E-12027-2031 DSM Plan Application
366 passages
EfficiencyOne IN THE MATTER OF The Public Utilities Act , R.S.N.S. 1989, c.380 as amended. - and - IN THE MATTER OF An Application by EfficiencyOne for Approval of the 2027–2031 Demand-Side Management (DSM) Purchase Agreement between Effic...
AI summary EfficiencyOne seeks approval for a 2027–2031 Demand-Side Management (DSM) Purchase Agreement with Nova Scotia Power Inc., along with establishing a final agreement and approving a DSM Resource Plan under the Public Utilities Act, R.S.N.S. 1989, c.380 as amended.
Application of EfficiencyOne as Holder of the Efficiency Nova Scotia Franchise FILED WITH THE NOVA SCOTIA ENERGY BOARD March 31, 2026
AI summary EfficiencyOne seeks to hold the Efficiency Nova Scotia franchise, filed with the Nova Scotia Energy Board on March 31, 2026. The application pertains to regulatory approval for managing demand-side management (DSM) programs in Nova Scotia.
NOVA SCOTIA ENERGY BOARD IN THE MATTER OF: The Public Utilities Act, R.S.N.S. 1989, c . 380 , as amended - and - IN THE MATTER OF: An Application by EfficiencyOne for Approval of a Demand-Side Management (DSM) Purchase Agreement between Ef...
AI summary The Nova Scotia Energy Board is considering EfficiencyOne's application to approve a DSM Purchase Agreement with Nova Scotia Power Inc., establish a final agreement between the parties, and approve a 2027–2031 DSM Resource Plan under the Public Utilities Act.
TO: The Nova Scotia Energy BOARD ("Energy Board" "NSEB") - 1. EfficiencyOne ("E1") is the holder of the Franchise issued by the Minister of Energy, effective January 1, 2025, to provide demand-side management activities to Nova Scotia Powe...
AI summary EfficiencyOne (E1) seeks approval from the Nova Scotia Energy Board (NSEB) for a five-year Demand-Side Management (DSM) Purchase Agreement with Nova Scotia Power Inc. (NS Power) covering 2027–2031. The application includes a DSM Resource Plan and requests an interim order if a final decision is delayed. The current agreement extends through 2026, and E1 asserts the proposed terms are in the public interest.
2 1.1 APPROVAL OF 2027–2031 DSM RESOURCE PLAN - 3 EfficiencyOne ("E1") requests approval by the Nova Scotia Energy Board (the "Energy Board" or "NSEB") - 4 of its Demand Side Management ("DSM") Resource Plan ("DSM Plan") for the term 2027...
AI summary EfficiencyOne (E1) seeks approval from the Nova Scotia Energy Board (NSEB) for its 2027–2031 Demand-Side Management (DSM) Resource Plan, aiming to reduce electricity costs for customers. The plan aligns with NSEB's 2025 decision on DSM's statutory purpose, emphasizing affordability, energy savings, and climate goals through programs and cost-benefit analysis.
1.2 APPROVAL OF PURCHASE AGREEMENT WITH NS POWER - E1 also requests the NSEB's approval of its Purchase Agreement with NS Power, together with the - associated Performance Targets, which is attached in redline form as Appendix "D" and in c...
AI summary E1 seeks NSEB approval for a Purchase Agreement with NS Power, including Performance Targets. The agreement's terms align with previously approved DSM Plans (2016–2018, 2019, 2020–2022, 2023–2025, 2026 Extension). Appendices D (redline) and E (clean) are provided.
2. REGULATORY AND POLICY CONTEXT - The following sections set out the regulatory and policy context for the 2027–2031 DSM Plan and explain - how E1 has responded to each requirement in developing this Application.
AI summary Section 2 outlines the regulatory and policy context for the 2027–2031 DSM Plan, explaining how E1 has addressed each requirement in developing its Application.
2.1 LEGISLATION AND POLICY
AI summary This section outlines the legislative and policy framework governing energy regulation in Nova Scotia, referencing key acronyms such as DSM, PUA, NSEB, NS Power, and E1. It sets the context for subsequent regulatory discussions.
2.1.1 PUBLIC UTILITIES ACT - This Application must comply with the requirements set out in the Public Utilities Act , R.S.N.S. 1989, c. - 380 (" PUA "). An overview of these obligations is set out below. Notably, since the last multi-year...
AI summary The document outlines obligations under the Public Utilities Act (PUA) for NS Power, including demand-side management (DSM) requirements. Legislative changes via Bill 228 (2022) and Bill 6 (2025) extended DSM mandates and plan terms. NS Power must enter DSM agreements with franchise holders, while the Minister of Energy oversees franchise granting for efficiency programs.
2.1.3 COMPLIANCE WITH STATUTORY REQUIREMENTS As set out in the regulatory overview in Section 2.1 above, this Application must satisfy the requirements of the PUA and the considerations in s. 6(2) of the ERBA . E1 respectfully submits that...
AI summary E1 argues that its 2027–2031 DSM Plan complies with the PUA and ERBA by meeting statutory requirements, including cost-effectiveness and portfolio-level PAC test compliance. The Plan is deemed 'cost-effective' and 'reasonably available' per NSEB interpretations, with support from prior NSUARB decisions.
2.1.4 PROVINCIAL CLIMATE CHANGE POLICY The statutory considerations outlined in ERBA's section 6(2), as well as the goals of DSM as set out in section 79A of PUA, establish the primary mandate for DSM. While the Province's climate and ener...
AI summary Nova Scotia's Provincial Climate Change Policy emphasizes demand-side management (DSM) under the Public Utilities Act (PUA) to reduce electricity costs while aligning with climate goals. The Clean Power Plan outlines transitioning to renewable energy, grid modernization, and affordability, guided by legislative acts like the Environmental Goals and Climate Change Reduction Act. The Nova Scotia Energy Board (NSEB) balances regulatory mandates with environmental objectives.
7 2.2.1 2023–2025 DSM PLAN DECISION 8 The following directives from the 2023–2025 DSM Plan Decision are relevant to this Application: - (a) To provide detailed plans and processes for each of its research initiatives prior to proceeding wi...
AI summary The 2023–2025 DSM Plan Decision outlines four directives for E1, including detailed planning, collaboration with NS Power, cost-effectiveness justification, and payback information. E1 is complying with these directives as part of its response to the NSEB's approval of the DSM Plan.
2.2.1.1 COMPLIANCE WITH 2023–2025 PLAN DECISION In response to the directive to provide detailed plans and processes for each of its research initiatives prior to proceeding with significant expenditures, documented and fully discussed wit...
AI summary E1 developed an Innovation Framework for 2027–2031, complying with NSUARB directives on avoided cost calculations. They incorporated updated IRP data from NS Power and addressed climate change goals through DSMAG. The NSUARB directed updates to avoided costs, with DSMAG tasked to resolve climate integration for future DSM plans.
2.2.2 2025 APPLICATION FOR APPROVAL OF NEW BCA TEST DECISION The following directives from the NSEB's 2025 Decision on E1's application for approval of a new BCA test are relevant to this Application: [13](#page-21-0) - (a) To use the Prog...
AI summary The NSEB outlines directives for E1's 2025 application to approve a new BCA test, requiring use of the PAC test with NS Power's WACC as the discount rate, strategic electrification programs to reduce GHG emissions and costs, inclusion of Eastward Energy in the DSM Advisory Group, and specific reporting requirements for DSM Plans.
2.2.2.1 COMPLIANCE WITH 2025 BCA DECISION - E1 has designed the 2027–2031 DSM Plan in accordance with the directives set out in the 2025 BCA Test - Decision. The specific compliance responses are summarized below. - First, E1 has used the...
AI summary E1 has designed the 2027–2031 DSM Plan in compliance with the 2025 BCA Test Decision, using the PAC test with NS Power's WACC, excluding initiatives failing to reduce both GHG and costs, and including future research on strategic electrification. E1 also provided required data to NSEB, noted NS Power's lack of long-run emissions data, and confirmed Eastward Energy's DSMAG participation.
2.2.3 2026 DSM EXTENSION DECISION - In approving E1's 2026 DSM Plan Extension, the NSEB issued the following directives relevant to this - Application: [14](#page-23-0) - (a) To continue engagement with the DSMAG on the Standardized Filing...
AI summary The NSEB approved E1's 2026 DSM Plan Extension with directives to engage DSMAG, assess program concerns, and revise mid-course adjustment processes. E1 addressed these in the 2027–2031 DSM Plan. References include Matter M12282 and NSEB Decision M12249.
pirit of the balanced plan principles. E1 submits that its efforts with respect to engagement satisfies the Board's requirement set out in section 1 of its Order in the matter of the 2026 Extension. Second, E1 has addressed concerns about...
AI summary E1 asserts compliance with the 2026 DSM extension decision, adjusting its demand response programs (reducing residential, expanding BNI) and collaborating with NS Power on locational and stacking issues. It plans to address potential double-counting of savings and includes innovation efforts in its 2027–2031 framework.
2.3 STANDARDIZED FILING FRAMEWORK - The Standardized Filing Framework was filed with the NSUARB (as it then was), as part of a Consensus - Agreement on 2016–2018 DSM Plan Application Deferred Matters[15](#page-27-1) and was accepted by the...
AI summary The Standardized Filing Framework (SFF) was established in 2016 by the NSUARB to ensure consistency in DSM Plan applications. Recent updates, driven by the NSEB and DSMAG, aim to align the SFF with regulatory requirements and stakeholder feedback. E1 seeks NSEB approval for revised framework recommendations, which will inform future DSM Plan applications, including the 2027–2031 Application.
2.3.1 THE 2022 INTEGRATED RESOURCE PLAN - The Standardized Filing Framework directs that the Resource Plan identified in NS Power's Integrated - Resource Plan ("IRP") will serve to inform the development of a Preferred DSM Plan by E1. The...
AI summary NS Power's 2022 Evergreen IRP includes 683.1 GWh energy savings and 123.9 MW demand savings through 2031. E1 must balance long-term DSM benefits with short-term affordability, guided by the 2016 Consensus Agreement and referenced decisions (M07543, M10473, M12249).
2.4 DSMAG ENGAGEMENT - E1 undertook extensive engagement during plan development with the DSMAG Feedback informed - program design, delivery approaches, and equity‑focused enhancements. - The DSMAG is a forum of regulatory stakeholders who...
AI summary E1 engaged the DSMAG throughout the 2027–2031 DSM Plan development, incorporating stakeholder feedback to refine program design and modelling. DSMAG members included representatives from energy stakeholders, consumer groups, and regulatory bodies, with iterative review processes ensuring transparency and equity-focused improvements.
1 Table 1: 2027–2031 DSM Advisory Group Engagement Activities DSMAG Engagement Activity: 2027–2031 Timeline E1 provided responses to DSMAG comments received on the Round 2 Modelling comments. E1 also shared highlights of the Preferred Plan...
AI summary The document outlines engagement activities of the DSM Advisory Group (DSMAG) from 2027–2031, including meetings, comments, and presentations related to the Preferred Plan and modeling assumptions. Key participants include E1, the Consumer Advocate, and various stakeholders.
3 3.1 AFFORDABILITY - THE PRIMARY DESIGN CONSIDERATION 4 Consistent with the PUA and the NSEB's regulatory framework, affordability is the primary consideration 5 in the design of the 2027–2031 DSM Plan. The NSEB confirmed in its 2025 BCA...
AI summary Affordability is the primary focus for the 2027–2031 DSM Plan, with E1 maintaining $63.75M annual investment (total $318.75M) to avoid inflationary increases. This prioritizes short-term cost stability over long-term savings, reflecting economic pressures and DSMAG feedback. Customer incentives now account for 71% of costs, emphasizing direct rebates.
3.2 ENERGY EFFICIENCY: SETTING APPROPRIATE LEVEL OF ENERGY SAVINGS E1 established energy savings levels by balancing IRP guidance, cost‑effectiveness, delivery capacity, and affordability. The Preferred Plan reflects a continuation and evo...
AI summary E1 set energy savings at 0.8% of NS Power's load, balancing affordability, cost-effectiveness, and sector allocation. This aligns with APEX's jurisdictional scan and the 2023-2026 DSM Plan. The Preferred Plan allocates 29%/71% to residential/BNI sectors, with 11% of residential savings directed to low-income programs, consistent with prior targets.
3.2.1 THE ROLE OF THE IRP IN ESTABLISHING THE APPROPRIATE LEVEL OF DSM ENERGY SAVINGS One of the primary planning considerations for the development of the DSM Plan is NS Power's IRP. The IRP represents the most recent, comprehensive, and...
AI summary The IRP is central to the DSM Plan, providing a stakeholder-vetted assessment of optimal resource mix for Nova Scotia's electricity needs. NS Power's 2022 IRP incorporates updated policies like GHG targets and renewable goals, with DSM energy savings levels serving as a benchmark. Key themes include decarbonization, renewables, and electrification.
3.3 DEMAND RESPONSE The demand response design in the 2027–2031 DSM Plan was informed by a combination of observed implementation experience, updated modelling assumptions, evaluation insights, DSMAG member feedback, and alignment with sys...
AI summary The 2027–2031 DSM Plan's demand response design prioritizes cost-effectiveness, achievability, and system value, informed by E1's refined assumptions, DSMAG feedback, and alignment with NS Power's IRP. Residential participation remains limited due to variable results, but Eco Shift's inclusion is justified for resilience and long-term maturation. Peer jurisdictions indicate improving cost-effectiveness over time.
3.3.1 WHY RESIDENTIAL LOAD CONTROL DEMAND RESPONSE MATTERS Strategic peak reduction can help lower long-term infrastructure costs and moderate upward pressure on electricity rates. The IRP identifies both increasing electrification and a g...
AI summary Residential load control demand response reduces infrastructure costs and moderates electricity rates by managing peak demand. Electrification trends, like heat pump adoption, increase peak demand, necessitating demand response programs. Eco Shift and Ontario's Peak Perks program demonstrate residential DR's role in grid flexibility. Expansion aligns with IRP planning and discussions with NS Power and NSIESO.
6 3.3.2 COST-EFFECTIVENESS: A PROGRAM MATURITY ROADMAP 7 The 2023–2025 DSM Plan positioned demand response as a development and learning phase, with a focus 8 on identifying effective program pathways and refining operational delivery for...
AI summary The 2023–2025 DSM Plan positions demand response as a development and learning phase, focusing on identifying effective program pathways and refining operational delivery for initiatives like Eco Shift. This approach aligns with the typical evolution of residential demand response programs in North America, emphasizing early-stage learning and operational refinement before scaling.
21 Table 3: Demand Response Initiatives in other Jurisdictions Jurisdiction and DSM Utility Early-Stage Insights Ontario (IESO Peak Perks / Smart Thermostat DR) • Early years focused on recruitment and platform testing. • First-year MW per...
AI summary The text discusses demand response initiatives in other jurisdictions, including Ontario's Peak Perks program and Massachusetts' Wi-Fi thermostat programs. It highlights early-stage insights such as initial challenges with recruitment, platform testing, and baseline methodologies, as well as improvements over time in program economics and capacity stabilization.
6 7 Through direct discussions with the IESO Demand Side Management team, the program is expected to 8 reach cost-effectiveness under the Program Administrator Cost (PAC) test within the next year, 9 approximately four years after its laun...
AI summary The program is expected to achieve cost-effectiveness under the Program Administrator Cost (PAC) test within the next year, four years after its launch, due to factors like increased demand response capacity, higher customer participation, coordinated marketing, and adoption of bring-your-own thermostat models. Ontario's experience offers insights for smaller jurisdictions.
21 3.3.3 TECHNOLOGY & FIELD LEARNING Program deployment to date has provided valuable operational experience and insights into the technologies that deliver the strongest performance and program economics. This includes heat pump hot water...
AI summary Program deployment has enhanced operational experience with technologies like heat pump hot water controllers, behind-the-meter batteries, and smart thermostats. Improvements in workflows, dispatch strategies, and vendor relationships have reduced costs and improved demand response reliability during peak events.
3.3.4 SUMMARY - Eco Shift continues to demonstrate measurable progress as it moves through its development phase. - Preliminary results show increasing customer participation and improved device responsiveness across - multiple technologie...
AI summary Eco Shift demonstrates measurable progress with increased customer participation and device responsiveness, enhancing demand response capacity and cost-effectiveness under PAC. Operational refinements, scaling participation, and alignment with constrained system areas are expected to reduce costs and improve reliability. Eco Shift is projected to achieve cost-effectiveness within two to three seasons.
3.4 SOLAR-PV - E1 submits that customer sited solar-PV falls squarely within the statutory definition of demand-side - management under section 79A(b)(v), which includes DSM activities relating to "the delivery of a - reduction in the amou...
AI summary E1 argues customer-sited solar-PV qualifies as demand-side management (DSM) under the PUA, reducing NS Power's required supply. The program targets Mi'kmaw communities to address participation barriers, align with equity goals, and support reconciliation. The 2027–2031 DSM Plan includes 200 installations (0.9% of total DSM investment) focused on these communities, with future expansion contingent on cost-effectiveness and Energy Board approval.
3.5 STRATEGIC ELECTRIFICATION Strategic electrification was added to E1's mandate by way of an update to section79A(b)(iv) of the PUA in 2022, as outlined in section [2.1.1](#page-8-3) above. The NSEB, in its decision on E1's BCA clarified...
AI summary Strategic electrification was added to E1's mandate via a 2022 PUA update. The NSEB requires strategic electrification to reduce both GHG emissions and electricity costs. E1 supports its inclusion in the 2027–2031 DSM Plan if it meets these criteria, though the Clean Power Plan lacks cost assumptions for guidance. The 2022 Evergreen IRP includes electrification scenarios but not optimal savings levels.
8 3.6 ENABLING STRATEGIES 9 Enabling Strategies are a foundational component of E1's DSM portfolio. These investments support the development, delivery, and long-term effectiveness of DSM programs by addressing structural, market, and info...
AI summary Enabling Strategies are a key component of E1's Demand-Side Management (DSM) portfolio, aimed at addressing structural, market, and informational barriers. The 2027–2031 DSM Plan includes targeted investments in education, research, development, and market transformation, with adjustments made for affordability and long-term effectiveness.
23 Table 4: Comparison of 2026 and 2027–2031 Annual Investment in Enabling Strategies 2026 DSM Extension ($M) 2027–2031 DSM Preferred Plan Annual Average ($M) Education & Outreach $1.6 $1.3 Development & Research $1.6 $1.4 Other Enabling S...
AI summary Table 4 compares annual investments in Enabling Strategies for the 2026 DSM Extension and the 2027–2031 DSM Preferred Plan. The total investment decreases from $7.0M in 2026 to $5.8M annually for the 2027–2031 period, with reductions observed in most categories except for Market Transformation.
1 4. AFFORDABILITY 2 Affordability continues to be a critical factor in determining the level of investment in a DSM Plan. E1 has 3 heard from several members of the DSMAG over the past several DSM Plans that consideration of short-4 term...
AI summary Affordability remains a key consideration in DSM Plan investments. E1 maintains annual investment at the 2026 level of $63.75 million without inflationary increases, balancing short-term affordability concerns (e.g., rising housing/energy costs) against NS Power's IRP-driven long-term economic benefits for ratepayers.
14 4.1 THE 2027–2031 DSM PLAN CONTINUES TO PRIORITIZE CUSTOMERS E1's DSM Plan continues to prioritize customers by ensuring that the investment in customer incentives remains not only the largest portion of the $63.75 million per year but...
AI summary E1's 2027–2031 DSM Plan prioritizes customers by increasing customer incentives from 66% to 71% of total investment compared to the 2026 DSM Extension, with annual funding of $63.75 million. This reflects a shift toward greater customer-focused spending within the overall DSM strategy.
1 Figure 2: 2027–2031 DSM Preferred Plan Average Annual Expenditures
AI summary The document presents Figure 2, which outlines the average annual expenditures for the 2027–2031 DSM Preferred Plan. It is part of a regulatory proceeding in Nova Scotia, focusing on demand-side management strategies and their financial implications. The figure is referenced in the context of energy policy and utility regulation, though specific data or analysis within the text is not provided.
4 Figure 3: 2026 DSM Plan Expenditures
AI summary Figure 3 outlines 2026 Demand-Side Management (DSM) Plan expenditures, part of a Nova Scotia regulatory proceeding. It references entities like NS Power, NSEB, and E1, with context on energy planning and regulatory frameworks under the Public Utilities Act and Energy and Regulatory Boards Act.
1 4.2 DSM REMAINS AT A LOWER COST THAN THE FUEL OPTION 2 DSM, and particularly its energy efficiency programs, is demonstrably lower in price than the fuel option 3 it displaces, making it a logical and affordable first choice investment f...
AI summary Demand-Side Management (DSM), especially energy efficiency programs, is shown to be more cost-effective than fuel options, with DSM costing less than fuel by up to 4 cents per kWh. This makes DSM a preferable investment for ratepayers, as it reduces fuel costs and benefits all ratepayers through the fuel adjustment mechanism (FAM).
Table 5: Cost Difference of DSM and Fuel Cost Difference Between DSM & Fuel Year Cost of Fuel as Compared to DSM (Difference $ per kWh) Fuel Cost as % of DSM 2015 0.031 271% 2016 0.029 283% 2017 0.024 229% 2018 0.037 296% 2019 0.040 312% 2...
AI summary Table 5 compares the cost difference between Demand-Side Management (DSM) and fuel over various years, showing that fuel costs are significantly higher than DSM costs, with fuel costs as a percentage of DSM costs increasing over time, except in 2024. Section 4.3 highlights that DSM continues to provide lasting benefits with a short payback period.
4.4 DSM CONTINUES TO BE THE LEAST RISK OPTION - DSM is a low-risk energy investment as there is: - Certainty with respect to the level in investment; - No unexpected costs associated with an investment in DSM; and - No variability in the c...
AI summary DSM is identified as the least risky energy investment due to capped spending, no unexpected costs, and E1's consistent performance. Ratepayers benefit from cost certainty, while fuel and capital projects by NS Power carry higher risks and volatility. E1's reliability ensures adherence to approved spending levels, minimizing financial uncertainty.
4.5 RATE AND BILL CONSIDERATIONS & RATE AND BILL IMPACT ANALYSIS (RBIA) FOR 2027–2031 E1's RBIA for the Preferred Plan demonstrates that participants in DSM benefit from bill savings. The reductions in energy use and demand achieved by par...
AI summary E1's Rate and Bill Impact Analysis (RBIA) for the Preferred Plan shows that DSM participants benefit from bill savings, with energy efficiency and demand response having positive effects on rates, and solar-PV having minimal impact. These findings are consistent with historical data from 2011 to 2026.
21 Table 6: Preferred Plan – Average Rate Impacts by Resource over 2027-2046 Residential Small General General Large General Small Industrial Medium Industrial Large Industrial Municipal DSM (All Resources) 0.58% 0.88% 0.74% 0.33% 0.76% -0...
AI summary Table 6 presents the average rate impacts by resource over the period 2027-2046 for various customer classes. The table highlights the impact of different resources such as DSM, Energy Efficiency, Demand Response, and Solar-PV on residential, small general, general, large general, small industrial, medium industrial, large industrial, and municipal customers.
4.5.1 HISTORICAL RBIA - 24 E1's 2026 Historical RBIA indicates that ratepayers are already positioned to accrue aggregate bill savings - in excess of $2.5 billion between 2011 and 2041 as a result of past DSM activities between 2011 and 20...
AI summary E1's 2026 Historical RBIA indicates that past Demand-Side Management (DSM) activities between 2011 and 2026 will result in over $2.5 billion in aggregate bill savings for ratepayers from 2011 to 2041. Figure 5 illustrates average rate and bill impacts by rate class.
4.5.2 2 027–2 03 1 RBIA Investment at the Preferred Plan level would result in average rate impacts that range between -0.1 percent and +0.9 percent by rate class, averaged over the lifetime of measures [(Figure 6)](#page-50-0). These figu...
AI summary Investment in the Preferred Plan for 2027–2031 results in minimal rate impacts (−0.1% to +0.9%) but significant bill reductions (0.04% to 37%) for DSM participants. Figures 6–8 illustrate these impacts, highlighting benefits for all customers despite negligible rate changes.
3 5. THE BALANCED PLAN APPROACH - 4 The portfolio was developed in accordance with the "Balanced Plan Approach" outlined in the - 5 Standardized Filing Framework, which directs E1 to "produce DSM Resource Plans that balance multiple - 6 as...
AI summary E1 developed a portfolio under the 'Balanced Plan Approach' to balance DSM aspects, achieving 435.4 GWh energy savings, 85.0 MW demand savings, and other metrics by 2031. Principles include energy/capacity avoidance, cost efficiency, non-electric benefits, and equitable access. The plan emphasizes value for Nova Scotians through diversified programs and market engagement.
6 5.1 SHORT- AND LONG-TERM ENERGY AND CAPACITY AVOIDANCE 7 The Preferred Plan achieves a balance of both short- and long-term energy capacity avoidance. Dunsky 8 Energy Consulting described the balanced plan approach, and in particular sho...
AI summary The Preferred Plan balances short- and long-term energy and capacity avoidance. Short-term savings focus on immediate measures like appliances, while long-term strategies involve market transformation through education and standards. DSM investments provide immediate bill savings and long-term avoided infrastructure costs.
ficiency measures, which is increasingly important in the current economic context. Several factors have contributed to changes in unit delivery costs between the 2023–2026 and 2027–2031 Plan periods: - (a) The conclusion of the federal go...
AI summary The document outlines factors increasing DSM program delivery costs between 2023–2026 and 2027–2031, including the end of federal grants, shifts to complex measures, inflation, and reduced savings from heat pump evaluations. E1's increased incentives and economic pressures are highlighted as key drivers.
5.3 AVOIDED ENERGY AND CAPACITY INVESTMENTS - DSM provides value to ratepayers in part by avoiding investments associated with supply side resources. - In Nova Scotia, the following categories of avoided system costs are applied to DSM: -...
AI summary Demand-Side Management (DSM) in Nova Scotia avoids energy and capacity investments by reducing demand. The Preferred Plan emphasizes energy efficiency, demand response, and solar-PV initiatives. Categories of avoided costs include energy, capacity, transmission, and distribution. EfficiencyOne (E1) expanded demand response programs to address NS Power's growing demand.
5.5 DIVERSITY OF PROGRAM DELIVERY - Diversity in program delivery is a key way to minimize risk and involves the diversification of measures, - markets and strategies. The Preferred Plan includes a full suite of programs and strategies tha...
AI summary Diversity in program delivery reduces risk by diversifying measures, markets, and strategies. The Preferred Plan includes a broad range of programs targeting residential and BNI sectors. E1's diversified portfolio aims to ensure equitable participation despite higher unit costs or lower benefit/cost ratios for some opportunities.
DIVERSE MEASURES - The Preferred Plan continues to evolve E1's measure mix. The Plan features 341 measures, and 11 - energy efficiency program components, and 2 demand response program components and one solar-PV - program component.
AI summary The Preferred Plan includes 341 measures, with 11 energy efficiency programs, 2 demand response programs, and 1 solar-PV program. E1's measure mix is evolving to incorporate diverse initiatives under the Nova Scotia regulatory framework.
DIVERSE STRATEGIES - The Preferred Plan includes diverse strategies recognizing that no single delivery model effectively - reaches the full range of customers, market sectors, and technologies served by DSM. The portfolio - incorporates a...
AI summary The Preferred Plan employs diverse DSM strategies, combining delivery models like turn-key partnerships, contractor-based delivery, and market-enabled offerings. It includes technical support, rebates, direct installation, and self-serve options. The heat pump water heater pilot is part of Enabling Strategies to support E1's model through 2031. 2023-2025 results and the 2026 Plan are referenced with residential behavior savings removed.
5.8 RATE IMPACTS In designing the Preferred Plan portfolio, E1 explicitly balanced near-term rate impacts with the long-term value delivered to ratepayers. The portfolio reflects a measured approach to investment, limiting it to the same i...
AI summary E1's Preferred Plan balances near-term rate impacts with long-term value by maintaining 2026 investment levels, diversifying programming across customer classes, and prioritizing cost-effective, long-lasting measures. The approach emphasizes affordability, system flexibility, and equity through targeted low-income programs and efficient delivery, supported by a forward-looking Rate and Bill Impact Analysis.
1 6. PREFERRED PLAN DETAILS
AI summary The section titled 'Preferred Plan Details' is part of a regulatory proceeding document in Nova Scotia, though no substantive content is provided in the given text. It likely outlines details of a preferred plan for energy management or utility regulation.
2 6.1 OVERVIEW - 3 The Preferred Plan represents a comprehensive suite of programs and service offerings which will deliver - 4 approximately 435.4 GWh of affordable, incremental net energy savings, 85.0 MW of cumulative system- - 5 peak d...
AI summary The Preferred Plan outlines a comprehensive suite of energy efficiency programs and service offerings that aim to deliver significant energy savings and demand reductions over the 2027–2031 period. It emphasizes affordability, long-term ratepayer benefits, and cost-effectiveness, with a focus on achieving energy efficiency at a lower lifetime unit cost compared to fuel costs.
6.2 HIGHLIGHTS OF THE 2027–2031 PLAN - Key highlights/portfolio insights of the 2027–2031 Preferred Plan include: - portfolio cost-effectiveness result of 2.4 for the Program Administrator Cost (PAC) test - demonstrating that the portfolio...
AI summary The 2027–2031 Preferred Plan highlights a portfolio cost-effectiveness result of 2.4, a $318.75 million investment in DSM resources, and expected lifetime benefits of $682.5 million for participating customers. The plan also includes new components like Mi'kmaw New Home Construction and residential solar-PV for Mi'kmaw communities.
Table 7: 2027–2031 Plan - Portfolio Level Insights Insights 2027–2031 Energy Efficiency Energy Savings as % of NS Power Load 0.8% Energy Savings (EE) Split (RES/BNI) 29/71 Demand Savings (EE) Split (RES/BNI) 44/56 Dedicated Low-Income & Eq...
AI summary Table 7 provides insights into the 2027–2031 plan, highlighting energy efficiency savings, demand response capacity, solar-PV generation, and associated costs and benefits. It includes metrics such as energy savings percentages, unit costs, and CO₂e savings across residential and BNI (Business and Non-Industrial) sectors.
6.3.1 2 PORTFOLIO SAVINGS & INVESTMENT - 3 Table 8 provides portfolio-level savings, inclusive of all proposed DSM resources for the 2027–2031 DSM - 4 Preferred Plan.
AI summary Table 8 outlines portfolio-level savings from all proposed DSM resources under the 2027–2031 DSM Preferred Plan. The data includes savings projections for demand-side management initiatives during this period.
6 Table 8: 2027–2031 DSM Preferred Plan Portfolio Savings and Investment 2027-2031 Portfolio Year Investment ($M) Lifetime Benefits ($ million) First-Year Energy Savings (GWh) Peak Demand Savings (MW) Lifetime Energy Savings (GWh) Low-Inco...
AI summary Table 8 outlines the 2027–2031 DSM Preferred Plan Portfolio Savings and Investment, showing annual investments, energy savings, peak demand reductions, and other metrics related to demand-side management programs in Nova Scotia.
1 6.3.2 PROGRAM SAVINGS & INVESTMENT - 2 Table 9, below, provides the five-year savings and investment details by program component for the - 3 2027–2031 Preferred Plan. Detailed information by year is provided in Appendix A.
AI summary This section introduces Table 9, which outlines five-year savings and investment details by program component for the 2027–2031 Preferred Plan, with detailed annual information provided in Appendix A.
- 5 Table 9: 2027–2031 DSM Preferred Plan Savings and Investment by Program Component 2027-2031 Investment ($ million) Lifetime Benefits ($ million) First Year Energy Savings (GWh) Lifetime Energy Savings (GWh) Peak Demand Savings (MW) Ava...
AI summary Table 9 presents the investment and savings projections for various residential energy efficiency programs under the 2027–2031 DSM Preferred Plan. The table highlights program components such as efficient product rebates, home energy assessments, and initiatives targeting low-income and equity impacts, detailing investments, lifetime benefits, energy savings, and other metrics.
1 6.4 KEY ENHANCEMENTS FOR 2027–2031 - 2 The 2027–2031 DSM Plan (Appendix A) provides fulsome program details on the activities proposed as - 3 part of the Purchase Agreement. [Table 10,](#page-65-1) below provides the modifications and en...
AI summary The 2027–2031 DSM Plan (Appendix A) outlines program details for the Purchase Agreement, with Table 10 highlighting modifications compared to the 2023–2026 Plan. Key enhancements focus on demand-side management initiatives and updated program structures.
5 Program Program Component Changes from 2023–2026 Plan 2027–2031 Status Residential Efficient Product Rebates Appliance Retirement • Component ended in 2025 following declining savings, rising delivery costs, and limited availability of s...
AI summary The document outlines changes to residential energy efficiency programs in Nova Scotia, including the retirement of the Appliance Retirement component, modifications to the Instant Savings program, and updates to the Affordable Multifamily Housing and Efficient Product Installation programs. These changes reflect adjustments in incentive levels, expansion of rebate categories, and enhancements to customer experience.
- 3 E1's success in implementing an approved DSM Plan is evaluated through Performance Targets. The 4 Standardized Filing Framework sets out the performance targets and thresholds which must be met - 5 through the execution of the DSM Plan...
AI summary E1's success in implementing an approved DSM Plan is evaluated through Performance Targets set by the Standardized Filing Framework. E1 is proposing targeted solar-PV activities and a new Performance Target as part of its Preferred Plan, with compliance measured based on achieving at least 90 percent of the targets over the NSEB-approved Purchase Agreement period.
16 Table 11: Proposed 2027–2031 DSM Preferred Plan Performance Targets Available Energy Peak Demand Low-Income & Demand Solar-PV DSM Resource Savings Savings Equity Energy Response Generation (GWh) (MW) Savings (GWh) Capacity (GWh) (MW) En...
AI summary Table 11 outlines the proposed 2027–2031 DSM Preferred Plan Performance Targets, including energy efficiency savings, peak demand reductions, low-income and equity energy savings, demand response capacity, and solar-PV generation targets.
19 8.1 MID-COURSE ADJUSTMENT PROCESS 20 On the issue of Mid-Course Adjustments (MCAs), the NSEB in its Decision in the 2026 Extension Plan 21 (M12249) stated: 22 [73] The concerns raised by the Industrial Group are serious. The potential f...
AI summary The NSEB expressed concerns about E1's Mid-Course Adjustment (MCA) process, citing potential unfair impacts on rate classes funding E1's work. The NSEB directed E1 to revise its MCA process to allow greater ratepayer input and align spending with NSEB-approved rate classes. E1 acknowledged these concerns and agreed to engage with the DSMAG to address issues related to cost management and program flexibility.
8.2 MID-TERM CHECK-IN - Following the 2022 amendment to the PUA extending DSM Plans from three years to five years, DSMAG - members expressed concerns regarding performance risk and oversight over the longer plan term. In - response to sta...
AI summary Following the 2022 PUA amendment extending DSM plans to five years, DSMAG raised concerns about oversight. E1 proposes a mid-term check-in process to enhance transparency and stakeholder engagement without reopening the plan, aligning with the Legislature's intent to reduce regulatory proceedings. E1 maintains existing reporting mechanisms and NSEB oversight remain intact.
8.3 OTHER REPORTING PROCESSES E1 will submit six reports annually to the NSEB, including quarterly reports (Q1-Q3), an annual progress report, annual DSM program evaluation reports, and annual audited financial statements. Over the 2027– 2...
AI summary E1 must submit 30 DSM reports to NSEB over 2027–2031, including quarterly, annual progress, program evaluation, and audited financial reports. NSEB verifies savings and allows DSMAG input. E1 will follow NSEB-approved measurement and evaluation protocols, with further details in Appendix A.
5 9.1 OVERVIEW - Pursuant to the NSUARB directive,[27](#page-73-4) 6 E1 is required to file one or more alternate scenarios (the "Alternate - 7 Scenario") in addition to its Preferred Plan filing. In the stakeholder engagement process prec...
AI summary E1 is required by the NSUARB to file an Alternate Scenario as part of its Preferred Plan, incorporating energy efficiency, demand response, solar-PV, and strategic electrification. Stakeholders emphasized addressing short-term affordability impacts, prompting E1 to provide a fully costed DSM scenario.
9.2 SCENARIO IN ACCORDANCE WITH THE STANDARDIZED FILING REQUIREMENTS. The Alternate Scenario represents a total investment in energy efficiency, demand response and solar PV of $308.4 million over the 2027–2031 DSM Plan. The design approac...
AI summary The Alternate Scenario invests $308.4 million in energy efficiency, demand response, and solar PV from 2027–2031. It maintains low-income and equity-focused investments while eliminating the Eco Shift program to address cost-effectiveness concerns and balance DSMAG perspectives.
10. CONCLUSION - Based on the supporting Evidence and Appendices, E1 respectfully requests approval from the Energy - Board for the Preferred Plan and related Purchase Agreement with NS Power. 27 M06733, NSUARB Order, E1 2016–2018 DSM Plan...
AI summary E1 requests approval for the Preferred Plan and related Purchase Agreement with NS Power, emphasizing its affordability and cost-effectiveness. The plan includes energy savings, demand reduction, and system benefits, with a total investment of $318.75 million over five years. E1 claims the application meets the mandatory approval test under the Public Utilities Act.
GLOSSARY OF TERMS Term Definition Alternate Scenario E1 provides one or more alternate scenario(s) with the same portfolio-level metrics as E1's proposed DSM Resource Plan (i.e., the Preferred Plan). Available Demand Response Capacity The...
AI summary The glossary defines key terms related to demand-side management (DSM) and energy efficiency programs, including alternate scenarios, demand response capacity, balance adjustments, and baseline measurements. These definitions are relevant to the regulatory process and program implementation.
1.1 OBJECTIVES OF THE 2027–2031 DSM PREFERRED PLAN - E1's objectives for the 2027–2031 DSM Preferred Plan include: - 1. deliver cost-effective demand side resources that support the successful implementation of a long-term electricity stra...
AI summary E1's 2027–2031 DSM Preferred Plan aims to deliver cost-effective demand-side resources aligned with ratepayer interests, ensure equitable access to services, and foster transparent stakeholder collaboration in resource planning.
1.2 REPORT ORGANIZATION - Appendix A provides the following: - overview of the development of the Preferred Plan including approach and methodology; - overview of the proposed portfolio and program targets, investment levels, and performan...
AI summary The report outlines its organizational structure, detailing sections covering DSM plan results, development approaches, portfolio overviews, program descriptions, enabling strategies, performance metrics, and reporting. Appendix A includes the Preferred Plan's methodology, program targets, and a DSM Purchase Agreement under the PUA. Sections 2–13 provide historical data, plan development, program specifics, and evaluation frameworks for 2027–2031.
7 2. PREVIOUS DSM PLAN RESULTS
AI summary The section reviews outcomes of past Demand Side Management (DSM) plans, focusing on energy efficiency, cost recovery mechanisms, and compliance with regulatory frameworks. It highlights metrics, challenges, and alignment with Nova Scotia's energy policies.
8 2.1 2023–2026 DSM PLAN 9 E1's current approved DSM Plan (2023–2026) provides for the delivery of DSM programs through the end of 2026. [1](#page-90-2) With three of the four Plan years now complete, E1 has made substantial progress towar...
AI summary E1 has made significant progress towards its 2023–2026 DSM Plan performance targets, achieving 82% of energy savings, 84% of demand savings, and 84% of energy savings for affordable housing and Mi'kmaw projects. The 2026 DSM Extension is expected to help achieve 90% compliance for all targets by December 31, 2026.
2 Table 1: 2023–2026 Approved Plan and Results Year Investment ($ million) Lifetime Benefits ($ million) First-Year Energy Savings (GWh) Lifetime Energy Savings (GWh) Peak Demand Savings (MW) Available Demand Response Capacity (MW) Low-Inc...
AI summary The table presents the 2023–2026 Approved Plan and Results for energy efficiency programs, detailing investments, benefits, energy savings, and program administrator costs. It compares approved plans with actual results and provides percentages of achievement for various metrics across the years.
2.2 DISCUSSION OF 2023-2025 RESULTS E1's 2025 Annual Progress Report (APR), filed March 31, 2026, provides detailed discussion of 2025 results and cumulative progress toward the 2023–2026 DSM Plan performance targets. Results for 2023 and...
AI summary E1's 2025 Annual Progress Report (APR) details 2025 results and cumulative progress toward 2023–2026 DSM Plan targets, noting implementation challenges like market changes and program adjustments. Results are contextualized within the DSM Plan period, with insights informing the 2026 DSM Extension and future planning. References to prior APRs (2023–2024) and regulatory approvals are included.
2.2.5 AVAILABLE DEMAND RESPONSE CAPACITY Demand response was introduced as a new program in 2023 following pilot initiatives undertaken from 2020-2022. In the 2023 season (December 1, 2022 to February 28, 2023), early implementation challe...
AI summary Demand Response (DR) program challenges in 2023–2025 included participant drop-outs, operational constraints, and technical issues like controller removals. E1 adjusted strategies for 2026, improving engagement and infrastructure, leading to early 2026/2027 results doubling 2024/2025 capacity. Target of 16.3 MW available capacity is expected to be met.
2.2.6 UNIT COST RESULTS Unit cost data is a calculation output reflecting E1's investment and energy savings over a defined time period. Actual results for the 2023–2025 period show a portfolio-level unit cost of $0.37/kWh, slightly lower...
AI summary The 2023–2025 unit cost for E1's energy efficiency programs was slightly lower than the approved plan, but residential unit costs have risen due to the pause of the Residential Behaviour program and changes in program components. These trends are expected to continue into 2026 and influence the development of the 2027–2031 DSM Preferred Plan.
2.2.7 2023–2026 DSM PLAN RATE CLASS RESULTS - 7 E1 has provided 2023–2025 rate class results, in addition to 2026 DSM Extension anticipated results, - 8 compared to the approved 2023–2026 Plan, in Table 2, below. 9 10 11 12 13 14 2025 actu...
AI summary E1 has provided 2023–2025 rate class results and 2026 DSM Extension anticipated results, compared to the approved 2023–2026 Plan. 2025 actual expenditures were slightly lower than the approved 2025 Plan, with the medium industrial rate class showing higher spending due to increased participation in the BNI Demand Response program.
3 2.3 CUMULATIVE DSM SAVINGS AND INVESTMENT: 2012-2025 4 [Table 4,](#page-100-0) below, presents E1's cumulative DSM Plan savings and expenditures from 2012 to 2025 compared with the corresponding Board-approved Plans.[4](#page-99-2) 5 6 7...
AI summary This section discusses E1's cumulative DSM savings and investment from 2012 to 2025, noting that expenditures are 6% below the Board-approved investment, while energy and demand savings are 5% above the approved targets. Factors such as program mix and market conditions are cited as reasons for the underspend in earlier years.
11 Table 4: Cumulative DSM Savings and Investment : 2012–2025 Plan as Approved Results Year Investment ($ million) First-Year Energy Savings (GWh) Peak Demand Savings (MW) Available Demand Response Capacity (MW) Low-income & Equity Energy...
AI summary Table 4 provides a detailed breakdown of cumulative demand-side management (DSM) savings and investment from 2012 to 2025, including energy savings, peak demand savings, and expenditures. It compares the approved plan with actual results for each year, highlighting trends in investment and savings over time.
1 3. PLAN DEVELOPMENT AND DESIGN APPROACH 2 E1 developed the 2027–2031 DSM Preferred Plan through a multi-phase process to establish a cost- 3 effective DSM portfolio. This process defined the DSM resources to be offered, the level of savi...
AI summary E1 developed the 2027–2031 DSM Preferred Plan through a multi-phase process involving stakeholder engagement, scenario modeling, and regulatory considerations. The plan incorporates updated avoided costs, aligns with climate targets, and reflects NSEB decisions on BCA and DSM extensions. Development was paused briefly due to PUA amendments and resumed after filing the 2026 DSM Extension.
3.1 DSMAG ENGAGEMENT IN THE DEVELOPMENT PROCESS DSMAG engagement played a central role in development of the 2027–2031 DSM Preferred Plan. Throughout the planning process, E1 engaged a range of DSMAG members including rate class representa...
AI summary DSMAG played a central role in developing the 2027–2031 DSM Preferred Plan through iterative engagement with stakeholders, including government representatives, industry groups, and experts. E1 incorporated feedback via modelling reviews, written submissions, and meetings, shaping both the Preferred Plan and Alternate Scenario.
3.2 PORTFOLIO DESIGN CONSIDERATIONS AND ASSUMPTIONS - E1 was guided by the following key considerations in developing the Preferred Plan: - cost-effectiveness; - determining appropriate energy and demand savings established using a percent...
AI summary E1's Preferred Plan prioritizes cost-effectiveness, achievable energy savings via a percent-of-load approach, support for Mi'kmaw communities post-2027, and balanced portfolio principles. Emphasis is on affordability, performance targets, and long-term ratepayer benefits through appropriate investment levels.
3.2.1 RESOURCE SCENARIO DESIGN In developing the Plan's design approach, E1 considered feedback from the DSMAG indicating limited support for the three design objectives historically used to guide recent DSM Plans: a 50/50 investment DATE...
AI summary E1 revised its DSM Plan design approach based on feedback from the DSMAG, maintaining the annual investment level, adjusting energy savings targets and allocations, and ensuring support for low-income and equity communities. The plan aligns with recommendations from APEX and includes a residential/BNI energy savings split of 29/71, with dedicated low-income savings of 11% of residential savings.
3.3 MODELLING - The "modelling process" refers to the use of DSM portfolio design tools to assess the comparative costs, - savings, and cost-effectiveness of various DSM resource scenarios to determine the Preferred portfolio - design for...
AI summary The modelling process evaluates DSM resource scenarios using ProCESS™ and DRSIM™ tools to assess cost-effectiveness, energy impacts, and expenditures for the 2027–2031 DSM Resource Plan. Guidehouse supports E1 in developing the preferred portfolio design through these analyses.
8 3.3.1 MODELLING PROCESS - 9 The following sections provide a high-level overview of the 2027–2031 DSM Resource Plan modelling - process, followed by a description of each stage in the process.
AI summary The text outlines the high-level overview and stages of the 2027–2031 DSM Resource Plan modelling process, focusing on Demand Side Management strategies.
3.3.1.1 MODEL CONFIGURATION - At the outset of the modelling process, E1 and Guidehouse reviewed and confirmed the overall modelling - framework for the 2027–2031 DSM Resource Plan, and configured the following modelling tools - associated...
AI summary E1 and Guidehouse configured ProCESS™ and DRSim™ models for the 2027–2031 DSM Resource Plan, aligning with NSEB directives. Model updates ensured parameters, inputs, and methodologies met E1's planning requirements and regulatory standards.
3.3.1.2 MODEL INPUTS AND ASSUMPTIONS - Once the models were configured, E1 and Guidehouse compiled the key modelling inputs and - assumptions required for all subsequent modelling steps associated with the DSM Plan. These included - global...
AI summary E1 and Guidehouse compiled model inputs and assumptions for the DSM Plan, including global factors (avoided costs, discount rates) and program-specific data. Inputs were reviewed and adjusted for 2027–2031, with new measures informed by engineering assumptions and external data. Details are in Attachment 1.
10 3.4 COST-EFFECTIVENESS - 11 In the Energy Board's Decision regarding E1's Application for approval of a New Benefit-Cost Analysis Test - for Evaluating Demand Side Management Plans (M12282), the Energy Board directed E1 to:[9](#page-107...
AI summary E1 must use the Program Administrator Cost (PAC) test for evaluating its 2027–2031 Demand Side Management (DSM) Plan, with NS Power's WACC (6.65%) as the discount rate. The Energy Board directed this under the Public Utilities Act (PUA), requiring portfolio-level cost-effectiveness screening. E1 achieved a PAC result of 2.4 (above the 1.0 threshold) and provided justifications for measures failing cost-effectiveness tests.
16 4.1 PORTFOLIO KEY INSIGHTS The 2027–2031 DSM Preferred Plan will invest $318.75 million to achieve 435.4 GWh of incremental cumulative net energy savings, 85.0 MW of cumulative system-peak demand savings, 29.3 MW of available capacity f...
AI summary The 2027–2031 DSM Preferred Plan is projected to invest $318.75 million to achieve significant energy savings, demand reductions, and solar-PV generation. Key insights and impacts are detailed in Table 5.
22 Table 5: 2027–2031 DSM Preferred Plan Portfolio Level Insights Insights 2027–2031 Energy Efficiency Energy Savings as % of NS Power Load 0.8% Energy Savings (EE) Split (RES/BNI) 29/71 Demand Savings (EE) Split (RES/BNI) 44/56 Dedicated...
AI summary Table 5 provides insights into the 2027–2031 DSM Preferred Plan Portfolio, detailing energy efficiency and demand response metrics, including energy savings percentages, cost splits between RES and BNI, and unit costs for energy and demand savings.
Generation Split (RES/BNI) First-Year Unit Cost ($/kWh) Lifetime Unit Cost ($/kWh) Lifetime Benefits ($ million) First Year Energy Savings (GWh) Lifetime Energy Savings (GWh) Peak Demand Savings (MW) Available Capacity (MW) First-Year CO 2...
AI summary The text presents a table with metrics related to energy generation and demand-side management (DSM) programs, including unit costs, energy savings, and capacity splits. It highlights the 'Total Preferred Plan' and provides data for the years 2027-2031, focusing on RES/BNI split and program performance indicators.
68.2 1 Levelized unit cost of demand response is calculated by taking the net present value of investment and available to the control of the cost of demand response is calculated by taking the net present value of investment and available...
AI summary The text discusses the calculation of the levelized unit cost of demand response, emphasizing the use of net present value of investment and available capacity. However, the content is repetitive and lacks clarity or additional context.
4.2 PORTFOLIO KEY OBSERVATIONS
AI summary Section 4.2 discusses portfolio key observations related to energy management, regulatory frameworks, and programs in Nova Scotia. It references acronyms like DSM, PUA, NSEB, and NS Power, highlighting topics such as demand response, energy efficiency, and utility rate design.
Key observations of the Preferred Plan include: - annual investment for the Preferred Plan is maintained at the 2026 DSM Extension approved investment level of $63.75 million, with no annual inflationary increases to the investment, to sup...
AI summary The Preferred Plan maintains a fixed annual investment of $63.75 million with no inflationary increases, aiming to support affordability. Energy savings have declined due to market shifts and program closures. The plan supports Mi'kmaw communities and shows strong cost-effectiveness with a 114% ROI and a 30-year solar-PV measure life. However, some low-income programs have lower PAC scores.
1 Figure 1: 2027–2031 DSM Preferred Plan – Payback DSM investment includes EE, DR, Solar-PV and Enabling Strategies. Green bars are nominal investment. Blue bars are nominal avoided cost. Yellow line is a 2027 net present value (NPV) of th...
AI summary The 2027–2031 DSM Preferred Plan – Payback includes investments in Energy Efficiency (EE), Demand Response (DR), Solar-PV, and Enabling Strategies. Green bars represent nominal investment, blue bars show avoided costs, and the yellow line depicts NPV using NS Power's WACC. The analysis evaluates cost recovery and financial viability of DSM initiatives.
7 Table 6: Summary of Changes and Enhancements in the 2027–2031 DSM Preferred Plan Area of Change Change/New Element Rationale and Context • Green Heat ended in 2025 • Green Heat ended due to declining participation • Appliance Retirement...
AI summary The 2027–2031 DSM Preferred Plan outlines several program adjustments, including the end of Green Heat and Appliance Retirement due to low participation and rising costs. The Mi'kmaw Home Energy Efficiency Project is set to conclude by mid-2027, and the Residential Behaviour program is being reevaluated for potential discontinuation.
DATE FILED: March 31, 2026 Page 24 of 112 Area of Change Change/New Element Rationale and Context beneficial initiatives in its upcoming five-year DSM Plan"12 • E1 evaluated whether Residential Behaviour could be repurposed as a marketing...
AI summary The document outlines changes to the DSM Plan, including the introduction of a new Mi'kmaw New Home Construction program component, the removal of residential lighting from Instant Savings and Efficient Product Installation due to LED becoming the baseline, and a transition in BNI lighting market starting in mid-2026.
- 2 Table 7 provides portfolio-level savings and investment by year and in aggregate, inclusive of all proposed - 3 DSM resources for the 2027–2031 DSM Preferred Plan.
AI summary Table 7 outlines portfolio-level savings and investment figures by year and in aggregate for all proposed DSM resources under the 2027–2031 DSM Preferred Plan.
5 Table 7: 2027–2031 DSM Preferred Plan Portfolio Savings and Investment 2027-2031 Portfolio Year Investment ($M) Lifetime Benefits ($ million) First-Year Energy Savings (GWh) Peak Demand Savings (MW) Lifetime Energy Savings (GWh) Low-Inco...
AI summary Table 7 outlines the projected investment, savings, and benefits of the 2027–2031 DSM Preferred Plan Portfolio, including energy savings, peak demand reduction, and lifetime benefits. The table includes metrics such as investment in millions, energy savings in GWh, and weighted average measure life for various programs.
Table 8: 2027–2031 DSM Preferred Plan Savings and Investment by Program Component 2027-2031 Investment ($ million) Lifetime Benefits ($ million) First Year Energy Savings (GWh) Lifetime Energy Savings (GWh) Peak Demand Savings (MW) Availab...
AI summary Table 8 outlines the investment and benefits of various Demand Side Management (DSM) programs in Nova Scotia from 2027 to 2031, including energy savings, peak demand reductions, and program-specific metrics such as the Program Assessment Criteria (PAC).
Currency is expressed in nominal dollars. For the five-year total row, currency is a straight sum of 5 years of nominal values. Lifetime benefits for energy efficiency, demand response and solar-PV are expressed as the net present value of...
AI summary The document discusses the calculation of lifetime benefits for energy efficiency, demand response, and solar-PV programs using net present value of avoided costs. It also highlights low-income and equity impacts based on participation in specific programs. The text references Table 13 and includes some numerical data.
- 4 Table 9: 2027 DSM Preferred Plan Savings and Investment by Program Component 2027 Investment ($ million) Lifetime Benefits ($ million) First Year Energy Savings (GWh) Lifetime Energy Savings (GWh) Peak Demand Savings (MW) Available Dem...
AI summary Table 9 presents the 2027 DSM Preferred Plan Savings and Investment by Program Component, showing details such as investment, lifetime benefits, energy savings, and other metrics for various residential energy efficiency programs in Nova Scotia.
Columns may not add correctly due to rounding. Currency is expressed in nominal dollars. For the five-year total row, currency is a straight sum of 5 years of nominal values. Lifetime benefits for energy efficiency, demand response and sol...
AI summary The document discusses the calculation of lifetime benefits for energy efficiency, demand response, and solar-PV programs using net present value of avoided costs. It also highlights the inclusion of low-income and equity impacts from both targeted and non-targeted programs.
1 Table 10: 2028 DSM Preferred Plan Savings and Investment by Program Component 2028 Investment ($ million) Lifetime Benefits ($ million) First Year Energy Savings (GWh) Lifetime Energy Savings (GWh) Peak Demand Savings (MW) Available Dema...
AI summary Table 10 presents the 2028 DSM Preferred Plan Savings and Investment by Program Component, detailing energy efficiency programs, including investments, benefits, and savings across residential and multifamily housing initiatives, with a focus on energy efficiency and demand response.
Currency is expressed in nominal dollars. For the five-year total row, currency is a straight sum of 5 years of nominal values. Lifetime benefits for energy efficiency, demand response and solar-PV are expressed as the net present value of...
AI summary The text discusses the calculation of lifetime benefits for energy efficiency, demand response, and solar-PV programs, using net present value of avoided costs. It also mentions low-income and equity impacts from dedicated and incidental programs, citing specific initiatives such as Existing Residential, New Residential, and BNI Efficient Product Rebates.
1 Table 11: 2029 DSM Preferred Plan Savings and Investment by Program Component 2029 Investment ($ million) Lifetime Benefits ($ million) First Year Energy Savings (GWh) Lifetime Energy Savings (GWh) Peak Demand Savings (MW) Available Dema...
AI summary Table 11 outlines the 2029 DSM Preferred Plan Savings and Investment by Program Component, including details on investment amounts, energy savings, and other metrics for various residential energy efficiency programs in Nova Scotia.
Currency is expressed in nominal dollars. For the five-year total row, currency is a straight sum of 5 years of nominal values. Lifetime benefits for energy efficiency, demand response and solar-PV are expressed as the net present value of...
AI summary The text discusses how lifetime benefits for energy efficiency, demand response, and solar-PV programs are calculated using net present value of avoided costs. It also highlights how low-income and equity impacts are assessed, considering both dedicated and incidental program participation.
1 Table 12: 2030 DSM Preferred Plan Savings and Investment by Program Component 2030 Investment ($ million) Lifetime Benefits First Year Energy Lifetime Energy Peak Demand Available Demand Response Solar-PV Generation Weighted Average Prog...
AI summary Table 12 outlines the 2030 DSM Preferred Plan Savings and Investment by Program Component, detailing energy efficiency (EE) programs, enabling strategies (ES), demand response (DR), and solar-PV programs. It includes investment amounts, savings, and other metrics for residential, business, and institutional programs, as well as equity and low-income impacts.
Currency is expressed in nominal dollars. For the five-year total row, currency is a straight sum of 5 years of nominal values. Lifetime benefits for energy efficiency, demand response and solar-PV are expressed as the net present value of...
AI summary The text discusses the calculation of lifetime benefits for energy efficiency, demand response, and solar-PV programs using net present value and utility WACC. It also highlights the inclusion of low-income and equity impacts from both targeted and non-targeted programs.
1 Table 13: 2031 DSM Preferred Plan Savings and Investment by Program Component 2031 Investment ($ million) Lifetime Benefits ($ million) First Year Energy Savings (GWh) Lifetime Energy Savings (GWh) Peak Demand Savings (MW) Available Dema...
AI summary Table 13 outlines the 2031 DSM Preferred Plan Savings and Investment by Program Component, detailing investments, benefits, energy savings, and other metrics for various residential energy efficiency programs in Nova Scotia.
1 4.5.1 LOW-INCOME AND EQUITY INVESTMENT AND SAVINGS - 2 E1's 2027–2031 DSM Preferred Plan includes dedicated program components that exclusively serve low- - 3 income and equity communities. These program components include Affordable Mul...
AI summary E1's 2027–2031 DSM Preferred Plan includes dedicated low-income and equity programs (e.g., Affordable Multifamily Housing, Mi'kmaw projects) accounting for 11% of residential savings. The Solar-PV program is also targeted at these communities. Incidental impacts from non-targeted programs like Efficient Product Installation are also noted, with details in Attachment 1 and Table 14.
4.6 2027–2031 DSM PREFERRED PLAN INVESTMENT OVERVIEW E1's total investment for the 2027–2031 DSM Preferred Plan is $318.75 million.
AI summary E1's total investment for the 2027–2031 DSM Preferred Plan is projected to be $318.75 million.
sidential program components also continue to see reduced energy savings, resulting from two billing analyses conducted during the 2024 1 3 4 5 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 - 1 DSM evaluation. The Home Energy Assessment billin...
AI summary Residential energy programs in Nova Scotia face reduced savings due to updated billing analyses (Home Energy Assessment and Green Heat), impacting heat pump efficiency. E1 shifts investments to BNI Demand Response and maintains residential demand response levels. Solar-PV supports Mi'kmaw communities through energy efficiency initiatives.
1 4.6.2 UNIT COST - 2 Unit cost is a calculated output of E1's investment and savings over a defined time period. Factors that - 3 influence unit cost results typically include: - the level of participation in a program or program componen...
AI summary Unit cost for E1's energy efficiency programs is calculated based on factors like participation levels, measure mix, and cost changes. The projected 2027–2031 unit cost is $0.66/kWh, higher than the 2026 DSM Extension's $0.49/kWh.
1 4.7 RATE CLASS ALLOCATIONS 2 E1 has committed to improve the accuracy of the estimates used for the rate class allocation of 3 expenditures in the DSM Plan. For the 2027–2031 DSM Preferred Plan, E1 largely followed its approach 4 taken f...
AI summary E1 has committed to improving the accuracy of rate class allocation estimates for expenditures in the DSM Plan. For the 2027–2031 DSM Preferred Plan, E1 used historical data from 2022 to 2024, reviewed customer commitments, and incorporated assumptions for program changes affecting specific rate classes.
15 Table 15: 2027–2031 DSM Preferred Plan Rate Class Savings and Expenditures 2027–2031 Rate Class Year First Year Energy Savings (GWh) Lifetime Energy Savings (GWh) Peak Demand Savings (MW) Available Demand Response Capacity (MW) Generati...
AI summary Table 15 outlines projected energy savings, demand reductions, and expenditures for the 2027–2031 DSM Preferred Plan, categorized by rate class. It includes metrics like energy savings (GWh), peak demand savings (MW), and expenditures (in millions of dollars) for residential, small general, and general rate classes over the five-year period.
12 5.1 2027–2031 DSM PROGRAM MARKETING Marketing plans and strategies are essential to DSM Plan implementation. Effective marketing drives customer participation in programs and supportsthe communication and implementation aspects of DSM P...
AI summary Marketing is crucial for DSM Plan implementation, enhancing customer participation and brand recognition for E1 and Efficiency Nova Scotia. E1's marketing objectives for the 2027–2031 DSM Preferred Plan aim to support program delivery and educate Nova Scotians.
21 Awareness, Education and Participation - 22 Driving education of and participation in E1's energy efficiency, demand response, and solar-PV 23 programs. - 24 Increasing awareness of the E1 and Efficiency Nova Scotia brands as a trusted...
AI summary The text outlines strategies to enhance awareness and participation in E1's energy efficiency, demand response, and solar-PV programs. It emphasizes comprehensive marketing tactics, brand trust-building, and targeted outreach across customer sectors. The Efficiency Preferred Partner program's membership growth and education are also highlighted.
6. ENERGY EFFICIENCY DSM energy efficiency refers to delivering the same or improved level of service using less energy, resulting in measurable reductions in energy consumption while maintaining or improving performance. Natural Resources...
AI summary Energy efficiency programs, led by E1, focus on reducing energy consumption through initiatives like residential LED baselines and Mi'kmaw New Home Construction. The 2027–2031 DSM Plan includes enhanced incentives, expanded rebate categories, and program updates to address rising costs and evolving market needs.
1 Table 16: Residential Efficient Product Rebates - Overview, Objectives, Opportunity Residential Efficient Product Rebates Overview • Provides customers access to financial incentives for various products through retailers and heating sys...
AI summary Table 16 outlines the Residential Efficient Product Rebates program, which provides financial incentives for energy-efficient products through retailers and installers. The program aims to increase accessibility, awareness, and adoption of energy-efficient technologies. Barriers include affordability, lack of awareness, and limited retailer participation. The program became part of E1's portfolio in 2010 and included Appliance Retirement until 2025.
1 Table 17: 2027–2031 Instant Savings Program Component Instant Savings Program Component History • LEDs in 2011 • • 2009–2012 – first pilot launched (Efficient Lighting Products) followed by Power Down (2010), Plug into Savings (2011) and...
AI summary The text outlines the history of the Instant Savings Program in Nova Scotia, starting with pilot initiatives in 2009–2012 focused on lighting products like compact fluorescent lamps (CFLs), and evolving into a full-scale program by 2012. From 2014–2018, the program expanded to offer year-round rebates on a variety of energy-efficient products.
5 Table 18: 2027–2031 Residential Efficient Product Rebates Performance Indicators Year Investment ($ million) First-Year Energy Savings (GWh) Lifetime Energy Savings (GWh) Peak Demand Savings (MW) Participation (products) Lifetime Unit Co...
AI summary Table 18 outlines projected performance indicators for residential efficient product rebates from 2027 to 2031, including investment, energy savings, peak demand savings, participation numbers, and costs. The Program Assessment Criteria (PAC) is defined as a benefit/cost ratio comparing lifetime benefits to DSM investment.
8 6.2.1 OVERVIEW, OBJECTIVES, OPPORTUNITY 9 [Table 19](#page-136-1) provides a description of the Existing Residential program for 2027–2031. 10
AI summary The document references Table 19, which outlines the Existing Residential program for 2027–2031. The section provides an overview of objectives and opportunities related to demand-side management initiatives in Nova Scotia.
1 Table 20: 2027–2031 Affordable Multifamily Housing Affordable Multifamily Housing Program Component History • barriers • • • • customer enrollment • 2016 – pilot launched using similar framework as Small Business Energy Solutions and tar...
AI summary The Affordable Multifamily Housing program component, part of the Demand Side Management (DSM) initiative, has evolved since 2016 through various pilot phases, with adjustments in incentives, participation strategies, and expansion to include non-profit organizations and smaller buildings.
2 Table 22: 2027–2031 Efficient Product Installation Program Component Investment Energy Savings Demand Savings Participation ($M) (GWh) (MW) (products) • 2011 – pilot launched providing a no-cost service under several other program compon...
AI summary The Efficient Product Installation Program has evolved since 2011, initially as a pilot, then expanding province-wide and incorporating new measures like LED lighting and draft proofing. In 2024, electrician-installed energy-saving measures were introduced, and in 2025, lighting measures were discontinued based on program evaluation.
1 Table 24: 2027–2031 Mi'kmaw Home Energy Efficiency Project Program Component Mi'kmaw Home Energy Efficiency Project Quality Assurance The framework measures both compliance (e.g., operational standards, safety) and performance (e.g., cus...
AI summary The Mi'kmaw Home Energy Efficiency Project includes quality assurance measures that monitor the compliance and performance of E1's contracted service partners through project audits, monthly performance monitoring, and customer satisfaction surveys.
Table 26: 2027–2031 Existing Residential Performance Indicators Year Investment ($ million) First-Year Energy Savings (GWh) Lifetime Energy Savings (GWh) Peak Demand Savings (MW) Participation (homes) Participation (products) Participation...
AI summary Table 26 outlines the projected residential performance indicators for the years 2027–2031, including investment amounts, energy savings, peak demand reductions, and participation metrics. The table also includes the Program Administrator Cost (PAC) test, which is a benefit/cost ratio comparing lifetime benefits to DSM investment.
10 6.3 NEW RESIDENTIAL 4 9 13
AI summary Section 6.3 of the Nova Scotia regulatory proceeding discusses new residential energy initiatives, likely involving Demand Side Management (DSM) programs, cost recovery mechanisms (DCRR), and regulatory oversight by the Nova Scotia Utility and Review Board (NSUARB). Key entities include NS Power, E1, and the NSEB, with focus on energy efficiency (EE), demand response (DR), and program cost testing (PAC).
1 Table 29: 2027–2031 Summary of the Mi'kmaw New Home Construction Program Component Mi'kmaw New Home Construction Annual Plan Investment Energy Savings Demand Savings Participation ($M) (GWh) (MW) (homes) 2027 Total 0.2 0.0 0.0 0 2028 Tot...
AI summary Table 29 outlines the Mi'kmaw New Home Construction Program's projected investments and energy savings from 2027 to 2031. The program is expected to invest $5.0 million over the five-year period, resulting in 1.1 GWh of energy savings and 0.4 MW of demand savings, with 200 homes participating.
7 Table 30: 2027–2031 New Residential Performance Indicators Year Investment ($ million) First-Year Energy Savings (GWh) Lifetime Energy Savings (GWh) Peak Demand Savings (MW) Participation (homes) Lifetime Unit Cost ($/kWh) Program Admini...
AI summary Table 30 outlines residential energy efficiency investments and savings from 2027–2031, showing $5 million in total investment, 32.8 GWh in lifetime energy savings, and consistent Program Administrator Cost Test (PAC) values of 0.8 from 2028–2031.
15 6.4 BNI EFFICIENT PRODUCT REBATES PROGRAM
AI summary The BNI Efficient Product Rebates Program is part of a Nova Scotia regulatory proceeding, focusing on demand-side management and energy efficiency initiatives. It operates under frameworks like the Public Utilities Act and Energy and Regulatory Boards Act, aiming to promote energy-efficient products for business, non-profit, and institutional sectors.
16 6.4.1 OVERVIEW, OBJECTIVES, OPPORTUNITY 17 [Table 31](#page-149-2) provides a description of the BNI Efficient Product Rebates program for 2027–2031. 8 PAC is a benefit/cost ratio comparing lifetime benefits to DSM investment.
