N-2NSPI Response to Complaint - Redacted
5 passages
REDACTED (CONFIDENTIAL INFORMATION REMOVED) March 9, 2026 C. Henwood NS Power completed its investigation at the customer's premises during the period of January 15 to February 12, 2026, using a meter‑base voltage data logger installed ons...
AI summary NS Power investigated a customer's power quality concerns during an extreme cold event, finding voltages within extreme operating limits but below normal ranges. Post-event AMI data showed stabilized voltages, with NS Power attributing the anomalies to exceptional system loading and weather impacts.
REDACTED (CONFIDENTIAL INFORMATION REMOVED) March 9, 2026 C. Henwood Tidewater substation and feeder 92H-331. To address the customer's immediate service conditions, NS Power implemented a quick corrective action by replacing the customer'...
AI summary NS Power addressed voltage issues at Tidewater substation and feeder 92H-331 through immediate conductor replacement and long-term upgrades requiring NSEB approval, including substation upgrades, transformer replacement, and new feeder construction. Contingency plans are in place to ensure reliability during delays.
REDACTED Nichols Customer Complaint Attachment 1 Page 3 of 5 REDACTED (CONFIDENTIAL INFORMATION REMOVED) Low voltage trends were identified for extended durations that do not relate to the customer's energy consumption. These voltage trend...
AI summary The document highlights low voltage trends during extreme cold weather, affecting customers unrelated to their energy consumption. These voltage drops occurred over extended periods and were attributed to supply-level issues during harsh weather conditions.
REDACTED Nichols Customer Complaint Attachment 1 Page 4 of 5 REDACTED (CONFIDENTIAL INFORMATION REMOVED) Outside of the extreme cold weather days, brief momentary voltage sags were identified in the recording that correspond with the custo...
AI summary The customer reported voltage sags during high load inrush, except during extreme cold. Analysis shows voltage trends do not exceed operating limits. Figures illustrate the voltage sags correlating with high demand periods.
Conclusions: During the time of the recording, the system experienced extreme cold weather, resulting in high loading conditions on the system. On the most affected days, the increased loading resulted in lower service voltage at the custo...
AI summary The report details voltage fluctuations during extreme cold weather, which caused temporary drops outside normal operating levels but remained within acceptable limits. NSPI notes service voltage has improved post-winter and plans 2026 infrastructure upgrades to resolve the issue.
101771Board Decision Letter (redacted)
3 passages
April 28, 2026 Greg Nichols Dear Mr. Nichols: M12730 – Nova Scotia Power Inc. DRO Appeal – Infrastructure Concerns (Greg Nichols) On March 3, 2026, you filed a complaint with the Nova Scotia Energy Board (Board) regarding a Nova Scotia Pow...
AI summary Greg Nichols complained about voltage issues at his home, leading to equipment aging. NS Power addressed the issue by replacing the service conductor and installing a data logger, acknowledging voltage fluctuations during cold weather but stating they were within acceptable limits.
e during the period remained within acceptable extreme voltage limits. NS Power provided a copy of the Power Quality Report to highlight the voltage fluctuation during the January cold weather events. NS Power further explained that the lo...
AI summary NS Power addressed voltage fluctuations on feeder 92H-331 during cold weather events, attributing the issue to feeder overloading. It outlined capital projects like the Tidewater Substation upgrade to resolve the problem and described contingency plans for power quality monitoring while awaiting project completion.
itoring devices on each feeder. In response to IR-5, NS Power described its contingency plan to address power quality issues while awaiting the completion of the proposed capital projects, including: … transferring load to another supply a...
AI summary The Board attributes a voltage issue to feeder overload and acknowledges NS Power's contingency plan, including load transfer and reconductoring. It directs NS Power to install voltage monitoring devices and submit a timeline for implementation by June 30, 2026, while rejecting liability claims for equipment wear.