Home›System Reliability›M06319›Evidence
Topic/Matter Intersection

Topic:"System Reliability" in M06319

Matter: P-886 Nova Scotia Power Inc. (NSPI) Rate Application 2007
118 passages 30 documents

System Reliability across all matters →

N-1-aNotice of Application and Direct Evidence - NSPI - REDACTED (Large File - 59 MB) 2 passages
1 7.5.2 Non-Firm Coincident Peak
1 7.5.2 Non-Firm Coincident Peak 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 24 25 26 27 28 29 30 31 32 Certain industrial customers who meet specific criteria may contract to have their electricity supply interrupted on short n...

AI summary The document discusses non-firm coincident peak demand, which refers to electricity that can be interrupted to maintain system stability. It outlines non-firm rate classes, notes that non-firm coincident peaks are typically around 400 MW, and explains that forecasted demand will remain stable unless there are major changes to the rate structure.

23 7.5.3 Total Coincident Firm Peak
23 7.5.3 Total Coincident Firm Peak Total Coincident Firm Peak is the demand at the time of NSPI's system peak that is attributable to all firm (non-interruptible) classes (for example residential, small general, etc.), but excludes the no...

AI summary Total Coincident Firm Peak refers to the demand during NSPI's system peak from non-interruptible customer classes, significantly influenced by weather. NSPI must maintain a 20% planning reserve margin to ensure reliability, with forecasts showing increasing demand, such as from 1,751 MW in 2005 to 2,224 MW in 2015.

N-1-aAppendix H - Proposed Tariffs (Large File - 21 MB) 15 passages
NOVA SCOTIA POWER INCORPORATED
NOVA SCOTIA POWER INCORPORATED LARGE INDUSTRIAL TARIFF (2 000 kV.A or 1 800 kW, and Over) Rate Code 23 - ( 4) The Company reserves the right to have a separate service agreement, if in the opinion of the Company issues not specifically set...

AI summary This section of the Large Industrial Tariff (Rate Code 23) outlines the requirements for high-demand customers (2,000 kV.A or 1,800 kW and over). It establishes the Company's right to enter into separate service agreements for specific issues and mandates that customers must ensure their load does not compromise power supply system integrity. Specific technical factors for assessment include reliability, harmonics, voltage flicker, unbalance, and stability, which will be governed by written operating agreements.

NOVA SCOTIA POWER INCORPORATED
NOVA SCOTIA POWER INCORPORATED LARGE INDUSTRIAL TARIFF (2 000 kV.A or 1 800 kW, and Over) Rate Code 23 - ( 4) The Company reserves the right to have a separate service agreement, if in the opinion of the Company issues not specifically set...

AI summary The text outlines the conditions for Nova Scotia Power Incorporated's Large Industrial Tariff (Rate Code 23) for high-capacity loads (2,000 kV.A or 1,800 kW and over). It specifies that the Company reserves the right to establish separate service agreements for unique issues. Furthermore, it mandates that customers must ensure their load does not compromise power supply system integrity, specifically regarding reliability, harmonics, voltage flicker, unbalance, and stability, as defined in a written operating agreement.

AVAILABILITY:
AVAILABILITY: This rider will be available to a minimum regular billing demand of 2 000 k V .A at 90% Power Factor, under the following terms and conditions: - (1) The customer has provided written notice of his desire to take service unde...

AI summary The text outlines the terms and conditions for a specific service rider requiring a minimum regular billing demand of 2,000 kVA at a 90% Power Factor. Key requirements include written notice from the customer to identify firm and interruptible load portions, a mandate for customers to reduce interruptible load within ten minutes of a request, and specific protocols for service restoration. It also specifies penalty charges for non-compliance and notice periods for converting between firm and interruptible service rates.

NOV A SCOTIA POWER IN CORPORA TED
NOV A SCOTIA POWER IN CORPORA TED LARGE INDUSTRIAL TARIFF (2 000 kV.A or 1 800 kW, and Over) Rate Code 23 (6) Interruption is limited to 16 hours per day and 5 days per week to a maximum of30% of the hours per month and 15% of the hours in...

AI summary The document specifies the interruption limits for customers under the Large Industrial Tariff (Rate Code 23), which applies to loads of 2,000 kV.A or 1,800 kW and over. It establishes that interruptions are restricted to a maximum of 16 hours per day and 5 days per week, further capped at 30% of monthly hours and 15% of annual hours.

SPECIAL CONDITIONS:
SPECIAL CONDITIONS: - ( 1) The Company reserves the right to have a separate service agreement if in the opinion of the Company, issues not specifically set out herein must be addressed for the ongoing benefit of the Company and its custom...

AI summary The text outlines special conditions for electricity supply agreements, emphasizing the Company's right to establish separate agreements for specific customer needs. It mandates that customers ensure their load does not compromise power supply system integrity, covering factors such as reliability, harmonics, voltage flicker, and stability. Additionally, it specifies adjustments to meter readings based on the voltage level of the supply point to account for transformer losses.

LARGE INDUSTRIAL TARIFF
LARGE INDUSTRIAL TARIFF (2 000 kV.A or 1 800 kW, and Over) Rate Code 23 (6) Interruption is limited to 16 hours per day and 5 days per week to a maximum of 30% of the hours per month and 15% of the hours in a year.

AI summary The document specifies the service requirements for the Large Industrial Tariff (Rate Code 23), which applies to customers with a demand of 2,000 kVA or 1,800 kW and over. It outlines specific limitations on service interruptions, restricting them to a maximum of 16 hours per day and 5 days per week, while further capping total annual and monthly interruption percentages to 15% and 30% respectively.

SPECIAL CONDITIONS:
SPECIAL CONDITIONS: - ( 1) The Company reserves the right to have a separate service agreement if in the opinion of the Company, issues not specifically set out herein must be addressed for the ongoing benefit of the Company and its custom...

AI summary The text outlines special conditions for power supply agreements, granting the Company the right to establish separate agreements for specific customer needs. It mandates that customers must ensure their load does not compromise power supply system integrity, with specific requirements to be defined in a written operating agreement. Key technical factors for assessing system integrity include reliability, harmonic levels, voltage flicker, unbalance, load rate of change, stability, and fault levels. Additionally, it specifies adjustments for transformer losses and transmission voltage metering.

1. Priority of Interruptions:
1. Priority of Interruptions: In the event of an interruption for reasons of supply integrity, rate classes will be called upon to provide capacity to NSPI in the following order: - 1. Generation Replacement and Load Following (GRLF) Rate;...

AI summary The document outlines the hierarchy of rate classes that Nova Scotia Power Inc. (NSPI) will contact during power supply interruptions caused by supply integrity issues. The priority order begins with the Generation Replacement and Load Following (GRLF) Rate, followed by the Extra Large Industrial Interruptible Rate, and finally the Interruptible Rider to the Large Industrial Rate. Additionally, it specifies that the Extra Large Industrial Interruptible Rate may be called upon for economic reasons, with calls made equitably to all customers under that specific rate.

2. Causes for Interruption:
2. Causes for Interruption: Interruptions to supply under this rate will be for either Supply or Economic reasons, as defined below. Calls will be made using the process defined in the Terms and Conditions of this rate.

AI summary The document specifies that interruptions to the electricity supply under the current rate structure will occur for two primary reasons: Supply or Economic reasons. It further notes that the specific process for making these calls is governed by the Terms and Conditions of the rate.

Supply Interruptions:
Supply Interruptions: A Supply Interruption is defined as: A request by the Company for the customer to reduce load, when deemed necessary by the Company, in order to avoid shortfalls in electricity supply. APPROVED: NOV A SCOTIA UTILITY A...

AI summary The document provides a formal definition of a 'Supply Interruption' as established by the Nova Scotia Utility and Review Board. It defines the term as a request from the utility company for customers to reduce their electricity load when necessary to prevent shortfalls in the power supply. The definition became effective on January 1, 2006.

Economic Interruptions:
Economic Interruptions: An Economic Interruption is defined as a request by the Company for the customer to reduce load in order for the Company to avoid unnecessarily high costs of electricity supply. For the purposes of Economic Interrup...

AI summary The document defines 'Economic Interruptions' as a mechanism where the Company requests customers to reduce their electrical load to avoid high supply costs. These high costs are specifically identified as those incurred when the Company is forced to dispatch peaking power combustion turbines or purchase import energy to replace the output of peaking power combustion turbines.

4. Advance Notice for Supply Interruptions:
4. Advance Notice for Supply Interruptions: Notification will be given at no less than 10 minutes prior to the starting time of a Supply Interruption of the entire subscribed load or any portion thereof.

AI summary The document specifies the notification requirements for supply interruptions. It mandates that customers must be provided with at least 10 minutes of advance notice before a supply interruption begins, whether the interruption affects the entire subscribed load or only a portion of it.

6. Frequency and Duration of Supply Interruptions:
6. Frequency and Duration of Supply Interruptions: Supply Interruptions will be limited to 16 hours per day and 5 days per week to a maximum of30% of the hours per month and 15% of the hours per year.

AI summary The document specifies the operational limits for supply interruptions. It establishes that interruptions are restricted to a maximum of 16 hours per day and 5 days per week. Furthermore, these interruptions must not exceed 30% of the total hours per month or 15% of the total hours per year.

7. Frequency and Duration of Economic Interruptions:
7. Frequency and Duration of Economic Interruptions: The annual maximum energy that may be called for interruption or buy through under Economic Interruption will be 0.31 GWh per MW of Tariff Demand subscribed under this rate. The frequenc...