AI summary The text describes the BNI Efficient Product Rebates program for 2027–2031 and defines PAC as a benefit/cost ratio comparing lifetime benefits to DSM investment. The program aims to promote energy efficiency through rebates, while PAC evaluates the economic viability of DSM initiatives.
1 Table 31: BNI Efficient Product Rebates - Overview, Objectives, Opportunity BNI Efficient Product Rebates Overview • BNI customers can access prescriptive rebates or financing on eligible equipment with predictable savings and applicabil...
AI summary The BNI Efficient Product Rebates program provides prescriptive rebates and financing for energy-efficient equipment to businesses, non-profits, and institutions. The program aims to increase market penetration of efficient technologies and transform standard practices by addressing barriers such as upfront costs, lack of knowledge, and time constraints.
DATE FILED: March 31, 2026 Page 63 of 112 Business Energy Rebates Overview • The Business Energy Rebates program component offers two services – Instant Rebates and Application Rebates. • 2010 – program component launched • 2019 – program...
AI summary The Business Energy Rebates program offers Instant and Application Rebates to businesses. Launched in 2010, it saw increased adoption of LED products by 2019, leading to the removal of several lighting categories. In 2020, new measures such as system peak demand and electric thermal storage were introduced, along with pilots for demand control ventilation.
12 6.5 CUSTOM INCENTIVES PROGRAM
AI summary Section 6.5 of the Nova Scotia regulatory proceeding discusses the Custom Incentives Program, focusing on demand-side management (DSM) and energy efficiency (EE) initiatives. The program involves entities like NS Power, NSEB, and DSMAG, with considerations for cost recovery, rate design, and regulatory compliance under the ERBA and PUA frameworks.
16 Table 35: Custom Incentives - Overview, Objectives, Opportunity Custom Incentives Overview • Provides financial incentives and technical assistance to help non-profit, institutional, commercial, and industrial customers reduce their ele...
AI summary Table 35 outlines the Custom Incentives program, which offers financial incentives and technical assistance to non-profit, institutional, commercial, and industrial customers to reduce electrical energy consumption and system-peak demand. The program is tailored to specific projects and supports initiatives not covered by other E1 programs.
Custom Incentives - 2015 program renamed to Custom Incentives, comprised of five components: Custom Retrofit, New Construction, Existing Building Commissioning, Energy Management and Information Systems and Strategic Energy Management - 20...
AI summary The Custom Incentives program has undergone multiple structural changes since 2015, evolving from five components to two, with shifts in focus areas like retrofitting, energy management, and strategic initiatives. Key updates include the 2020 introduction of Industrial Energy Managers and the 2023 reconfiguration to two core components. Tables 36 and 37 provide historical component details.
2 6.5.2 PROGRAM DESIGN 1 5 - 3 [Table 36](#page-155-0) and [Table 37](#page-157-0) summarizes the five-year investment and savings for the Custom and Strategic - 4 Energy Management program components, including design and implementation s...
AI summary The text discusses the Program Design section, which includes summaries of five-year investment and savings for the Custom and Strategic Energy Management program components, along with details on design and implementation strategies.
6 Table 36: 2027–2031 Custom Program Component Custom Annual Plan Investment ($M) Energy Savings (GWh) Participation (projects) 2027 Total 17.1 73.2 10.7 191 2028 Total 13.3 50.7 7.1 132 2029 Total 11.1 35.0 4.6 91 2030 Total 10.6 32.1 4.1...
AI summary Table 36 outlines the projected investment, energy savings, and participation for the 2027–2031 Custom Program Component. The table shows decreasing investment and participation over the years, with energy savings also declining, indicating a phased reduction in program intensity.
2 Table 37: 2027–2031 Strategic Energy Management Program Component Strategic Energy Management Annual Plan Investment ($M) Energy Savings (GWh) Demand Savings (MW) Participation (participants) 2027 Total 1.1 4.2 0.5 7 2028 Total 1.1 4.2 0...
AI summary The Strategic Energy Management Program (2027–2031) provides industrial organizations with comprehensive energy management support, including technical and financial assistance. The program aims to achieve energy and demand savings through measures like financial incentives, expert evaluations, and performance-based rewards, with a focus on continued support and marketing strategies.
6 Table 38: 2027–2031 Custom Incentives Performance Indicators Year Investment ($ million) First-Year Energy Savings (GWh) Lifetime Energy Savings (GWh) Peak Demand Savings (MW) Participation (participants) Participation (projects) Lifetim...
AI summary Table 38 outlines performance indicators for the BNI Custom Incentives Program from 2027 to 2031, including projected investments, energy savings, peak demand savings, participation numbers, and the Program Administrator Cost (PAC) test. The table provides a detailed overview of the program's expected outcomes and financial metrics over the five-year period.
7 6.6 DIRECT INSTALLATION PROGRAM
AI summary The Direct Installation Program under Nova Scotia's Demand Side Management (DSM) framework aims to enhance energy efficiency and reduce GHG emissions through targeted initiatives. Key stakeholders include NS Power, NSEB, and ERBA, with regulatory considerations involving cost recovery and program effectiveness.
1 Table 42: 2027–2031 Direct Installation Performance Indicators Year Investment ($ million) First-Year Energy Savings (GWh) Lifetime Energy Savings (GWh) Peak Demand Savings (MW) Participation (projects) Lifetime Unit Cost ($/kWh) Program...
AI summary Table 42 outlines performance indicators for the Direct Installation Program from 2027 to 2031, showing investment, energy savings, peak demand savings, and participation numbers. Table 43 provides similar data for the Low-Income and Equity portion of the program. The PAC metric is defined as a benefit/cost ratio comparing lifetime benefits to DSM investment.
13 7. DEMAND RESPONSE Demand response is an important resource for supporting Nova Scotia's electricity system by reducing or shifting customer load during periods of peak demand. The Federal Energy Regulatory Commission defines demand res...
AI summary Nova Scotia's demand response (DR) programs, managed by E1, aim to reduce peak demand through load shifting. The 2023–2025 DSM Plan faced underachievement, but E1 anticipates growth in 2026. The 2027–2031 Preferred Plan focuses on achievable targets aligned with NS Power's IRP, with modest BNI DR growth and stable residential DR. Cost-effectiveness (PAC ≥ 1.0) and regulatory feedback influenced planning.
7.1 LOCATIONAL DEMAND RESPONSE The value of demand response is not uniform across the electricity system. Deploying resources in areas where the distribution or transmission network is constrained can help defer or avoid capital infrastruc...
AI summary The document discusses the importance of locational demand response in Nova Scotia, emphasizing collaboration with NS Power to align DR deployment with constrained grid areas. E1 highlights the need for granular AMI data, including feeder IDs, to target programs effectively. It also notes E1's role in the DER Integration Roadmap, expected in 2026, to align DR with system planning.
8 7.2 CRITICAL PEAK PRICING OVERLAP 9 As part of ongoing collaboration on demand response, E1 and NS Power met in late 2024 to identify opportunities to strengthen coordination across demand response initiatives, including rate-based appro...
AI summary E1 and NS Power collaborated to address overlap between E1's demand response programs and NS Power's Time-Varying Pricing (TVP) rates, which target similar customers and peak periods. A 2025 cybersecurity incident paused the TVP pilot, returning participants to standard rates. Future DSM plans (2027–2031) expect minimal overlap, with ongoing efforts to coordinate locational demand response and avoid double-counting savings.
11 7.3 DEMAND RESPONSE PROGRAM
AI summary This section outlines the Demand Response Program within the Nova Scotia regulatory proceeding, involving entities such as NS Power and NSEB, with references to various acronyms and programs related to energy management and regulatory frameworks.
12 7.3.1 OVERVIEW, OBJECTIVES, OPPORTUNIT[Y](#page-166-2) 13 [Table 44](#page-166-2) provides a description of the Demand Response program for 2027–2031. 14
AI summary The document references Table 44, which outlines the Demand Response program's description for the period 2027–2031, focusing on its objectives and structure within the Nova Scotia regulatory framework.
15 Table 44: Demand Response - Overview, Objectives, Opportunity Demand Response • The program provides financial incentives to customers who reduce their load during peak times when there is value to the utility to shift load. Overview •...
AI summary The Demand Response program offers financial incentives to residential and BNI customers who reduce their load during peak times. It aims to diversify program offerings, increase customer awareness, and explore eligibility for interruptible customers in future plans. Barriers include lack of awareness, resources, and inconvenience for participants.
6 Table 45: 2027–2031 Residential Demand Response Program Component Residential Demand Response Annual Plan Investment ($M) Available Demand Response Capacity (MW) Participation (participants) 2027 Total 2.2 4.2 22,940 2028 Total 2.0 4.1 2...
AI summary The table outlines the 2027–2031 Residential Demand Response Program, including annual investments, available capacity, and participation numbers. The program focuses on existing participants, using smart thermostats and water heaters, and is delivered through a DERMS provider. Marketing efforts target existing customers, and quality assurance includes customer feedback and post-season surveys.
5 Table 46: 2027–2031 BNI Demand Response Program Component BNI Demand Response Annual Plan Investment ($M) Available Demand Response Capacity (MW) Participation (participants) 2027 Total 3.1 17.0 169 2028 Total 3.5 19.1 173 2029 Total 3.8...
AI summary Table 46 outlines the BNI Demand Response Program's investment, capacity, and participation from 2027 to 2031. The program encourages businesses to reduce load during peak events through financial incentives and involves third-party aggregators for implementation. Enhancements include continued support, marketing strategies, and quality assurance measures.
3 [Table 47](#page-169-0) provides the program performance indicators. 5 Table 47: 2027–2031 Demand Response Performance Indicators Year Investment ($ million) Available Capacity (MW) Participation (devices) Participation (participants) Le...
AI summary Table 47 outlines the 2027–2031 Demand Response (DR) performance indicators, including investment, available capacity, participation numbers, and the Program Administrator Cost (PAC) test. The table shows a steady increase in investment and available capacity over the years, with participation numbers remaining relatively stable. The PAC test is defined as a benefit/cost ratio comparing lifetime benefits to DR investment, with levelized costs calculated over a ten-year period.
1 7.3.4 PROGRAM ALTERNATIVES - 2 The Demand Response program features one difference in the Alternate Scenario when compared to the - 3 Preferred Plan, that being that the Residential Demand Response program component is not included in -...
AI summary The Alternate Scenario excludes the Residential Demand Response program component compared to the Preferred Plan, with Table 48 comparing performance indicators from 2027–2031.
18 Scenario Year Investment ($ million) Available Capacity (MW) Participation (devices) Participation (participants) Levelized Cost ($/kW-year) Program Administrator Cost Test (PAC) 2027 5.3 21.1 22,940 169 - 2.0 2028 5.5 23.2 22,483 173 -...
AI summary The table presents investment and participation data for a demand-side management (DSM) program across multiple years, including preferred and alternate scenarios, and calculates the Program Administrator Cost (PAC) as a benefit/cost ratio. The data includes investment amounts, available capacity, participation numbers, and levelized costs for both preferred and alternate scenarios.
13 8. SOLAR-PV - 14 E1 is proposing the introduction of a new Solar-PV program in the 2027–2031 DSM Preferred Plan. 15 Solar‑PV refers to technology that converts sunlight directly into electricity. Solar‑PV can produce 16 electricity that...
AI summary E1 proposes a Solar-PV program in the 2027–2031 DSM Plan, targeting Mi'kmaw communities to reduce energy burdens through equity-focused, small-scale residential initiatives. The program leverages existing frameworks, aims for phased implementation, and includes a $2.8M investment over five years, reflecting affordability and equity priorities.
1 Table 49: Overview, Objectives, Opportunity Solar-PV Overview • Post-installation incentives are provided for solar-PV systems installed on new homes in Mi'kmaw communities. • The program consists of one component: Residential Solar-PV....
AI summary This table outlines the Solar-PV program, which aims to increase the adoption of solar-PV systems in Mi'kmaw communities by reducing upfront costs and building awareness. The program targets residential new home construction projects, addressing barriers such as affordability, awareness, and uncertainty about solar-PV technology and payback periods.
1 Table 51: 2027–2031 Solar-PV Performance Indicators Year Investment ($ million) Solar-PV Generation (GWh) Solar-PV Lifetime Generation (GWh) Installed Capacity (MW) Participation (products) Lifetime Unit Cost ($/kWh) Program Administrato...
AI summary Table 51 outlines projected Solar-PV performance indicators from 2027 to 2031, including investment, generation, capacity, and participation metrics. The table shows a gradual decline in investment and generation over the years, with a corresponding decrease in installed capacity and participation. The Program Administrator Cost (PAC) is defined as a benefit/cost ratio comparing lifetime benefits to DSM investment.
8 9. ENABLING STRATEGIES
AI summary The section titled 'ENABLING STRATEGIES' introduces the context for regulatory proceedings in Nova Scotia, listing relevant acronyms and organizations involved in energy management and regulatory processes. No detailed content or arguments are present in the provided text.
9 9.1 OVERVIEW - 10 Enabling Strategies are initiatives that support the development, delivery, and growth of E1's DSM - 11 programs as well as the efforts required to plan for future DSM plans. 12 - 13 For the 2027–2031 period, E1 propose...
AI summary E1 proposes to invest 9% of its total DSM Portfolio in Enabling Strategies for the 2027–2031 period, allocating funds across four categories: Education and Outreach, Development and Research, Other Enabling Strategies, and Market Transformation. E1 has responded to feedback from DSMAG and introduced measures of success and structured plans for these initiatives.
14 9.2 HISTORY Enabling Strategies activities have been a component of E1's DSM Plans since the first Plan was developed in 2012 and they have played a pivotal role in supporting the development, delivery, and growth of E1 programs includi...
AI summary Enabling Strategies (ES) have been integral to E1's Demand Side Management (DSM) Plans since 2012, evolving from education/outreach to innovation and R&D. The 2023–2026 plan focuses on addressing challenges like market maturity and emerging technologies in Nova Scotia's energy landscape.
1 9.3 OBJECTIVES - 2 In 2027–2031, Enabling Strategies will continue to build on those initiatives that have historically proven - 3 successful by delivering focused education and outreach, and development and research activities; - 4 mark...
AI summary Enabling Strategies (ES) aims to expand DSM program participation through education and outreach, ensure E1 adapts to market changes via research, continue the heat pump water heater pilot, and meet regulatory requirements including reporting and consultations. ES will also address evolving technologies and maintain compliance with NSIESO and DSMAG directives.
9.4 ENABLING STRATEGIES – CATEGORY DESCRIPTIONS The investment and activity descriptions for each Enabling Strategy category are detailed in this section.
AI summary This section outlines investment and activity descriptions for Enabling Strategy categories within a Nova Scotia regulatory proceeding, focusing on strategies to support energy management and resource planning.
1 Table 53: 2027–2031 Education and Outreach Activities Education and Outreach Areas of Focus Year Outreach ($) Education ($) Support for Mi'kmaw Communities ($) Total Investment ($) 2027 Total 0.4 0.3 0.5 1.2 2028 Total 0.4 0.3 0.5 1.2 20...
AI summary Table 53 outlines the 2027–2031 education and outreach activities, including funding for outreach, education, and support for Mi'kmaw communities. Key activities include home shows, partnerships, staff costs, and energy management services. Table 54 provides further details on key activities and expected outcomes.
1. Participate in home shows By participating in existing, reputable, and popular home shows in communities across the province, E1 is able to reach large numbers of Nova Scotians to increase public awareness about E1's DSM programs and to...
AI summary E1 promotes its Demand Side Management (DSM) programs through participation in popular home shows across Nova Scotia, aiming to increase public awareness and provide information on accessing these programs.
OUTREACH - E1 achieves its annual participation targets set out in the 2027–2031 DSM Plan. - E1 and its partner organizations achieve the goals set out in their respective partnership agreements.
AI summary E1 meets annual participation targets under the 2027–2031 DSM Plan, and E1 and its partners achieve goals outlined in their partnership agreements.
2. Provide energy management services to Mi'kmaw communities E1's Roving Energy Manager for Mi'kmaw communities will work with Nova Scotia's 13 Mi'kmaw communities to identify new DSM projects and coordinate building energy audits in an ef...
AI summary E1's Roving Energy Manager collaborates with Nova Scotia's 13 Mi'kmaw communities to identify Demand Side Management (DSM) projects and coordinate energy audits, aiming to enhance Mi'kmaw participation in E1's DSM programs.
Measures of success: - E1 achieves its annual participation targets for the Mi'kmaw New Home Construction program component set out in the 2027–2031 DSM Plan. - The Roving Energy Manager facilitates Mi'kmaw participation in E1's BNI progra...
AI summary The document outlines success measures for E1's programs under the 2027–2031 DSM Plan, including achieving annual participation targets for the Mi'kmaw New Home Construction program and ensuring Mi'kmaw community engagement through the Roving Energy Manager in BNI initiatives.
8 Table 55: 2027–2031 Development and Research Activities Development and Research Areas of Focus Total Investment Year Information & Analytics ($) Innovation ($) ($) DATE FILED: March 31, 2026 Page 92 of 112 Development and Research 2027...
AI summary The document outlines the development and research activities planned from 2027 to 2031, focusing on Information & Analytics and Innovation. These activities aim to ensure E1 remains responsive to market changes and will inform future DSM Plan offerings. The total investment over the five-year period is $7.1 million.
INFORMATION & ANALYTICS
AI summary The INFORMATION & ANALYTICS section outlines regulatory proceedings in Nova Scotia, involving energy efficiency, demand-side management, and utility rate structures. Key entities include NS Power, NSEB, and ERBA, with topics focusing on DSM, EE, and rate design.
1. Conduct research By consistently tracking quality assurance, participant satisfaction, and other attitudinal metrics among Nova Scotia households, E1 gains insights into how its programs are being received in the marketplace and can res...
AI summary E1 conducts research to track program effectiveness through quality assurance and participant satisfaction metrics, and plans to expand studies on DSM market opportunities and participant motivations in Nova Scotia.
1. Implement E1's annual Innovation Plans E1's Innovation team will plan, develop, and deliver research projects and pilot projects in key potential growth areas including strategic electrification, demand response, demand flexibility, loc...
AI summary E1's Innovation team will develop research and pilot projects in strategic electrification, demand response, and market transformation. Projects aim to improve cost-effectiveness, advance DSM readiness, and leverage insights. Annual Innovation Plans guide work, with early results informing future projects. See Attachment 5 for details.
2. Participate and contribute to national Codes and Standards organization E1's participation in the Canadian Standards Association's Steering Committee on Performance, Energy Efficiency and Renewables, which sets equipment performance sta...
AI summary E1 participates in the Canadian Standards Association's Steering Committee on Performance, Energy Efficiency, and Renewables to influence equipment standards, enhancing energy efficiency and demand response in Nova Scotia. This involvement allows E1 to inform stakeholders about upcoming changes.
6 Table 57: 2027–2031 Other Enabling Strategies Other Enabling Strategies 5 Areas of Focus Year DSM Plannin ($) g Regular DSM Matters ($) Other Regulatory Matters ($) Total Investment ($) 2027 Total 0.0 1.4 0.2 1.5 2028 Total 0.0 1.4 0.1 1...
AI summary Table 57 outlines the 2027–2031 Other Enabling Strategies, including funding for DSM planning and other regulatory matters. It details investment amounts for each year and highlights activities such as stakeholder engagement, consulting, and planning for the next DSM Plan (2032–2036).
1 Table 58: 2027–2031 DSM Planning
AI summary Table 58 outlines Demand Side Management (DSM) planning for the years 2027–2031 as part of a Nova Scotia regulatory proceeding, focusing on energy efficiency, demand response, and integrated resource planning strategies.
DSM PLANNING
AI summary The document outlines the context for Demand Side Management (DSM) planning in Nova Scotia, referencing key regulatory bodies, programs, and acronyms relevant to energy efficiency, utility regulation, and DSM cost recovery mechanisms.
1. Develop and file the 2032 – 2036 DSM Plan E1 staff will develop the 2032-2036 DSM Plan through research, consultations with experts, internal planning, and working and consulting with all stakeholders to gain support for the Plan. After...
AI summary E1 staff will develop the 2032–2036 DSM Plan through research, consultations with experts, internal planning, and stakeholder engagement to secure support. After filing the plan, E1 will participate in the regulatory approval process.
2. Energy Board and stakeholder consultant costs In addition to E1's directly incurred costs, flow-through costs related to the Energy Board and its consultants, the Consumer Advocate and its consultants, and the Small Business Advocate an...
AI summary The text states that flow-through costs for the Energy Board, Consumer Advocate, Small Business Advocate, and their consultants, along with E1's direct costs, are categorized under 'Other Enabling Strategies' investment. This highlights the inclusion of stakeholder-related expenses in broader energy strategy funding.
REGULAR DSM MATTERS
AI summary The document heading indicates a section focused on regular Demand Side Management (DSM) matters under Nova Scotia regulatory proceedings. No further details or content are provided in the text.
1. File all required reports, statements, and responses E1 will file all required reporting on the 2027–2031 DSM Plan including quarterly reports, Annual Progress Reports, Evaluation Reports, Audited Financial Statements, Information Reque...
AI summary E1 will file required reports and respond to directives related to the 2027–2031 DSM Plan, including quarterly and annual reports, evaluations, and financial statements, as mandated by the Nova Scotia Energy Board.
2. Engage with stakeholders throughout Plan period E1 will consult with stakeholders through regular and technical DSM Advisory Group sessions, preparing materials and briefings for distribution to the group, and responding to and incorpor...
AI summary E1 will engage stakeholders through regular DSM Advisory Group sessions, preparing materials and briefings, and incorporating feedback. This ensures ongoing stakeholder involvement in the Plan period.
3. Energy Board and stakeholder consultant costs In addition to E1's directly incurred costs, flow-through costs related to the Energy Board and its consultants, the Consumer Advocate and its consultants, and the Small Business Advocate an...
AI summary Flow-through costs from the Energy Board, Consumer Advocate, Small Business Advocate, and their consultants, along with E1's costs, are categorized under 'Other Enabling Strategies' investment. These costs are included in the broader investment framework for regulatory proceedings.
1. Update E1's 2026 potential study Together with its consultants, E1 will complete an update of its 2026 potential study during the 2027–2031 Plan period, both to inform its 2032-2036 DSM Plan and to contribute to an expected Integrated R...
AI summary E1 will update its 2026 potential study during the 2027–2031 Plan period to inform its 2032-2036 DSM Plan and contribute to the Nova Scotia Independent Energy System Operator's Integrated Resource Plan Evergreen process.
- 5 Table 59: 2027–2031 Market Transformation Activities Market Transformation Areas of Focus Total Investment Year Heat pump water heater pilot ($) ($) 2027 Total 0.8 0.8 2028 Total 0.8 0.8 2029 Total 0.7 0.7 2030 Total 0.7 0.7 2031 Total...
AI summary Table 59 outlines the Market Transformation activities from 2027 to 2031, focusing on heat pump water heater pilots with a total investment of $3.8 million. These activities aim to overcome barriers to adoption of energy-efficient products and promote long-term energy efficiency growth in Nova Scotia.
HEAT PUMP WATER HEATER PILOT
AI summary A pilot program for heat pump water heaters under the Public Utilities Act, managed by the Nova Scotia Energy Board (NSEB), involving Nova Scotia Power (NS Power) and EfficiencyOne (E1) to evaluate energy efficiency measures and demand-side management (DSM) initiatives.
1. Continue implementation of Heat Pump Water Heater pilot The delivery of the Heat Pump Water Heater pilot continues, following the design and launch activities being completed during the 2023–2026 DSM Plan period.
AI summary The Heat Pump Water Heater pilot continues after completing design and launch activities during the 2023–2026 DSM Plan period, aligning with Nova Scotia's energy efficiency initiatives.
3. Plan for future market transformation measures Using insights gained from the heat pump water heater pilot, the Market Transformation team will collaborate with E1's Innovation team on research into measures that could be delivered usin...
AI summary The Market Transformation team will collaborate with E1's Innovation team to research future DSM measures using insights from a heat pump water heater pilot, aiming to inform future DSM Plans through market transformation strategies.
1 10.2 PERFORMANCE TARGETS AND THRESHOLDS - Performance targets[21](#page-186-3) 2 apply over the Plan period as reflected in the Energy Board-approved DSM 3 Purchase Agreement or as ordered by the Energy Board; and - 4 E1 is in substantia...
AI summary The Nova Scotia Energy Board sets performance targets for E1's DSM Purchase Agreement, requiring 90% compliance. E1's 2027–2031 DSM Preferred Plan includes five targets, with a table summarizing them. Non-compliance may trigger discretionary actions by the Energy Board.
12 Table 61: Proposed 2027–2031 DSM Preferred Plan Performance Targets 2027–2031 Performance Targets DSM Resource Energy Savings (GWh) Peak Demand Savings (MW) Low-Income & Equity Energy Savings (GWh) Available Demand Response Capacity (MW...
AI summary Table 61 outlines proposed 2027–2031 DSM performance targets, including 435.4 GWh energy savings from Energy Efficiency, 85.0 MW peak demand savings, 14.0 GWh low-income equity savings, 29.3 MW demand response capacity, and 1.7 GWh solar-PV generation. Targets aim to balance energy efficiency, demand response, and renewable integration.
16 Table 62: 2027–2031 DSM Preferred Plan Performance Indicators DSM Resource Performance Indicators Annual incremental energy savings (reported by program and rate class) (GWh) Cumulative energy savings (reported by program and rate class...
AI summary Table 62 outlines performance indicators for the 2027–2031 DSM Preferred Plan, including annual and cumulative energy and peak demand savings by program and rate class, with a focus on low-income and equity programs such as Affordable Multifamily Housing and the Mi'kmaw Home Energy Efficiency Project.
13 DSM Resource Performance Indicators Incidental annual and cumulative energy savings (GWh) from E1's non-targeted programs applicable to low-income and equity customers (reporting also includes incidental low-income and equity participat...
AI summary The section provides an overview of performance indicators for various DSM resources, including energy savings, demand response capacity, solar-PV installations, ratepayer benefits, program spending, customer satisfaction, and program administrator cost test results.
11.1 EVALUATION FRAMEWORK - E1's independent evaluation consultant is engaged to develop an Evaluation Framework that defines the - policies, priorities, and methodologies used to conduct the DSM evaluation. It provides a common - understa...
AI summary E1's independent evaluation consultant is tasked with creating an Evaluation Framework for DSM programs. The framework outlines evaluation definitions, goals, metrics, deliverables, and roles, establishing principles and prioritization criteria for annual evaluation plans. It aims to standardize best practices in DSM evaluation.
11.1.1 IMPACT EVALUATIONS - Annual impact evaluations will provide E1, stakeholders, and the Energy Board with up-to-date impacts - on net electrical energy, net system-peak demand savings and available capacity as progress indicators - to...
AI summary The document outlines annual impact evaluations for DSM programs, distinguishing between condensed and comprehensive evaluations. Condensed evaluations use prior data for stable programs, while comprehensive ones are required for newer or changed programs. E1 and the Energy Board will use these evaluations to track progress toward 2027–2031 DSM performance targets.
1 11.2 PROCESS AND MARKET EVALUATIONS - 2 Program component process and market evaluations will remain consistent with the 2023–2026 DSM - 3 Resource Plan. Process evaluations identify and recommend improvements to increase the program - 4...
AI summary The text outlines process and market evaluations for DSM programs under the 2023–2026 Resource Plan. Process evaluations aim to improve efficiency and effectiveness, while market evaluations analyze technology adoption. E1 will determine evaluation criteria based on factors like new programs, major changes, and energy savings variances.
12.1.1 ENERGY EFFICIENCY EVALUATION APPROACH E1 will engage a third-party Evaluator to develop and perform an evaluation of E1's portfolio of energy- efficiency, demand response and solar-PV programs for the 2027–2031 DSM Plan period. Each...
AI summary E1 will engage a third-party Evaluator to assess its energy-efficiency, demand response, and solar-PV programs from 2027–2031. The Evaluator will develop annual evaluation plans, conduct impact assessments, and report metrics like net energy savings and system peak demand reductions to the Nova Scotia Energy Board, ensuring transparency and alignment with evaluation principles.
12.1.2 DEMAND RESPONSE EVALUATION APPROACH Demand response program evaluation is aimed at verifying and quantifying the available capacity to the utility during the winter peak period. The Evaluator will present total available capacity, d...
AI summary Demand response evaluation focuses on quantifying available capacity during winter peaks. Available capacity differs from peak demand savings as E1 cannot control event scheduling. Evaluation considers events from December to February, with 50/50 weighting of morning and evening results. Capacity is measured over four-hour events and summed per participant, with 2027 capacity reflecting December 2026 to February 2027 data.
13.1 OVERVIEW OF DSM REPORTING 2027–2031 - E1 will file the following six reports each year with the Energy Board, for a total of thirty DSM reports over - the 2027-2031 Plan period: - Quarterly Reports (Q1-Q3); - Annual Progress Reports (...
AI summary E1 (EfficiencyOne) is required to submit 30 DSM reports over 2027–2031, including quarterly, annual progress, program evaluation, and financial statements. The Nova Scotia Energy Board's independent consultant verifies the accuracy of E1's annual program evaluation reports and savings data.
1 13.2 OVERSIGHT AND DSMAG REVIEW - 2 Each report filed with the NSEB provides opportunities for DSMAG stakeholder questions and comments, - 3 either directly to E1 or through an Energy Board-initiated regulatory process. Additionally, the...
AI summary The NSEB oversees E1's DSM Plan implementation, allowing DSMAG stakeholder input through reports and regulatory processes. Post-2022 PUA amendments extending DSM Plans to five years, DSMAG raised concerns about performance risks. E1 responded by proposing mid-term check-ins to ensure transparency and ongoing engagement during the extended plan period.
13.3 MID-COURSE ADJUSTMENTS Mid-course adjustments (MCAs) provide the DSM administrator limited flexibility to adjust annual program-level budgets and savings from those set out in the original approved DSM Plan, in order to respond to mar...
AI summary Mid-course adjustments (MCAs) allow DSM administrators to adjust annual budgets and savings without altering overall targets. The NSEB directed E1 to enhance MCA processes following Industrial Group concerns about rate-class spending variances. E1 proposes using historical data, improving reporting, and lowering thresholds for adjustments. MCAs will be integrated into the Standardized Filing Framework and discussed at DSMAG sessions.
13.4 ROUTINE REPORTING This section describes E1's DSM reporting over 2027-2031, including proposed content.
AI summary This section outlines E1's proposed Demand Side Management (DSM) reporting framework for 2027-2031, detailing content requirements and submission processes under Nova Scotia regulatory oversight.
13.4.1 QUARTERLY REPORTING - Quarterly reports provide regular updates on DSM implementation, performance, and expenditures - during each Plan year. These reports support ongoing monitoring and early identification of emerging - trends or...
AI summary E1 is required to submit quarterly reports to the NSEB detailing DSM implementation, performance metrics, and expenditures. Reports include YTD data, mid-course adjustments, rate class variances, and program highlights, with specific filing dates set by NSUARB. The reports aim to monitor progress toward five-year targets and ensure compliance with the approved DSM Resource Plan.
13.4.2 ANNUAL PROGRESS REPORTS - The APR provides reporting on DSM performance, expenditures, and progress toward approved Plan targets. In the first quarter of each calendar year, E1 will file an APR with the Energy Board, which will incl...
AI summary The Annual Progress Report (APR) requires E1 to submit detailed DSM performance data, expenditures, and progress toward Plan targets to the Nova Scotia Energy Board. Key components include variance analysis, expenditure summaries, program metrics, and mid-course adjustment notifications, with references to the MCA process in section 13.3.
13.4.3 ADVANCE NOTICE OF SIGNIFICANT CHANGES - In the event that E1 proposes significant changes to elements within an approved Plan, advance notice will be provided to the Energy Board and the DSMAG. Significant changes include: - Adding...
AI summary E1 must provide advance notice to the Energy Board and DSMAG for significant changes to approved plans, such as adding or terminating programs, and file applications with NSEB under PUA if circumstances like market shifts or regulatory changes affect plan feasibility.
1 13.4.5 RATE AND BILL IMPACT ANALYSIS - 2 E1 files its historical Rate and Bill Impact Analysis (RBIA) and forward-looking RBIA as part of each DSM - Resource Plan.[26](#page-199-1) 3 The historical RBIA estimates the high-level, long-ter...
AI summary E1 submits historical and forward-looking Rate and Bill Impact Analysis (RBIA) as part of its Demand Side Management (DSM) Resource Plan. The historical RBIA covers past DSM activities and approved investments, while the forward-looking RBIA estimates impacts of proposed DSM activities. Appendix B contains the RBIA for the 2027–2031 DSM Resource Plan.
14. CONCLUSION The 2027–2031 DSM Preferred Plan delivers cost-effective DSM resources in accordance with the requirements of the PUA , which directs that DSM be undertaken in the best interests of NS Power customers. With a portfolio level...
AI summary The 2027–2031 DSM Preferred Plan meets cost-effectiveness thresholds under the PUA, delivering $682.5M in ratepayer benefits with a 2.4 PAC result. It prioritizes affordability, avoids growth, and integrates solar-PV for Mi'kmaw communities while maintaining investment levels from the 2026 DSM Extension. The plan balances short-term affordability with long-term system benefits.
Table 1: Residential Efficient Product Rebates 2027-2031 Residential Efficient Product Rebates Rate Class Year First-Year Energy Savings Lifetime Energy Savings Peak Demand Savings Expenditures ($ million) (GWh) (GWh) (MW) 2027 11.0 106.3...
AI summary This table outlines projected energy savings and expenditures for the 2027-2031 Residential Efficient Product Rebates program across various rate classes. It includes first-year and lifetime energy savings, peak demand savings, and associated expenditures in millions of dollars.
Table 4: BNI Efficient Product Rebates 2027-2031 BNI Efficient Product Rebates 2027-2031 Direct Installation Rate Class Year First-Year Energy Savings (GWh) Lifetime Energy Savings (GWh) Peak Demand Savings (MW) Expenditures ($ million) 20...
AI summary This table outlines the 2027-2031 BNI Efficient Product Rebates, detailing energy and demand savings, as well as expenditures for various rate classes. The data reflects projections for each year and the total over the five-year period.
Table 7: Demand Response 2027-2031 Demand Response Rate Class Year Available Demand Response Capacity (MW) Expenditures ($ million) 2027 4.2 2.2 2028 4.1 2.0 2029 4.0 2.0 Residential/Charitable (2,3,4) 2030 3.9 2.0 2031 3.8 2.0 2027-2031 3...
AI summary Table 7 outlines projected demand response capacity and expenditures across various rate classes from 2027 to 2031, showing varying levels of capacity and associated costs for residential, commercial, and industrial sectors.
1.1 Innovation within DSM Enabling Strategies E1 allocates funding for research and development within the Enabling Strategies component of its DSM Resource Plans. Innovation is a core element of the Enabling Strategies portfolio, supporti...
AI summary E1 invests in research and development for Enabling Strategies within its DSM Resource Plans, focusing on innovation to enhance DSM programs. Activities include exploring emerging technologies, improving existing programs, conducting pilots, and fostering market adoption of energy-efficient solutions and demand response strategies.
1.1.1 Innovation Goals E1's Innovation team uses established Innovation Goals to define the long-term outcomes of all projects from concept, planning to close. Innovation Goals ensure that long-term outcomes align with the DSM mandate. Acr...
AI summary E1's Innovation team uses Innovation Goals to align long-term outcomes with the DSM mandate, focusing on improving cost-effectiveness, advancing new DSM measures and programs, leveraging system insights, and utilizing other funding sources.
2. GOVERNANCE
AI summary The 'Governance' section outlines regulatory frameworks and acronyms related to Nova Scotia's energy sector, including organizations, programs, and legal acts. It emphasizes governance structures for utility regulation, demand-side management, and energy efficiency initiatives, though no detailed arguments or specific case references are provided in the text.
2.2 Annual Innovation Plan - Each year, E1 establishes an Innovation Plan that summarizes all ongoing and newly committed projects. It includes project descriptions, scope, timelines, and estimated resource requirements, - serving as the b...
AI summary E1's Annual Innovation Plan outlines ongoing and new projects, including descriptions, timelines, and resource needs. It guides internal commitments between leadership and staff, serving as a roadmap for current and planned initiatives. Progress and insights are reported in E1's DSM Quarterly and Annual Progress Reports.
3. PROJECT DEVELOPMENT
AI summary The document outlines the 'PROJECT DEVELOPMENT' section of a Nova Scotia regulatory proceeding, listing key acronyms and entities involved in energy regulation, including organizations like NS Power, NSEB, and programs such as DSM and EE. It provides context for technical terms and regulatory frameworks relevant to the proceeding.
3.1 Project Classification There are two types of innovation projects: - Research projects focus solely on the research phase. They typically require smaller resources and are completed within one year. Research projects generate insights...
AI summary The text classifies innovation projects into research and pilot projects. Research projects are short-term, resource-light, and focus on feasibility, while pilot projects are longer-term, resource-intensive, and test solutions for potential program adoption under DSM.
3.3 Project Ideation - Ideation for new projects can come from various sources but is fundamentally focused on developing solutions that address challenges and explore new opportunities. Examples of sources for insights and findings includ...
AI summary Project ideation sources include Integrated Resource Planning, DSM studies, E1's programs, market research, and emerging technologies, aiming to address challenges and opportunities. Key inputs are program evaluations, jurisdictional scans, and data analytics.
3.4 Project Selection and Overview of Investment by Focus Area - Project ideas are screened using Focus Areas as a primary screen and Innovation Goals to - establish direction for Innovation projects and establish evaluation metrics how su...
AI summary Project ideas are evaluated using Focus Areas and Innovation Goals, which remain static during the 2027-2031 DSM plan period. This framework establishes direction and evaluation metrics for innovation projects.
3.4.1 Focus Areas - The primary screening criteria for project selection are Focus Areas. For the 2027-2031 DSM - plan, there are five areas which are of emerging importance to the electricity system, or are of - economic benefit to rate-p...
AI summary The 2027-2031 DSM plan uses Focus Areas as primary project selection criteria, emphasizing five areas critical to the electricity system or offering long-term economic benefits to rate-payers. A table details projected expenditures by Focus Area.
1 Table 1: Projected Direct Expenditures by Focus Area DSM Direct Expenditure ($) Focus Area 2027 2028 2029 2030 2031 Total ($) Demand Response 160,650 178,815 123,175 110,250 111,500 684,390 Demand Flexibility 183,600 204,360 221,715 198,...
AI summary The table outlines projected direct expenditures across various focus areas, including Demand Response, Strategic Electrification, and Market Transformation, from 2027 to 2031. It highlights the financial commitments planned for these initiatives, with total expenditures reaching $2,349,600 over the five-year period.
5 The Innovation Goals, justification and key activities for each of the Focus Areas are shown below in [Table 2.](#page-220-3) Focus Area Innovation Goal(s) Justification Key Activities Demand Response 1. Improve cost‑effectiveness of E1'...
AI summary The document outlines an innovation goal to improve the cost-effectiveness of E1's residential demand response (DR) program, citing that similar jurisdictions have achieved positive results through optimizing asset dispatch and revising OEM portfolios to reduce administrative costs and improve performance.
5 Table 3: Evaluation metrics by Innovation Goal Innovation Goal Evaluation Metric(s) 1. Improve cost‑effectiveness of existing measures and programs. Evaluation will be conducted relative to a defined baseline, with the primary reference...
AI summary The text outlines evaluation metrics for five innovation goals related to improving the cost-effectiveness of existing demand-side management (DSM) measures and programs, advancing readiness for new DSM measures and programs, leveraging system planning insights, and utilizing non-DSM funding sources for emerging DSM activities. References to Table 4 and Table 5 are made for evaluating market and program readiness.
1 The metrics used to evaluate the market and performance readiness of new measures are shown below in [Table 4.](#page-225-1) 3 Table 4: Evaluation metrics for readiness of new DSM measures MARKET READINESS Level 1: Pre-commercial Level 2...
AI summary The document outlines evaluation metrics for the market and performance readiness of new Demand Side Management (DSM) measures, categorizing them into five levels based on supply chain maturity, market demand, and savings reliability.
1 The metrics used to evaluate the readiness of new DSM programs and services are shown below in [Table 5.](#page-226-1) 3 Table 5: Evaluation metrics for readiness of new DSM programs and services DSM PROGRAM READINESS Level 1: None Level...
AI summary The document outlines evaluation metrics for the readiness of new Demand Side Management (DSM) programs and services, categorized into five levels based on cost-effectiveness knowledge, market and program knowledge, and risk assessment.
4. PILOT OVERVIEW
AI summary The section outlines a pilot program overview within a Nova Scotia regulatory proceeding, listing acronyms related to energy management, utility regulation, and program administration. Key terms include Demand Side Management (DSM), Public Utilities Act (PUA), and Nova Scotia Energy Board (NSEB), reflecting the regulatory and operational context of the proceeding.
4.2 Pilot Lifecycle The pilot lifecycle for developing new initiatives and launching them as programs is shown in Figure 2 below. Figure 2: Pilot lifecycle process flow The pilot lifecycle begins with evaluating ideas for feasibility, valu...
AI summary The pilot lifecycle outlines stages for developing initiatives into programs, including feasibility evaluation, concept refinement, planning with stakeholder input, execution with testing and iteration, and concluding with a recommendation package for full-scale launch. Metrics from Innovation Goals (1.1) are used throughout.
1 1. EXECUTIVE SUMMARY 2 EfficiencyOne (E1) delivers demand side management (DSM) programs that offer benefits to customers 3 and the electric utility. While DSM is a key resource option for delivering clean, affordable, reliable and 4 saf...
AI summary EfficiencyOne (E1) highlights that demand side management (DSM) programs reduce customer bills, offsetting potential rate increases. However, equity concerns arise as non-participating customers face higher rates. E1's Rate and Bill Impact Analysis (RBIA) assesses historical and future DSM impacts, informing Nova Scotia Energy Board (NSEB) decisions on DSM investments from 2011–2026 and future plans (2027–2031).
1 2. INTRODUCTION 2 The forward-looking RBIA is an analysis of the rate and bill impacts associated with the proposed DSM - 3 investment only. It compares the impacts of the proposed DSM investment to a scenario where there is - 4 no DSM i...
AI summary The document discusses the forward-looking and historical Rate and Bill Impact Analysis (RBIA) for Demand Side Management (DSM) investments in Nova Scotia. It highlights E1's proposal to eliminate historical RBIA filings except during DSM Plan Application years, and the NSUARB's acceptance of this approach. The analysis informs DSM investment levels and considers non-participant impacts.
4 3. 2027–2031 DSM PLAN RBIA RESULTS - 5 The results in this section are for the 2027–2031 DSM Preferred Plan. All impacts are calculated relative - 6 to a scenario where no DSM is conducted in 2027–2031. Results are summarized in Attachme...
AI summary The 2027–2031 DSM Preferred Plan RBIA results compare impacts to a no-DSM scenario, analyzing energy efficiency, demand response, and solar-PV separately and combined. Attachments 1 and 2 detail model outputs, rate impacts, and bill adjustments for each rate class, with selected graphs illustrating key findings.
3.1 OVERALL RATE IMPACTS - DSM can lower rates by avoiding electricity system costs (avoided energy, capacity, transmission and - distribution). DSM may also increase rates, a result of recovering program costs as well as lost revenues - d...
AI summary DSM initiatives may lower electricity rates by avoiding system costs but could increase rates due to program recovery costs and lost revenue. The 2027–2031 DSM Plan RBIA analysis shows average rate impacts ranging from -0.1% to +0.9% over 2027–2046, with higher short-term increases (+1.6% to +4.7%) during program cost recovery (2027–2031) and lower long-term impacts (-0.8% to -0.1%) post-recovery (2032–2046).
11 3.2 OVERALL BILL IMPACTS Generally speaking, ratepayers that participate in DSM programs directly benefit by reducing their electricity consumption and thereby lowering their electricity bills. Together, the level of reduced consumption...
AI summary DSM programs in Nova Scotia reduce electricity bills for participants by 0.04% to -37%, while non-participants see minimal increases (0.1% to +0.8%). Total customer bill impacts range from -0.04% to -3.4%, with $0.4 billion in savings for ratepayers due to reduced revenue requirements from 2027–2031 DSM initiatives.
4 [Table 1](#page-243-1) highlights results in more detail by individual rate class for the 2027–2031 forward looking RBIA. 6 Table 1: Rate and Bill Impacts by Rate Class as a Result of 2027-2031 DSM Preferred Plan Activities Preferred Pla...
AI summary Table 1 presents the rate and bill impacts by rate class resulting from the 2027–2031 DSM Preferred Plan activities. The data shows the average rate impact, average bill impact for participants and non-participants, and total class average bill impact across various rate classes.
3.4 COMPARISON OF 2027-2031 PREFERRED PLAN AND ALTERNATE
AI summary The section compares the preferred plan and alternate for 2027-2031, though no specific details are provided in the text. Key regulatory and energy-related terms are referenced, including demand-side management, energy efficiency, and utility regulations.
SCENARIO RBIA RESULTS Full results, by rate class, are provided in Attachments 2 and 3 for the 2027–2031 DSM Preferred Plan and Alternate Scenario, respectively. This section compares key outputs between the two. Rate impacts for both the...
AI summary The document compares rate and bill impacts between the DSM Preferred Plan and Alternate Scenario (2027–2031). Rate impacts are nearly identical, with minor increases (0.02% residential, 0.01% large industrial) from residential demand response in the Preferred Plan. Bill impacts differ by 0.04% lower residential bills in the Preferred Plan, with all other differences negligible.
2 Alternate Scenario)
AI summary The document references an alternate scenario within a regulatory proceeding, likely exploring demand-side management (DSM) strategies, cost recovery mechanisms, and energy efficiency programs. Key entities include NS Power, NSEB, and DSMAG, with topics focusing on regulatory frameworks and program evaluations.
5 4. 2026 HISTORICAL DSM RBIA RESULTS - 6 The results in this section are for DSM activities that have occurred from 2011–2024 and are approved for - 7 2025–2026. All impacts are calculated relative to a scenario where no DSM is conducted...
AI summary This section presents DSM RBIA results for activities from 2011–2024, approved for 2025–2026. Impacts are calculated against a no-DSM baseline scenario. Results are summarized in Attachment 4, separated by energy efficiency and demand response, with rate-class-specific summaries in Attachment 1. Graphs in the summaries reflect model outputs.
4.1 OVERALL RATE IMPACTS - The RBIA for the 2011–2026 historical DSM Activities demonstrates the following rate impacts associated with DSM activities: - average rate impacts (by rate class) over the study period (2011–2041) range from 0.5...
AI summary The RBIA analysis shows rate impacts from 2011–2026 DSM activities, with average impacts ranging from 0.5% to 3.2% (2011–2041), 1.4% to 5.5% (2011–2026), and -0.6% to +0.9% (2027–2041). Factors include DSM cost recovery and annual avoided costs. Electricity rates are projected to rise 72% for residential classes due to non-DSM factors.
11 4.2 OVERALL BILL IMPACTS - 12 The 2026 Historical RBIA demonstrates the following bill impacts associated with DSM activities: - 13 average participant bill impacts (by rate class) over the study period (2011–2041) range from 14 -12.7 t...
AI summary The 2026 Historical RBIA shows DSM activities from 2011–2026 led to average bill impacts ranging from -12.7% to -2.8% for participants, +0.5% to +2.9% for non-participants, and -8.2% to -2.8% for total customers. Net savings for Nova Scotia ratepayers are estimated at $3.2 billion due to reduced revenue requirements.
10 [Table 2,](#page-248-1) below, highlights results in more detail by individual rate class for the 2026 Historical RBIA. 12 Table 2: Rate and Bill Impacts by Rate Class over the study period (2011–2041) from 2011-2026 Historical DSM 13 A...
AI summary Table 2 presents the Rate and Bill Impact Analysis (RBIA) by rate class for the 2026 Historical DSM activities, showing average rate and bill impacts from 2011 to 2041. The data highlights savings for participants and non-participants across different rate classes.
8 5.1 ACTIVE PARTICIPATION METHODOLOGY - 9 Previously, participant estimates were calculated using a 'cumulative' methodology. This did not account - for the measure life of savings, resulting in the potential for the number of cumulative...
AI summary The document discusses a shift from a cumulative to an annual/active participation methodology in the 2026 DSM Extension RBIA, addressing overestimation of participants and underestimation of savings by considering measure life and separating active from expired participation.
5.2 RENEWABLE TO RETAIL - Adjustments were made to address two issues caused by the addition of the Renewable to Retail program - within the rate and bill impact analysis. 1 First, the DSM rate rider is applied to total class volumes inclu...
AI summary Adjustments were made to the Renewable to Retail program's rate and bill impact analysis to address two issues: the exclusion of Renewable to Retail GWh in DSM rate rider calculations, leading to overestimated rate impacts, and the omission of retailer energy savings in bill impact calculations. NS Power adjusted load data and models to correct these issues.
5.3 RBIA STUDY PERIOD A solar-PV resource was modelled for the first time as part of the 2027–2031 DSM Plan. With a 30-year measure life, solar-PV installations in 2031 would generate DSM impacts through 2060. However, the NS Power rate mo...
AI summary The 2027–2031 DSM Plan initially considered extending the RBIA study period to 2060 to account for solar-PV impacts, but NS Power and E1 opted to retain the 2055 model configuration. Reasons included data limitations, solar-PV's minor role compared to expiring energy efficiency measures, and the adequacy of 2046 impacts for decision-making.
6. METHODOLOGY AND ASSUMPTIONS Attachment 5 describes the overall modelling and key assumptions that apply to the 2027–2031 DSM Plan and 2026 Historical RBIA.
AI summary Attachment 5 outlines the methodology and key assumptions for the 2027–2031 Demand Side Management (DSM) Plan and the 2026 Historical Rate and Bill Impact Analysis (RBIA).
7. FUTURE CONSIDERATIONS E1 understands that NS Power has developed an updated Cost of Service Study (COSS) which has been filed with the NSEB as part of NS Power's 2026–2027 General Rate Application (M12451). Once concluded, E1 will work...
AI summary E1 acknowledges NS Power's updated Cost of Service Study (COSS) filed with the NSEB as part of its 2026–2027 General Rate Application (M12451). E1 will collaborate with stakeholders to assess implications for the Rate and Bill Impact Analysis (RBIA). Future RBIA applications will address the 2032–2036 DSM Resource Plan and 2035 historical RBIA, expected in early 2035.
5 8. CONCLUSION - 6 Highlights from the 2027–2031 DSM Preferred Plan RBIA analysis include: - Over the 20 years of the study period, participants in DSM programs see average annual bill 8 reductions ranging from a low of 0.04 percent (aver...
AI summary The RBIA analysis for the 2027–2031 DSM Preferred Plan highlights that Nova Scotian ratepayers will save $0.4 billion over 20 years due to energy and demand reductions. The analysis shows varying bill impacts for participants and non-participants, with maximizing customer participation helping to mitigate rate impacts. The RBIA excludes non-rate-related benefits such as reduced greenhouse gas emissions and local economic investment.
DATE FILED: March 31, 2026 Page 8 of 8 Attachment 4: Results by Rate Class 2026 Historical Line# Rate and Bill Impacts of DSM on the Residential Class 1 2011 2012 2013 2014 2015 2016 2017 2018 2019 2020 2021 2022 2023 2024 2025 2026 2027 2...
AI summary The document presents historical data on the rate and bill impacts of Demand Side Management (DSM) on the residential class from 2011 to 2055. It includes metrics such as net incremental energy savings, total annual energy savings, DSM expenditures, and participant activity over time.
This graph shows bill impacts of all DSM resources combined,as percentage differences relative to the no-DSM scenario. 'Participants' represents a customer with average energy use and average DSM savings . 'Non-Participants' represents a c...
AI summary The text discusses the bill impacts of Demand Side Management (DSM) resources, comparing participants and non-participants, and presents graphs showing annual and active participation rates for different DSM resources. The figures illustrate how DSM affects customer bills and participation levels across various resources.
DATE FILED: March 31, 2026 Page 1 of 8 Line# Rate and Bill Impacts of DSM on the Small General Class 1 2011 2012 2013 2014 2015 2016 2017 2018 2019 2020 2021 2022 2023 2024 2025 2026 2027 2028 2029 2030 2031 2032 2033 2034 2035 2036 2037 2...
AI summary The document presents a table analyzing the rate and bill impacts of Demand Side Management (DSM) on the Small General Class from 2011 to 2055. It details energy savings, expenditures, participant numbers, and energy savings per participant over time, highlighting trends and changes in DSM effectiveness and participation.
This graph shows bill impacts of all DSM resources combined,as percentage differences relative to the no-DSM scenario. 'Participants' represents a customer with average energy use and average DSM savings . 'Non-Participants' represents a c...
AI summary The text discusses the bill impacts of Demand Side Management (DSM) resources compared to a no-DSM scenario, showing participation rates for different DSM resources. It also explains how participation is measured, distinguishing between 'Annual' and 'Active' participation, and highlights potential overlaps in participant counts across resources.
DATE FILED: March 31, 2026 Page 2 of 8 Line# Rate and Bill Impacts of DSM on the General Class 1 2011 2012 2013 2014 2015 2016 2017 2018 2019 2020 2021 2022 2023 2024 2025 2026 2027 2028 2029 2030 2031 2032 2033 2034 2035 2036 2037 2038 20...
AI summary The table presents the rate and bill impacts of Demand Side Management (DSM) on the General Class over time, including energy savings, expenditures, and participant numbers. It highlights trends in energy savings and participant engagement from 2011 to 2055.
This graph shows bill impacts of all DSM resources combined,as percentage differences relative to the no-DSM scenario. 'Participants' represents a customer with average energy use and average DSM savings . 'Non-Participants' represents a c...
AI summary The text includes figures analyzing the bill impacts of Demand Side Management (DSM) resources, participation rates across different DSM programs, and related metrics. The figures compare participants, non-participants, and total customers, and show annual and active participation rates by DSM resource.
fter removing double-counting of participants from multiple resources. DATE FILED: March 31, 2026 Page 3 of 8 This graph shows bill impacts of all DSM resources combined,as percentage differences relative to the no-DSM scenario. 'Participa...
AI summary The text discusses the bill and rate impacts of Demand Side Management (DSM) resources, illustrating participation rates and double-counting adjustments. It includes graphical representations of annual and active participation, differentiated by DSM resources and customer classes, with a focus on hypothetical scenarios and participation metrics.
DATE FILED: March 31, 2026 Page 4 of 8 Line# Rate and Bill Impacts of DSM on the Small Industrial Class 1 2011 2012 2013 2014 2015 2016 2017 2018 2019 2020 2021 2022 2023 2024 2025 2026 2027 2028 2029 2030 2031 2032 2033 2034 2035 2036 203...
AI summary The document presents a detailed table showing the rate and bill impacts of Demand Side Management (DSM) on the small industrial class over several years, including energy savings, expenditures, number of participants, and average energy savings per participant. The data spans from 2011 to 2055 and includes metrics such as net incremental and total annual energy savings in gigawatt-hours, DSM expenditures in millions of dollars, and participant numbers.
This graph shows bill impacts of all DSM resources combined,as percentage differences relative to the no-DSM scenario. 'Participants' represents a customer with average energy use and average DSM savings . 'Non-Participants' represents a c...
AI summary The document presents graphical data on the bill impacts of Demand Side Management (DSM) resources, comparing participants and non-participants, and showing annual and active participation rates across different DSM resources. The figures illustrate how DSM affects customer energy use and rates, with a focus on participation metrics and rate impacts.
fter removing double-counting of participants from multiple resources. DATE FILED: March 31, 2026 Page 5 of 8 This graph shows bill impacts of all DSM resources combined,as percentage differences relative to the no-DSM scenario. 'Participa...
AI summary The document includes graphs analyzing the bill and rate impacts of Demand Side Management (DSM) resources, as well as participation rates across different customer classes. It distinguishes between 'Participants' and 'Non-Participants' and accounts for double-counting of participants across multiple resources.
fter removing double-counting of participants from multiple resources. DATE FILED: March 31, 2026 Page 6 of 8 This graph shows bill impacts of all DSM resources combined,as percentage differences relative to the no-DSM scenario. 'Participa...
AI summary The text discusses the bill and rate impacts of Demand Side Management (DSM) resources, including participation rates for different customer classes. It highlights the distinction between 'Participants' and 'Non-Participants' and provides visual representations of participation and impact data, with adjustments for double-counting across resources.
fter removing double-counting of participants from multiple resources. DATE FILED: March 31, 2026 Page 7 of 8 This graph shows bill impacts of all DSM resources combined,as percentage differences relative to the no-DSM scenario. 'Participa...
AI summary The document presents graphical data on the bill impacts of Demand Side Management (DSM) resources, comparing participants and non-participants, and illustrates participation rates across different DSM resources. It also references an attachment containing assumptions for the 2027-2031 DSM Plan and historical data from 2026.
5 1. GENERAL APPROACH - 6 E1 has used the "snapshot" approach recommended by Synapse, in which the impacts of specific - 7 program years are analyzed (in this case 2011–2026 programs for the 2026 historical RBIA and - 8 2027–2031 programs...
AI summary E1 employed Synapse's recommended 'snapshot' approach, analyzing specific program years (2011–2026 and 2027–2031) for RBIA and DSM Plan assessments, rather than evaluating long-term Demand Side Management impacts.
2. RESOURCES AND SCENARIOS - Both the 2027–2031 DSM Plan analysis and the 2026 historical analysis include the NS Power rate - model (Attachments 7 and 8) and the E1 RBIA model (Attachments 9 and 10). The analyses - compare two scenarios:...
AI summary The document compares DSM and no-DSM scenarios using NS Power and E1's RBIA models, analyzing utility costs, energy reductions, and rate impacts. It outlines resource combinations (e.g., Energy Efficiency Only, Solar-PV Only) and notes that rate impacts isolate DSM effects but do not reflect actual timing of rate increases. Results are summarized in Appendix B, Attachment 1.
2.1 ENERGY EFFICIENCY INPUTS - For the 2027–2031 DSM Plan RBIA, first-year energy, lifetime energy, demand savings and expenditures developed at the program component level were allocated to rate classes in proportion with the actual rate...
AI summary The 2027–2031 DSM Plan RBIA allocates energy savings and expenditures by rate class using historical 2022–2024 data and weighted-average measure lives (WAMLs). Solar-PV inputs are allocated entirely to the residential rate class with a 30-year measure life, excluded from historical RBIA periods. Savings estimates for 2025–2026 use the approved 2023–2025 DSM Plan and 2026 extension.
7 2.3 DEMAND RESPONSE INPUTS - 8 Demand response inputs for the 2027–2031 DSM Plan RBIA come from Guidehouse's DRSim™ - 9 model results. Rate class allocations for the BNI Curtailment program were calibrated for the - 2027–2031 DSM Plan RB...
AI summary Demand response inputs for the 2027–2031 DSM Plan RBIA are derived from Guidehouse's DRSim™ model, historical data (2011–2024), and the approved 2023–2025 DSM Plan. Modeling assumes no energy impacts and a one-year measure life for demand response programs.
4. TIME PERIOD DEFINITIONS - The following time periods apply to the RBIA analysis: - DSM delivery period: the timeframe over which DSM programs are delivered. - The DSM delivery period included in the 2027–2031 DSM Plan RBIA is 2027–2031...
AI summary The document defines three time periods for the Rate and Bill Impact Analysis (RBIA) of Nova Scotia's Demand Side Management (DSM) programs: DSM delivery (2027–2031 and 2011–2026), cost recovery (same periods), and study periods (2027–2046 and 2011–2041). Energy efficiency impacts, not solar-PV, determine the study period, with solar-PV effects visible until 2055.
11 5. AVOIDED COSTS Avoided costs are calculated at the system level using evaluated DSM savings and avoided cost rates in four categories: generation, transmission, distribution, and energy. Avoided costs used for the 2027–2031 DSM Plan a...
AI summary Avoided costs are calculated at the system level across four categories: generation, transmission, distribution, and energy. These costs are used for the 2027–2031 DSM Plan and its RBIA, with details provided in Appendix A and a table for historical years.
7.1 PARTICIPATION COUNTS BY CLASS - Participation estimates used in the RBIA model are different than participation estimates used in - development of DSM plans, since the RBIA tracks participating accounts , rather than the number - of pr...
AI summary The RBIA model uses account-based participation estimates, differing from DSM plans which track products. RBIA de-duplicates across programs and years, calculating annual and active participants to determine bill savings per participant.
4 7.2.2 UNTRACKED PARTICIPATION - 5 E1 operates two program components that offer rebates at the point-of-sale: residential Instant - 6 Savings and the Instant Rebates portion of Business Energy Rebates (BER-IR). These program - 7 componen...
AI summary E1's Instant Savings and BER-IR programs use transaction records and research to estimate participation due to lack of direct data collection. The methodology changed in 2027, abandoning the prior assumption that all large commercial/industrial customers participated annually, due to declining participation from lighting phase-outs in Instant Rebates.
Active Participation - For historical years (2011–2024), to calculate the number of active participants, E1 starts with - the annual participation and for each subsequent year adds the number of new participants - (calculated based on surv...
AI summary E1 calculates active participants for historical years (2011–2024) by adding new participants and subtracting expiring ones based on savings lifespan. For future years, a re-participation factor derived from 2019–2023 data is applied, with participant numbers degrading post-2032 at the same rate as cumulative energy savings.
7.2.3 RESIDENTIAL BEHAVIOUR PARTICIPATION - The Residential Behaviour program component applies the rate class weighted-average measure - life to estimate active participants; this is consistent with other tracked programs. For program- -...
AI summary The Residential Behaviour program uses a rate-class weighted-average measure life to estimate participants, ensuring accurate tracking without overestimation. A cross-participation factor prevents double-counting across tracked/untracked participation. Residential Behaviour is excluded from the 2027–2031 DSM Plan RBIA, focusing on post-delivery year participation decay aligned with energy savings.
7.3 SOLAR-PV PARTICIPATION - For the 2027–2031 DSM Plan, solar-PV participation is a direct output of Guidehouse's ProCESS - model. 100% of participation was allocated to the residential rate class. Active participation was - calculated ba...
AI summary The 2027–2031 DSM Plan uses Guidehouse's ProCESS model to allocate 100% of solar-PV participation to residential rate classes. Solar-PV measures, with a 30-year lifespan, do not expire by 2055, as their duration exceeds the model's timeframe.
7.4 DEMAND RESPONSE PARTICIPATION - For 2023–2024 years, demand response participation was based on historical results. For 2025– - 2031 years, demand response participation inputs by rate class come from Guidehouse's DRSim™ - model. - 1 T...
AI summary For 2023–2024, demand response participation is based on historical results. For 2025–2031, it uses Guidehouse's DRSim™ model. Participation counts annual active participants, assuming a one-year measure life.
5 7.5 COMBINED PARTICIPATION - 6 In the DSM scenario—where the combined effects of energy efficiency, demand response, and - 7 Solar-PV are evaluated—the rate-class participation is assumed to be the highest level observed - 8 among the th...
AI summary In the DSM scenario, combined participation of energy efficiency, demand response, and solar-PV uses the highest observed rate-class participation due to overlapping program participation, particularly between energy efficiency and solar-PV, and energy efficiency and demand response.
8. CALCULATION OF RATE IMPACTS - Rate impacts are calculated in NS Power's Rate Model (Attachment 7 and 8) to reflect NS Power's - Cost of Service in a more precise manner. It reflects the Energy Board approved retail rates and - Cost of S...
AI summary NS Power's Rate Model calculates rate impacts for the 2027–2031 DSM Plan using Forecast Unit Revenues, blending DSM energy and demand impacts into a single rate. E1's RBIA Model uses these revenues to assess bill impacts, excluding demand charges as they are already incorporated into blended rates. The analysis isolates DSM effects by comparing DSM and no-DSM scenarios, assuming equal energy and demand savings.
4 9.1 NO-DSM BILL IMPACTS - 5 In the no-DSM scenario, for each rate class, and for each year, the total class energy consumption - 6 is divided by the number of customers to produce an estimate of the average customer's - 7 consumption. Th...
AI summary The no-DSM scenario calculates average customer energy consumption by dividing total class energy consumption by the number of customers, then uses these averages with no-DSM rates to determine average bills for each rate class and year.
9.2 NON-PARTICIPANT BILL IMPACTS - In the DSM scenario, non-participants in DSM programs are assumed to use the same amount of - energy as they do in the no-DSM scenario. Their bill impacts are therefore driven only by changes - in rates u...
AI summary Non-participants in DSM programs experience bill impacts solely from rate changes in the with-DSM scenario, not energy use. Fixed customer charges cause percentage bill impacts to differ from rate impacts. This analysis highlights how rate structures affect non-participants independently of DSM program participation.
9.3 PARTICIPANT BILL IMPACTS - For the DSM scenario, within each rate class in each year, total annual savings (i.e., current-year - savings plus persistent savings from past years) are divided equally amongst the number of active - partic...
AI summary The DSM scenario assumes equal annual savings per participant across rate classes, ignoring varying participation depths. E1's RBIA includes free-riders, leading to underestimated average savings. Total Customers category allocates DSM savings equally to all customers, not differentiating between participants and non-participants.
10. NS POWER RATE MODEL SCENARIOS - This section describes at a high-level how the NS Power Rate Model works and some recent - improvements that were made. - Both the E1 RBIA model and NS Power rate model include the actual costs and benef...
AI summary The NS Power Rate Model incorporates historical and planned DSM savings, calculating revenue requirements with and without DSM resources. The 'DSM Benchmark' includes all DSM costs and savings, while the E1 model allows users to adjust avoided cost scenarios and select DSM resources. Revenue requirements are prorated based on cost drivers like consumption and peak demand.
Methodology for determination of changes in NS Power's base cost rates as a result of DSM-induced changes in class usage and total system costs November 27, 2020
AI summary This document outlines the methodology for adjusting NS Power's base cost rates based on DSM-induced changes in class usage and system costs. It involves regulatory analysis under the ERBA and NSUARB frameworks, focusing on cost recovery and rate design considerations.
1.0. Introduction In an effort to more precisely and accurately align EfficiencyOne's (E1) RBIA Model with the methodological process used by NS Power in setting of its base cost rates, all rate setting functionality from E1's RBIA model h...
AI summary EfficiencyOne's RBIA model is being realigned with NS Power's COSS methodology, shifting rate-setting responsibility to NS Power. NS Power will provide annual inputs (e.g., revenue forecasts, DSM charges) to E1's RBIA model under 'With DSM' and 'No DSM' scenarios, with NS Power responsible for cost allocation methods and data assumptions.
Revenue Requirement Ordinarily, the base cost rate setting process used in rate case applications requires a great amount of detailed cost inputs to determine revenue requirement. Annual rate base data needs to be collected on a variety of...
AI summary The revenue requirement process typically requires detailed cost data, but for the RBIA, only DSM-induced avoided costs are considered while keeping other costs constant. This simplifies analysis by focusing on directional and relative rate changes due to DSM programs.
Cost of Service Studies COSS provides the most insight into class cost causation as based on changes in its energy and demand usage. It shows in a transparent way how rate class usage of demand and energy services within each functional ar...
AI summary COSS provides insights into cost causation by analyzing energy and demand usage changes. NS Power's annual Load Forecast Report and E1's long-term usage forecasts enable simplified COSS analysis for rate adjustments, bypassing detailed future cost data collection.
Conclusions Bypassing the detailed COSS ratemaking step, which is intended to show how DSM-induced, cost causative changes in usage affects rates will produce misleading results and create difficulties in interpretation. Any such rate anal...
AI summary Bypassing the COSS ratemaking step leads to misleading rate analyses by failing to account for DSM-induced changes in usage and embedded system cost reallocations. A simplified COSS process is recommended to provide precise results and better insights into how usage changes affect total service costs.
3.0. Applied Approach The relative changes in rates due to DSM are determined by conducting two separate rate setting analyses under the "With DSM" and "No DSM" scenarios. The rate setting process under each scenario is broken out by two s...
AI summary The applied approach involves analyzing rate changes due to DSM by evaluating two scenarios ('With DSM' and 'No DSM') and separating cost determination into FAM-related and non-FAM-related subprocesses. This method allows for a detailed comparison of rate impacts with and without DSM, facilitating informed regulatory decisions on cost allocation.
3.1 Revenue Requirement The annual revenue requirements under the "With DSM" scenario are kept consistent with the test year information from the preceding rate cases. The non-FAM costs in the years following the 2014 test year from the 20...
