSC, on the basis of national demand-side management (DSM) studies carried out in 2010 and 2011. In its net savings calculations, Econo...

AI summary The evaluation of the Performance Plus program found that free-ridership levels decreased from 79% in 2010 to 32% in 2011, while spillover effects were not significant. Market effects were estimated at 5%, leading to a net-to-gross ratio of 0.73. The program achieved net energy savings of 2.454 GWh and demand savings of 0.861 MW in 2011.

Section 1738
g equivalent weight to both market effect percentages found; i.e., from participating and non-participating builder interviews. The final market effects were therefore evaluated at 5 percent for 2011. In light of the above, Econoler recomm...

AI summary The evaluation of the Performance Plus program in 2011 found that market effects were estimated at 5%, based on interviews with participating and non-participating builders. Econoler recommended increasing the number of interviews in future evaluations to better capture market effects. Net savings were calculated using the interactive effects factors and the Net-to-Gross Ratio (NTGR).

Section 1742
7 0.001 0.026 0.002 0 0.036 0 0.122 N/A N/A N/A (GWh) – at Meter Line Loss Factor 1.105 1.105 1.105 1.105 1.105 1.105 1.105 1.105 N/A N/A N/A Total Net Energy Savings 2.505 0.001 0.029 0.002 0 0.040 0 0.134 N/A N/A N/A (GWh) – at Generator...

AI summary The document presents data on energy savings and demand reductions related to the Performance Plus Program by Efficiency Nova Scotia Corporation, including line loss factors and net-to-gross ratios, and references an evaluation report from 2011.

Section 1744
acked Savings from ENSC 1.560 MW 1.560 MW 0.46 0.717 MW Evaluation Results 1.324 MW 1.180 MW 0.73 0.861 MW As per the last table, the evaluated net energy savings exceeded those tracked by ENSC by more than 80 percent. This is mainly due t...

AI summary The evaluation of the Performance Plus Program by ENSC shows that net energy savings exceeded initial tracking by over 80%, primarily due to adjustments in the house rating baseline and the inclusion of energy and demand savings from efficient lighting. The Net-to-Gross Ratio (NTGR) increased from 0.46 to 0.73, reflecting changes in free-rider evaluation approaches. Demand savings realization was lower at 120% due to adjustments in peak demand savings calculations.

Section 1766
who signs the form, we need to have a box check to identify who is signing this form, the builder or the owner in case we need some clarification or contact that person for evaluation purposes. Assignment of rebate to builder Insert a form...

AI summary The document outlines questions related to the Performance Plus Program by Efficiency Nova Scotia Corporation, including delivery agents, free-ridership, barriers, evaluation processes, and database usability. It seeks insights for process interviews and program evaluation.

Section 1835
tors and Drives category is identified in three different ways. This will facilitate the site sampling process and the savings validation once a systematic validation can be conducted. Ref.: 5725 10 Business Energy Rebates Program Efficien...

AI summary The Business Energy Rebates Program, managed by Efficiency Nova Scotia Corporation, has seen significant growth in participation, with 106 participants in 2011 compared to 13 in the first year. The program was upgraded with streamlined application processes, market push strategies, and free-rider screening. Econoler provided recommendations for further improvements.

Section 1858
rporation 2011 Evaluation Report 4 IMPACT EVALUATION 4.1 OBJECTIVE AND APPROACH OF THE IMPACT EVALUATION The impact evaluation is aimed at determining the gross and net savings of the program for 2011. Both energy and demand savings were c...

AI summary The impact evaluation for 2011 assesses the program's energy and demand savings by analyzing factors such as savings methodology, installation rates, and free-ridership. It involved on-site visits, participant surveys, and interviews to verify data and establish adjustment ratios for energy savings calculations.

Section 1892
rms of net savings. To that effect, the program objectives include any distortion effects, whether positive or negative. They also include interactive effects, when not taken into account in the base case. These parameters are usually base...

AI summary The text discusses the importance of documenting program parameters and refining marketing plans for the Business Energy Rebates program. It emphasizes the need to account for distortion and interactive effects in program objectives and to use performance indicators for monitoring and evaluation.

Section 1914
Efficiency Nova Scotia Corporation 2011 Evaluation Report Q: Please describe who are the program partners and what are their roles. This should guide us in asking the appropriate questions in the process evaluation. (Sales leads, marketing...

AI summary The document contains a series of questions for evaluating the Efficiency Nova Scotia Corporation (ENSC) Business Energy Rebates (BER) program, including inquiries about program partners, design considerations, barriers, evaluation plans, marketing strategies, and database usability. It also includes an interview guide for participants in the program evaluation.

Section 1985
lues for the fields listed above. Nevertheless, these invoices were approved by the PM. The missing information might not be essential for program administration but is useful for evaluation purposes. For each sale, the information in the...

AI summary The evaluation of the Smart Lighting Choices Program highlights that while invoices contain necessary information for rebate administration, additional details such as product specifications are missing. The Program Manager uses product numbers to determine lamp wattage and ballast types for tracking savings. The Evaluator suggests improvements to invoice consistency and program evaluation.

Section 2052
med 25 on-site visits as well as a telephone survey of 27 program participants. The analysis and program evaluation results are presented separately for each of the two C&I Custom program components. PROGRAM OVERVIEW The C&I Custom program...