AI summary The text outlines the parameters for Economic Interruptions, establishing an annual maximum energy limit of 0.31 GWh per MW of subscribed Tariff Demand. It specifies that the frequency and duration of these interruptions must be mutually agreed upon via a separate agreement, with a minimum duration of three hours per event. If the Company exhausts the customer's apportioned energy, it must invite the customer to participate in additional mutually beneficial interruption opportunities.

SPECIAL CONDITIONS
SPECIAL CONDITIONS - 1. The Company reserves the right to have a separate service agreement if in the opinion of the Company, issues not specifically set out herein must be addressed for the ongoing benefit of the Company and its customers...

AI summary The document outlines special conditions for customers using the rate, emphasizing the preservation of power supply system integrity. It mandates that customers ensure their load does not cause issues such as voltage flicker, unbalance, or stability problems, with specific requirements to be defined in separate operating agreements. Additionally, it grants customers the option to enter into separate agreements with NSPI for special fuel purchase arrangements to influence variable energy costs within the rate formula, subject to UARB approval.

N-1-aAppendix F - Load Forecast Report (Large File - 16 MB) 7 passages
Figure 2 Annual Net System Peak (Winter-ending)
Figure 2 Annual Net System Peak (Winter-ending) - 1 Over the longer term, Net System Peak is forecast to increase from 2143 MW in 2005, to 2639 - 2 MW in 2015, which represents an annual growth rate of2.1 percent. - 4 The actual hourly pea...

AI summary The document presents a forecast of the annual net system peak (winter-ending) for Nova Scotia. It notes a historical growth rate of 2.1 percent from 2005 to 2015. The 2006 actual peak was significantly lower than the 2004 record due to a large industrial customer shutdown and a mild winter. The 2007 forecast assumes a return to 30-year average temperatures and explicitly excludes any load reductions from Demand Side Management (DSM) or conservation programs.

1 Losses
1 Losses 3 System losses have averaged 7.0 percent of NSR over the past five years and are expected to 4 remain in the 7 percent range over the 1 0 year forecast period. 5 2

AI summary The document provides historical and forecasted data regarding system losses. System losses have averaged 7.0 percent of the Net System Requirement (NSR) over the past five years. This percentage is projected to remain within the 7 percent range throughout the upcoming 10-year forecast period.

17 System Losses and Unbilled Sales
17 System Losses and Unbilled Sales 18 19 The load forecast is developed using NSPI "billed" sales rather than "accrued" sales to provide a 20 longer historical time series upon which to base the models. Billed sales refers to the amount o...

AI summary Nova Scotia Power Inc. (NSPI) explains its methodology for developing load forecasts, noting that it utilizes 'billed' sales rather than 'accrued' sales to provide a longer historical time series. The text distinguishes between billed sales, accrued sales, and 'unbilled' sales, which result from billing delays. Additionally, NSPI details system losses, estimating transmission losses at 3.0% of the transmission energy requirement and distribution losses at approximately 6.2% of distribution sales, resulting in an average total system loss of 6.9% of the Net System Requirement (NSR).

9 Net System Requirement
9 Net System Requirement 10 11 The Net System Requirement (NSR) is the energy required to supply the sum of residential, 12 commercial, and industrial electricity sales, plus the associated system losses within the province 13 of Nova Scot...

AI summary The document defines the Net System Requirement (NSR) as the total energy needed to supply residential, commercial, and industrial electricity sales in Nova Scotia, including associated system losses. It specifies that the NSR excludes loads served by industrial self-generation, exports, and transmission losses related to energy exports. The text references Table 5 for the specific annual NSR figures.

26 System Losses and Unbilled Sales
26 System Losses and Unbilled Sales 27 28 This category includes NSPI transmission losses, distribution losses and the year-over-year 29 change in unbilled sales. The annual change in unbilled sales is currently in the order of 14 30 GWh,...

AI summary The text outlines the components of system losses and unbilled sales for Nova Scotia Power Inc. (NSPI). It specifies that transmission losses are forecast at approximately 3.0% of the transmission system energy requirement, while distribution losses are forecast at 6.2% of distribution-level sales. Residential and commercial classes are noted to have higher losses due to lower service voltages. The overall forecast for NSPI losses is an average of 6.9% of the Net System Requirement (NSR). Losses for municipal utilities are excluded from this category and accounted for in their respective municipal rate classes.

5 Peak Demand
5 Peak Demand 6 7 The Total System Peak is defined as the highest single hourly average demand experienced in a 8 year. It includes both firm and interruptible loads and due to the weather-sensitive load 9 component in Nova Scotia, the Tot...

AI summary The document defines the Total System Peak as the highest single hourly average demand in a year, typically occurring between December and February in Nova Scotia due to weather-sensitive loads. It details the methodology for forecasting Net System Peaks, which involves using forecast monthly energies and historical coincident load factors for most rate classes, while individual demand contributions for large customers are assessed based on specific history. The system peak for 2007 is forecast at 2256 MW, with a projected long-term growth rate of 2.1 percent by 2015.

3 Peak Forecast
3 Peak Forecast Year Net System Peak MW Growth % Non-Firm Peak MW Growth % Firm Peak MW Growth % 2000 2009 6.6 412 33.3 1597 1.3 2001 1988 -1 369 -10.4 1619 1.4 2002 2078 4.5 348 -5.7 1730 6.9 2003 2074 -0.2 291 -16.4 1783 3.1 2004 2238 7....

AI summary The document provides a historical overview of peak electricity demand in Nova Scotia from 2000 to 2015. It tracks three distinct categories: Net System Peak MW, Non-Firm Peak MW, and Firm Peak MW. The data illustrates varying growth rates over the 15-year period, with Net System Peak showing significant fluctuations and Firm Peak demonstrating a steady upward trend of approximately 1.3% to 3.1% annually in the early 2000s before stabilizing.

N-2-aRIRs 40 to 69 - NSUARB to NSPI - REDACTED (Large File - 34 MB) 8 passages
Response IR-44: (cont'd)
Response IR-44: (cont'd) Estimated 2008 Initiative Cost (in millions) Vegetation management $ 3.6 Succession planning 1.7 $ HVCA upgrade (Third Party Call Overflow) 2.0 $ Electric Reliability Compliance (NERC, FERC, NPCC) 0.3 $ Relay Testi...

AI summary The document provides a breakdown of estimated costs for several operational initiatives in 2008, totaling $10.6 million. Key expenditures include vegetation management, succession planning, HVCA upgrades, and compliance with reliability standards (NERC, FERC, NPCC). It notes that most of these costs will be subject to escalation factors in subsequent years, with the specific exception of succession planning, which is projected to decrease starting in 2009.

Response IR-47: (cont'd)
Response IR-47: (cont'd) Coincident Losses (MW) Jan Feb Mar Apr May Jun Jul Aug Sep Oct Nov Dec Residential 156.7 130.9 92.0 75.1 71.8 42.0 45.0 37.7 55.1 77.4 102.4 165.3 ETS 3.1 2.5 1.6 1.5 0.8 0.6 0.6 0.3 0.8 0.9 1.6 2.9 Small General 8...

AI summary The document provides a detailed breakdown of monthly coincident losses (in MW) across various electricity customer classes, including Residential, ETS, Small General, Demand, Lg. General, Unmetered, Small, Industrial (Medium and Lg. Ind. Firm), Interrupt., Mersey, GRLF, Municipal, and ELIIR. It explains the methodology for calculating the monthly system peak, which is the sum of peak coincident class sales (derived from monthly sales and coincident load factor) and coincident hourly losses.

Response IR-47: (cont'd)
Response IR-47: (cont'd) Class (MW) Sales Losses Generation Residential 895.1 156.7 1051.8 ETS 16.8 3.1 19.9 Small General 56.4 8.5 64.9 General Demand 411.3 35.1 446.4 Lg. General 56.3 4.0 60.3 Unmetered 17.0 3.2 20.2 Small Industrial 30....

AI summary The document provides a breakdown of electricity sales, losses, and generation by customer class for the year 2007 and specifically for January 2007. It identifies the non-firm coincident peak as the sum of coincident sales and losses for interruptible classes, which include the Large Industrial-Interruptible Rider, GRLF, and ELI 2P-RTP. The data serves to quantify the load profile and system requirements for various residential, industrial, and municipal categories.

Section 193
In the case of actual data for 2005, monthly system peak is determined from the SCADA data. Hourly load data is collected for large customers (greater than 2 MV A), which includes all customers on non-firm rates. The non-firm coincident pe...

AI summary The text describes the methodology used to determine monthly system peak and coincident peak loads for the year 2005 using SCADA data. It explains the process for calculating non-firm coincident peak by summing customer loads on non-firm rates at the hour of the monthly system peak, including estimated losses. Conversely, the firm coincident peak is derived by subtracting the non-firm coincident peak from the total system peak, specifically referencing data from January 2005.

January 2005 Non-firm Classes Load
January 2005 Non-firm Classes Load Lg. Industrial Interruptible Rider 92 GRLF 0 ELIIR 290 Losses 10 Total Non-firm : 392 Note: The figures presented have been rounded.

AI summary The document provides a table detailing the load for various non-firm classes as of January 2005. It specifies load figures for the Large Industrial Interruptible Rider (92), ELIIR (290), and losses (10), resulting in a total non-firm load of 392. The data includes a Grid Reliability Loss Factor (GRLF) of 0 and notes that all figures presented have been rounded.