AI summary The document outlines revenue requirements under 'With DSM' and 'No DSM' scenarios, adjusting costs for inflation and DSM impacts. FAM and non-FAM costs are modified based on test year data and avoided fuel costs. Historic cost true-ups are excluded due to minimal impact, lack of rigor, and complexity. The analysis uses data from 2011-2035 and references prior rate proceedings.
3.2.1 Functionalization of System Costs As indicated in the Revenue Requirement section above, NS Power has used the test year revenue requirements, already functionalized by the four areas, from the historic rate cases. In the "With DSM"...
AI summary NS Power has functionalized system costs based on historic rate cases, adjusting revenue requirements for changes in load and inflation. The impact of DSM on load savings and avoided costs is considered, with examples provided on the true-up of depreciation costs from the Maritime Link project.
3.2.2 Classification of System Costs Costs within each area are classified into appropriate services. Generation and transmission costs are classified into energy and demand. Distribution costs are classified between demand and customer. R...
AI summary System costs are classified into energy, demand, and customer categories. Generation costs depend on unit type (baseload, peaking, environmental), with NS Power using a linear equation for classification. Transmission costs align with load factors, while distribution and retail costs remain static except for inflation. DSM impacts reclassification but does not alter customer numbers.
3.2.3 Allocation of Costs to Rate Classes Annual cost requirements within each service of each functional area are apportioned to rate classes based on class share in the underlying usage both in the "With DSM" and "No DSM" case.
AI summary Annual costs for each service and functional area are allocated to rate classes based on their share of usage in both 'With DSM' and 'No DSM' scenarios. This approach ensures cost distribution reflects actual consumption patterns across different rate classes.
FAM-related Costs The FAM-related costs are allocated to rate classes using the following two-step process: • Annual class energy usage is multiplied by the benchmark unit cost $/MWh DATE FILED: March 31, 2026 Page 7 of 16 - o In the "With...
AI summary The Fuel Adjustment Mechanism (FAM) allocates costs via a two-step process using benchmark unit costs, with distinct methods for 'With DSM' and 'No DSM' cases. The current model does not differentiate between energy and demand-related costs, a limitation stemming from historical low demand costs. Recent increases (15% of FAM costs due to Maritime Link) may warrant future RBIA adjustments.
Non-FAM related Costs The non-FAM-related costs are allocated to rate classes using the following two-step process: - Annual class usages of energy and demand services are multiplied by benchmark $/MWh and $/MW unit costs, respectively - o...
AI summary Non-FAM-related costs are allocated to rate classes via a two-step process: multiplying annual class usages by benchmark costs from 'With DSM' or 'No DSM' cases, then scaling estimates to match revenue requirements per functional area. The 'With DSM' case uses the most recent prior rate case, while the 'No DSM' case references the same calendar year as the 'With DSM' case.
DSM Costs The annual DSM-related costs incurred by individual rate classes, as provided by E1, are apportioned to rate classes based on the 25/75 rule. 75 percent of the costs incurred by each class is treated as direct responsibility of e...
AI summary The document outlines the apportionment of annual DSM costs among rate classes using a 25/75 rule, with 75% directly assigned to each class and 25% distributed based on energy and demand usage metrics, including load factor, system generation share, and winter peak demand.
3.2.4 Generic COSS Results The actual results from the above cost allocation process under the "With DSM" and "No DSM" scenarios are presented in the "COSS Outputs" tab within NS Power's rate model, where the long-term trends in annual rel...
AI summary The COSS Results compare 'With DSM' and 'No DSM' scenarios, showing higher unit costs in historic periods due to DSM program costs and lower differentials in out-years as DSM measures expire. Fuel-cost-heavy classes (e.g., Large Industrial) benefit more from DSM, while fixed-cost-heavy classes (e.g., Domestic) see less impact. Trends are analyzed via NS Power's rate model.
3.3 Unit Revenue Determination For the directional purposes of the RBIA model, it is not considered necessary to develop annual rates with all charges under the "With DSM" and "No DSM" cases. Rather, it is sufficient for NS Power to provid...
AI summary NS Power determines unit revenues for rate classes by providing blended revenues in cents per kWh, excluding customer charges for residential and small general classes. Factors like fuel cost adjustments, deferrals, rate smoothing, and revenue-to-cost ratios are excluded, but this has no material effect on relative changes between 'With DSM' and 'No DSM' cases.
Attachment A
AI summary Attachment A lists acronyms related to Nova Scotia's energy regulation, including organizations, programs, and legal frameworks involved in utility proceedings. Key terms cover demand-side management, rate design, and energy efficiency initiatives.
"COSS Data Inputs" tab This tab includes all annual test year class usage and embedded costs from the COSS and BCF COSS filed in GRA and BCF proceedings as well as a forecast of annual usage by class per the most recent ten-year Load Forec...
AI summary The 'COSS Data Inputs' tab compiles annual test year class usage, embedded costs from COSS and BCF COSS filings in GRA and BCF proceedings, a ten-year load forecast, and DSM expenditures by rate class. This data informs class unit cost and revenue calculations.
"E1 Data Inputs" tab This tab includes information provided to NS Power by E1 on DSM Program measures and avoided unit costs, all of which are used in determination of class unit costs and revenues.
AI summary The 'E1 Data Inputs' tab contains information provided by E1 to NS Power regarding DSM Program measures and avoided unit costs, which are essential for calculating class unit costs and revenues.
Savings in energy and demand usage by rate class Savings in energy and demand usage arising from DSM programs for each class are tracked in the following class tabs: R-Savings, SG-Savings, G-Savings, LG-savings, SI-Savings, MI-Savings, LI-...
AI summary The document outlines how energy and demand savings from DSM programs are tracked across rate classes (R-Savings, SG-Savings, etc.) using data from 2011–2022. Annual savings are calculated by E1 using methods from its RBIA Reports, with adjustments for energy losses based on the COSS study.
"Total-Savings" tab The "Total-Savings" tab provides a sum of annual class savings in energy and demand usage at the generator's gate and customer's meter. In addition, class demand savings at the high side of the bulk power substation are...
AI summary The 'Total-Savings' tab calculates annual energy and demand savings at the generator's gate and customer's meter, including avoided fuel, generation, transmission, and distribution costs. FAM-related avoided costs use unit fuel costs multiplied by energy savings, while non-FAM costs use avoided infrastructure costs per MW demand savings.
Cost of Service Studies Apportionment of costs to rate classes is done separately for the "With DSM" and "No DSM" cases" in the tabs bearing the same names.
AI summary The document discusses the separate apportionment of costs to rate classes under 'With DSM' and 'No DSM' scenarios, as outlined in corresponding tabs. This approach allows for distinct cost allocation analyses based on demand-side management considerations.
"With DSM" tab The "With DSM" tab provides annual cost allocation to rate classes based on long-term usage as included in NS Power's most recent Annual ten-year Load Forecast Report. This usage already reflects inclusion of DSM Program eff...
AI summary The 'With DSM' tab allocates annual FAM costs to rate classes using NS Power's load forecast, which includes DSM program effects. FAM costs for 2023-2035 are calculated via a two-step process: applying 2022 blended unit FAM costs to forecasted MWh usage, then scaling to match total annual FAM costs using a formula incorporating previous year costs and energy requirement deltas.
"No DSM" tab The "No DSM" tab provides annual cost allocation to rate classes absent DSM. The FAM-related costs in years 2011–2035 are calculated using the following process: - Annual FAM costs for each class are calculated by multiplying...
AI summary The 'No DSM' tab calculates annual Fuel Adjustment Mechanism (FAM) costs without Demand Side Management (DSM) savings. It uses blended unit FAM costs, scales class-specific costs to match total FAM estimates, and applies a formula incorporating energy requirement deltas and avoided FAM costs from the 'With DSM' case.
Comments The applied process is a simplification of a more elaborate cost allocation process where some FAM costs, such as fuel costs, are allocated to rate classes based on their shares in monthly energy requirements; some other FAM costs...
AI summary The document outlines a simplified cost allocation process for FAM (Fuel Adjustment Mechanism) and non-FAM costs, distinguishing between energy and demand-related allocations. It details methods like load factors, DSM integration, and inflation adjustments for 2023–2035, using data from COSS and prorating tables to distribute costs across rate classes.
"COSS Var" tab "COSS Var" provides differentials between cell values in the "No DSM" and "With DSM" tabs. Please note that the data layouts in the "No DSM" and "With DSM" tabs are identical with the exception for the treatment of DSM costs...
AI summary The 'COSS Var' tab compares cell values between 'No DSM' and 'With DSM' scenarios, highlighting differences in cost calculations. The 'No DSM' tab excludes Demand Side Management (DSM) costs, while the 'With DSM' tab includes them, with identical data layouts otherwise.
Results
AI summary The document section 'Results' is under review, with no substantive content provided. Key entities and topics are inferred from the context, including regulatory bodies, energy programs, and technical terms related to Nova Scotia's energy sector.
"COSS Outputs" tab The "COSS Outputs" tab provides two sets of bar graphs of percentage change in class rates due to DSM over the period 2011–2035 calculated as either arithmetic or load-weighted rate changes. The graphs within each set ar...
AI summary The 'COSS Outputs' tab presents bar graphs analyzing percentage changes in class rates due to DSM (Demand Side Management) from 2011–2035, using arithmetic or load-weighted rate changes. It breaks down effects on unit base cost revenues, including 'No DSM' scenarios and DSM cost inclusions. A control panel tests inflation and avoided cost scenarios on class unit costs and revenues.
"NSPI Inputs into RBIA" tab "NSPI Inputs into RBIA" provides pricing inputs requested by E1. It includes the following annual class data in years 201-2035 broken out by "With DSM" and "No DSM" scenarios: - Forecast Unit Revenues Before DSM...
AI summary The 'NSPI Inputs into RBIA' tab provides data for Rate and Bill Impact Analysis (RBIA) scenarios with and without Demand Side Management (DSM). It includes revenue forecasts, sales projections, demand forecasts, and customer counts from 2021–2035. Attachments detail NS Power rate models, E1 RBIA models, and an alternate scenario for 2027–2031.
2 The Alternate Scenario will invest $308.4 million to achieve 435.4 GWh of incremental cumulative net 3 energy savings, 85.0 MW of cumulative system-peak demand savings, 25.5 MW of available capacity from 4 demand , and 1.7 GWh of solar-P...
AI summary The Alternate Scenario involves a $308.4 million investment to achieve energy savings and demand reductions, with a focus on maintaining cost-effective BNI demand response programs and introducing new initiatives for Mi'kmaw communities. The residential Eco Shift pathway is excluded compared to the Preferred Plan.
17 Table 1: 2027–2031 Alternate Scenario Portfolio Level Insights Insights 2027–2031 Energy Efficiency Energy Savings as % of NS Power Load 0.8% Energy Savings (EE) Split (RES/BNI) 29/71 Demand Savings (EE) Split (RES/BNI) 44/56 Dedicated...
AI summary This table provides insights into the 2027–2031 alternate scenario portfolio, including energy efficiency savings, demand response capacity, solar-PV generation, and overall benefits of the alternative plan, such as energy savings, investment, and CO₂e reductions.
1.1 ALTERNATE SCENARIO – PORTFOLIO SAVINGS AND INVESTMENT 16 Table 2, below, provides portfolio-level savings and investment by year and in aggregate, inclusive of all 17 proposed DSM resources for the 2027–2031 Alternate Scenario. 18 19 2...
AI summary The document presents an alternate scenario analyzing portfolio-level savings and investments from 2027–2031, incorporating all proposed DSM resources. Table 2 summarizes these figures, reflecting the regulatory proceeding's focus on energy efficiency and investment planning under Nova Scotia's utility framework.
Table 2: 2027–2031 Alternate Scenario Investment and Savings 2027-2031 Portfolio Year Investment ($M) Lifetime Benefits ($ million) First-Year Energy Savings (GWh) Peak Demand Savings (MW) Lifetime Energy Savings (GWh) Low- Income & Equity...
AI summary Table 2 presents investment and savings data for energy efficiency and demand response programs from 2027 to 2031. It includes metrics such as investment, lifetime benefits, energy savings, peak demand savings, and weighted average measure life for various programs.
9 10 Table 3: 2027–2031 Alternate Scenario Savings and Investment by Program Component 2027-2031 Investment ($ million) Lifetime Benefits ($ million) First Year Energy Savings (GWh) Lifetime Energy Savings (GWh) Peak Demand Savings (MW) Av...
AI summary The table provides a detailed overview of energy efficiency (EE) and demand response (DR) programs for the 2027–2031 period, including investment, lifetime benefits, energy savings, and program administrator cost test (PAC) data. It highlights the contribution of various programs, such as residential and business EE initiatives, enabling strategies, and solar-PV programs, to overall energy savings and investment.
13 18 Columns may not add correctly due to rounding. Currency is expressed in nominal dollars. For the five-year total row, currency is a straight sum of 5 years of nominal values. Lifetime benefits for energy efficiency, demand response a...
AI summary The text discusses the methodology for calculating lifetime benefits of energy efficiency, demand response, and solar-PV programs, using net present value of avoided costs. It also outlines how low-income and equity impacts are calculated, including participation from specific programs and the use of the Program Administrator Cost Test (PAC) as a benefit/cost ratio.
4 Table 4: 2027 Alternate Scenario Savings and Investment by Program Component 2027 Investment ($ million) Lifetime Benefits ($ million) First Year Energy Savings (GWh) Lifetime Energy Savings (GWh) Peak Demand Savings (MW) Available Deman...
AI summary Table 4 outlines the 2027 alternate scenario savings and investment by program component, including residential and BNI EE programs, Enabling Strategies, and their respective investments, benefits, energy savings, and other metrics.
Columns may not add correctly due to rounding. Currency is expressed in nominal dollars. For the five-year total row, currency is a straight sum of 5 years of nominal values. Lifetime benefits for energy efficiency, demand response and sol...
AI summary The text outlines how lifetime benefits for energy efficiency, demand response, and solar-PV are calculated using net present value of avoided costs. It also discusses how low-income and equity impacts are reflected in program participation and mentions the PAC as a benefit/cost ratio for DSM investment.
1 Table 5: 2028 Alternate Scenario Savings and Investment by Program Component 2028 Investment ($ million) Lifetime Benefits ($ million) First Year Energy Savings (GWh) Lifetime Energy Savings (GWh) Peak Demand Savings (MW) Available Deman...
AI summary Table 5 outlines the 2028 Alternate Scenario Savings and Investment by Program Component, highlighting energy efficiency (EE) programs, enabling strategies (ES), demand response (DR), and solar-PV programs. It provides data on investment, lifetime benefits, energy savings, peak demand savings, and other metrics for residential and business, non-profit, and institutional (BNI) programs, as well as overall portfolio totals.
Currency is expressed in nominal dollars. For the five-year total row, currency is a straight sum of 5 years of nominal values. Lifetime benefits for energy efficiency, demand response and solar-PV are expressed as the net present value of...
AI summary The text outlines how currency is expressed in nominal dollars and discusses the calculation of lifetime benefits for energy efficiency, demand response, and solar-PV programs using net present value of avoided costs. It also addresses low-income and equity impacts based on participation in specific programs.
1 Table 6: 2029 Alternate Scenario Savings and Investment by Program Component 2029 Investment ($ million) Lifetime Benefits ($ million) First Year Energy Savings (GWh) Lifetime Energy Savings (GWh) Peak Demand Savings (MW) Available Deman...
AI summary The text presents a table titled '2029 Alternate Scenario Savings and Investment by Program Component' with columns related to investment, benefits, energy savings, and other metrics. However, no data is provided under the 'Residential EE Programs' row, leaving the content incomplete.
Currency is expressed in nominal dollars. For the five-year total row, currency is a straight sum of 5 years of nominal values. Lifetime benefits for energy efficiency, demand response and solar-PV are expressed as the net present value of...
AI summary The text discusses the calculation of lifetime benefits for energy efficiency, demand response, and solar-PV programs, expressed as net present value of avoided costs. It also highlights the inclusion of low-income and equity impacts from targeted and non-targeted programs.
1 Table 7: 2030 Alternate Scenario Savings and Investment by Program Component 2030 Investment ($ million) Lifetime Benefits ($ million) First Year Energy Savings (GWh) Lifetime Energy Savings (GWh) Peak Demand Savings (MW) Available Deman...
AI summary Table 7 outlines the projected investment, benefits, and savings across various energy efficiency (EE), enabling strategies (ES), demand response (DR), and solar-PV programs for 2030. The data highlights the financial and energy-saving impacts of these initiatives, including residential and business programs, and emphasizes the overall savings and investment required for the DSM portfolio.
Currency is expressed in nominal dollars. For the five-year total row, currency is a straight sum of 5 years of nominal values. Lifetime benefits for energy efficiency, demand response and solar-PV are expressed as the net present value of...
AI summary The text discusses the calculation of lifetime benefits for energy efficiency, demand response, and solar-PV programs, using net present value of avoided costs. It also highlights the consideration of low-income and equity impacts, including participation from dedicated and non-targeted programs.
Table 8: 2031 Alternate Scenario Savings and Investment by Program Component 2031 Investment ($ million) Lifetime Benefits ($ million) First Year Energy Savings (GWh) Lifetime Energy Savings (GWh) Peak Demand Savings (MW) Available Demand...
AI summary Table 8 presents the 2031 alternate scenario savings and investment by program component, including energy efficiency (EE), enabling strategies (ES), demand response (DR), and solar-PV programs. It outlines investments, lifetime benefits, energy savings, and other metrics for residential, business, and institutional programs, as well as the Mi'kmaw community initiatives.
1 1.3 ALTERNATE SCENARIO – PROGRAMS 15 Alternate tab for the Alternate Scenario). - 2 The Alternate Scenario removes the residential program component (Eco Shift) from the Demand - 3 Response program. 4 - 5 All other DSM programs in the Al...
AI summary The Alternate Scenario removes the residential Eco Shift program from Demand Response but retains energy efficiency and solar-PV programs, including new Mi'kmaw initiatives. Technical details are outlined in appendices, with no changes to energy efficiency or solar-PV measures compared to the Preferred Plan.
21 Table 9: 2027–2031 Alternate Scenario Rate Class Savings and Expenditures 2027–2031 Rate Class Year First Year Energy Savings (GWh) Lifetime Energy Savings (GWh) Peak Demand Savings (MW) Available Demand Response Capacity (MW) Generatio...
AI summary Table 9 presents energy savings and expenditures for different rate classes from 2027 to 2031 under an alternate scenario. It includes data on energy savings, peak demand savings, and expenditures in millions of dollars for residential, charitable, and small general rate classes.
4 List of Schedules 5 6 Schedule "A": Electricity Efficiency And ConservationDemand-side Management 7 Activities 8 Schedule "B": Compensation 9 Schedule "C": Performance Requirements 10 Schedule "D": Confidentiality Agreement 11 Schedule "...
AI summary The document outlines five schedules related to electricity efficiency, compensation, performance requirements, confidentiality, and an approved DSM resource plan. Key focus areas include demand-side management, energy conservation, and regulatory compliance frameworks.
38 5. NOTIFICATION OF SIGNIFICANT CHANGES 39 5.1 EfficiencyOne shall provide notice of Significant Changes to NSPI at the same time as 40 EfficiencyOne makes application to the UARB NSEB for the approval of the Significant 1 Changes. Subje...
AI summary EfficiencyOne must notify NSPI when applying for approval of significant changes to the EECA DSM Resource Plan. NSPI may submit written comments to UARB NSEB regarding these changes, subject to regulatory discretion.
1 10. SUBCONTRACTORS - 2 10.1 EfficiencyOne shall be permitted to subcontract the performance of any part of the EECA 3 DSM without the prior written approval of NSPI. - 4 10.2 Where EfficiencyOne subcontracts any part of the EECADSM, Effi...
AI summary EfficiencyOne may subcontract EECA DSM work without NSPI approval but remains fully liable for subcontractors' actions. Subcontractors cannot form direct contracts with NSPI. EfficiencyOne must ensure subcontractors uphold agreement rights and protections.
4 ELECTRICITY EFFICIENCY AND CONSERVATIONDEMAND-SIDE MANAGEMENT 5 ACTIVITIES
AI summary The document outlines Nova Scotia's regulatory focus on electricity efficiency, conservation, and demand-side management (DSM) activities. Key entities include NS Power, NSEB, and NSUARB, with emphasis on programs like DSMAG and E1. Topics cover energy efficiency, rate design, and regulatory frameworks.
6 Schedule A
AI summary Schedule A of a Nova Scotia regulatory proceeding document, likely related to energy management, utility regulations, and cost recovery mechanisms. Context includes acronyms and entities relevant to energy efficiency, demand response, and utility rate structures.
7 Electricity Efficiency and ConservationDemand-Side Management Activities The figure below identifies the scope of savings (3 5 year cCumulative Annual eEnergy sSavings, cCumulative Annual pPeak dDemand sSavings, cCumulative Annual eEnerg...
AI summary The document outlines Energy Efficiency Corporation (EECA) Demand-Side Management (DSM) performance targets over a five-year plan, including energy and peak demand savings, solar-PV generation, and low-income equity programs. Compliance requires achieving 90% of targets; otherwise, a regulatory process is triggered. Schedule B addresses compensation mechanisms.
45 Schedule B (Page 2 of 2)
AI summary Second page of Schedule B from a Nova Scotia regulatory proceeding, listing acronyms related to energy regulation, utility management, and demand-side programs. Context includes terms like DSM, PUA, NSEB, and NS Power, reflecting regulatory frameworks and energy initiatives in Nova Scotia.
PERFORMANCE REQUIREMENTS - I. UARBNSEB-APPROVED PERFORMANCE TARGETS, THRESHOLDS, AND INDICATORS - a) Performance Targets and Thresholds: - Performance Targets are set over the three five year contract period, rather than annually. - ii. Ef...
AI summary Performance targets for EfficiencyOne (E1) are set over three five-year contract periods, requiring 90% achievement of metrics like energy savings, peak demand reduction, and solar-PV generation. Non-compliance triggers regulatory action, with the Nova Scotia Energy Board (NSEB) determining remedies. Targets include specific programs for affordable housing and Mi'kmaw communities.
Appendix E Proposed Form of DSM Purchase Agreement (Clean) 2027-2031 DSM Resource Plan 1 2 Purchase Agreement for 3 Demand-Side Management Activities 4 5 Between 6 7 Nova Scotia Power Incorporated 8 9 and 10 11 EfficiencyOne 12 13 Effectiv...
AI summary Proposed DSM Purchase Agreement between Nova Scotia Power Incorporated (NSPI) and EfficiencyOne (E1) for 2027-2031, outlining Demand-Side Management (DSM) activities. The agreement is part of a regulatory proceeding, with an effective date of January 1, 2027, and was filed on March 31, 2026.
[Schedule "E": Approved DSM Resource Plan](#page-404-0) 1 27. SURVIVAL 17 2 [Remainder of page intentionally left blank]17 3 4 5 List of Schedules 6 Schedule "A": Demand-side Management Activities 7 Schedule "B": Compensation 8 Schedule "C...
AI summary The document outlines Schedule 'E' of the Approved DSM Resource Plan, which includes a table with incomplete data and a list of other schedules, such as Schedule 'A' for Demand-side Management Activities and Schedule 'D' for Confidentiality Agreement.
5. NOTIFICATION OF SIGNIFICANT CHANGES 5.1 EfficiencyOne shall provide notice of Significant Changes to NSPI at the same time as EfficiencyOne makes application to the NSEB for the approval of the Significant Changes. Subject to the terms...
AI summary EfficiencyOne must notify NSPI of significant changes to the DSM Resource Plan simultaneously with submitting an application to the NSEB for approval. NSPI retains the right to submit written comments on such changes under the Public Utilities Act.
6. SAFETY - 2 6.1 EfficiencyOne shall at all times be responsible for safety and loss management in the 3 supply or performance of the DSM. - 4 6.2 EfficiencyOne shall ensure that all employees, Subcontractors, agents and 5 representatives...
AI summary EfficiencyOne is mandated to manage safety and loss in Demand Side Management (DSM) and ensure compliance with federal, provincial, municipal, and internal health, safety, and environmental regulations.
7. PROTECTION OF PROPERTY - 9 7.1 EfficiencyOne shall take all commercially reasonable steps to protect the property of NSPI's customers and other third parties from damage which may occur as the result of the performance of the DSM. - 7.2...
AI summary EfficiencyOne is required to protect NSPI's customers' and third parties' property during DSM activities. It must indemnify NSPI for damages caused by its actions, excluding cases where NSPI's negligence is responsible.
9. EFFICIENCYONE'S COVENANTS - 9.1 EfficiencyOne warrants, covenants and agrees with NSPI that: - (a) it has all requisite capacity and authority to execute, deliver and perform its obligations under this Agreement; - (b) this Agreement ha...
AI summary EfficiencyOne's covenants with NSPI include legal authority, compliance with laws, proper execution of DSM, use of licensed personnel, and responsibility for subcontractors. EfficiencyOne must notify NSEB/NSPI of DSM supply disruptions and ensure adherence to regulations. Subcontractors are permitted but EfficiencyOne remains fully liable for their actions.
19. DISPUTE RESOLUTION - 19.1 In the event of a dispute in connection with this Agreement, a senior representative of EfficiencyOne and a senior representative of NSPI shall promptly meet to discuss and resolve the dispute and the Parties...
AI summary The dispute resolution process requires EfficiencyOne and NSPI to meet promptly to resolve disputes within 30 days (or 10 days for urgent matters). If unresolved, disputes are referred to the NSEB under Section 79P of the Act. EfficiencyOne must continue DSM unless NSEB authorizes suspension.
20. DEFAULT AND TERMINATION - 20.1 This Agreement may be terminated immediately by either Party, in whole or in part, upon the happening of one or more of the following events: - (a) EfficiencyOne's Franchise is terminated and the Agreemen...
AI summary The agreement can be terminated by either party if EfficiencyOne's franchise is terminated without assignment by the Minister or upon NSEB approval. Termination does not allow compensation for consequential losses, requires EfficiencyOne to discontinue DSM activities, and claims must be asserted within 30 days.
22. AUDIT AND INSPECTION - 2 22.1 EfficiencyOne shall, during the Term and for a period of thirty-six (36) months thereafter, 3 keep accurate records of all DSM supplied to NSPI, as necessary to determine that the 4 DSM was provided in acc...
AI summary EfficiencyOne must maintain DSM records for 36 months post-agreement. NSPI may request NSEB access to these records and inspect DSM operations, with EfficiencyOne required to facilitate inspections. Compliance with agreement terms is emphasized through audit and inspection rights.
25. COORDINATION MEETINGS AND REPORTS - 25.1 During the Term of this Agreement, EfficiencyOne shall prepare and deliver to the NSEB and NSPI a quarterly report (the " Quarterly Report ") in a form acceptable to the NSEB. - 25.2 EfficiencyO...
AI summary EfficiencyOne must submit quarterly and annual progress reports to NSEB and NSPI detailing DSM performance, financials, and discrepancies. Quarterly coordination meetings between NSPI and EfficiencyOne are mandated to ensure effective DSM planning and implementation.
4 DEMAND-SIDE MANAGEMENT ACTIVITIES
AI summary This section outlines Demand-Side Management (DSM) activities in Nova Scotia, referencing regulatory frameworks, utility programs, and energy efficiency initiatives. Key entities include Nova Scotia Power, the Nova Scotia Energy Board (NSEB), and the Public Utilities Act (PUA), with acronyms covering DSM, rate design, and distributed energy resources.
5 Schedule A 6 Demand-Side Management Activities 7 8 The figure below identifies the scope of savings (5 year cumulative energy savings, 9 cumulative peak demand savings, cumulative energy savings from Low Income & Equity (includes Afforda...
AI summary Schedule A outlines the scope of demand-side management (DSM) activities over a five-year term, including energy and peak demand savings, low-income and equity programs, demand response capacity, and solar-PV generation.
14 15 Cumulative Net Energy Savings at Generator over the Term (GWh) Cumulative Net Peak Demand Savings at Generator over the Term (MW) Cumulative Energy Savings – Low Income & Equity (GWh) Available Demand Response Capacity (MW) Cumulativ...
AI summary The text presents a table with performance targets related to energy savings and generation, including cumulative net energy savings, peak demand savings, low-income and equity energy savings, available demand response capacity, and cumulative net solar-PV generation. However, the table lacks specific numerical data and is incomplete.
25 Schedule B (Page 1 of 2)
AI summary Schedule B (Page 1 of 2) from a Nova Scotia regulatory proceeding document lists acronyms and terms related to energy regulation, utility operations, and demand-side management. Key entities include NS Power, NSEB, and ERBA, with topics covering energy efficiency, rate design, and regulatory frameworks.
37 Schedule B (Page 2 of 2)
AI summary Schedule B (Page 2 of 2) from a Nova Scotia regulatory proceeding lists acronyms related to energy regulation, utility management, and policy frameworks. It includes terms for demand-side management, rate design, and energy efficiency programs, reflecting the context of utility oversight and regulatory analysis in Nova Scotia.
Permitted Scope of Use 2. The Recipient may use the Confidential Information solely for the purposes of providing or receiving DSM, as the case may be, in accordance with the Legislation and the Purchase Agreement and for no other reason o...
AI summary The recipient is restricted to using confidential information solely for Demand Side Management (DSM) purposes under the Legislation and Purchase Agreement, with no other permitted uses.
4 2. BACKGROUND - 5 On June 16, 2015, EfficiencyOne (E1), Nova Scotia Power Incorporated (NS Power), the Consumer - 6 Advocate, the Small Business Advocate, the Ecology Action Centre, the Affordable Energy Coalition, - 7 and the Industrial...
AI summary The document outlines the history of the Standardized Filing Framework for DSM applications in Nova Scotia. Key milestones include the 2015 Consensus Agreement, NSUARB approval in 2015, adoption in 2016, updates in the 2023–2025 DSM Plan, and the 2026 DSM Extension decision directing continued engagement with DSMAG.
22 3. STANDARDIZED FILING FRAMEWORK
AI summary The document outlines a standardized filing framework within a Nova Scotia regulatory proceeding, focusing on energy and utility regulations. It includes acronyms related to demand-side management, energy efficiency, and utility rate structures, indicating a structured approach to regulatory compliance and reporting.
26 Table 1: Glossary of Terms Term Definition Available demand response The capacity available to NS Power to reduce system peak demand via demand capacity response events. Cumulative net demand Sum of incremental net demand savings across...
AI summary The glossary defines key terms related to demand-side management (DSM) and energy efficiency, including cumulative net demand and energy savings, DSM forecasts, and resource plans. These definitions help clarify the scope and performance metrics of DSM programs.
3 Table 3: Program Description Template Item Description 1. Overview Intent, target market, and type of service or rebate. 2. Objectives Long-term objectives for the program. 3. Opportunity Summary of market potential for the program, incl...
AI summary This section outlines a program description template for regulatory proceedings, including program objectives, design, performance indicators, and alternatives. It is part of a demand-side management standards section.
4.1 Objectives - Ensure consistency in the overall Demand Side Management (DSM) planning, evaluation, 4 reporting in Nova Scotia; - Consolidate Board decisions and directives as they pertain to DSM; and - Ensure that DSM Resource Plans bal...
AI summary The objectives focus on ensuring consistency in Demand Side Management (DSM) planning and reporting in Nova Scotia, consolidating Board decisions related to DSM, and balancing DSM Resource Plans to meet multiple objectives.
4.2 DSM Resource Plan Research
AI summary Section 4.2 discusses research related to Demand Side Management (DSM) resource planning in Nova Scotia, involving regulatory bodies, programs, and analyses of energy efficiency, demand response, and cost recovery mechanisms.
4.2.1 DSM Baseline Study - E1 will work with the NSIESO on IRP activities, [6](#page-418-1) which may include commissioning a DSM baseline - study in advance of each DSM Potential Study to identify current stocks of electricity consuming -...
AI summary E1 is collaborating with NSIESO on IRP activities, including commissioning a DSM baseline study prior to each DSM Potential Study to identify current electricity-consuming devices across all market sectors.
4.2.2 DSM Potential Study - E1 will work with the NSIESO on IRP activities, 6 including the commission of a DSM Potential study - in advance of each IRP exercise. The DSM Potential study identifies DSM resources that are - achievable over...
AI summary E1 will collaborate with NSIESO on IRP activities, including commissioning a DSM Potential study before each IRP exercise. The study identifies achievable DSM resources over the planning horizon and informs Candidate Resource Plans for the IRP.
4.2.3 Integrated Resource Plan - Integrated resource planning establishes directional information for DSM planning. The Preferred - Resource Plan identified in the IRP will inform the development of a preferred DSM Resource Plan - by E1, i...
AI summary The Integrated Resource Plan (IRP) provides directional guidance for Demand Side Management (DSM) planning. The Preferred Resource Plan in the IRP will inform E1's development of a preferred DSM Resource Plan, including analysis of alternate DSM scenarios as per the Framework.
4.2.4 Avoided Costs - NSIESO will work with the DSM franchise holder to develop avoided cost calculations for demand- - side management resources[.6](#page-412-1)
AI summary NSIESO will collaborate with the DSM franchise holder to develop avoided cost calculations for demand-side management resources. The process involves evaluating the financial benefits of DSM initiatives to inform regulatory decisions.
4.3 DSM Resource Plan Development
AI summary This section discusses the development of a Demand Side Management (DSM) Resource Plan, focusing on strategies to manage energy demand, improve efficiency, and integrate programs like demand response and energy efficiency initiatives.
4.3.1 Balanced Plan Approach - E1 will produce DSM Resource Plans that balance multiple aspects of DSM for the benefit of - customers, including: - Short-term and long-term energy and capacity avoidance; - Program delivery costs; - Avoided...
AI summary E1 will develop DSM Resource Plans balancing energy and capacity avoidance, program costs, avoided investments, non-electric benefits, program diversity, business relationships, market access, and rate impacts to ensure equitable customer benefits.
4.3.3 Performance Metrics - The following performance metric definitions and performance requirements were established - under the 2016–2018 DSM Plan. [1](#page-408-4) - 4.3.3.1 Definitions - The following definitions are used: - Performan...
AI summary The section defines performance metrics, indicators, targets, and thresholds under the 2016–2018 DSM Plan, emphasizing their roles in tracking progress and ensuring compliance with Board-approved goals.
Performance Targets - Performance targets apply over the Plan period as reflected in the Board-approved DSM Purchase - Agreement or as ordered by the Board. - E1 is in substantial compliance if it achieves 90 percent or greater on each app...
AI summary E1 must achieve 90% or more of approved performance targets under the Board-approved DSM Purchase Agreement. Failure below 90% may trigger Board action. E1 will propose specific DSM resource targets, including energy savings, peak demand reductions, low-income equity measures, and demand response capacity, for Board approval.
Performance Indicators - E1 will propose DSM resource specific performance indicators within each DSM Resource Plan - application for consideration and approval by the Board. Performance indicators may include - annual incremental and cumu...
AI summary E1 will propose DSM-specific performance indicators for approval by the Board, including energy savings, peak demand reductions, low-income impacts, demand response capacity, ratepayer benefits, spending, and PAC test results, with the Board retaining authority to order additional metrics.
4.3.4 DSM Programs - E1 will propose DSM programs for Residential and the Business, Non-profit and Institutional (BNI) - sectors which may include Residential Efficient Product Rebates, Existing Residential, New - Residential, BNI Efficien...
AI summary E1 will propose Demand Side Management (DSM) programs targeting Residential and Business, Non-Profit & Institutional (BNI) sectors, including rebates, incentives, and demand response initiatives. The proposal outlines various program types such as residential and BNI efficient product rebates, custom incentives, and direct installation.
4.8.2 Quarterly Reports - E1 will file quarterly reports with the Board for quarters one through three of each year. Reporting - requirements were established under the 2013–2015 DSM Plan Settlement Agreement and - continue to evolve: [9](...
AI summary E1 is required to submit quarterly reports to the Nova Scotia Utility and Review Board, detailing program performance, variances, forecasts, and equity outcomes under the 2013–2015 DSM Plan Settlement Agreement. Reports must include mid-course adjustments, variance explanations, year-end forecasts, rate-class expenditures, and Enabling Strategies updates.
4 4.8.5 Rate and Bill Impact Analysis - 5 Each DSM Resource Plan application will include: - 6 a historical RBIA summarizing the long-term impact to rates and bills of all DSM activities up to and including those of the previous calendar y...
AI summary Each DSM Resource Plan application must include a historical RBIA and a forward-looking RBIA. NS Power is required to provide a rate-impact analysis for the proposed DSM Plan and alternate scenarios.
13 4.9 Demand Side Management Advisory Group - 14 The DSM Advisory Group is a forum intended to facilitate the timely sharing of information, - 15 exchanging of ideas, and meaningful discussion amount members on current or emerging DSM - 1...
AI summary The Demand Side Management Advisory Group (DSMAG) serves as a forum for members to share information, exchange ideas, and discuss current or emerging demand-side management (DSM) issues in a collaborative manner.
18 5. CONSOLIDATED ENDNOTES AND SOURCES - 1. M06733 E1 2016–2018 DSM Resource Plan, NSUARB Order, October 7, 2015. The Order approved the 2016–2018 DSM Plan and the Consensus Agreement. (Parties agreed to establish the Standardized Filing...
AI summary The document lists consolidated endnotes and sources from Nova Scotia regulatory proceedings, including approvals of DSM plans, directives on cost recovery, and the adoption of the PAC test. Key references include NSUARB decisions, the 2024 Energy Reform Act establishing NSIESO, and requirements for enhanced reporting and rate class analysis. Regulatory frameworks, cost-effectiveness criteria, and compliance with the Public Utilities Act are emphasized.
E-32025 DSM Evaluation Reports
677 passages
2025 DSM PROGRAMS EVALUATION REPORTS Final DSM Reports March 24, 2026 In Collaboration with:
AI summary Final evaluation reports for 2025 Demand Side Management (DSM) programs, submitted on March 24, 2026. The document outlines collaboration efforts but lacks detailed content in the provided text.
2025 DSM PROGRAMS EVALUATION Final Report
AI summary The document presents a final report evaluating the 2025 Demand Side Management (DSM) programs in Nova Scotia, assessing their effectiveness, outcomes, and alignment with regulatory goals. It likely includes analysis of program performance, cost-benefit assessments, and recommendations for future improvements.
DEFINITIONS Accuracy Reflects the proximity of measurements to the true value. Adjustment ratio The ratio of evaluated results to tracked results. This ratio expresses the adjustment made to tracked savings or other tracked values such as...
AI summary The text provides definitions related to energy efficiency and demand response programs, including terms such as adjustment ratio, available demand response capacity, and baseline. These definitions are critical for understanding how energy savings and program effectiveness are measured.
EfficiencyOne (E1), an independent, non-profit organization, is responsible for helping Nova Scotians improve the energy efficiency of their homes and workplaces by designing, marketing, and delivering demand-side management (DSM) for Nova...
AI summary EfficiencyOne (E1), a non-profit organization, delivers demand-side management (DSM) programs through the Efficiency Nova Scotia (ENS) franchise. E1's 2025 DSM program portfolio achieved significant energy and demand savings, including 129.444 GWh in net electrical energy savings and 60,748 tonnes of CO2 eq in avoided emissions. Econoler, along with other evaluators, conducted the evaluation of these programs.
1 Evaluation Scopes and Objectives The 2025 Portfolio Evaluation Plan was based on the Evaluation Schedule outlined in the Overall Strategic Evaluation Plan[4](#page-10-1) that provides the framework and approach to guide evaluation planni...
AI summary The 2025 Portfolio Evaluation Plan is based on the Overall Strategic Evaluation Plan and outlines factors for prioritizing evaluation activities, including program savings, uncertainty, changes in program design, regulatory requirements, and evaluation scheduling. The plan includes three evaluation categories: impact, process, and market evaluations.
Table 1: 2025 Portfolio Evaluation Plan PY2025 Program Components Impact Process Market Residential DSM Program Components Appliance Retirement Condensed Instant Savings Condensed Affordable Multifamily Housing Condensed Affordable Single-...
AI summary Table 1 outlines the 2025 Portfolio Evaluation Plan, detailing the evaluation approach for various program components under residential and BNI DSM programs. Most programs are evaluated using a condensed approach, while some, like Residential Behaviour and Strategic Energy Management, require comprehensive evaluations. The table also notes that certain programs have ended or are subject to specific evaluation conditions.
1.1 Impact Evaluation Objectives and Scope The impact evaluation activities were aimed at determining: - › Gross electrical energy and peak demand savings at the meter and at the generator - › Available DR capacity for DR programs - › Net-...
AI summary The impact evaluation objectives include assessing energy savings, demand response capacity, net-to-gross ratios, effective useful life, and GHG emissions. Two evaluation types (comprehensive and condensed) are outlined, with factors like program maturity and complexity influencing their application.
Demand-side Management Measure Assessment Document The impact evaluation scope for 2025 also included an update of the Demand-side Management Measure Assessment (DSM MA) document. The DSM MA was updated to include new products added to pro...
AI summary The 2025 update to the DSM MA document focused on aligning with updated program offerings, removing outdated products (e.g., lighting from Instant Savings), revising algorithms for residential and commercial measures, and correcting technical inconsistencies. Annual adjustment ratios were also updated. Key changes included additions like smart thermostat load control and removals such as specific LED fixtures and heat pump water heaters.
Table 2: 2025 Participant and Non-participant Surveys Program Component Number of Respondents BNI Business Energy Rebates – Application Rebates 57 Demand Response Residential Demand Response 103 Total 160 › In-depth interviews with program...
AI summary Table 2 presents survey data from 2025 participant and non-participant surveys, including 160 respondents across BNI programs such as Business Energy Rebates and Residential Demand Response. In-depth interviews were conducted with 70 market actors and stakeholders between May 2025 and January 2026 to evaluate program impacts, including free-ridership and spillover effects.
Table 3: 2025 Interviews Completed Program Component 1 Program Manager/ E1 Staff/Business Development Manager Service Providers/ Distributors/Retailers/Builders Participants Program Manager in Other Jurisdictions Residential Appliance Reti...
AI summary Table 3 outlines the number of interviews conducted in 2025 for various program components, including Residential, Business Energy Rebates, and Demand Response. The data indicates the involvement of program managers, service providers, participants, and managers from other jurisdictions.
Site Visits and Project Reviews with Follow-up Site Visits or Interviews The Evaluator performed a total of 133 project reviews during the summer and fall of 2025, 49 of which were complemented through site visits and 24 were complemented...
AI summary The Evaluator conducted 133 project reviews in 2025, including site visits and phone interviews, to assess various energy efficiency programs. These reviews included validation of EFLHs for Affordable Multifamily Housing and technical reviews for Business Energy Rebates and other programs, with follow-ups to gather data on free-ridership and participant feedback.
Table 4: 2025 Site Visits and Project Reviews with Follow-up Site Visits or Interviews Program Component Project Reviews Followed by Site Visits Project Reviews Followed by Phone Interviews Project Reviews Without Site Visits or Phone Inte...
AI summary Table 4 outlines the 2025 site visits and project reviews conducted under various programs, including Affordable Multifamily Housing, Business Energy Rebates, Strategic Energy Management, and Demand Response, with specific numbers of reviews followed by site visits, phone interviews, or no follow-up.
2.1.4 Metering or Billing Data Analyses In 2025, a Residential Behaviour billing analysis was performed on the months for which AMI data were available (i.e. January to April 2025)[7](#page-18-3) to calculate net electrical energy savings,...
AI summary In 2025, a Residential Behaviour billing analysis used AMI data (Jan-April 2025) to assess net electrical energy savings via difference-in-difference methods. Metering data analyses for Residential Demand Response updated inservice rates and DR capacities for smart thermostats, EV controls, and batteries during Dec 2024–Feb 2025, focusing on winter DR events.
Table 5: Comparison of 2025 Evaluated and Tracked Electrical Energy Savings at the Generator a Program Component Tracked Results Evaluated Results DSM Program Annual Gross Savings (GWh) Annual Net Savings (GWh) Annual Gross Savings (GWh) N...
AI summary Table 5 compares the evaluated and tracked electrical energy savings from various programs in 2025. It includes data on residential and BNI programs, showing gross and net savings, net-to-gross ratios, lifetime savings, and net realization rates for each component.
Table 6: Comparison of 2025 Evaluated and Tracked Peak Demand Savings at the Generator a Program Component Tracked Results Evaluated Results Difference DSM Program Annual Gross Savings (MW) Annual Net Savings (MW) Available Capacity (MW) A...
AI summary Table 6 compares the evaluated and tracked peak demand savings at the generator for various programs in 2025. It highlights differences in net savings and available capacity across residential, BNI, and demand response programs, with varying net realization rates.
4.1.1 Residential DSM Programs
AI summary The section outlines residential demand-side management (DSM) programs, focusing on initiatives to improve energy efficiency and reduce consumption in residential sectors through various measures and incentives.
Instant Savings - › Instant Savings surpassed its net electrical energy savings target by 18% and fell short of its peak demand savings target by 52%. - › Following the removal of LED lighting products and dehumidifiers from the Instant Sa...
AI summary Instant Savings exceeded its net electrical energy savings target by 18% but missed its peak demand savings target by 52%. Participation dropped 71% after removing LED lighting and dehumidifiers. Controls now account for 61% of rebated products and 68% of energy savings. Discrepancies exist between evaluator and E1 tracked savings, and the program's NTGR was updated to 0.77 in 2025.
Existing Residential In 2025, the net electrical energy savings for Existing Residential reached 35.274 GWh at the generator, while the net peak demand savings amounted to 9.584 MW at the generator. Existing Residential is comprised of Aff...
AI summary In 2025, Existing Residential programs achieved 35.274 GWh net electrical energy savings and 9.584 MW peak demand savings. The programs include Affordable Multifamily Housing, Affordable Single-family Homes, Efficient Product Installation, Green Heat, Home Energy Assessment, Mi'kmaw Home Energy Efficiency Project, and Residential Behaviour.
Residential Behaviour - › Residential Behaviour has been paused since May 2025 due to a cybersecurity incident at NS Power in spring 2025 whereby AMI data were no longer available. The evaluation was, therefore, limited to the four months...
AI summary Residential Behaviour program was paused in May 2025 due to a cybersecurity incident at NS Power, limiting evaluation to January-April 2025. Achieved 5.555 GWh savings, falling short of the planned 29.771 GWh.
4.1.2 Business, Non-profit, and Institutional DSM Programs
AI summary This section outlines demand-side management (DSM) programs targeting business, non-profit, and institutional sectors in Nova Scotia, focusing on initiatives like energy efficiency incentives, rebates, and demand response strategies to reduce energy consumption and costs.
Business Energy Rebates - › In 2025, BER achieved 40.244 GWh in net electrical energy savings and 5.332 MW in net peak demand savings at the generator, thus exceeding by 5% the planned net electrical energy savings of 38.451 GWh and fallin...
AI summary In 2025, Business Energy Rebates (BER) exceeded planned electrical energy savings by 5% but fell 26% short of peak demand savings targets. Participation in Application Rebates dropped 36%, reducing overall savings. Adjustments to ratios for lighting and HVAC measures, along with higher NTGR values, impacted tracking accuracy. Revisions to the tracking sheet slightly increased savings but raised error risks.
Custom Incentives In 2025, Custom Incentives achieved 34.519 GWh in net electrical energy savings and 6.744 MW in net peak demand savings at the generator through its two components, namely Custom and Strategic Energy Management. Custom co...
AI summary In 2025, Custom Incentives achieved 34.519 GWh in net electrical energy savings and 6.744 MW in net peak demand savings through its Custom and Strategic Energy Management components. Custom includes Retrofit, Pay-for-Performance, New Construction, and Building Optimization services.
Custom - › Custom achieved 30.487 GWh in net electrical energy savings and 6.372 MW in net peak demand savings at the generator in 2025, thereby surpassing by 26% the planned electrical energy savings of 24.160 GWh and by 32% the planned p...
AI summary Custom program achieved 30.487 GWh in electrical energy savings and 6.372 MW in peak demand savings in 2025, exceeding targets by 26% and 32% respectively. Participation trends, adjustment ratios (0.993–1.011 for Retrofit), free-ridership levels (8%–38%), and a 8% discrepancy between Evaluator and E1 savings tracking were reported.
Strategic Energy Management - › In 2025, SEM achieved 4.031 GWh in net electrical energy savings and 0.372 MW in net peak demand savings at the generator, thus exceeding the 2.657 GWh target by 52% and the planned 0.289 MW in net peak dema...
AI summary In 2025, Strategic Energy Management (SEM) exceeded energy and peak demand savings targets by 52% and 29%, respectively, with 11 completed projects. However, energy savings per participant declined. Compressed air leak repairs contributed 54% of savings, and E1's measurement guidelines were largely followed despite evaluator adjustments.
4.1.3 Demand Response DSM Programs
AI summary The section discusses Demand Response DSM Programs, focusing on their role in demand-side management, including program design, participant incentives, and evaluation metrics. Key aspects include the integration of demand response with broader energy efficiency initiatives and regulatory oversight.
The Evaluator reviewed the EUL values of all measures offered by E1 and their associated lifetime electrical energy savings. The Evaluator found that the DSM portfolio generated 1,476.864 GWh in lifetime net electrical energy savings. [17]...
AI summary The Evaluator analyzed the EUL values of measures in the E1 DSM portfolio, finding that the portfolio generated 1,476.864 GWh in lifetime net electrical energy savings. The weighted average EUL of the measures is 11.4 years, with building envelope measures like insulation contributing significantly to lifetime savings.
Table 8: 2025 Evaluated Net Lifetime Electrical Energy Savings at the Generator DSM Program Program Component Annual Net Electrical Energy Savings (GWh) Lifetime Net Electrical En ergy Savings (GWh) Weighted Average EUL (years) Share of An...
AI summary Table 8 presents the 2025 evaluated net lifetime electrical energy savings at the generator for various DSM programs, including appliance retirement, efficient product rebates, and home energy assessments. The table highlights the contribution of residential and BNI programs to annual and lifetime energy savings, with the residential subtotal contributing 36% of annual and 45% of lifetime savings, and BNI programs contributing 64% of annual and 55% of lifetime savings.
The Evaluator established the reduced GHG emissions due to the DSM portfolio at 60,748 tonnes of CO2 eq in terms of annually avoided net GHG emissions. [Table](#page-36-1) 9 below presents the GHG emission reductions of each program compon...
AI summary The Evaluator determined that the DSM portfolio resulted in 60,748 tonnes of CO2 eq in annual avoided net GHG emissions. Table 9 provides a breakdown of GHG emission reductions by program component and the overall portfolio in 2025.
Table 9: 2025 Evaluated GHG Emission Reductions DSM Program Program Component Gross Annual Avoided GHG Emissions in CO2 eq Tonnes Net Annual Avoided GHG Emissions in CO2 eq Tonnes Residential Efficient Appliance Retirement 96 54 Product Re...
AI summary Table 9 presents evaluated GHG emission reductions from various DSM programs in 2025, showing both gross and net annual avoided emissions in CO2 eq tonnes. The data includes contributions from residential and business programs, with specific values for each component such as appliance retirement, efficient product rebates, and home energy assessments.
5 DSM Portfolio Performance This section presents a comparison of evaluated savings with E1 planned savings at the program and component levels. It also presents satisfaction results, annual savings performance, as well as the historical p...
AI summary This section compares evaluated savings with E1 planned savings at program and component levels, detailing satisfaction results, annual savings performance, and historical contributions of individual program components to overall portfolio savings.
Table 10: 2025 Planned Net Savings and Evaluated Results Planned Savings Evaluated Results Variance Program Component and DSM Program Net Electrical Energy Savings (GWh) Net Peak Demand Savings (MW) Available DR Capacity (MW) Net Electrica...
AI summary Table 10 outlines the 2025 planned net savings and evaluated results for various residential and BNI programs under Demand Side Management (DSM). The data highlights discrepancies between planned and actual savings and capacity, with some programs showing significant variances.
5.3 Historical Portfolio Analysis This subsection presents year-over-year program performance (GWh electrical energy savings) and the contribution of individual program components to portfolio savings (% electrical energy savings). [Table]...
AI summary This subsection provides a year-over-year analysis of program performance in terms of electrical energy savings (GWh) and the contribution of individual program components to overall portfolio savings (% electrical energy savings). Tables 11, 12, and 13 offer a historical overview of program component performance and changes in the DSM portfolio composition.
Table 11: Evaluated Net Electrical Energy Savings at the Generator, 2020-2025 Electrical Energy Savings (GWh) Electrical Energy Savings (%) DSM Program Program Component 2020 2021 2022 2023 2024 2025 2020 2021 2022 2023 2024 2025 Residenti...
AI summary This table presents evaluated net electrical energy savings by program and year from 2020 to 2025, highlighting contributions from residential and BNI (Business, Non-profit, and Institutional) programs. It includes energy savings from initiatives like appliance retirement, efficient product rebates, and home energy assessments, with percentages indicating the share of total savings.
b Residential Behaviour was introduced in 2024. c Custom includes four services: Retrofit, Pay-for-Performance, New Construction, and Building Optimization. d Strategic Energy Management includes Energy Management Information System since...
AI summary The text introduces new developments in residential behavior programs, outlines custom services under the Residential Behaviour initiative, and notes the merger of Strategic Energy Management with Energy Management Information Systems in 2022.
Table 12: Evaluated Net Peak Demand Savings at the Generator, 2020-2025 DSM Peak Demand Savings (MW) Peak Demand Savings (%) Program Program Component 2020 2021 2022 2023 2024 2025 2020 2021 2022 2023 2024 2025 Residential Residential Appl...
AI summary Table 12 evaluates the net peak demand savings from various energy efficiency programs in Nova Scotia from 2020 to 2025, highlighting the contributions of residential, BNI, and overall portfolio programs in reducing peak demand in megawatts and percentages.
c Strategic Energy Management includes Energy Management Information Systems. In 2023, the two program components were merged. b Custom includes four services: Retrofit, Pay-for-Performance, New Construction, and Building Optimization.
AI summary Strategic Energy Management has been expanded to include Energy Management Information Systems, and in 2023, two program components were merged. Custom services include Retrofit, Pay-for-Performance, New Construction, and Building Optimization.
Table 13: Evaluated Net Available DR Capacity, 2023-2025 DSM Program Component (MW) Available DR Capacity Available DR Capacity (%) Program 2023 2024 2025 2023 2024 2025 Demand Response Demand Residential Demand Response 0.058 0.057 0.854...
AI summary Table 13 shows the evaluated net available demand response (DR) capacity for 2023-2025, with BNI Demand Response contributing the majority of capacity. In 2025, E1 achieved 129.444 GWh in net electrical energy savings and 23.556 MW in net peak demand savings, but both metrics decreased compared to 2024.
uction can be achieved for the grid. - › Program documentation has not kept pace with program changes. - The Evaluator noted that Residential DR program changes, dates of program changes. and rationales thereof are not clearly documented i...
AI summary The Residential Demand Response (RDR) program faces documentation gaps, with program changes not clearly recorded. While participant retention is high (90%), integration with EPI (Efficient Product Installation) has led to 40% non-enrollment in RDR among EPI participants. Issues include lack of unique identifiers and incomplete device data collection by installers.
Business Energy Rebates – Instant Rebates To validate 2024 market evaluation results and determine timing for when a baseline for Business Energy Rebates – Instant Rebates LED fixtures should take effect as well as to identify the implicat...
AI summary A market study evaluated the Business Energy Rebates – Instant Rebates program, noting increased LED adoption in commercial lighting markets, declining prices, and shifts in distributor practices. The study also identified implications for baseline adjustments and program adaptations in response to market transformation.
CONCLUSIONS AND RECOMMENDATIONS Overall, 2025 evaluated net electrical energy savings and peak demand savings for the E1 DSM portfolio were 129.444 GWh and 23.556 MW respectively above the values tracked by E1, while available DR capacity...
AI summary The 2025 evaluation of the E1 DSM portfolio shows energy and peak demand savings above tracked values, but DR capacity was below. A cross-cutting recommendation calls for reviewing how savings are distributed between DSM-funded and government-funded programs, especially for whole home renovations, to ensure clear and aligned savings calculation approaches.
Table 14: 2025 Recommendations on Residential Program Components No. Recommendation ASFH/HEA/MHE EP – R1 Review how savings are distributed between DSM-funded and government-funded programs for whole home renovation program components (HEA...
AI summary The recommendation focuses on reviewing how savings are distributed between DSM-funded and government-funded programs for whole home renovation components, ensuring that savings calculation approaches are clearly defined and aligned, particularly for households with both electric and non-electric heating systems.
Components Bibliographic References Southern California Edison, Pool Pump Demand Response Potential, June 2008, p. 19. Northeast Energy Efficiency Partnership (NEEP), Mid-Atlantic Technical Reference Manual Version 10, May 2020, p. 195. Hy...
AI summary The document lists bibliographic references from various studies and reports on energy efficiency, demand response, and load forecasting, including works by Southern California Edison, Hydro-Québec, and Nova Scotia Power. These sources cover topics like heat pump systems, technical reference manuals, and energy use analysis.
Program Components Bibliographic References National Renewable Energy Laboratory, "Chapter 21: Estimating Net Savings – Common Practices", The Uniform Methods Project, October 2017, p. 3, available at: https://www.nrel.gov/docs/fy17osti/68...
AI summary The document includes references to energy efficiency evaluation methods and programs, citing sources such as the National Renewable Energy Laboratory and the Nova Scotia Utility and Review Board. It also references reports from Nova Scotia Power and Emera Inc. related to emissions and annual performance.
Calculation of the Weighted Average of Adjustment Ratios In 2025, the Evaluator used a stratified sample for BNI DR, selecting the 20 largest projects and 10 randomly selected projects among the 138 remaining projects. Therefore, the weigh...
AI summary In 2025, the Evaluator calculated a weighted average adjustment ratio of 0.615 for BNI DR using a stratified sample of 30 projects, combining 20 largest and 10 randomly selected projects from 138. The formula incorporated stratum weights and capacity metrics to reflect project distribution.
Calculation of the Standard Error Since the overall adjustment ratio is based on a stratified weighted average, the Evaluator also calculated a stratified weighted standard error for the adjustment ratio instead of a simple standard error....
AI summary The Evaluator calculated a stratified weighted standard error for the adjustment ratio using a formula from the Uniform Methods Project (UMP) Chapter 11, resulting in a standard error of 160 for evaluated available DR capacity. This approach accounts for stratified sampling in adjustment ratio calculations.
Where: H is the number of strata (2) and h represents each stratum. - $N_h$ is the number of projects in the population for a stratum. - $n_h$ is the number of projects in the sample for a stratum. & lt;sup>2 Khawaja, M.S., Rushton, J. and...
AI summary The text outlines statistical methods for calculating adjustment ratios in demand response (DR) capacity evaluations, using strata-based sampling. It presents formulas for weighted standard error calculations and notes a weighted standard error of 160 for BNI DR projects. The methodology references the Uniform Methods Project by NREL.
Calculation of the Margins of Error The margin of error on the adjustment ratio of BNI DR available DR capacity was established by using the following formula, which compares the error in evaluated available DR capacity divided by the eval...
AI summary The margin of error for BNI DR's adjustment ratio was calculated using a 90% confidence level (t=1.699) and a sample size of 30, resulting in a 7.1% margin. For small programs like SEM, a census approach was used, eliminating the need for margin calculations. The methodology applies to BER-AR, Custom, and BNI DR programs in 2025.
NTGR Calculations Free-ridership algorithm Low Free-i Partici • High Free-ric Participa Medium Free-ri Participa D5. [ASK ONLY IF DLC Premium=YES] Without the Business Energy Rebates Program, what is the ikelihood that you would have purch...
AI summary The text presents a table related to free-ridership algorithms and includes questions about the Business Energy Rebates Program and the likelihood of purchasing DLC Premium LED lighting products without the program. It also references efficiency scores and energy-efficient lighting products.
RESIDENTIAL EFFICIENT PRODUCT REBATES PROGRAM Final Report 2025 DSM EVALUATION March 4, 2026
AI summary Final Report on the 2025 DSM Evaluation for the Residential Efficient Product Rebates Program, dated March 4, 2026. The document assesses the program's effectiveness in promoting energy-efficient product adoption and its alignment with broader demand-side management goals.
ABBREVIATIONS ARCA ARCA Canada Inc. ARet Appliance Retirement ASFH Affordable Single-family Homes BNI Business, non-profit, and institutional DA Delivery agent DR Demand response DSM Demand-side management DSM MA Demand-side Management Mea...
AI summary This document provides a list of abbreviations and their full forms used in the Nova Scotia regulatory proceeding, including terms related to energy efficiency, demand-side management, and utility programs.
[Table](#page-83-0) 2 below presents the participation levels, NTGRs, evaluated gross and net savings at the generator, annual GHG emission reductions, as well as effective useful life (EUL) values for each program component and for Reside...
AI summary The text discusses the 2025 DSM MA, a reference document that provides parameters for calculating energy and peak demand savings from E1's DSM program portfolio. It includes effective useful life values for all measures and refers to these values for the evaluation conducted during the last year of the 2023-2025 DSM cycle.
Instant Savings Findings and Recommendations This subsection presents the key findings from the 2025 Instant Savings evaluation. The Evaluator has no specific recommendation for Instant Savings. 2025 Instant Savings-Finding: Instant Saving...
AI summary The 2025 Instant Savings program exceeded its net electrical energy savings target by 18% but missed peak demand savings by 52%. Participation dropped 71% after removing LED lighting and dehumidifiers. Controls now dominate rebated products (61%), and discrepancies exist between evaluated and tracked savings (NTGR: 0.77 vs. 0.98).
Program Tracked and Evaluated Savings [Table](#page-85-0) 3 below compares E1 tracked electrical energy and peak demand savings to evaluated savings at the generator. The realization rate and NTGR are also presented and correspond to the r...
AI summary The table compares E1 tracked electrical energy and peak demand savings to evaluated savings at the generator, highlighting realization rates and NTGR values, which are calculated as the ratio of net savings to gross savings.
INTRODUCTION EfficiencyOne (E1), an independent and non-profit organization, is responsible for helping Nova Scotians improve the energy efficiency of their homes and workplaces by designing, marketing, and delivering demand-side managemen...
AI summary EfficiencyOne (E1), a non-profit organization, manages demand-side management (DSM) programs in Nova Scotia, funded by Nova Scotia Power (NS Power) ratepayers. E1's 2025 DSM program portfolio includes the Residential Efficient Product Rebates program, which has two components: Appliance Retirement (ARet) and Instant Savings. ARet was discontinued in January 2025, and an evaluation report was commissioned by E1.
Table 4: Types of Evaluation Conducted for Each Program Component, 2025 2025 Program Program Component Process Market Impact Residential Efficient Product Rebates ARet Condensed Instant Savings Condensed For each program, the Evaluator pre...
AI summary Table 4 outlines the types of evaluation conducted for each program component in 2025, including the Residential Efficient Product Rebates and Instant Savings. The Evaluator prepared a DSM evaluation report detailing key findings, energy savings, peak demand savings, and GHG emissions avoided.
1.1 ARet Description Through ARet, E1 promotes the retirement of old, inefficient household appliances such as refrigerators, freezers, room air conditioners, and dehumidifiers. ARet educates Nova Scotians about the cost of maintaining old...
AI summary ARet, managed by E1, retires inefficient household appliances in Nova Scotia, offering rebates and free pick-up services. ARCA Canada Inc. handles collection and recycling. Eligibility requires appliances to be 10+ years old, with specific size and rebate criteria. The program aimed for 1.247 GWh energy savings in 2025 but was discontinued in January 2025.
3.2.2 Peak Demand Savings Peak demand savings correspond to the demand savings that coincide in time with the peak demand period of the electricity system. The projected electricity peak demand period in Nova Scotia is between 5 p.m. and 7...
AI summary Peak demand savings in Nova Scotia occur during 5 p.m.–7 p.m. on non-holiday weekdays from December to February. Unitary peak demand savings remained unchanged in 2025, with detailed calculations provided in the 2025 DSM MA.
3.2.3 Interactive Effects Interactive effects occur when the implementation of an energy efficiency measure has an impact on the energy consumption of other elements such as heating and cooling equipment. For ARet, retiring old appliances...
AI summary Interactive effects from appliance retirement (ARet) influence heating and cooling loads, with older appliances releasing more waste heat. The 2025 DSM MA evaluates these effects, concluding they are negligible (0% factor). This impacts energy consumption calculations for efficiency programs.
5.3 Participation History In 2025, 113,696 eligible products were rebated in participating stores across Nova Scotia, a total that represents a decrease of 71% compared to 2024. As presented in [Table](#page-103-1) 13 below, sales of ENERG...
AI summary In 2025, rebate participation in Nova Scotia saw a significant decrease in sales of ENERGY STAR certified LED products, attributed to changes in the Instant Savings program following the 2024 'Lights Out' campaign. However, sales of control products, such as timers and thermostats, increased substantially, contributing the majority of energy savings.
Table 14: 2025 Instant Savings Evaluation Approach Evaluation Objective Research Question Methodology Calculate gross results › Are the data in the tracking sheet complete, accurate, and consistent? › Are the unitary savings for appliance...
AI summary This section outlines the evaluation approach for the 2025 Instant Savings program, focusing on calculating both gross and net results. It includes methods such as tracking sheet audits, DSM Measure Assessment updates, literature reviews, and GHG emission reduction calculations.
Measure Assessment Update A unitary savings review was conducted for certain measures to update the DSM MA following the change to a LED baseline assumption for residential lighting. This prompted the removal of all rebates on LED lamps an...
AI summary The DSM MA was updated following a LED baseline assumption change, removing LED lamp rebates (except motion-sensor units), adjusting lighting control wattage, and revising EUL values. Savings algorithms for smart thermostats and fans were also updated. Amendment 18 to Canada's Energy Efficiency Regulations was reviewed but found to have no impact on Instant Savings during this evaluation period.
7.2.1 Installation Rates The installation rates of products sold under Instant Savings are assumed to be 100% except for smart power controllers for audiovisual equipment (smart power strips) for which the installation rate is assumed to b...
AI summary Installation rates for products under Instant Savings are assumed to be 100%, except for smart power strips at 86%. The 2025 DSM MA provides further details on these assumptions.
7.2.2 Unitary Energy Savings [Table](#page-108-1) 15 below summarizes the tracked and evaluated electrical energy savings values for the product categories rebated through Instant Savings, which were revised as part of the 2025 DSM MA upda...
AI summary The document discusses revisions to unitary energy savings values for LED products, lighting controls, and smart thermostats as part of the 2025 DSM MA update. Changes are attributed to new baseline assumptions and algorithm updates. The Evaluator also reviewed Amendment 18 to Canada's Energy Efficiency Regulations and found no impact on unitary savings for rebated products.
Table 15: 2025 Instant Savings Tracked and Evaluated Unitary Energy Savings[15](#page-108-4) Product Tracked Savings [kWh/year] Evaluated Savings [kWh/year] Dimmer Switches 8.20 3.42 Indoor Motion Sensors with Dimmer Switches 25.9 10.8 Out...
AI summary Table 15 presents the tracked and evaluated energy savings for various products under the 2025 Instant Savings program. The data shows a significant difference between tracked and evaluated savings, indicating potential discrepancies in the actual energy savings achieved by these products.
Peak demand savings correspond to the demand savings that coincide in time with the peak demand period of the electricity system. The projected electricity peak demand period in Nova Scotia is defined as the coldest days (with an on-peak t...
AI summary The document discusses updates to unitary peak demand savings for energy efficiency measures, particularly LED products and lighting controls, as part of the 2025 DSM MA. These updates were made following discussions with the Evaluator and changes to the LED baseline assumption for residential lighting products. The table summarizes the tracked and evaluated savings for rebated products.
Table 16: 2025 Instant Savings Tracked and Evaluated Unitary Peak Demand Savings Product Tracked Savings [W] Evaluated Savings [W] ENERGY STAR Certified LED Fixtures with Motion Sensors 32.6 2.37 Dimmer Switches 1.33 0.554 Solar Fixtures 1...
AI summary Table 16 presents the tracked and evaluated unitary peak demand savings for various energy-efficient products in 2025. The table includes products like LED fixtures, dimmer switches, and bathroom fans, with significant differences between tracked and evaluated savings. Section 7.2.4 discusses interactive effects related to these savings.
7.2.5 Effective Useful Life The Evaluator validated the EUL values based on the 2025 DSM MA. The EUL values are used in the calculation of electrical energy savings that are expected to persist over time. [Table](#page-109-3) 17 below summ...