AI summary The C&I Custom programs offer technical assistance, financial incentives, and project financing to medium and large C&I customers to reduce energy consumption and demand. The C&IC program component, launched in 2008, was upgraded in 2011 with improved staffing, focus on larger projects, and enhanced sales outreach to improve peak demand savings.

Section 2060
rams in the overall executive summary of the 2011 demand-side management (DSM) programs, the Evaluator has the following recommendations that are aimed at optimizing specific aspects of each program: Recommendations for the C&IC Program: C...

AI summary The Evaluator recommends clearly defining M&V requirements for the C&IC Program before signing the PDA, ensuring compliance with IPMVP standards. Templates for M&V plans were introduced in 2011 to standardize activities under the program and assist participants in developing their own plans.

Section 2061
ates should significantly help program participants develop their own M&V plan and is a first step toward standardizing the M&V activities performed under the C&IC program. C&IC-R2. Envisage performing third-party M&V for a number of C&IC...

AI summary The document discusses recommendations for the C&IC program, suggesting that third-party monitoring and verification (M&V) should be used for certain projects to ensure compliance and reduce risk. It also mentions the importance of developing standardized M&V plans for program participants.

Section 2077
g computer-assisted telephone interviewing (CATI). The average length of the survey was 17.5 minutes. The participant survey was used to gain a better understanding of the following program features: > previous program participation; > how...

AI summary The participant survey, conducted via computer-assisted telephone interviewing (CATI), aimed to understand program features such as previous participation, learning sources, spillover effects, motivations, and satisfaction. The survey lasted 17.5 minutes on average. Appendix III and VII provide demographic data and the questionnaire, respectively. Table 3 outlines sample sizes and sampling errors for 2010 and 2011.

Section 2231
Program 13. Develop an evaluation plan in parallel with program design and Design and development: This program has no evaluation plan. The Evaluator strongly Implementation recommends that for each new program, an evaluation plan be prepa...

AI summary The text emphasizes the importance of developing an evaluation plan alongside program design, comparing actual building consumption with simulations for accuracy, and setting performance indicators for project delivery. These steps aim to improve program effectiveness and ensure accurate monitoring and verification.

Section 2232
h when data are available. 15. Set performance indicators on project delivery process: In different sections of the program manual there are references to time limits to perform a given task. With the aim of evaluating project delivery pro...

AI summary The document recommends establishing performance indicators for project delivery efficiency and clarifying minimum requirements for CINC projects to improve compliance and reduce issues during the M&V step. It also suggests providing standardized documentation and examples to assist participants in meeting CPG requirements.

Section 2259
interested in internal procedures. Q: Do you have a participation flow chart that illustrates the different steps for the participants that could be a good support for the program manual writing? Ref.: 5725 80 Commercial & Industrial Custo...

AI summary The text includes questions and comments related to program eligibility, internal procedures, terminology consistency, time limits, and program funding caps in the Commercial & Industrial Custom and New Construction Program. Concerns are raised about free-ridership, clarity of documentation, and potential barriers caused by funding limitations.

Section 2260
cts because of that limitation? Section 4.4.2.2 C: The 85% ratio for incentive of the total program budget seems a very good ratio for a new program. I have to congratulate you if this is the case. Q: I understand that you do not allow red...

AI summary The text includes questions and comments regarding program design, payback periods, commissioning plans, legal reviews, training materials, marketing strategies, program logic models, and potential distortion effects such as free-riders and spillovers. These discussions pertain to the evaluation and structure of the Commercial & Industrial Custom and New Construction Program.

Section 2261
eral Q: is there a program logic model? Q: When the program was initially designed did it include some distortion effects (free-riders, spillover) and were they quantified to establish net savings? Q: Do you perform the cost effectiveness...

AI summary The text contains a series of questions related to the evaluation of the Commercial & Industrial Custom and New Construction Program, including program logic models, distortion effects, cost-effectiveness tests, program partners, evaluation plans, and database usability. It also references an evaluation report and recommendations.

Section 2266
Care to comment? Q: In the appendix A, we count eleven (11) forms for that program. Could that be a reason for any bottleneck in tracking the program data and entering them in a centralized database? C: Custom Client Response Process (afte...

AI summary The text discusses questions raised during a regulatory proceeding regarding program data tracking, methodology appendices, marketing strategies, and program evaluation. It highlights concerns about bottlenecks, missing appendices, and the need for evaluation plans and cost-effectiveness testing.

Section 2270
that use the Whole Building Path Participant in the kick-off meeting with ENSC and the client Site inspections Measurement & Verification (M&V) Design assistance, if needed Other Ref.: 5725 91 Commercial & Industrial Custom and New Constru...

AI summary The text outlines various stages and processes involved in a commercial and industrial energy efficiency program, including kick-off meetings, site inspections, measurement and verification, and design assistance. It also includes a series of questions regarding program verification, commissioning, and relationships with stakeholders such as clients, consultants, and contractors.

Section 2417
in future evaluations. The Evaluator recommends increasing the number of sites where data loggers are installed in order to obtain a more reliable self-declaration ratio. 4.2.3 Installation Rate The installation rate of the program was ass...