Response IR-62: (cont'd)
Response IR-62: (cont'd) - c) The amount of funds transferred to the Control Centre was $65,000, associated with the transfer of a Regional Engineer to the Control Centre to be mentored and trained as future Bulk Power System Security Engi...

AI summary The response provides specific financial details regarding operational costs. It identifies a $65,000 expenditure for transferring and training a Regional Engineer into the Control Centre for Bulk Power System Security. Additionally, it notes a $146,000 increase in reactive maintenance costs, primarily attributed to storm-related trouble calls.

Response IR-63:
Response IR-63: - a. The material cost associated with the streetlight repairs are increasing by $30,000 for a total cost of $307,000. - b. The material cost associated with service repairs is increasing by $1,000 for a total cost of$38,00...

AI summary Nova Scotia Power Inc. (NSPI) provides a breakdown of cost increases for streetlight and service repairs. The response specifies that material costs for streetlight repairs are increasing by $30,000 to a total of $307,000, while service repair material costs are increasing by $1,000 to a total of $38,000. NSPI clarifies its responsibility for repairs to the customer's service mast (weather head). Additionally, NSPI justifies its 2007 forecast for system maintenance reactive work, which includes a $199,000 increase in materials based on historical trends and projected work volumes.

Response IR-64:
Response IR-64: - a. The statement indicates that contract costs increased due to spending requirements for the system maintenance group, which employs multiple contractors to perform and assist in specialty work functions. These contracto...

AI summary Nova Scotia Power Inc. (NSPI) explains that contract costs rose because of increased spending requirements for the system maintenance group. This group utilizes various third-party contractors to perform specialty work functions, including excavation, transportation, environmental cleaning, and communication tower services. NSPI notes that these contracts are awarded following the company's standard procurement policies and guidelines.

N-2-bRIRs 70 to 75 - NSUARB to NSPI - REDACTED (Large File - 33 MB) 2 passages
Maintain System Integrity
Maintain System Integrity The customer will make all necessary arrangements to ensure that its load does not unduly deteriorate the integrity of the power supply system, either by its design and/or operation. Specific requirements shall be...

AI summary The customer must ensure their load does not negatively impact the power supply system's integrity. Specific requirements will be outlined in a separate operating agreement, and factors such as reliability, harmonic levels, voltage flicker, and stability will be considered in the assessment.

Maintain System Integrity
Maintain System Integrity The customer will make all necessary arrangements to ensure that its load does not unduly deteriorate the integrity of the power supply system, either by its design and/or operation. Specific requirements shall be...

AI summary The document outlines the customer's responsibility to maintain system integrity by ensuring their load does not negatively impact the power supply system. Specific requirements will be detailed in an operating agreement, with factors such as reliability, harmonic levels, voltage flicker, and fault levels considered in the assessment.

N-2-bRIRs 77 to 84 - NSUARB to NSPI - REDACTED (Large File - 35 MB) 3 passages
2006 Rate Application
2006 Rate Application In July 2005, Nova Scotia Power filed a general rate application requesting an average 15% increase in electricity prices for 2006, primarily a result of rising fuel commodity prices. In November, as a result of benef...

AI summary Nova Scotia Power (NSPI) filed a 2006 general rate application initially requesting a 15% price increase due to rising fuel commodity costs. Following the renegotiation of a natural gas supply contract, NSPI lowered the requested increase to an average of 13%. The application also includes a $19 million request for operating cost increases aimed at enhancing customer service, improving network reliability, and implementing new energy efficiency and conservation measures.

Hurricane Juan
Hurricane Juan In Q3, 2003 Nova Scotia was struck by Hurricane Juan, a Category Two hurricane causing extensive damage to Nova Scotia Power's transmission and distribution system. The total cost of the hurricane to the company was $12.6 mi...

AI summary The document details the financial impact of Hurricane Juan on Nova Scotia Power Inc. in Q3 2003. The Category Two hurricane caused extensive damage to the company's transmission and distribution infrastructure. The total cost incurred by the company amounted to $12.6 million, which is broken down into $4.0 million in net after-tax operating costs recorded in 2003 and $8.6 million in capital costs.

Capacity
Capacity To ensure reliability of service, NSPI maintains a generating capacity greater than firm peak demand. The total company-owned generation capacity to 2,293 MW, which is supplemented by 57 megawatts in service contracted with indepe...

AI summary Nova Scotia Power Inc. (NSPI) manages a generating capacity of 2,293 MW, supplemented by 57 MW of contracted capacity, to ensure service reliability and meet regional planning criteria. The company emphasizes maximizing capacity utilization to improve operating efficiency and defer capital investment. Key strategies include maintaining high asset availability through planned maintenance, managing interruptible loads, and optimizing export sales. NSPI reported a capacity utilization of 78% in 2005, a slight decrease from 2004 due to scheduled turbine inspections.

N-2-bRIR 76 - NSUARB to NSPI - REDACTED (Large File - 46 MB) 7 passages
To My Fellow Shareholders
el procurement process issues. Of course, ma intaining productive regulatory re lationships is an ongoing process, and NSPI wi ll continue to work to understand regulatory expectations, and meet them. These are encouraging developments. Em...

AI summary The text outlines Emera's business performance and growth strategy. It highlights the successful acquisition of the Bear Swamp hydro-electric facility, which contributed $4 million in operating earnings in 2005. It also notes the receipt of a Presidential Permit for Bangor Hydro Electric's Northeast Reliability Interconnect transmission project, a $100 million investment aimed at improving grid reliability and efficiency. Finally, the document mentions the strong performance of Emera's energy marketing business, which generated $24 million in margin in 2005.

Hurricane Juan
Hurricane Juan In Q3, 2003 Nova Scotia was struck by Hurricane Juan, a Category Two hurricane causing extensive damage to Nova Scotia Power's transmission and distribution system. The total cost of the hurricane to the Company was $12.6 mi...

AI summary The text describes the impact of Hurricane Juan, a Category Two hurricane, on Nova Scotia Power's infrastructure during Q3 2003. The storm caused extensive damage to the company's transmission and distribution systems. The total financial impact was $12.6 million, which is broken down into $4.0 million in net after-tax operating costs recorded in Q3 2003 and $8.6 million in capital costs.

2006 Rate Application
2006 Rate Application In July 2005, Nova Scotia Power filed a general rate application requesting an average 15% increase in electricity prices for 2006, primarily a result of rising fuel commodity prices. In November, as a result of benef...

AI summary Nova Scotia Power filed a 2006 general rate application seeking an average 15% price increase, largely driven by rising fuel commodity prices. Following the renegotiation of a natural gas supply contract, the company reduced its requested increase to 13%. The application also includes a request for $19 million in additional operating costs intended to enhance customer service, improve network reliability, and fund new energy efficiency and conservation initiatives.

Capacity
Capacity To ensure reliability of service, NSPI maintains a generating capacity greater than firm peak demand. The total companyowned generation capacity is 2,293 MW, wh ich is supplemented by 57 megawatts in service contracted with indepe...

AI summary Nova Scotia Power Inc. (NSPI) manages a total generating capacity of 2,293 MW plus 57 MW of contracted capacity to ensure service reliability. The company emphasizes maximizing capacity utilization to improve operating efficiency and defer capital investments. Strategies for optimization include maintaining high plant availability, managing interruptible loads to shift demand from peak to off-peak periods, and optimizing export sales. NSPI reports high performance in capacity-related indicators, ranking among the top units in Canada.

open for discussion
open for discussion Electricity is the spark of modern life. Essential to many of the comforts we enjoy, it is also critical to health and well-being, economic growth and development. At Emera, we care about electricity. It is our business...

AI summary Emera outlines its commitment to stakeholder engagement and its role in the evolving energy landscape. The company acknowledges the importance of electricity for health, economic growth, and well-being while recognizing the need to balance rising energy demands and costs with environmental goals. Emera emphasizes a collaborative approach, seeking dialogue with customers, regulators, and industry partners to address challenges related to service reliability, renewable energy, and conservation.

Getting Connected The Northeast Rei iabi I ity Interconnect
Getting Connected The Northeast Rei iabi I ity Interconnect Reliability, stability and power quality ... combined with reasonable rates, these elements create a robust electrical system. Bangor Hydro is committed to building a strong syste...

AI summary Bangor Hydro discusses its commitment to electrical system reliability, stability, and power quality through the Northeast Reliability Interconnect (NRI). The NRI is a 345 kV transmission line between Maine and New Brunswick designed to support economic development. The company emphasizes a collaborative, multi-stakeholder approach to environmental protection and route selection for the project. Additionally, the text briefly mentions a customer's participation in a Nova Scotia Power forum regarding residential energy efficiency.

Trenton Unit 6 Receives Top Honours
Trenton Unit 6 Receives Top Honours Nova Scotia Power's outstanding operational performance continued in 2005. For the second year in a row, an NSPI generating unit was recognized as the top performing plant in Canada. The Canad ian Electr...

AI summary Nova Scotia Power Inc. (NSPI) received national recognition for its operational excellence in 2005. The Canadian Electricity Association (CEA) named the Trenton Unit 6 generating unit as the top-performing plant in Canada due to its high capacity factor, operating at capacity for over 98 percent of the year. Additionally, four other NSPI units were ranked among the top ten thermal plants in the country, highlighting the utility's strong performance in electricity generation.

N-2-bRIRs 1 to 26 - AEC to NSPI - REDACTED (Large File - MB) 1 passage
How does power get restored?
How does power get restored? Our goal is to restore service to the largest number of affected customers first. First, we check the overall system, repairing damage to power plants, high voltage transmission lines and substations so we have...