AI summary The Evaluator validated updated Effective Useful Life (EUL) values based on the 2025 DSM MA, which are used to calculate electrical energy savings over time. EUL values for LED fixtures with motion sensors and solar fixtures were updated due to a change in the LED baseline assumption, while other measures remained unchanged. The gross and net weighted average EUL for Instant Savings was set at 9.3 years.
Table 18: Evaluated 2025 Instant Savings Gross Electrical Energy and Peak Demand Savings LED Non-A- type Lamps LED ENERGY STAR LED Fixtures 0.44 Product Category R, BR, and Decorative Others Recessed Downlight Fixtures Without Motion Senso...
AI summary Table 18 presents evaluated 2025 instant savings for gross electrical energy and peak demand savings across various product categories, including LED lamps, fixtures, and motion sensors. It includes metrics such as unitary energy savings, installation rates, and lifetime energy savings.
Evaluated 2025 Instant Savings Gross Electrical Energy and Peak Demand Savings (Continued) Product Category Efficient Combined Washers/Dryers Room Air Purifiers Dehumidifiers Pool Pumps Heat Pump Water Heaters High-efficiency Dishwashers B...
AI summary The document evaluates the 2025 Instant Savings Gross Electrical Energy and Peak Demand Savings for various product categories. It includes data on the number of units installed, energy savings, and peak demand savings, along with adjustments for interactive effects. Smart thermostats for electric heat and dimmer switches are noted as having the most significant impact on savings revisions.
Table 23: Evaluated 2025 Instant Savings Net Electrical Energy and Peak Demand Savings LED Non-A-ty /pe Lamps LED EN ERGY STAR Fixture es · Dimensor Indoor Outdoor #Product Category R, BR, and Decorative Others Recessed Downlight Fixtures...
AI summary Table 23 presents evaluated 2025 instant savings for net electrical energy and peak demand savings across various product categories, including LED lamps, fixtures, and motion sensors, with calculations for gross and net savings, NTGR, line loss factors, and effective useful life.
7.4 Realization Rate [Table](#page-122-1) 24 below compares the electrical energy and peak demand savings established through this evaluation to those tracked by E1. It also includes the realization rate, representing the ratio of evaluate...
AI summary This section discusses the realization rate, which is the ratio of evaluated net savings to tracked net savings for electrical energy and peak demand savings. It references a table comparing 2025 Instant Savings tracked by E1 and evaluated savings at the generator.
Gross Savings NTGR Net Savings Realization Rate Value Unit Value Value Unit Value Electrical Energy Savings Tracked Savings by E1 16.337 GWh 0.98 15.981 GWh 72% Evaluation Results 14.817 GWh 0.77 11.430 GWh Tracked Savings by E1 0.757 MW 0...
AI summary The table presents energy savings data, including gross and net savings, NTGRs, and realization rates for electrical energy savings tracked by E1 and evaluation results. NTGRs are calculated as the ratio of net savings to gross savings and vary by product category.
APPENDIX IV Instant Savings Net-to-Gross Ratio Literature Review
AI summary This literature review examines the Instant Savings Net-to-Gross Ratio (NTGR), a metric used to evaluate the effectiveness of energy efficiency programs. It focuses on how NTGR quantifies the relationship between immediate cost savings and total program costs, influencing decisions on demand-side management (DSM) and incentive structures.
EfficiencyOne
AI summary The document introduces EfficiencyOne (E1) within the context of Nova Scotia's regulatory proceedings, focusing on energy efficiency programs and related acronyms. It highlights topics such as demand-side management, appliance retirement, and heat pump initiatives, while referencing Efficiency Nova Scotia and Nova Scotia Power.
EXISTING RESIDENTIAL PROGRAM Final Report 2025 DSM EVALUATION March 13, 2026
AI summary The document presents the Final Report of the 2025 Demand-side Management (DSM) Evaluation for the Existing Residential Program, dated March 13, 2026. It assesses the program's performance and outcomes as part of Nova Scotia's energy efficiency initiatives.
EXECUTIVE SUMMARY This report presents the 2025 demand-side management (DSM) results of the Existing Residential program administered by EfficiencyOne (E1). This program is comprised of seven components: (1) Affordable Multifamily Housing...
AI summary This report details the 2025 demand-side management (DSM) outcomes for EfficiencyOne's Existing Residential program, which includes components like Affordable Multifamily Housing, Efficient Product Installation, and Home Energy Assessments. The program promotes energy efficiency through financial incentives and direct installations in residential and affordable housing sectors.
Table 2: Overall 2025 Existing Residential Participation and Evaluated Savings Participation Level Gross Savings NTGR Net Savings Value Unit Value Unit Value Value Unit AMH Electrical Energy Savings 98 Projects 1.378 GWh 1.00 1.378 GWh Lif...
AI summary Table 2 presents the 2025 residential participation and evaluated savings across various programs, including energy savings, GHG emission reductions, and net-to-gross ratios (NTGR). The data highlights participation levels, gross and net savings, and the effective useful life (EUL) of different initiatives such as AMH, ASFH, EPI, Green Heat, HEA, MHEEP, and Residential Behaviour.
AMH Findings and Recommendations This subsection presents the key findings from the 2025 AMH evaluation. The Evaluator has no specific recommendation for AMH. 2025 AMH-Finding: In 2025, AMH achieved 1.378 GWh in net electrical energy savin...
AI summary The 2025 AMH evaluation found that the program achieved 1.378 GWh in net electrical energy savings (27% below target) and 0.648 MW in peak demand savings (13% above target). Participation increased by 18% to 98 projects, with 19% higher energy savings and 14% higher peak demand savings compared to 2024. EFLH values were correctly applied to prescriptive heat pump projects, and savings aligned with E1 tracking.
ASFH Findings and Recommendations This subsection presents the key findings from the 2025 ASFH evaluation. The Evaluator has no specific recommendation for ASFH. 2025 ASFH-Finding: ASFH achieved 6.135 GWh in net electrical energy savings a...
AI summary The 2025 ASFH program exceeded its energy and peak demand savings targets by 114% and 183%, respectively, with 1,920 homes participating—a 59% increase from 2024. Energy savings were 1% higher than E1-tracked figures due to inclusion of 2024 unclaimed savings from non-modelled heat pump measures.
Residential Behaviour Findings and Recommendations This subsection presents the key findings from the 2025 Residential Behaviour evaluation. The Evaluator has no specific recommendation for Residential Behaviour. 2025 Residential Behaviour...
AI summary The 2025 Residential Behaviour evaluation found the program paused since May 2025 due to a NS Power cybersecurity incident, limiting data to January–April 2025. Achieved 5.555 GWh savings (vs. target 29.771 GWh). No specific recommendations were made.
Table 3: Comparison of 2025 Tracked and Evaluated Savings at the Generator Gross Savings NTGR Net Savings Realization Rate Value Unit Value Unit Electrical Energy Savings Tracked Savings by E1 1.378 GWh 1.00 1.378 GWh 100% Evaluation Resul...
AI summary Table 3 compares tracked and evaluated savings for various energy efficiency programs in Nova Scotia in 2025, including electrical energy and peak demand savings. The table includes data for programs such as Affordable Multifamily Housing, Affordable Single-family Homes, Efficient Product Installation, Green Heat, and others, with metrics like Net-to-Gross Ratios and Realization Rates.
EfficiencyOne (E1), an independent and non-profit organization, is responsible for helping Nova Scotians improve the energy efficiency of their homes and workplaces by designing, marketing, and delivering demand-side management (DSM) for N...
AI summary EfficiencyOne (E1) is an independent, non-profit organization responsible for designing, marketing, and delivering demand-side management (DSM) programs in Nova Scotia through the Efficiency Nova Scotia (ENS) franchise. E1's 2025 DSM program portfolio includes residential and BNI programs, and it commissioned Econoler to evaluate these programs. The evaluation report focuses on the Existing Residential program and outlines comprehensive and condensed impact evaluation methods.
Table 4: Types of Evaluations Conducted for Each Program Component, 2025 2025 Program Program Component Process Market Impact Existing Residential AMH Condensed ASFH Condensed EPI Condensed Green Heat Condensed HEA Condensed MHEEP Condense...
AI summary Table 4 outlines the types of evaluations conducted for each program component in 2025, including program components like AMH, ASFH, EPI, Green Heat, HEA, and MHEEP, with a focus on impact assessments. The Residential Behaviour component received a comprehensive evaluation involving cumulative billing analysis using AMI data.
1.1 AMH Description AMH provides affordable housing owners and non-profit organizations, such as rehabilitation or transition houses, with incentives for building-wide energy retrofit projects with the intent of reducing electrical and non...
AI summary AMH provides incentives for energy retrofits in affordable multifamily housing and non-profits, requiring energy audits unless prescriptive measures are used. Funding comes from electricity ratepayers and the Province of Nova Scotia, with updated incentive amounts and energy savings targets for 2025. Two project paths (comprehensive and prescriptive) are outlined, with savings calculated via modeling tools or the 2025 DSM MA.
EUL Update Using the effective useful life (EUL) values for common measures presented in the 2025 Demand-side Management Measure Assessmen[t](#page-166-2) 2 (DSM MA) and the proportions of savings generated by individual measures implement...
AI summary The Evaluator calculated an average Effective Useful Life (EUL) for comprehensive projects using EUL values from the 2025 DSM MA and savings proportions from AMH projects. The 2025 DSM MA serves as a reference for calculating energy savings and EUL values for E1's DSM program measures.
3.2.1 Electrical Energy Savings For AMH, the Evaluator typically multiplies tracked savings by adjustment ratios to establish evaluated savings. In 2025, no previously established adjustment ratios were applied to electrical energy savings...
AI summary The Evaluator discusses electrical energy savings evaluation methods for AMH, noting that 2025 adjustments omitted ratios due to high error margins. A 2024 EFLH value update for mini-split heat pumps was validated via desk reviews, allowing tracked savings to be used for 2025 evaluations. Other projects also relied on tracked savings due to unacceptably high error margins in prior adjustment ratios.
3.2.2 Peak Demand Savings Peak demand savings correspond to the demand savings that coincide in time with the peak demand period of the electricity system. The projected electricity peak demand period in Nova Scotia is defined as the colde...
AI summary Peak demand savings in Nova Scotia are calculated during cold peak periods (Dec-Feb, 5-7 PM) using a 0.283 W/kWh ratio from the 2025 DSM MA for comprehensive projects and equations for prescriptive ones. The 2025 AMH evaluation used tracked savings directly without adjustment ratios.
3.2.3 Interactive Effects In a home, interactive effects occur when the implementation of energy efficiency measures has an impact on the energy consumption of other factors such as heating and cooling. The interactive effects of space hea...
AI summary Interactive effects in energy efficiency measures impact heating and cooling in homes. Comprehensive projects already account for these effects via engineering calculations or simulations, while the 2025 DSM MA includes them for prescriptive projects when applicable.
3.4 Realization Rate [Table](#page-172-1) 10 below compares the electrical energy and peak demand savings established through the 2025 evaluation to those calculated in the 2025 tracking sheet. It also includes the realization rate, repres...
AI summary This section discusses the realization rate, comparing evaluated net savings from the 2025 evaluation to tracked net savings in the 2025 tracking sheet, focusing on electrical energy and peak demand savings.
4 AMH Key Findings and Recommendations As mentioned previously, the main objectives of the 2025 AMH evaluation were as follows: › Calculate AMH gross and net results, namely first-year and lifetime electrical energy savings, peak demand sa...
AI summary The 2025 AMH evaluation found that while net electrical energy savings targets were unmet (1.378 GWh vs. 1.880 GWh target), peak demand savings exceeded expectations (0.648 MW vs. 0.572 MW target). Participation reached a record high with 98 projects, and EFLH values were correctly applied to heat pump projects. Savings tracked by E1 aligned with evaluator calculations.
Table 11: Implementation Status of Past Recommendations for ASFH # Past Recommendations Status Comments 2024-ASFH-R7 Update the DA/contractor training guides on the record keeping/reporting processes and use of the software tools to reflec...
AI summary The document discusses the implementation status of past recommendations for Affordable Single-family Homes (ASFH), specifically the update of DA/contractor training guides. E1 has completed the recommendation by updating training guides and providing regular training sessions, including monthly meetings and ad-hoc training related to software tools.
7.2 Gross Savings For ASFH, the gross savings associated with building envelope and heat pump measures are calculated based on pre-retrofit and post-retrofit HOT2000 simulations, while the gross savings associated with smart thermostats ar...
AI summary The section outlines methodology for calculating gross savings for Affordable Single-family Homes (ASFH), including simulation approaches for building envelope and heat pump measures, unitary values for smart thermostats, and retroactive adjustments to non-modelled heat pump calculations post-2024 DSM evaluation. The Evaluator applied updated methods retroactively from April 2024, affecting reported savings.
Non-modelled Energy Savings Smart thermostats are not modelled in HOT2000. Instead, electrical energy savings are calculated based on unitary energy savings values from the 2025 Demand-side Management Measure Assessment (DSM MA),[10](#page...
AI summary Non-modelled energy savings for smart thermostats and heat pumps are calculated using the 2025 DSM MA and 2024 Green Heat analysis. Savings are allocated between electrical and non-electrical sources based on electric space heating percentages in ASFH programs, with no modifications to unitary savings values in the 2025 DSM MA.
7.2.2 Peak Demand Savings Peak demand savings correspond to the demand savings that coincide in time with the peak demand period of the electricity system. The projected electricity peak demand period in Nova Scotia is between 5 p.m. and 7...
AI summary Peak demand savings in Nova Scotia are calculated using a 0.283 MW/GWh ratio from Navigant's 2016-2018 DSM Plan for ASFH, with exceptions for heat pumps. The 2025 DSM MA provides unitary peak demand savings values, which were not revised in 2025. Smart thermostats use separate calculations, and the Evaluator validated Navigant's method.
7.2.3 Interactive Effects In a home, interactive effects occur when the implementation of energy efficiency measures has an impact on the energy consumption of other factors such as heating and cooling. Since ASFH building envelope and hea...
AI summary The text explains that interactive effects occur when energy efficiency measures impact other home energy factors. ASFH and heat pump measures directly target heating/cooling loads, so no additional factors are applied. Smart thermostats aren't modeled in HOT2000 and don't affect other elements, so no interactive effects for them.
7.2.4 Effective Useful Life As part of the 2025 DSM MA activities, the Evaluator reviewed the EUL values used in the calculation of electrical energy savings that are expected to persist over time. The EUL values for building envelope upgr...
AI summary The Evaluator reviewed Effective Useful Life (EUL) values for building envelope upgrades and space heating equipment in 2025 DSM MA activities. These values, based on installations by HEA and ASFH participants, remained unchanged for all ASFH measures in 2025.
7.3.1 Evaluated Net Savings Net savings are defined as the changes in energy use that are specifically attributable to ASFH. Since spillover and free-ridership effects were considered nil, the net electrical energy savings are equal to the...
AI summary Evaluated Net Savings for Affordable Single-family Homes (ASFH) show 114% and 183% exceedance of electrical energy and peak demand targets. Net savings equal gross savings due to nil spillover and free-ridership. GHG emission reductions match gross reductions. Data sources include Nova Scotia Power and Emera Inc.
7.4 Realization Rate [Table](#page-186-1) 18 below compares the electrical energy and peak demand savings established through this evaluation to those calculated in the 2025 tracking sheet. It also includes the realization rate, representi...
AI summary The text introduces a realization rate, which is the ratio of evaluated net savings to tracked net savings, comparing electrical energy and peak demand savings from the current evaluation to those in the 2025 tracking sheet.
8 ASFH Key Findings and Recommendations As previously mentioned, the main objectives of the 2025 ASFH evaluation were as follows: › Calculate gross and net ASFH results, namely electrical first-year and lifetime energy savings, peak demand...
AI summary The 2025 ASFH program exceeded electrical energy and peak demand savings targets by 114% and 183%, respectively. Participation grew by 59% compared to 2024, with 1,920 homes enrolled. Evaluator results aligned closely with E1's tracking, differing by only 1% due to unclaimed 2024 savings from non-modelled heat pumps.
9.1 EPI Description EPI provides participants with free-of-charge direct installations of energy efficient products. EPI has played a pivotal role in transforming the residential lighting market by making energy efficient products more aff...
AI summary EPI provides free direct installations of energy-efficient products, focusing on electrician-installed measures to support residential demand response. The program has shifted its focus from lighting to other energy-efficient products since June 2025. E1 contracts service providers to deliver EPI across the province, and the program is available to both homeowners and renters.
Table 20: Implementation Status of Past Recommendations for EPI # Past Recommendations for EPI Status Comments 2024- EPI-R1 Recommendation #1: To improve the smart thermostat installation rate, explore and implement strategies to reduce th...
AI summary This table outlines the implementation status of past recommendations for the Efficient Product Installation (EPI) program. Recommendation #1 focused on improving smart thermostat installation rates by reducing participant dissatisfaction and disconnections through follow-up calls, installer education, and additional educational materials. E1 implemented several measures, including automated emails, refresher training, mandatory installations, and communication protocols. The Evaluator acknowledges the improvements made.
9.3 Participation History As presented in [Figure](#page-190-1) 9 below, EPI had 9,245 DSM participants, which represents a 7.5% decrease in participation compared to 2024 levels.[14](#page-190-2) In 2025, 90,666 efficient products were in...
AI summary EPI's DSM participation dropped 7.5% in 2025, with efficient product installations declining 40% due to LED phase-out. Despite lower product volumes, average savings fell only 12% due to higher efficiency from electrician-installed products. Smart thermostats now drive 51% of energy savings despite comprising only 11% of installations.
Calculations Using Evaluation Results Building on all the above methods and collected data, the Evaluator calculated first-year and lifetime electrical energy and peak demand savings per the calculation methodology presented in Subsection...
AI summary The Evaluator calculated first-year and lifetime electrical energy and peak demand savings using collected data and methodologies outlined in Subsection 11.2, focusing on energy efficiency and demand-side management outcomes.
11.2 Gross Savings For EPI, gross savings correspond to the change in energy consumption resulting from installing energy efficient products in participant homes compared to the consumption level had those installations not occurred. [16](...
AI summary Gross savings for EPI are calculated as the energy consumption reduction from installing efficient products in homes, compared to baseline consumption. The Evaluator used the 2025 DSM MA and applied a 2019 adjustment ratio to correct discrepancies in lamp replacement tracking.
11.2.2 Unitary Energy Savings For EPI, E1 establishes separate unitary savings values for single-family homes and apartments. For the 2025 evaluation, the Evaluator used the unitary savings values from the 2025 DSM MA. That document provid...
AI summary EfficiencyOne (E1) establishes separate unitary energy savings values for single-family homes and apartments using the 2025 DSM MA document, which details inputs, references, and calculations for EPI's product types.
11.2.3 Unitary Peak Demand Savings Peak demand savings correspond to the demand savings that coincide in time with the peak demand period of the electricity system. The projected electricity demand peak period in Nova Scotia is between 5 p...
AI summary Unitary peak demand savings refer to demand reductions during Nova Scotia's peak electricity period (5-7 PM, Dec-Feb). The Evaluator uses the 2025 DSM MA, which provides parameters for calculating energy and peak demand savings for E1's DSM programs, including effective useful life values for measures.
11.2.4 Interactive Effects In a home, interactive effects occur when the implementation of energy efficiency products has an impact on the energy consumption of other elements such as heating and cooling. In the case of EPI, replacing ligh...
AI summary Interactive effects occur when energy efficiency products, like LED lighting and hot water insulation, alter heating and cooling demands in homes. The 2025 evaluation used factors from the DSM MA to calculate energy savings, considering product type, location, and home type.
11.2.6 Effective Useful Life The EUL values used in the calculation of electrical energy savings that are expected to persist over time are presented in the 2025 DSM MA. The equivalent EUL values are applied to each product gross and net f...
AI summary The Effective Useful Life (EUL) values in the 2025 DSM MA are used to calculate long-term electrical energy savings. Equivalent EUL values are applied to gross and net first-year savings, resulting in differing weighted average EUL values for gross and net lifetime savings. Subsections 11.2.7 and 11.3.4 provide further details.
Table 22: Evaluated 2025 EPI Gross Electrical Energy and Peak Demand Savings per Measure - Single-family Homes LED Lamps Product Category 9 W Replacing 29 W 40 W 43 W 60 W 72 W 100 W 150 W Number of Units Number of Units 238 244 7,833 498...
AI summary Table 22 evaluates the 2025 EPI gross electrical energy and peak demand savings per measure for single-family homes, focusing on LED lamps replacing various wattage bulbs. The table provides data on installation rates, energy savings, and adjustment ratios across different wattage categories.
Evaluated 2025 EPI Gross Electrical Energy and Peak Demand Savings per Measure - Single-family Homes (Continued) Consumer Electronics and Accessory Lighting Product Category Solar Security Fixtures Indoor Motion Sensors Outdoor Motion Sens...
AI summary The document evaluates the 2025 EPI Gross Electrical Energy and Peak Demand Savings per Measure for single-family homes, providing data on various product categories including solar security fixtures, motion sensors, and dimmer switches, with details on installation rates, energy savings, and peak demand reductions.
LED Lamps Product Category 18 W Replacing 100 W PAR20 7 W Replacing 50 W PAR38 15 W Replacing 90 W PAR38 15 W Replacing 120 W PAR38 15 W Replacing 150 W Number of Units Number of Units 55 39 - - - Installation Rate (%) 94% 94% 94% 94% 94%...
AI summary The table provides details on LED lamp installations, including the number of units, installation rates, energy savings, and peak demand savings for various product categories. It includes factors such as interactive effects, line loss, and adjustment ratios, which are used to calculate gross energy savings at the meter and generator.
Table 24: Evaluated 2025 EPI Gross Electrical Energy and Peak Demand Savings Total for Single family Homes Total for Apartments Grand Total Number of Units Number of Units 87,456 3,210 90,666 Installation Rate (%) 91% 92% 91% Number of Uni...
AI summary Table 24 evaluates the 2025 EPI (Efficient Product Installation) program's gross electrical energy and peak demand savings, showing data for single-family homes and apartments. It includes metrics like installation rates, energy savings, and line loss factors, with calculations based on weighted averages for different product types and rate codes.
GHG Emission Reduction Calculations To calculate net avoided GHG emissions (in CO₂ equivalent) for Green Heat, the Evaluator multiplied net energy savings by the most recent Nova Scotia-specific GHG emission factor for electricity generati...
AI summary The document outlines methods for calculating net avoided GHG emissions for Green Heat by multiplying energy savings with Nova Scotia-specific emission factors from NS Power. It references the 2025 DSM MA as a key resource for evaluating energy savings and useful life values of DSM measures.
15.2 Gross Savings For Green Heat, gross savings correspond to the change in energy consumption resulting from actions taken by participants compared to the consumption level had those actions not occurred. [22](#page-30-0) For the 2025 ev...
AI summary The text defines gross savings for Green Heat as the change in energy consumption due to participant actions, referencing the 2025 DSM MA for evaluation. It emphasizes measuring consumption differences between scenarios with and without program participation.
15.2.2 Unitary Energy Savings To establish Green Heat unitary savings, the Evaluator relied on a combination of billing analyses, energy models, engineering algorithms, and literature reviews. The 2025 DSM MA provides a detailed descriptio...
AI summary The Evaluator used billing analyses, energy models, and literature reviews to establish Green Heat unitary savings. The 2025 DSM MA provides detailed inputs and calculations for measure categories, with no updates to unitary energy savings values.
15.2.3 Unitary Peak Demand Savings Peak demand savings correspond to the demand savings that coincide in time with the peak demand period of the electricity system. The projected electricity peak demand period in Nova Scotia is defined as...
AI summary Peak demand savings in Nova Scotia are defined as savings occurring during the coldest days (−15 °C) between 5 p.m. and 7 p.m. from December to February on non-holiday weekdays. No updates were made to unitary peak demand savings values in the 2025 DSM MA, referencing NREL's Uniform Methods Project for definitions.
15.3 Effective Useful Life As part of the 2025 DSM MA activities, the Evaluator reviewed the EUL values used in the calculations of electrical energy savings that are expected to persist over time. All EUL values used in previous years rem...
AI summary The 2025 DSM MA review confirmed that EUL values from prior years remained unchanged. Equivalent EUL values were applied to gross and net first-year electrical energy savings to calculate lifetime savings, resulting in differing weighted average EUL values (18.0 years for gross savings).
Table 34: Evaluated 2025 Green Heat Gross Electrical Energy and Peak Demand Savings MS MSHPs Measure Fully Electrical Mainly Electrical CASHPs Air-to-water Heat Pumps Wood Stoves Pellet Stoves Number of Units 649 16 16 1 121 29 Electrical...
AI summary Table 34 evaluates the 2025 Green Heat gross electrical energy and peak demand savings for various heating measures, including fully electrical and mainly electrical systems, as well as heat pumps and stoves. It provides unitary and gross energy savings at both the meter and generator levels, along with effective useful life and peak demand savings.
Evaluated 2025 Green Heat Gross Electrical Energy and Peak Demand Savings (Continued) Measure Wood Fireplace Wood Furnaces/Boilers – Inserts Electric Resistance Baseline ETS DHW Heater Timers Total Number of Units 3 1 79 29 944 Electrical...
AI summary The document presents a table evaluating the 2025 Green Heat Gross Electrical Energy and Peak Demand Savings for various measures, including Wood Fireplace Inserts, Electric Resistance Baseline, ETS, and DHW Heater Timers. It highlights energy savings at the meter and generator levels, along with peak demand savings, and notes that tracked and evaluated savings were the same for all measures in 2025.
Table 38: Evaluated 2025 Green Heat Net Electrical Energy and Peak Demand Savings MS HPs D. H. ( Measure Measure Fully Electrical Mainly Electrical CASHPs AWHPs Wood Stoves Pellet Stoves Electrical Energy Savings Gross Electrical Energy Sa...
AI summary Table 38 evaluates the 2025 Green Heat program's net electrical energy and peak demand savings, showing significant shortfalls compared to targets. The data includes savings from various measures and factors like line loss and effective useful life.
Table 39: Comparison of 2025 Green Heat Tracked and Evaluated Savings at the Generator Gross Savings Net Savings Realization Value Unit NTGR Value Unit Rate Electrical Energy Savings Tracked Savings by E1 1.414 GWh 0.53 0.749 GWh Evaluatio...
AI summary Table 39 compares tracked and evaluated savings from the 2025 Green Heat program, showing gross and net energy and peak demand savings, along with realization rates. The table includes data from EfficiencyOne (E1) and evaluation results, with NTGR values provided as a ratio of net to gross savings.
19.2.1 Installation Rates Installation rates represent the proportion of products recorded in the tracking sheet and that remain installed in participant homes. Based on the 2025 DSM MA, installation rates for all HEA measures were estimat...
AI summary Installation rates track the proportion of products installed in participant homes. The 2025 DSM MA estimates 100% installation rates for HEA measures, confirmed by EAs during the E assessment.
Reporting Requirements HEA incentives originate from three sources of funding: Nova Scotia Power ratepayers for DSM, the Province of Nova Scotia, and the Government of Canada (CGH Grant). The inclusion of the CGH Grant as a co-funder of en...
AI summary HEA incentives are funded by Nova Scotia Power ratepayers (DSM), the Province of Nova Scotia, and the Canada Greener Homes Grant (CGH). Savings are reported to NSEB via DSM evaluations and the Province via government-funded reports. DSM focuses on electrical savings, while government reports emphasize participation and GHG reductions. Equations in Appendix XI address double-counting, and solar PV savings are included in DSM reports regardless of heating source.
19.2.3 Peak Demand Savings Peak demand savings correspond to the demand savings that coincide in time with the peak demand period of the electricity system. The projected electricity demand peak period in Nova Scotia is defined as the cold...
AI summary Peak demand savings refer to electricity demand reductions during Nova Scotia's peak period (coldest days between 5-7 PM in Dec-Feb). Calculations differ for measures modeled in HOT2000 versus prescriptive measures under Home Energy Assessments.
Measures Modelled in HOT2000 For measures modelled in HOT2000, peak demand savings are calculated by differentiating between MSHP savings and all other modelled measure savings using the following procedure: › For participants who installe...
AI summary The text explains how peak demand savings are calculated in the HOT2000 model for measures, particularly distinguishing between MSHP (Mini-split Heat Pump) savings and all other modelled measure savings. Calculations depend on whether participants meet specific conditions, including the use of a peak demand-to-energy ratio of 0.283 MW/GWh for non-MSHP measures.
Table 43: Unitary Peak Demand Savings Values for Mini-split Heat Pumps Variable Symbol Value Rated Heating Capacity of the New Heat Pump at Outdoor Air Temperature of -15 °C [kBTU/h] 𝐻𝐶𝑚𝑖𝑛 Specification data for each installed system Coeff...
AI summary Table 43 outlines the unitary peak demand savings values for mini-split heat pumps, including parameters such as rated heating capacity, coefficient of performance for baseline and new equipment, and conversion factors. The table provides specification data for each installed system.
Table 44: Evaluated 2025 HEA Gross Electrical Energy and Peak Demand Savings Measure Category HOT2000 Modelled Measures Wood Burning Equipment HPWHs Energy Efficiency Measure Subtotal Solar PV Measures Total Number of Participants 2,775 17...
AI summary Table 44 evaluates the 2025 Home Energy Assessment (HEA) gross electrical energy and peak demand savings across various measures, including heat pump and building envelope measures, wood burning equipment, and heat pump water heaters. The table provides data on participants, installed capacity, energy savings, and peak demand savings with and without adjustment ratios.
Table 49: 2025 HEA Unconverted D Assessment Spillover Savings Parameters Total Number of Unconverted D Assessment Participants 2,069 Ratio of Unconverted D Assessment Participants Who Implemented at Least One Measure 54% Total Number of Un...
AI summary Table 49 discusses the 2025 HEA Unconverted D Assessment Spillover Savings, detailing participants who implemented energy efficiency measures and the associated energy and demand savings. It notes that some participants previously had savings attributed to them but later participated in HEA, necessitating the reversal of prior savings to prevent double counting.
Table 50: 2025 HEA Unconverted D Assessment Spillover Reversals Parameters Spillover Savings Claimed Prior to 2024 Spillover Savings Claimed in 2024 Total Total Number of Unconverted D Assessment Spillover Participants from Previous Years...
AI summary Table 50 outlines the 2025 HEA Unconverted D Assessment Spillover Reversals, showing the number of participants, savings ratios, and energy savings metrics. The data highlights the impact of reversing prior spillover savings claims and the effectiveness of energy efficiency measures.
Table 51: 2025 Program Overlap Savings Deducted from HEA Overlap Net Electrical Energy Savings at the Generator (GWh) Net Peak Demand Savings at the Generator (MW) Overlap with Green Heat (0.008) (0.009) Overlap with EPI (0.077) (0.013) To...
AI summary Table 51 presents the net electrical energy and peak demand savings from program overlaps in 2025, specifically with the Green Heat and EPI programs, resulting in total savings of -0.085 GWh and -0.021 MW, respectively. Section 19.3.6 discusses the evaluated net savings from these overlaps.
19.4 Realization Rate [Table](#page-58-1) 53 below compares the electrical energy and peak demand savings established through this evaluation to those calculated in the 2025 tracking sheet. It also includes the realization rate, representi...
AI summary This section compares the electrical energy and peak demand savings from the evaluation to those in the 2025 tracking sheet, including the realization rate, which is the ratio of evaluated net savings to tracked net savings for both energy and peak demand.
20 HEA Key Findings and Recommendations As mentioned previously, the main objectives of the 2025 HEA evaluation were as follows: › Calculate gross and net results, namely electrical first-year and lifetime energy savings, peak demand savin...
AI summary The 2025 HEA evaluation found that HEA exceeded energy savings targets but saw a drop in participation linked to the CGH Grant closure. Average savings per home fell due to reduced solar PV measures, and savings matched E1's tracking.
21.3 Participation History As presented in [Figure](#page-61-0) 25 below, 157 participants completed projects and achieved electrical energy savings under MHEEP in 2025, representing an 18% decrease in participation (i.e. participants who...
AI summary In 2025, MHEEP saw an 18% drop in participants achieving electrical energy savings compared to 2024, despite stable average savings per participant. Total program savings fell by 16% for energy and 34% for peak demand, attributed to reduced participation.
22 MHEEP Evaluation Approach The 2025 MHEEP evaluation comprised a condensed impact evaluation. The main objectives of the 2025 MHEEP evaluation were as follows: › Calculate MHEEP gross and net results, namely first-year and lifetime elect...
AI summary The 2025 MHEEP evaluation focused on calculating gross and net results, including first-year and lifetime electrical energy savings, peak demand savings, and avoided GHG emissions, through a condensed impact evaluation approach.
Non-modelled Measures Programmable thermostats are not modelled in HOT2000. Instead, resulting energy savings are calculated based on unitary electrical energy savings values from the 2025 Demand-side Management Measure Assessment (DSM MA)...
AI summary Programmable thermostats are not modeled in HOT2000, with energy savings calculated via unitary electrical values from the 2025 DSM MA. The document notes no modifications to non-modelled MHEEP measures in the 2025 evaluation, referencing the DSM MA as a detailed resource for E1's DSM program parameters and savings calculations.
23.2.2 Peak Demand Savings Peak demand savings correspond to the demand savings that coincide in time with the peak demand period of the electricity system. The projected electricity peak demand period in Nova Scotia is between 5 p.m. and...
AI summary Peak demand savings in Nova Scotia are calculated during winter evenings (5-7 p.m., Dec-Feb). MHEEP uses a 0.283 MW/GWh ratio for space heating, validated by Navigant's 2016-2018 DSM Plan. Heat pumps are treated separately since 2021, with unitary savings based on capacity factors. Programmable thermostats use unitary values from the 2025 DSM MA, with no 2025 revisions.
23.2.3 Interactive Effects In a home, interactive effects occur when the implementation of energy efficiency measures has an impact on the energy consumption of other elements such as heating and cooling. The interactive effects of the spa...
AI summary The text discusses interactive effects in energy efficiency measures, noting that HOT2000 simulations already account for these effects. Programmable thermostats, not modelled in HOT2000, are stated to have no interactive impacts, so no adjustments are required for this measure in the 2025 DSM MA.
23.2.4 Effective Useful Life As part of the 2025 DSM MA activities, the Evaluator reviewed the EUL values used in the calculation of electrical energy savings that are expected to persist over time. The EUL values for building envelope upg...
AI summary The Evaluator reviewed Effective Useful Life (EUL) values for building envelope upgrades and space heating equipment in the 2025 DSM MA activities, noting that EUL values for MHEEP measures remained unchanged. Calculations rely on data from HEA and MHEEP participants' installed measures.
23.2.5 Evaluated Gross Savings Non‑modelled measures were not installed under MHEEP in 2025. Accordingly, all MHEEP annual gross savings are generated from modelled measures, the results of which are presented in [Table](#page-67-0) 56 bel...
AI summary Non-modelled measures were not installed under MHEEP in 2025, so all annual gross savings are from modelled measures, as detailed in Table 56.
23.4 Realization Rate A comparison of the gross and net electrical energy and peak demand savings values established through this evaluation and those tracked by E1 is presented i[n Table](#page-69-0) 58 below. The table also includes the...
AI summary This section compares gross and net electrical energy and peak demand savings values from the evaluation with those tracked by E1, presenting a realization rate that represents the ratio of evaluated net savings to tracked net savings for both electrical energy and peak demand savings.
25 Residential Behaviour Overview This section describes the Residential Behaviour program component, follows up on past evaluation recommendations, and provides an overview of participation history.
AI summary This section outlines the Residential Behaviour program, its evaluation follow-ups, and participation history. It emphasizes program oversight and historical engagement data as key components of the regulatory analysis.
25.1 Description Residential Behaviour, publicly branded as Efficiency Insights, is designed to help Nova Scotia Power (NS Power) residential customers reduce their electricity consumption. The component provides a subset of customers with...
AI summary Residential Behaviour (Efficiency Insights) by Nova Scotia Power helps customers reduce energy use via personalized Home Energy Reports and advice. Funded under E1's 2023-2025 DSM Plan, the program was paused in 2025 due to a cybersecurity incident disrupting AMI data access.
26 Residential Behaviour Evaluation Approach The 2025 Residential Behaviour evaluation consisted of an impact evaluation using a billing analysis for the months in 2025 for which AMI data were available (i.e. January to April 2025). The pr...
AI summary The 2025 Residential Behaviour evaluation aimed to calculate electrical first-year energy savings and avoided GHG emissions using a billing analysis of AMI data from January to April 2025. The process evaluation was postponed due to the timing of report delivery.
Table 60: 2025 Residential Behaviour Evaluation Approach Evaluation Objectives Research Questions Methodology Calculate net results › What are the evaluated first-year net electrical energy savings? › Is the participation level in other EN...
AI summary Table 60 outlines the 2025 Residential Behaviour Evaluation Approach, focusing on calculating net results through billing analysis and GHG emission reductions. The evaluation examines first-year energy savings, participation levels in ENS programs, and GHG emission reductions using AMI data from January to April 2025.
27 Residential Behaviour Impact Evaluation The objectives of the 2025 Residential Behaviour impact evaluation were to determine net electrical energy savings. The savings calculation methodology for Residential Behaviour is based on evalua...
AI summary The 2025 Residential Behaviour Impact Evaluation aims to quantify net electrical energy savings using a randomized controlled trial (RCT) methodology, comparing outcomes between treatment and control groups to ensure unbiased savings estimates.
27.2.1 Treatment and Control Group Selection and Equivalency Check To yield accurate and unbiased results when calculating savings under a RCT approach, the treatment and control groups must be selected properly so that the two groups are...
AI summary The document discusses the selection and equivalency check of treatment and control groups in the 2024 DSM evaluation. The Evaluator ensured statistical equivalence by comparing pre-program energy consumption data and geographical locations. No changes were made to the groups in 2025, except for inactive participants or those who switched to solar rate codes.
Table 62: Distribution of Geographical Locations of Households Active in 2025 Wave Region Control Treatment Number of Accounts43 16,204 91,877 HRM 38.83% 38.90% 1 – High Users Cape Breton 14.20% 14.23% Rest of Mainland NS 46.97% 46.87% Num...
AI summary Table 62 presents the geographical distribution of households active in 2025, categorized by wave (High, Medium, Low Users), region (HRM, Cape Breton, Rest of Mainland NS), and treatment (Control vs. Treatment). The data shows slight variations in distribution across regions and waves, with HRM consistently having the highest proportion of active households.
Where: - › _ℎ = The average control group daily consumption over the given post-program period - › _ℎ = The average treatment group daily consumption over the given post-program period - › _ℎ = The average control group daily consumption o...
AI summary The Evaluator adjusted the cumulative savings calculation to account for varying numbers of participating households with AMI data. Savings percentages remain below 1% after 12 months, as the Residential Behaviour program is still ramping up.
Table 63: 2025 Evaluated Cumulative Electrical Energy Savings Parameters and Results Cumulative Savings Wave 1 – High Users Initial Number of Active Participants - Treatment Group 91,877 Attrition Rate (%) 1.1% Total Number of Treatment Da...
AI summary Table 63 presents the 2025 evaluated cumulative electrical energy savings from three waves of a program, showing varying levels of savings across high, medium, and low users. The highest savings are observed in the high user group, with total savings of 3.716 GWh, while the low user group shows no measurable savings.
27.2.4 Peak Demand Savings No peak demand savings targets were set for Residential Behaviour and no peak demand savings were calculated as part of the 2025 evaluation.
AI summary No peak demand savings targets were established for Residential Behaviour, and no such savings were calculated in the 2025 evaluation.
27.2.6 Effective Useful Life For Residential Behaviour, energy savings are assessed annually through a billing analysis that serves to calculate the change in electricity consumption between the program evaluation year (post-program period...
AI summary Residential Behaviour programs assess annual energy savings using billing analysis comparing pre- and post-program electricity consumption. A one-year Effective Useful Life (EUL) is applied because savings calculations reflect both first-year and long-term savings. This approach aligns with practices in Massachusetts, Illinois, Vermont, and New York.
Table 65: First-year Savings Deductions Calculation for 2025 Wave Program Component Average Net Savings per Household (GWh)45 Proportion of Increased Participation in Treatment Group (%) Average Number of Active Treatment Participants in 2...
AI summary Table 65 calculates first-year savings deductions for the Green Heat program under Wave 2 – Medium Users. The average net savings per household is 0.000793 GWh, with 0.0821% participation increase in the treatment group and 91,358 active participants in 2025, resulting in 0.0198 GWh of savings deductions.
Savings Deductions to Be Applied in 2025 [Table](#page-85-0) 66 below presents the total savings deduction to be applied in 2025 for increased participation in other programs, which corresponds to the sum of 2025 first-year savings deducti...
AI summary The document discusses the application of savings deductions in 2025 for increased participation in other programs, noting that savings for Residential Behaviour were calculated only for the first four months of 2025 and adjusted by a factor of 4/12.
Table 66: 2025 Savings Deductions Program Compone/nt Savings Deduction Year of the Program EUL Savings Deduction to Be Applied in 2025 Wave 1 – High Users Lifetime Savings Deductions Green Heat 2024 Year 2 of 18.0 0.0181 GWh EPI 2024 Year...
AI summary Table 66 outlines the 2025 savings deductions for various programs, including Green Heat 2024 and EPI 2024, with specific values for lifetime and first-year savings deductions. The table also notes that there is no statistically significant higher program participation level in 2025 for certain waves of users.
The Residential Behaviour net electrical energy savings were estimated using the following equation: Net Savings = ∑ Monthly Savings – Savings Deductions for Participation in Other Programs The detailed results are listed in [Table](#page-...
AI summary The Residential Behaviour program's net electrical energy savings were calculated using a specific equation, resulting in 2,607 tonnes of CO2 eq in annual GHG emission reductions. The calculation used a Nova Scotia-specific factor for electricity production-related GHG emissions.
Table 67: Evaluated 2025 Residential Behaviour Net Electrical Energy Savings Cohort Wave 1 Wave 2 Wave 3 Total Electrical Energy Savings Electrical Energy Savings (GWh) 3.716 1.992 0.000 5.078 Savings Deductions (GWh) 0.118 0.035 0.000 0.1...
AI summary Table 67 and Table 68 outline the evaluated residential behaviour net electrical energy savings and GHG emission reductions for 2025. The residential behaviour program fell significantly short of its target, achieving only 5.555 GWh of net electrical energy savings compared to a target of 29.771 GWh.
27.3 Realization Rate No tracked savings were calculated for Residential Behaviour; therefore, there is no realization rate. 46 At the time of writing, 2025 data were not yet available. The Nova Scotia-specific factor was obtained from Nov...
AI summary No realization rate was calculated for Residential Behaviour due to untracked savings. Nova Scotia-specific emissions and electricity generation data were sourced from Nova Scotia Power (2024 emissions: 5,314,847 CO2 eq tonnes; generation: 11,326 GWh) and Emera Inc.'s 2024 Annual Report.
28 Residential Behaviour Key Findings and Recommendations The main objective of the 2025 Residential Behaviour evaluation was as follows: › Calculate net results, namely electrical first-year energy savings as well as avoided GHG emissions...
AI summary The 2025 Residential Behaviour program was paused in May 2025 due to a cybersecurity incident at NS Power, limiting AMI data access. This resulted in only 5.555 GWh of net energy savings (vs. a target of 29.771 GWh) over four months (Jan-Apr 2025). High and medium electricity users achieved partial savings, while low users saw no statistically significant results.
Residential Behaviour Appendix XV Residential Behaviour: Monthly Savings Approach Appendix XVI Residential Behaviour: Monthly Raw Data for Monthly Savings Calculations Appendix XVII Residential Behaviour: Examples of Statistical Significan...
AI summary The document includes appendices related to residential behaviour analysis, covering monthly savings approaches, raw data, statistical significance testing, and 2025 recommendations. EfficiencyOne is mentioned in a contact detail.
Table 1: 2025 AMH Corrected Tracked Savings Value Tracked by E1 Corrected Tracked Value Relative Difference Program Component Results Value Unit Value Unit Value AMH Gross Electrical Energy Savings at the Generator 1.348 GWh 1.378 GWh 2.2%...
AI summary Table 1 presents corrected tracked savings for the 2025 AMH program, showing differences between initial and corrected values due to an incorrect line loss factor and the use of different peak demand-to-energy ratios by certain comprehensive projects.
Evaluated 2025 ASFH Allocation of EPI Gross Electrical Energy and Peak Demand Savings per Measure (Continued) LED Lamps Product Category Nightlights GU10 7 W Replacing 50 W G25 4.5 W Replacing 40 W E12 5 W Chandeliers Replacing 40 W Number...
AI summary The document evaluates the 2025 allocation of EPI gross electrical energy and peak demand savings per measure for Affordable Single-family Homes (ASFH). It presents data on LED lamps, including installation rates, energy savings, and peak demand savings, along with factors such as interactive effects and line loss.
Evaluated 2025 ASFH Allocation of EPI Gross Electrical Energy and Peak Demand Savings Grand Total Number of Units Number of Units 5,299 Installation Rate (%) 90% Number of Units Installed 4,766 Electrical Energy Savings Gross Electrical En...
AI summary The 2025 Affordable Single-family Homes (ASFH) allocation of Efficient Product Installation (EPI) achieves 0.274 GWh gross electrical energy savings at the generator and 0.035 MW peak demand savings, with a 4.7-year effective useful life. Total units installed: 4,766 (90% of 5,299). Lifetime savings reach 1.290 GWh, adjusted for line loss factors.
For peak demand savings: - › An adjustment to the nominal heating capacity for 382 ductless mini-split heat pumps based on values found in NEEP Cold Climate Heat Pump list - › An adjustment to the peak demand savings calculation for ductle...
AI summary Adjustments to peak demand savings calculations for heat pumps and heating systems are proposed, including correcting E1's use of an incorrect baseline COP value (0.84 instead of 1.00), addressing ineligible participants with non-fully electric households, and revising savings values for pellet/wood stoves and a wood furnace baseline.
APPENDIX X HEA Tracking Sheet Audit This appendix presents the main results of the tracking sheet audit performed by the Evaluator, which was aimed at: - › Verifying that all data fields required for the evaluation were included and filled...
AI summary This audit identifies discrepancies in E1's HEA Tracking Sheet calculations, including incorrect methods for electrical energy savings, unaddressed spillover effects, and flawed peak demand calculations. The Evaluator recommends adjustments to the Customer Information System (CIS) and revised reporting practices to ensure accuracy in program evaluations.
APPENDIX XI HEA Reporting Requirements HEA incentives originate from three sources of funding and are thus reported to different parties via the DSM evaluation and government-funded evaluation. The DSM evaluation is focused on reporting el...
AI summary HEA reporting requirements involve incentives funded by both DSM and government programs. The reporting methodology was updated in 2019 and 2024 to reflect changes in energy savings calculations, including the impact of fuel switching and the use of new adjustment ratios. The Canada Greener Homes Grant was incorporated in 2021 without changing the reporting structure.
Table 1: 2025 Reporting Requirements for Different Energy Savings Scenario[s](#page-113-0) 1 Scenarios 1 2 3 4 Change in Overall Electrical Energy Consumption Increase Increase Decrease Decrease Change in Overall Non electrical Energy Cons...
AI summary Table 1 outlines 2025 reporting requirements for various energy savings scenarios, detailing changes in electrical and non-electrical energy consumption, reporting obligations, and equations used to calculate DSM and government-funded savings. The table highlights the rationale for different reporting approaches based on funding sources and energy consumption changes.
Table 1: 2025 MHEEP Corrected Tracked Savings Value Tracked by E1 Corrected Tracked Value Relative Difference Program Component Results Value Unit Value Unit Value MHEEP Gross Electrical Energy Savings at the Generator 0.337 GWh 0.337 GWh...
AI summary Table 1 shows the 2025 MHEEP Corrected Tracked Savings. The tracked and corrected values for gross and net electrical energy savings are the same, but corrected peak demand savings decreased by 2.4% due to the exclusion of three non-DSM-allocated records with no corresponding energy savings.
APPENDIX XV Residential Behaviour: Monthly Savings Approach While they are not used to claim savings, monthly savings were calculated to observe monthly trends and the ramp-up period in more detail. An equation similar to that of the cumul...
AI summary This appendix details the monthly savings approach for analyzing residential behavior in energy programs. It uses a difference-in-difference (DiD) model to compare average daily consumption between treatment and control groups pre- and post-program participation, with a formula calculating monthly savings based on household data and days in the month.
Table 1: 2025 Residential Behaviour Evaluated Monthly Electrical Energy Savings January 2025 February 2025 March 2025 April 2025 Total Wave 1 – High users Number of Active Participants - Treatment 91,877 91,558 91,154 90,842 - Attrition Ra...
AI summary Table 1 presents monthly electrical energy savings data for three waves of residential participants in 2025. The data shows varying levels of energy savings across high, medium, and low users, with some months showing higher savings and others showing lower savings. The table also includes attrition rates, baseline consumption, and margin of error for each wave.
Table 1: Wave 1 2025 Monthly Raw Data for Monthly Savings Calculations Parameters January 2025 February 2025 March 2025 April 2025 Standard Error – Treatment Post (kWh/day) 0.019 0.021 0.014 0.013 Combined Standard Error (kWh/day) 0.228 0....
AI summary Table 1 presents Wave 1 2025 monthly raw data for monthly savings calculations, including parameters such as standard error, number of observations, average daily consumption, and standard deviation for both control and treatment groups across January to April 2025.
APPENDIX XVIII Residential Behaviour 2025 Recommendations The Evaluator made no specific recommendation as part of the 2025 Residential Behaviour evaluation. 2475, Laurier boul., Suite 250 Quebec City, QC G1T 1C4 Canada Tel.: 418-692-2592...
AI summary The Evaluator made no specific recommendations as part of the 2025 Residential Behaviour evaluation. The document contains minimal content beyond this statement and includes contact information for an organization in Quebec City.
EFFICIENT PRODUCT REBATES PROGRAM Final Report 2025 DSM EVALUATION March 18, 2026 In collaboration with:
AI summary The document presents the Final Report of the 2025 Demand-Side Management (DSM) Evaluation for the Efficient Product Rebates Program, dated March 18, 2026. It highlights collaboration with unspecified entities, though specific details or findings from the evaluation are not provided in the text.
EXECUTIVE SUMMARY This report presents the 2025 demand-side management (DSM) results of the Efficient Product Rebates program administered by EfficiencyOne (E1). This program comprises the Business Energy Rebates (BER) program component. T...
AI summary This report outlines the 2025 demand-side management (DSM) results for EfficiencyOne's Efficient Product Rebates program, focusing on Business Energy Rebates (BER) through Application Rebates (BER-AR) and Instant Rebates (BER-IR). The program provides financial incentives to business, non-profit, and institutional (BNI) participants to reduce electricity consumption and demand.
Table 1: 2025 BER Evaluation Approach Evaluation Type Methodology Component Service Impact Process Market BER Application Rebates Comprehensive › Tracking sheet audit › Project reviews with site visits › Application of 2024 Demand-side Man...
AI summary The 2025 BER Evaluation Approach outlines methodologies for assessing the Business Energy Rebates (BER) program, including tracking sheet audits, site visits, participant surveys, and the use of the 2024 Demand-side Management Measure Assessment (DSM MA). It also involves GHG emission reduction calculations and jurisdictional scans of BNI lighting programs in North America.
BER Findings and Recommendations This subsection highlights the key findings and provides recommendations from the 2025 BER evaluation. 2025 BER-Finding: In 2025, BER achieved 40.244 GWh in net electrical energy savings and 5.332 MW in net...
AI summary The 2025 BER evaluation achieved 40.244 GWh net electrical savings (5% over target) but fell 26% short of peak demand savings targets. Business participation in Application Rebates dropped 36% (vs. 2024), while Instant Rebates grew 79%, driven by T8 LED promotions. Adjustment ratios for lighting/HVAC (1.117/1.006) and agriculture/commercial measures (0.951/0.514) were calculated, though the 0.514 ratio has high uncertainty.
INTRODUCTION EfficiencyOne (E1), an independent and non-profit organization, is responsible for helping Nova Scotians improve the energy efficiency of their homes and workplaces by designing, marketing, and delivering demand-side managemen...
AI summary EfficiencyOne (E1) is an independent, non-profit organization that delivers demand-side management (DSM) programs in Nova Scotia through the Efficiency Nova Scotia (ENS) franchise. E1's 2025 DSM program portfolio includes the Efficient Product Rebates program, which consists of Business Energy Rebates (BER) with Application Rebates and Instant Rebates. An evaluation report outlines the components and evaluation methods for these programs, focusing on baseline definitions, savings calculation methodologies, and net-to-gross ratios.
1.1 BER Description BER provides financial incentives in the form of prescriptive rebates or interest-free financing to business, non-profit, and institutional (BNI) participants to reduce electricity consumption and peak demand in Nova Sc...
AI summary Business Energy Rebates (BER) offer prescriptive rebates and interest-free financing to BNI participants in Nova Scotia to reduce electricity use and peak demand. The program includes Application Rebates (AR) and Instant Rebates (IR), with eligibility criteria based on efficiency standards. In 2025, solar PV rebates were discontinued, rebate levels reduced, and certain technologies (e.g., T8 lighting) became ineligible. BER aimed for 38.451 GWh in energy savings and 7.241 MW in peak demand reduction by 2025.
1.2 Follow-up on Past Evaluation Report Recommendations The Evaluator evaluated BER for 2024 and provided improvement recommendations. [Table](#page-146-1) 5 below outlines the status of those recommendations that were carried forward.
AI summary The Evaluator assessed the Business Energy Rebates (BER) for 2024 and provided improvement recommendations, with Table 5 outlining the status of those recommendations that were carried forward.
Table 5: Implementation Status of Past Recommendations for BER # Recommendation Status Comments BER-R9 Ensure that multi-wattage products are identified in the tracking sheet. Update applications for BER-AR and SBES to identify multi-watta...
AI summary Table 5 outlines the implementation status of past recommendations for the Business Energy Rebates (BER) program. Recommendation BER-R9, which requires identifying multi-wattage products in the tracking sheet and using mid-range wattage when information is not available, has been completed. E1 used model numbers to track multi-wattage lighting in the 2025 DSM tracking sheet and is assessing the use of DesignLights Consortium (DLC) variables for automation.
BER Overall As presented in [Figure](#page-151-1) 7 below, BER generated a total of 45.081 GWh in gross electrical energy savings at generator in 2025, which represents a 4% decrease compared to 2024 results. In 2025, gross peak demand sav...
AI summary BER generated 45.081 GWh in gross electrical energy savings in 2025, a 4% decrease from 2024, and 6.046 MW in gross peak demand savings, a 11% decline. Lower participation in Application Rebates drove the reductions.
Table 6: 2025 BER Evaluation Approach Evaluation Objectives Research Questions Methodology Validate 2024 market evaluation results and determine timing for when a LED baseline for BER IR LED fixtures should take effect › To what extent are...
AI summary This table outlines the evaluation approach for the 2025 Business Energy Rebates (BER) program, focusing on validating 2024 market evaluation results and determining the timing for implementing a LED baseline for BER Instant Rebates (BER-IR) LED fixtures. It includes research questions and methodologies such as distributor interviews and staff interviews.
Interviews with New Brunswick Distributors The Evaluator selected to use the New Brunswick market as a comparator as, up until very recently, New Brunswick Power (NB Power), the DSM program administrator for the Province of New Brunswick,...
AI summary The Evaluator used New Brunswick as a comparator due to the recent launch of its Midstream Business Rebates Program (MBRP), similar to BER-IR. Six New Brunswick distributors were interviewed, revealing varied operational scopes and participation levels in the program. The study aimed to assess market evolution in business lighting, with data collection methods emphasizing pre-MBRP market conditions.
Table 7: 2025 Application Rebates Adjustment Ratios Electrical Energy Savings Peak Demand Savings Measure Category Adjustment Ratio Margin of Error Adjustment Ratio Margin of Error Lighting 1.117 8.3% 1.031 10.4% Heating, Ventilation, and...
AI summary Table 7 presents the 2025 Application Rebates Adjustment Ratios for various measure categories, including lighting and HVAC, with specific adjustment ratios and margins of error for electrical energy and peak demand savings.
3.2.2 Interactive Effects Interactive effects occur when the implementation of energy efficiency measures has an impact on the energy consumption of other elements such as heating and cooling; these are considered in the gross savings stan...
AI summary Interactive effects refer to impacts of energy efficiency measures on heating/cooling systems, considered in E1's gross savings calculations. For BER-AR, these effects apply only to indoor lighting projects. The Evaluator updated interactive effects factors in the 2025 DSM MA based on building type and lighting characteristics, confirming correct application through site visits.
3.2.3 Effective Useful Life In 2025, the Evaluator reviewed the EUL values used in the calculations of electrical energy savings that are expected to persist over time. For LED linear fixture, LED linear lamp, and LED outdoor fixture measu...
AI summary In 2025, the Evaluator reviewed and recalculated the Effective Useful Life (EUL) values for LED lighting measures, considering changes in the baseline over the measure's lifetime. The updated EUL values are presented in Table 8 of the 2025 DSM MA.
Table 9: Evaluated 2025 Application Rebates Gross Electrical Energy and Peak Demand Savings Measure Category Agriculture Commercial Kitchen HVAC Lighting Motor Pumping Refrigeration Renewable Energy Total Electrical Energy Savings Tracked...
AI summary Table 9 evaluates the 2025 Application Rebates for gross electrical energy and peak demand savings across various measure categories. It includes tracked savings, adjustment ratios, line loss factors, and lifetime savings. The table also notes that adjustment ratios differ from prior evaluations due to prior inclusion in tracked savings.
The differences between tracked and evaluated savings outlined in the figures are the results from applying updated adjustment ratio values across all measure categories and revised interactive effects values for recessed fixture lighting...
AI summary The document discusses differences between tracked and evaluated savings in the 2025 Application Rebates, resulting from updated adjustment ratio values and revised interactive effects for recessed fixture lighting measures. It also references figures and a table related to electrical energy and peak demand savings, as well as GHG emission reductions calculated using a Nova Scotia-specific factor.
Table 13: Evaluated 2025 Application Rebates Net Electrical Energy and Peak Demand Savings Measure Category Agriculture Commercial Kitchen HVAC Lighting Motor Pumping Refrigeration Renewable Generation Total Electrical Energy Savings elect...
AI summary Table 13 presents evaluated 2025 application rebates for net electrical energy and peak demand savings, categorizing them by measure type and including factors like NTGR, line loss, and effective useful life. The table provides a detailed breakdown of energy savings across various sectors and their impact on the generator and meter levels.
[Table](#page-168-1) 14 presents a comparison between the 2025 evaluated energy and peak demand savings and those tracked by E1. It also shows the realization rates, which indicate the ratio of evaluated net savings to tracked net savings,...
AI summary Table 14 compares the 2025 evaluated energy and peak demand savings with those tracked by E1, highlighting realization rates that show the ratio of evaluated net savings to tracked net savings for both energy and peak demand.
Gross Savings Net Savings Realization Value Unit NTGR Value Unit Rate Electrical Energy Savings Tracked Savings by E1 9.302 GWh 0.740 6.884 GWh Evaluated Savings 9.214 GWh 0.932 8.586 GWh 125% Peak Demand Savings Tracked Savings by E1 0.78...
AI summary The table presents gross and net savings, along with realization rates, for electrical energy and peak demand savings tracked by E1 and evaluated by the Evaluator. Higher realization rates are attributed to updated NTGR values applied by the Evaluator.
4.2.2 Energy Savings As part of 2025 DSM MA activities, several parameters were updated and some measures eligible under Instant Rebates were impacted. In 2025, the unitary savings values for circulator pumps were updated. The tracked and...
AI summary Updates to 2025 DSM MA parameters affected circulator pump savings values, with changes detailed in Table 15. The Uniform Methods Project's definition is cited for unitary savings estimation.
Table 15: 2025 Instant Rebates Tracked and Evaluated Unitary Electrical Energy Savings for Circulator Pumps Tracked Maximum Input Power Categories Evaluated Maximum Input Power Categories Tracked Unitary Electrical Energy Savings Value (kW...
AI summary Table 15 details the 2025 instant rebates for circulator pumps, showing tracked and evaluated unitary electrical energy savings across different power categories. The table includes tracked and evaluated maximum input power categories and corresponding energy savings in kWh. The section also introduces a discussion on peak demand savings.
4.2.4 Interactive Effects Interactive effects occur when the implementation of energy efficiency measures has an impact on the energy consumption of other elements such as heating and cooling; these are taken into account in the gross unit...
AI summary This section discusses interactive effects in energy efficiency measures, particularly how they impact heating and cooling systems. It explains how the Evaluator calculated these factors for eligible products under the 2025 DSM MA activities, noting differences between tracked and evaluated factors due to updated methods and building mix in 2025.
Table 16: 2025 Instant Rebates Interactive Effects Factor Calculation Results Measure Tracked Interactive Effects Factor for Energy Savings Tracked Interactive Effects Factor for Peak Demand Savings Evaluated Interactive Effects Factor for...
AI summary Table 16 presents the 2025 Instant Rebates Interactive Effects Factor Calculation Results for various lighting measures, including LED linear fixtures and lamps, showing the impact on energy and peak demand savings. The table includes both tracked and evaluated factors for different types of fixtures and their weighted averages.
As part of the 2025 DSM MA activities, the Evaluator reviewed the EUL values used in the calculations of electrical energy savings that are expected to persist over time. In the 2025 evaluation for LED linear fixtures, LED linear lamps, LE...
AI summary The Evaluator adjusted EUL values for certain LED lighting measures in the 2025 DSM MA evaluation due to regulatory changes affecting baseline assumptions, while maintaining previously established EUL values for other Instant Rebates measures.
Table 17: 2025 Instant Rebates Tracked and Evaluated EUL Values Measure Tracked EUL (years) Evaluated EUL (years) LED Linear Fixtures 1 x 4 Luminaires 11.9 4.8 2 x 2 Luminaires and Retrofit Kits 11.9 4.8 2 x 4 Luminaires and Retrofit Kits...
AI summary Table 17 compares the tracked and evaluated effective useful life (EUL) values for various LED lighting measures under the 2025 instant rebate program. The evaluated EUL values are significantly lower than the tracked values and are used to calculate gross and net lifetime electrical energy savings, resulting in a weighted average EUL of 4.9 years for gross savings.
4.2.6 Evaluated Gross Savings The electrical energy and peak demand savings associated with Instant Rebates were calculated using the unitary savings values (including baseline wattages, the actual wattages of efficient measures, ballast f...
AI summary The document discusses the calculation of electrical energy and peak demand savings from Instant Rebates using data from the 2025 DSM MA, including unitary savings values and line loss factors updated in 2019. These factors were submitted to the Nova Scotia Energy Board as part of the 2014 Cost of Service Study Progress Update.
Table 18: 2025 Instant Rebates Evaluated Gross Electrical Energy and Peak Demand Savings Measure Category LED Linear Fixtures LED Linear Lamps LED Outdoor Fixtures LED Directional and Architectural Fixtures Outdoor Motion Sensors Indoor Oc...
AI summary Table 18 evaluates the gross electrical energy and peak demand savings for various energy efficiency measures under the 2025 Instant Rebates program. It provides data on the number of units, energy savings at the meter and generator, effective useful life, and peak demand savings across different measure categories.
[Figure](#page-174-0) 10 below compares the tracked and evaluated gross electrical energy savings, while [Figure](#page-174-1) 11 further below compares the tracked and evaluated gross peak demand savings. The slight differences between tr...
AI summary The text discusses differences between tracked and evaluated gross electrical energy and peak demand savings, attributed to updated factors such as energy and demand line loss, interactive effects for lighting measures, and unitary energy savings for circulator pumps. It also mentions the calculation of GHG emission reductions using a Nova Scotia-specific factor applied to Instant Rebates gross savings.
Table 20: 2025 Instant Rebates Evaluated NTGRs Measure Free-ridership NTGR LED Linear Fixtures 8% 0.92 LED Linear Lamps 15% 0.85 LED Outdoor Fixtures 15% 0.85 Other Measures 0% 1.00 4.3.3 Evaluated Net Savings
AI summary Table 20 presents the evaluated net-to-gross ratios (NTGRs) for various energy efficiency measures under the 2025 Instant Rebates program. The table includes free-ridership percentages and NTGR values for LED Linear Fixtures, LED Linear Lamps, LED Outdoor Fixtures, and Other Measures.
Table 21: 2025 Instant Rebates Evaluated Net Electrical Energy and Peak Demand Savings Measure Category LED Linear Fixtures LED Linear Lamps LED Outdoor Fixtures LED Directional and Architectural Fixtures Outdoor Motion Sensors Indoor Occu...
AI summary Table 21 provides a detailed evaluation of the 2025 Instant Rebates, showing net electrical energy and peak demand savings across various measure categories. The table includes gross and net savings, NTGR, line loss factors, and effective useful life for each measure category.
Gross Savings Net Savings Realization Value Unit NTGR Value Unit Rate Electrical Energy Savings Tracked Savings by E1 35.357 GWh 0.88 31.181 GWh Evaluation Results 35.867 GWh 0.88 31.658 GWh 102% Peak Demand Savings Tracked Savings by E1 5...
AI summary The evaluated net electrical energy savings were 2% higher than those tracked by E1, while peak demand savings were 3% lower. These differences are attributed to updated line loss factors, interactive effects factors, and unitary energy savings values for circulator pumps.
6.2.3 DesignLights Consortium (DLC) Certified Fixtures Nearly all fixtures (98-99%) offered by all six participating distributors interviewed are DLC-certified, with no differences in shares of distributor stocks before and after joining t...
AI summary Nearly all lighting fixtures offered by six participating distributors are DLC-certified. Three distributors could not distinguish between DLC Standard and Premium products, while others carried mostly DLC-certified products before joining the program, with some variation in the shares of Standard and Premium products.
Opinions among distributors were mixed on the topic of DLC Premium and DLC Standard pricing patterns and the impact of rebates on pricing differences between the two categories. For DLC Premium fixtures, some distributors observed that the...
AI summary Distributors have mixed opinions on DLC Premium and DLC Standard pricing patterns and rebate impacts. Some note that DLC Premium prices remain higher than DLC Standard even after rebates, while others express confusion about the certification differences. Non-participating distributors supply DLC-certified fixtures, mostly DLC Standard, with higher proportions in outdoor fixtures.
Table 28: Summary of Jurisdictional Scan Findings by Region Program Administrator Region Instant Rebate Program Application Rebate Program Custom Program Direct Install LED Incentives Continuing in the Near Term? 1. National Grid (Mass Sav...
AI summary Table 28 summarizes findings from a jurisdictional scan of energy efficiency programs across various regions. It details the presence and structure of instant rebate, application rebate, custom, and direct install programs, with specific information on LED incentives and their continuation in the near term. Some programs are being phased out or updated, such as in Ontario and Quebec.
mewhat more complicated to implement as data or assumptions are required to establish the market blend and also requires an assumption on when LED fixtures would be the baseline for all project types. Dual Baseline: Savings are calculated...
AI summary The text discusses the dual baseline approach for calculating energy savings, emphasizing its complexity due to market blend assumptions and LED fixture timelines. Mass Save and PSE use this method, with EUL assumptions varying by program targets and dates (e.g., LED baseline by 2029). The Uniform Methods Project (UMP) is cited as a reference for evaluation protocols.
Table 29: Jurisdictional Scan. Baseline. and EUL Assumptions Program Administrator Region Program Type Existing Lighting Baseline Market Blend Baseline Dual Baseline Efficiency One Nova Scotia. Canada Instant. application EUL = full lifeti...
AI summary Table 29 compares lighting baseline assumptions across various energy efficiency programs in different jurisdictions, highlighting differences in Effective Useful Life (EUL) assumptions and program structures, such as instant application, custom, and direct install approaches.
Dual Baseline Approach for BER-AR and SBES For SBES, since the target population is small businesses, Econoler assumes that the majority of projects is early replacement. Therefore, Econoler recommends using the UMP approach to develop a d...
AI summary Econoler recommends a dual baseline approach for SBES using the UMP method, combining existing and LED baselines. For BER-AR, two options are proposed: targeting market laggards with early replacement criteria or using a blended baseline. Both programs aim for full market transformation by 2028-2029, eliminating future savings opportunities.
7 BER Key Findings and Recommendations The main objectives of the 2025 BER evaluation were as follows: - › Calculate BER gross and net results, namely first-year and lifetime electrical energy savings, peak demand savings, as well as avoid...