AI summary The evaluation of the Small Business Energy Solutions Program highlights the need for more data loggers and on-site visits to improve the reliability of installation and self-declaration ratios. Discrepancies between on-site data and tracking sheets suggest potential issues with reporting and updates.

Section 2458
ng a minimum number of installations? Page 7 Q: If the main objective of ENSC is to save electricity, why are municipal utilities not eligible for the bill financing of 20% like the clients of NSP? Q: What is the proportion (%) of particip...

AI summary The text contains a series of questions raised during a regulatory proceeding regarding the Small Business Energy Solutions Program operated by Efficiency Nova Scotia Corporation. The questions focus on program eligibility, incentive levels, verification processes, and administrative procedures.

Section 2460
satisfaction (say from 1 to 10) for most of the questions instead of a straight yes or no or not sure. C: Replace question # 3, by if the score is under .8, ask for the reason(s). Source: General Q: Could you please describe who the progra...

AI summary The text outlines a process evaluation questionnaire for Efficiency Nova Scotia Corporation's Small Business Energy Solutions Program, aimed at gathering feedback from program partners regarding their roles, program design, barriers, cost-effectiveness testing, marketing strategies, and database usability.

E-5Savings Verification Report of the DSM Administrator's 2011 Demand Side Management Programs 6 passages
Scan America® Goals Statement p. p. 5
Scan America® Goals Statement - Excellence in the integration of knowledge, method, and practice - Improvement and learning at all levels - Contextually sound measurement, analysis, and reporting - Anticipate and meet the needs of our clie...

AI summary Scan America® outlines six core goals emphasizing integration of knowledge and practice, continuous improvement, contextually sound analysis, client-centricity, ethical research awareness, and innovation. The statement reflects organizational priorities in research and service delivery.

I. Executive Summary p. p. 5
I. Executive Summary This report is a savings verification review conducted by H. Gil Peach & Associates, LLC for the Nova Scotia Utility and Review Board (Board). It reports on verification of savings estimated by Econoler, the Independen...

AI summary The report by H. Gil Peach & Associates, LLC for the Nova Scotia Utility and Review Board verifies savings estimates from Econoler for the DSM Administrator's 2011 programs. It reviews evaluation methods, data tracking, and QA/QC processes to recommend adjustments to savings data.

Specific Action Items p. p. 5
rt term metering or by use of usage and billing data from the customer information system), the more valid, stable, intersubjective, transparent and accurate the impact evaluation results. 5 The DSM Administrator or the Evaluator at the di...

AI summary The text emphasizes improving impact evaluation through electrical measurement, passive monitoring, and site visits. It recommends the DSM Administrator to ensure evaluators conduct site visits and implement evaluation improvements. Key stakeholders include the DSM Administrator and Evaluator, with a focus on transparency and accuracy in program assessments.

Recommendation SV9 [Related to Evaluation Recommendation ARet-R3] p. p. 5
nt and Verification Protocol (IPMVP). We recommend that this recommendation not be implemented for 2012. The reasons for not supporting the Evaluator's recommendation in this area are practical. - (1) This program has been excellent in its...

AI summary The text opposes implementing evaluation recommendations for 2012, citing practical concerns. IPMVP is criticized as an imprecise framework, while industrial clients require simple measurement methods. Separating M&V functions for C&IC projects is deemed theoretically sound but potentially disruptive to industry relations.

(14) Commercial & Industrial Custom Program (C&IC) p. p. 5
(14) Commercial & Industrial Custom Program (C&IC) The Commercial and Industrial (C&I) Custom Program was first implemented in the 2008 program year. The program provides financial incentives to large commercial and industrial customers th...

AI summary The Commercial & Industrial Custom Program (C&IC) has been well-managed since 2008, offering incentives for energy efficiency. It uses rigorous data tracking, monitoring, and verification, with free-ridership controlled at 7%. The Evaluator recommends adjusting building simulations and including peak demand savings for accuracy. New construction is included but may become a separate program.

(15) Small Business Energy Solutions Program – SBES p. p. 5
(15) Small Business Energy Solutions Program – SBES The Small Business Energy Solutions Program provides direct installation of energyefficient lighting retrofits to small businesses and includes small government, institutional and health...

AI summary The SBES program offers energy-efficient lighting retrofits to small businesses, with clients covering 20% of costs. Efficiency Nova Scotia funds 80%, and financing options are available. Evaluations recommend improving tracking sheets for better savings validation and collecting more data on heat sources and air conditioning use to enhance impact estimation accuracy.

E-6Net-to-Gross Evaluation Methodology Report with Appendix A - Presentation to PDWG 6 passages
2.4 Custom – Retrofit and New Construction p. p. 13
2.4 Custom – Retrofit and New Construction The Custom program offers incentives and financing for energy efficient equipment including compressed air, industrial processes, refrigeration, motors, lighting and other electrical end-uses. The...

AI summary The Custom program provides incentives and financing for energy-efficient equipment in sectors like industrial processes and lighting. Participation requires a feasibility study and a measurement and verification (M&V) plan. Free-ridership is anticipated to be low due to these process requirements.

Free-Ridership p. pp. 14-15
Free-Ridership A telephone survey is used to gather participant responses related to free-ridership. Participants are considered to be free-riders when they declare they would have installed the efficient products without the incentives an...