AI summary Nova Scotia Power Inc. outlines its prioritized strategy for restoring electrical service following a power outage. The process begins with system-wide repairs to power plants, high-voltage transmission lines, and substations to establish a power supply. Priority is then given to critical services (hospitals, fire, police), followed by high-density housing and large neighborhoods to maximize the number of customers restored quickly. Finally, repairs are directed toward small groups and individual customers.

N-2-dRIR 40 to 75 - CA to NSPI - REDACTED (Large File - 23 MB) 1 passage
9/29/2004
9/29/2004 0 111 100 Key Performance Indicators 2003YE 100 100 2002 YE W 16 3-Y ear A verage Measure Pg# Mean 1st Q N= NSPI Qt Mean 1st Q N= NSPI Qt Mean 1st Q N= NSPI Qt Pg# Cost = 50% of Score; Mathematical Weighting: 50%/(10 /20)=1.000 l...

AI summary The document presents key performance indicators for Nova Scotia Power Inc. (NSPI) in 2003 and 2002, including metrics related to transmission and distribution costs, reliability, and safety. These metrics are evaluated based on scoring criteria, with cost accounting for 50% of the score, reliability 40%, and safety 10%.

N-2-dRIRs 1 to 46 - CME to NSPI - REDACTED (Large File - 18 MB) 4 passages
RESPONSE TO INFORMATION REQUEST
RESPONSE TO INFORMATION REQUEST TO: NSPI FROM: CME Question IR-26: Reference Page 113, Lines 22-39 Provide a breakdown of costs experienced over the years by NSPI that have increased costs outside of property damage that was not insured. A...

AI summary Campbell Scott Management (CME) is responding to an Information Request (IR-26) from the Utility and Rate Board (UARB) regarding Nova Scotia Power Inc. (NSPI). The response focuses on identifying costs incurred by NSPI due to weather events that were not related to uninsured property damage. Additionally, it seeks to outline NSPI's risk management strategies and specific measures implemented to mitigate risks associated with weather-related impacts on the grid.

Examples of costs incurred by NSPI that were weather related and not insured include the following:
Examples of costs incurred by NSPI that were weather related and not insured include the following: • Hurricane Juan (September 2003) $6.0 million • Ice storm (November 2004) $2.8 million • Wind storm (November 2005) $1.7 million • Snow/wi...

AI summary Nova Scotia Power Inc. (NSPI) provided a list of historical weather-related costs that were not covered by insurance. These include costs from Hurricane Juan (2003), an ice storm (2004), and wind and snow storms in 2005. In all instances, the expenses incurred by the company exceeded the amounts provided for in the approved rates, resulting in the company bearing the additional costs directly.

Preamble
In order to mitigate weather related risks, NSPI designs, operates and maintains the system within good utility practices. NSPI has also presented to the UARB a report that recommends increased spending on the NSPI Distribution Vegetation...

AI summary Nova Scotia Power Inc. (NSPI) maintains the distribution system in accordance with good utility practices to mitigate weather-related risks. NSPI submitted a report to the Utility and Rate Board (UARB) recommending increased investment in the Distribution Vegetation Management program specifically aimed at storm hardening the system.

Strengths:
Strengths: - A supportive regulatory environment with cost-of-service regulation mitigates most operating risks. - A dominant industry position due to monopoly service franchise, geographic isolation, and limited interconnections presently...

AI summary The document outlines the strengths of the utility's current operating position. It highlights a supportive regulatory environment that mitigates operating risks and a dominant market position secured by a monopoly franchise and geographic isolation. Additionally, the text notes that market capacity exceeds demand and that the company possesses sufficient operating cash flows to support maintenance-oriented capital expenditures over the next three to five years.

N-2-gRIRs 30 to 91 - SEB to NSPI - REDACTED (Large File - 29 MB) 1 passage
FOR THE YEAR ENDING DECEMBER 31, 2007
FOR THE YEAR ENDING DECEMBER 31, 2007 (1) (2) ENERGY (3) (4) CLASS NON- (5) SYSTEM (6) SYSTEM (7) DEMAND (8) SYSTEM (9) SYSTEM MWH LINE ENERGY COINCIDENT COINCIDENT COINCIDENT LINE COIN. PEAK COINCIDENT SALES LOSSES REQUIREMENT DMD. (KW) F...

AI summary This table presents energy sales, losses, and demand data across various customer classes for the year ending December 31, 2007. It includes metrics such as energy requirement, system losses, demand factor, and load/demand factor for different categories of users, including domestic, industrial, and municipal.

N-2-gRIRs 1 to 25 - Stutz to NSPI - REDACTED (Large File - 18 MB) 1 passage
Rationale
NSPI's regulated businesses see the credit report on Emera Inc., published Sept. 1, 2005, on RatingsDirect, Standard & Poor's Web-based credit research and analysis system, at www.ratingsdirect.com.) The ratings on Halifax, Nova Scotia-bas...

AI summary Nova Scotia Power Inc. (NSPI) highlights the creditworthiness of its parent company, Emera Inc., citing its vertically integrated utility operations in Nova Scotia and Maine. The text emphasizes that 95% of Emera's cash flow and assets are derived from regulated utility operations with a stable residential and commercial customer base. Key factors supporting this stability include regulated cash flows, relatively flat operating costs since 2002, and reliable transmission and distribution performance, despite limited organic growth in mature markets.

N-7-aRIRs 85 to 104 [105 to 107 (Filed 03/05/2007)] - NSUARB to NSPI - REDACTED 1 passage
Response IR-98:
Response IR-98: - a. The Net Operating Capability as used in reliability studies is the 2,283 MW within the accuracy noted. - b. The 1.3 MW is the installed capacity.

AI summary The response outlines the Net Operating Capability as 2,283 MW and the installed capacity as 1.3 MW, as noted in reliability studies.

N-7-bRIRs 19 to 22 - MEUNSC to NSPI - REDACTED 1 passage
RESPONSE TO INFORMATION REQUEST
RESPONSE TO INFORMATION REQUEST TO: NSPI FROM: MEUNSC Question IR-19: NSPI's demand billed rates make no provision for anomalous situations which may create demand spikes (examples: cold load pick up, capacitor failure). Can the words "sub...

AI summary Nova Scotia Power Inc. (NSPI) opposes adding the phrase "subject to any correction for anomalies" to its demand-based tariffs. NSPI argues that its current ratcheted demand charge is already designed to recover costs associated with winter peak demands and send price signals to large customers. The company contends that phenomena like cold load pick-up are understood industry effects rather than "anomalies" and notes that the Board previously declined to order rate changes regarding this specific issue in a 2005 proceeding.

N-7-bRIRs 142 to 143 - SEB to NSPI - REDACTED (Large File - 45 MB) 3 passages
Operational Excellence
Operational Excellence - CEA ranks Point Tupper #1 and Lingan Unit 3 #2 on thermal operating performance - Operating excellence enables high utilization - Capacity managed with surgical capital additions and incentives to shift peak load

AI summary The document highlights the operational performance of specific assets, noting that the CEA ranks Point Tupper as #1 and Lingan Unit 3 as #2 for thermal operating performance. It emphasizes that operational excellence is a key driver for high utilization. Furthermore, it describes a strategy for managing capacity through targeted capital additions and the use of incentives to shift peak load.

Listening to Customers
Listening to Customers - Increased investment in conservation - Increased vegetation management to improve reliability - Customer service initiatives - CEO "on the line" explaining request to customers - UARB improving process with "Issues...

AI summary The document highlights a series of customer-centric initiatives and commitments being presented during the regulatory proceeding. Key themes include increased investment in energy conservation, improved vegetation management for system reliability, and enhanced customer service initiatives. Notably, the CEO is actively engaging with customers to explain requests, and the Utility Advisory Review Board (UARB) is refining its process using an 'Issues List' to better address customer concerns.

Re-investing in Key Transmission
Re-investing in Key Transmission - Stranded cost recovery provides pool of capital to reconfigure BHE's asset base - Focus on transmission investments - "Northeast Reliability Interconnect" will provide second U.S. / Canada link in northea...

AI summary The text outlines a strategy for re-investing in key transmission infrastructure by leveraging stranded cost recovery to reconfigure the BHE asset base. Key projects include the 'Northeast Reliability Interconnect,' a $110M investment intended to create a second U.S./Canada link to improve reliability and facilitate cross-border electricity sales during offsetting peak seasons. Additionally, the text highlights successful permitting as a strategic strength and identifies further investment opportunities ranging from $70M to $200M in other Maine transmission projects.

N-40RIRs Attachment SEB-NSPI - 4a (Large File - 40 MB) 1 passage
Attachment SEB-NSPI-4a
Attachment SEB-NSPI-4a Name of Respondent - (556) System Control and Load Dispatching The state of the state of the state of the state of the state of the state of the state of the state of the state of the state of the state of the state...

AI summary The provided document is a table fragment titled 'Attachment SEB-NSPI-4a' listing a respondent for 'System Control and Load Dispatching'. The text contains a significant amount of repetitive 'state of the state' filler text and includes numerical values, but it does not contain substantive arguments, qualitative analysis, or meaningful narrative information regarding the regulatory proceeding.

N-40RIRs Attachment SEB-NSPI - 2a, pt. 1 (Large File - 22 MB) 10 passages
CHARACTER OF SERVICE
CHARACTER OF SERVICE Three-phase service directly from the Company's 44 kV or higher transmission system (transmission) or distribution lines (primary). Three phase service at the secondary voltage of transformation facilities supplied fro...