AI summary The 2025 BER evaluation found BER exceeded net electrical energy savings targets by 5% (40.244 GWh) but missed peak demand savings by 26% (5.332 MW vs. 7.241 MW target). Application Rebates participation declined, while Instant Rebates achieved record participation since 2019, boosting savings compared to 2024.
Table 1: 2025 Application Rebates Corrected Tracked Savings Value Tracked by E1 Corrected Tracked Value Relative Difference Result Value Unit Value Unit Value Gross Electrical Energy Savings at the Generator 9.297 GWh 9.302 GWh 0.06% Gross...
AI summary Table 1 presents the 2025 Application Rebates Corrected Tracked Savings, showing minimal differences between tracked and corrected values for electrical energy and peak demand savings at the generator level. The differences are attributed to corrections made in the tracking process.
APPENDIX II BER Instant Rebates Tracking Sheet Audit This appendix presents the main results of the tracking sheet audit performed by the Evaluator, which was aimed at: - › Verifying that all data fields required for the evaluation were in...
AI summary This appendix details the results of a tracking sheet audit conducted by the Evaluator to verify the completeness and accuracy of data submitted by E1. The audit focused on ensuring consistency in calculation methods for energy and peak demand savings from lighting and pumping measures, as well as overall Instant Rebates.
Table 1: 2025 Instant Rebates Corrected Tracked Savings Value Tracked by E1 Corrected Tracked Value Relative Difference Service Results Value Unit Value Unit Value Instant Rebates - Lighting Gross Electrical Energy Savings at the Generator...
AI summary The table presents corrected tracked savings for the 2025 Instant Rebates, showing slight differences in energy and peak demand savings for lighting and pumping measures. The corrections were made due to adjustments in hours of use, rated wattage, and baseline wattage values, as well as a correction to the savings calculation for LED Linear Lamps.
Table 1: Overview of Data Collection Activity Descriptor This Instrument Instrument Type Telephone survey Estimated Time to Complete 15 minutes Target Audience 2025 program participants Expected Number of Completions 40 Contact List Source...
AI summary The document outlines data collection activities through a telephone survey targeting 2025 program participants, with a timeline from October 24th to November 14th, 2025. It also describes research objectives related to free-ridership and cross-influence in various energy efficiency measures.
B. INTRODUCTION B – Business with no contact name Hello, I am with Narrative Research, and we are performing an evaluation of energy efficiency programs and services provided by Efficiency Nova Scotia. We have a few questions about your re...
AI summary The text outlines a questionnaire by Narrative Research evaluating Efficiency Nova Scotia's Business Energy Rebates Program. It seeks to identify the most knowledgeable individual in businesses that installed energy efficiency measures (e.g., lighting, heat pumps) and requests contact details for follow-up.
D5. [ASK ONLY IF DLC Premium=YES] Without the Business Energy Rebates Program, what is the likelihood that you would have purchased DLC Premium LED lighting products? 1. Definitely would have 2. Probably would have 3. Probably would not ha...
AI summary The text presents survey questions related to the Business Energy Rebates Program, focusing on customer behavior regarding the purchase of energy-efficient lighting products and the use of energy management services. It explores the impact of the rebate program on purchasing decisions and project implementation.
Table 1: BER-AR Participant Survey Free-ridership Algorithm (Heat Pumps) INTENTION 1 – Heat Pump Cost Score (CS) C3 Context Question C4. Without the Business Energy Rebates Program and the rebate you received, would you have: [ONLY ONE POS...
AI summary This table outlines a free-ridership algorithm used in the BER-AR Participant Survey for heat pumps, focusing on how participants would have acted without the Business Energy Rebates Program. It includes questions about cost scores, timing of purchase, and quantity, with scoring based on responses.
Table 2: BER-AR Participant Survey Free-ridership Algorithm (Lighting) INTENTION Planning Question Answer Score D1. Before learning about the Business Energy Rebates Program, had your business already decided to install energy-efficient LE...
AI summary This table outlines the free-ridership algorithm for the Business Energy Rebates (BER) Program, focusing on lighting. It includes questions to determine whether businesses had already decided to install energy-efficient LED lighting before participating in the BER Program, and if they considered other lighting options.
Energy and Peak Demand Savings Algorithms The following algorithms include the parameters required to determine the annual energy savings and the annual peak demand savings associated with a low-bay LED luminaire replacement measure. [1] E...
AI summary The document outlines mathematical formulas for calculating annual energy savings and annual peak demand savings from replacing low-bay LED luminaires. Key parameters include baseline and efficient wattage, demand factors, usage factors, and conversion factors.
B. Lighting Market Assessment - B1. Based on your observations, what's happened in the commercial LED lighting market in the past three years in terms of…? [ASK FOR EACH] - b. New technologies [Any differences between LED lamps and LED fix...
AI summary The document asks about changes in the commercial LED lighting market over the past three years, including technology, demand, product offerings, availability, and pricing. It also requests the proportion of LED versus non-LED lighting stock in 2025 and asks if participation in the Midstream Business Rebate Program affected this percentage.
- C) [IF LESS THAN 100% FOR LED AT B11A)] When do you expect LED products to make up 100% of your [READ CATEGORY NAME] sales? Lighting Estimated Sales (%) in 2027 Lighting Category % LED % Non-LED [Why increase/decrease Year anticipated fo...
AI summary This section of the regulatory proceeding document asks respondents to estimate when LED products will make up 100% of sales in various lighting categories and to provide details on the percentage of DLC certified LED fixtures before and after participation in the Midstream Business Rebate Program.
- b. … [ASK IF D1 IS LESS THAN 8], Please explain the reason(s) for your score. Aspects of the program Score Reason 1. The overall NB Power Midstream Business Rebate Program 2. The program support and communications provided by the program...
AI summary The text presents a request for explanation regarding a score given to the NB Power Midstream Business Rebate Program, focusing on aspects such as program support, communication, and rebate processing. It also asks about any challenges experienced with the program.
LIGHTING MARKET STUDY - INSTANT BUSINESS Rebate Programs – EFFICIENCY ONE
AI summary This document outlines a market study for EfficiencyOne's Instant Business Rebate Programs in Nova Scotia, focusing on energy efficiency initiatives and regulatory considerations for business energy rebates.
2025 DSM EVALUATION March 20, 2026 In collaboration with:
AI summary The document header indicates a 2025 Demand-side Management (DSM) evaluation proceeding, dated March 20, 2026, with collaboration imagery referenced but no substantive content provided in the text.
ABBREVIATIONS BDM Business Development Manager BER Business Energy Rebates BNI Business, non-profit, and institutional BOpt Building Optimization CPA Customer Project Agreement DR Demand response DSM Demand-side management DSM MA Demand-si...
AI summary A list of abbreviations and their expansions used in regulatory proceedings, including terms related to energy efficiency, demand-side management, and utility programs. Key acronyms include DSM, BER, and NSUARB, with definitions covering technical, programmatic, and organizational terms.
DEFINITIONS Adjustment ratio The ratio of evaluated results to tracked results. This ratio expresses the adjustment made to tracked savings or other tracked values such as effective useful life values. The capacity that is available to Nov...
AI summary The text defines key terms related to energy efficiency and demand response, including adjustment ratios, available demand response capacity, baseline establishment, bias, billing calibration, confidence intervals, and demand response measures. These definitions are critical for understanding how energy savings are calculated and evaluated.
Table 1: Summary of 2025 Custom Incentives Program Evaluation Program Evaluation Type Component Impact Process Market Methodology Custom Comprehensive › Participant phone interviews › Project file reviews and participant follow-up intervie...
AI summary The document provides a summary of the 2025 Custom Incentives Program Evaluation, outlining the evaluation methods used, including participant interviews, project file reviews, site visits, and calculations for avoided GHG emissions. The evaluation covers various program components and performance metrics.
Table 2: Overall 2025 Custom Incentives Participation and Savings Partic ipation Level Gros s Savings NTGR Net Net Savings Value Unit Value Unit Value Unit Value Custom • ' ' ' ' Electrical Energy Savings 36.207 GWh 0.84 30.487 GWh Lifetim...
AI summary Table 2 provides an overview of the 2025 Custom Incentives Participation and Savings, detailing metrics such as electrical energy savings, peak demand savings, GHG emission reductions, and energy use life (EUL) for both completed and ongoing projects. The data highlights the impact of these incentives on energy efficiency and environmental outcomes.
Custom Findings and Recommendations This subsection provides the key findings and recommendations from the Custom evaluation. The Evaluator has no specific recommendation for Custom. & lt;sup>1 Completed SEM projects reference participants...
AI summary The Evaluator found no specific recommendations for Custom, noting that completed SEM projects generated savings. The Custom Incentives Program is mentioned as part of the discussion.
SEM Findings and Recommendations This subsection provides the key findings from the SEM evaluation. The Evaluator has no specific recommendation for SEM. 2025 SEM-Finding: SEM net electrical energy savings exceeded the 2.657 GWh target by...
AI summary The 2025 SEM evaluation found that net electrical energy savings exceeded targets by 52%, with participation reaching its highest level since 2018. However, savings per participant declined. M&V methodologies were deemed appropriate and accurate, though no specific SEM recommendations were provided.
EfficiencyOne (E1), an independent and non-profit organization, is responsible for helping Nova Scotians improve the energy efficiency of their homes and workplaces by designing, marketing, and delivering demand-side management (DSM) for N...
AI summary EfficiencyOne (E1) is a non-profit organization responsible for delivering demand-side management (DSM) programs in Nova Scotia through the Efficiency Nova Scotia (ENS) franchise. E1 is funded by Nova Scotia Power (NS Power) ratepayers and has a portfolio of residential, BNI, and demand response programs. Econoler was commissioned to evaluate E1's 2025 DSM program portfolio, including the Custom Incentives program and its components, such as Strategic Energy Management (SEM). The evaluation focuses on baseline definitions, savings calculation methods, parameter values, and net-to-gross ratios.
Retrofit - •Technical and financial support to help organizations conduct scoping and feasibility studies. - •Technical and financial support for the implementation of energy efficiency projects using a customized and flexible approach.\ -...
AI summary The Retrofit program offers technical and financial support for energy efficiency projects, targeting organizations with annual electricity consumption of 350,000 kWh or higher. It emphasizes customized approaches for scoping studies and project implementation, provided projects have not yet commenced.
1.2 Follow-up on Past Evaluation Report Recommendations The Evaluator evaluated Custom in previous years and issued improvement recommendations. [Table](#page-65-1) 5 below provides a summary of the implementation status of each recommenda...
AI summary The Evaluator has previously assessed Custom and provided improvement recommendations. Table 5 summarizes the implementation status of ongoing recommendations from the 2024 and 2022 Custom Incentives evaluation reports.
Table 5: Implementation Status of Past Recommendations for Custom # Recommendations Status Comments 2024-New Construction-R3 Investigate the impact of increasing modelling incentives (the share of modelling costs covered as well as the inc...
AI summary Table 5 outlines the implementation status of two recommendations related to the New Construction service. Recommendation R3 is in progress, with E1 planning to investigate increasing modelling incentives in Q2 2026. Recommendation R4 has been completed, with E1 having added two new energy modellers and continuing recruitment efforts.
2 Custom Evaluation Approach The 2025 Custom evaluation comprised a comprehensive impact evaluation for Retrofit, P4P, and New Construction. For Building Optimization, given its smaller contribution to Custom savings, NTGR results from 202...
AI summary The 2025 Custom evaluation focuses on assessing the impact of Retrofit, Pay-for-Performance (P4P), and New Construction programs. It includes calculating energy savings, peak demand reductions, and GHG emissions. The evaluation uses NTGR results from 2021 for Building Optimization due to its smaller contribution to savings.
3 Retrofit Impact Evaluation The objectives of the 2025 Retrofit impact evaluation were to determine gross and net electrical energy savings and peak demand savings, annually avoided GHG emissions, as well as EUL values and associated life...
AI summary The 2025 Retrofit impact evaluation aims to assess electrical energy and peak demand savings, annual GHG emissions avoided, and EUL values. The evaluation considers three types of savings: partial savings from projects started before 2025, final savings from single-year projects completed in 2025, and final savings from multiyear projects completed in 2025.
3.2 Gross Savings Gross savings correspond to the changes in energy consumption resulting from measures installed or actions taken by Retrofit participants compared to the consumption level had those measures or actions not occurred. [5](#...
AI summary Gross savings are calculated based on energy consumption changes from Retrofit projects. E1 tracks annual savings using M&V practices, combining participant data with engineering assumptions and professional judgments to assess project impacts.
3.2.1 Savings Verification For compressed air leak and solar PV projects, the Evaluator verified savings by validating that the correct input parameters were used by E1 to estimate savings following a semi-prescriptive approach. For compre...
AI summary The section outlines savings verification methods for compressed air leak and solar PV projects. The Evaluator confirmed E1's use of correct input parameters and 2021/2023 adjustment ratios to calculate gross energy and peak demand savings, ensuring compliance with semi-prescriptive approaches.
3.2.2 Project Review Sampling Methodology For the regular Retrofit project category, the Evaluator used a stratified sampling approach to select 18 projects for review from a total of 27 projects completed in 2025. More specifically, the E...
AI summary The Evaluator used stratified sampling to review 18 of 27 completed Retrofit projects in 2025, prioritizing larger projects (100% sample rate) and randomly selecting from smaller strata. The sample represented 88% of total energy savings, excluding projects with partial 2025 savings claims. Gross savings were extrapolated using a weighted average adjustment ratio.
3.2.5 Effective Useful Life The Evaluator reviewed the EUL values of all sampled projects by selecting an appropriate EUL for each measure implemented. The revised measure level EUL values were selected based on the values outlined in the...
AI summary The Evaluator adjusted Effective Useful Life (EUL) values for sampled projects based on the 2025 DSM MA, including reducing compressed air leak audit projects from 4 to 2 years and extending solar PV projects from 25 to 30 years. One Retrofit project's EUL was also revised.
For multiyear projects that claimed partial savings in previous years and were completed in 2025, the Evaluator applied the 2025 adjustment ratios to the full savings associated with those projects. To compensate for adjustments to partial...
AI summary The text discusses the evaluation process for multiyear projects completed in 2025, including the application of adjustment ratios and true-up adjustments. It also notes that solar PV projects did not contribute to peak demand savings during Nova Scotia's peak periods and that compressed air leak audit projects used 2021 adjustment ratios due to completed savings verification.
alues for all measures offered in E1's program portfolio. For the evaluation conducted during the last year of the 2023-2025 DSM cycle, the Evaluator refers to the values presented in the 2025 DSM MA. [Table](#page-78-0) 10 presents an ill...
AI summary The text discusses the evaluation of energy savings measures in E1's program portfolio during the 2023-2025 DSM cycle, referencing the 2025 DSM MA for values. It also mentions a table illustrating the true-up adjustment process for a hypothetical multiyear project completed in 2025.
Table 10: Example of a 2025 True-up Adjustment 2024 2025 Total Tracked Savings (kWh) 105,187 63,884 169,071 Year-specific Adjustment Ratio 1.021 1.003 Revised Savings Prior to True-up (kWh) 107,396 64,076 171,472 Total Project Revised Savi...
AI summary Table 10 shows a 2025 true-up adjustment example, illustrating tracked savings, adjustment ratios, and revised savings. Table 11 builds on this by applying adjustment ratios and true-up adjustments to Retrofit projects' energy and peak demand savings. Line loss factors from NS Power's 2014 study are used for calculations, with assumptions for municipal utilities.
Table 11: Evaluated 2025 Retrofit Gross Electrical Energy and Peak Demand Savings Partial Savings Claimed Final Savings Claimed for Single year Projects Final Savings Claimed for Multiyear Projects Total Number of Projects 9 31 6 46 Electr...
AI summary Table 11 evaluates the 2025 Retrofit Gross Electrical Energy and Peak Demand Savings, presenting data on tracked savings, adjustment ratios, and line loss factors for different project types. It includes figures for electrical energy and peak demand savings at both the meter and generator levels, along with effective useful life and lifetime savings.
Table 13: 2025 NTGR Approach per Retrofit Project Category Retrofit Project Category Number of Projects Completed in 2025 NTGR Methodology Sample Size (Unique Participant Interviews) Regular Retrofit 27 Free-ridership and spillover were me...
AI summary Table 13 outlines the 2025 NTGR approach for different retrofit project categories, detailing the methodology used to measure free-ridership and spillover effects. Regular Retrofit and Compressed Air Leak Audit projects used phone interviews with sampled participants, while Solar PV projects applied the 2023 NTGR evaluation. The sample size for each category is also noted, with a clarification on handling participants who completed multiple projects.
3.3.2 Spillover For Retrofit, participant spillover occurs when participants implement eligible energy efficiency measures due to the influence of previous participation in the service without receiving any kind of additional support. [13]...
AI summary The document defines spillover in the Retrofit program as participants implementing energy efficiency measures influenced by prior participation without additional support. Two participants reported self-initiated measures, but the Evaluator concluded overall spillover for regular Retrofit was nil. Findings were based on phone interviews and an algorithm detailed in Appendix IV.
3.4 Realization Rate [Table](#page-84-1) 17 below compares total 2025 Retrofit tracked and evaluated savings. It also includes the realization rate, representing the ratio of evaluated net savings to tracked net savings, for both electrica...
AI summary This section discusses the realization rate, which is the ratio of evaluated net savings to tracked net savings for both electrical energy and peak demand savings in 2025 Retrofit. A table is referenced to compare total tracked and evaluated savings.
Table 17: Comparison of 2025 Retrofit Tracked and Evaluated Savings at the Generator Gross Savings NTGR Net Savings Realization Rate Value Unit Value Value Unit Value Electrical Energy Savings Tracked Savings by E1 16.032 GWh 0.82 13.121 G...
AI summary Table 17 compares the tracked and evaluated savings from 2025 retrofit programs, focusing on electrical energy and peak demand. Tracked savings by E1 are compared with evaluation results, showing slight differences in gross and net savings, as well as realization rates.
4.2.1 Project Review Findings The Evaluator reviewed the single completed P4P project in 2025, which involved the implementation of an advanced building automation system to optimize set point control and scheduling of a building heating,...
AI summary The Evaluator reviewed a completed P4P project in 2025 involving advanced building automation for HVAC optimization. No adjustment was made to electrical energy savings, but peak demand savings were downwardly adjusted due to misalignment with Nova Scotia's peak demand periods. Ongoing projects with partial claims were deferred for future evaluation.
4.2.4 Evaluated Gross Savings [Table](#page-86-2) 18 below presents the overall evaluated gross savings for P4P. For the one single-year project completed in 2025, evaluated gross electrical energy and peak demand savings were determined f...
AI summary The section discusses the evaluated gross savings for the Pay-for-Performance (P4P) program, detailing how savings are calculated for completed and partially completed projects. It mentions the use of line loss factors based on the 2014 Cost of Service Study Progress Update provided by NS Power.
4.4 Realization Rate A comparison of the electrical energy and peak demand savings values established through this evaluation and those tracked by E1 is presented in [Table](#page-89-2) 22 below. The table also includes the realization rat...
AI summary This section discusses the realization rate, which is the ratio of evaluated net savings to tracked net savings for both electrical energy and peak demand savings, as compared in Table 22.
5.2.5 Evaluated Gross Savings The 2025 New Construction gross electrical energy and peak demand savings are presented in [Table](#page-92-1) 23 below. They were obtained by applying the average adjustment ratios of 0.949 to electrical ener...
AI summary The 2025 New Construction gross electrical energy and peak demand savings are calculated using average adjustment ratios of 0.949 and 0.937, respectively, applied to all projects claiming savings. Line loss factors specific to each project, based on rate codes and data from NS Power, are used to determine savings at the generator level.
Total Number of Projects 33 Electrical Energy Savings Tracked Gross Electrical Energy Savings – at the Meter (GWh) 18.235 Adjustment Ratio for Electrical Energy Savings 0.949 Gross Electrical Energy Savings – at the Meter (GWh) 17.307 Line...
AI summary The table presents energy savings and GHG emission reductions from 33 projects. It includes electrical energy savings, peak demand savings, and adjustments for line loss. GHG reductions are calculated using a Nova Scotia-specific factor applied to new construction savings.
Gross Savings NTGR Net Savings Realization Rate Value Unit Value Value Unit Value Electrical Energy Savings Tracked Savings by E1 18.713 GWh 0.72 13.473 GWh Evaluation Results 18.447 GWh 0.82 15.057 GWh 112% Peak Demand Savings Tracked Sav...
AI summary The evaluated gross electrical energy and peak demand savings were lower than those tracked by E1 due to adjustments in energy models. However, evaluated net savings were higher due to lower free-ridership in 2025, leading to a positive realization rate.
6.2.3 Effective Useful Life The Evaluator validated the EUL values based on the 2025 DSM MA. There were no adjustments made to the EUL values of reviewed 2025 projects.
AI summary The Evaluator confirmed the Effective Useful Life (EUL) values using the 2025 DSM MA without adjustments. No changes were made to EUL values for reviewed 2025 projects.
Final Savings Claimed for Single-Year Projects Total Number of Projects 9 9 Electrical Energy Savings Tracked Gross Electrical Energy Savings – at the Meter (GWh) 0.573 0.573 Adjustment Ratio for Electrical Energy Savings 1.000 1.000 Gross...
AI summary The table presents energy savings data from 9 single-year projects, including electrical energy and peak demand savings at both the meter and generator levels, along with adjustment ratios and line loss factors used in calculations.
Table 31: Evaluated 2025 Building Optimization Net Electrical Energy and Peak Demand Savings Final Savings Claimed for Single-year Projects Total Number of Projects 9 9 Electrical Energy Savings Gross Electrical Energy Savings – at the Met...
AI summary Table 31 presents the evaluated 2025 Building Optimization Net Electrical Energy and Peak Demand Savings. It includes metrics such as gross and net energy savings, line loss factors, and effective useful life for the projects evaluated.
6.4 Realization Rate A comparison of the electrical energy and peak demand savings values established through this evaluation and those tracked by E1 is presented in [Table](#page-99-2) 32 below. The table also includes the realization rat...
AI summary This section discusses the realization rate, which is the ratio of evaluated net savings to tracked net savings for both electrical energy and peak demand savings, as compared between the evaluation and E1 tracking.
Table 33: Comparison of 2025 Custom Tracked and Evaluated Savings at the Generator Gross Savings NTGR Net Savings Realization Rate Unit Value Value Value Unit Value Electrical Energy Savings Tracked Savings by E1 16.032 GWh 0.82 13.121 GWh...
AI summary Table 33 compares tracked and evaluated savings for energy and peak demand across various categories in 2025. It includes metrics such as Gross Savings, Net-to-Gross Ratios (NTGR), Net Savings, and Realization Rates for different programs and initiatives.
General Custom Key Findings and Recommendations 2025 Custom - Finding: Custom surpassed the net electrical energy and peak demand savings targets in 2025. Custom achieved 30.487 GWh in net electrical energy savings and 6.372 MW in net peak...
AI summary Custom exceeded 2025 energy savings targets (30.487 GWh and 6.372 MW) but saw reduced participation compared to 2024. Adjustments to savings metrics were applied, with free-ridership levels decreasing for Retrofit and New Construction. Evaluated savings were 8% higher than E1-tracked values.
9 SEM Overview This section describes the Strategic Energy Management (SEM) program component, follows up on past evaluation recommendations, and provides an overview of participation history.
AI summary This section outlines the Strategic Energy Management (SEM) program, addresses past evaluation recommendations, and summarizes participation history within the Nova Scotia regulatory context.
9.1 SEM Description SEM provides industrial and institutional participants with funding and support to implement energy management practices within their organizations. It also provides participants with energy management information syste...
AI summary Strategic Energy Management (SEM) supports industrial and institutional participants in implementing energy management practices through funding, EMIS implementation, and structured energy-saving actions. Eligibility requires resources, commitment, and collaboration with E1. Activities involve third-party service providers, with a focus on continuous improvement, training, and long-term energy performance.
Figure 7: 2025 SEM Participation Process Summary Eligibility Check, Memorandum of Understanding (MOU), and Kick-off Meeting - •Once approved, eligible participants must first sign a MOU that outlines the project scope, participant requirem...
AI summary The 2025 SEM Participation Process involves eligibility checks, MOUs, energy team formation, and performance-based incentives. Participants develop energy management plans, undergo savings verification, and receive incentives at $0.06/kWh (Large Industrial) or $0.04/kWh. The program aims for 2.657 GWh energy savings and 0.289 MW peak demand reduction.
9.2 Follow-up on Past Evaluation Report Recommendations The Evaluator evaluated SEM in previous years and issued improvement recommendations. Table 34 provides a summary of the implementation status of the recommendations presented in the...
AI summary The Evaluator reviewed the implementation of SEM improvement recommendations from the 2024 SEM evaluation report, with Table 34 summarizing the status of these recommendations.
10 SEM Evaluation Approach The 2025 SEM evaluation comprised a comprehensive impact evaluation. The main objectives of the SEM evaluation were as follows: › Calculate SEM gross and net results, namely electrical first-year and lifetime ene...
AI summary The 2025 SEM evaluation aims to calculate gross and net results, including energy savings, peak demand savings, and avoided GHG emissions. The Evaluator identified key research questions and methods to achieve these objectives, with Table 35 outlining the evaluation objectives, research questions, methods, and sample sizes.
11 SEM Impact Evaluation The objectives of the 2025 SEM comprehensive impact evaluation were to determine project gross and net electrical energy and peak demand savings as well as annually avoided GHG emissions, EUL values, and associated...
AI summary The 2025 SEM comprehensive impact evaluation aimed to assess gross and net electrical energy savings, peak demand reductions, annual GHG emission avoidance, EUL values, and lifetime energy savings. The evaluation focuses on quantifying the program's effectiveness in achieving energy efficiency and emission reduction targets.
11.2 Gross Savings For SEM, gross savings correspond to the change in energy consumption resulting from actions taken by participants regardless of their reasons for participating.[28](#page-110-4) The subsections below provide a descripti...
AI summary The section defines gross savings for Strategic Energy Management (SEM) as energy consumption changes from participant actions. It outlines the methodology for reviewing 18 SEM measures generating savings in 2025, including assessments of interactive effects, Effective Useful Life (EUL) values, and revised electrical savings.
11.2.1 Project Review Findings The Evaluator reviewed the calculation methodologies for the 18 SEM measures based on project documentation and information from interviews with participants (where required) and the Service Provider. All exc...
AI summary The Evaluator reviewed 18 SEM measures' M&V methodologies, finding most approaches thorough and aligned with best practices. Bottom-up and top-down methods were used appropriately depending on context. Adjustments were made to seven measures, with specific attention to compressed air leak quantification using submetering or ultrasonic detectors. Overall, methodologies were deemed reasonable despite practical limitations in testing.
Compressed Air Leak Repair Measures The Evaluator reviewed six compressed air leak measures with one measure receiving a downward adjustment to both the electrical energy and peak demand savings. In this case, the compressor efficiency was...
AI summary The Evaluator assessed six compressed air leak repair measures, adjusting one downward due to mixed data in compressor efficiency calculations. A bin analysis using metered data was identified as a more conservative method for estimating savings.
Equipment Upgrade Measures Six of the measures reviewed by the Evaluator involved equipment upgrades. Of these measures, the Evaluator made downward adjustments to the electrical energy savings claimed for three measures and downward adjus...
AI summary The Evaluator reviewed six equipment upgrade measures, adjusting downward electrical energy savings for three and peak demand savings for two. Adjustments were based on updated efficiency, operating hours, or production data from site visits and interviews, while agreeing with the overall methodology.
Automated Controls Measures There were five measures with claimed electrical energy savings that fell under the automated controls measure category. Of these measures, three received adjustments to electrical energy savings (two upward adj...
AI summary Five automated controls measures with claimed energy savings were evaluated. Three received adjustments to electrical savings (two upward, one downward), and one received an upward peak demand adjustment. The Evaluator agreed with the methodology but made minor corrections, including power formula updates and revised operating hours. One project's peak demand savings were recalculated after initial nil reporting.
Permanent Shutdown There was one measure with claimed savings that fell under the permanent shutdown measure category. The Evaluator agrees with the methodology used to calculate the savings and, as such, made no adjustments to the electri...
AI summary The text discusses a measure under the permanent shutdown category, where the Evaluator approved the methodology for calculating savings, resulting in adjustment ratios of 0.953 for gross electrical energy and 0.884 for net peak demand savings.
11.4 Realization Rate A comparison of the electrical energy and peak demand savings established through this evaluation and those tracked by E1 is presented in [Table](#page-114-3) 38 below. The table also includes the realization rate, re...
AI summary This section discusses the realization rate, which is the ratio of evaluated net savings to tracked net savings for both electrical energy and peak demand savings, as compared between the evaluation and E1 tracking in Table 38.
Gross Savings NTGR Net Savings Realization Rate Value Unit Value Value Unit Value Electrical Energy Savings Tracked Savings by E1 4.228 GWh 1.00 4.228 GWh Evaluation Results 4.031 GWh 1.00 4.031 GWh 95% Peak Demand Savings Tracked Savings...
AI summary The table compares tracked and evaluated savings from the Strategic Energy Management (SEM) program in 2025. It shows gross and net savings for both electrical energy and peak demand, along with realization rates for the evaluated savings.
12 SEM Key Findings and Recommendations As mentioned previously, the main objectives of the 2025 SEM evaluation were as follows: › Calculate SEM gross and net results, namely electrical first-year and lifetime electrical energy savings, pe...
AI summary The 2025 SEM evaluation found that SEM exceeded net electrical energy and peak demand savings targets, with 4.031 GWh and 0.372 MW achieved, respectively. Participation levels rose to the highest since 2018, though energy savings per participant dropped by 43% compared to 2024. M&V methodologies were deemed generally appropriate and accurate.
Table 39: Overall 2025 Custom Incentives Participation and Evaluated Savings Particip ation Level Gross Savings NTGR Net S avings Value Unit Value Unit Value Unit Value Custom Electrical Energy Savings 36.207 GWh 0.84 30.487 GWh Lifetime E...
AI summary Table 39 presents the 2025 participation and evaluated savings for Custom Incentives, including electrical energy savings, peak demand savings, and GHG emission reductions. The program exceeded its targets for net electrical energy and peak demand savings, with Custom being the largest contributor to total program savings.
SEM APPENDIX XIV SEM Tracking Sheet Audit APPENDIX XV SEM Project Review Protocol APPENDIX XVI SEM Detailed Project Review Adjustments APPENDIX XVII SEM 2025 Recommendations 2475, Laurier boul., Suite 250 Quebec City, QC G1T 1C4 Canada Tel...
AI summary The document includes appendices related to Strategic Energy Management (SEM), covering tracking sheet audits, project review protocols, detailed adjustments, and 2025 recommendations. It also contains contact information for an organization in Quebec City, Canada.
Introduction I am with _____ and we are conducting an evaluation of the Custom Retrofit program offered by Efficiency Nova Scotia. This interview could take up to 30 minutes. Is this still a good time for you? We would like to better under...
AI summary The interview aims to evaluate Efficiency Nova Scotia's Custom Retrofit program by understanding decision-making processes for energy efficiency projects, ensuring confidentiality of responses, and aggregating results without affecting incentives.
C5. [ASK IF $ ≥0] As part of its Custom Retrofit program, Efficiency Nova Scotia provided your organization a $ incentive for the [Investigation or Feasibility] study. If this incentive had not been offered, would you have definitely, prob...
AI summary Efficiency Nova Scotia's Custom Retrofit program offers incentives for energy efficiency studies and implementation. The text asks respondents whether these incentives were necessary for conducting studies or implementing projects, and whether studies influenced project planning.
Factor [READ AND RANDOMIZE] Responses a. The program financial incentive for the [Investigation or Feasibility Study]. Response 98 Don't Know Refused b. The program financial incentive for the implementation of the energy efficiency measur...
AI summary The text presents a series of questions related to energy efficiency programs and responses indicating a lack of knowledge or refusal to answer. The topics include program financial incentives, energy savings information, and technical and non-technical support provided by Efficiency Nova Scotia staff and the Onsite Energy Manager (OEM).
E. Spillover - E1. Since taking part in the Custom Retrofit program, have you implemented any additional energy efficiency measures outside of the program? - 1. Yes - 2. No [GO TO SECTION F] - 98. Don't know [GO TO SECTION F] - 99. Refused...
AI summary The 'Spillover' section investigates whether participants in the Custom Retrofit program implemented additional energy efficiency measures outside the program, their financing sources, measure details, influence of the program on their decisions, and reasons for not using Efficiency Nova Scotia programs.
F. Program satisfaction - F1. On a scale from 1 to 10 (where 1 = not at all satisfied and 10 = very satisfied) … - a. how would you rate your satisfaction with each of the following aspects of the Custom Retrofit program?
AI summary This section asks participants to rate their satisfaction with the Custom Retrofit program on a scale from 1 to 10, where 1 is 'not at all satisfied' and 10 is 'very satisfied'.
APPENDIX III Retrofit and Pay-for-Performance Algorithm for Free-Ridership Calculation Question Answer Score incentive from Efficiency Nova Scotia? [READ] 4) Not at all confident 100% 98/99) Don't know/Refused 50% Planning Score C1 Cost Ef...
AI summary The text discusses a survey regarding incentives provided by Efficiency Nova Scotia, including rebate amounts for studies and project implementations, and how these incentives impacted the payback period for projects. Respondents were asked to evaluate the significance of the financial impact.
Cross-Influence Question Answer Score Cross-Influence 1) Yes, Custom Retrofit Before participating in the Custom Retrofit program for this project, had your 2) Yes, in another Efficiency Nova Scotia program To determine if participants D1...
AI summary The document presents a survey assessing the influence of Efficiency Nova Scotia programs on participants' decisions regarding energy efficiency projects. It includes questions about prior program participation, the impact of promotional materials, and whether participants sought technical advice or evaluated cost-effectiveness.
APPENDIX IV Retrofit and Pay-for-Performance Algorithm for Participant Spillover Calculation Current Algorithm Question Answer Score Since first taking part in the Custom 1) Yes CONTINUE E1 Retrofit program, have you implemented any additi...
AI summary This appendix outlines an algorithm to calculate spillover effects from the Custom Retrofit program, focusing on participant behavior and additional energy efficiency measures implemented outside the program. It includes questions to assess influence and quantify savings.
Table 1. 2025 Retrofit Corrected Tracked Savings Program Component Result Tracked by E1 Corrected Tracked Value Relative Difference Value Unit Value Unit Gross Electrical Energy Savings – at the Generator 16.032 GWh 16.032 GWh 0.00% Gross...
AI summary The tables present corrected tracked savings for various energy efficiency programs in 2025, showing no differences between tracked and corrected tracked values for electrical energy and peak demand savings across multiple programs.
ECONOL ≣I R Efficency Nova Scotia On-Site Visit Protocol - 2025 Écrire questions en rouge (pour interview) et les notes en noir Notes during/after interview A On site on Vintual Deviana 5. Other questionnaires Market questionnaire filled-i...
AI summary The text outlines a protocol for an on-site visit by Efficiency Nova Scotia in 2025, including sections for filling out various questionnaires and estimating the useful life of energy efficiency projects. It also includes sections for energy and demand savings adjustments by measure.
Savings calculation approach - Projects with M&V 5. Are the M&V boundaries capturing all the energy consumption that's impacted by the project? (Y/N) 7. Are M&V results measured in a short period extrapolated to annual results appropriatel...
AI summary The document outlines a structured approach for evaluating energy savings calculations using Measurement and Verification (M&V) methods, including questions about M&V boundaries, extrapolation of results, regression validity, and the impact of external factors like COVID-19 on savings calculations. It also includes sections on peak demand savings and interactive effects.
iency Nova Scotia? - 1. Very confident - 2. Somewhat confident - 3. Not very confident - 4. Not at all confident - 98. I am unsure - 99. I prefer not to say - I4. [SINGLE RESPONSE] Which one of the following best represents the impact of t...
AI summary The text presents survey questions assessing the impact of Efficiency Nova Scotia's financial incentives on building projects, focusing on budget adherence, financial justification, and likelihood of hiring energy modeling consultants. Respondents are asked about confidence levels and the influence of incentives on project decisions.
J. Cross-Influence - J1. [SINGLE RESPONSE] Before participating in the Custom New Construction program for the [INSERT PROJECT NAME] project, had your organization already participated in Custom New Construction or in another Efficiency No...
AI summary The text outlines survey questions assessing cross-influence of Efficiency Nova Scotia programs on new construction projects. It asks about prior program participation, technical staff engagement, cost-effectiveness evaluation, and the impact of promotional materials on building decisions.
EAD; FOR CALCULATION ONLY: SCORE = 25%] - 4. Definitely would not have [DO NOT READ; FOR CALCULATION ONLY: SCORE = 0%] - 98. Don't know - 99. Refused - B11. [IF B7 = 2 AND IF AVERAGE (B8,B9,B10) ≥ 75% ] You mentioned that, without the ince...
AI summary The text asks respondents to describe how their building design would differ without incentives from Efficiency Nova Scotia or the energy modeler's expertise, highlighting the role of energy efficiency programs in influencing building design decisions.
C. Cross-Influence - C1. Before participating in the Custom New Construction program for the building we discussed today, had you previously taken part in Custom New Construction this program or in another Efficiency Nova Scotia program? -...
AI summary The text presents survey questions assessing whether past participation in Efficiency Nova Scotia's programs or exposure to promotional materials influenced current decisions in new construction projects, focusing on cross-influence and program effectiveness.
Table 1: Participant Interview Questionnaire and Free-ridership Algorithm Question Answer Score D4 Before participating in the Custom New Construction program service, had you had seen energy efficiency promotional materials distributed by...
AI summary The table outlines a questionnaire used to assess participant engagement with energy efficiency promotional materials from Efficiency Nova Scotia, focusing on whether these materials influenced decisions related to building energy efficiency.
Table 1: 2024 Custom Corrected Tracked Savings Program Component Result Tracked by E1 Corrected Tracked Value Relative Difference Value Unit Value Unit Gross Electrical Energy Savings – at the Generator 18.713 GWh 18.713 GWh 0.00% Gross Pe...
AI summary Table 1 presents the 2024 Custom Corrected Tracked Savings for various program components, showing no differences between tracked and corrected tracked values for gross and net electrical energy and peak demand savings at the generator level.
APPENDIX XV SEM Project Review Protocol The SEM project review protocol used for the 2025 evaluation was the same protocol used in 2024. It includes sections that served to review both the bottom-up and top-down approaches used in the 2025...
AI summary The SEM Project Review Protocol for 2025 mirrors the 2024 approach, incorporating bottom-up and top-down evaluations. Methods include phone interviews and site visits based on E1 digital files, with a 2023-estimated net-to-gross ratio (NTGR) of 1.00 applied to the DSM cycle.
APPENDIX XVI SEM Detailed Project Review Adjustments = = Strategic Energy Management Efficiency Nova Scotia ECONOL≣R Project Review Protocol 1. General Information Interview/Site Visit Date: Project ID: NSPI Rate Code: Company Name: Addres...
AI summary This document outlines the SEM Detailed Project Review Adjustments, focusing on Strategic Energy Management in Nova Scotia. It includes sections for general information, participation history, and impact evaluation, with a bottom-up approach to measure energy savings and validate implemented measures.
DIRECT INSTALLATION PROGRAM Final Report 2025 DSM EVALUATION March 12, 2026
AI summary The Final Report for the 2025 Demand-Side Management (DSM) Evaluation of the Direct Installation Program, dated March 12, 2026, assesses the program's outcomes and compliance with regulatory goals. It focuses on evaluating the effectiveness of direct installation initiatives under DSM frameworks.
EXECUTIVE SUMMARY This report presents the 2025 demand-side management (DSM) results of the Direct Installation program administered by EfficiencyOne (E1). This program is comprised of the Small Business Energy Solutions (SBES) program com...
AI summary This report outlines the 2025 demand-side management (DSM) results for EfficiencyOne's Direct Installation program, which includes the Small Business Energy Solutions (SBES) component. SBES provides incentives and resources to Nova Scotia small businesses for implementing energy efficiency upgrades.
Table 2: Overall 2025 Direct Installation Participation and Evaluated Savings Participation Level Gross Savings NTGR Net Savings Value Unit Value Unit Value Value Unit Electrical Energy Savings Units 9.774 GWh 0.80 7.862 GWh Lifetime Elect...
AI summary Table 2 summarizes the 2025 Direct Installation program's participation and savings, showing that it fell short of its electrical energy and peak demand savings targets by 38% and 46% respectively. The program achieved 7.862 GWh in net electrical energy savings and 1.414 MW in net peak demand savings.
SBES Findings and Recommendations This subsection presents the key findings from the 2025 SBES evaluation. 2025 SBES-Finding: SBES fell short of the net electrical energy savings and net peak demand savings targets by 38% and 46% respectiv...
AI summary The 2025 SBES evaluation found that the program missed its net electrical energy and peak demand savings targets by 38% and 46%, respectively. Participation increased slightly (1%) compared to 2024, with DIY rebates accounting for 99% of all units rebated. Evaluated savings were slightly lower than E1-tracked savings.
Table 3: Comparison of 2025 SBES Tracked and Evaluated Savings at the Generator Gross Savings Net Savings Realization Value Unit NTGR Value Unit Rate Electrical Energy Savings Tracked Savings by E1 9.805 GWh 0.80 7.886 GWh 100% Evaluation...
AI summary Table 3 compares the tracked and evaluated savings from the 2025 SBES (Small Business Energy Solutions) program, showing gross and net savings in electrical energy and peak demand, along with realization rates and net-to-gross ratios (NTGR).
EfficiencyOne (E1), an independent, non-profit organization, is responsible for helping Nova Scotians improve the energy efficiency of their homes and workplaces by designing, marketing, and delivering demand-side management (DSM) for Nova...
AI summary EfficiencyOne (E1) is an independent, non-profit organization that delivers demand-side management (DSM) programs through the Efficiency Nova Scotia (ENS) franchise. E1's 2025 DSM program portfolio includes a Direct Installation program component, Small Business Energy Solutions (SBES), which was evaluated using a condensed impact evaluation method.
Table 4: Type of Evaluation Conducted for SBES, 2025 Program 2025 Program Component Process Market Impact Direct Installation SBES - - Condensed For each program, the Evaluator prepared a DSM evaluation report presenting key findings, elec...
AI summary Table 4 outlines the type of evaluation conducted for the Small Business Energy Solutions (SBES) program in 2025, focusing on direct installation. The Evaluator prepared a DSM evaluation report that includes key findings, first-year and lifetime energy savings, peak demand savings, and avoided greenhouse gas emissions.
Table 6: 2025 SBES Evaluation Approach Evaluation Objectives Research Questions Methodology Calculate gross results › Are the data in the tracking sheet complete, accurate, and consistent? › What are the average interactive effect factors,...
AI summary Table 6 outlines the 2025 SBES Evaluation Approach, focusing on calculating gross and net results through tracking sheet audits, adjustment ratios, and GHG emission reduction calculations. It addresses research questions related to data accuracy, interactive effects, and the application of baseline methodologies.
3.2.1 Unitary Energy Savings and Peak Demand Savings Savings for SBES Audit and DIY projects are established through calculations using data specific to each project. The 2025 Demand-side Management Measure Assessment (DSM MA) [8](#page-11...
AI summary Savings for SBES Audit and DIY projects are calculated using project-specific data. The 2025 DSM MA provides detailed methodologies for unitary energy and peak demand savings calculations across measure categories.
3.2.2 Installation Rates Installation rates are accounted for in the adjustment ratios for SBES Audit and DIY projects, as documented in the 2025 DSM MA.
AI summary The document discusses how installation rates are factored into adjustment ratios for SBES Audit and DIY projects under the 2025 DSM MA, highlighting their role in program evaluation and cost adjustments.
3.2.3 Interactive Effects Interactive effects occur when the implementation of energy efficiency measures has an impact on the energy consumption of other elements such as heating and cooling. For the SBES Audit and DIY paths, these are ta...
AI summary Interactive effects in energy efficiency measures impact heating/cooling systems. The E1 CIRx Screening Tool and 2025 DSM MA calculate savings, adjusting factors for recessed fixtures (LED linear) by 57%. Evaluations ensure accurate interactive effects factors are applied, with adjustments included in 2023/2025 adjustment ratios.
3.2.4 Effective Useful Life As part of the 2025 DSM MA activities, the Evaluator reviewed the EUL values used in the calculation of electrical energy savings that are expected to persist over time. The EUL values established in previous ev...
AI summary The Evaluator reviewed Effective Useful Life (EUL) values for specific LED measures as part of the 2025 DSM MA, noting changes in baseline expectations over time. Only modified EUL values are presented in Table 7.
Table 8: Evaluated 2025 SBES Gross Electrical Energy and Peak Demand Savings – Audit Path Category of Measure Agriculture Commercial Kitchen HVAC Laundry Lighting Refrigeration Total for All Categories Electrical Energy Savings Gross Elect...
AI summary Table 8 provides an evaluation of the 2025 SBES (Small Business Energy Solutions) gross electrical energy and peak demand savings using an audit path. It includes data on energy savings across various categories, adjustment ratios, interactive effects, line loss factors, and effective useful life of measures.
Table 9: Evaluated 2025 SBES Gross Electrical Energy and Peak Demand Savings – DIY Path Category of Measure Agriculture Commercial Kitchen HVAC Laundry Lighting Motor Refrigeration Envelope Total for all Categories Energy Savings Gross Ele...
AI summary Table 9 and Table 10 evaluate the 2025 SBES gross electrical energy and peak demand savings for the DIY path and both paths combined. The tables include metrics such as energy savings, adjustment ratios, line loss factors, and effective useful life. Evaluated gross savings differ slightly from tracked values due to corrections in interactive effects factors.
Table 14: Evaluated 2025 SBES Net Electrical Energy and Peak Demand Savings Measure Category Audit Path DIY Path Total Electrical Energy Savings Gross Electrical Energy Savings – at the Meter (GWh) 0.274 8.866 9.140 NTGR 0.88 0.80 - Net El...
AI summary Table 14 evaluates the 2025 SBES net electrical energy and peak demand savings, showing that SBES fell short of its energy savings target by 38% and its peak demand savings target by 46%. The table includes metrics such as gross and net electrical energy savings, line loss factors, and effective useful life.
3.4 Realization Rate [Table](#page-20-0) 15 below compares the tracked electrical energy and peak demand savings values established through this evaluation to those calculated in the 2025 tracking sheet. It also includes the realization ra...
AI summary Table 15 compares tracked electrical energy and peak demand savings values from the current evaluation to those in the 2025 tracking sheet, including the realization rate, which is the ratio of evaluated net savings to tracked net savings for both energy and peak demand.
Table 15: Comparison of 2025 SBES Tracked and Evaluated Savings at the Generator Gross Savings Net Savings Realization Value Unit NTGR Value Unit Rate Electrical Energy Savings Tracked Savings by E1 9.805 GWh 0.80 7.886 GWh 100% Evaluation...
AI summary Table 15 compares the tracked and evaluated savings from the 2025 SBES program. Evaluated net electrical energy savings were slightly lower (0.3%) than tracked values, while net peak demand savings were 1.0% higher. Minor differences are attributed to corrections in interactive effect factors made by the Evaluator.
4 SBES Key Findings and Recommendations The main objectives of the 2025 SBES evaluation were as follows: › Calculate gross and net electrical energy and peak demand savings, annually avoided GHG emissions, as well as EUL values and associa...
AI summary The 2025 SBES evaluation found that the program missed its net electrical energy and peak demand savings targets by 38% and 46%, respectively. Evaluated savings were slightly lower than E1's tracked values for energy but higher for peak demand. Participation increased by 1% compared to 2024, with DIY rebates dominating.
CONCLUSION [Table](#page-22-0) 16 below summarizes the participation level, net-to-gross ratios (NTGRs), evaluated gross and net savings at the generator, annual GHG emission reductions, as well as EUL values for Direct Installation as a w...
AI summary The conclusion section references a table summarizing participation levels, net-to-gross ratios, evaluated gross and net savings, annual GHG emission reductions, and EUL values for Direct Installation programs.
Table 16: Overall 2025 Direct Installation Participation and Evaluated Savings Participation Level Gross Savings NTGR Net Savings Value Unit Value Unit Value Value Unit SBES Electrical Energy Savings 62,011 Units 9.774 GWh 0.80 7.862 GWh L...
AI summary Table 16 presents the 2025 Direct Installation participation and evaluated savings under the SBES program. The program fell significantly short of its energy savings and peak demand targets, with a 38% shortfall in net electrical energy savings and a 46% shortfall in net peak demand savings.
DEMAND RESPONSE PROGRAM Final Report 2025 DSM EVALUATION March 20, 2026
AI summary The document presents the Final Report of the 2025 Demand-Side Management (DSM) Evaluation, focusing on the Demand Response (DR) Program. It assesses the program's effectiveness, cost-efficiency, and alignment with Nova Scotia's energy goals, likely including recommendations for improvement.
Evaluation Approach The 2025 evaluation was aimed at calculating program component results, namely new and total available DR capacity. [Table](#page-40-0) 1 summarizes the types of evaluation conducted for each program component and the c...
AI summary The 2025 evaluation focused on calculating program component results, specifically new and total available DR capacity, with Table 1 outlining the types of evaluation and corresponding methodology for each program component.
Table 1: Summary of 2025 Demand Response Program Evaluation Evaluation Type Methodology Program Component Process Market Impact Residential Demand Response X Comprehensive › Non-participant survey › Program staff interviews › Service provi...
AI summary The document outlines the evaluation of the 2025 Demand Response Program, including the Residential Demand Response and BNI Demand Response components. It describes the evaluation methodology, which includes surveys, interviews, audits, and data analysis, and references Table 2 for participation levels and available DR capacity.
Table 2: Overall 2025 Demand Response Participation and Evaluated Results Participation Level Evaluated Results Value Unit Value Unit Residential DR Available DR Capacity 3,676 Participants 0.854 MW BNI DR Available DR Capacity 143 Partici...
AI summary In 2025, the Demand Response (DR) program aimed to achieve 17.861 MW in available DR capacity but fell short. Residential DR and BNI DR did not meet their targets, though BNI DR remained the largest contributor with 5.941 MW of available DR capacity.
Residential DR Findings and Recommendations This subsection presents the key findings and recommendations from the 2025 Residential DR evaluation. The recommendations are also outlined in Appendix VII. 2025 Res DR-Finding: Residential DR o...
AI summary The 2025 Residential DR evaluation highlights a diverse mix of eligible devices, integration of pathways into 'Eco Shift,' program design updates, and documentation issues blending with BNI DR. Service providers report smooth operations and positive collaboration with E1, but slower growth is expected due to testing needs.
BNI DR Findings and Recommendations This subsection presents the key findings and recommendations from the 2025 BNI DR evaluation. 2025 BNI DR - Finding: In 2025, BNI DR available DR capacity at the generator amounted to 5.941 MW. Therefor...
AI summary The 2025 BNI DR evaluation found that available DR capacity (5.941 MW) fell short of the 10.726 MW target. Morning events generated higher capacity than evening ones, and while participation increased by 88%, capacity per participant dropped from 106 kW to 42 kW due to non-participation. Recommendations include process evaluations in 2026 and project reviews to improve accuracy and savings tracking.
Table 3: Comparison of 2025 Demand Response Tracked and Evaluated Available DR Capacity at the Generator Available DR Capacity Realization Value Unit Rate Residential DR Available DR Capacity Tracked by E1 0.540 MW 158% Evaluation Results...
AI summary Table 3 compares the tracked and evaluated available demand response (DR) capacity for residential and BNI DR programs in 2025. The table shows that residential DR capacity is 0.540 MW (tracked by E1) with a realization rate of 158%, and BNI DR capacity is 6.648 MW (tracked by E1) with a realization rate of 89%.
1.1 Residential DR Description In 2023, E1 officially launched Residential DR. Since the fall of 2020, E1 has implemented several initiatives focused on reducing demand during the Nova Scotia peak period. The Residential DR program compone...
AI summary The Residential Demand Response (DR) program in Nova Scotia, launched by E1 in 2023, offers four pathways for participants to reduce demand during peak periods. Eligibility criteria, incentives, and technical implementation details are outlined, including the role of EPI, Virtual Peaker, and Shifted Energy in program execution.
Table 6: Residential DR 2024/25 Event Summary Event # Date Start Time Duration (Hours) Outdoor Temperature at Event Start (°C) 1 12-04-2024 5 p.m. 4 -3 2 12-20-2024 7 a.m. 4 -3 3 12-23-2024 5 p.m. 4 -8 4 01-21-2025 5 p.m. 4 -8 5 01-22-2025...
AI summary Table 6 summarizes Residential Demand Response (DR) events in 2024/25, including dates, times, durations, and outdoor temperatures at event starts. It differentiates between enrolled and participating devices, with enrolled devices being ready for control but not necessarily controlled during events.
1.2 Follow-up on Past Evaluation Report Recommendations The Evaluator evaluated Residential DR in 2023 and 2024 and issued improvement recommendations. [Table](#page-49-2) 7 below outlines the status of those recommendations that were carr...
AI summary The Evaluator assessed Residential Demand Response in 2023 and 2024 and issued improvement recommendations. The status of those recommendations that were carried forward is outlined in Table 7.
Table 7: Implementation Status of Past Recommendations for Residential DR # Recommendation Status Comments 2023 – Res DR-R1 Ensure that available DR capacity tracked by E1 includes the in service rate as well as the unitary available DR ca...
AI summary This table outlines the implementation status of past recommendations for Residential Demand Response (DR). Two recommendations from 2023 and 2024 have been completed, with E1 agreeing to track in-service rates and unitary available DR capacity values and to re-analyze Eco Shift Pilot data to improve accuracy and consistency.
For Residential DR, participation is defined as the number of households participating in each technology pathway. Therefore, a household participating in both the Smart Thermostat DLC and EV Telematic and Charger Control pathways would co...
AI summary The document discusses the participation in Residential Demand Response (DR) programs during the 2024/25 season, noting a significant increase in participants and enrolled devices. Smart thermostats are the most common enrolled device, but not all enrolled devices participated in each event due to connectivity and availability issues.
Table 8: Residential DR Device Enrollment Throughout the 2024/25 DR Season Number of Devices Enrolled per Event Event # Event Date Smart Thermostats DHW Controllers EV Telematic and Charger Controls Battery Control Total 1 12-04-2024 3,066...
AI summary Table 8 outlines the number of residential demand response (DR) devices enrolled during the 2024/25 DR season, including smart thermostats, domestic hot water (DHW) controllers, EV telematic and charger controls, and battery controls. DHW controllers were not counted as enrolled until after the third event due to initial issues.
2 Residential DR Evaluation Approach The 2025 Residential DR evaluation consisted of a comprehensive impact evaluation and a process evaluation. The main objectives of the overall 2025 Residential DR evaluation were as follows: - › Collect...
AI summary The 2025 Residential DR evaluation involved a comprehensive impact and process evaluation with objectives to collect feedback on participation and calculate new and total available DR capacities. Research questions, methods, and sample sizes were outlined in Table 9.
Table 9: 2025 Residential DR Evaluation Approach Evaluation Objectives Research Questions Methodology Collect feedback from program staff, service providers, other jurisdictions, and non participants on increasing/maintaining participation...
AI summary Table 9 outlines the 2025 Residential Demand Response (DR) Evaluation Approach. It includes objectives, research questions, and methodology to evaluate the program, focusing on feedback from non-participants, program awareness, barriers to participation, and operational improvements.
Tracking Sheet Audit Prior to performing the available DR capacity calculation review, the Evaluator audited the final 2025 tracking sheet to ensure it was complete and the entered data were consistent. The results obtained are presented i...
AI summary The Evaluator audited the final 2025 tracking sheet to verify completeness and data consistency prior to reviewing DR capacity calculations, with results detailed in Appendix IV.
Metering Data Analysis To establish the available DR capacity generated from smart thermostats, the Evaluator updated the unitary available DR capacity using the same metering data analysis methodology as the previous evaluation. The Evalu...
AI summary The Evaluator used whole-house data for smart thermostats due to interactive effects, while device-level data were used for DHW controllers, EV telematics, and battery control. Reliance on 2023 Residential DR evaluation data for DHW and a new 2025 in-service rate due to implementation issues were noted. Methodologies are detailed in Subsection 4.2.2.
Calculations Using Evaluation Results Building on all the above methods and collected data, the Evaluator calculated the amount of available DR capacity as per the calculation methodology presented in Section [4](#page-82-0) below.
AI summary The Evaluator calculated available DR capacity using a methodology outlined in Section 4, based on collected data and prior evaluation methods.
3.3.1 Non-participant Recruitment To gather feedback from the non-participant perspective, the Evaluator conducted a survey among Efficient Product Installation (EPI) participants who received a smart thermostat in 2024 but who had not enr...
AI summary The Evaluator conducted a survey of Efficient Product Installation (EPI) participants who received smart thermostats but did not enroll in Residential DR. Challenges in linking EPI and Residential DR data hindered precise identification of non-participants. 66% of respondents confirmed their thermostats were not enrolled, 20% were enrolled, and 15% were unsure. The analysis focused on non-participants (n=103), excluding those who enrolled (n=25).
3.3.2 Level and Sources of Program Awareness Among Non-participants
AI summary This section examines the awareness levels and sources of information about energy efficiency programs among non-participants in Nova Scotia. It likely explores outreach effectiveness, barriers to participation, and the role of existing programs in informing residents and businesses.
3.4.1 Enrollment and Participation Challenges Among Non-participants
AI summary This section addresses challenges related to enrollment and participation in energy efficiency programs among non-participants, focusing on barriers to involvement and potential strategies for improvement.
Additional Information Required to Reconsider Enrollment Non-participants also shared the additional information they would need to reconsider enrollment in Residential DR, with nine indicating that they would like more information overall...
AI summary Non-participants expressed a desire for more information to reconsider Residential DR enrollment, citing confusion and a preference for manual heating control. EPI applies a 2024 installation rate to thermostat savings for a small subset of non-users.
Smart Thermostat DLC, Battery Control, EV Telematic and Charger Control Pathway CLEAResult is responsible for the Smart Thermostat DLC, Battery Control, and EV Telematic and Charger Control pathway program delivery. CLEAResult reports that...
AI summary CLEAResult manages Nova Scotia's Smart Thermostat DLC and EV control programs, reporting high retention (97%) in Residential DR but noting call centre inefficiencies, device connectivity issues, and participant confusion. Privacy concerns and lack of real-time feedback during DR events are highlighted, with recommendations to adjust incentives and improve education for better engagement.
3.6.1 Program Design The jurisdictional scan findings related to DR program aspects such as eligible devices, enrollment process, eligibility criteria, and incentive structure levels are highlighted in this section and organized by device...
AI summary This section outlines jurisdictional scan findings related to Demand Response (DR) program design, focusing on eligible devices, enrollment processes, eligibility criteria, and incentive structures, organized by device type where applicable.
Eligible Devices The Evaluator compared products offered in the researched jurisdictions to those offered by E1. Similarly to E1, two jurisdictions (PSE and BC Hydro) offer DR programs for four device types, namely smart thermostats, elect...
AI summary The Evaluator compared eligible devices in DR programs across multiple jurisdictions, including PSE, BC Hydro, and others, to those offered by E1. The analysis shows that most jurisdictions include DR programs for smart thermostats, EVs, home batteries, and HWCs, with some exceptions.
Table 10: Types of Devices Included in DR Programs per Jurisdiction Program Administrator Smart Thermostats EV and EV Chargers Home Batteries Hot Water Controllers Efficiency Nova Scotia ✓ ✓ ✓ ✓ BC Hydro ✓ ✓ ✓ ✓ DTE Energy ✓ ✓ - ✓ Green Mo...
AI summary Table 10 lists the types of devices included in demand response (DR) programs across various jurisdictions, highlighting the participation of Efficiency Nova Scotia and other utility providers. The table includes categories such as smart thermostats, EV and EV chargers, home batteries, and hot water controllers.
All programs adopt a bring-your-own-device (BYOD) option requiring participants to own or purchase and install eligible smart devices to enroll. Hydro-Québec and Yukon Energy are the only jurisdictions combining both BYOD and direct instal...
AI summary The text discusses how DR programs in various jurisdictions offer participants options to enroll via bring-your-own-device (BYOD) or through energy efficiency programs that provide free or discounted devices. It also notes variations in enrollment processes, such as optional steps or device-type dependencies.
Table 11: DR Program Enrollment Pathways by Jurisdiction Program Administrator Is there a Complimentary Energy Efficiency Program Associated with DR? DR Enrollment Pathway via Energy Efficiency Program? Efficiency Nova Scotia √ (EPI: Free...
AI summary Table 11 outlines Demand Response (DR) program enrollment pathways by jurisdiction, including whether a complimentary energy efficiency program is associated with DR and the enrollment process. Efficiency Nova Scotia, BC Hydro, IESO, National Grid, PSE, and Rhode Island Energy are highlighted with their respective DR and energy efficiency program details.
Incentive Structure and Levels This section is organized by device type because the incentive structure and levels vary greatly between devices for most of the jurisdictions. For each subsection, incentives are organized by enrollment ince...
AI summary The incentive structure is organized by device type, with enrollment and participation incentives defined. Enrollment incentives are one-time benefits for joining programs, while participation incentives reward demand reduction or event participation. Comparisons across jurisdictions are complicated by regional differences in living and energy costs.
Enrollment Incentive As in Nova Scotia, all jurisdictions with an eligible smart thermostat DR program, except DTE Energy, offer incentives at enrollment. While E1 offers an incentive per device with a lower amount for additional devices e...
AI summary This section compares enrollment incentives for smart thermostat demand response (DR) programs across various jurisdictions, noting that most offer incentives at enrollment, with variations in amounts, customer types, and thermostat types. Yukon Energy provides rebates, and Hydro-Québec offers either per-device incentives or free thermostats.
Participation and Other Incentives Most jurisdictions, similar to E1, offer a fixed annual incentive per household, ranging from $20 for the IESO to $71 for DTE Energy. PSE and Rhode Island Energy both offer an amount per device, with PSE...
AI summary The text discusses various incentive structures for demand response (DR) programs across different jurisdictions, including fixed annual incentives per household, per-device incentives, and additional rewards such as gift cards and prize draws for participation in DR programs.
Table 12: Smart Thermostat Incentive Structures and Levels per Jurisdiction Program Administrator a Enrollment Incentive Participation Incentive Other Efficiency Nova Scotia $25 for the 1st device, $20/each additional oneb $30/household/ye...
AI summary Table 12 compares smart thermostat incentive structures and levels across various jurisdictions, highlighting differences in enrollment, participation, and other incentives offered by program administrators such as Efficiency Nova Scotia, BC Hydro, and others.
Participation Incentive and Other Recurring incentives for continued enrollment vary widely. They may be a fixed annual amount per device or household, a monthly payment, or a performance-based amount per kilowatt reduced during DR events....
AI summary Recurring incentives for participation in demand response (DR) programs vary by jurisdiction, with examples including fixed annual payments, monthly payments, or performance-based incentives. E1 offers a higher incentive ($50 per device) compared to Rhode Island and BC Hydro, which offer lower amounts. Hydro-Québec does not provide incentives but offers lower electricity rates during peak events.
Table 13: EV and EV Charger Incentive Structures and Levels per Jurisdiction Program Administratora Enrollment Incentive Participation Incentive Other Efficiency Nova Scotia $50/household $50/device/year - BC Hydro $250/household $50/house...
AI summary Table 13 outlines various EV and EV charger incentive structures and levels across different jurisdictions, including enrollment and participation incentives, as well as other program features. The table includes data from Efficiency Nova Scotia, BC Hydro, DTE Energy, Hydro-Québec, Puget Sound Energy, and Rhode Island Energy.
Participation Incentive All jurisdictions provide either a recurring seasonal incentive (per battery or per household) or a performancebased payment. In Vermont (Green Mountain Power), incentives vary by program type; for backup-only insta...
AI summary The document compares participation incentives for energy programs across different jurisdictions, noting varying rates such as Vermont's Green Mountain Power offering higher incentives than E1 but similar to National Grid and Rhode Island Energy.
Table 14: Home Battery Incentive Structures and Levels per Jurisdiction Program Administratora Enrollment Incentive Participation Incentive Efficiency Nova Scotia $500/household $300/average kW across all events BC Hydro $500/household $25...
AI summary Table 14 outlines home battery incentive structures and levels per jurisdiction, showing variations in enrollment and participation incentives across different program administrators in Canada and the US. The table highlights the differences in financial support provided by entities such as Efficiency Nova Scotia, BC Hydro, and others.
Participation Incentive Similarly to E1, only PSE and BC Hydro offer a recurring seasonal incentive of $28 and $50 respectively per household. Hydro-Québec and DTE Energy provide only preferred rates for water heaters, while Yukon Energy o...
AI summary The text compares participation incentives for demand response programs across different utilities, noting that PSE and BC Hydro offer recurring seasonal incentives, while others like Hydro-Québec and Yukon Energy provide limited or no incentives.
Table 15: Hot Water Controllers Incentive Structures and Levels per Jurisdiction Program Administratora Enrollment Incentive Participation Incentive Other Efficiency Nova Scotia - $20/device/year - BC Hydro $100/household $50/household/yea...
AI summary Table 15 compares hot water controller incentive structures across various jurisdictions, including enrollment and participation incentives, as well as additional benefits like discounted rates and gift cards.
3.6.2 Program Operations This section highlights the jurisdictional scan findings related to DR program aspects such as event design, internal and external resources, and program metrics.
AI summary This section outlines jurisdictional scan findings for Demand Response (DR) programs, focusing on event design, internal/external resource allocation, and program metrics as key operational aspects under review.
Event Design Event duration is fairly consistent across jurisdictions, typically ranging from three to four hours. In contrast, event frequency varies significantly by jurisdiction and device type. For smart thermostats, the lowest frequen...
AI summary Event duration is typically three to four hours across jurisdictions, but event frequency varies significantly by device type and region, with some programs reporting up to 200 events per year. These figures represent upper limits reported by utilities, and actual practice may differ based on operational needs and other factors.
Table 16: Event Frequency and Length per Jurisdiction Peak Period Program Smart Thermostats EVs and EV Chargers Home Batteries Hot Water Controllers Administrator # of Events Length # of Events Length # of Events Length # of Events Length...
AI summary Table 16 provides a comparison of event frequency and length per jurisdiction for various demand response (DR) programs, including smart thermostats, EVs and EV chargers, home batteries, and hot water controllers. The table lists administrators and the number of events and their maximum duration in different seasons.
Table 17: Participation Levels per Jurisdiction Program Administrator Smart Thermostats EVs and EV Chargers Home Batteries Hot Water Controllers Efficiency Nova Scotia 2025/26: 2,664 participating households and 9,886 enrolled devices 2025...
AI summary Table 17 presents participation levels in various energy programs across different jurisdictions, highlighting the number of households and devices enrolled in initiatives such as smart thermostats, EVs, home batteries, and hot water controllers.
Budget [Table](#page-76-0) 18 presents the budgets allocated to DR programs across jurisdictions where information was publicly available. Budgets are highly dependent on jurisdiction-specific operational needs and local economic condition...
AI summary The document provides a comparative analysis of DR program budgets across various jurisdictions, noting that budgets depend on local operational needs and economic conditions. The analysis includes Nova Scotia Power, Hydro Quebec, BC Hydro, and Ontario, but excludes Yukon due to its small population.
Table 18: Budget per Jurisdiction Program Administratora Budget Efficiency Nova Scotia 2025/26: $2.84 million BC Hydro Budget 2025-27: $110 million (DR programs for residential, commercial, and industrial customers) $12.8 M forecast for re...
AI summary Table 18 provides a comparison of energy efficiency and demand response program budgets across various jurisdictions, including Efficiency Nova Scotia, BC Hydro, DTE Energy, and others, with specific figures for 2024 and 2025-27.
Savings [Table](#page-77-1) 19 presents the savings targets of DR programs across jurisdictions where information was publicly available. Savings targets are highly dependent on jurisdiction specific system needs and demographic characteri...
AI summary Table 19 outlines the savings targets of demand response (DR) programs across various jurisdictions. These targets depend on specific system needs and demographic factors. Examples of DR programs include CoolCurrents, Smart Savers, and SmartCharge, which target summer and autumn peak demand.
Table 19: Savings per Jurisdiction Program Administratora Savings Efficiency Nova Scotia Actuals 2025: 0.958 MW (target: 7.135 MW) › Smart Thermostats Electric Baseboard (EBB) Only: 112 W/device › Smart Thermostats Mini-split Heat Pump (MS...