AI summary A telephone survey assesses free-ridership by determining if participants would have purchased energy-efficient products without program incentives. Questions focus on purchase quantity, efficiency, timing, and program influence on decisions.

Internal Spillover p. pp. 15-17
Internal Spillover Following their participation, some participants may have bought and installed other energy efficient products promoted by the program. If their decision was influenced by the program raising their awareness of the advan...

AI summary The document discusses measuring 'internal spillover' from a program, where participants may adopt additional energy-efficient products post-participation. Surveys and follow-up calls assess spillover by identifying product types, purchase dates, and program influence on decisions.

EXISTING HOUSES – ENERGUIDE p. pp. 32-34
EXISTING HOUSES – ENERGUIDE - › Spillover will be measured through participant surveys. - › SO will occur when participants decide to implement additional energy efficiency upgrades recommended in their energy audit following their partici...

AI summary The text outlines methods to measure spillover effects (SO) from energy efficiency programs through participant surveys. SO occurs when participants implement additional upgrades post-program. Surveys will identify and quantify SO by tracking implemented upgrades, their dates, and program influence on decisions.

SMART LIGHTING CHOICES p. pp. 44-45
SMART LIGHTING CHOICES - › Free-ridership will be measured through vendor interviews. - › As this program offers rebates at the retail level, only FR will be taken into account as distortion effect. - › In this case, FR corresponds to what...

AI summary The proceeding discusses measuring free-ridership (FR) via vendor interviews for the SMART LIGHTING CHOICES program. Only FR is considered a distortion effect due to retail-level rebates. FR is defined as potential market sales of T8 lamps and electronic ballasts without program implementation.

SMALL BUSINESS ENERGY SOLUTIONS p. pp. 47-48
SMALL BUSINESS ENERGY SOLUTIONS - › Free-ridership will be measured through participant surveys. - › Participants will be considered as FR when they declare that they would have bought the efficient lighting products without the financial...

AI summary The document outlines the method for measuring free-ridership (FR) in the Small Business Energy Solutions program through participant surveys. FR is defined as participants who would have purchased efficient lighting products without the program's financial incentives and free installation. Criteria include purchase intent, product efficiency, timing, and program influence.

E-9(r)ENSC (Consumer Advocate) Responses to IR-1 to IR-27 (REVISED) 4 passages
1 Commercial Sector Econometric Model Detail 2 3 4 5 $COMENG = 0.01906 \ RQTOS + 0.01362 \ RPDI + 0.2685 \ DOMENG + 0.4245 \ COMENG_{-1}$ 6 7 Forecast Model for ComEng 8 Regression(4 regressors, 0 lagged errors) 10 Coefficient Std. Error t-Statistic Percentile 11 ROTOS 0.01906 0.005582 3.414 0.9979 ComEngWA1 0.4245 DomEng 0.2685 RPDI 0.01362 12 0.08265 5.136 1.000 0.04757 5.644 0.004529 3.009 13 1.000 14 0.9942 15 16 17 Within-Sample Statistics 18 No. parameters 4 19 Sample size 30 20 Std. deviation 502.23 Mean 2656.21 Adj. R-square 1.00 Durbin-Watson 2.03 Ljung-Box(18) 13.7 P=0.25 Forecast error 29.91 21 22 23 BIC 34.94 MAPE 0.76% 24 MAD 20.48 p. p. 44
1 Commercial Sector Econometric Model Detail 2 3 4 5 $COMENG = 0.01906 \ RQTOS + 0.01362 \ RPDI + 0.2685 \ DOMENG + 0.4245 \ COMENG_{-1}$ 6 7 Forecast Model for ComEng 8 Regression(4 regressors, 0 lagged errors) 10 Coefficient Std. Error t...

AI summary The Commercial Sector Econometric Model forecasts ComEng using variables like RQTOS, RPDI, DOMENG, and lagged COMENG. The model shows high statistical significance (t-statistics >3.0) and a near-perfect fit (Adj. R-square = 1.00). Forecast accuracy is strong (MAPE = 0.76%, MAD = 20.48), with low residual errors (Durbin-Watson = 2.03).

Industrial Model Input Variables and Contributions p. p. 47
Industrial Model Input Variables and Contributions

AI summary The document examines input variables and their contributions in an industrial energy model, focusing on pricing structures (e.g., ELI 2P-RTP, RQTOS), consumption metrics (DOMENG, COMENG), and statistical methods (Ljung-Box, BIC). Key factors include demand-side management (DSM), income indicators (RPDI), and climate variables (HDD, CHDD).

Figure 4 2009 NSPI Sector Sales p. pp. 70-75
Figure 4 2009 NSPI Sector Sales 13 20 In Province Annual Billed Sales = 11,578 GWh 22 23

AI summary Figure 4 from the 2009 NSPI Sector Sales analysis reports Province Annual Billed Sales of 11,578 GWh. The data is part of a regulatory proceeding examining energy sector metrics, including sales figures and potential correlations with factors like consumer spending and weather patterns.

- 10 numbers refer to the numbers as listed in Appendix I of each evaluation report. p. p. 133
- 10 numbers refer to the numbers as listed in Appendix I of each evaluation report. Efficient Products – Appliance Retirement All tracking sheet recommendations have been implemented through a migration of all projects to the DMS. ENSC is...