AI summary The text defines the 'Character of Service' regarding three-phase electricity delivery from the Company's infrastructure. It specifies that service can be provided directly from the transmission system (44 kV or higher) or distribution lines (primary), as well as from transformation facilities at secondary voltages. Additionally, it establishes a capacity limitation, stating the Company is not required to serve loads exceeding 20,000 kVa of capacity, unless supplied from transmission facilities of 115 kV or higher.

SEASONAL CAPACITY
SEASONAL CAPACITY Additional capacity, hereinafter referred to as "seasonal capacity," can be supplied on a year-toyear basis during the billing months of October through May provided the Consumer gives a minimum of two months written noti...

AI summary The document defines 'seasonal capacity' as additional capacity provided on a year-to-year basis during the October through May billing months. To obtain this capacity, consumers must provide the Company with at least two months' written notice, subject to the Company's determination of availability. The Company reserves the right to suspend delivery during system emergencies and is not obligated to construct additional facilities to meet seasonal capacity demands.

Issued: November 1, 2006
Issued: November 1, 2006 Fuel Cost Rider 60 in Rates Fuel Adjust. Jan '06 Apr '06 Jui'06 Oct '06 ./ $ 0.014484 $ 0.000232 0 014484 ,~-<~?~f-=t. £.~ 0.014484 0.001052 J 0.007713/ 0.014484 Average 0.002307/ ._l_u_Rc_14_-_o_u_K_E_E_N_ER_G_Y_I...

AI summary This document provides a quarterly rider update for Keen Energy Services for the first and second quarters of 2006. It lists specific monetary adjustments for various riders, including Fuel Rider 60, Qualified Pollution-Rider 62, Emission Allowance Riders, DSM On-Going Expenses, Midwest ISO Management Cost and Revenue Adjustment, Summer Reliability Adjustment, and Clean Coal Operating Cost. The data is broken down by specific customer classes (RS, cs, LLF, HLF, TS) and specifies effective dates for the adjustments.

Standard Contract Rider No. 67 Recovery of Preapproved Purchased Power Costs to Meet Retail Customer Peak Load Requirements (Purchased Power Tracker)
Standard Contract Rider No. 67 Recovery of Preapproved Purchased Power Costs to Meet Retail Customer Peak Load Requirements (Purchased Power Tracker) ALLOCATED SHARE OF SYSTEM PEAK DEMAND FOR THE COMPANY'S RETAIL CUSTOMERS, BY RATE GROUP A...

AI summary The document introduces Standard Contract Rider No. 67, which outlines the mechanism for recovering preapproved purchased power costs required to meet retail customer peak load requirements. It specifically references the allocation of the system peak demand for the Company's retail customers, broken down by rate group and wholesale electric customers. These figures are expressed as a percentage of the system peak demand developed in Cause No. 42359, based on data from the summer months of 2002.

STANDARD CONTRACT RIDER NO. 70 SUMMER RELIABILITY ADJUSTMENT APPLICABLE TO ALL RETAIL RATE SCHEDULES
STANDARD CONTRACT RIDER NO. 70 SUMMER RELIABILITY ADJUSTMENT APPLICABLE TO ALL RETAIL RATE SCHEDULES Estimated Summer Reliability Factor Per kWh Line to be Applied to Customer Line No. Rate Groups Bills No. (A) RateRS $0.000385 2 Rates CS...

AI summary The document outlines Standard Contract Rider No. 70, which establishes a Summer Reliability Adjustment applicable to all retail rate schedules. It provides specific estimated summer reliability factors per kWh for various rate groups, including residential, commercial, and industrial customers, as well as specific industrial entities like NUCOR and Air Liquide. The adjustment became effective during the first billing cycle of November 2006.

STANDARD CONTRACT RIDER NO. 70 SUMMER RELIABILITY ADJUSTMENT APPLICABLE TO ALL RETAIL RATE SCHEDULES
STANDARD CONTRACT RIDER NO. 70 SUMMER RELIABILITY ADJUSTMENT APPLICABLE TO ALL RETAIL RATE SCHEDULES ALLOCATED SHARE OF COINCIDENT SYSTEM PEAK DEMAND APPLICABLE TO COMPANY'S RETAIL CUSTOMERS, BY RATE GROUP, AND WHOLESALE ELECTRIC CUSTOMERS...

AI summary The document introduces Standard Contract Rider No. 70, which establishes a Summer Reliability Adjustment applicable to all retail rate schedules. It specifies the allocation of the coincident system peak demand share for both retail and wholesale electric customers. These allocations are expressed as percentages of the coincident system peak demand developed in Cause No. 42359, specifically focusing on the four-month period from June through September 2002.

RJDER IS (NC) INTERRUPTIBLE POWER SERVICE
RJDER IS (NC) INTERRUPTIBLE POWER SERVICE Available at the Company's option to non-residential customers receiving concurrent service from the Company on Schedules G, GA, I, GT, IT, or OPT who are not served under Rider SCG. Under this Rid...

AI summary The document describes the RJDER IS (NC) Interruptible Power Service, a provision available to non-residential customers on specific schedules (G, GA, I, GT, IT, or OPT) who are not under Rider SCG. Under this rider, customers agree to reduce and maintain their load at specified levels upon the Company's request. The Company reserves the right to request service interruptions at any time during capacity problems, subject to the terms of individual contracts.

3. Control Notices and Limitations:
3. Control Notices and Limitations: The Customer shall be notified of all initiations of Interruption Periods at least thirty (30) minutes prior to such times, and the Customer shall fully comply with the Company's requests to reduce and m...

AI summary This section outlines the operational requirements and limitations for the RJDERIS(NC) Interruptible Power Service. It mandates that the Company provide customers with at least 30 minutes' notice before initiating an Interruption Period. Customers are required to maintain their load within the Firm Contract Demand during these periods. The Company is limited to 150 hours of interruptions annually, with a daily maximum of 10 hours unless a mutual agreement for extension is reached with the customer.

RIDER IS (SC) INTERRUPTIBLE POWER SERVICE
RIDER IS (SC) INTERRUPTIBLE POWER SERVICE Available at the Company's option to non-residential customers receiving concurrent service from the Company on Schedules G, GA. I, GT, IT, OPT, or PG. Under this Rider the Customer agrees, at the...

AI summary The text describes the 'Rider IS (SC) Interruptible Power Service,' which is an optional service available to non-residential customers on various rate schedules (G, GA, I, GT, IT, OPT, or PG). Under this rider, customers agree to reduce and maintain their electrical load at specified levels upon the Company's request. The Company reserves the right to interrupt service at any time when capacity problems occur, subject to the specific provisions of the individual contract.

I . General Provisions:
I . General Provisions: Contracts for interruptible power service will be accepted by the Company on the basis of successive contracts, and each contract shall specify an interruptible, integrated demand of not more than 50,000 KW to be su...

AI summary The text outlines the general provisions for interruptible power service contracts. The Company will accept successive contracts with an integrated demand limit of 50,000 KW per contract, capped at a total of 1,100,000 KW across all nonresidential schedules. Customers may opt to apply the rider only to submetered portions of their load. The Company reserves the right to conduct annual tests of the rider's provisions with advance notice, and continued service is contingent upon satisfactory customer performance during requested interruptions.

N-40RIRs Attachment SEB-NSPI - 2a, pt. 4 (Large File - 19 MB) 8 passages
AVAILABILITY
AVAILABILITY This Rider is available on a voluntary basis in conjunction with Company's Large General Service and Large General Service (Time-of-Use) Schedules for electric service used by a nonresidential customer provided Customer contra...

AI summary The text outlines the availability and eligibility criteria for a specific Rider related to large nonresidential electric service. The Rider is voluntary and applies to customers with contracts of at least 1,000 kW on Large General Service or Large General Service (Time-of-Use) Schedules, specifically for loads subject to curtailment. It is capped at a total system curtailable load of 300,000 kW and is explicitly excluded for short-term or temporary service.

4. CURTAILABLE PERJOD
4. CURTAILABLE PERJOD The Curtailable Period shall be an eight-hour period unless Company specifies a shorter period at the time the Customer is notified. Customer shall be given a minimum of 30-minutes notice before requested curtailment...

AI summary The text defines the parameters for the 'Curtailable Period,' which is generally an eight-hour window during which the Company may request a Customer to reduce their energy requirements. Customers must receive at least 30 minutes of notice. The Company distinguishes between Capacity Level 1 (where firm energy purchases are anticipated) and Capacity Level 2 (where firm energy purchases are not anticipated) curtailments. The Company's determination of the level is binding, and it is not liable if notice is not received despite using reasonable diligence. Annual capacity curtailment is capped at 400 hours.

4. CURTAILABLE PERIOD
4. CURTAILABLE PERIOD The Curtailable Period shall be an eight-hour period unless Company specifies a shorter period at the time Customer is notified. Customer shall be given a minimum of 30-minutes notice before RIDER-58E Sheet 1 of3 requ...

AI summary The text defines the 'Curtailable Period' for customers under RIDER-58E, establishing an eight-hour maximum duration per 24-hour period, with a total annual cap of 400 hours. Customers must receive at least 30 minutes' notice before requested curtailments. The Company distinguishes between Capacity Level 1 and Level 2 curtailments based on the availability of reserves and firm energy purchases. The Company's determination of the curtailment level is binding, and it is not liable for missed notifications if reasonable diligence is exercised.

Force Majeure
Force Majeure The Company shall not be subject to any liability or damages for inability to provide service, and the Customer shall not be subject to any liability or damage for such inability to receive service, to the extent that such in...