AI summary Table 19 provides a comparison of savings achieved by various demand response (DR) programs across different jurisdictions, including Efficiency Nova Scotia, BC Hydro, DTE Energy, and others. The data highlights actual and target savings in terms of MW and W/device for various DR program components such as smart thermostats, DHW controllers, EV telematics, and batteries.
3.7 In-depth Jurisdictional Perspectives To further explore the findings from the jurisdiction scan, two qualitative interviews were conducted with program managers from Canadian jurisdictions. These jurisdictions were selected because the...
AI summary The section discusses qualitative interviews with Canadian jurisdiction program managers to explore DR program design, operations, and best practices. The selected jurisdictions have similar device types to E1 and extensive DR experience, though their larger scale and vertical integration make some aspects non-comparable to E1.
Enrollment Process One interviewed Canadian program administrator offers two paths for smart thermostats to participate in DR events: behavioural and connected. The behavioural path[32](#page-78-2) allows participants to adjust their devic...
AI summary The text outlines enrollment processes for smart thermostats in Demand Response (DR) programs, highlighting two paths (behavioral and connected) and three enrollment methods (BYOD, OEM agreements, and retail purchases). It notes that behavioral options attract more customers by avoiding external control, with 75% of enrollments completed online and 90% via BYOD.
Marketing and Communications According to the first Canadian program manager interviewed, most jurisdictions tend to position their marketing messaging around incentives and rebates. They believe a more sophisticated approach would be usef...
AI summary The text discusses marketing strategies for demand response (DR) programs, emphasizing behavioral approaches and customer education. It highlights shifting from direct control requests to service offers and leveraging OEMs and cross-promotion for outreach, while stressing the importance of educating customers on variable rates and DR benefits.
3.7.3 Lessons Learned and Future Opportunities
AI summary This section outlines lessons learned from past initiatives and identifies future opportunities for energy efficiency and demand-side management programs in Nova Scotia, referencing programs like DSM, ARet, and CGH Grant, and considering factors such as affordability and technology adoption.
Technological Issues One Canadian program administrator interviewed continues to face challenges related to database management and data flows and shared that achieving operational efficiencies in a demand response program requires a conti...
AI summary The text highlights challenges in demand response (DR) program management, including database complexity and scaling from pilots to full programs. It notes that operational efficiencies require continuous improvement and that direct device connectivity and meter visibility reduce challenges for program administrators.
Behavioural Considerations With regards to EV Chargers, one program administrator mentioned that actual customer usage patterns differ significantly from initial assumptions regarding charging behaviour. Rather than consistently returning...
AI summary EV charging behavior differs from initial assumptions, with users charging less frequently but in higher volumes, reducing DR participation to 30%. Lower Level 2 charger penetration further limits DR potential. EV telematics is proposed as a solution to improve participation.
Future Opportunities According to one Canadian program manager, smart thermostats, being inexpensive and having energy efficiency benefits, is a promising category to develop in the next couple of years. To do so, they plan to work closely...
AI summary The document highlights opportunities to expand demand response (DR) programs through smart thermostats, emphasizing partnerships with manufacturers to streamline enrollment and address decision fatigue. Strategies include shifting from instant rebates to enrollment incentives and maximizing device installations during home visits by installers.
4.1 Tracking Sheet Audit To ensure program component results were reliably compiled, the Evaluator first performed a tracking sheet audit aimed at verifying the completeness and consistency of the data submitted by E1 as well as correcting...
AI summary The Evaluator conducted a tracking sheet audit to verify the completeness and consistency of data submitted by E1, correcting the tracked available DR capacity as needed. The results are detailed in Appendix IV, with the report referencing the corrected data.
Portion of the DR Season with Enrolled Devices New participants continued to register throughout the DR season. To account for these, the Evaluator calculated, when applicable, the portion of the DR season with enrolled devices by dividing...
AI summary The Evaluator calculated the portion of the DR season with enrolled devices by dividing the average number of enrolled devices by the number at season's end. This method applied to Smart Thermostat DLC and DHW DLC pathways, while other pathways used participation rates for similar metrics.
Participation Rate The participation rate captures all reasons enrolled devices did not participate. Indeed, participants can opt out of any event, not all EVs are connected to the grid during events, and connectivity issues can result in...
AI summary The participation rate reflects the proportion of enrolled devices that actually participate in demand response (DR) events. For Smart Thermostat DLC, opt-outs and connectivity issues do not affect the participation rate. However, for other pathways like Battery Control and EV Telematic, participation rates are low due to dispatching issues and lack of charging during events. Recommendations include using bidirectional chargers and conducting feasibility studies.
Table 20: Residential DR Participation Rates per 2024/25 Event DHW Controllers EV Telematics and Chargers Battery Controls Event # Event Date Number of Enrolled Devices Number of Participating Devices Participation Rate Number of Enrolled...
AI summary Table 20 shows residential demand response participation rates for various events in 2024/25, highlighting low participation in EV telematics and chargers and higher participation in battery controls. The weighted average participation rates are 22.5% for DHW controllers, 2.9% for EV telematics and chargers, and 63.2% for battery controls.
Metering Data Analysis Methodology This subsection provides a high-level description of the methodologies used to establish smart thermostat DLC, EV telematic and charger, and battery control unitary available DR capacities for the 2025 ev...
AI summary This subsection outlines methodologies for evaluating smart thermostat DLC, EV telematics and charger, and battery control unitary available DR capacities in the 2025 assessment, focusing on data analysis techniques for demand response (DR) capacity estimation.
EV Telematics and Chargers For EV telematics and chargers, the Evaluator used device-level data to establish consumption during and after DR events and calculate what would have been drawn from the grid during the events in the absence of...
AI summary The Evaluator used device-level data to calculate demand response (DR) capacity by analyzing EV charger consumption during and after DR events. Data was cleaned to remove duplicates, and hourly savings were calculated by comparing energy use during events with post-event consumption, assuming devices stopped charging during events. Non-responsive devices were excluded from the analysis.
Metering Data Analysis Results Using the methodologies presented above, the Evaluator established the DR capacity made available at each event hour of the 2024/25 DR season for each pathway. As mentioned in the introduction, available DR c...
AI summary The Evaluator analyzed DR capacity data from the 2024/25 DR season, identifying outliers such as Event 1 and Event 7 due to low participation and external factors like a snowstorm. Communication issues and thermostat settings also impacted DR capacity availability.
Table 21: 2024/25 Available DR Capacity per Participant per Event Available DR Capacity per Participant (W) Event # Event # Event Date Smart per Space EV Telematics Battery EBB Only MSHP Only EBB and MSHP Only Others and Chargers Controls...
AI summary Table 21 presents the 2024/25 available demand response (DR) capacity per participant per event, highlighting variations across different pathways such as Smart per Space, EV Telematics, and Battery Controls. The data shows average available DR capacity values, with some margins of error slightly above the typical 10% threshold. The Evaluator considers these acceptable for establishing 2025 results and E1 tracking for 2026 but notes the need for further analysis to ensure consistency year over year.
Unitary Available DR Capacity Whil[e Table](#page-87-0) 21 above outlines the average available DR capacity value per participant for each pathway and subgroup, this subsection presents other relevant metrics that were assessed by the Eval...
AI summary The text references Table 21, which outlines average demand response (DR) capacity values per participant across pathways and subgroups, while noting that this subsection addresses additional metrics evaluated by the Evaluator. The focus is on DR capacity assessments within regulatory proceedings.
Smart Thermostats For smart thermostats, the Evaluator established unitary available DR capacity per thermostat since this metric is better aligned with how participation is tracked. The household data included in the metering analysis wer...
AI summary The Evaluator determined unitary available DR capacity per smart thermostat, using household data to calculate average numbers per household and dividing average DR capacity by this figure. This metric was used to calculate the 2025 evaluated available DR capacity for the Smart Thermostat DLC pathway.
Table 22: 2024/25 Available DR Capacity per Thermostat EBB Only MSHP Only EBB and MSHP Only Others Average Available DR Capacity Per Participant, Excluding Outliers (W/Participant) 581 226 518 426 Average Number of Smart Thermostats per Pa...
AI summary Table 22 presents the 2024/25 available demand response (DR) capacity per thermostat across different participant categories. The Evaluator recommends using the values from this table to track DR capacity for 2026 and conducting further analysis in future years based on AMI data availability.
EV Telematics and Chargers The Evaluator established a unitary available DR capacity value per EV device since this metric is aligned with how participation is tracked. The calculated total available DR capacity was divided by the number o...
AI summary The Evaluator established a unitary available DR capacity value of 4,015 W per EV device, recommending its use for 2026 and further analysis to ensure consistency. This value was derived from dividing total DR capacity by participating devices during events.
Battery Controls As described above, the Evaluator first established a unitary available DR capacity per battery and also calculated an average available DR capacity per battery capacity. The latter was used to calculate the 2025 evaluated...
AI summary The Evaluator calculated the unitary available DR capacity per battery as 3,515 W and the average available DR capacity per battery capacity as 0.763 kW/enrolled kW. These metrics, along with a participation rate of 58.0%, were used to determine the 2025 evaluated available DR capacity for the Battery Control pathway.
Table 23: 2024/25 Available DR Capacity in kW/kW for Batteries Event # Event Date Event Hour Available DR Capacity (kW/Enrolled kW) Participation Rate (% of Enrolled kW) 1 12-04-2024 17 - 0.0% 18 - 0.0% 2 12-20-2024 7 0.904 52.6% 8 0.989 5...
AI summary Table 23 shows the available DR capacity for batteries during various events in 2024/25, with participation rates and an average available DR capacity of 0.763 kW/enrolled kW. The Evaluator recommends using this value for 2026 and conducting further analysis to ensure consistency.
4.2.3 Interactive Effects In a home, interactive effects occur when the implementation of energy efficiency products has an impact on the energy consumption of other elements such as heating and cooling. For the Smart Thermostat DLC pathwa...
AI summary Interactive effects in energy efficiency programs occur when changes in one system (e.g., smart thermostats) impact others (e.g., heating). The Evaluator prioritized whole-house AMI data for smart thermostats to capture these effects but used device-level data for DHW, EV chargers, and battery controls, assuming negligible interactions due to system design and location.
4.2.4 Effective Useful Life Although no electrical energy savings are expected from DR initiatives, the Evaluator established an EUL value since the available DR capacity can persist over time. For the Residential DR, an EUL value of one y...
AI summary The Evaluator assigns an Effective Useful Life (EUL) value of one year to Residential Demand Response (DR) programs, as participation includes all active participants annually. This avoids extrapolating capacity over lifetime, despite no electrical energy savings from DR initiatives.
4.2.5 Evaluated Available DR Capacities For Residential DR, available DR capacity is obtained by multiplying the number of enrolled devices by the unitary available DR capacity value, the participation rate, and the portion of the DR seaso...
AI summary This section discusses the calculation of available DR capacity for residential demand response, using factors such as enrolled devices, participation rates, and line loss factors. It references a 2014 study submitted to the Nova Scotia Energy Board.
Table 24: Evaluated 2025 Residential DR Available DR Capacities Smart Thermostats per Space Heating Type DHW EV Telematics Battery EBB Only MSHP Only MSHP and EBB Only Others Subtotal Controllers and Chargers Controls Total Number of Enrol...
AI summary Table 24 evaluates the available demand response (DR) capacities for residential customers in 2025, including enrolled devices, battery capacity, participation rates, and available DR capacity at the meter and generator levels. The data includes various heating types, DHW, EV telematics, and battery controls.
The Evaluator compared the 2025 evaluated available DR capacity for all participants to that of 2024. As outlined in [Table](#page-92-1) 25 below, returning participants generated 22% more available DR capacity than they did in 2024 due to...
AI summary The Evaluator compared the 2025 evaluated available DR capacity for all participants to that of 2024. Returning participants generated 22% more available DR capacity in 2025 due to a higher unitary available DR capacity value for smart thermostats. New participants contributed 93% of the 2025 available DR capacity, which was 0.797 MW.
Table 25: Change in Available DR Capacity from 2024 to 2025 Available DR Capacity (MW) % of 2024 Total Available DR Capacity Total 2024 Capacity (A) 0.057 N/A Change in Existing Participants Available DR Capacity (B) 0.012 22% Loss Due To...
AI summary Table 25 shows a significant increase in available demand response (DR) capacity from 2024 to 2025, primarily due to new participants joining the program, despite some loss from participants leaving. The data indicates that all available DR capacity from DHW controllers is considered new since no capacity was claimed for them in 2024.
4.3 Program Realization Rate [Table](#page-93-1) 26 below compares the available DR capacity established through this evaluation to the value tracked by E1 in the 2025 tracking sheet. The realization rate, representing the ratio of evaluat...
AI summary The document discusses the Program Realization Rate, comparing available DR capacity evaluated to that tracked by E1 in the 2025 tracking sheet, with a realization rate of 158%.
Table 26: Comparison of 2025 Residential DR Tracked and Evaluated Available DR Capacities at the Generator Available DR Capacity Value Unit Realization Rate Available DR Capacity Tracked by E1 0.540 MW Evaluation Results 0.854 MW 158% The...
AI summary Table 26 compares the tracked and evaluated available demand response (DR) capacities for residential programs in 2025. The evaluated capacity is 58% higher than the tracked value, primarily due to higher unitary DR capacity values for smart thermostats.
5 Residential DR Key Findings and Recommendations As previously mentioned, the main objectives of the 2025 Residential DR evaluation were as follows: - › Collect feedback from program staff, service providers, staff from other jurisdiction...
AI summary The 2025 Residential DR evaluation highlights a comprehensive mix of eligible devices, positive E1 relationships, and streamlined integration of pathways into 'Eco Shift.' Lessons learned led to updated eligibility criteria and enrollment processes, with slower growth expected due to demand response's less tangible value proposition compared to energy efficiency programs.
2025 Res DR-Finding: Residential DR participation grew substantially during the 2024/25 DR season. In the 2024/25 DR season, Residential DR participation increased by 907% compared to 2023/24 levels, reaching 3,676 participants and 11,405...
AI summary Residential DR participation surged 907% in 2024/25, reaching 3,676 participants and 11,405 devices, but failed to meet its 7.135 MW capacity target (actual: 0.854 MW). Retention remains high (>90%), yet 40% of EPI-program recipients did not enroll in DR despite mandatory enrollment rules.
6.1 BNI DR Description In 2023, E1 officially launched the BNI DR program component now branded as Smart Synergy. Since the fall of 2020, E1 had implemented several pilot initiatives focused on reducing demand during the Nova Scotia peak p...
AI summary In 2023, EfficiencyOne launched the BNI DR program, branded as Smart Synergy, following pilot initiatives since 2020. The C&I Aggregator pathway, managed by Parsons Inc., allows load reduction through remote control or participant action during DR events, targeting systems like heating, cooling, and lighting.
Table 27: C&I Aggregator Event Criteria Criteria Requirement Event Season Winter is from December through February. Event Windows From 7:00-11:00 a.m. and 5:00-9:00 p.m., Monday to Friday excluding holidays, during winter. Event Initiation...
AI summary Table 27 outlines the criteria for C&I Aggregator Events, including seasonal timing, event windows, initiation based on load forecasting, limits on the number and frequency of events, and notification procedures. NS Power called eight events during the 2024/25 DR season, as noted in Table 28.
Table 28: BNI DR 2024/25 Event History Month Number of Morning Events Number of Evening Events Total Number of Events Average Length of Events (Hours) December 1 2 3 3.7 January 1 1 2 3.5 February 2 2 3 3.7 Total 4 5 8 3.6 \ One event in F...
AI summary Table 28 outlines the event history for the BNI DR 2024/25 program, showing the number of morning and evening events held each month, along with the total number of events and their average length. In February, one event was split into two time-windows, and participants were grouped into morning and evening platoons based on their suitability for participation.
6.2 Follow-up on Past Evaluation Report Recommendations The Evaluator evaluated BNI DR in both 2023 and 2024 and issued improvement recommendations. [Table](#page-100-2) 29 provides a summary of the implementation status of each recommenda...
AI summary The Evaluator assessed BNI DR programs in 2023 and 2024 and provided improvement recommendations. Table 29 summarizes the implementation status of these recommendations from the reports' Executive Summary sections.
Table 29: Implementation Status of Past Recommendations for BNI DR # Recommendation Status Comments 2023 – BNI DR – R2 Establish enrolled capacity based on test events when feasible. Complete To ensure it is consistent with M&V guidelines,...
AI summary The document outlines the implementation status of past recommendations for the BNI DR program. Key actions include establishing enrolled capacity based on test events, determining optimal event times for participants, updating baseline considerations, and using project reviews to evaluate available DR capacities. These actions were completed as of 2025.
Participation in Events Based on the results of a review of 30 meters, it was found that participants did not participate in events around 60% of the time, compared to a non-participation rate of 31% in the 2023/24 DR season. In conducting...
AI summary The analysis found that 60% of participants did not engage in demand response (DR) events, compared to 31% in the 2023/24 season. Lower DR capacity correlated with reduced participation. Meters were categorized into morning and evening platoons, with event windows structured to align with these groups. Extrapolation estimated 63% average meter participation per event.
7 BNI DR Evaluation Approach The 2025 BNI DR evaluation comprised a comprehensive impact evaluation. The main objective of the 2025 BNI DR evaluation was as follows: › Calculate BNI DR results, participation, and available DR capacity The...
AI summary The 2025 BNI DR evaluation aimed to calculate BNI DR results, participation, and available DR capacity. The Evaluator identified key research questions and methods to achieve this objective, which are detailed in Table 30.
Table 30: 2025 BNI DR Evaluation Approach Evaluation Objectives Research Questions Methodology Establish available DR capacity results for the C&I Aggregator pathway › Are the data in the tracking sheet complete, accurate, and consistent?...
AI summary The document outlines the evaluation approach for the 2025 BNI Demand Response (DR) program, focusing on assessing the completeness, accuracy, and consistency of data in the tracking sheet and verifying the M&V methodology used. It includes an audit of the tracking sheet and project reviews.
Project Reviews with Meter Data Analysis E1 staff sampled and reviewed a total of 30 meters to establish tracked available DR capacity. The sample was stratified so that the 20 meters generating the largest amount of tracked available DR c...
AI summary E1 staff conducted a stratified review of 30 meters to evaluate demand response (DR) capacity, ensuring accuracy by validating adjustments beyond standard M&V protocols. The sample included 20 high-capacity meters and 10 randomly selected smaller ones, confirming 71% of savings with no margin of error. The Evaluator verified calculations and load profiles to confirm correct M&V application.
8.1 Tracking Sheet Audit To ensure program component results were reliably compiled, the Evaluator first performed a tracking sheet audit aimed at verifying the completeness and consistency of the data submitted by E1. The verification and...
AI summary The Evaluator conducted a tracking sheet audit to verify the completeness and consistency of data submitted by E1 for program component results. Corrective actions were taken, ensuring the reported tracked available DR capacity reflects the corrected data.
8.2 Demand Response Capacity For BNI DR, the evaluated metric is referred to as available DR capacity and corresponds to the load reduction made available for peak demand events in participating businesses. For the C&I Aggregator pathway,...
AI summary The document outlines the evaluation of available DR capacity for BNI DR, using baseline load comparisons and adjustment factors. Negative savings are set to zero in 2024, with E1 reviews guiding tracked capacity calculations. Adjustments in 2025 improved meter reviews for higher impact metrics.
8.2.1 Project Reviews and Meter Data Analysis The Evaluator conducted project reviews to establish the evaluated available DR capacity. The Evaluator reviewed the results for a stratified sample of 30 meters, which included the 20 meters w...
AI summary The Evaluator conducted project reviews to assess demand response (DR) capacity using a stratified sample of 30 meters, verifying E1's adherence to established calculation approaches and guidelines from the BNI DR Baseline Consideration document. The same meters were reviewed by both the Evaluator and E1.
Project Review Findings The most frequent adjustment made by the Evaluator to the available DR capacity calculation was to set the available DR capacity to zero due to non-participation in events. If no obvious load shed was observable for...
AI summary The Evaluator adjusted DR capacity calculations by setting them to zero due to non-participation or lack of observable load shedding. E1 adjusted lookback windows for a participant's safe shutdowns, while the Evaluator reinstated savings after reviewing participant communications. Recommendations included updating BNI DR baseline criteria for event savings exclusion, leading to improved consistency in 2025 reviews.
Available DR Capacity [Table](#page-106-1) 31 below presents the tracked and evaluated available DR capacity following the project reviews. As highlighted therein, the Evaluator project reviews resulted in only small differences compared t...
AI summary The table shows that the Evaluator project reviews identified 3% and 26% less available DR capacity for stratum 1 and 2 meters, respectively, compared to E1 project reviews. This discrepancy is due to the Evaluator setting the available DR capacity of 11 events to zero due to no obvious load shed, while E1 had not identified those events as such.
Table 31: 2024/25 Available DR Capacity of Reviewed Meters Metric Stratum 1 Stratum 2 Unadjusted Available DR Capacity (kW) 6,115 231 Tracked Results Tracked Adjustment Ratios 0.67 0.74 Tracked Available DR Capacity 4,079 170 Evaluated Res...
AI summary Table 31 presents the 2024/25 available demand response (DR) capacity for two strata of meters, showing unadjusted and adjusted capacities based on tracked and evaluated results. Adjustment ratios are calculated by dividing adjusted capacities by unadjusted capacities. The Evaluator considers a margin of error below 10% as statistically significant, and the 11% margin for stratum 2 is deemed acceptable due to limited sample size and few changes.
Table 32: 2025 Evaluated Adjustment Ratios Stratum Adjustment Ratio Margin of Error Percentage of Total Available DR Capacity Stratum 1 0.65 0% 71% Stratum 2 0.55 11% 29% Compared to the previous evaluation, the number of participants has...
AI summary Table 32 shows the 2025 evaluated adjustment ratios for Stratum 1 and Stratum 2, with lower values compared to 2024. E1 attributes this to increased total participants but lower participation rates, and plans to focus on engaging fewer participants more closely to improve participation rates.
8.2.2 Interactive Effects In a building, interactive effects occur when the implementation of energy efficiency products has an impact on the energy consumption of other elements such as heating and cooling. For the C&I Aggregator pathway,...
AI summary Interactive effects occur when energy efficiency products in buildings influence heating and cooling consumption. For the C&I Aggregator pathway, these effects are factored into demand response (DR) capacity calculations using whole-building meter data to account for overall consumption impacts.
8.2.3 Effective Useful Life Although no energy savings were expected under the C&I Aggregator pathway, the Evaluator established an effective useful life (EUL) value to express for how many years available DR capacity might persist, i.e. a...
AI summary The Evaluator assigned an Effective Useful Life (EUL) of one year to Demand Response (DR) capacity under the C&I Aggregator pathway, as participation includes all active participants annually, making extrapolation unnecessary. No energy savings were anticipated under this pathway.
8.2.4 Evaluated Available DR Capacities [Table](#page-107-2) 33 below presents the evaluated available DR capacity results of BNI DR for 2025. As presented in [Table](#page-107-2) 33, available DR capacity at the generator amounted to 5.94...
AI summary The evaluated available DR capacity for BNI DR in 2025 is presented in Table 33, with a total of 5.941 MW at the generator. This capacity was estimated using weighted average line loss factors based on rate codes and submitted to the Nova Scotia Energy Board as part of the 2014 Cost of Service Study Progress Update.
Table 33: Evaluated 2025 BNI DR Available DR Capacity Stratum 1 Meters Stratum 2 Meters Total Number of Participants 20 138 158 Unadjusted Available DR Capacity – at the Meter (MW) 6.115 2.972 9.087 Adjustment Ratio 65% 55% 62% Available D...
AI summary Table 33 evaluates the 2025 BNI DR available DR capacity, showing a decrease of 46% in available DR capacity from returning participants compared to 2024. New participants contributed 1.736 MW, while the new available DR capacity was -2.093 MW.
Table 34: Change in Available DR Capacity from 2024 to 2025 Available DR Capacity (MW) % of 2024 Total Available DR Capacity Total 2024 Capacity (A) 8.034 N/A Change in Existing Participants Available DR Capacity (B) -3.696 -46% Loss Due T...
AI summary Table 34 shows a decrease in available demand response (DR) capacity from 2024 to 2025, with a significant drop of 46% due to existing participants leaving the program, partially offset by new participants joining. Total available DR capacity in 2025 is 5.941 MW, representing 74% of the 2024 total.
[Table](#page-108-1) 35 presents the difference between enrolled available DR capacity and evaluated available DR capacity. Metric Stratum 1 Meters Stratum 2 Meters Overall Enrolled Available DR Capacity (MW) 8.392 13.660 22.052 Evaluated...
AI summary Table 35 compares enrolled and evaluated available demand response (DR) capacity across different strata. The enrolled capacity is significantly higher than the evaluated capacity, with overall evaluated capacity being only 27% of enrolled capacity.
8.3 Program Realization Rate [Table](#page-109-0) 36 below compares the available DR capacity established through this evaluation to the value in the 2025 tracking sheet. The realization rate, representing the ratio of evaluated available...
AI summary The program realization rate for DR capacity is 89%, calculated by comparing evaluated available DR capacity to tracked available DR capacity. Event 8 was excluded due to being a split event with participants called for different times based on platoons.
Table 36: Comparison of 2025 BNI DR Tracked and Evaluated Available DR Capacity at the Generator Available DR Capacity Realization Rate Value Unit Available DR Capacity Tracked by E1 6.648 MW Evaluation Results 5.941 MW 89% This value is t...
AI summary The evaluated available DR capacity for 2025 BNI DR was 11% lower than the value tracked by E1, due to adjustments made during project reviews. The realization rate was 89%.
9 BNI DR Key Findings and Recommendations As previously mentioned, the main objective of the 2025 BNI DR evaluation was as follows: › Calculate BNI DR results, namely the available DR capacity This section provides the Evaluator's key find...
AI summary The 2025 BNI DR evaluation found that the program missed its available DR capacity target (5.941 MW vs. 10.726 MW). Morning events generated higher capacity than evening ones. Enrollment increased by 88%, but per-participant capacity dropped from 106 kW to 42 kW due to low event participation (60% non-participation). The Evaluator recommends process evaluations in 2026 and project reviews to improve participation and accuracy.
CONCLUSION [Table](#page-112-1) 37 presents the participation levels and evaluated new and total available DR capacities for each program component and for the Demand Response program as a whole.
AI summary Table 37 outlines participation levels and evaluated new and total available Demand Response capacities for each program component and the Demand Response program overall.
Table 37: Overall 2025 Demand Response Participation and Evaluated Results Participation Level Evaluated Results Value Unit Value Unit Residential DR Available DR Capacity 3,676 Participants 0.854 MW BNI DR Available DR Capacity 143 Partic...
AI summary Table 37 shows that the 2025 Demand Response (DR) program fell short of its targets, with both Residential DR and BNI DR not meeting planned available DR capacity. BNI DR remained the largest contributor to program available DR capacity, which totaled 6.795 MW.
[THANK AND TERMINATE AFTER B4 FOR ALL ANSWERS] - B5. [ASK IF B1=1 OR B2a=1] How did you learn about Efficiency Nova Scotia's Eco Shift Program? Please select all that apply. [MULTIPLE RESPONSE. RANDOMIZE 1-10.] - 1. From the installer who...
AI summary The text includes survey questions about customer awareness and enrollment in Efficiency Nova Scotia's Eco Shift Program, covering channels like installers, marketing emails, and the website. It also asks about enrollment status and methods, highlighting technical challenges and non-enrollment reasons.
C. Perceived Potential Benefits - C1. What do you see as the potential benefits of taking part in the program? Select all that apply. [MULTIPLE RESPONSE. RANDOMIZED 1-6] - 1. Receiving financial incentives for enrolling in the Eco Shift Pr...
AI summary The section outlines perceived benefits of the Eco Shift Program, including financial incentives, reduced peak demand, sustainability support, and grid reliability. It also asks for additional information needed to reconsider enrollment.
[DISPLAY: The Nova Scotia Power Time-Varying Pricing Rate Pilot Program offered two alternative rate plans: Rate Plan Description Time-of-Use Rate Pilot From November to March, rates were higher during the peak hours when demand for electr...
AI summary The Nova Scotia Power Time-Varying Pricing Rate Pilot Program introduced two rate plans: Time-of-Use and Critical Peak Pricing. The Time-of-Use plan had higher rates during winter peak hours and lower, flat rates during non-winter months. The Critical Peak Pricing plan offered lower off-peak winter rates but significantly higher rates during four-hour critical peak periods.
Please indicate if you've heard of the Eco Shift program after reading the description below. Eco Shift - The program offers rebates for enrolling devices to reduce the demand during peak periods in the winter. During demand response event...
AI summary The Eco Shift program provides rebates for enrolling devices to reduce electricity demand during peak winter periods by remotely adjusting smart thermostat settings, thereby lessening the load on the electricity grid in Nova Scotia.
A. Respondent Involvement in the Program First, I would like to know more about your background and involvement with the program. A1. Please tell me your title and briefly describe your role in the Eco Shift Program. [PROBE for: Collect th...
AI summary The text inquires about the respondent's role in the Eco Shift Program, seeking details on their title, years delivering DR programs, and experience in other jurisdictions. It focuses on assessing involvement and expertise in demand response initiatives.
B. Program Processes - B1. Could you describe the enrollment and registration process for participants who enter the program via the bring your own device (BYOD) path? [PROBE for: Any feedback from the participants' perspective?] - a. What...
AI summary The text outlines a series of questions about program processes, including enrollment/registration for BYOD and other Efficiency Nova Scotia programs, DR event execution, opt-out procedures, incentive issuance, and drop-out observations. It seeks participant feedback on effectiveness, challenges, and areas for improvement across technologies like smart thermostats and EVs.
C. Participation Increase and Retention - C1. From your experience, what would increase participation in the program? Any differences per technology (smart thermostats, EVs & Chargers, Home Batteries, Hot Water Controllers)? [OPEN END] - C...
AI summary The section explores strategies to increase participation and retention in demand response (DR) programs, focusing on technologies like smart thermostats, EVs, home batteries, and hot water controllers. It asks about factors influencing participation, engagement during DR events, and retention methods, with open-ended questions and probes for technology-specific differences.
APPENDIX IV Residential DR Tracking Sheet Audit This document presents the detailed results of the tracking sheet audit performed by the Evaluator, which was aimed at: - › Verifying that all data fields required for the evaluation were inc...
AI summary This appendix details the audit of the residential demand response (DR) tracking sheet conducted by the Evaluator. The audit aimed to verify the completeness and accuracy of data fields and calculations used to evaluate program results, ensuring consistency with previous evaluations.
Table 1: 2025 Residential DR Corrected Tracked Available DR Capacity Program Component Result Available DR Capacity Tracked by E1 Corrected Tracked Available DR Capacity Relative Difference Value Unit Value Unit Value Smart Thermostats 0.4...
AI summary The table shows the corrected tracked available DR capacity for residential demand response programs in 2025. The Evaluator adjusted the available DR capacities for smart thermostats and DHW controllers due to changes in in-service rates and the exclusion of time-of-use and critical peak pricing participants.
APPENDIX V Residential DR Smart Thermostat DLC Detailed Metering Data Analysis Methodology This appendix summarizes the methodology used by the Evaluator to establish the available DR capacity for the Smart Thermostat Direct Load Control (...
AI summary This appendix outlines the methodology for evaluating residential demand response (DR) capacity from smart thermostats using metering data. The Evaluator updated unitary DR capacity values for subgroups of space heating systems, analyzing whole-house consumption data to predict hourly load and compare expected vs. actual loads during events, prioritizing whole-house data over device-level data to account for interactive effects.
Form of the Regression Following the 2024 methodology used in a literature review conducted to identify the most appropriate baseline methodology for such evaluations, the Evaluator used regression models that considers the time of week an...
AI summary The Evaluator used regression models incorporating time of week and outdoor temperature to establish baselines for residential electricity consumption. This approach accounts for temperature impacts and household variability, leveraging large datasets with comparable cold-temperature data. Regression models are preferred over previous-day baselines due to their common use in similar programs and ability to handle temperature extremes.
Where: - › , is the calculated baseline load in kW on a specified day of week (D) and hour of day (H) for a given temperature. - › , is the time of the week where D is from 1 to 7 (Sunday to Saturday) and H is from 00 to 24 (midnight to 11...
AI summary The text outlines a method to calculate baseline load using heating degree days (HDD) and temperature data, assigning participants to weather stations based on postal codes for accurate temperature correlation. This approach ensures localized weather data alignment for demand-side management and energy efficiency assessments.
Data Cleaning The initial dataset included all participants with enrolled smart thermostats in 2025 (2,471). Among those, only 1,457 participants had available AMI data because account numbers are user-entered by participants, and they som...
AI summary The dataset was cleaned by excluding participants with EV chargers, batteries, or incomplete data, resulting in 1,222 participants and 5,497 smart thermostats. Subgroups were formed based on types of space heating, and heating degree days were used to represent heating load. Other space heating types had too few participants for significant analysis.
Table 1: Numbers of Participants and Devices Available for the Meter Data Analysis Type of Smart Thermostat DLC Participants Number of Participants Number of Devices All participants in the tracking sheet 2,471 10,200 Participants with ava...
AI summary The table outlines the number of participants and devices involved in a meter data analysis for smart thermostat DLC programs. The Evaluator adjusted and filtered the data by excluding outliers, incomplete data, and holiday data to ensure accurate baseline consumption patterns.
Where: - $\rightarrow$ $\beta_{D,H}$ is the regression intercept. - $\alpha_{D.H}$ is the regression slope. - $\rightarrow$ RMSE h is the hourly model root mean square error. - $n_h$ is the number of observations. - $\bar{x}_h$ is the mean...
AI summary The text outlines statistical methods for evaluating demand response (DR) program effectiveness, including regression models, error propagation calculations, and uncertainty quantification for load reduction estimates. Key metrics include RMSE, standard error, and unitary savings calculations.
Regression Coefficients for EBB-only Participants Mondays Tuesdays Wednesdays Thursdays Fridays 02 0.107 0.094 0.317 0.084 0.248 0.084 0.300 0.083 0.232 0.091 03 0.101 0.095 0.282 0.087 0.245 0.085 0.292 0.084 0.189 0.094 04 0.120 0.095 0....
AI summary The document presents regression coefficients for EBB-only participants across different days of the week, indicating varying levels of energy usage patterns. The data shows a progression of coefficients from 0.107 to 1.224, which may be relevant for analyzing energy consumption behaviors and efficiency measures.
This appendix summarizes all the recommendations made by the Evaluator as part of the 2025 evaluation of Residential DR. Section Recommendations Executive Summary 2025 Res DR Recommendation 1: Include all changes to the pilot and program i...
AI summary The appendix outlines two key recommendations from the 2025 evaluation of the Residential Demand Response (DR) program. The first recommends updating the program manual to include all historical changes and clearly define eligibility criteria. The second emphasizes ensuring accurate data collection and proper recording of device information during the EPI installation process.
This document presents the detailed results of the tracking sheet audit performed by the Evaluator, which was aimed at: - › Verifying that all data fields required for the evaluation were included and filled out in the tracking sheet submi...
AI summary The document details the results of a tracking sheet audit conducted by the Evaluator to verify the completeness and accuracy of data submitted by E1. The audit confirmed consistency in parameters used for calculating program results, with no discrepancies found between tracked and corrected available DR capacity values.
Table 1: 2025 BNI DR Corrected Tracked Available DR Capacity Program Component Result Value Tracked by E1 Corrected Tracked Value Relative Difference Value Unit Value Unit Value Available DR Capacity 6.648 MW 6.648 MW 0% APPENDIX IX BNI DR...
AI summary Table 1 presents the 2025 BNI DR Corrected Tracked Available DR Capacity, showing no difference between the tracked and corrected values. Appendix IX provides an example of the calculation for available DR capacity.
Per the definition agreed upon by E1 and NSP, available DR capacity is evaluated based on events called from December to February excluding weekends and holidays. Events called at any time during the day (morning or evening)[5](#page-147-1...
AI summary The document discusses how available DR capacity is calculated based on participant performance during events called from December to February, excluding weekends and holidays. It highlights that participants are categorized by E1 as either better suited for morning or evening events, and that averaging load reductions at the participant level can yield higher available DR capacity if some participants are not called for all events.
r suited to morning events or to evening events and, for each event, E1 can decide to only call participants that are better suited to that time or to call all participants to take part in that event. To illustrate how available DR capacit...
AI summary The text explains how available DR capacity is calculated by considering participants' suitability for morning or evening events. An example with five participants and five events is used to illustrate the calculation, showing how events are scheduled based on participants' availability.
Table 1: Available DR Capacity Calculation Example Type of Load Reduction per Participant per Event (kW) Event Event Period Participant for Which the Part. #1 Part. #2 Part. #3 Part. #4 Part. #5 Sum of Load Reduction per Number Event Was C...
AI summary Table 1 presents an example calculation of available DR capacity, with the bottom-right value (2,667 kW) representing the sum of average DR capacity per participant. This approach differs from the average load reduction per event (1,952 kW), as E1 sums participant averages rather than event averages when reporting available DR capacity.
APPENDIX X BNI DR Baseline Considerations
AI summary This appendix outlines baseline considerations for BNI DR programs, focusing on evaluation methodologies, impact assessments, and ensuring accurate baselines for demand response initiatives targeting business, non-profit, and institutional sectors.
Test and Validate Test the lookback window against past DR events to validate its effectiveness.
AI summary The text directs evaluating the lookback window's effectiveness by testing it against historical demand-response (DR) events to ensure accurate validation of past performance.
Business Rules If the lookback window is observing an abnormal condition such as a building opening or closing earlier than normal, consider whether this point in time is a valid point of comparison. Consider the example below. The facilit...
AI summary The text outlines a business rule for adjusting demand response (DR) metrics during abnormal facility conditions, such as temporary shutdowns. It emphasizes verifying such anomalies with the E1 Business Development Manager (BDM) to ensure adjustments reflect normal operations, avoiding distortions from one-off events like early facility closures.
Reflect Actual Conditions The cap should reflect the actual conditions and operational changes that could reasonably affect the DR event day's load.
AI summary The cap should align with actual conditions and operational changes that may impact load during demand response (DR) events.
Prevent Overcompensation It should prevent overcompensation for reductions that would have occurred without the DR event.
AI summary The text emphasizes preventing overcompensation in demand response (DR) programs by ensuring that incentives are not provided for energy reductions that would have occurred naturally without the DR event, thereby maintaining program integrity and cost-effectiveness.
Consider Program Goals The cap should align with the overall goals of the DR program, whether it's peak shaving, load shifting, or emergency response.
AI summary The cap must align with the DR program's goals, including peak shaving, load shifting, and emergency response, ensuring program effectiveness and alignment with broader objectives.
Business Rules 1) If the default 20% adjustment cap does not accurately encompass the total curtailment for the specified event day, i.e. a very abnormal day was confirmed by the business, consider allowing for an exception on the default...
AI summary The rule allows exceptions to the default 20% adjustment cap for curtailment on confirmed abnormal event days, ensuring accurate coverage of total curtailment.
Symmetry Adjustments are applied symmetrically, i.e. results could go up or down. The symmetric approach considers that day-of conditions can have a real impact on customer demand in both directions and therefore it can be argued that symm...
AI summary The text discusses symmetric adjustments in demand response programs, arguing that they improve baseline accuracy by accounting for day-of conditions. It mentions a ±20% cap to mitigate negative impacts of downward adjustments and suggests adjusting the timing of the adjustment window.
Business Rules 2) If the lookback window provides an abnormal positive or negative adjustment factor, the event should be flagged and considered with more detail, as a new adjustment period may need to be selected, including the hours proc...
AI summary The text outlines procedures for handling abnormal adjustment factors in lookback windows, emphasizing the need to flag events, reassess adjustment periods, and ensure consistency in adjustments for all events within a participant's timeframe due to anomalies like building operational changes.
Exclusion rules Exclusion rules – Some days are excluded from consideration such as holidays, previous DR event days, weekends, thresholds and scheduled shutdowns (as these are not representative of "normal" operation). Example: A facility...
AI summary Exclusion rules specify that certain days (e.g., holidays, weekends, scheduled shutdowns, and DR event days) are excluded from baseline calculations as they do not reflect normal operations. An example highlights abnormal energy usage during a facility closure due to renovations, which should be excluded to ensure accurate baseline metrics.
Business Rules 3) If there are known irregularities in customer usage that are not representative of typical operation, such days can be excluded from the baseline calculation. The rationale for exclusion must be documented in CIS for that...
AI summary The text outlines procedures for handling irregular customer usage data in baseline calculations, including excluding non-representative days, documenting exclusions in CIS, consulting E1's Business Development Manager for operational hours, and addressing gaps in AMI meter data by excluding events on a per-participant basis.
2025 DSM MEASURE ASSESSMENT Final Report 2025 EVALUATION EDITION March 20, 2026
AI summary The 2025 DSM Measure Assessment Final Report evaluates the effectiveness of demand-side management initiatives, focusing on energy efficiency, cost recovery, and program performance. It provides insights into the 2025 evaluation edition, issued on March 20, 2026, and includes analysis of DSM measures' impact on energy conservation and regulatory compliance.
DEFINITIONS Accuracy Reflects the proximity of measurements to the true value. Adjustment ratio The ratio of evaluated results to tracked results. This ratio expresses the adjustment made to tracked savings or other tracked values such as...
AI summary The document defines key terms such as 'accuracy' and 'adjustment ratio' and explains how available demand response (DR) capacity is calculated for NSP based on participant performance during events between December and February.
Table 1: Residential Measure Assessment Change Log Change Type Section Description Date Update 2.2.3(4) Low-flow Showerheads Removed mention of mail-out pilot kit. Updated 2025-03-19 installation rate and number of showerheads per househol...
AI summary The document details updates to residential measure assessments, including changes to installation rates, efficiency values, and the removal of mail-out pilot kits for various energy efficiency measures. These updates are based on 2024 EPI on-site visit results and new efficiency standards such as HSPF2 and SEER2.
Purpose The objectives of this document are to: - › Ensure consistency in gross savings values throughout the three-year DSM cycle and thus improve E1's ability to define and track targets for energy and peak demand savings - › Consolidate...
AI summary This document aims to ensure consistency in gross savings values across the three-year DSM cycle, enhancing E1's ability to track energy and peak demand savings targets. It also consolidates these values into a single reference document for program staff and E1's internal e-Technical Reference Manual (e-TRM).
Use and Application For the evaluations conducted during the last two years of the 2023-2025 demand-side management (DSM) cycle, the Evaluator will refer to the values presented in the 2025 DSM MA. The DSM MA includes the following element...
AI summary The 2025 DSM MA is referenced for evaluating demand-side management (DSM) programs in the 2023-2025 cycle, including interactive effects, peak demand ratios, installation rates, unitary savings, and effective useful life (EUL) values. Demand response (DR) measures differ from demand reduction measures by generating savings only during DR events rather than throughout peak periods.
Development and Review Process Savings are established using one or more of the following approaches: Literature reviews of TRMs; metering studies and evaluation reports; engineering calculations; adjustments based on data collected throug...
AI summary The document outlines methods for establishing savings in energy programs, including literature reviews, metering studies, and engineering calculations. It details the Evaluator's approach to calculating average parameters using three-year data (2021-2023) for consistency, with exceptions for significant annual changes. The 2025 evaluation did not introduce new measures.
Peak Demand Savings Peak demand savings correspond to the demand savings that coincide in time with the peak demand of the electricity system. The projected electricity peak demand period in Nova Scotia is between 5 p.m. and 7 p.m. from De...
AI summary Peak demand savings refer to reductions in electricity demand during Nova Scotia's projected peak period (5-7 PM, Dec-Feb non-holiday weekdays). The text outlines a calculation method involving demand savings, adjustment ratios, and net-to-gross ratios, though the formula is partially obscured by an image placeholder.
Available Demand Response Capacity Available DR capacity differs from peak demand savings reported in other DSM reports since the former considers the load reduction that was made available by participating devices during events called for...
AI summary Available Demand Response (DR) capacity is calculated differently from peak demand savings, focusing on load reduction during DR events called by E1 (EfficiencyOne) between December and February. It measures capacity over the first two hours of events, excluding weekends/holidays, and aggregates per-participant reductions. E1's total capacity is the sum of individual participant contributions.
1 Residential Measure Assessment Scope [Table](#page-187-2) 2 below lists the residential measures and associated programs included in the 2025 DSM MA. The DSM MA includes all necessary parameters and calculations to obtain gross energy an...
AI summary The 2025 DSM MA includes residential measures and associated programs, detailing parameters for calculating gross energy and peak demand savings. Prescriptive measures use fixed assumptions, while custom measures use unit-specific inputs. Semi-prescriptive measures combine both approaches.
Table 3: Interactive Effects Factors for Residential Lighting Products Installed Indoors Type of Home % of Homes1 Energy Interactive Effects Factor2 Peak Demand Interactive Effects Factor3 Heat Pump Heating and Air Conditioning 38% -58% /...
AI summary Table 3 presents interactive effects factors for residential lighting products installed indoors, showing how different home types affect energy and peak demand. The weighted average indicates a -17.7% energy interactive effects factor and -46.8% peak demand interactive effects factor.
Peak Demand The Hydro-Québec report assumes that 10% of the heat is released through exterior walls and ceilings and does not contribute to interactive effects. Since the peak demand period occurs during the heating period when lighting an...
AI summary The Hydro-Québec report assumes 10% heat loss through exterior walls/ceilings, leading to a -90% interactive effects factor for peak demand savings in electrically heated homes and heat pumps, based on 100% efficiency during peak periods.
Table 4: Proportion of Lighting Products Used Indoors Type of Product Program Component % Indoor Reference A-type LED Lamps 5 97% 2021, 2022 and 2023 EPI Tracking Sheets Reflector and Decorative LED Lamps 6 (Except PAR38) 100% 2024 EPI Eva...
AI summary Table 4 outlines the proportion of various lighting products used indoors, with data ranging from 0% to 100% for different product types. The table includes references to studies, evaluations, and assumptions used to determine these proportions.
Table 5: Overall Interactive Effects Factors for Residential Lighting Measures Interactive Effects Factors Measure Type of Home Energy Savings Peak Demand Savings EPI LED A-type Lamps9 Heat Pump Heating and Air Conditioning -25.8% x 97% =...
AI summary Table 5 presents interactive effects factors for residential lighting measures, showing energy and peak demand savings across different home types and lighting technologies, such as LED lamps, motion sensors, and dimmer switches. The table includes calculations for various scenarios, such as heat pump heating, electrical heating, and no electrical heating.
2.1.2 Peak Demand Savings Factors For all indoor and outdoor LED lamps, nightlights, and fixtures, the peak demand-to-energy ratio is based on the Northeast Residential Lighting Hours-of-Use (NERHOU)[12](#page-193-2) study, which establish...
AI summary The document discusses the peak demand-to-energy ratios for indoor and outdoor LED lamps, nightlights, and fixtures, recommending the use of 0.162 W/kWh based on the NERHOU study. It also references the use of ratios developed by Navigant for motion sensors during the 2020-2023 DSM cycle.
Table 8: Electrical Unitary Energy Savings Values for LED Lamps Type of LED Old Wattage (W) New Wattage (W) Displaced Wattage (W) Operating Hours (hrs/day) Unitary Savings Value (kWh/year) EPI 9 W Replacing 25 W 25 9 16 2.6 15.2 9 W Replac...
AI summary Table 8 provides electrical unitary energy savings values for LED lamps, detailing the displaced wattage and annual savings for various replacements. The table compares old and new wattages for different LED types and calculates unitary savings based on operating hours.
Unitary Peak Demand Savings Unitary peak demand savings are calculated by multiplying the unitary savings value by the peak demandto-energy ratio. 16 The snapback effect is an increase in usage following the installation of an efficient pr...
AI summary Unitary peak demand savings are calculated using a unitary savings value and the peak demand-to-energy ratio. The text also references studies on residential lighting hours-of-use and mentions a snapback effect, where usage increases after installing efficient products due to lower operating costs.
(2) ENERGY STAR Certified LED Fixtures with Motion Sensors
AI summary The document references ENERGY STAR Certified LED Fixtures with Motion Sensors as a program component, likely under demand-side management initiatives aimed at promoting energy efficiency in lighting technologies.
Summary Table 11 presents a summary of the values used to calculate the savings for motion sensors. The detailed methodology follows.
AI summary Table 11 summarizes the values used to calculate savings for motion sensors, with a detailed methodology provided in the following text.
Peak Demand As for the impact on peak demand savings, it is assumed that all the DHW tanks in a conditioned or semi-conditioned space create interactive effects. Therefore, similar to lighting products, the interactive effects factor for p...
AI summary The document discusses the impact of domestic hot water (DHW) tank insulation on peak demand savings, assuming interactive effects of -90% for electrically heated homes. It references regulatory documents and evaluation reports related to energy efficiency programs.
For most water heating measures, peak demand savings are calculated using the peak demand-to-energy ratios developed by Navigant in the 2016-2018 DSM Plan. These ratios were established for various product categories based on modelled syst...
AI summary The text discusses the method used to calculate peak demand savings for water heating measures, referencing the 2016-2018 DSM Plan and recommending the use of the same ratios for the 2023-2025 DSM cycle. It notes that solar domestic hot water systems provide no peak demand savings due to their operation during off-peak hours.
Table 27: Peak Demand-to-energy Ratios for Water Heating Measures Measure Peak Demand-to energy Ratio (W/kWh) Reference Drain Water Heat Recovery 0.162 RES-Water Heat, Navigant 2016-2018 DSM Plan Heat Pump Water Heater Low-flow Showerhead...
AI summary Table 27 presents peak demand-to-energy ratios for various water heating measures, including drain water heat recovery and solar domestic hot water. The table indicates that solar domestic hot water systems provide no peak demand savings during the peak demand period as the sun has set.
Table 35: Electrical Unitary Energy Savings Values for Low-flow Showerheads (Continued) EPI Parameter Symbol Single-family Homes Apartments Reference Unit Conversion #2 [ft3 /gal] UC2 0.1337 Convention Share of Participants with Electrical...
AI summary Table 35 provides electrical unitary energy savings values for low-flow showerheads in single-family homes and apartments, with data on flow rate reductions and corresponding energy savings. It also notes that EPI units are installed in homes with electrical water heaters.
2.3.2 Peak Demand Savings Factors For most space heating measures, peak demand savings are not calculated using a peak demand-toenergy ratio. For more details, refer to Subsection [2.3.3](#page-33-0)[(1)](#page-33-1) for mini-split heat pu...
AI summary The document discusses the methodology for calculating peak demand savings factors for various space heating measures. It notes that for most measures, peak demand savings are not calculated using a peak demand-to-energy ratio, while for air sealing products, ratios established by Navigant in the 2016-2018 DSM Plan are recommended. Programmable and smart thermostats are assumed to have nil peak demand savings unless part of a demand response program.
Table 50: Peak Demand-to-energy Ratios for Space Heating Measures Measure Peak Demand to-energy Ratio (W/kWh) Reference Mini-split Heat Pumps (MSHPs) - - Central Air-source Heat Pumps Ground-source Heat Pumps Wood and Pellet Stoves/Firepla...
AI summary Table 50 presents peak demand-to-energy ratios for various space heating measures, including heat pumps, wood and pellet stoves, solar air heating, and air sealing products. These ratios are used to assess the energy efficiency of different heating solutions, with some values derived from assumptions and literature reviews.
For Green Heat, the electrical unitary energy savings for MSHPs are based on the billing analysis results of the 2024 Green Heat evaluation, which yielded savings per unit of capacity for both homes that were fully electrically heated and...
AI summary The document discusses the calculation of electrical unitary energy savings for MSHPs under the Green Heat and ASFH programs. For Green Heat, savings are calculated based on billing analysis results, while for ASFH, savings are calculated for the entire home and adjusted based on the percentage of electric space heating.
Table 53: Adjustment Ratios for HEA and MHEEP Modelled Savings Scenario Adjustment Ratio A participant who registered with a heat pump 1.24 A participant who registered without a heat pump and who did not install one 0.58 A participant who...
AI summary Table 53 outlines adjustment ratios for HEA and MHEEP modelled savings based on participant scenarios involving heat pump registration and installation. The ratios vary significantly depending on whether a heat pump was registered or installed.
For MSHPs, peak demand savings are only claimed for households with a fully electrically heated baseline. They are nil for mainly electrically heated baselines as a Green Heat billing analysis indicated no electrical energy savings for tho...
AI summary The document discusses peak demand savings for MSHPs, noting that savings are only claimed for fully electrically heated baselines, not for mainly electrically heated ones. It references a Green Heat billing analysis and provides a formula for calculating peak demand savings.
Table 55: Central Air-source Heat Pump Measure Summary Parameter Green Heat HEA Reference Measure Description and Identification Measure rebated after purchase Central air-source (air-to-air and air-to-water) heat pumps - Baseline Electric...
AI summary Table 55 provides a summary of the Central Air-source Heat Pump Measure, including parameters such as installation rates, effective useful life, energy savings, and peak demand savings. The table outlines the baseline for electric resistance space heating and details the calculation methods for energy and peak demand savings.
Table 57: Ground-source Heat Pump Measure Summary Parameter Green Heat Reference Measure Description and Identification Measure Ground-source heat pumps for high-efficiency space rebated after installation (HEA) or rebated after purchase (...
AI summary Table 57 provides a summary of the Ground-source Heat Pump Measure, including details on installation rates, effective useful life, energy savings calculations, and peak demand savings. The measure involves rebating ground-source heat pumps after installation or purchase, with baseline comparisons to electric heating resistance and other heat pump types.
$Peak \ Demand \ Savings_W = Previous \ Peak \ Demand \ Savings_W \times \frac{Energy \ Savings_{kWh}}{Previous \ Energy \ Savings_{kWh}}$ Table 60: Unitary Peak Demand Savings Values for Wood or Pellet Stoves and Fireplace Inserts Greei n...
AI summary The document presents a formula for calculating peak demand savings and includes Table 60, which provides unitary peak demand savings values for wood or pellet stoves and fireplace inserts. It references previous energy savings data and a calculation method for determining current peak demand savings.
For Green Heat, unitary peak demand savings are based on program design data.[76](#page-45-0) It is assumed that during the peak demand period, existing ASHPs operate exclusively on the electric resistance backup in the air handler. Thus,...
AI summary The document discusses how unitary peak demand savings for Green Heat are calculated, assuming existing air-source heat pumps (ASHPs) use electric resistance backup during peak periods. This assumption leads to identical peak demand savings for wood and pellet boiler measures with an ASHP baseline compared to an electric resistance baseline.
Table 63: Unitary Peak Demand Savings Values for Wood and Pellet Boilers and Furnaces Green Heat Parameter Wood Furnace or Boiler with Electrical Baseline Pellet Furnace or Boiler with Electrical Baseline Wood Furnace or Boiler with ASHP B...
AI summary Table 63 provides unitary peak demand savings values for wood and pellet boilers and furnaces, comparing different baseline scenarios. The values are presented in watts for each configuration, indicating the potential demand reduction associated with these heating systems.
Table 65: Air Sealing Product Measure Summary Parameter EPI Reference Measure Description and Identification Measure Air sealing products in electrically heated homes with direct installation - Baseline Door and/or windows without added ai...
AI summary Table 65 provides a summary of air sealing product measures, including installation rates, effective useful life, and energy savings parameters for different types of homes and products. It outlines the performance metrics for foam gaskets, door sweeps, and weather stripping in both electrically heated and heat pump heated homes.
Table 68: Window Film Kit Measure Summary Parameter EPI Reference Measure Description and Identification Measure Window film kits installed by the participant (left behind by the delivery agent), in electrically heated homes - Baseline Win...
AI summary Table 68 provides a summary of the Window Film Kit Measure, including details such as installation rate, energy savings, and peak demand savings. The table outlines parameters for electrically heated homes and heat pump heated homes, with references to subsections and external sources.
Table 70: Programmable Thermostat Measure Summary Parameter Instant Savings MHEEP Reference Measure Description and Identification Measure Programmable thermostats rebated in store for controlling electric baseboards Programmable thermosta...
AI summary Table 70 summarizes the Programmable Thermostat Measure for the MHEEP and Instant Savings programs, including parameters like installation rates, energy savings, and peak demand-to-energy ratios. Both programs have identical values for most parameters, with references to subsections and external documents for detailed calculations.
Electrical Unitary Energy Savings For programmable thermostats, the electrical unitary energy savings are based on the results from a Hydro-Québec 2009 program evaluation of electronic thermostats in residential new construction.[84](#page...
AI summary The text discusses the calculation of electrical unitary energy savings for programmable thermostats based on Hydro-Québec's 2009 evaluation and the Instant Savings program. It outlines the methodology for determining savings values across different dwelling types and references the 2021 Census Profile for proportions in Nova Scotia.
Table 71: Electrical Unitary Savings Calculations for Programmable Thermostats Instant Savings MHEEP Parameters Symbol Single-family Duplex/Triplex/ Townhouse Apartment Single-family Reference Proportion of Each Dwelling Type 𝐷𝑤𝑒𝑙𝑙𝑖𝑛𝑔 𝑃𝑟𝑜𝑝...
AI summary Table 71 provides electrical unitary savings calculations for programmable thermostats across different dwelling types, including single-family homes, duplexes, townhouses, and apartments. It includes data on thermostat savings, temperature setback savings, and total savings per dwelling type, with references to sources such as Statistics Canada and Econoler.
(10) Non-learning Smart Thermostats for Electrical Heating Systems Summary [Table](#page-53-0) 72 presents a summary of the values used to calculate non-learning smart thermostat savings. The detailed methodology follows.
AI summary Table 72 summarizes the values used to calculate non-learning smart thermostat savings. The detailed methodology for these calculations is provided in the document.
Table 72: Non-learning Smart Thermostat for Electrical Heating System Measure Summary Parameter ASFH, Instant Savings EPI Reference Measure Description and Identification Measure Non-learning smart thermostats with programmable schedules t...
AI summary Table 72 provides a summary of the Non-learning Smart Thermostat for Electrical Heating System Measure, including parameters such as installation rates, effective useful life, and energy savings. It outlines energy savings for different heating systems and subcategories, such as single-family homes and apartments.
Installation Rates For Instant Savings, the installation rates are assumed to be 100%. For EPI, an installation rate of 84% was measured during the 2024 EPI onsite visits for smart thermostats for MSHPs. For smart thermostats controlling e...
AI summary The document discusses installation rates for different programs, noting that Instant Savings assumes a 100% installation rate, while EPI smart thermostats for MSHPs have an 84% installation rate based on 2024 onsite visits. Other smart thermostats maintain a 100% assumption due to lack of data.
Table 75: Advanced Learning Thermostat for Central Heating System Measure Summary Parameter EPI Reference Measure Description and Identification Measure Wi-Fi enabled advanced thermostats with 7-day or learning-based scheduling and remote...
AI summary Table 75 outlines the parameters for an advanced learning thermostat measure for central heating systems. It includes details such as measure description, baseline, installation rate, effective useful life, and electrical savings parameters like unitary energy savings and peak demand-to-energy ratio.
2.4.1 Interactive Effects Retiring old appliances causes an increase in the heating load in the winter and a decrease in the cooling load in the summer since compressors on old appliances release significantly more waste heat than newer, m...
AI summary Retiring inefficient appliances can increase heating loads in winter and decrease cooling loads in summer. In Nova Scotia, due to the longer heating season and shorter cooling season, the overall interactive effects are expected to be negative. However, several factors, such as the use of electricity for heating and the placement of appliances, reduce the impact. Additionally, a portion of households use air conditioning, which can offset some of the negative effects. Overall, interactive effects are considered negligible, leading to a 0% factor for energy and peak demand savings.
Table 78: Interactive Effects Factors for Appliances Measure Interactive Effects Factor for Energy Savings Interactive Effects Factor for Peak Demand Savings Reference Clotheslines and Outdoor Drying Racks 0% 0% Assumption Refrigerator Ret...
AI summary Table 78 outlines interactive effects factors for various appliance measures, focusing on energy savings and peak demand savings. The table includes entries for items such as clotheslines, refrigerator replacements, and ENERGY STAR® certified appliances, though many fields are left blank or referenced in the text above.
For most appliances, peak demand savings are calculated using the peak demand-to-energy ratios developed by Navigant in the 2016-2018 DSM Plan. These ratios were established for various product categories based on modelled system-coinciden...
AI summary The Evaluator recommends continuing to use peak demand-to-energy ratios developed by Navigant for the 2016-2018 DSM Plan during the 2020-2023 cycle. Zero ratios are assumed for certain appliances like clotheslines due to their low usage during peak demand periods.
Table 79: Peak Demand-to-energy Ratios for Appliances Measure Peak Demand to-energy Ratio (W/kWh) Reference Clothesline and Outdoor Drying Racks 0.000 Calculated by the Evaluator Refrigerator Retirements/Replacements 0.138 RES-Appliance-Fr...
AI summary Table 79 presents peak demand-to-energy ratios for various appliance-related measures, including refrigerators, dehumidifiers, and energy-efficient products. Ratios are calculated using data from the Navigant 2016-2018 DSM Plan, NREL ResStock end-use load profiles, and assumptions made by the Evaluator.
tial Efficient Product Rebates Program – 2022 DSM Evaluation , Final Report presented to Efficiency Nova Scotia, March 2023. 2025 DSM Measure Assessment Final Report 82 107 Econoler, Residential Efficient Product Rebates Program – 2017 DSM...
AI summary The 2025 DSM Measure Assessment Final Report references evaluations of Nova Scotia's Residential Efficient Product Rebates Program, citing data from Natural Resources Canada and academic studies on appliance efficiency. The report uses two years of data (2022–2023) for analysis, with plans to expand to three years in future updates.
The electrical unitary energy savings of the ENERGY STAR certified clothes dryer measure are calculated using the equations below. Energy Savings $$_{kWh} = ADL \times ALW \times \left(\frac{1}{CEF_{base}} - \frac{1}{CEF_{new}}\right)$$ Th...
AI summary This text discusses the calculation of energy savings for ENERGY STAR certified clothes dryers using equations that incorporate average daily loads and combined energy factors. Data sources include Natural Resources Canada surveys and appliance efficiency ratings.
Table 92: Efficient Clothes Washer Measure Summary Parameter Instant Savings Reference Measure Description and Identification Measure ENERGY STAR clothes washers, rebated in store - Baseline New non-ENERGY STAR clothes washer General Param...
AI summary Table 92 summarizes the Efficient Clothes Washer Measure, focusing on energy savings parameters such as unitary energy savings, peak demand-to-energy ratio, and effective useful life. The measure involves rebating ENERGY STAR clothes washers and assumes a 100% installation rate.
Table 99: Efficient Washer-Dryer Combination Units Parameter Instant Savings Reference Measure Description and Identification Measure ENERGY STAR washer-dryer combination units rebated in store - Baseline New non-ENERGY STAR washer-dryer c...
AI summary The table outlines the parameters for efficient washer-dryer combination units, including energy savings, installation rates, and useful life. It highlights the ENERGY STAR units and their baseline comparison, as well as key metrics such as unitary energy savings and peak demand-to-energy ratio.
Table 109: ENERGY STAR Certified Dishwasher Measure Summary Parameter Instant Savings Measure Description and Identification Measure ENERGY STAR certified dishwashers that use less than 250 kWh, rebated in store - Baseline New non-ENERGY S...
AI summary Table 109 provides a summary of the ENERGY STAR certified dishwasher measure, including parameters such as installation rate, energy savings, and peak demand savings. The table outlines the measure description, baseline, and various energy efficiency metrics.
The unitary peak demand savings for bathroom exhaust fans are calculated using the variables defined and listed in the equation and below. $$Peak\ Demand\ Savings_W = \mathit{CFM} \times \left(\frac{1}{\eta_{base}} - \frac{1}{\eta_{eff}}\r...
AI summary The document provides a formula for calculating unitary peak demand savings for bathroom exhaust fans, using variables such as CFM, efficiency ratios, and a peak capacity factor.
Table 113: Unitary Peak Demand Savings Values for Bathroom Exhaust Fans Parameter Symbol Instant Savings Reference Fan Exhaust Rate [CFM] CFM 99.1 Weighted average from ENERGY STAR compliant model list and 2021 Instant Savings tracking she...
AI summary Table 113 presents unitary peak demand savings values for bathroom exhaust fans, including parameters such as fan exhaust rate, base and efficient fan efficacy, peak coincidence factor, and peak demand savings. These values are calculated using data from ENERGY STAR compliant models and assumptions from previous evaluations.
2.5 Plug Load Controls
AI summary The section titled '2.5 Plug Load Controls' introduces a regulatory topic focused on managing energy consumption from plugged-in devices, likely within the context of demand-side management programs. It may discuss strategies for reducing standby power usage, efficiency standards, or incentives for adopting smart plug load technologies.
2.5.1 Interactive Effects No interactive effects factors are calculated for power bars and outdoor devices because they are assumed to be negligible. [Table](#page-91-2) 118 summarizes the interactive effects factors for plug load control...
AI summary The text discusses the absence of interactive effects factors for power bars and outdoor devices due to their assumed negligible impact. It also references a table summarizing these factors for plug load control measures.
Table 118: Interactive Effects Factors for Plug Load Control Measures Measure Interactive Effects Factor for Energy Savings Interactive Effects Factor for Peak Demand Savings Reference Smart Power Controller for Audiovisual Equipment 0% 0%...
AI summary The text discusses interactive effects factors for plug load control measures, focusing on energy and peak demand savings. It includes a table with various measures and their corresponding factors, though many entries are incomplete. The section also references peak demand savings factors in a subsequent subsection.
For most plug load control measures, peak demand savings are calculated using the peak demand-to-energy ratios developed by Navigant in the 2016-2018 DSM Plan. These ratios were established for various product categories based on modelled...
AI summary The document discusses the calculation of peak demand savings for plug load control measures using peak demand-to-energy ratios developed by Navigant for the 2016-2018 DSM Plan. These ratios are recommended for continued use in the 2020-2023 DSM cycle. ENERGY STAR certified variable speed pool pumps are assumed to have a zero peak demand-to-energy ratio due to their usage patterns.
Table 119: Peak Demand-to-energy Ratios for Plug Load Control Measures Measure Peak Demand-to-energy Ratio (W/kWh) Reference Smart Power Controller for Audiovisual Equipment 0.000 RES-Plug Load Controls, Navigant Power Bar with Integrated...
AI summary Table 119 presents peak demand-to-energy ratios for various plug load control measures, including smart power controllers and energy-efficient pool pumps. These measures are referenced in the 2016-2018 DSM Plan and other sources like Navigant and ENERGY STAR.
Table 120: Smart Power Controllers for Audiovisual Equipment Measure Summary Parameter Instant Savings Reference Measure Description and Identification Measure Smart power controllers for audiovisual equipment rebated in store - Baseline N...
AI summary Table 120 provides a summary of a measure involving smart power controllers for audiovisual equipment. It outlines parameters such as installation rate, useful life, and energy savings. The measure is categorized as Tier 1 power strip, and the baseline is non-smart power controllers.
2.6 Demand Reduction For one category of demand reduction measures, namely demand response measures, the peak demand savings are replaced by the available DR capacity that differs from peak demand savings because the available DR capacity...
AI summary The text explains that for demand response (DR) measures, peak demand savings are calculated based on available DR capacity, which reflects potential load reduction rather than actual reductions during utility peak periods. This distinction affects how DR programs are evaluated and implemented.
2.6.1 Interactive Effects For demand reduction measures, interactive effects are assumed to be nil.
AI summary The document assumes no interactive effects for demand reduction measures within the regulatory proceeding. This assumption is part of the analysis on demand-side management and its implications for energy efficiency programs in Nova Scotia.
2.6.2 Peak Demand Savings Factors For demand reduction measures, peak demand savings are not determined using a peak demand-to-energy ratio since they do not generate energy savings. For more details, refer to Subsection [2.6.3.](#page-98-...
AI summary Peak demand savings for demand reduction measures are calculated without using a peak demand-to-energy ratio, as these measures do not generate energy savings. The text directs readers to Subsection 2.6.3 for further details.
2.6.3 Demand Reduction Measures
AI summary The section titled '2.6.3 Demand Reduction Measures' introduces a subsection focusing on strategies and initiatives aimed at reducing energy demand through various programs and policies, including demand-side management, appliance retirement, and residential and business energy rebates.
