NON-CONFIDENTIAL 1 Request IR-4: 23 during P61 overloaded planning events involving the N-1 outage of 345 kV line L 24 8002 (which supplies 103H-T81). This violation was found in both the near- and 25 long-term planning horizons. The P6 pl...
AI summary The text discusses a planning event involving the N-1 outage of a 345 kV line (L-8002) and its impact on the power system, including the overload of a transformer and potential solutions such as adjusting corridor flow limits, increasing overload ratings, or adding a new parallel transformer. The transformer involved is critical to the Metro Halifax power supply.