AI summary This section of the tariff defines the 'Force Majeure' provisions for the Large General Service Transmission Delivery (Time of Use - 1,000 KW and Over) schedule. It stipulates that neither the Company nor the Customer shall be liable for damages or service failures caused by events beyond their control as defined in Rule 4, Part II, Section C. During such events, minimum Billing Demands are waived, though specific term minimum guarantees for special facilities extension costs may still apply. The party claiming Force Majeure is required to make diligent efforts to remedy the situation.

Preamble
In case of a system emergency, firm service will have priority over interruptible service even if maximum curtailable hours have been exhausted. Curtailment Period: The Curtailment Period is the period which the customer shall reduce KW de...

AI summary The text outlines the operational protocols for system emergencies and demand curtailment. It establishes that firm service takes priority over interruptible service during emergencies. It defines the Curtailment Period as the duration a customer must reduce demand to the Firm Demand Level (FDL) based on Company notification. Provisions are made for notification methods, including a minimum four-hour notice (reduced to ten minutes during emergencies), and defines 'Penalty Demand' as the integrated demand exceeding the FDL within a 15-minute window during a Curtailment Period.

AVAILABILITY
AVAILABILITY This Rider is available only in conjunction with Company's Lighting and Power (LP) or Large Lighting and Power (LLP) rate schedules to Customers who contract for not less than 1000 kW of curtailable power. The applicable rate...

AI summary This section outlines the eligibility and limitations for a specific Rider related to curtailable power. It is available only to customers contracting at least 1000 kW of curtailable power under Lighting and Power or Large Lighting and Power rate schedules. Key constraints include a single point of delivery, exclusion of backup power for customer-owned generation, and a capacity limit of 5% of the Company's projected aggregate peak demand. Customers must also ensure that curtailment does not cause damage or impact public safety.

CONDITIONS OF SERVICE
CONDITIONS OF SERVICE Customer may choose to have Total kW or some portion thereof designated as Curtailable kW. The amount of Total kW not designated as Firm kW shall constitute Customer's Curtailable kW. Customer's service must be equipp...

AI summary The text outlines the conditions of service for the Experimental Curtailable Service Rider, which allows customers to designate a portion of their Total kW as 'Curtailable kW.' Customers are responsible for installing the necessary equipment and metering to reduce load during curtailment events. The Company may request curtailment to maintain service integrity, avoid system peaks, or manage load. The Company provides notice requirements for both non-emergency (30 minutes) and emergency (10 minutes) curtailments via telephonic communication.

LIMITATIONS ON CURTAILMENTS
LIMITATIONS ON CURTAILMENTS Curtailments under this Rider are limited as follows: Daily Limit: No longer than 12 hours in any day, measured from midnight to midnight, except during system emergencies as described below. Annual Limit: No mo...

AI summary The document outlines the limitations and measurement rules for the Experimental Curtailable Service Rider for Southwestern Electric Power Company. It establishes a daily curtailment limit of 12 hours and an annual limit of 400 hours, excluding interruptions caused by equipment failures. During system emergencies involving public pleas for energy conservation, these daily limits are suspended, though these events still count toward the annual limit. It also specifies that any curtailment under 15 minutes is counted as a full 15-minute period.

N-40RIRs Attachment SEB-NSPI - 2h 1 passage
Section 66
http://www.pacificoro.com/ Voltage: Transmission Power Factor: 90%

AI summary The provided text contains a URL for Pacific Oro and technical specifications regarding voltage and transmission power factor, specifically noting a power factor of 90%.

N-40RIRs Attachment SEB-NSPI - 2a, pt. 2 (Large File - 15 MB) 7 passages
PROTECTIVE EQUIPMENT
PROTECTIVE EQUIPMENT Customer shall provide, at his expense, suitable relaying equipment and devices as specified by the Company so as to protect the Company's System and its service to other electric users from disturbances or faults that...

AI summary The document outlines the requirements for customers regarding protective equipment and voltage regulation. It mandates that customers are responsible for providing and maintaining suitable relaying equipment and devices at their own expense. This equipment must meet company specifications to protect the utility's system and other users from faults or disturbances originating from the customer's system. Additionally, customers are required to provide all necessary voltage regulating devices.

APPLICABILITY
APPLICABILITY Available to all commercial and industrial customers with total firm capacity requirements of at least 5,000 KW, at the sole discretion of the Company and only when the Company has available capacity in excess of its firm sys...

AI summary The text outlines the applicability criteria for a specific electricity service schedule. It is available to commercial and industrial customers with firm capacity requirements of at least 5,000 KW, subject to the Company's discretion and excess capacity. The service requires that the power utilization can be interrupted at any time without causing damage to property, persons, public health, safety, or welfare. It explicitly excludes standby, temporary, resale, or standalone interruptible services.

SCHEDULING PROCEDURES
SCHEDULING PROCEDURES The Company and the Customer shall agree upon detailed procedures for requesting, providing notice of, and implementing interruptions, and shall set forth the same in the Contract for Power Service.

AI summary The document establishes the requirement for the Company and the Customer to mutually agree on specific procedures regarding power service interruptions. These procedures must include protocols for requesting, providing notice of, and implementing interruptions, and must be formally documented within the Contract for Power Service.

GENERAL CONDITIONS
GENERAL CONDITIONS EPEC may make intentional interruptions at any time and from time to time, at EPEC's sole discretion, for up to 400 hours in any calendar year. However, EPEC may not interrupt the customer (1) due solely to differences i...

AI summary The text outlines the general conditions for Interruptible Power Service provided by Eastern Power Corporation (EPEC). It specifies that EPEC may perform intentional interruptions for up to 400 hours annually, provided the interruptions are not solely due to marginal cost differences or non-firm off-system sales. Requirements for customer notice are established: at least 4 hours for non-emergency situations and a minimum of 30 minutes for emergencies. It also defines 'emergency conditions' and the calculation for counting interruption hours.

41.2.5. PEAK LOAD CONDITIONS
41.2.5. PEAK LOAD CONDITIONS Peak Load Conditions are defined as those conditions on any day that could result in the Entergy System establishing a monthly peak.

AI summary The text provides a formal definition of Peak Load Conditions within the context of the Entergy System. It specifies that these conditions are defined as any circumstances occurring on a given day that have the potential to result in the establishment of a monthly peak for the system.

41.2.6. CAPACITY SHORTAGE CONDITIONS
41.2.6. CAPACITY SHORTAGE CONDITIONS Capacity Shortage Conditions are defined as those conditions on any day in which the Company has insufficient generating resources, including firm purchases, capable of supplying its load requirements w...

AI summary The document provides a formal definition for Capacity Shortage Conditions. These conditions occur on any given day when the Company lacks sufficient generating resources, including firm purchases, to meet the load requirements within the Entergy Arkansas, Inc. (EAI) service area.

41.4.1. The maximum hours per interruption are as follows:
41.4.1. The maximum hours per interruption are as follows: Days Per Interruptions Hours Per Hours Per Season Month Per Day Interruption Month Summer Months 10 1 4 35 Other Months 10 2 3 55 - 41 .4.2. The Company shall not discriminate amon...

AI summary The document specifies the maximum allowable hours and frequency for power interruptions for customers under a specific Rider. During summer months, the limit is set at 1 interruption per day for a maximum of 4 hours, totaling 35 hours per month. During other months, the limit is 2 interruptions per day for a maximum of 3 hours each, totaling 55 hours per month. Additionally, the Company is required to provide non-discriminatory service and make best reasonable efforts to interrupt customers equally.

N-40RIRs Attachment SEB-NSPI - 2a, pt. 5 (Large File - 20 MB) 3 passages
AVAILABILITY
AVAILABILITY This schedule is available to all customers on an annual basis for transmission service where facilities of adequate capacity and suitable phase and voltage are available. Service will be supplied at one point of delivery thro...

AI summary The text defines the availability and requirements for a specific transmission service schedule. It states that the service is available to customers annually, provided there is adequate capacity and suitable phase and voltage. The service is restricted to single points of delivery with one meter and is only applicable to billing demands of 10,000 kilowatts or greater, with metering adjusted to the service voltage.

Capacity Charge for Highly Fluctuating Loads:
Capacity Charge for Highly Fluctuating Loads: Should the Customer operate equipment with highly fluctuating, intermittent, or abnormal characteristics that make it necessary for the Company to install special facilities to serve the Custom...

AI summary The text outlines a specific tariff provision for customers operating equipment with highly fluctuating, intermittent, or abnormal characteristics. If these characteristics necessitate the installation of special facilities by the Company to maintain service stability or prevent disturbances to other customers, an additional capacity charge is applied. The charge is set at $1.00 per month per kilovolt-ampere (KVA) or fraction thereof of the transformer capacity installed specifically to serve that customer.

LIMITATIONS ON INTERRUPTIONS: Interruptions under this Rider are limited as follows:
LIMITATIONS ON INTERRUPTIONS: Interruptions under this Rider are limited as follows: Daily Limit: No more than two curtailments per calendar day of up to a total of 12 hours, measured from midnight to midnight, except in system emergencies...

AI summary This text outlines the limitations and operational rules for load curtailments under an interruptible power service rider. It establishes a daily limit of two curtailments (up to 12 hours total) and an annual limit of 200 hours, with fractions of an hour rounding up. The Company maintains the right to perform one-hour test interruptions, particularly if the customer has been compliant. It also defines the measurement of interruption time and specifies that limits are waived during system emergencies or public power shortage pleas.