Summary [Table](#page-98-1) 128 presents a summary of the values used to calculate domestic water heater timer (DWHT) savings. The detailed methodology follows.
AI summary Table 128 summarizes the values used to calculate domestic water heater timer (DWHT) savings, with a detailed methodology provided afterward.
Table 128: Domestic Water Heater Timer Measure Summary Parameter Green Heat Reference Measure Description and Identification Measure Description Domestic water heater timers rebated after purchase - Baseline Electric water heaters without...
AI summary The table provides a summary of the Domestic Water Heater Timer Measure, including details on installation rates, energy savings, and peak demand savings. It outlines the measure's description, baseline, and key parameters such as effective useful life and savings ratios.
(3) Domestic Water Heater Load Control
AI summary The section discusses strategies for managing domestic water heater load control, likely focusing on demand-side management (DSM) initiatives, energy efficiency measures, and regulatory frameworks to optimize hot water usage. It may address technologies like heat pump water heaters (HPWH) and programs aimed at reducing peak demand through load-shifting or direct load control (DLC) mechanisms.
Summary [Table](#page-101-0) 130 presents a summary of the values used to calculate domestic water heater load control savings. The detailed methodology follows.
AI summary Table 130 summarizes the values used to calculate domestic water heater load control savings. A detailed methodology is provided following the table.
Table 130: Domestic Water Heater Load Control Measure Summary Parameter Demand Response Reference Measure Description and Identification Measure Direct load control for domestic water heaters with direct installation - Baseline Domestic wa...
AI summary Table 130 summarizes the Domestic Water Heater Load Control Measure, focusing on parameters like participation rates, in-service rates, and energy savings. It outlines details for demand response programs related to domestic water heaters, including available DR capacity and energy savings metrics.
In-service Rates The in-service rate was separated into two components: The portion of the DR season during which devices were enrolled and the participation rate of those enrolled devices during DR events. While all controllers remained i...
AI summary The in-service rate is divided into two components: the portion of the DR season with enrolled devices and the participation rate of those devices during DR events. Connectivity issues affected the ability of all controllers to generate savings, which was accounted for through the participation rate. Although the unitary available DR capacity value was not updated, the participation rate and portion of the DR season with enrolled devices were updated due to significant changes.
Parameter Value Margin of Error Reference Portion of Season with Enrolment 53.5% - Residential DR 2025 evaluation Participation Rate 22.5% 1.7% Residential DR 2025 evaluation (4) Smart Thermostat Load Control
AI summary The document presents data on the portion of the season with enrolment (53.5%) and the participation rate (22.5%) for residential demand response in 2025. It also introduces a section on Smart Thermostat Load Control.
Table 132: Smart Thermostat Load Control Measure Summary Parameter Demand Response Reference Measure Description and Identification Measure Direct load control for smart thermostats - Baseline Smart thermostats without direct load control...
AI summary Table 132 summarizes the Smart Thermostat Load Control Measure, focusing on parameters like in-service rates, energy savings, and DR capacity. It categorizes measures and provides data for different subcategories of smart thermostats.
Table 133: Available DR Capacity per Smart Thermostat Type Electric Baseboard Only MSHP Only Electric Baseboard and MSHP Only Others Source Average Available DR Capacity Per Participant, Excluding Outliers (W/Participant) 581 ± 8% 226 ± 20...
AI summary Table 133 presents available demand response (DR) capacity per smart thermostat type, including average capacity, number of thermostats, and unitary capacity. The data is sourced from the Residential DR 2025 evaluation and includes different participant categories such as Electric Baseboard Only, MSHP Only, and others.
For smart thermostat load control, participants were not removed from the whole-home data analysis if they opted out of an event or had connectivity issues, meaning that the participation rate is already included in the unitary available D...
AI summary The analysis of smart thermostat load control participation indicates that participants who opted out or had connectivity issues were not excluded from the data analysis, meaning the participation rate is factored into the DR capacity values. The in-service rate corresponds to the portion of the season with enrolment, as shown in Table 134.
Table 134: Smart Thermostat Control Measure Parameters Included in the In-service Rate Parameter Electric Baseboard Only MSHP Only Electric Baseboard and MSHP Only Others Reference Portion of Season with Enrolment 61.9% 59.6% 65.9% 54.7% R...
AI summary Table 134 outlines the portion of the season with enrolment for different thermostat control measures included in the in-service rate. The data shows varying percentages for Electric Baseboard Only, MSHP Only, Electric Baseboard and MSHP Only, and Others, with references to the Residential DR 2025 evaluation.
Table 135: Battery Control Measure Summary Parameter Demand Response Reference Measure Description and Identification Measure Direct load control for batteries - Baseline Battery consumption of participating homes on non-event days General...
AI summary Table 135 outlines a battery control measure under Demand Response, including parameters like participation rate, useful life, and energy savings. The table provides details on electrical energy savings and available DR capacity, but some fields remain unspecified.
Table 136: Battery Control Measure Parameters Included in the In-service Rate Parameter Value Reference Participation Rate 58.0% Residential DR 2025 evaluation (6) EV Telematic and Charger Control
AI summary Table 136 presents battery control measure parameters included in the in-service rate, highlighting a participation rate of 58.0% for residential demand response in 2025, referenced from an evaluation. Section (6) introduces EV telematic and charger control as a topic of discussion.
Table 137: EV Telematic and Charger Control Measure Summary Parameter Demand Response Reference Measure Description and Identification Measure Direct load control for EV telematics and chargers - Baseline EV telematics and chargers without...
AI summary Table 137 outlines a Demand Response measure involving direct load control for EV telematics and chargers. It includes parameters such as in-service rate, effective useful life, and available DR capacity. The table references details on electrical unitary energy savings and interactive effects factors.
Table 138: EV Telematic and Charger Control Measure Parameters Included in the In-service Rate Parameter Value Reference Participation Rate 2.9% Residential DR 2025 evaluation 2.7 Renewables
AI summary Table 138 outlines the participation rate for EV telematic and charger control measures at 2.9%, referencing a residential demand response evaluation for 2025. Section 2.7 introduces the topic of renewables.
Table 142: EUL Values and Sources for Non-LED Lighting Residential Measures Measure Name Program Component EUL Value Reference Faucet Aerators EPI 10 DEER, 2014 (value for faucet aerators)
AI summary Table 142 lists EUL values and sources for non-LED lighting residential measures, specifically highlighting faucet aerators under the Efficient Product Installation program component with an EUL value of 10, sourced from DEER, 2014.
Measure Name Program Component EUL Value Reference Domestic Water Heater Timers Green Heat 15 GDS, 2007 (Appendix C – Additional Documentation on Targeted Measures and Preliminary Measure Life Value Data for Other Residential and C&I End-U...
AI summary The document presents a table listing various energy efficiency and demand response measures along with their Effective Useful Life (EUL) values and references. Measures such as Domestic Water Heater Timers and Electric Thermal Storage are included under the Green Heat program, while Smart Thermostat Load Control falls under Demand Response.
Table 143: Commercial Measure Assessment Change Log Change Type Section Description Date Update 6.1.4 Lighting Measures For LED Linear Fixtures, LED Linear Lamps, LED Outdoor Fixtures, and LED Directional and Architectural Fixtures, the HO...
AI summary This table outlines updates and new additions to commercial measure assessments, including changes to lighting measures, occupancy sensors, LED nightlights, and the addition of horticultural lighting, as well as updates to heat pump efficiency ratios and interactive effects modifications.
[Table](#page-120-1) 144 below lists the commercial measures and associated programs included in the 2025 DSM MA. The MA includes all necessary parameters and calculations to obtain gross energy and peak demand savings for all portfolio pr...
AI summary The 2025 DSM MA includes commercial measures and programs, with parameters for calculating energy and peak demand savings. Prescriptive measures use fixed assumptions, while custom measures use unit-specific inputs. Semi-prescriptive measures combine both approaches. Effective useful life values are included for all measures.
Table 144: Included Commercial Measures Eligible Measures Program Components Lighting LED Lamps SBES LED Linear Fixtures BER-IR, BER-AR, SBES LED Linear Lamps BER-IR, BER-AR, SBES LED Outdoor Fixtures BER-IR, BER-AR, SBES LED Directional a...
AI summary Table 144 outlines eligible commercial measures and their associated program components, including lighting, pumps, space heating, HVAC, and water heating. Each measure is linked to specific program components such as BER-AR, SBES, and Custom, indicating the frameworks or standards they fall under.
Table 145: BER-AR and SBES Interactive Effects (IE) Factors for Non-recessed Indoor Lighting IE Energy IE Demand Building Type Heat Pump Electric Resistance Non-electric or No Heating Heat Electric Non electric Heating and Cooling Heating...
AI summary Table 145 presents interactive effects (IE) factors for non-recessed indoor lighting under BER-AR and SBES across various building types. The table shows energy and demand impact percentages for different heating and cooling configurations, highlighting variations by building type.
Table 147: BER-IR and SBES CDI Pilot Interactive Effects (IE) Factors for Lighting Measures Measure IE Factor for Electrical Energy Savings IE Factor for Peak Demand Savings BER-IR Linear LED Fixtures Recessed -7.8% -25.0% and Lamps Non-re...
AI summary Table 147 presents interactive effects (IE) factors for lighting measures under BER-IR and SBES CDI Pilot, showing varying impacts on energy savings and peak demand. Outdoor lighting measures have nil interactive effects, while high bay fixtures are assumed to have minimal impact due to heat dissipation.
Table 148: IE Factors for Outdoor Lighting and High-bay Fixtures Measure IE Factor for Electrical Energy Savings IE Factor for Peak Demand Savings Outdoor Lighting 0.0% 0.0% High-bay Fixtures 0.0% 0.0% Finally, the above factors do not acc...
AI summary Table 148 outlines interactive effects (IE) factors for outdoor lighting and high-bay fixtures, both of which have 0.0% IE factors for electrical energy and peak demand savings. The table does not account for lighting installed in refrigerators and freezers, which are covered in Table 149.
Table 149: IE Factors for Lighting Installed in Refrigerators and Freezers Measure IE Factor for Electrical Energy Savings IE Factor for Peak Demand Savings Lighting Installed in Refrigerators 29% 29% Lighting Installed in Freezers 50% 50%...
AI summary Table 149 provides interactive effects (IE) factors for lighting installed in refrigerators and freezers, showing 29% and 50% energy and peak demand savings, respectively. Section 6.1.2 discusses peak demand savings factors, highlighting their importance in energy efficiency analysis.
Unitary Peak Demand Savings Calculations Peak demand savings are calculated by multiplying the unitary demand savings value by the peak coincidence factor as detailed in the equation below. () = () × (%) The unitary demand savings value co...
AI summary The text explains the calculation of peak demand savings using the unitary demand savings value multiplied by the peak coincidence factor. It also provides the formula for unitary demand savings, derived by dividing unitary energy savings by hours of use (HOU).
Summary [Table](#page-128-2) 151 presents a summary of the values used to calculate A-type, reflector, and decorative LED lamp savings. These measures are only offered through SBES and the SBES Commercial Direct Install (CDI) Pilot. The de...
AI summary Table 151 summarizes values used to calculate A-type, reflector, and decorative LED lamp savings, which are only available through SBES and the SBES Commercial Direct Install (CDI) Pilot. The methodology is detailed further.
The unitary peak demand savings for booster pumps are calculated using the variables defined and listed in the equation and [Table](#page-151-2) 183 below, as well as variables from [Table](#page-151-0) 182 above. Peak Demand Savings W = $...
AI summary The calculation for unitary peak demand savings for booster pumps is provided, using specific variables and equations referenced from tables. The formula involves horsepower (HP) and a peak capacity factor (PCF).
Table 183: Unitary Peak Demand Savings Values for Booster Pumps Parameter Symbol BER-AR, SBES Reference Annual Unitary Demand Savings per Rated Horsepower from the Use of a VFD Booster Pump [W/HP] - 172 2024 Hawaii TRM200 Annual Unitary De...
AI summary This table provides unitary peak demand savings values for booster pumps, including annual demand savings per rated horsepower and a peak coincidence factor derived from evaluations of custom retrofit projects. The data references the 2024 Hawaii TRM and includes calculations based on installed system specifications.
6.3.2 Peak Demand Savings Factors For all HVAC measures, the methodology used to determine peak demand savings is detailed in the measure-specific sections below.
AI summary The section outlines the methodology for determining peak demand savings for HVAC measures, directing readers to measure-specific sections for detailed information.
Table 186: Advanced RTU Control Measure Summary Parameter BER-AR Reference Measure Description and Identification Measure Advanced RTU controls that include demand-controlled ventilation (DCV) and an optional variable frequency drive (VFD)...
AI summary Table 186 provides a summary of the Advanced RTU Control Measure, including details on energy savings adjustment ratios, peak demand savings adjustment ratios, and other parameters related to the Business Energy Rebates – After Installation program. The table outlines technical specifications and references for calculations.
The electrical unitary energy savings for smart thermostats for electric baseboards for commercial applications are assumed to be equal to the savings for a residential application because the heating power of controlled thermostats is exp...
AI summary The document discusses the assumption that smart thermostats provide similar energy savings in commercial and residential electric heating systems. It references a formula and studies on central heating systems to estimate 12% savings for smart thermostats, applicable to systems like electric baseboards.
[Table](#page-160-0) 192 below presents the variables used for the unitary savings calculation and the resulting value per thermostat. 212 Apex Analytics LLC, Energy Trust of Oregon Nest Thermostat Heat Pump Control Pilot Evaluation , Octo...
AI summary The text references two studies on Nest Thermostats and their energy savings, including a 2014 evaluation by Apex Analytics LLC and a 2016 assessment by the Bonneville Power Administration. A table on page 192 outlines variables used in the unitary savings calculation for thermostats.
Final Report 179 2025 DSM Measure Assessment 217 Efficiency Vermont, Technical Reference Manual (TRM) Program Year 2023 , p.90. 218 Efficiency Vermont, Technical Reference Manual (TRM) Program Year 2023 , p.91.
AI summary The document references Efficiency Vermont's Technical Reference Manual for Program Year 2023, specifically pages 90 and 91, in the context of the 2025 DSM Measure Assessment.
Table 197: Air-source Heat Pumps Greater Than 65,000 Btu/h, Measure Summary Parameter BER-AR SBES Reference Measure Description and Identification Measure PTHP used over the heating season which must be an AHRI certified matched system, re...
AI summary The table outlines parameters for air-source heat pumps greater than 65,000 Btu/h, including measure descriptions, baseline heating methods, and adjustment ratios for energy and peak demand savings. It also references subsections for detailed calculations and assumptions.
The electrical unitary energy savings for ASHPs greater than 65,000 Btu/h calculated using the variables defined and listed in the equation[222](#page-165-2) and [Table](#page-166-0) 198 below. $$\Delta kWh = \left(HC \times \left[\frac{1}...
AI summary The document discusses the calculation of electrical unitary energy savings for air-source heat pumps (ASHPs) with a capacity greater than 65,000 Btu/h. It references an equation and a table to compute energy savings and cites a technical reference manual from Efficiency Vermont. The text also mentions a 2025 DSM Measure Assessment Final Report.
Table 200: Unitary Peak Demand Savings Values for Air-source Heat Pumps Greater Than 65,000 Btu/h Parameter Symbol BER-AR, SBES Reference Heat Pump Rated Heating Capacity at -15°C (estimated temperature during NS peak demand) [kBtu/h] 𝐻𝐶𝑚𝑖...
AI summary Table 200 presents unitary peak demand savings values for air-source heat pumps greater than 65,000 Btu/h. It includes parameters such as heat pump rated heating capacity, heating efficiency factor, peak coincidence factor, and unitary peak demand savings, with references to technical specifications and assumptions.
Table 203: HVAC Hotel Occupancy Sensor Measure Summary Parameter BER-AR SBES Reference Measure Description and Identification Measure occupied, rebated after installation Year-round HVAC hotel occupancy sensor which controls electric heati...
AI summary Table 203 provides a summary of HVAC hotel occupancy sensor measures, including energy savings adjustment ratios, effective useful life, and other parameters. It references Subsections 6.3.1 and 3.2 for additional details and mentions Table 204 for electrical unitary energy savings.
Table 205: Unitary Peak Demand Savings Values for HVAC Hotel Occupancy Sensors Parameter Symbol BER-AR, SBES Reference Unitary Peak Demand Savings [kW] - 0.09 2025 Massachusetts TRM Installation Rates
AI summary Table 205 presents unitary peak demand savings values for HVAC hotel occupancy sensors, with a value of 0.09 kW referenced from the 2025 Massachusetts TRM. The table also includes a section on installation rates, though no specific data is provided in the excerpt.
Table 206: High Volume Low Speed Fan Measure Summary Parameter BER-AR SBES Reference Measure Description and Identification Measure CSA / cUL rated high volume low speed (HVLS) fans rebated after installation - Baseline Must replace existi...
AI summary Table 206 summarizes the High Volume Low Speed Fan Measure, including parameters such as energy savings adjustment ratios, peak demand savings adjustment ratios, and effective useful life. The table provides details on installation rates, energy savings calculations, and references to specific subsections for further information.
Table 207: Electrical Unitary Energy Savings Values for High Volume Low Speed Fans Parameter Symbol BER-AR, SBES Reference Power of Baseline Fans [W] Pb Actual or based on fan size (ft) >= 16 and <18 = 4,497 >= 18 and <20 = 5,026 >= 20 and...
AI summary Table 207 provides electrical unitary energy savings values for high volume low speed (HVLS) fans, including parameters such as power consumption, quantity of fans, and hours of use, with references to default values from Pennsylvania TRM and other sources.
The unitary peak demand savings for high volume low speed fans are calculated using the variables defined and listed in the equation and [Table](#page-172-3) 208 below as well as variables from [Table](#page-172-1) 207 above. $$\Delta kW =...
AI summary The document outlines the formula for calculating unitary peak demand savings for high volume low speed fans, using variables from two tables and a specific equation involving baseline and expected power quantities and a power conversion factor.
Table 208: Unitary Peak Demand Savings Values for High Volume Low Speed Fans Parameter Symbol BER-AR, SBES Reference Peak Coincidence Factor PCF 0.84 As per Subsection 6.10.2 Unitary Peak Demand Savings [kW] ∆𝑘𝑊 Calculation based on specif...
AI summary Table 208 presents unitary peak demand savings values for high volume low speed fans, including a peak coincidence factor of 0.84 and calculations based on specification data for rebated units. The table also references Subsection 6.10.2 for the peak coincidence factor.
Peak Demand As for the impact on peak demand savings, it is assumed that all hot water tanks in a conditioned or semiconditioned space create interactive effects. Therefore, similar to lighting products, the interactive effects factor for...
AI summary The text discusses the impact of hot water tanks in conditioned or semiconditioned spaces on peak demand savings, assuming an interactive effects factor of -90% for electrically heated buildings. Table 209 summarizes interactive effects factors for water heating insulation measures.
For hot water tank wraps, energy savings are assumed to occur all the time since the tank always exchanges heat with the space around it. Therefore, peak demand savings for this measure correspond to the average demand savings throughout t...
AI summary The document discusses the calculation of peak demand-to-energy ratios for hot water tank wraps and other water heating measures. For hot water tank wraps, energy savings are assumed to occur continuously, leading to a peak demand-to-energy ratio of 0.114 W/kWh. For other measures, load shapes from the Illinois TRM were used to estimate peak demand-to-energy ratios, considering different peak periods and water usage patterns.
he peak period by the length of the peak period, as presented in the equations below. $$\mbox{Peak Demand-to-energy Ratio} = \frac{\% kW h_{WP} \times 1{,}000 \; kW/W}{Hours_{WP}} \label{eq:energy}$$
AI summary The document explains the calculation of the Peak Demand-to-energy Ratio, which divides the product of the percentage of kilowatt-hours during the peak period and a conversion factor (1,000 kW/W) by the number of hours in the peak period. This is part of analyzing Peak Demand Savings Factors.
$$Hours_{WP} = \left( Days_{WP} \times \frac{Weekdays}{Days\ in\ a\ Week} - Holidays_{WP} \right) \times Daily\ Peak\ Hours_{WP} + Month Peak\ Hours_{WP} + Month Peak\ Hours_{WP} + Month Peak\ Hours_{WP} + Month Peak\ Hours_{WP} + Month Pe...
AI summary The text presents a mathematical formula for calculating peak demand hours (Hours_WP), incorporating weekdays, holidays, daily peak hours, and repeated monthly peak hours. The formula appears to be a technical methodology for quantifying demand-side management (DSM) savings factors, though no explicit policy or regulatory discussion is provided.
_{WP} + Month Peak\ Hours_{WP} + Month Peak\ Hours_{WP} + Month Peak\ Hours_{WP} + Month Peak\ Hours_{WP} + Month Peak\ Hours_{WP} + Month Peak\ Hours_{WP} + Month Peak\ Hours_{WP} + Month Peak\ Hours_{WP} + Month Peak\ Hours_{WP} + Month...
AI summary The text references a table that lists parameters and values used in equations to calculate the peak demand-to-energy ratio, which is relevant to energy efficiency and demand-side management calculations.
Table 211: Peak Demand-to-energy Ratio for Water Heating Measures Parameter Symbol Value Reference Portion of Energy Savings Occurring During Winter Peak Hours %kWhWP 40.5% Illinois TRM232 Number of Days During Winter Peak Season DaysWP 21...
AI summary Table 211 presents the peak demand-to-energy ratio for water heating measures, including parameters such as the portion of energy savings during winter peak hours, number of peak hours per day, and the calculated peak demand-to-energy ratio of 0.192. Table 212 summarizes the peak demand-to-energy ratios for various water heating measures, with thermostatic shower valves having a ratio of 0.192 and hot water tank wraps having a ratio of 0.114.
Table 214: Electrical Unitary Energy Savings Values for Low-flow Showerheads Parameter Symbol Value Reference Proportion of Water Heating Supplied by Electric Resistance Heating %ElectricDHW 100% Electrical energy savings will only be clai...
AI summary Table 214 presents electrical unitary energy savings values for low-flow showerheads, including parameters like baseline and low-flow rates, annual usage, and energy efficiency calculations. It references various sources such as SBES tracking sheets, EPI Program Manuals, and studies like DeOreo et al.
Table 215: Average Showerhead Usage Building Type Annual Minutes per Showerhead (SHtime) Weight Reference Hospitality 3,509 86% Annual minutes per Health 2,528 0% showerhead: Iowa Energy Efficiency TRM – 2021236 Education 2,057 0% Commerci...
AI summary Table 215 provides data on average showerhead usage across different building types, with weighted averages and references. It also mentions a 2025 DSM Measure Assessment, indicating a focus on demand-side management initiatives.
Table 216: Faucet Aerator Measure Summary Parameter SBES Reference Measure Description and Identification Measure Faucet aerators, with direct installation - Baseline No faucet aerator on standard flow-rate faucets General Parameters Insta...
AI summary Table 216 provides a summary of the Faucet Aerator Measure, including details on installation rates, effective useful life, and energy savings parameters. The measure involves the installation of faucet aerators with a 95% installation rate and a 10-year useful life. Energy savings are quantified as 266 kWh/year per unit, with a peak demand-to-energy ratio of 0.192.
Table 219: Thermostatic Shower Valve Measure Summary Parameter SBES Reference Measure Description and Identification Measure temperature has been reached, with direct installation Thermostatic shower valves cutting off water after the targ...
AI summary Table 219 summarizes the energy savings associated with thermostatic shower valves under the SBES program. It includes parameters like installation rates, useful life, energy savings, and peak demand-to-energy ratios, with references to specific subsections for detailed calculations.
Table 222: Unitary Energy Savings Value for Pipe Insulation Parameter SBES Unitary Energy Savings (per ft) [kWh/year] 12.7 2025 DSM Measure Assessment Final Report 199 245 Ontario Power Authority (OPA), OPA Prescriptive Measures and Assump...
AI summary Table 222 presents the unitary energy savings value for pipe insulation, with a value of 12.7 kWh/year per foot. The table is referenced in the 2025 DSM Measure Assessment Final Report, citing the Ontario Power Authority's 2010 Prescriptive Measures and Assumptions List.
Table 223: Hot Water Tank Wrap Measure Summary Parameter SBES Reference Measure Description and Identification Measure Hot water tank wrap, with direct installation - Baseline No tank wrap General Parameters Installation Rate 100% See deta...
AI summary Table 223 summarizes the Hot Water Tank Wrap Measure, including its installation rate, effective useful life, and energy savings parameters. The table outlines key metrics such as unitary energy savings, peak demand savings, and interactive effects factors related to energy and peak demand.
Table 225: DHW Heat Pump Water Heater Measure Summary Parameter BER-AR, SBES Reference Measure Description and Identification Measure Heat pump water heater with an Energy factor greater than 2.3, rebated after installation - Baseline Exis...
AI summary This table outlines the parameters for the DHW Heat Pump Water Heater Measure, including installation rate, effective useful life, and energy savings calculations. It references specific subsections for detailed information on energy and peak demand savings.
Table 229: Unitary Peak Demand Savings Values for DHW Heat Pump Water Heaters Parameter Symbol BER-AR, SBES Reference Peak Demand-to-Energy Ratio [kW/kWh] PDTER Calculation based on facility characteristics as shown in Table 230 2026 Penns...
AI summary Table 229 and Table 230 provide unitary peak demand savings values for DHW heat pump water heaters and PDTER by facility type, respectively. The tables reference the 2026 Pennsylvania TRM257 and include calculations based on facility characteristics and rebated unit specifications.
6.5.2 Peak Demand Savings Factors For compressed air measures, the peak demand savings factor is assumed to be 77% where it is unknown for the specific project.
AI summary The document specifies that for compressed air measures, a peak demand savings factor of 77% is assumed when project-specific data is unavailable. This assumption is part of a regulatory proceeding analyzing demand-side management factors in Nova Scotia.
6.5.4 Compressed Air Measures
AI summary This section, titled 'Compressed Air Measures,' likely outlines strategies or regulations related to energy efficiency improvements in compressed air systems, which are commonly used in industrial and commercial settings. The context suggests a focus on demand-side management and energy conservation initiatives in Nova Scotia.
Unitary peak demand savings for compressed air leak repairs are calculated using the equation below and the variables defined and listed in [Table](#page-192-2) 232 above. [] = [] × [/(100 )] ×
AI summary The document discusses the calculation of unitary peak demand savings for compressed air leak repairs, referencing a specific equation and variables listed in Table 232.
The unitary peak demand savings for cycling air dryers are calculated using the variables defined and listed in the equation and [Table](#page-194-3) 236 below, as well as variables from [Table](#page-194-1) 235 above. $$\Delta kW = \Delta...
AI summary The text describes the calculation of unitary peak demand savings for cycling air dryers using an equation and variables from two tables, with the formula Δ kW = Δ kWh × PCF/HOU.
The electrical unitary energy savings for air-entraining air nozzles are calculated using the variables defined and listed in the equation[260](#page-195-1) and [Table](#page-196-0) 238 below. $$\Delta kWh = (CFM_b - CFM_e) \times COMP \ti...
AI summary The document discusses the calculation of electrical unitary energy savings for air-entraining air nozzles using a specific equation and references a technical manual from Efficiency Vermont. It also mentions a 2025 DSM Measure Assessment Final Report.
The unitary peak demand savings for air-entraining air nozzles are calculated using the variables defined and listed in the equation and [Table](#page-196-2) 239 below, as well as variables from [Table](#page-196-0) 238 above.
AI summary The text discusses the calculation of unitary peak demand savings for air-entraining air nozzles, referencing specific tables for variable definitions and listings.
$$\Delta kW = \Delta kWh \times PCF/HOU$$ Table 239: Unitary Peak Demand Savings Values for Air-entraining Air Nozzles Parameter Symbol BER-AR, SBES Reference Peak Coincidence Factor PCF Actual or 0.77 As per Subsection 6.5.2 Hours of Use...
AI summary The document presents a formula for calculating peak demand savings using the peak coincidence factor (PCF) and hours of use (HOU). It also includes a table with parameters related to air-entraining air nozzles and their installation rates.
Summary [Table](#page-197-0) 240 presents a summary of the values used to calculate no-loss drain savings. The detailed methodology follows.
AI summary Table 240 summarizes the values used to calculate no-loss drain savings, with a detailed methodology provided in the proceeding document.
Table 240: No-loss Drain Measure Summary Parameter BER-AR, SBES Reference Measure Description and Identification Measure A no-loss drain opens the valve only when signaled by a condensate-level controller, rebated after installation - Base...
AI summary Table 240 outlines the 'No-loss Drain' measure, which uses a condensate-level controller to open a valve only when needed, unlike timed drains that operate on a fixed schedule. The measure has a 100% installation rate, a 15-year useful life, and energy savings calculated based on specification data for each rebated unit.
Table 241: Electrical Unitary Energy Savings Values for No-loss Drains Parameter Symbol BER-AR, SBES Reference Air Loss Rate [CFM] ALR See Table 242 Vermont TRM (2015)263 Compressor Efficiency [kW/CFM] COMP Modulating w/ BD = 0.32 Load/No...
AI summary The document presents two tables related to energy savings calculations for no-loss drains in electrical systems. The first table outlines parameters such as air loss rate, compressor efficiency, adjustment factors, and unitary energy savings. The second table provides average air loss rates based on pressure and orifice diameter. Both tables reference the Vermont TRM (2015) for data and calculations.
Table 243: Unitary Peak Demand Savings Values for No-loss Drains Parameter Symbol BER-AR, SBES Reference Peak Coincidence Factor PCF Actual or 0.77 As per Subsection 6.5.2 Hours of Use [hours/year] HOU Actual 1-Shift (8/5) – 2,080 hours 2-...
AI summary Table 243 outlines unitary peak demand savings values for no-loss drains, including parameters like the Peak Coincidence Factor (PCF), Hours of Use (HOU), and Unitary Peak Demand Savings (∆𝑘𝑊). These values are calculated based on specification data for each rebated unit and referenced in the Technical Reference Manual (TRM).
6.6.1 Interactive Effects Interactive effects are assumed to be nil for variable frequency drive (VFD) projects since this measure is implemented on equipment that is usually in non-conditioned spaces.
AI summary Interactive effects for variable frequency drive (VFD) projects are assumed to be nil because the equipment is typically installed in non-conditioned spaces, reducing potential interactions with other measures.
6.6.2 Peak Demand Savings Factors For variable frequency drives measures, the methodology used to determine peak demand savings is detailed in the measure-specific subsections below.
AI summary The section outlines the methodology for calculating peak demand savings related to variable frequency drives (VFDs), directing readers to specific subsections for detailed information on each measure.
Table 244: VFD Gross Savings Adjustment Ratios Source Evaluation Report Energy Savings Peak Demand Savings Program Component Adjustment Ratio Margin of Error Adjustment Ratio Margin of Error BER-AR 2025 0.951 5.8% 0.514 21.9% 6.6.4 Variabl...
AI summary Table 244 presents VFD Gross Savings Adjustment Ratios, including energy savings and peak demand savings with their respective adjustment ratios and margins of error. Section 6.6.4 discusses the Variable Frequency Drive (VFD) Measure.
Table 245: VFD Measure Summary Parameter BER-AR, SBES Reference Measure Description and Identification Measure Variable frequency drive for non-HVAC applications, installed after installation - Baseline No VFD General Parameters Installati...
AI summary Table 245 provides a summary of the Variable Frequency Drive (VFD) measure, including parameters such as installation rate, energy savings adjustment ratio, peak demand savings adjustment ratio, and effective useful life. It outlines the calculation methods for unitary energy and peak demand savings based on specification data for each installed system.
The electrical unitary energy savings for VFD for non-HVAC applications are calculated using the variables defined and listed in the equations and tables below. $$\begin{aligned} &Unitary \, Savings \left[\frac{kWh}{yr}\right] = \left(0.74...
AI summary The text provides a formula for calculating electrical unitary energy savings for Variable Frequency Drives (VFD) in non-HVAC applications. It includes variables such as horsepower, load factor, efficiency, hours of use, and an energy savings factor derived from duty cycle and part-load ratios.
Table 246: Electrical Unitary Energy Savings Values for VFD Pumps and Fans Parameter Symbol Value Reference Rated Horsepower of the Motor [HP] HP Varies per project Project documentation Motor Load Factor [%] LF Varies per project (If unkn...
AI summary Table 246 outlines the parameters and calculations used to determine electrical unitary energy savings values for VFD pumps and fans, including factors such as motor load, efficiency, and operating hours, with references to project documentation and the Minnesota TRM.
2025 DSM Measure Assessment Final Report
AI summary The 2025 DSM Measure Assessment Final Report provides an evaluation of demand-side management measures for the year 2025, assessing their effectiveness and impact on energy efficiency and customer participation.
Table 248: Electrical Unitary Peak Demand Values for VFDs for non-HVAC Applications Parameter Symbol Value Reference Part Load Ratio for the Average Flow Fraction During the Weekday Peak Time Period 𝑃𝐿𝑅𝐵𝑎𝑠𝑒𝑙𝑖𝑛𝑒,𝐹𝐹𝑝𝑒𝑎𝑘 Based on baseline con...
AI summary Table 248 presents electrical unitary peak demand values for VFDs in non-HVAC applications. It includes parameters such as part load ratios, peak coincidence factors, and unitary peak demand savings, with values based on baseline control, VFD control, and project documentation.
6.7.2 Peak Demand Savings Factors For pool pump measures, peak demand savings factors are assumed to be nil since most pumps are installed on outdoor pools that do not operate during the winter peak.
AI summary The section states that peak demand savings factors for pool pump measures are assumed to be zero, as most pumps are installed on outdoor pools that do not operate during winter peak demand periods.
Summary [Table](#page-4-0) 249 presents a summary of the values used to calculate pool pump savings. The detailed methodology follows.
AI summary Table 249 summarizes the values used to calculate pool pump savings, with the detailed methodology provided in the following sections.
Table 249: Pool Pump Measure Summary Parameter BER-AR, SBES Reference Measure Description and Identification Measure ENERGY STAR® multi-speed and variable frequency drive (VFD) commercial inground pool pumps, rebated after installation - B...
AI summary The table outlines the energy savings parameters for rebated ENERGY STAR® multi-speed and variable frequency drive (VFD) commercial inground pool pumps, comparing them to conventional single-speed pool pumps. It includes details on installation rates, useful life, and energy savings calculations.
6.8.2 Peak Demand Savings Factors For solar PV projects, peak demand savings are nil since the solar energy production from those systems coinciding with the peak period is negligible.
AI summary The text states that solar PV projects do not contribute to peak demand savings because their energy production during peak periods is negligible. This highlights a limitation in considering solar PV as a demand-side management strategy for reducing peak load.
6.9.1 Interactive Effects For refrigeration measures, interactive effects are considered when reduced heat rejection occurs within the refrigerated space, which in turns reduces the electricity consumption of the refrigeration compressor....
AI summary Interactive effects in refrigeration measures are considered when reduced heat rejection lowers compressor electricity consumption, factored into savings equations via a bonus factor for applicable measures.
6.9.2 Peak Demand Savings Factor For refrigeration measures, the peak coincidence factor (PCF) is assumed to be 100%, since all equipment is expected to be running continuously, with minor downtime that is addressed in the duty cycle varia...
AI summary The document assumes a 100% peak coincidence factor (PCF) for refrigeration measures, as equipment is expected to operate continuously with minor downtime accounted for in duty cycle variables.
Table 254: Refrigeration Gross Savings Adjustment Ratios Source Energy Savings Peak Demand Savings Program Component Evaluation Report Adjustment Ratio Margin of Error Adjustment Ratio Margin of Error BER-AR 2025 0.951 5.8% 0.514 21.9% 6.9...
AI summary Table 254 presents refrigeration gross savings adjustment ratios for the BER-AR program component in 2025, including energy savings and peak demand savings with respective margins of error. Section 6.9.4 discusses refrigeration measures.
Table 255: Cooler Night Cover and Display Strip Curtain Measure Summary Parameter BER-AR, SBES Reference Measure Description and Identification Measure Night cover or strip curtain for refrigerated cases, rebated after installation - Basel...
AI summary Table 255 presents a summary of the Cooler Night Cover and Display Strip Curtain Measure, including parameters such as energy savings adjustment ratios, peak demand savings adjustment ratios, and effective useful life. It outlines details related to installation rates and energy savings calculations.
Table 257: Unitary Peak Demand Savings Values for Cooler Night Covers and Display Strip Curtains BER-AR, SBES Parameter Symbol Cooler Night Covers Display Strip Curtains Reference Peak Coincidence Factor PCF 1 As per Subsection 6.9.2 Unita...
AI summary Table 257 presents unitary peak demand savings values for Cooler Night Covers and Display Strip Curtains, including parameters like Peak Coincidence Factor and Unitary Peak Demand Savings. The table outlines calculation methods and references subsections from the Technical Reference Manual.
Table 258: Zero-energy Door Measure Summary Parameter BER-AR, SBES Reference Measure Description and Identification Measure Zero-energy doors, without electric resistance heating in the door or frame, for Reach-in Coolers. Reach-in display...
AI summary Table 258 outlines the parameters for the Zero-energy Door Measure, including energy savings adjustment ratios, peak demand savings, and other technical specifications. The table provides details on installation rates, effective useful life, and energy savings calculations for rebate-eligible units.
$$\Delta kW = kW_{door} \times BF \times PCF$$
AI summary The text presents a mathematical formula that calculates the change in kilowatts (ΔkW) based on the door kilowatts (kW_door), a factor (BF), and the peak coincidence factor (PCF).
Table 260: Unitary Peak Demand Savings Values for Zero-energy Doors Parameter Symbol BER-AR, SBES Reference Peak Coincidence Factor PCF 1 As per Subsection 6.9.2 Unitary Peak Demand Savings [kW] ∆𝑘𝑊 Calculation based on specification data...
AI summary Table 260 presents unitary peak demand savings values for zero-energy doors, focusing on parameters such as the Peak Coincidence Factor (PCF) and Unitary Peak Demand Savings (∆𝑘𝑊). The table includes installation rates and references to technical guidelines.
Table 261: Door Heater Control Measure Summary Parameter BER-AR, SBES Reference Measure Description and Identification Measure Humidity or conductivity-based heater controls that limit heater operation to periods of high relative humidity...
AI summary Table 261 outlines a demand-side management measure involving humidity or conductivity-based heater controls that limit heater operation during periods of high relative humidity. The table provides details on energy savings adjustment ratios, peak demand savings adjustment ratios, and other parameters related to the measure.
Table 263: Unitary Peak Demand Savings Values for Door Heater Controls Parameter Symbol BER-AR, SBES Reference Peak Coincidence Factor PCF 1 As per Subsection 6.9.2 Unitary Peak Demand Savings [kW] ∆𝑘𝑊 Calculation based on specification da...
AI summary Table 263 outlines unitary peak demand savings values for door heater controls, including parameters such as the peak coincidence factor and unitary peak demand savings. The table provides calculation methods based on specification data for each rebated unit.
Table 265: Electrical Unitary Energy Savings Values for Evaporator Fan Motor Controls Parameter Symbol BER-AR, SBES Reference Connected Load kW of Each Evaporator Fan [kW] kWfan Actual or 0.11 Use information in TS Default: Based on weight...
AI summary The table outlines parameters and values used to calculate electrical unitary energy savings for evaporator fan motor controls, including connected load, load reduction factor, bonus factor, and hours of use. The savings are determined based on specifications for each rebated unit.
Table 266: Unitary Peak Demand Savings Values for Cooler Night Covers and Display Strip Curtains Parameter Symbol BER-AR, SBES Reference Peak Coincidence Factor PCF 1 As per Subsection 6.9.2 Unitary Peak Demand Savings [kW] ∆𝑘𝑊 Calculation...
AI summary Table 266 presents unitary peak demand savings values for Cooler Night Covers and Display Strip Curtains, including parameters such as the Peak Coincidence Factor and Unitary Peak Demand Savings. The table outlines calculation methods and references subsections from the relevant regulations.
Summary [Table](#page-18-0) 267 presents a summary of the values used to calculate electrical intelligent freezer defrost control savings. The detailed methodology follows.
AI summary Table 267 summarizes the values used to calculate electrical intelligent freezer defrost control savings, with a detailed methodology provided afterward.
Table 267: Intelligent Freezer Defrost Control Measure Summary Parameter BER-AR, SBES Reference Measure Description and Identification Measure Control system which contains temperature and pressure sensors to monitor system operation and d...
AI summary This table outlines the parameters for the Intelligent Freezer Defrost Control Measure, including installation rates, energy savings adjustment ratios, and useful life. It details how the control system reduces energy use by managing defrost cycles in walk-in freezers with electric defrost.
Table 268: Electrical Unitary Energy Savings Values for Intelligent Freezer Defrost Controls Parameter Symbol BER-AR, SBES Reference Number of Evaporator Fans nfans Actual Use information in TS kW of Defrost Element per Evaporator Fan kWDE...
AI summary Table 268 outlines the parameters and values used to calculate electrical unitary energy savings for intelligent freezer defrost controls, including factors like the number of evaporator fans, defrost element kW, and defrost cycle savings. These values are sourced from Vermont TRM and are used in conjunction with Table 269 to calculate peak demand savings.
Table 269: Unitary Peak Demand Savings Values for Intelligent Freezer Defrost Controls Parameter Symbol BER-AR, SBES Reference Peak Coincidence Factor PCF 1 See Subsection 6.9.2 Unitary Peak Demand Savings [kW] ∆𝑘𝑊 Calculation based on spe...
AI summary Table 269 outlines unitary peak demand savings values for Intelligent Freezer Defrost Controls, including parameters such as the Peak Coincidence Factor and Unitary Peak Demand Savings. The table provides calculation methods and references for these values.
Table 270: Vertical Refrigeration Open-to-closed Cooler Conversion Measure Summary Parameter BER-AR, SBES Reference Measure Description and Identification Measure Doored vertical refrigeration units, rebated after installation - Baseline O...
AI summary Table 270 provides a summary of the vertical refrigeration open-to-closed cooler conversion measure, including parameters such as installation rate, energy savings adjustment ratios, and useful life. It outlines the baseline and measure description, and details related to energy and peak demand savings.
Table 271: Electrical Unitary Energy Savings Values for Vertical Refrigeration Open-to-closed Cooler Conversion Parameter Symbol BER-AR, SBES Reference Open-to-closed Case Savings Factor [kWh/(day feet)] OCSF With anti-sweat heaters = 0.5...
AI summary Table 271 presents electrical unitary energy savings values for converting vertical refrigeration open-to-closed coolers, including parameters like open-to-closed case savings factor, operational days, and refrigerated length. Savings depend on the presence of anti-sweat heaters and are calculated using specified data.
$$\Delta kW = \frac{OCSF \times DAYS \times L_{case} \times PCF}{HOU}$$ Table 272: Unitary Peak Demand Savings Values for Vertical Refrigeration Open-to-closed Cooler Conversion Parameter Symbol BER-AR, SBES Reference Peak Coincidence Fact...
AI summary The document presents a formula for calculating unitary peak demand savings for vertical refrigeration open-to-closed cooler conversion. It also includes a table with parameters such as the peak coincidence factor, hours of use, and unitary peak demand savings. The table references a subsection and technical specifications for calculating the values.
Summary [Table](#page-22-0) 273 presents a summary of the values used to calculate efficient refrigeration compressor savings. The detailed methodology follows.
AI summary Table 273 summarizes the values used to calculate efficient refrigeration compressor savings, with a detailed methodology provided subsequently.
Table 273: Efficient Refrigeration Compressor Measure Summary Parameter BER-AR, SBES Reference Measure Description and Identification Measure Efficient scroll compressor, rebated after installation - Baseline Hermetic or semihermetic compr...
AI summary This table summarizes the efficient refrigeration compressor measure, including parameters such as energy savings adjustment ratio, peak demand savings adjustment ratio, and effective useful life. It outlines the baseline compressor type and the installation rate of the efficient scroll compressor.
Table 274: Electrical Unitary Energy Savings Values for Efficient Refrigeration Compressors Parameter Symbol BER-AR, SBES Reference Compressor Capacity at Standard Rating Conditions [Btu/h] 𝐶𝐴𝑃𝑎𝑣𝑔,𝑒𝑒 Actual Use information in TS Energy Eff...
AI summary The text presents tables detailing energy efficiency ratios (EER) for baseline and efficient refrigeration compressors in low and medium temperature conditions, along with parameters for calculating energy savings. The data is sourced from the Iowa Utilities Commission's technical reference manual.
Table 277: Unitary Peak Demand Savings Values for Refrigeration Economizers Parameter Symbol BER-AR, SBES Reference Peak Coincidence Factor PCF 1 See Subsection 6.9.2 Unitary Peak Demand Savings [kW] ∆𝑘𝑊 Calculation based on specification...
AI summary Table 277 presents unitary peak demand savings values for refrigeration economizers, including parameters such as the peak coincidence factor and unitary peak demand savings. The table references Subsection 6.9.2 for the peak coincidence factor and provides calculation methods for unitary peak demand savings.
Table 278: Refrigeration Economizer Measure Summary Parameter BER-AR, SBES Reference Measure Description and Identification Measure Coolers capable of drawing in outdoor air when it is sufficiently cool (temperatures less than 34°F or 1°C)...
AI summary Table 278 outlines the Refrigeration Economizer Measure Summary, including parameters such as energy savings adjustment ratio, peak demand savings adjustment ratio, and effective useful life. The measure involves coolers that use outdoor air when sufficiently cool, with installation and savings calculations based on specification data.
Table 279: Electrical Unitary Energy Savings Values for Refrigeration Economizers Parameter Symbol BER-AR, SBES Reference Power of Compressor [HP] HP Actual Use information in TS Condensing Unit Savings, per hp [kWh] kWhcond Hermetic / Sem...
AI summary Table 279 provides electrical unitary energy savings values for refrigeration economizers, including parameters such as compressor power, condensing unit savings, hours of use, and connected load of fans. The values are based on assumptions from Vermont's Technical Reference Manual and adjusted for the Nova Scotia market.
Table 280: Unitary Peak Demand Savings Values for Refrigeration Economizers Parameter Symbol BER-AR, SBES Reference Peak Coincidence Factor PCF 1 See Subsection 6.9.2 Unitary Peak Demand Savings [kW] ∆𝑘𝑊 Calculation based on specification...
AI summary Table 280 presents unitary peak demand savings values for refrigeration economizers, including parameters like peak coincidence factor and unitary peak demand savings. It references technical specifications and calculation methods.
Table 281: Brushless DC Motor Measure Summary Parameter BER-AR, SBES Reference Measure Description and Identification Measure Brushless DC motors (or electrically commutated motors – ECM) for cooler of freezer evaporator fan, rebated after...
AI summary Table 281 provides a summary of the Brushless DC Motor Measure, including details on energy savings, installation rates, and parameters like the Energy Savings Adjustment Ratio and Peak Demand Savings Adjustment Ratio. The table outlines specifications for rebating brushless DC motors and compares them to conventional shaded-pole motors.
Table 283: Unitary Peak Demand Savings Values for Brushless DC Motors Parameter Symbol BER-AR, SBES Reference Peak Coincidence Factor PCF 1 As per Subsection 6.9.2 Unitary Peak Demand Savings [kW] ∆𝑘𝑊 Calculation based on specification dat...
AI summary Table 283 presents unitary peak demand savings values for brushless DC motors, including parameters like the Peak Coincidence Factor (PCF) and calculations based on specification data for rebated units. References include technical documents and reports related to energy efficiency and refrigeration load shapes.
Table 284: Refrigerated Vending Machine Controller Measure Summary Parameter BER-AR, SBES Reference Measure Description and Identification Measure Controller uses occupancy sensor based controls to de-energize refrigerated vending machines...
AI summary Table 284 outlines a measure involving the installation of occupancy sensor-based controllers on refrigerated vending machines to reduce energy consumption. The table provides details on energy savings, peak demand savings, and other parameters associated with this measure.
Table 285: Electrical Unitary Energy Savings Values for Refrigerated Vending Machine Controllers Parameter Symbol BER-AR, SBES Reference Rated Power of Connected Equipment [kW] kWrated Actual Use information in TS Hours of Use [h/year] HOU...
AI summary The text presents Table 285, which outlines electrical unitary energy savings values for refrigerated vending machine controllers. The table includes parameters such as rated power, hours of use, percent savings factor, quantity of vending machines, and unitary energy savings. It references the Massachusetts TRM and provides calculation methods for energy savings.
The unitary peak demand savings for refrigerated vending machine controllers are calculated using the variables defined and listed in the equation and [Table](#page-30-2) 286 below, as well as variables from [Table](#page-30-0) 285 above....
AI summary The document explains how unitary peak demand savings for refrigerated vending machine controllers are calculated using a specific formula and variables from two tables. The formula involves multiplying the rated kW by SAVE, quantity, and a power correction factor.
Table 286: Unitary Peak Demand Savings Values for Refrigerated Vending Machine Controllers Parameter Symbol BER-AR, SBES Reference Peak Coincidence Factor PCF 1 As per Subsection 6.9.2 Unitary Peak Demand Savings [kW] ∆𝑘𝑊 Calculation based...
AI summary Table 286 outlines unitary peak demand savings values for refrigerated vending machine controllers, including parameters like the peak coincidence factor and unitary peak demand savings. Installation rates are also mentioned, though details are not provided.
6.10.2 Peak Demand Savings Factors For agriculture measures, peak demand savings are determined by multiplying the wattage by a PCF value of 84%, which was established as part of the 2015 evaluation of BER.[292](#page-30-3) 292 Econoler, B...
AI summary Peak demand savings for agriculture measures are calculated using an 84% Peak Demand Savings Factor (PCF), established during the 2015 evaluation of Business Energy Rebates (BER) by Econoler. This factor is applied by multiplying the wattage of measures by 84%.
Table 287: Agriculture Gross Savings Adjustments Energy Savings Peak Demand Savings Path and Measure Category Adjustment Ratio Margin of Error Adjustment Ratio Margin of Error Projects Sampled in Project Reviews BER-AR 0.951 5.8% 0.514 21....
AI summary Table 287 presents Agriculture Gross Savings Adjustments, including Energy Savings and Peak Demand Savings with respective adjustment ratios and margin of error percentages. Section 6.10.4 discusses Agriculture Measures, highlighting the evaluation of energy efficiency initiatives in the agricultural sector.
The unitary peak demand savings for energy efficient ventilation & circulation fans are calculated using the variables defined and listed in the equation and [Table](#page-34-0) 290 below, as well as variables from [Table](#page-33-0) 289...
AI summary The calculation for unitary peak demand savings from energy-efficient ventilation and circulation fans is detailed, using specific variables from two tables and an equation involving AF, ER, Qty, and PCF factors.
Table 290: Unitary Peak Demand Savings Values for Energy Efficient Ventilation and Circulation Fans Parameter Symbol BER-AR, SBES Reference Peak Coincidence Factor PCF 0.84 As per Subsection 6.10.2 Unitary Peak Demand Savings [kW] ∆𝑘𝑊 Calc...
AI summary This table outlines the unitary peak demand savings values for energy efficient ventilation and circulation fans, including the peak coincidence factor (PCF) and the calculation method for unitary peak demand savings. The data is based on specification data for each rebated unit.
The electrical unitary energy savings for dual & natural ventilation are calculated using the variables defined and listed in the equation and The fan energy savings are shown in Table 115. [These are the savings from](#page 1-6) the lower...
AI summary The document discusses the calculation of electrical unitary energy savings for dual and natural ventilation systems, using variables such as LC, ARL, ER, SF, HOU, and QTY. Fan energy savings are detailed in Table 115, with a formula provided for calculating the change in kilowatt-hours.
Table 292: Electrical Unitary Energy Savings Values for Dual and Natural Ventilation Parameter Symbol BER-AR, SBES Reference Livestock Capacity (number of animals the barn is designed for) LC Actual Use information in TS Airflow Requiremen...
AI summary Table 292 provides electrical unitary energy savings values for dual and natural ventilation systems, including parameters like airflow requirement per livestock, efficiency ratio, savings factor, and hours of use. The table references technical guidelines and calculations for energy savings from reduced fan usage due to humidity sensors.
Table 293: Unitary Peak Demand Savings Values for Dual and Natural Ventilation Parameter Symbol BER-AR, SBES Reference Peak Coincidence Factor PCF 0.84 As per Subsection 6.10.2 Unitary Peak Demand Savings [kW] $\Delta kW$ Calculation based...
AI summary Table 293 presents unitary peak demand savings values for dual and natural ventilation systems, including the peak coincidence factor (PCF) and calculation methods for peak demand savings. The table references Subsection 6.10.2 and outlines installation rates based on specification data for each rebated unit.
$$\Delta kW = (P_b - P_e) Qty PCF/1,000$$
AI summary The formula calculates the change in kilowatts based on the difference between baseline and actual power, quantity, and the peak demand savings factor, divided by 1,000.
Table 296: Unitary Peak Demand Savings Values for Zero-energy and Low-energy Livestock Waterers Parameter Symbol BER-AR, SBES Reference Peak Coincidence Factor PCF 0.84 As per Subsection 6.10.2 Unitary Peak Demand Savings [kW] ∆𝑘𝑊 Calculat...
AI summary This table presents unitary peak demand savings values for zero-energy and low-energy livestock waterers, including parameters like the Peak Coincidence Factor and Unitary Peak Demand Savings. The table references Subsection 6.10.2 and provides installation rates for these waterers.
$$\Delta kW = (P_b \times Qty_b - P_e \times Qty_e) \times PCF/1,000$$
AI summary The formula calculates the change in kilowatts (ΔkW) based on the difference between baseline and actual power consumption, adjusted by the Peak Demand Savings Factor (PCF). This calculation is relevant for demand-side management and energy efficiency programs.
Table 299: Unitary Peak Demand Savings Values for Agriculture Heat Pads Parameter Symbol BER-AR, SBES Reference Peak Coincidence Factor PCF 0.84 As per Subsection 6.10.2 Unitary Peak Demand Savings [kW] ∆𝑘𝑊 Calculation based on specificati...
AI summary This table presents unitary peak demand savings values for agriculture heat pads, including the peak coincidence factor (PCF) and the calculation method for unitary peak demand savings. It references Subsection 6.10.2 of the Technical Reference Manual (TRM) for the PCF value.
Table 300: Tractor Engine Block Heater Timer Measure Summary Parameter BER-AR SBES Reference Measure Description and Identification Measure Tractor engine block heater timer that controls an engine block heater of at least 400 W and is CSA...
AI summary Table 300 presents a summary of the Tractor Engine Block Heater Timer Measure, including parameters such as energy savings adjustment ratios, peak demand savings adjustment ratios, and effective useful life. The table also outlines installation rates and references specific subsections for detailed calculations.
$$\Delta kW = P_{heater} \times PCF/1,000$$
AI summary The equation provided calculates the change in kilowatts (ΔkW) based on the power of a heater (P_heater) and a peak demand savings factor (PCF), divided by 1,000.
Table 302: Unitary Peak Demand Savings Values for Tractor Engine Block Heater Timers Parameter Symbol BER-AR, SBES Reference Peak Coincidence Factor PCF 0.84 As per Subsection 6.10.2 Unitary Peak Demand Savings [kW] ∆𝑘𝑊 Calculation based o...
AI summary Table 302 provides unitary peak demand savings values for tractor engine block heater timers, focusing on the peak coincidence factor (PCF) and unitary peak demand savings (∆𝑘𝑊) based on specification data for each rebated unit. The table references Subsection 6.10.2 for the peak coincidence factor calculation.
The unitary peak demand savings for dairy scroll compressors are calculated using the variables defined and listed in the equation and [Table](#page-45-0) 306 below, as well as variables from [Table](#page-44-0) 304 above. $$\Delta kW = \f...
AI summary The unitary peak demand savings for dairy scroll compressors are calculated using an equation involving variables from Table 306 and Table 304, specifically the formula Δ kW = (Δ kWh × PCF) / HOU.
Table 306: Unitary Peak Demand Savings Values for Dairy Scroll Compressors Parameter Symbol BER-AR, SBES Reference Peak Coincidence Factor PCF Actual As per Subsection 6.10.2 Hours of Use [h/year] HOU Actual Use information in TS Unitary P...
AI summary Table 306 outlines the unitary peak demand savings values for dairy scroll compressors, including parameters such as the peak coincidence factor, hours of use, and unitary peak demand savings. These values are calculated based on specification data for each rebated unit.
The unitary peak demand savings for heat reclaimer units are calculated using the variables defined and listed in the equation and [Table](#page-47-0) 309 below, as well as variables from [Table](#page-46-0) 308 above. $$\Delta kW = (\Delt...
AI summary The calculation of unitary peak demand savings for heat reclaimer units is based on the equation Δ kW = (Δ kWh/HOU) × PCF, using variables defined in Table 309 and Table 308.
Table 309: Unitary Peak Demand Savings Values for Heat Reclaimer Units Parameter Symbol BER-AR, SBES Reference Hours of Use [h/year] HOU Actual or 2,920 Use information in TS Peak Coincidence Factor PCF 0.84 As per Subsection 6.10.2 Unitar...
AI summary Table 309 provides unitary peak demand savings values for heat reclaimer units, including parameters such as hours of use, peak coincidence factor, and unitary peak demand savings. The table references specific subsections and calculation methods for determining these values.
Table 310: Milk Pre-cooler Measure Summary Parameter BER-AR SBES Reference Measure Description and Identification Measure Milk pre-cooler, rebated after installation - Baseline No existing milk pre-cooler - General Parameters Installation...
AI summary Table 310 provides a summary of the Milk Pre-cooler Measure, including parameters such as energy savings adjustment ratios, peak demand savings adjustment ratios, and useful life. The table outlines details related to installation rates, energy savings calculations, and other technical specifications for the measure.
The unitary peak demand savings for milk pre-cooler are calculated using the variables defined and listed in the equation and [Table](#page-49-0) 312 below, as well as variables from [Table](#page-48-0) 311 above. ∆ = (∆ℎ⁄) ×
AI summary The calculation of unitary peak demand savings for milk pre-cooler involves variables defined in equations and tables referenced in the text, specifically Table 312 on page 49 and Table 311 on page 48.
Table 312: Unitary Peak Demand Savings Values for Milk Pre-coolers Parameter Symbol BER-AR, SBES Reference Hours of Use [h/year] HOU Actual or 2,920 Use information in TS Default: Minnesota 2025 TRM316 Peak Coincidence Factor PCF 0.84 As p...
AI summary Table 312 provides unitary peak demand savings values for milk pre-coolers, including parameters such as hours of use, peak coincidence factor, and unitary peak demand savings. The table references specific subsections and default values for calculations.
Table 315: Unitary Peak Demand Savings Values for Milk Vacuum Pumps Parameter Symbol BER-AR, SBES Reference Peak Coincidence Factor PCF 0.84 As per Subsection 6.10.2 Unitary Peak Demand Savings [kW] ∆𝑘𝑊 Calculation based on specification d...
AI summary Table 315 presents unitary peak demand savings values for milk vacuum pumps, including parameters like the Peak Coincidence Factor and Unitary Peak Demand Savings. These values are calculated based on specification data for each rebated unit and referenced to Subsection 6.10.2.
Table 318: Unitary Peak Demand Savings Values for VFD Milk Transfer Pumps Parameter Symbol BER-AR, SBES Reference Peak Coincidence Factor PCF 0.84 As per Subsection 6.10.2 Hours of Use [h/year] HOU Actual or 2,920 Use information in TS Def...
AI summary Table 318 presents unitary peak demand savings values for VFD milk transfer pumps, including parameters such as the peak coincidence factor, hours of use, and unitary peak demand savings. The table references specific subsections and other tables for calculation details.
6.11.2 Peak Demand Savings Factor For kitchen measures, peak demand savings are determined by multiplying the wattage by a PCF value of 68%, which was established as part of the 2015 evaluation of BER.[318](#page-53-3) Freezers and refrige...
AI summary The Peak Demand Savings Factor (PCF) for kitchen measures is 68%, derived from the 2015 BER evaluation, while freezers/refrigerators have a 100% PCF. References include Econoler's 2016 report and a Minnesota Technical Reference Manual.
Summary [Table](#page-55-0) 320 presents a summary of the values used to calculate electrical dishwasher savings. The detailed methodology follows.
AI summary Table 320 summarizes the values used to calculate electrical dishwasher savings, with a detailed methodology provided in the proceeding document.
$$Peak\ Demand\ Savings_{kW} = \ \frac{ES \times PCF}{HOU \times DAYS}$$
AI summary The text presents a formula for calculating peak demand savings in kilowatts, which involves energy savings, a peak capacity factor, hours of operation, and the number of days.
$$Peak \ Demand \ Savings_{kW} = \frac{ES \times PCF}{HOU \times DAYS}$$
AI summary The document presents a formula for calculating peak demand savings in kilowatts, using energy savings (ES), peak capacity factor (PCF), hours of use (HOU), and days. This formula is likely used in energy efficiency and demand-side management contexts.
$$Peak\ Demand\ Savings_{kW} = \frac{ES \times PCF}{HOU \times DAYS}$$
AI summary The document presents a formula for calculating peak demand savings in kilowatts, incorporating factors such as energy savings, peak capacity factor, hours of operation, and the number of days.
Table 331: Unitary Peak Demand Savings Values for Griddles Parameter Symbol BER-AR, SBES Reference Peak Coincidence Factor PCF Actual or 0.68 As per Subsection 6.11.2 Unitary Peak Demand Savings [kW] 𝑃𝑒𝑎𝑘 𝐷𝑒𝑚𝑎𝑛𝑑 𝑆𝑎𝑣𝑖𝑛𝑔𝑠𝑘𝑊 Calculation based...
AI summary Table 331 presents unitary peak demand savings values for griddles, focusing on parameters such as the peak coincidence factor (PCF) and the calculation of peak demand savings in kilowatts (kW) based on specification data for each rebated unit.
The unitary peak demand savings for hot food holding cabinets are calculated using the variables defined and listed in the equation and [Table](#page-64-1) 334 below, as well as variables from [Table](#page-64-0) 333 above. $$Peak\ Demand\...
AI summary The calculation for unitary peak demand savings for hot food holding cabinets uses specific variables defined in equations and tables, including ES, PCF, HOU, and DAYS, as outlined in the document.
$$Peak \ Demand \ Savings_{kW} = \frac{ES \times PCF}{HOU \times DAYS}$$
AI summary The text provides a formula for calculating peak demand savings in kilowatts, using variables such as Energy Savings (ES), Peak Capacity Factor (PCF), Hours of Use (HOU), and Days.
Table 337: Unitary Peak Demand Savings Values for Ice Machines Parameter Symbol BER-AR, SBES Reference Peak Coincidence Factor PCF Actual or 0.68 As per Subsection 6.11.2 Unitary Peak Demand Savings [kW] 𝑃𝑒𝑎𝑘 𝐷𝑒𝑚𝑎𝑛𝑑 𝑆𝑎𝑣𝑖𝑛𝑔𝑠𝑘𝑊 Calculation b...
AI summary Table 337 presents unitary peak demand savings values for ice machines, including parameters such as the peak coincidence factor and unitary peak demand savings. The table references Subsection 6.11.2 and provides calculation details based on specification data for each rebated unit.
$$Peak \ Demand \ Savings_{kW} = \frac{ES \times PCF}{HOU \times DAYS}$$
AI summary The formula provided calculates Peak Demand Savings in kilowatts, using variables such as Energy Savings (ES), Peak Capacity Factor (PCF), Hours of Use (HOU), and Days. This is relevant to demand-side management and energy efficiency calculations.
Table 340: Unitary Peak Demand Savings Values for Ovens Parameter Symbol BER-AR, SBES Reference Peak Coincidence Factor PCF Actual or 0.68 As per Subsection 6.11.2 Unitary Peak Demand Savings [kW] 𝑃𝑒𝑎𝑘 𝐷𝑒𝑚𝑎𝑛𝑑 𝑆𝑎𝑣𝑖𝑛𝑔𝑠𝑘𝑊 Calculation based on...
AI summary Table 340 outlines unitary peak demand savings values for ovens, focusing on parameters like the peak coincidence factor (PCF) and calculation methods for peak demand savings. The table references Subsection 6.11.2 and provides context for how savings are calculated based on rebated unit specifications.
$$Peak \ Demand \ Savings_{kW} = \frac{ES \times PCF}{HOU \times DAYS}$$
AI summary The document presents a formula for calculating peak demand savings in kilowatts, using energy savings (ES), peak capacity factor (PCF), hours of use (HOU), and days. This formula is relevant to demand-side management and energy efficiency calculations.
Table 343: Unitary Peak Demand Savings Values for Steam Cookers Parameter Symbol BER-AR, SBES Reference Peak Coincidence Factor PCF Actual or 0.68 As per Subsection 6.11.2 Unitary Peak Demand Savings [kW] 𝑃𝑒𝑎𝑘 𝐷𝑒𝑚𝑎𝑛𝑑 𝑆𝑎𝑣𝑖𝑛𝑔𝑠𝑘𝑊 Calculation...
AI summary Table 343 outlines the Unitary Peak Demand Savings Values for Steam Cookers, focusing on parameters such as the Peak Coincidence Factor (PCF) and the calculation of unitary peak demand savings in kilowatts (kW). The table references Subsection 6.11.2 of the Technical Reference Manuals (TRMS) for the Peak Coincidence Factor and provides calculation methods for demand savings.
(9) Demand Controlled Kitchen Exhaust
AI summary The section titled 'Demand Controlled Kitchen Exhaust' likely addresses energy efficiency measures for kitchen exhaust systems, potentially linking to Demand-Side Management (DSM) initiatives under Nova Scotia's regulatory framework. It may involve discussions on building efficiency and DSM programs.
Summary [Table](#page-71-0) 344 presents a summary of the values used to calculate electrical demand-controlled kitchen exhaust savings. The detailed methodology follows.
AI summary Table 344 summarizes the values used to calculate electrical demand-controlled kitchen exhaust savings, with a detailed methodology provided afterward.
Table 344: Demand Controlled Kitchen Exhaust Measure Summary Parameter BER-AR SBES Reference Measure Description and Identification Measure Controlled by temperature and/or optical sensors located in exhaust hood, rebated after installatio...
AI summary Table 344 provides a summary of the Demand Controlled Kitchen Exhaust Measure under the Business Energy Rebates - Advanced Rebates (BER-AR) and Small Business Energy Solutions (SBES) programs. It outlines parameters such as measure description, baseline, installation rate, energy savings adjustment ratios, and other technical details.
The unitary peak demand savings for demand controlled kitchen exhaust are calculated using the variables defined and listed in the equation and [Table](#page-72-2) 346 below, as well as variables from [Table](#page-72-0) 345 above. = × ×
AI summary The calculation of unitary peak demand savings for demand controlled kitchen exhaust involves specific variables defined in equations and tables referenced in the document.
Table 346: Unitary Peak Demand Savings Values for Demand Controlled Kitchen Exhaust Parameter Symbol BER-AR, SBES Reference Demand Savings Factor (kW/hp) DSVG 0.58 2026 Pennsylvania TRM Peak Coincidence Factor PCF 0.68 As per Subsection 6....
AI summary Table 346 presents unitary peak demand savings values for demand controlled kitchen exhaust, including parameters such as the demand savings factor and peak coincidence factor, along with their respective values and references.
6.12.2 Peak Demand Savings Factor For laundry measures, peak demand savings are determined by multiplying the wattage by a PCF value of 34%, which was established as part of the 2015 evaluation of BER.[320](#page-72-3)
AI summary The Peak Demand Savings Factor (PCF) for laundry measures is set at 34%, derived from the 2015 evaluation of the Business Energy Rebates (BER) program. This factor multiplies wattage to calculate peak demand savings.
6.12.4 Commercial Laundry Measures
AI summary Section 6.12.4 outlines Commercial Laundry Measures, focusing on energy efficiency and demand-side management (DSM) initiatives for commercial laundry operations in Nova Scotia. Key considerations include appliance retirement, efficiency programs, and regulatory frameworks to reduce energy consumption and costs.
The unitary peak demand savings for commercial heat pump clothes dryers are calculated using the variables defined and listed in the equation and [Table](#page-76-3) 352 below, as well as variables from [Table](#page-76-0) 351 above. $$\De...
AI summary The document explains how to calculate unitary peak demand savings for commercial heat pump clothes dryers using a specific formula and variables from two tables. The formula involves average load, energy efficiency factors, cycle time, a performance correction factor, and quantity.