AI summary The document discusses the implementation of tracking sheet recommendations by ENSC through migration to the DMS, planning for energy savings indices, and the use of PDA figures for NCWB project savings. It also outlines actions to monitor participant satisfaction, increase data logger installations, and conduct more on-site visits as part of program improvements.

E-11(r)ENSC (Multeese) Responses to IR-1 to IR-11 (REVISED) (REDACTED) 1 passage
upgrades, in the Low Income program. p. p. 8
upgrades, in the Low Income program. 1 Request IR-2: 16  the level of satisfaction of program participants such as energy users and partners 17 (e.g. trade allies, energy auditors , retailers) 18  the scope of issues raised in past impac...

AI summary The text discusses requests and responses related to program evaluations, including participant satisfaction, free ridership, and the derivation of TRC for components of the Efficient Products program. It also references the process used to develop Figure 4.2 and the significance of TRC values.

E-13Navigant RAM Tool Update Report and Cover Letters - April 13, 2012 3 passages
1 Introduction p. p. 4
1 Introduction On March 30, 2012, Efficiency Nova Scotia Corporation (ENSC) identified an error in an IR prepared by Navigant on behalf of ENSC as evidence in NSUARB-E-ENSC-R-12 (the Proceeding). In addressing this error, Navigant subseque...

AI summary Efficiency Nova Scotia Corporation (ENSC) identified an error in a report by Navigant, affecting the Energy Efficiency Resource Assessment Model (RAM Tool) used for ENSC's 2013–2015 DSM Plan. Navigant revised the RAM Tool, addressed systemic errors, and adjusted the Total Resource Cost (TRC) calculation to align with California's approach, which treats free rider incentives as costs. The report outlines error details, revisions, and quality assurance measures.

6 Navigant Energy Practice Model Quality Assurance/Quality Control Policies p. pp. 8-9
6 Navigant Energy Practice Model Quality Assurance/Quality Control Policies It is Navigant's Energy Practice Quality Assurance/Quality Control (QA/QC) policy that all analytic models used for client engagements are subject to an independen...

AI summary Navigant's QA/QC policy mandates independent reviews of analytic models, including the RAM Tool. Despite this, an error in the RAM Tool was not detected during the review, raising questions about the effectiveness of the QA/QC process.

6.2 Changes to Energy Practice Quality Assurance/Quality Control Policies p. p. 9
6.2 Changes to Energy Practice Quality Assurance/Quality Control Policies In light of this incident, Navigant's Energy Practice is currently reviewing its QA/QC policies and the various analytic tools used across the practice with a view t...

AI summary Navigant is revising its QA/QC policies following an incident, proposing changes like using tested modules, enhancing independent reviews, adding multiple reviewers, formal documentation, and exploring alternative modeling software for ENSC. The internal review is ongoing, with confidence in improved QA/QC processes.

E-19ENSC Financial Statements - December 31, 2011 3 passages
Auditor's Responsibility p. p. 2
Auditor's Responsibility Our responsibility is to express an opinion on these financial statements based on our audit. We conducted our audit in accordance with Canadian generally accepted auditing standards. Those standards require that w...

AI summary The auditor's responsibility involves expressing an opinion on financial statements in accordance with Canadian auditing standards. The audit includes procedures to assess material misstatements, evaluate internal controls, accounting policies, and the reasonableness of management's estimates. The auditor concludes that obtained evidence is sufficient for their opinion.

3. FINANCIAL INSTRUMENTS p. p. 3
3. FINANCIAL INSTRUMENTS The Corporation's financial instruments include cash and cash equivalents, accounts receivable, accounts payable and Harmonized Sales Tax ("HST") receivable and payable balances. It is management's opinion that the...

AI summary The Corporation's financial instruments include cash, accounts receivable, and HST balances. Management asserts minimal exposure to interest, currency, or credit risks beyond those in Note 16. All financial assets and liabilities are measured at amortized cost, approximating fair value due to liquidity.

16. RISK MANAGEMENT (Continued) p. p. 3
16. RISK MANAGEMENT (Continued)

AI summary The document section continues the discussion on risk management within a Nova Scotia regulatory proceeding, involving entities such as NSPI, UARB, and CRA. Key topics include cost allocation methodologies and tax considerations, though specific arguments or cited matters are not detailed in the provided text.

E-21Direct Testimony of Paul Chernick (Consumer Advocate) 3 passages
PUBLICATIONS
r Business , Cambridge Energy Research Associates, 1987, pp. 63–72. - "The Relevance of Regulatory Review of Utility Planning Prudence in Major Power Supply Decisions," in Current Issues Challenging the Regulatory Process , Center for Publ...

AI summary A list of publications related to utility regulation, energy economics, and conservation programs. Topics include regulatory review, power plant methodologies, conservation program cost-effectiveness, revenue stability ratemaking, and capacity/energy classifications. Entities include academic institutions, research organizations, and publishers involved in the field.

PRESENTATIONS
bution Companies," District of Columbia Natural Gas Seminar; Washington, D.C., May 23 1989. - "Conservation and Load Management for Natural Gas Utilities," Massachusetts Natural Gas Council; Newton, Massachusetts, April 3 1989. - New Engla...

AI summary The text lists past seminars and presentations on utility regulation topics, including conservation, environmental externalities, rate-making policies, and power plant performance, attended by individuals or organizations involved in energy and regulatory affairs.