N-40RIRs Attachment SEB-NSPI - 2a, pt. 3 (Large File - 23 MB) 9 passages
Availability of Service.
Availability of Service. Available for general service customers with normal annual load factors greater than 55 percent. The customer shall contract for a sufficient capacity to meet normal maximum requirements, but in no case shall the c...

AI summary The text specifies the eligibility criteria for general service customers regarding the availability of service. To qualify, customers must maintain normal annual load factors exceeding 55 percent. Additionally, customers are required to contract for sufficient capacity to meet their normal maximum requirements, with a minimum contractual capacity threshold of 1,000 kVA.

Conditions of Service.
Conditions of Service. - 1. The Company reserves the right to curtail service to the customer at any time and for such period of time that in the Company's sole judgement the operation of its system requires curtailment of customer's servi...

AI summary The text outlines the Conditions of Service for interruptible power supply, specifying the Company's rights to curtail service for system operations. It establishes minimum availability requirements for contract capacity (145 hours weekly and 630 hours monthly), except during emergencies. Customers are required to respond to curtailment requests within ten minutes and are responsible for maintaining substations. It also details options for auxiliary switching and billing for non-interruptible service.

TARIFF I.R.P. (Interruptible Power)
TARIFF I.R.P. (Interruptible Power) (Cont'd from Sheet No. 14.2) The customer shall contract for capacity sufficient to meet normal maximum interruptible power requirements, but in no event will the amount contracted for be less than 10,00...

AI summary The document outlines the contractual terms for the Interruptible Power (I.R.P.) tariff. Customers must contract for capacity between 10,000 kVA and 50,000 kVA to meet normal maximum requirements. If demand exceeds the contracted capacity, the Company may notify the customer to reduce demand or interrupt service. Initial contracts must last at least two years, with a one-year notice period for termination. The Company reserves the right to require longer initial contract periods if new facilities are necessary.

AVAILABILITY OF SERVICE
AVAILABILITY OF SERVICE This rider shall be made available to customers seNed under the applicable power schedules who contract for not less than 1 ,000 kilowatts of their total requirements to be subject to curtailment upon notification b...

AI summary The text defines the eligibility requirements for a specific rider regarding the availability of service. It specifies that the rider is available to customers under applicable power schedules who contract for a minimum of 1,000 kilowatts of their total requirements. These customers must be subject to curtailment upon notification by the Company.

RIDER NO.4 INTERRUPTIBLE POWER SERVICE Applicable to Rate Nos. 22, 41, 42 and 53
RIDER NO.4 INTERRUPTIBLE POWER SERVICE Applicable to Rate Nos. 22, 41, 42 and 53 Availability of Rider No. 4 is limited to customers taking service under this rider on N December 31 , 1996, and only on the amount of service under contract...

AI summary The document defines the terms and limitations of Rider No. 4, which provides Interruptible Power Service to specific customers. Eligibility is restricted to those who contracted for the service by December 31, 1996, based on their service amounts as of that date. To qualify, customers must agree to interrupt at least 1,000 kW of their electric requirement upon the Company's request. The Company maintains the right to determine interruption times and durations, subject to an aggregate system load limit of 64,000 kW in the East System.

GENERAL:
GENERAL: The Company reserves the right to assure itself that any agreed upon interruptible load has a reasonable probability of being on the Company's system during peak load periods and can be readily interrupted. The Company also reserv...

AI summary The Company establishes terms and conditions for interruptible loads, asserting the right to ensure such loads are present on the system during peak periods and can be readily interrupted. It reserves the right to mandate additional metering at the customer's expense to verify interruptions. Furthermore, the Company explicitly disclaims all liability for any loss, damage, or injury resulting from the interruption or curtailment of these loads as stipulated in the agreement.

Rider No. 57 to Electric General Service and Large General Service- Curtailment Service (con't)
Rider No. 57 to Electric General Service and Large General Service- Curtailment Service (con't) customer, provided the customer was alerted to the possibility of curtailment 12 or more hours prior to the beginning of the curtailment period...

AI summary The text outlines the operational rules for Rider No. 57, which governs the Curtailment Service for Electric General Service and Large General Service. It specifies notice requirements for curtailments intended to avoid MAPP capacity purchases (12 hours notice, with a 2-hour minimum) and those due to operating conditions. It also defines the maximum duration of curtailment periods, the annual limit of 16 such periods during summer peak months, and the methodology for randomly rotating curtailable groups. Finally, it establishes a statewide limit of 190,000 kW for total curtailable load.

Rider No. 2 to Electric General Service and Large General Service (Except Price Schedule LCL) -Curtailment Service (can't)
Rider No. 2 to Electric General Service and Large General Service (Except Price Schedule LCL) -Curtailment Service (can't) Option B customers may request a change in the firm power level annually. In addition, on 24 hours' notice, customer...

AI summary This document outlines Rider No. 2 for Electric General Service and Large General Service regarding Curtailment Service. It details two options for customers: Option B allows for annual firm power level changes and 24-hour service cancellation (with forfeiture of summer credits), while Option A requires immediate notification for increases. The Company reviews expected loads annually and may adjust minimum firm power levels based on historical demand. It also includes provisions for standby generators, minimum billing, and tax adjustments.

Rider No.2 to Electric General Service and Large General Service (Except Price Schedule LCL) -Curtailment Service (con't)
Rider No.2 to Electric General Service and Large General Service (Except Price Schedule LCL) -Curtailment Service (con't) r customer, provided the customer was alerted to the possibility of curtailment 12 or more hours prior to the beginni...

AI summary The text outlines the operational procedures for Rider No.2 Curtailment Service, specifically regarding notice periods and duration for load curtailment. It specifies that customers must be notified 12 hours in advance, unless the Company provides 2-hour notice to avoid MAPP capacity purchases. Curtailment periods are capped at 6 hours or until notice of termination. The Company will randomly group participants by net C loads and rotate between groups. Participation is limited to a state-wide total of 190,000 kW.

N-44RIRs 76 to 136 - CA to NSPI - REDACTED (Large File - 19 MB) 1 passage
RESPONSE TO INFORMATION REQUEST
RESPONSE TO INFORMATION REQUEST TO: NSPI FROM: CA Question IR-1 09: Referring to page 15, could Accenture, if hired by NSPI, provide system assessment, design, and/or implementation for any of the systems that are recommending to be replac...

AI summary The response confirms that Accenture can provide system assessment, design, and implementation services if hired by NSPI for systems recommended for replacement.

N-46Rebuttal Evidence of NSPI - Appendix A to J - REDACTED (Large File 27 MB) 12 passages
Strengths
Strengths - Regulated operations contribute to earnings and cash flow stability - Cash flow from operations are expected to remain sufficient to fund capital expenditures and dividends - Geographic isolation and limited interconnections ar...

AI summary The text highlights the financial and operational strengths of the regulated utility. It notes that regulated operations provide stable earnings and cash flow, which are sufficient to support capital expenditures and dividend payments. Furthermore, the company benefits from geographic isolation and limited interconnections, creating barriers to entry for competitors. Additionally, the transition to cleaner burning coal is expected to provide a short-term reduction in emissions.

Emera Inc. Generation Asset Performance
Emera Inc. Generation Asset Performance 2005 2004 2003 2002 2001 Thermal capacity utilization (%) 78 82 78 77 77 Generating capacity availaiblity (%) 90 92 91 91 91 Cost of fuel and purchased power (mil. C$) 374 303 278 336 302 NSPI's gene...

AI summary The document provides a performance overview of Emera Inc.'s generation assets, specifically focusing on thermal capacity utilization, generating capacity availability, and fuel and purchased power costs from 2001 to 2005. It notes that while Nova Scotia Power Inc. (NSPI) relies on coal-fired facilities, its generation portfolio benefits from diversification within its fossil fuel-fired assets. The utility asserts that it maintains adequate capacity and reserves to satisfy provincial load obligations.

Section 71
The reliability of NSPI's electricity transmission and distribution operations is typically within industry benchmarks but deteriorated to below industry average in 2004 (see table 4). System performance suffered during a severe winter sto...

AI summary The text evaluates the historical reliability of Nova Scotia Power Inc.'s (NSPI) electricity transmission and distribution operations. While generally meeting industry benchmarks, performance fell below average in 2004 due to a severe winter storm, leading to significant customer criticism. However, an independent study defended the utility's maintenance practices. In contrast, Bayonne Hydroelectric Corporation's (BHEC) wire operations are noted as consistently meeting regulatory benchmarks.

Nova Scotia Power Inc. Reliability\
Nova Scotia Power Inc. Reliability\ Reliability measures 2005 2004 2003 2002 2001 System Average Interruption Frequency Index (SAIFI; interruptions per year) 3.54 3.79 2.85 2.62 2.48 ') ()()h_ 1 ')-') 1

AI summary The document provides historical data regarding the reliability of the electrical system managed by Nova Scotia Power Inc. Specifically, it lists the System Average Interruption Frequency Index (SAIFI), which measures the average number of interruptions per year. The data shows a fluctuation in reliability from 2001 to 2005, with the SAIFI reaching a peak of 3.79 in 2004 before decreasing to 3.54 in 2005.

DATE FILED: January 17, 2007 [21-Dec-2006] Emera Inc.
DATE FILED: January 17, 2007 [21-Dec-2006] Emera Inc. CEA region 2 composite SAIFI 2.46 2.3 2.8 2.56 2.67 System Average Interruption Duration Index (SAIDI; minutes) 620 1 '1 05 343 368 243 CEA region 2 composite SAIDI 391 317 222 291 263...

