REDACTED REDACTED (CONFIDENTIAL INFORMATION REMOVED) 2026 ACE Plan CONFIDENTIAL (Attachments Only) 1 Distribution Upgrades and Replacements 2 3 Figure 44: Distribution Upgrades and Replacements 2026 ACE Plan Forecast D005 Unplanned Replace...
AI summary The 2026 ACE Plan outlines forecasts for distribution upgrades and replacements, including unplanned equipment replacement, regulatory replacements, and provincial storm-related expenditures. These forecasts are based on historical spending averages, adjusted for inflation, and may vary depending on annual decisions and storm activity.
1 2 The forecast for D005 for 2026 was developed based on the previous 5-year average for spend 3 from 2021-2025 plus an annual inflation of 1.80 percent. This forecast resulted in an estimated 4 8,446 person days of work at a unit cost of...
AI summary The forecast for D005 in 2026 is based on the previous 5-year average of spend from 2021-2025, factoring in 1.80% annual inflation. The forecast includes overtime labour costs due to unplanned asset failures occurring at any time, including outside normal business hours. Historical data on equipment failures is referenced, with more details to be provided in future ATO filings.
Major Extreme 2 3 4 Figure 75 below provides detail on outage causes for the three event days experienced so far in 5 2025. 6 7 Figure 75: Detail on Outage Causes for identified Event Days Significant Major Extreme CEA Hours of Hours of Ho...
AI summary The document provides an analysis of outage causes for three event days in 2025, highlighting that the majority of outages were due to loss of supply and tree contacts, with scheduled outages and unknown causes contributing smaller proportions.
9 Foreign Interference 10,087 0 0 4.03% Total 250,026 0 0 1 2 Over 20 percent of all identified event day outage hours in 2025 have been caused by tree contacts. 3 Furthermore, a significant portion of events coded as adverse weather are l...
AI summary The text highlights that over 20% of event day outage hours in 2025 were caused by tree contacts, emphasizing the need for continued investment in vegetation management and right-of-way widening. Several capital projects are identified to address these issues in 2026.
2026 ACE Plan C0080206 Page 2 of 5 JUSTIFICATION: Justification Criteria: Thermal Sub Criteria: Equipment Replacement/ Refurbishment Why do this project? NS Power conducts condition and risk assessment and analysis based on the annual boil...
AI summary NS Power is proposing the replacement of boiler components such as tubes, tube shielding, and tube locks to enhance system reliability, mitigate the risk of unplanned outages, and ensure safe and cost-effective operation. The project is necessary due to the increased risk of failures from degraded components and the potential for higher costs from emergency repairs.
ment 2026 Start Date: 2026/08 In-Service Date: 2026/10 Final Cost Date: 2027/04 Function: Steam Forecast Amount: $1,024,385 DESCRIPTION: This project will replace refractory components in the Point Aconi boiler system, following inspection...
AI summary This project involves replacing refractory components in the Point Aconi boiler system to ensure safe and efficient operation, reduce thermal losses, and prevent unplanned outages. The work includes key areas such as cyclones, combustor-to-cyclone crossover ducts, and lower combustor sections, with a forecasted cost of $1,024,385.
onfirm this was done in its applications to the Board. In accordance with the Board’s directive, NS Power provided notice of this investment to participants in the DDA proceeding on December 3, 2025. Summary of Related CIs +/- 2 years: Pur...
AI summary NS Power is replacing refractory components in the Steam Production Plant at Point Aconi to ensure boiler reliability and prevent unplanned outages. The project is justified under the Thermal Equipment Replacement/Refurbishment criteria and aligns with the Board’s directive to notify participants in the DDA proceeding.
black start capability, 10-minute reserve, Volt-Ampere Reactive support and additional firm energy capacity to the NS Power electrical system. The unit was originally commissioned by NS Power in 1976 Summary of Related CIs +/- 2 years: Pur...
AI summary The document discusses the refurbishment of a gas turbine at Burnside to maintain essential ancillary services, citing wear and damage identified in a 2025 borescope inspection. The project is justified based on thermal criteria and equipment replacement needs to prevent unplanned outages and ensure system reliability.
ting investment. These units offer valuable operational flexibility and enhance system security through black start capability, rapid response, and improved system stability. Why do this project now? Completing the refurbishment of this en...
AI summary This text discusses the need to refurbish an engine in 2026 to prevent unplanned failures. Inspection in 2025 revealed damage to blades in the low-pressure and high-pressure compressor stages, indicating hidden wear that can only be confirmed through depot-level disassembly. The project is necessary due to the risk of failure and the need for compliance with OEM procedures.
f Retirement: Accounting Policy 6420 – Retirement and disposal of Capital Assets • Percentage of Asset Pool: 0.23% JUSTIFICATION: Justification Criteria: Transmission Plant Why do this project? The installation of the new switches will ena...