EXPERT TESTIMONY
n MP system; historical, current, and projected. Review of MP planning prudence prior to and during excess; efforts to sell capacity. Cost of excess capacity. Recommendations for ratemaking treatment. 63. Massachusetts Division of Insuranc...

AI summary The document outlines regulatory proceedings involving rate-making, risk assessment, and insurance rate calculations. Cases include analysis of underwriting profit margins, cost recovery for conservation programs, and comparisons of risks from power contracts. Topics span Massachusetts insurance regulations, utility pricing, and impacts of the 1986 Tax Reform Act on profit calculations.

E-23Direct Testimony of Tim Woolf (Synapse) 1 passage
Q. How do you recommend the results of your incremental analysis be used? p. p. 24
Q. How do you recommend the results of your incremental analysis be used? - A. Again, I present the incremental rate and bill impact analysis to illustrate how such an analysis could be used in the future to assist with a decision about DS...

AI summary The response recommends using incremental rate and bill impact analyses to inform DSM program funding decisions, improve participation tracking methods, and conduct parallel analyses for BNI sector programs. It emphasizes balancing cost reductions and rate increases, enhancing data accuracy, and targeting under-participating customers.

E-25Evidence of Canadian Oil Heat Association - Nova Scotia 3 passages
18 Q. Please elaborate on why you believe that Programs based on the preliminary p. p. 5
18 Q. Please elaborate on why you believe that Programs based on the preliminary - 19 screening by Dunsky are incorrect. - A. Dunsky concluded that higher emissions of C0 2 and other pollutants made it unlikely to20 - receive government su...

AI summary The respondent challenges Dunsky's preliminary screening, arguing that higher emissions and risks like oil spills and price volatility do not preclude government support for heating oil. Dunsky's assessment of low likelihood for fuel switching is contested.

5 OIL TANK CORROSION p. pp. 11-12
5 OIL TANK CORROSION - 6 Q. ENSC and Dunsky seem to have given some weight to risks associated with oil - 7 tank leakage issues. What does COHA say in response? - A. First, this seems somewhat arbitrary as no other fuel is evaluated for "p...

AI summary COHA-NS responds to concerns about oil tank corrosion risks by highlighting that modern non-corrosive storage systems (fibreglass, resin, double-bottom steel) are now standard. They note that 90% of replaced tanks under their 'Retire Your Tank' program were non-corrosive, supported by CSA-B139.09 regulations banning single-wall steel tanks in Nova Scotia. COHA argues risks from oil leaks are overstated compared to other fuels like natural gas or wood.

Condensing Hydronic Boiler Field Experience p. pp. 44-45
he CO level was 2 ppm, NOx emissions were 109 ppm and the SO2 level was 62 ppm. Figure 21 Condensing boiler at Standfordville, NY site Another located in Walden, New York is shown in figure 22. Temperature data loggers were again installed...

AI summary The text discusses field trials of condensing hydronic boilers at two New York sites, noting improper installation leading to suboptimal efficiency and emissions. Measurements showed varying CO, NOx, and SO2 levels, with efficiency at 90.8% in one case. The sites had complex thermal systems not optimized for condensing operations.

08964Consumer Advocate (ENSC) IR-1 to IR-27 1 passage
1 Request IR-13:
1 Request IR-13: 2 3 Please provide specific examples from each program area where recommendations made by Econoler have or will be implemented. 4 5 Request IR-14: 6 7 Please provide an update on the status of progress regarding developmen...

AI summary The document contains a series of requests directed at Energy Nova Scotia Corporation (ENSC) regarding the implementation of recommendations, progress on evaluation plans, free ridership in the Green Heating Program, program changes to meet energy savings targets, re-evaluation of the Low Income Home target, and the evaluation plan for Enabling Strategies.

08965Avon (ENSC) IR-1 to IR-27 2 passages
3 Request IR-2
3 Request IR-2 - Reference: Econoler Report, February 23, 2012, E-03, p.3, Table 24 - Please include columns to show $ budget, $ actual and TRC tests for each DSM program.5 - (a) Please provide an explanation for any variance of 20% or mor...

AI summary Request IR-2 seeks clarification on DSM program reporting, including budget/actual/TRC test columns, explanations for spending/savings variances exceeding 20%, and actions taken by ENSC. The NSUARB references the Econoler Report (2012) and demands transparency on program adjustments.

22 Request IR-24
22 Request IR-24 - (a) Does ENSC have a "program manager" (or similarly otherwise titled individual)23 - responsible to liaise with each Large Industrial customer with respect to its DSM24 - programs?25 - (b) What, if any, surveys were don...

AI summary The document contains questions directed to ENSC regarding DSM program management, including the existence of a program manager for Large Industrial customers, survey practices for 2013-2015 DSM planning, tracking of BNI program measures by customer class, cost allocation methodologies, and requests for variance analysis of DSM expenditures from 2010-2012. ENSC is also asked about the value of customer engagement in DSM planning.

120092013 Annual Progress Report 1 passage
12 6.3 Traditional Process Evaluation p. p. 0
12 6.3 Traditional Process Evaluation 13 14 The 2013 and 2014 Evaluation will contain a traditional process evaluation. This includes some elements of 15 a management audit, as outlined in the UARB Savings Verification Study, March 2011, p...