AI summary The document presents reliability metrics for CEA Region 2, specifically focusing on the System Average Interruption Frequency Index (SAIFI) and the System Average Interruption Duration Index (SAIDI). The data covers a five-year period, with a note clarifying that reliability measures exclude outages caused by Hurricane Juan in 2003 and the northeast August 14 blackout.

Nova Scotia Utility and Review Board
Nova Scotia Utility and Review Board Mailing address PO Box1692, Unit •M• Halifax. Nova Smtia B313S3 [email protected] Web www.nsuarb.ca Office 3rd Floor 1601 Lower Water Street Halifax, Nova Scotia B3J 3P6 902 424-4448 t 902 424-3919 f...

AI summary The Nova Scotia Utility and Review Board is reviewing Nova Scotia Power Industrial's (NSPI) request to recover $3.6 million for a Distribution System Vegetation Management program. While the Board acknowledges that vegetation encroachment is a primary cause of power outages and supports the program's necessity for reliability, it notes that NSPI failed to include this foreseeable expenditure in its 2007 test year revenue requirement filing. Consequently, approving the request now would result in a revenue requirement increase.

Liberty Conclusions
Liberty Conclusions - "1. NSPI based its proposed vegetation management program for the distribution system on reasonable assumptions. The well-planned program appears to maximize the benefits to customers for the requested level of spendi...

AI summary Nova Scotia Power Industrial (NSPI) submitted a proposed vegetation management program for its distribution system. The analysis concludes that the program is built on reasonable assumptions and is well-planned to maximize customer benefits relative to the requested spending. While the program is expected to improve system reliability, it is noted that it may not fully address existing customer dissatisfaction issues.

Customer Requested Work Program (CRW)
Customer Requested Work Program (CRW) NSPI's Customer Requested Work Program is directed at addressing safety issues associated with vegetation in proximity to power lines. NSPI typically receives between three thousand and four thousand c...

AI summary Nova Scotia Power Industrial (NSPI) manages a Customer Requested Work Program (CRW) to address safety concerns regarding vegetation encroachment near power lines. NSPI receives 3,000 to 4,000 customer calls annually, with approximately 50% requiring crew dispatch. The company notes an increasing trend in these requests and has assumed an annual cost of $900,000 for vegetation management in its submission.

Section 117
The large hazard tree program targets large trees, near NSPI plant that have died or are dying . . The objective of the program is to remove the tress before they fall apart. The classic example of this in our region is American White Elm,...

AI summary The text describes the Large Hazard Tree Program (LHT), which aims to proactively remove large, dying, or dead trees near Nova Scotia Power Industrial (NSPI) facilities. Using the American White Elm affected by Dutch Elm Disease as a primary example, the program seeks to prevent heavy limbs from falling and causing significant damage to infrastructure or resulting in power outages.

By Fax Only: 428-6542
By Fax Only: 428-6542 Mr. Eric Ferguson Manager, Regulatory Affairs Nova Scotia Power Inc. 14 th Floor, Barrington Tower P. O. Box 910, Scotia Square Halifax, NS B3J 2W5 Dear Mr. Ferguson: November Power Outage Review Decision Reports - NS...

AI summary The Nova Scotia Utility Review Board is requesting comments from Nova Scotia Power Inc. (NSPI) regarding Liberty Consulting Group's feedback on the November Power Outage Review Decision Reports. Specifically, the Board seeks clarification on the financial estimates for vegetation management spending, including the origin of the $325 per span unit price for trimming and the defined roles of various personnel, such as linemen, scopers, foresters, and contract tree trimmers.

Liberty concluded:
Liberty concluded: - 1. NSPI based its proposed vegetation management program for the distribution system on reasonable assumptions. The well-planned program appears to maximize the benefits to customers for the requested level of spending...

AI summary The Nova Scotia Utility and Review Board (UARB) concluded that Nova Scotia Power Industrial's (NSPI) proposed vegetation management program for the distribution system is based on reasonable assumptions. The Board found that the program is well-planned and effectively maximizes customer benefits relative to the requested spending level. However, it noted that while the program is expected to improve system reliability, it may not fully address existing issues regarding customer dissatisfaction.

Liberty recommends that the UARB:
Liberty recommends that the UARB: - 1. Require that NSPI justify the portion of the vegetation management budget related to customer-requested work and hazard trees. - 2. Approve the requested level of annual spending of at least $7 millio...

AI summary Liberty recommends that the Nova Scotia Utility and Review Board (UARB) require Nova Scotia Power Industrial (NSPI) to provide a detailed justification for the portion of its vegetation management budget dedicated to customer-requested work and hazard trees. While Liberty acknowledges that NSPI's proposed non-cyclical approach is more cost-effective than a cyclical one, it argues that a cyclical program would offer superior storm hardening and reliability for rural customers. Liberty supports the requested annual spending of at least $7 million provided the budget is used exclusively for distribution vegetation management.

57968Amended Board Order (and attached Schedules A to C) 1 passage
Maintain System Integrity
Maintain System Integrity The customer will make all necessary arrangements to ensure that its load does not unduly deteriorate the integrity of the power supply system, either by its design and/or operation. Specific requirements shall be...

AI summary The customer is required to ensure their load does not negatively impact the integrity of the power supply system. Specific requirements will be outlined in a separate operating agreement, and factors such as reliability, voltage levels, and stability will be considered in assessments.

57966Supplementary Board Order 1 passage
OP - Organization Profile
OP - Organization Profile - 1 . Latest regulated annual reports of NSPI and EMERA. - 2. Current organization chart of NSPI showing all positions reporting no further than two levels down from the President and CEO, including a full organiz...

AI summary The document outlines a list of information requests related to NSPI's organizational structure, asset details, fuel specifications, reliability statistics, customer data, and compliance with emissions targets. These requests are part of a regulatory proceeding and aim to gather detailed operational and financial data.

57968Amended Board Order (and attached Schedules A to C) 2 passages
SPECIAL CONDITIONS:
SPECIAL CONDITIONS: - (1) The Company reserves the right to have a separate service agreement if in the opinion of the Company, issues not specifically set out herein must be addressed for the ongoing benefit of the Company and its custome...

AI summary The special conditions outline the Company's right to establish separate service agreements, customer responsibilities for maintaining power supply integrity, and adjustments to meter readings based on voltage levels and transformer losses.

Maintain System Integrity
Maintain System Integrity The customer will make all necessary arrangements to ensure that its load does not unduly deteriorate the integrity of the power supply system, either by its design and/or operation. Specific requirements shall be...

AI summary The customer is required to ensure that its load does not negatively impact the integrity of the power supply system. Specific requirements will be outlined in a separate operating agreement, and factors such as reliability, voltage levels, and system stability will be considered in the assessment.

57974NSPI Compliance Filing 2007 Rate Application - REDACTED (Large File - 36 MB) 3 passages
LARGE INDUSTRIAL TARIFF
LARGE INDUSTRIAL TARIFF (2 000 kV.A or 1 800 kW, and Over) Rate Code 23 - (4) The Company reserves the right to have a separate service agreement, if in the opinion of the Company issues not specifically set out herein, must be addressed f...

AI summary The Large Industrial Tariff outlines conditions for customers with high power usage, including requirements for service agreements, load management, and system integrity. The Company reserves the right to enforce specific operational agreements to ensure reliability and stability of the power supply system.

SPECIAL CONDITIONS:
SPECIAL CONDITIONS: - ( 1) The Company reserves the right to have a separate service agreement if in the opinion of the Company, issues not specifically set out herein must be addressed for the ongoing benefit of the Company and its custom...

AI summary The Company reserves the right to establish separate service agreements when necessary for the benefit of the Company and its customers. Customers are required to ensure their load does not compromise the integrity of the power supply system. Specific conditions related to reliability, voltage, and transformer losses are outlined.

Maintain System Integrity
Maintain System Integrity The customer will make all necessary arrangements to ensure that its load does not unduly deteriorate the integrity of the power supply system, either by its design and/or operation. Specific requirements shall be...

AI summary The customer must ensure its load does not negatively impact the power supply system's integrity through design or operation. Specific requirements will be outlined in a separate operating agreement, with considerations including reliability, voltage and current levels, flicker, stability, and fault levels.

86472Submission - Re: Future Filing Requirements and comments on Board Draft Strawman 1 passage
OP - Organization Profile
OP - Organization Profile - 1. Latest regulated annual reports of NSPI and EMERA - 2. Current organization chart ofNSPI showing all positions reporting no further than two levels down from the President and CEO, including a full organizati...

AI summary The document outlines a list of requested information for a regulatory proceeding, including organizational profiles, financial documents, and operational data related to NSPI and EMERA. It includes details on assets, reliability statistics, customer information, and emissions targets.

86477Submission - Re: Rate Hearing Future Filing Requirements 1 passage
(b) Reliability Statistics
(b) Reliability Statistics 33. In P-886, UARB IR-34 asked NSPI to "provide reliability statistics, in the same format as UARB IR-38 in P-882." SEB submits: that NSPI be required to file with its Application reliability statistics in the sa...

AI summary The UARB requested NSPI to provide reliability statistics in a specific format. SEB submits that NSPI should file reliability statistics in the same format as previously specified in UARB IR-34 in P-886 and UARB IR-38 in P-882 to assess NSPI's operational performance and efficiency.

Disclaimer: These summaries were generated by AI from the filings they describe. We take care to make them accurate, but errors are possible - and they aren't advice. Only the filings themselves are the record: if you're relying on something here, confirm it against the source documents or the Nova Scotia Energy Board's own record. Full disclaimer →