AI summary The project involves replacing two end-of-life switches (22N-603 and 22N-604) to enable live-line operation, reducing outages and improving reliability. The current switches are difficult to operate and their failure could lead to unplanned outages. A new ground grid and switches will allow more efficient operations and mitigate risks.
ng Station to the transmission grid, enabling the delivery of renewable hydroelectric energy. Its continued degradation poses operational, financial, and environmental risks. Why do this project now? The 96H-T1 transformer is consistently...
AI summary The document discusses the need to replace a transformer due to oil leaks and its location near a river, which poses environmental risks. Replacement is deemed necessary due to the transformer's degraded condition, lack of OEM support, and the cost-effectiveness of replacement over refurbishment.
timated August 2026); therefore, the Final Cost Date (June 2029) is six months after the last circuit breaker is expected to be replaced on this project (December 2028). Why do this project this way? Proactively replacing Pennsylvania circ...
AI summary NS Power is proactively replacing Pennsylvania circuit breakers on the transmission system due to the unavailability of replacement parts and manufacturer support. The project is being staged to reduce risk and ensure achievable annual scopes without excessive outages. A 10% contingency has been allocated for potential overtime and cost increases.
Retirement and Disposal of Capital Assets • Percentage of Asset Pool: 0.01% JUSTIFICATION: Justification Criteria: Distribution System Sub Criteria: Deteriorated Conductor Why do this project? This project is designed to mitigate the circu...
AI summary This project aims to replace a severely deteriorated conductor and associated overhead components on a distribution line to mitigate circuit risk, improve reliability, and prevent unplanned outages. The conductor has reached the end of its service life and poses increased operational risks.
d past outage performance has confirmed that conductor replacement is necessary. Delaying this project increases the likelihood of additional unplanned interruptions for customers served by this line. This project is deemed in service when...
AI summary The document discusses a conductor replacement project necessary to prevent additional unplanned outages. The project is phased, with the first distribution transformer replacement expected in August 2026 and the final cost date set for July 2027. The approach focuses on replacing the most deteriorated sections of the line. A 10% contingency has been applied to cover potential risks such as additional equipment replacement and tree trimming.
oles and Fixtures Distribution Plant – Overhead Conductors and Devices Distribution Plant – Line Transformers Estimated Life of the Asset: 45 years Retirement Information: • Categorization of Retirement: Accounting Policy 6420 - Retirement...
AI summary The document discusses a project to replace deteriorated poles and conductors on feeder 57C-426H to improve outage performance and enable future customer connections. The project is part of a broader effort to enhance the reliability of the distribution feeder, which has historically had poor performance due to an off-road section.
REDACTED (CONFIDENTIAL INFORMATION REMOVED) 2026 ACE Plan C0080612 Page 5 of 5 Legend: Inclusions: Date: December 12, 2025 Page 430 of 782 REDACTED REDACTED (CONFIDENTIAL INFORMATION REMOVED) 2026 ACE Plan C0080111 Page 1 of 5 CI Number: C...
AI summary This document outlines the 2026 RTU Deployment project, which involves installing 21 Remote Terminal Units (RTUs) in Nova Scotia substations to improve grid operation and emergency response times. The project is part of General Plant function and has a forecasted cost of $8,322,655.
2026 ACE Plan Appendix D Page 61 of 179 Nova ScoƟa Power Inc. Capital Planning & Capital Expenditure JusƟficaƟon Criteria Summary Document Forced Outage Rate Unplanned outages result in replacement genera on, o en at a higher cost than the...
AI summary Nova Scotia Power Inc. outlines capital expenditure justification criteria, emphasizing unplanned outages' cost impacts via probabilistic production models. System design adheres to NPCC and NERC standards, with NERC requirements enforced through NSEB regulatory approval. Transmission criteria combine protection performance and system dynamics, ensuring compliance with single contingency design principles.
1 2.0 RELIABILITY PERFORMANCE ANALYSIS 2 3 NS Power has developed the Plan to deliver a 20 percent improvement in the performance 4 standards overall average duration of outages (SAIDI) and to achieve the Performance Standards 5 SAIFI targ...
AI summary NS Power's Plan aims to improve system reliability by reducing outages caused by tree contacts and equipment failures, targeting a 20% improvement in SAIDI and achieving a SAIFI target of 2.05 by 2029. Grid modernization, including RTUs and remote connectivity, will mitigate outage impacts and enhance fault isolation.