AI summary The 2013 and 2014 evaluations include a traditional process evaluation, akin to a management audit but not a full review. Dr. Gil Peach emphasized it focuses on suggesting process improvements and documenting organizational workflows. Key areas assessed include program design, staffing, data tracking, and interdepartmental communication.

120102012 DSM Evaluation Reports 20 passages
1 EVALUATION OBJECTIVES & METHODOLOGY p. p. 8
1 EVALUATION OBJECTIVES & METHODOLOGY

AI summary The section outlines the evaluation objectives and methodology for assessing energy efficiency programs and initiatives. It sets the framework for analyzing program effectiveness, cost recovery, and compliance with regulatory standards.

2 DSM PORTFOLIO PERFORMANCE p. p. 15
2 DSM PORTFOLIO PERFORMANCE

AI summary The section discusses the performance of the Demand-Side Management (DSM) portfolio, likely covering program outcomes, efficiency initiatives, and related metrics under Nova Scotia's regulatory framework.

Table 11: General Recommendations on ENSC Program Manuals p. p. 28
Table 11: General Recommendations on ENSC Program Manuals No. Recommendations OV-R2. Update the program manuals with the most recent information on eligible measures: Program manuals are widely used by the Evaluator throughout the program...

AI summary The document recommends updating ENSC program manuals with the most recent eligible measure information and implementing quality assurance protocols for all programs. These updates aim to improve evaluation accuracy and ensure consistent quality across ENSC initiatives.

3.2.5 Marketing and Outreach Activities p. p. 103
objectives to be achieved, clarify reasonable expectations and, finally, improve the overall execution of the marketing strategy. The Evaluator has the following recommendation on the marketing plan: Make the performance indicators more qu...

AI summary The Evaluator recommends making performance indicators in the marketing plan more quantitative and specific, focusing on the performance of individual marketing strategy tools rather than general program status, and indicating revision dates to ensure ongoing effectiveness.

Table 4: Program Manual Content – Instant Savings p. pp. 0-1
Table 4: Program Manual Content – Instant Savings Program Manual Content 2011 2012 Document revisions 4 4 Program description (including nature or type of program) 4 4 Program justification Δ 4 Program objectives 1 1 Incentives 4 4 Eligibi...

AI summary Table 4 outlines the content of the Instant Savings program manual across different years, detailing sections such as program description, incentives, eligibility, and evaluation plans. It shows the inclusion or absence of various elements in the manual for 2011 and 2012.

3.2.5 Marketing and Outreach Activities p. pp. 64-158
proved contractors for the benefit of participants is being studied in consultation with ENSC trade allies. The marketing strategy implemented can make the difference between a program's success and failure. To assess the effectiveness of...

AI summary The document discusses the importance of quantitative performance indicators in the marketing plan for energy efficiency programs. It highlights that while performance indicators have been integrated since 2011, they should be made more specific and measurable to improve the effectiveness of the marketing strategy and support informed decision-making.

This Appendix presents all recommendations made by the Evaluator throughout the report as well as the sections where the recommendations originated. p. pp. 51-52
This Appendix presents all recommendations made by the Evaluator throughout the report as well as the sections where the recommendations originated. Sections Recommendations Marketing and Outreach Activities 8. Make the performance indicat...

AI summary The appendix outlines a recommendation to enhance the marketing plan by making performance indicators more quantitative and specific, focusing on the effectiveness of individual marketing strategies and including revision dates to ensure ongoing relevance and accuracy.

Table 6: Program Manual Content – Performance Plus p. pp. 148-149
Table 6: Program Manual Content – Performance Plus Program Manual Content 2012 Document revisions Program description (including nature or type of program) Program justification Program objectives Incentives Eligibility criteria Program pa...

AI summary Table 6 outlines the content of the Program Manual for the Performance Plus initiative, detailing sections such as program description, objectives, incentives, eligibility, and evaluation plans. It includes a list of program manual content items for the year 2012, indicating what information is included, partially included, or missing.

CONCLUSION p. pp. 190-192
CONCLUSION The 2012 evaluation of Performance Plus demonstrated that the program underwent a series of changes that altered its design and implementation. Indeed, Performance Plus went from attributing distinctive incentives for every impl...

AI summary The 2012 evaluation of the Performance Plus program showed significant improvements since 2011, including better program design, increased promotion, and higher participant satisfaction. The program saw an increase in participants and achieved higher energy and demand savings. However, program partners noted that more marketing and information on the assessment process were needed.

IN3. On a scale from 1 to 10 (where 1 is very poor and 10 is excellent), how would you rate your satisfaction in regard to the…? p. pp. 0-1
IN3. On a scale from 1 to 10 (where 1 is very poor and 10 is excellent), how would you rate your satisfaction in regard to the…? Aspects of the program Score 1=very poor 10=excellent Reason If you answered 8 or less, please share the reaso...

AI summary The text presents a survey assessing participant satisfaction with various aspects of an energy efficiency program, including program marketing, relationships with ENSC staff, and the assessment process. It includes questions about the appropriateness of the EnerGuide methodology and the need for additional information or changes to the assessment process.

2.2.5 Participant Survey p. pp. 58-59
2.2.5 Participant Survey A telephone survey with a total of 181 program participants was conducted by Econoler's subcontractor, Corporate Research Associates, Inc. (CRA), from its offices in Halifax. The interviews were conducted in Octobe...

AI summary A telephone survey of 181 RDI program participants was conducted in October 2012 by CRA using CATI technology. The survey aimed to gather feedback on spillover, free-ridership, program awareness, participant motivations, satisfaction, and recommendations for improvement. Only non-low-income participants who joined the program since July 2012 were surveyed.

PA2 Score: p. p. 136
PA2 Score: FR4. Level of influence (Scale 0 to 10) Factors a, b and c = Program factors

AI summary The document references the PA2 Score and discusses the Level of influence on a scale from 0 to 10, focusing on Program factors a, b, and c. This appears to be part of a regulatory evaluation or assessment process.

DEFINITIONS p. p. 140
DEFINITIONS Base Case A base case details the information on how assumed gross savings used in the tracking sheet have been established. Usually, these savings are calculated with a series of variables such as hours of operation, wattage o...

AI summary The text defines key terms related to energy efficiency programs, including base case, demand savings, distortion effects, and net-to-gross ratio. It outlines how energy savings are calculated, considering factors like interactive effects and free-ridership.

3.3 TRACKING SHEET p. pp. 159-160
n. The tracking sheet includes a column where some energy savings are calculated by the DA using old energy savings values, but this column is only used for establishing the DA's targeted performance. In the light of these observations, th...

AI summary The tracking sheet is used to calculate energy savings and monitor program performance, but it has issues with incomplete data collection. The Evaluator recommends collecting more detailed installation data and ensuring all fields are systematically filled out for better program evaluation and on-site visits.

4.1 OBJECTIVE AND APPROACH OF THE IMPACT EVALUATION p. pp. 170-174
4.1 OBJECTIVE AND APPROACH OF THE IMPACT EVALUATION The impact evaluation is aimed at determining the gross and net savings of the program for 2012. Both energy and demand savings were examined in this evaluation. To do so, the following p...

AI summary The impact evaluation assesses the gross and net savings of the MURB program for 2012, analyzing unitary savings values, installation rates, and free-ridership. On-site visits and interviews were conducted to validate installation and savings calculations, focusing only on tenant units.

Executive Summary p. p. 192
Executive Summary 3. Collect quantity of products installed in the tracking sheet for each individual tenant unit\ : In 2012, the quantity of products installed in each individual unit was only collected on paper forms from mid-August. In...

AI summary The text discusses recommendations for improving data collection and tracking sheets in energy efficiency programs. It suggests collecting product installation data by unit number instead of tenant names to respect privacy and improve landlord communication. It also recommends enhancing the tracking sheet with additional fields for better evaluation of program impacts and savings.

Marketing and Outreach Activities p. pp. 194-195
Marketing and Outreach Activities 9. Make the performance indicators more quantitative: To make the current performance indicators in the marketing plan more precise, specific and effective, they should be modified to reflect more quantita...

AI summary The text discusses improvements to marketing performance indicators and data collection in a program. It recommends making performance indicators more quantitative, ensuring all fields in the tracking sheet are filled, and collecting additional data such as CFL installation location and heating/air conditioning information for better evaluation.

4.1 OBJECTIVE AND APPROACH OF THE IMPACT EVALUATION p. pp. 100-101
4.1 OBJECTIVE AND APPROACH OF THE IMPACT EVALUATION The impact evaluation for mail-in rebate is aimed at determining the gross and net savings of this component of BER for 2012. Both energy and demand savings were considered in the evaluat...

AI summary The impact evaluation for the mail-in rebate component of the Business Energy Rebates (BER) program in 2012 aimed to determine gross and net savings, considering energy and demand savings. The evaluation involved analyzing parameters such as savings methodology, equipment characteristics, and free-ridership, supported by tracking sheets, 50 on-site visits, and participant surveys.

RECOMMENDATIONS p. pp. 13-101
s during which the facility is closed, or in some cases by taking into consideration that the equipment operates continuously during the peak demand hours. Ref.: 5790 xi Custom-R4. Promote more active and extensive use of the M&V procedure...

AI summary The document recommends promoting the use of M&V procedures for Standard Custom Retrofit projects, emphasizing the importance of conducting M&V on large projects and those with significant energy savings potential. It highlights the need to define M&V procedures early in project planning to ensure accurate baseline data collection.

5.1 OBJECTIVE AND APPROACH OF THE IMPACT EVALUATION p. p. 187
5.1 OBJECTIVE AND APPROACH OF THE IMPACT EVALUATION This Impact Evaluation section aims at determining the gross and net savings of CDI for 2012. Both energy and demand savings are considered in this evaluation. To do so, the following par...

AI summary This section outlines the approach used to evaluate the impact of the Commercial Demand Initiative (CDI) in 2012, focusing on energy and demand savings. Econoler analyzed factors such as unitary savings values, installation rates, interactive effects, and free-ridership, using data from program tracking sheets, literature, on-site visits, and participant surveys to calculate net savings.

Disclaimer: These summaries were generated by AI from the filings they describe. We take care to make them accurate, but errors are possible - and they aren't advice. Only the filings themselves are the record: if you're relying on something here, confirm it against the source documents or the Nova Scotia Energy Board's own record. Full disclaimer →