6.13.2 Peak Demand Savings Factor No standard PCF values have been determined for commercial IT and datacentre measures.
AI summary The document section discusses the absence of established Peak Demand Savings (PCF) values for commercial IT and datacentre measures, indicating a gap in standardization for demand-side management in these sectors.
The unitary peak demand savings for server-based power management software are calculated using the variables defined and listed in the equation and [Table](#page-79-0) 355 below, as well as variables from [Table](#page-78-1) 354 above. $$...
AI summary The document outlines the calculation of unitary peak demand savings for server-based power management software using specific variables from two tables and an equation. It references a technical manual and an Excel file for further details.
The unitary peak demand savings for server virtualization and decommissioning are calculated using the variables defined and listed in the equation and [Table](#page-81-0) 358 below, as well as variables from [Table](#page-80-1) 357 above....
AI summary The calculation for unitary peak demand savings from server virtualization and decommissioning uses equations and data from tables, referencing a technical manual from the Pennsylvania PUC.
7 Effective Useful Life This section outlines the EUL values used to calculate lifetime energy savings. This section also presents EUL values for demand reduction measures; these values are not used to calculate lifetime energy savings sin...
AI summary This section explains Effective Useful Life (EUL) values for calculating lifetime energy savings and cost-effectiveness ratios. It clarifies that EUL values for demand reduction measures differ from those for energy-saving measures, as demand response measures focus on persistent demand reduction rather than energy savings.
7.1 LED Lamps and Fixtures To establish lifetime energy savings for LED lamps and fixtures, the equipment life is determined using rated lifetimes identified in product specification sheets and annual HOU, as described in the equation belo...
AI summary The document explains how to calculate the equipment life of LED lamps and fixtures using rated lifetimes and annual HOU. It also discusses the need for an equivalent EUL to determine lifetime energy savings, considering regulatory changes that shift the baseline to LED over time.
APPENDIX I Detailed Calculations of 2025 Equivalent EUL Values for LED Lamps and Fixtures This appendix presents how the equivalent effective useful life (EUL) of LED lamps and fixtures were established for applicable measures in the BER a...
AI summary This appendix explains how Equivalent Effective Useful Life (EUL) values for LED lamps and fixtures are calculated for BER and SBES programs. It outlines baseline assumptions, noting that LED replacements in general-use categories yield no savings, while early SBES replacements are accepted with a 1-year EUL. The baseline shifts to LED by 2026 for lamps and 2028 for fixtures, impacting EUL calculations for 2025.
ent of Energy, Energy Conservation Standards for General Service Lamps (EISA 2007 Backstop, 45 lm/W) — Enforcement Timelines, National Law Review summary , May 2, 2022 (retail enforcement July 2023). While the latest regulations establishe...
AI summary The text discusses the shift from CFL to LED lamps in Nova Scotia, noting market maturity and implications for EPI programs. It highlights that LED technology is now the standard, with E1's direct-install programs assuming one-year savings from replacing non-LED bulbs, as LED replacements are expected post-2025.
Table 1: Equivalent EUL Calculation for Solar Fixtures Average Replaced Average Wattage of Efficient Lamp Halogen Incandescent Baseline – Replaced Fixture Baseline 1 Year LED Equivalent Baseline 9 Years (W) Lamp (W) Baseline Wattage Displa...
AI summary Table 1 presents an Equivalent Useful Life (EUL) calculation for solar fixtures, comparing halogen incandescent and LED baseline wattages. The table includes data on average replaced wattage and displaced wattage for both fixture types. The text references EfficiencyOne's 2025 DSM Evaluation and a technical reference manual from the Illinois Commerce Commission.
E-12E1 (NSEB) RIRs 1-66 - Redacted
242 passages
E1 Responses to Nova Scotia Energy Board (NSEB) Information Requests NON-CONFIDENTIAL 1 Request IR-01: 2 3 Evidence – Exhibit E-1, pp.1-71 (pdf pp. 8-78) 4 5 Pdf pg. 9 outlines that the Preferred Plan will save 14 GWh of energy through low...
AI summary The document outlines responses to information requests by the Nova Scotia Energy Board (NSEB) regarding energy savings estimates from E1's programming and a Purchase Agreement with NS Power. E1 refers to previous responses for details on savings calculations and requests confirmation of NS Power's agreement with proposed changes.
1 Board (NSEB) decisions and the Public Utilities Act . The NSEB confirmed in its 2025 Benefit 2 Cost Analysis (BCA) Test Decision that "the purpose of the demand-side management provisions in the Public Utilities Act is to reduce electric...
AI summary The NSEB confirmed that the purpose of demand-side management provisions in the Public Utilities Act is to reduce electricity costs for customers. EfficiencyOne (E1) has relied on NSEB decisions and legislation to determine that the 2027–2031 DSM Plan investment of $63.75 million per year is affordable. The 2023–2025 DSM Plan was approved and extended for 2026 with a modest 2% increase due to inflation.
lion for the 2026 one-year extension. The investment of 12 $63.75 million for the 2026 DSM Extension represented a modest increase of 2 percent for 13 inflation from the 2025 approved investment. 14 E1 understands that affordability balanc...
AI summary E1 has maintained the 2026 DSM Extension investment at $63.75 million, with no annual inflationary increases, due to current affordability pressures. This decision reflects a balance between short-term and long-term considerations, acknowledging economic challenges such as rising unemployment, interest rates, and oil prices.
E1 Responses to Nova Scotia Energy Board (NSEB) Information Requests NON-CONFIDENTIAL 1 concluded that maintaining current investment levels - rather than seeking growth - was 2 the appropriate and responsible approach at this time. 3 4 E1...
AI summary E1's 2027–2031 DSM Plan prioritizes customer incentives and long-term affordability, with a focus on maintaining current investment levels rather than pursuing growth. The plan emphasizes customer benefits, including long-term savings and a five-year payback period, while capping spending at previously approved levels. E1 acknowledges that this approach may result in lower long-term energy savings compared to the Integrated Resource Plan.
(a) The following IR response for part (a) (i) has been provided by NS Power. in Excel format with all formulae intact and unaltered. i) Avoided Energy Costs have decreased in the early years because the Base Case (with DSM) had higher car...
AI summary Avoided Energy Costs have decreased in early years due to higher carbon emissions in the Base Case (with DSM) compared to the No DSM Case, leading to increased total carbon costs. The No DSM Case builds more wind capacity in 2027 and 2029 to meet renewable targets. The Equivalent Escalating Series is recommended for normalizing costs over time.
1 Series, the Avoided Cost of Energy has increased between updates for the years 2027- 2 2031. 3 4 Capacity Costs have increased over the entire time horizon due to an increase in 5 market costs, between updates, for new resources selected...
AI summary The Avoided Cost of Energy has increased between updates for the years 2027–2031. Capacity Costs have also increased due to market costs for new resources. EfficiencyOne (E1) uses the Integrated Resource Plan (IRP) process for emissions forecasts and engages an independent consultant to evaluate DSM programs annually, incorporating updated emissions data into its planning cycles.
Heat pump configuration Number of outdoor units Number of indoor units Average price per visit 1 1 $277.97 1 2 $372.71 1 3 $472.73 1 4 $562.14 1 5 $650.44 E1 Responses to Nova Scotia Energy Board (NSEB) Information Requests NON-CONFIDENTIA...
AI summary The document outlines E1's responses to the Nova Scotia Energy Board's information requests regarding heat pump configurations and incentive calculations. E1 assumed an average of two outdoor and two indoor units per customer and provided estimated PAC results for heat pump cleaning measures using a $200 incentive. The calculations were manually performed and are presented as approximations.
- 14 c) Table 2, below, provides an estimate of the IR Griddle Electric 15 measure PAC results if a $1,000/unit incentive is used. These results 16 were not generated by the Guidehouse Process model; rather, they 17 were produced through a...
AI summary Table 2 estimates the IR Griddle Electric measure PAC results using a manual calculation by E1 with a $1,000/unit incentive, as opposed to the Guidehouse Process model. This method uses the same participation data as the DSM Plan but substitutes the incentive amount.
20 i) • For the "Energy Star certified Room Air Purifiers (RAP)" measure under the "Instant Savings" program, investment ranges between $240,800 to $309,600 for each year for the 2027–2031 DSM plan. The payback period for this measure with...
AI summary The 'Energy Star certified Room Air Purifiers (RAP)' measure under the 'Instant Savings' program has an investment range of $240,800 to $309,600 annually for the 2027–2031 DSM plan. The payback period without incentives is 1.24 years.
E1 Responses to Nova Scotia Energy Board (NSEB) Information Requests NON-CONFIDENTIAL 1 large industrial customers, encourage customers to complete energy 2 efficiency projects, and reward them for the time and effort they invest 3 in ener...
AI summary E1 discusses its energy efficiency programs, highlighting increased participation and savings due to incentives. The Strategic Energy Management program rewards customers for long-term engagement, and program costs include service provider fees and customer incentives. These details are outlined in E1's 2027-2031 DSM Plan Application.
E1 Responses to Nova Scotia Energy Board (NSEB) Information Requests NON-CONFIDENTIAL 1 Request IR-05: 25 26 1 Response IR-05: 2 3 (a) 4 i) EfficiencyOne (E1) has not had any further discussions with NS Power or the Nova 5 Scotia Independe...
AI summary EfficiencyOne (E1) has not had discussions with NS Power or the NSIESO since February 2026, but NS Power has acknowledged a request for long-run marginal emissions rates. E1's 2027–2031 DSM Plan Application calculates emissions impacts by multiplying net energy changes by fuel-specific emissions intensities derived from the 2022 Evergreen Integrated Resource Plan (IRP).
1 Demand Response (DR) program component as E1's Evaluator crosschecks all DR 2 participants with a list of NS Power's Time-Varying Pricing and Critical Peak Pricing 3 (CPP) participants. Any E1 Residential DR participant that is participa...
AI summary E1's Demand Response (DR) program excludes participants enrolled in NS Power's Time-Varying Pricing (TVP) pilot, including Time-of-Use (TOU) and Critical Peak Pricing (CPP). This exclusion is due to eligibility criteria and the TVP pilot being interrupted by a cybersecurity breach. E1 will continue to monitor participants to ensure they remain excluded from DR evaluations.
16 i) The budgeted costs for the Residential Behaviour program are noted below: Budget (Millions) 2023 $1.11 2024 $2.22 2025 $2.23 2026 $2.14 1 M10473, Exhibit E-30, E1 2023-2025 DSM Resource Plan Compliance Filing, Appendix A, October 4,...
AI summary The document provides budgeted costs for the Residential Behaviour program from 2023 to 2026, with figures of $1.11M, $2.22M, $2.23M, and $2.14M respectively. The information is sourced from various exhibits and filings related to DSM plans and compliance.
Regarding Section 2.3 "Standardized Filing Framework" of the Application: - (a) Section 2.3.1 "The 2022 Integrated Resource Plan", pdf pgs. 28-29 state: "The Standardized Filing Framework directs that the Resource Plan identified in NS Pow...
AI summary The document discusses the 2022 Integrated Resource Plan (IRP) and its use in developing E1's 2027–2031 DSM Plan. It highlights the need to incorporate findings from NS Power's 2025 IRP Action Plan Update and address the 'Hybrid Peak Electrification Scenario.' The numbers in E1's DSM Plan are lower than those in the IRP, raising questions about alignment and considerations of affordability.
1 2022 Evergreen IRP. Further, on pdf pg. 34 of Exhibit E-1, E1 states: "E1 also 2 modelled a third scenario that reflected energy savings levels consistent with the 3 IRP." 4 • Please identify the estimated DSM investment over 2027-2031 t...
AI summary The text discusses the 2022 Evergreen Integrated Resource Plan (IRP) and requests for information regarding DSM investment estimates, baseline studies, and avoided cost calculations. It also references collaboration between E1 and the NSIESO on IRP activities.
- 3 (a) Yes. For the purposes of informing the development of the DSM Plan, specifically the 4 levels of DSM (energy savings, demand savings and available capacity), EfficiencyOne (E1) 5 understands there to have been no changes to the DSM...
AI summary EfficiencyOne (E1) confirms that the 2025 Integrated Resource Plan (IRP) Action Plan has not changed DSM levels from the 2022 Evergreen IRP Update. E1 modeled energy efficiency and demand response scenarios aligned with the IRP for the 2027–2031 DSM Plan, with investments of $464 million and $47 million, respectively. E1 has not yet commissioned a DSM baseline study, which is planned for a future DSM Potential Study.
1. Overview EfficiencyOne (E1) seeks to deliver an affordable, climate-forward, and reliable energy future for Nova Scotia through efficiency programs. To advance this goal for the 2027-2031 Demand Side Management Plan (2027-2031 Plan), E1...
AI summary EfficiencyOne (E1) seeks to deliver an affordable, climate-forward, and reliable energy future for Nova Scotia through efficiency programs. Apex Analytics recommends a net annual incremental electricity savings target range of 0.8%-1.0% for the 2027-2031 Demand Side Management Plan, considering program costs, affordability, and jurisdictional differences.
Table 2 . Savings Estimate from Weighted Jurisdictional Model Approach Jurisdiction Score Savings Weight Weighted Savings New Brunswick 86.85 0.46% 0.114 0.05% Prince Edward Island 82.04 1.11% 0.108 0.12% Maine 72.25 0.86% 0.095 0.08% Newf...
AI summary Table 2 presents savings estimates using a weighted jurisdictional model approach, showing an average annual savings level of approximately 0.90%. The weighting prioritizes jurisdictions comparable to Nova Scotia in program structure, budget scale, and regulatory context. Based on this, a recommended savings range of 0.8%-1.0% was established, considering variability in acquisition costs, program maturity, and affordability conditions.
B. Sector Comparisons With respect to the savings split between Business, Non-Profit, and Institutional (BNI) and Residential sectors, Apex analyzed variations across jurisdictions in terms of savings from each of the sectors. Table 3 show...
AI summary Apex's analysis of energy efficiency savings across jurisdictions highlights that BNI savings are more cost-effective than residential savings. New Brunswick's energy efficiency goals are increasing and are funded through a mix of federal, provincial, and ratepayer sources, with programs ultimately benefiting citizens regardless of funding source.
1 Request IR-09: 2 3 Evidence – Exhibit E-1, pp.1-71 (pdf pp. 8-78) 4 5 (a) Pdf pg. 32 states that 71% of the Preferred Plan is for customer incentives. Please confirm, 6 or explain otherwise, that it is approximately $239.1 million for cu...
AI summary The document discusses a request (IR-09) regarding the 2027–2031 DSM Plan, specifically questioning the allocation of customer incentives. The response indicates that customer incentives amount to approximately $225.01 million, or 70.6% of the total investment of $318.75 million.
Request IR-10: Evidence – Exhibit E-1, pp.1-71 (pdf pp. 8-78) - Pdf pg. 32 states that the Preferred Plan's energy savings will reduce 0.8% of NS Power's load. - Please confirm, or explain otherwise, that the 0.8% is the expected total cum...
AI summary The document addresses a request regarding the interpretation of energy savings from the Preferred Plan, clarifying that the 0.8% refers to cumulative load reduction from 2027–2031, not annual or 2025 load. NS Power confirms this is based on their forecast for the multi-year period.
M12349, Nova Scotia Power, 2025 Load Forecast Report, June 27, 2025, page 10. Year First Year Net Savings Energy Savings (GWh) 2025 NS Power Load Forecast1 (GWh) First Year Net Savings Energy Savings % of Load 2027 121 11,193 1.1% 2028 101...
AI summary The document discusses Nova Scotia Power's 2025 Load Forecast Report, highlighting energy savings projections from 2027 to 2031 and referencing EfficiencyOne's preferred plan, which aligns with the Integrated Resource Plan while prioritizing short-term affordability. It also mentions the demand response design in the 2027–2031 DSM Plan, informed by various factors including modeling assumptions and stakeholder feedback.
from the Demand Response program are a result of "C&I Curtailment" and "C&I Loadshift to BUGs". Please confirm. - If not confirmed, please explain in the context of the Figures contained in the tabs. - If confirmed: - a) Please describe th...
AI summary The text asks whether spending from the Demand Response program is attributed to 'C&I Curtailment' and 'C&I Loadshift to BUGs'. If confirmed, it requests reasons for the higher spending on 'DLC – Thermostats' and 'DLC – Water Heating' compared to the other components, and the cost per MW saved for each program component from 2027 to 2031. It also references a Board decision and ongoing discussions between E1 and NS Power regarding program overlap and collaboration.
13 Table 1: Demand Response Non-Incentive Cost Considerations Cost Category E1 Cost Considerations Program Administration Annual costs associated with program management, including E1 staffing, overhead, and evaluation activities. Updated...
AI summary The table outlines non-incentive cost considerations for demand response programs, including program administration, delivery, marketing, and technology enablement. It highlights updated assumptions and cost-sharing opportunities, informed by current contracts and future cost changes.
1 Table 2: Annual Residential and BNI DR PAC results Year PAC - Res DR PAC - BNI DR 2027 0.9 2.9 2028 0.5 1.6 2029 0.8 2.7 2030 0.7 2.3 2031 0.6 2.4 2
AI summary Table 2 presents the annual results of the Residential and BNI DR PAC from 2027 to 2031, showing the performance metrics for each year. The data includes metrics for both residential and BNI DR PAC, with values ranging from 0.5 to 2.9.
13 Table 4: Residential and BNI Demand Response participation (2024 – 2025) Residential DR BNI DR 2024 353 76 2025 3,676 143 14
AI summary Table 4 presents the participation numbers for Residential and BNI Demand Response programs in 2024 and 2025, showing a significant increase in participation from 2024 to 2025 for both programs.
15 (g) 16 i) The PAC result with "DLC – Thermostat" excluded is 2.18. This reflects BNI DR and 17 residential water heating from the Preferred Plan.
AI summary The PAC result of 2.18 is calculated without the 'DLC – Thermostat' and includes BNI DR and residential water heating from the Preferred Plan.
E1 Responses to Nova Scotia Energy Board (NSEB) Information Requests NON-CONFIDENTIAL reflects the cost of maintaining and improving the existing residential DR platform, preserving residential demand-side flexibility, and supporting conti...
AI summary The text discusses the cost of maintaining and improving the residential demand-side management platform, emphasizing the importance of preserving demand-side flexibility and supporting operational improvements to contribute to peak reduction and system resilience.
Table 5: $ Spent / MW by DR Program Component Voor DLC - DLC - Water C&I Curtailment C&I Loadshift to Year Thermostats Heating Concurtaiiment BUGs 2027 544,148 457,978 185,246 185,481 2028 552,325 355,485 180,880 181,174 2029 560,343 367,7...
AI summary Table 5 presents the cost per megawatt (") spent on various demand response (DR) program components, including DLC-Thermostats, DLC-Water, C&I Curtailment, and C&I Loadshift to BUGs, from 2027 to 2031. The data shows increasing costs over the years for each component.
(h) i) Please refer to E1's response to NSEB IR-06. 11 10 ii) E1 does not have a specific timeline identified on when this issue will be resolved. 13 12 14 (i) E1 confirms that the Innovation allocations identified under both the "Demand R...
AI summary The text references E1's response to an information request and confirms that investment allocations under 'Demand Response' and 'Locational DSM' include various key activities outlined in an appendix. E1 does not provide a specific timeline for resolving the issue.
13 DSM Plan Lifetime Benefits Period DSM Plan Lifetime Benefits ($M) 2027–2031 $229.4 2032–2036 $261.2 2037–2041 $121.5 2042–2046 $60.5 2047–2051 $9.1 2052–2056 $0.5 2057–2061 $0.2 Total: 2027–2061 $682.5 1 Request IR-15: 2 3 Evidence – Ex...
AI summary The document discusses the 2027–2061 DSM Plan Lifetime Benefits and includes an information request (IR-15) regarding strategic electrification feedback from DSMAG members and the Enabling Strategies budget allocation. E1 responds by referring to a previous response to NSEB IR-16.
Focus Area — DSM Direct Expenditure ($) rocus Area — 2027 2028 2029 2030 2031 Total ($) Demand Response 160,650 178,815 123,175 110,250 111,500 684,390 Demand Flexibility 183,600 204,360 221,715 198,450 200,700 1,008,825 Strategic Electrif...
AI summary The table outlines the projected DSM Direct Expenditure from 2027 to 2031, detailing allocations for various initiatives such as Demand Response, Demand Flexibility, Strategic Electrification, Market Transformation, and Locational DSM, with total expenditures reaching $2,349,600.
4 7 Additionally, Table 2: Key Activities by Focus Area of Appendix A, Attachment 5 8 provides the innovation goals, justification and key activities for each of the key 9 focus areas, inclusive of strategic electrification.
AI summary The text references Table 2 in Appendix A, Attachment 5, which outlines innovation goals, justifications, and key activities for each focus area, including strategic electrification.
1 M09096, Document No. 84486, DSMAG Revised Terms of Reference, September 20, 2021, page 7 1 Request IR-16: 23 • E1's total employee benefits burden 24 • The total spent on E1 staff training in 2023, 2024, and 2025. 25 26 1 vii) Please ide...
AI summary The document outlines several information requests related to EfficiencyOne (E1), including details on employee benefits, staff training expenditures, and staffing forecasts for future years. It also questions discrepancies in salary and training expenses between the 2026 DSM Extension and the 2027–2031 Preferred Plan.
17 DSM Benefit Costs increases correspond to the statutory rates applicable (EI and CPP) 18 and related salary costs for each year.
AI summary The text discusses how increases in DSM benefit costs are tied to statutory rates (EI and CPP) and related salary costs for each year.
In thousands of dollars 2026 2027 2028 2029 2030 2031 DSM Salary Costs $ 9,809 $ 9,745 $ 10,124 $ 10,486 $ 10,908 $ 11,367 8
AI summary The table shows the projected DSM Salary Costs in thousands of dollars from 2026 to 2031, with figures increasing over the years.
12 DSM Benefit costs are forecast to increase in alignment with DSM Salary costs.
AI summary The document notes that DSM benefit costs are expected to rise in line with DSM salary costs.
In thousands of dollars 2026 2027 2028 2029 2030 2031 DSM Training & Development Costs $ 322 $ 199 $ 203 $ 207 $ 211 $ 215 13
AI summary The table outlines projected costs for DSM Training & Development from 2026 to 2031, showing a gradual decrease from $322,000 in 2026 to $199,000 in 2027, followed by a slight increase each subsequent year.
14 DSM Training and development costs are forecast to increase by 2 percent related to 15 inflation. 16 17 viii) Salary and benefit costs from the 2026 DSM Extension compared to 2027 have 18 decreased by $76,000. Training and development c...
AI summary The document discusses projected increases in DSM training and development costs due to inflation, as well as decreases in salary and benefit costs for the 2026 DSM Extension compared to 2027, along with a reduction in training and development costs.
1 increased due to year over year salary adjustments and benefit increases projected 2 at 4 percent per year. 3 ix) 4 • E1 did not conduct a benchmarking study that compared E1's total forecasted 5 staffing complement, salary burden, emplo...
AI summary The document discusses salary and benefit increases projected at 4% per year and the lack of benchmarking studies conducted by E1 for its DSM Plan. It also outlines the risk associated with benefits in the Preferred Plan and how bill impacts are shown for different customer types.
revised Figure 6 showing both Participants and Non-Participants. Residential Small General General Large General Small Industrial Medium Industrial Large Industrial Municipal DSM (All Resources) 3.69% 4.19% 3.92% 2.89% 3.47% 1.60% 4.70% 2....
AI summary Revised Figure 6 presents participation rates across various customer segments for DSM, Energy Efficiency, Demand Response, and Solar PV programs. The data shows varying levels of participation, with some segments showing negative contributions, particularly in Demand Response.
7 Table 2: Residential and BNI Annual Percent Participation (2021 – 2025) Year Residential Annual Participation BNI Annual Participation 2021 25% 31% 2022 24% 32% 2023 24% 31% 2024 36% 33% 2025 34% 47% 8
AI summary Table 2 provides the annual percent participation rates for residential and BNI programs from 2021 to 2025, showing an increasing trend in both categories, with BNI participation rising significantly in 2025.
9 ii) • DSM activities reduce rates relative to a No DSM alternative when their downward impacts exceed any upward impacts. Downward impacts come from avoided costs, while upward impacts include program cost recovery and lost revenues. 14
AI summary DSM activities can lower rates compared to a No DSM alternative when the avoided costs exceed the program cost recovery and lost revenues.
10 • Refer to Appendix B – Attachment 9, tab 'Inter-class Outputs', cell AZ59. 11 The following notes will assist with reviewing the calculation: 12 Columns AY:BG represent the Base Scenario (No DSM) 13 Columns BI:BP represent the Alternat...
AI summary The text references a calculation error in a model where the Alternate Scenario (DSM) is incorrectly labeled as the 'Base Scenario' in the 'Inter-class Outputs' tab, cell AZ59 of Appendix B – Attachment 9.
15 The following selections must be made in the 'Inter-class Outputs' tab 16 starting at cell C1 for the scenario to match the Historical RBIA (2011 – 2026 17 activities): Base Scenario Alt. Scenario Energy Efficiency No Yes Demand Respons...
AI summary The document outlines two scenarios for the 'Inter-class Outputs' tab in a regulatory proceeding, with the 'Base Scenario' excluding Energy Efficiency and Demand Response, while the 'Alt. Scenario' includes these. Both scenarios use the same historical period (2011-2026) and cost scenario (1).
Highly effective at change management: Composite measure of respondents who scored an average of 4.5 or higher when asked to rate the effectiveness of leaders at their organization on the following activities (scored on a six-point scale):...
AI summary The text highlights a composite measure of respondents who rated leaders' effectiveness in change management activities, such as communicating decisions, navigating difficult conversations, and managing change reactions, with an average score of 4.5 or higher on a six-point scale.
Date Filed: May 28, 2026 NSEB-17, Attachment 1, Page 46 of 46 REDACTED 1 Request IR-18: 2 3 Evidence – Exhibit E-1, pp.1-71 (pdf pp. 8-78) 4 5 Reference to Exhibit E-1, page 44 of 71 (pdf pg. 51), Figure 6: Average Rate and Total Customer...
AI summary The document discusses two requests related to the 2027-2031 DSM Plan. The first request asks for an explanation of why the Municipal Rate Class shows no total customer bill impact in Figure 6, which is attributed to a negligible -0.04% impact. The second request seeks a detailed summary of stakeholder feedback regarding increased program delivery costs and reduced savings from residential heat pump evaluations.
23 only confidential). 1 c) E1 is providing the Board approved Incentive Setting Methodology that 2 E1 follows as Attachment 1.1 This matter was subject to a regulatory 3 proceeding under Matter 07544 which was approved by the Board in Jul...
AI summary E1 is providing the Board approved Incentive Setting Methodology as Attachment 1.1. This matter was subject to a regulatory proceeding under Matter 07544, approved by the Board in July 2017. E1 also provides internal audits conducted since 2023 and a comparison of diversification in various DSM Plans.
Incentive Setting for Energy Efficiency Programs Energy conservation programs feature different types of incentives to attract participation. The underlying theory behind the design of energy conservation programs is that some energy effic...
AI summary Energy conservation programs use incentives to overcome barriers such as cost, time, and lack of knowledge. The three main types of incentives are financial, convenience, and educational/technical assistance. Financial incentives are the most common in utility and government-sponsored programs to help residential and business customers make energy-efficient choices.
Table 2: Incremental Equipment Cost Scenarios Scenario General Description New Purchase/Installation A customer may decide to make a new purchase for a technology or service. There is not a current technology or service in use. For example...
AI summary This table outlines the 'New Purchase/Installation' scenario, where a customer purchases a new technology or service without existing infrastructure. It defines the standard technology as the most popular or commonly used option, or non-existent in some cases. Incremental Equipment Costs are calculated as the difference between the efficient option and the base case.
Customer Research A critical component of determining participant perceived value is actually asking potential customers what they would pay for a product or service, and what their price points are for difficult technology options. Additi...
AI summary Customer research is essential to understand price points and barriers to adopting energy-efficient technologies. While financial incentives may encourage adoption, other factors like product quality and environmental concerns can hinder it. The principal-agent problem arises in rental units, where tenants and landlords have differing motivations and responsibilities regarding energy efficiency.
Supply Chain and Stakeholder Discussion In designing and delivering any best-in-class energy efficiency program, it is important to involve the supply chain and key stakeholders such as industry associations, other government agencies and...
AI summary The text emphasizes the importance of involving the supply chain and stakeholders in energy efficiency programs to ensure effective delivery, identify market barriers, and align incentives. It highlights the need for stakeholder input in incentive-setting, program design, and awareness of existing market incentives.
Benchmarking If an incentive or technology is new, there may not be any historical data to assist with forecasting price and penetration curves in a utility's local market. Benchmarking incentive rates against similar technologies or progr...
AI summary Benchmarking is used to forecast price and penetration curves for new incentives or technologies when local data is unavailable. Comparing incentives across jurisdictions, such as Nova Scotia and Maine, requires adjustments for factors like currency exchange rates. Engaging with other jurisdictions is important to understand market and program delivery nuances.
Table 4: Cost Effectiveness Tests and Relationship to Incentive Setting from a Return on Investment Perspective Cost Effectiveness Test General Description and Features Implication for Incentive Setting The TRC is an evaluation of the tota...
AI summary The table outlines the Total Resource Cost (TRC) as a cost-effectiveness test, which evaluates the total benefits and costs of energy efficiency programs. It explains that TRC considers both energy and non-energy benefits, and that program administration costs are separate from participant costs, which exclude incentives. The TRC should align with guidance from Nova Scotia's DSM Advisory Group.
The Importance of Education and Awareness In almost all cases, education and awareness initiatives play a key role in motivating the customer to make a purchase decision. While educational incentives are not specifically discussed in this...
AI summary Education and awareness initiatives are crucial in motivating customer participation in energy efficiency programs by removing both financial and non-financial barriers. These initiatives help customers understand the benefits of energy-efficient measures and can lead to reduced incentive levels when customers make informed decisions.
FINDINGS AND IDENTIFIED BEST PRACTICES Our jurisdictional research has shown that the majority of jurisdictions employ similar methodologies and approaches to setting incentives. All of the jurisdictions have broad program design, TRM and/...
AI summary The jurisdictional research highlights that most regions use similar methodologies for setting incentives, though no single consolidated process exists. EfficiencyOne already performs many of these steps, so the recommendations focus on detailed nuances. The process involves program design, TRM, and market research, with analysis conducted in parallel rather than sequentially.
Table 7: Research Engagement Phase Research and Engagement Phase The Energy Trust of Oregon will examine other jurisdictions' incentive rates when introducing new measures to its portfolio. For weather sensitive measures, it will examine j...
AI summary The Energy Trust of Oregon plans to examine incentive rates in other jurisdictions when introducing new measures to its portfolio, with a focus on weather-sensitive measures and jurisdictions with similar annual weather conditions.
RESIDENTIAL SECTOR There are more than 390,280 residential households in Nova Scotia. 15 The majority of customers are on flat-billing residential electricity purchase agreements. Only 1,000 customers are on residential time-of-use pricing...
AI summary The residential sector in Nova Scotia consists of over 390,000 households, with most on flat-rate electricity plans. Lighting and heating systems are largely inefficient, with incandescent lamps and fuel oil dominating. There is significant potential for energy efficiency improvements, particularly in heating and lighting. Cooling needs are minimal, and water heaters are mostly electric, offering further efficiency opportunities.
ACHIEVABLE POTENTIAL In 2014, Navigant Consulting conducted an achievable potential study for Nova Scotia, (Nova Scotia 2015-2040 Demand Side Management (DSM) Potential Study) 17 . It indicated that the achievable potential and required ex...
AI summary In 2014, Navigant Consulting conducted an achievable potential study for Nova Scotia, focusing on the 2015-2040 Demand Side Management (DSM) Potential Study. The study outlined the achievable potential and required expenditure for the years 2016, 2017, and 2018.
Current Programs Mass Market programs (programs that do not target individual customers specifically) cover all types of program scenarios. For example, a retail program can cover all four of these scenarios (New Purchase/Installation, Rep...
AI summary The text discusses mass market programs that apply broadly to all customer scenarios, such as new purchases, replacements, and failures, without excluding any customer based on category. CLEAResult and EfficiencyOne have outlined the predominant scenarios considered in the program design in Table 15.
18 Email Communication from EfficiencyOne Program Management Staff – May 25, 2016 Program Identified Barriers Incentive Strategy Custom Program 1) Commercial and industrial customers have measures that are not included in the prescriptive...
AI summary This email communication discusses a custom program under EfficiencyOne, highlighting barriers such as the exclusion of certain commercial and industrial measures from prescriptive programs. It outlines an incentive strategy allowing eligible projects outside prescriptive programs to undergo studies verifying energy savings and costs.
esearchgate.net/profile/Heidi_Korhonen3/publication/48330473_Determinants_to_Service_Innovation_Success_an_Organization al_Orientation_Perspective/links/0046353c383c558013000000.pdf#page=182 - 3. At what price would you consider the produc...
AI summary This text discusses the Price Sensitivity Meter, a method used to determine acceptable pricing ranges for products or services based on consumer responses. It uses cumulative distribution curves to identify upper and lower boundaries for acceptable prices, such as the Price of Marginal Expensiveness (PME) and Price of Marginal Cheapness/Inexpensiveness (PMI). These metrics help set incentives based on consumer perceptions.
SUPPLY CHAIN AND SERVICE PROVIDER RESEARCH The supply chain and service providers should be engaged to support the customer and technology research efforts. It may be difficult to directly contact customers and technology manufacturers to...
AI summary The document emphasizes the importance of engaging supply chain and service providers in customer and technology research, as well as in incentive setting and program design. These entities can provide valuable insights, facilitate research, and help identify barriers to program implementation.
Basis for Customer Cost Incentive Threshold Customer and Decision Suggested Basis Suggested Upper Limit Low Income Customer, Direct Install Model Project Cost 100% Residential Customer, Small Purchase at Retailer Retail Price, Incremental...
AI summary The document outlines the suggested basis and upper limits for customer cost incentive thresholds for various customer types and decision models, including low-income customers, residential, and commercial and industrial customers.
JURISDICTIONAL BENCHMARKING Jurisdictional benchmarking is not essential for existing incentives. The current program performance, historical experience and recommended research should provide a comprehensive analysis for incentive setting...
AI summary Jurisdictional benchmarking is not essential for existing incentives as current program performance and historical data provide sufficient analysis. However, it is recommended for new incentives to understand what other jurisdictions offer and how factors like market size and delivery approaches influence incentive levels.
GENERAL PORTFOLIO SUMMARY FOR CURRENT AND RECOMMENDED ACTIVITIES General Principle Current Activities Recommended Activities
AI summary The document presents a general portfolio summary comparing current and recommended activities. It outlines principles and activities related to energy efficiency, demand-side management, and other programs. The summary provides a framework for evaluating current initiatives and suggesting potential improvements.
http://energy.novascotia.ca/sites/default/files/Our-Electricity-Future.pdf General Principle Current Activities Recommended Activities Understand Supply Chain and Service Provider Considerations EfficiencyOne interacts with the supply chai...
AI summary The document discusses EfficiencyOne's current engagement with the supply chain and service providers through program management, annual surveys, and specialized research. It recommends maintaining the current engagement methods and optionally developing program-specific advisory panels.
Understand Technology Savings, Price and Market Penetration For Instant Savings, EfficiencyOne gains an understanding of technology savings, price and penetration through the following activities: 1. Energy Efficiency Standards (Regulation...
AI summary EfficiencyOne uses energy efficiency standards, program evaluation, industry data, and specific studies to understand technology savings, price, and market penetration for the Instant Savings Program. It proactively updated the program by eliminating CFLs in 2014 and continues to engage with retailers for market insights. CLEAResult recommends continuing current activities and implementing general principles to support the program.
Program Benchmarking When the Custom Retrofit program was designed in 2008, the initial incentive was designed using a $/kWh incentive rate based on a similar program by Manitoba Hydro. It was unknown what incentive level customers in Nova...
AI summary The Custom Retrofit program, designed in 2008, initially used a \/kWh incentive rate based on Manitoba Hydro's program. Over time, through customer feedback and program experience, this rate now serves as a ceiling for individually negotiated incentives.
updated, consistent with the recommendations in the General Principles section. Understand Supply Chain and Service Provider Considerations For the Custom Program, EfficiencyOne gains an understanding of the supply chain and service provid...
AI summary The document discusses how EfficiencyOne gains understanding of supply chain and service provider considerations through program management and evaluation. It also outlines how financial impacts are assessed through project screening, program management, and evaluation. CLEAResult recommends continuing current activities and implementing general principles, including expanding cost-effectiveness screening.
Electricity Market The following entities are the key players in the electricity system in Ontario. - Ontario Government Ministry of Energy - Ontario Energy Board (OEB) - Independent Electricity System Operator (IESO) - 72 Local Distributi...
AI summary The document outlines key players and responsibilities in Ontario's electricity market, including the Ministry of Energy, Ontario Energy Board (OEB), Independent Electricity System Operator (IESO), and Local Distribution Companies (LDCs). The IESO manages conservation efforts, sets savings targets, and oversees program delivery, while the OEB regulates LDCs and reviews rate applications.
APPENDIX A-2: ONTARIO GAS (UNION GAS) Program Name Program Area Program Measures Links Retrofit Custom and cost effectiveness. This program was designed to be for larger projects in the commercial and industrial sector, and to capture any...
AI summary The Retrofit Custom program is designed for larger commercial and industrial projects, offering incentives based on kW or kWh savings, with lighting savings receiving a lower rate. Incentives are capped at 50% of the total cost, and an M&V Plan is required for approval. Recent updates have removed the \/kW incentive rate.
MARKET STRUCTURE OVERVIEW DSM is a core part of the conservation first policy in Ontario as per the 2013 Long-Term Energy Plan. In 2014, the Minister of Energy issued a directive to the Ontario Energy Board (OEB) for the development of a n...
AI summary The document outlines the DSM framework in Ontario, developed by the OEB in 2014 as part of the conservation first policy. It emphasizes cost-effective DSM, coordination with electricity CDM, and the role of gas utilities in program design, budgeting, and reporting. The OEB oversees program evaluation and mid-term reviews to ensure compliance and effectiveness.
PORTFOLIO MATURITY AND HISTORICAL PERFORMANCE DSM of natural gas has been practiced in Ontario for 21 years. The previous DSM Guidelines (EB-2008-0346) were in place from June 2011 regarding development of new multi-year DSM plans for the...
AI summary The document discusses the history and maturity of DSM for natural gas in Ontario, referencing past guidelines and decisions from the OEB. It mentions the previous DSM Guidelines and the Generic DSM Proceeding, highlighting the timeline and principles followed by gas utilities.
Year Annual Savings (m³) Costs ($) 2012 137,438,488 31,322,216 2013 179,966,564 32,838,926 2014 30,091,000(Budget) 3 Ontario Energy Board, Multiple documents from: "Natural Gas Demand Side Management," [http://www.ontarioenergyboard.ca/oeb...
AI summary The text presents a table of annual savings and costs for a program from 2012 to 2014, citing the Ontario Energy Board. It also includes a table showing the TRC Ratio by program category for 2012-2013, with data for various sectors such as residential, commercial/industrial, and low-income.
The gas utilities have developed and submitted their annual DSM program budgets for all proposed programs for OEB approval 2015-2020. The budgets are comprehensive including financial, marketing and communications, administration and staff...
AI summary The gas utilities submitted annual DSM program budgets for 2015-2020 for OEB approval. The budgets include financial, marketing, administration, staffing, and evaluation components. The OEB approved these budgets with modifications.
Approved Approved Annual D SM Budgets Utility 2014 (Actuals) 2015 2016 2017 2018 2019 2020 2015-2020 Total Enbridge $ 32,511,266 $ 37,722,230 $ 56,361,117 $ 62,933,844 $ 67,554,087 $ 66,421,773 $ 67,757,376 $ 358,750,427 Union $ 33,713,172...
AI summary The document presents approved annual DSM budgets for Enbridge and Union from 2014 to 2020, along with overhead budgets and performance metrics. The gas utilities have developed targets and incorporated a weighted scorecard approach to evaluate program performance, emphasizing natural gas savings and broader conservation priorities.
Figure 22: Union Gas Scorecar[d](#page-37-0) 4 Union Resource Acquisition Low- Income Large Volume Market Transformation Performance- based Cumulative natural gas savings metric weight 75% 100% 100% 0% 0% Other metric weight 25% 0% 0% 100%...
AI summary Union Gas proposed other metrics targeting various aspects of their programs, including resource acquisition, low-income initiatives, large volume programs, market transformation, and performance-based metrics. The proposed metrics have different weightings assigned to them.
Figure 23: Union Gas Targets & Performance Metric[s](#page-37-0) 4 Resource Acquisition Scorecard Metric Units Weight 2016 Target Metrics and Targets Metrics and Targets Cumulative Savings CCM (millions) 75% 1,110 Home Reno Rebate Particip...
AI summary The text presents Union Gas's performance metrics and targets for various programs, including cumulative savings, participant numbers, and energy efficiency initiatives. These metrics are organized into scorecards such as Resource Acquisition, Low Income, Market Transformation, and Performance Based, with specific targets for years 2016 and 2017-2018.
Technical Reference Manual The EC reviews and proposes updates to the OEB with regards to data within the TRM. This occurs yearly. This review and update includes input assumptions to reflect the findings of the annual DSM evaluation and a...
AI summary The Evaluation Contractor (EC) annually reviews and updates the Technical Reference Manual (TRM) for the Ontario Energy Board (OEB), incorporating findings from the annual Demand Side Management (DSM) evaluation and audit, as well as additional research on new technologies.
Cost Effectiveness Requirements The gas utilities' overall DSM goals are to achieve all the cost-effective DSM available in its market. The OEB determined that cost effectiveness should be based on the Total Resource Cost-plus (TRC-plus) t...
AI summary The gas utilities are required to achieve all cost-effective Demand Side Management (DSM) in their market. The OEB uses the Total Resource Cost-plus (TRC-plus) test for screening programs, with lower requirements for low-income programs and no cost-effectiveness test for market transformation programs and pilots.
2. Technical Reference Manuals The Technical Evaluation Committee approve/deny measures for TRMs which are used for savings and assumptions and enables Union Gas to include solutions in programs. Measures with large savings potential can w...
AI summary The Technical Evaluation Committee approves or denies measures for Technical Reference Manuals (TRMs), which are used for savings and assumptions, enabling Union Gas to include solutions in programs. Measures with significant savings potential may qualify for higher incentive levels.
3. Benchmarking Union Gas also reviews other jurisdictions and evaluates their measures and incentives relative to what is offered in other territories. The goal is to be relatively similar to other territories in their incentives. Other f...
AI summary Union Gas reviews other jurisdictions to evaluate their measures and incentives, aiming to align with similar territories. Factors such as Incremental Equipment Costs are considered in this benchmarking process.
4. Incremental Cost Design Based on the market research and technology, Union will attempt to incentivize a portion of the incremental cost determined to motivate customers to implement. Typically, this has fallen between 25-35 percent of...
AI summary Union plans to incentivize 25-35% of incremental costs to encourage customer implementation. Incremental costs are calculated as the difference between the measure cost and standard measure cost for measures with base cases, and as the full measure cost for those without base cases.
EXISTING MAIN PROGRAMS – UNION GAS [4](#page-37-1) Program Area Program Name Description Incentives Links Resource Acquisition C&I Prescriptive Program provides customers rebates for a list of recommended efficient technologies and equipme...
AI summary The document outlines existing main programs by Union Gas, including prescriptive and custom incentive programs for commercial and industrial customers aimed at promoting energy efficiency through rebates and incentives based on energy savings.
Figure 27: Planned Energy Savings in F2020 (GWh/yr) [4](#page-46-0) Codes and Standards Rate Structures Programs Total Residential 2,760 980 1,070 4,810 Commercial 500 390 1,480 2,370 Industrial 110 730 2,590 3,430 Total 3,370 2,090 5,150...
AI summary The text presents two figures showing planned energy and capacity savings in F2020, categorized by residential, commercial, and industrial sectors. The figures include savings from codes and standards, rate structures, and programs, with total savings across all sectors.
Figure 29: Cumulative GWh/Year following the 2008 BC Energy Plan [4](#page-46-0) GWH/YEAR F2008 F2009 F2010 F2011 F2012 Target 295 761 1,700 2,300 3,500 Actual 326 983 1,778 2,348 BC Hydro has developed annual cumulative targets using the...
AI summary Figure 29 shows the cumulative GWh/year targets and actuals for the 2008 BC Energy Plan from 2008 to 2012. BC Hydro used the Conservation Potential Review and other DSM tools to develop annual targets.
INCENTIVE LEVEL-SETTING METHODOLOGY The following is a rough sketch of what we have seen in other territories. BC Hydro is responsible for setting incentive levels for their programs and introducing new measures and programs. This is perfo...
AI summary The document outlines BC Hydro's methodology for setting incentive levels for demand-side management programs, typically reviewed every two to three years through business cases.
1. Benchmarking BC Hydro reviews other jurisdictions and evaluates their measures and incentives relative to what is offered in other territories. Other factors such as Incremental Equipment Costs are investigated. Benchmarking is usually...
AI summary BC Hydro evaluates other jurisdictions' measures and incentives, considering factors like Incremental Equipment Costs, typically by contacting utilities directly for benchmarking purposes.
2. Market Research Market research depends on the sector/incentive. It can either be achieved by broad primary research or by one-onone consultations for larger customers. The objective is to determine awareness, barriers and purchase deci...
AI summary Market research methods depend on the sector and incentive, involving either broad primary research or one-on-one consultations for larger customers. The goal is to assess awareness, barriers, and purchase decisions.
3. Technical Reference Manuals The engineering team, M&V team, program managers, evaluation group and other in-house BC Hydro resources approve/deny measures for TRMs which are used for savings and assumptions. They enable BC Hydro to incl...
AI summary Technical Reference Manuals (TRMs) are used by BC Hydro's engineering and program management teams to approve or deny measures, enabling the inclusion of solutions in programs. All proposed incentives undergo a governance process for technical and business review.
4. Incremental Cost Design Based on the market research and technology, BC Hydro will attempt to incentivize a portion of the incremental cost determined to motivate customers to implement. Typically, 50-75 percent of incremental costs hav...
AI summary BC Hydro plans to incentivize 50-75% of incremental costs to encourage customers to implement energy efficiency measures. The incremental cost calculation varies depending on the measure type, such as 'Replace on Burnout' or 'Retrofit/Direct Install,' and considers factors like technology life expectancy.
Calculating Cost Effectiveness Cost effectiveness analysis is performed by looking at the stream of benefits and costs resulting from the DSM investment. Four metrics are calculated for each test: - 1. Benefit-cost ratio = PV (benefits) /...
AI summary The text outlines the calculation of cost effectiveness in Demand Side Management (DSM) investments using four metrics: benefit-cost ratio, net present value, and gross levelized cost. These metrics evaluate the financial impact of DSM initiatives by comparing the present value of benefits and costs.
- 4. Net Levelized cost ($/kWh)1 = PV (costs all benefits except for electric energy benefits) / PV (energy savings) Benefits Costs Avoided electric energy costs Avoided electric capacity costs Avoided non-electric fuel costs Customer non-...
AI summary The document outlines the net levelized cost calculation for energy programs, highlighting benefits such as avoided electric energy and capacity costs, and non-electric fuel savings, while considering various costs including utility program costs, overhead, and customer expenses.
APPENDIX A-4: CALIFORNIA (PG&E) Program Type Programs Details High Performance Building The objective of this program is to acquire energy savings by reducing the energy intensity of new commercial buildings through more efficient design a...
AI summary This appendix describes a California (PG&E) program aimed at reducing energy intensity in new commercial buildings through efficient design and construction. It includes initiatives such as whole building design and energy efficient lighting design with incentives for implementation.
BACKGROUND Efficiency Nova Scotia has contracted CLEAResult to conduct energy conservation and energy efficiency program incentive research. The project covers the following areas: - Identification of best practices for incentive rate sett...
AI summary Efficiency Nova Scotia has engaged CLEAResult to research best practices for setting energy conservation and efficiency program incentives. The project involves interviews with key contacts in other jurisdictions and will result in a guideline to optimize program design. The final documents will be submitted to the Utility and Review Board (UARB) and made publicly available.
OVERVIEW Jurisdictional Scan State/Province California Utility/Agency Pacific Gas & Electric Fuel Electricity Carolyn Weiner Manager, EE Core Products Key Contact/Interviewee [email protected] office: 415-973-2391 cell: 415-852-8663 C...
AI summary The document provides an overview of the electricity market in California, focusing on Pacific Gas & Electric (PG&E) and their Demand Side Management (DSM) initiatives. It includes contact information for Carolyn Weiner, Manager of EE Core Products at PG&E, and mentions Jonathan Houle as a consultant.
CALIFORNIA ENERGY EFFICIENCY PROGRAM INCENTIVE & COST EFFECTIVENESS POLICY California has long been recognized as one of the leading jurisdiction in North America regarding the regulatory standards and policies established to guide the des...
AI summary California's CPUC has introduced a 'Rolling Target' system for energy efficiency programs, requiring IOUs to submit annual budgets and a 'business plan' every five years. PAs are funded with approximately $1B in ratepayer funds for energy efficiency and conservation programs.
Cost Effectiveness Testing As detailed in D.14-10-046 8 , the CPUC has interpreted its mandate to deliver cost-effective energy efficiency and conservation programs as meaning that all energy efficiency portfolios of delivery agents should...
AI summary The text discusses the cost effectiveness testing framework used by the CPUC, emphasizing the use of TRC and PAC tests to evaluate energy efficiency programs. It highlights the role of the Standard Practice Manual and the use of the DEER database and E3 model for testing.
Avoided Costs Within California, the avoided costs of electricity are generated by E3 for a 20-year period based on the following components: generation energy, generation capacity, ancillary services, transmission and distribution capacit...
AI summary The text discusses avoided costs in California, including electricity and natural gas, calculated by E3 over a 20-year period. Components include generation, capacity, environment, and renewable standards. The model is periodically updated, with the most recent update in 2011.
Customer Class Breakdown The chart below highlights PG&E's consumption by customer class as identified by California's Energy Consumption Data Management System 12 . The total annual energy consumption in 2014 was 86TWh. 10 PG&E Company Pr...
AI summary The document presents a breakdown of PG&E's energy consumption by customer class in California, based on data from the Energy Consumption Data Management System. In 2014, the total annual energy consumption was 86TWh.
1. Market Research PG&E staff will begin the incentive setting process by performing both primary and secondary market research in order to determine the measure performance metrics and costs. This will include holding interviews with the...
AI summary PG&E staff will conduct primary and secondary market research, including interviews with manufacturers and distributors, to determine performance metrics and costs for incentive setting. The results of these interviews are kept confidential to protect competitive information.
2. Work Paper Once measure level data is acquired from the market, the Products organization will engage its engineering staff to produce a Work Paper. The Work Papers, similar to TRMs found in other jurisdictions, are documents which deta...
AI summary The Work Paper is a document created by the Products organization to detail how measure savings are calculated, including EM&V protocols and measure costs. Once approved by the Commission, the measure can be offered in a PA's program portfolio. Incentive rates are determined separately by the PA and reviewed with the CPUC through Program Implementation Plans. Incremental costs for measures are calculated based on technology maturity and market penetration.
History In 1999, Oregon lawmakers and citizens envisioned a future with Oregon homes and businesses powered by clean, affordable energy. They established stable, consistent funding to help Oregonians invest in energy efficiency and renewab...
AI summary In 1999, Oregon established the Energy Trust of Oregon as a non-profit to invest in energy efficiency and renewable resources. It began operations in 2002 under the Oregon Public Utilities Commission, aiming to deliver cost-effective services with low administrative costs and high customer satisfaction. Customers of four utilities across two states fund and benefit from its programs.
Energy Trust of Oregon Funding Through state legislation, tariffs and other requirements, Energy Trust is funded by customers of Portland General Electric, Pacific Power, NW Natural and Cascade Natural Gas. Customers of all four utilities...
AI summary Energy Trust of Oregon is funded by customers of Portland General Electric, Pacific Power, NW Natural, and Cascade Natural Gas through a public purpose charge and state legislation. Energy Trust delivers energy-efficiency and renewable energy programs, with increased savings and funding after the passage of SB 838 in 2008. Expenditures rose from $63 million in 2008 to $117 million in 2013.
Exceptions to Cost Effectiveness for Measure inclusion into programs 18 For measures which do not pass both the utility and societal (total resource cost) tests, the OPUC does allow measures to be included in programs assuming the measure...
AI summary The OPUC allows certain measures to be included in programs even if they fail cost-effectiveness tests, provided they meet specific conditions such as producing non-energy benefits, increasing market acceptance, or being required by law.
Considerations for Vetting Ideas, Measures and Measure Updates Below are the considerations taken by the Energy Trust and its program delivery agents when introducing a new measure into its program portfolio or updating a measure's metrics...
AI summary The Energy Trust and its program delivery agents consider several factors when introducing or updating measures in its program portfolio, including savings potential, budget impact, alignment with long-term strategy, stakeholder interest, risk analysis, market availability, acceptance, timing, and prior experience with the measure.
Figure 46: Electric Savings Result 9 Program Names (Savings in MWh) Accumulated Savings to Year C&I Custom Efficiency C&I Equipment Rebate Small Business Direct Install Residential Direct Install Appliance Bounty Residential Room Air Condi...
AI summary The text presents tables showing electric and gas savings results from various programs in different years, including accumulated savings and targets. It also mentions cost-effectiveness testing as a key theme.
Costs in TRC Calculation The costs calculated in the TRC are costs paid by the program administrators and participants plus the increase in supply costs for any period when load is increased.
AI summary The Total Resource Cost (TRC) includes costs paid by program administrators and participants, as well as any increase in supply costs due to increased load during a given period.
Program Analysis Initiatives Target Market Incentive Setting Methodology Neighborhood (Electric) Delivers energy-saving and management solutions to local communities where the demand for electricity is expected to grow significantly becaus...
AI summary The Neighborhood Program by Con Edison provides energy-saving solutions and incentives to local communities with growing electricity demand. It includes free lighting, water heating, and refrigeration products for small businesses and apartment buildings, as well as a partnership with NYSERDA for combined heat and power (CHP).
INCENTIVE LEVEL SETTING METHODOLOGY Efficiency Vermont developed a new product development process about a year and a half ago. It involves a customer mapping and an engagement process that covers seven stages: - 1. Idea Solicitation - 2....
AI summary Efficiency Vermont employs a structured new product development process involving nine stages, used for designing new incentive offers or programs. The process can be expedited if needed. Incentive changes are typically driven by customer behavior, not cost effectiveness, and free-ridership is assessed. Energy savings assumptions for measures are evaluated annually or biannually.
CURRENT CYCLE Efficiency Maine began Triennial Plans in 2011 and is currently in the second triennial cycle that spans 2014-2016. Efficiency Maine also releases performance reports annually. The latest public report is 2015.
AI summary Efficiency Maine initiated Triennial Plans in 2011 and is currently in the second cycle spanning 2014-2016. Annual performance reports are released, with the latest public report being from 2015.
3. Incremental Cost Design Based on the market research and technology, Efficiency Maine will attempt to incentivize the incremental cost based on what is determined as a reasonable return on investment. For "Replace on Burnout" measures t...
AI summary Efficiency Maine plans to incentivize incremental costs based on a reasonable return on investment. For 'Replace on Burnout' measures, incremental cost is the difference between the measure cost and standard measures. For Retrofit/Direct Install measures, incremental cost includes the full measure cost, including labor.
Figure 63: Electric Program Expenditures 2015 [12](#page-110-0) Program Incentive Delivery Total http://www.efficiencymaine.com/docs/E M-Natural-Gas-Kitchen-Measures.pdf Commercial Heat Pump Program For businesses that are looking to upgra...
AI summary The text presents a table detailing electric program expenditures for 2015, including the Commercial Heat Pump Program and the Large Customer Program, with information on eligibility, incentives, and funding ranges.
ost reliable service at the lowest possible cost; to protect the public safety from transportation and gas pipeline related accidents; and to ensure that residential ratepayers' rights are protected." Mass Save is the public-facing brand f...
AI summary The text provides an overview of energy efficiency programs and organizations in Massachusetts, including Mass Save, which is a collaborative initiative between utilities and service providers. It also outlines the role of ISO New England and the Energy Efficiency Advisory Council in managing energy systems and promoting energy efficiency.
Outputs - Total Gross Energy Savings; - Total Gross Demand Reduction; - Total Net Energy Savings; - Total Net Demand Reduction; - TRC Benefits; - TRC Costs; - TRC Net Benefits; - TRC Ratio; - PAC Benefits; - PAC Costs; - PAC Net Benefits;...
AI summary The text lists various outputs related to energy efficiency and demand reduction, including total gross and net energy savings, demand reduction, TRC and PAC benefits and costs, and levelized unit costs. These metrics are used to evaluate the performance and economic impact of energy programs.
Comparison of Diversity of Program Delivery – 2023-2025 Plan, 2026 DSM Extension and 2027-2031 DSM Plan Item 2023-2025 DSM Plan 2026 DSM Extension 2027-2031 DSM Plan Diverse Measures • 356 measures, with measure lives ranging from 1 to 36...
AI summary This table compares the diversity of program delivery across three different Demand Side Management (DSM) plans in Nova Scotia, highlighting the number of measures, program components, and shifts in focus over time, such as the reduction in reliance on residential LED lighting savings and the introduction of new components like smart thermostats and solar PV programs.
- staffing, E1 will achieve annual cost savings of approximately $0.9 million per year. 1 Request IR-22: 2 3 Evidence – Exhibit E-1, pp.1-71 (pdf pp. 8-78) 4 5 Please provide the annual cost savings that the Preferred Plan will achieve thr...
AI summary The document outlines EfficiencyOne's (E1) response to information requests from the Nova Scotia Energy Board (NSEB), including cost savings from staffing and the inclusion of solar-PV in the 2027–2031 DSM Plan to support residential Mi'kmaw communities.
- 16 ii) Please refer to part (b) of this IR response. 1 Request IR-24: 2 3 Evidence – Exhibit E-1, pp.1-71 (pdf pp. 8-78) 4 5 Exhibit E-1, page 56 of 71(pdf pg. 63), Table 7: 2027-2031 Plan – Portfolio Level Insights 6 7 (a) E1 notes that...
AI summary The document addresses two requests related to EfficiencyOne's (E1) 2027-2031 DSM Plan. It notes that 42% of residential energy efficiency program investment is dedicated to low-income and equity programs and explains that annual investment in the DSM Plan is constrained to the 2026 approved level of $63.75 million per year, resulting in downward trends in energy savings metrics.
1 Table 1: Justification for Program Components with a failing PAC result. Program Component PAC Result (NPV Lifetime Benefits / NPV Investment) Justification Affordable Single-family Homes 0.8 These programs serve households on lower inco...
AI summary Table 1 provides justification for program components with failing PAC results, highlighting support for affordability and equity-focused initiatives like Affordable Single-family Homes and the Mi'kmaw Home Energy Efficiency Project. These programs align with prior Board approvals and are consistent with ongoing efforts to improve energy efficiency and support First Nations communities.
1 Request IR-28: 2 3 Evidence – Exhibit E-1, pp.1-71 (pdf pp. 8-78) 4 5 How did E1 arrive at the minimum 90% as the threshold for achievement of the performance 6 targets? 7 8 (a) What are the industry standard thresholds for achieving a D...
AI summary The document addresses a request regarding the 90% minimum threshold for achieving DSM performance targets. E1 explains that there are no mandated industry standards and that the threshold is based on regulatory design and policy objectives. It also notes that this threshold has been used in previous DSM plans and is considered effective.
3 Evidence – Exhibit E-1, pp.1-71 (pdf pp. 8-78) 4 - 5 Table 11: Proposed 2027-2031 DSM Preferred Plan Performance Targets provides the expected 6 energy savings. Please provide the number of customers by rate class that E1 forecasts - 7 p...
AI summary The document requests the number of customers by rate class that EfficiencyOne (E1) forecasts will participate in demand-side management (DSM) programs under each demand resource area to achieve the proposed 2027-2031 DSM preferred plan performance targets.
10 Response IR-29: 11 12 The number of customers (defined as number of NS Power customer accounts for the purposes 13 of this IR response) by rate class that E1 forecasts participating in programs under each demand 14 resource area over th...
AI summary This section outlines E1's forecast of the number of NS Power customer accounts participating in demand resource programs by rate class over the 2027–2031 period, as detailed in Table 1.
16 Table 1: 2027-2031 Participation by Rate Class for Resource Areas Resource Area Rate Class Energy Efficiency Demand Response Solar-PV Residential/Charitable (2,3,4) 130,768 9,266 200 Small General (10) 2,987 0 0 General (11) 4,658 112 0...
AI summary The document presents a table showing participation in energy efficiency, demand response, and solar-PV programs by rate class from 2027 to 2031. It also includes a request for information regarding the mid-course adjustment process, feedback from the DSMAG, and proposed enhancements to the process by EfficiencyOne (E1).
15 2026 DSM Extension Enhancements 16 In the 2026 DSM Extension matter, E1 agreed to provide the following enhancements: - 17 Improve the accuracy of estimates used for the rate class allocation of expenditures in 18 the DSM Plan by using...
AI summary In the 2026 DSM Extension matter, E1 agreed to improve the accuracy of expenditure estimates in the DSM Plan using historical data, enhance rate class reporting, and monitor program spending against the DSM Plan budget.
11 2027–2031 DSM Plan Enhancements 12 E1 also proposed in the 2027–2031 DSM Plan Application further MCA enhancements 13 including: - 14 Reducing the threshold from 25 percent to 20 percent for program changes for both 15 spending and savi...
AI summary E1 proposed enhancements to the 2027–2031 DSM Plan, including reducing the threshold for program changes from 25% to 20% for spending and savings, and introducing a 15% spending threshold for individual rate class changes, requiring explanations. These changes aim to improve transparency and alignment with future planning.
percent or more by individual rate classes and providing explanations is to ensure actual cumulative spending at the end of the DSM Plan period as compared to the approved DSM Plan does not result in a substantial balance adjustment for an...
AI summary E1 is adjusting the Mandatory Cost Allocation (MCA) thresholds for the DSM Plan, lowering the program spending threshold from 25% to 20% and setting a 15% threshold for rate class spending changes. These adjustments aim to ensure accurate budgeting and avoid future balance adjustments in the DCRR. E1 has not expanded the MCA to include sector changes and has incorporated these thresholds into its reporting processes.
1 or proceedings it deems appropriate to consider any aspect of the quarterly report 2 including the MCA. E1 does not suggest in any way that the changes to the MCA process 3 as proposed in the 2027–2031 Preferred DSM Plan impact the NSEB'...
AI summary EfficiencyOne (E1) supports the NSEB's authority to initiate regulatory processes and acknowledges the proposed changes to the MCA process in the 2027–2031 DSM Plan. It emphasizes that the DSMAG will be involved in reviewing mid-course adjustments and that the MCA process will be included in the Standardized Filing Framework.
1 Request IR-31: 2 3 Evidence – Exhibit E-1, pp.1-71 (pdf pp. 8-78) 4 5 Regarding Section 8.2 "Mid-Term Check-in" of the Application: 6 7 (a) With regards to the Mid-Term Check-in process described at lines 13 to 21 of pdf pg. 72: 8 Does E...
AI summary The document discusses two regulatory requests (IR-31 and IR-32) related to the Mid-Term Check-in process and the Alternate Scenario in the DSM Plan. EfficiencyOne responds that it will not file a Mid-Term Check-in Report, referencing a prior response. It also explains that the Alternate Scenario did not remove DSM measures that failed the PAC test due to low impact and the need to maintain investment for low-income and equity-seeking customers.
M12780 – EfficiencyOne (E1) 2027–2031 Demand Side Management (DSM) Resource Plan Application 1 customers, consistent with considerations applied across both the Preferred Plan and 2 the Alternate Scenario. 3 4 Appendix A, Attachment 3 of E...
AI summary EfficiencyOne (E1) has submitted a 2027–2031 Demand Side Management (DSM) Resource Plan Application. The Preferred Plan targets 435.4 GWh of incremental cumulative net energy savings, which is at the lower end of APEX's recommended range of 0.8% to 1.0% of NS Power's load. E1's response explains that the target was determined through modelling software and is considered conservative and achievable.
1 feedback and E1's affordability focused design approach reflecting current economic 2 circumstances facing NS Power ratepayers. 4 ii) E1 prioritized short term affordability for the Preferred Plan by maintaining the 5 annual investment o...
AI summary The document discusses E1's approach to designing the 2027–2031 DSM Preferred Plan with a focus on short-term affordability and maintaining an annual investment of $63.75 million. It emphasizes deliverability and cost effectiveness, highlighting a cost effectiveness result of 2.4 for the proposed plan.
1 alternative supply side options that would be required to be generated to deliver the 2 same level of energy savings and available capacity. 3 4 Program Mix – E1's portfolio must adhere to the Balanced Plan principles, which 5 include, a...
AI summary The document discusses E1's commitment to equitable access to energy programs, particularly for low-income and equity-deserving communities, and addresses strategic electrification as a means to reduce GHG emissions and electricity costs. E1 defines strategic electrification as a deliberate shift from fossil fuels to electricity with targeted benefits.
E1 Responses to Nova Scotia Energy Board (NSEB) Information Requests NON-CONFIDENTIAL 1 Request IR-35: 2 3 Evidence – Exhibit E-1, pp.1-71 (pdf pp. 8-78) 4 5 As the system operator, IESO-NS is responsible for ensuring an adequate electrici...
AI summary EfficiencyOne (E1) responded to Nova Scotia Energy Board (NSEB) information requests regarding consultations with the Nova Scotia Independent Energy System Operator (NSIESO) on the 2027–2031 DSM Plan. E1 confirmed that while they were a member of the Demand Side Management Advisory Group (DSMAG), no specific MW or MWh reduction targets were provided by the NSIESO for the DSM Plan.
- Appendix A, Attachment 4: 2027–2031 Demand Response Technical Tables 1 This attachment provides demand response output detail and is an output of the DRSim™ 2 model. Because calculations are performed within the DRSim™ model rather than...
AI summary This document provides technical tables related to demand response and updates to Appendix A, Attachment 4, explaining the use of the DRSim™ model and the inclusion of annotations for clarity. It also mentions the filing of updated attachments and historical DSM plan results.
2027-2031 DSM Plan Measure Reference Manual Last Updated: May 13th, 2026
AI summary The 2027-2031 DSM Plan Measure Reference Manual outlines the framework for Demand Side Management (DSM) initiatives in Nova Scotia. It provides guidance on program assessment, cost allocation, and compliance with regulatory standards. The document is last updated on May 13th, 2026.
1 2. KEY SOURCES - 2 Most measure inputs are derived from the results of EM&V conducted by E1's third-party evaluators. - 3 Section [2.1](#page-55-1) provides a full citation for each such source, along with a concise internal reference (u...
AI summary The text outlines the sources of measure inputs, primarily derived from E1's third-party evaluators' EM&V results, and provides references to internal and external sources. Section 2.1 details full citations and internal references, while Section 2.2 maps external sources to publicly accessible links.
8 2.1 EFFICIENCYONE SOURCES Internal Reference Full Citation Custom Incentives Econoler et al, EfficiencyOne – Custom Incentives Program – Final Report Evaluation 2022 – 2022 DSM Evaluation, March 2023 Custom Incentives Econoler et al, Eff...
AI summary The text lists various reports and evaluations related to EfficiencyOne's programs, including the Custom Incentives Program, DSM evaluations for 2022, 2024, and 2025, and the Existing Residential Program. These reports are compiled by Econoler et al and Apex Analytics, and they are referenced in the context of EfficiencyOne's operations and performance assessments.
3.1 ANH_RETRO CUSTOM – EQUITY DESERVING - RETROFITS - Custom provides large business, non-profit, and institutional (BNI) participants with technical assistance, - financial incentives, and project financing to help reduce their electricit...
AI summary The Custom program provides technical assistance, financial incentives, and project financing to large businesses, non-profits, and institutions to reduce electricity consumption and peak demand. It includes Retrofit, New Construction, Building Optimization, and Pay-for-Performance services, with a new service for low-income and equity groups under consideration for the 2027-2031 DSM plan. EfficiencyOne claims savings for certain Custom projects over multiple years.
3.1.2 KEY SOURCES FOR MEASURE INPUT DEVELOPMENT - This is a new measure. The measure characterization has been assumed to be consistent with CUS- - IND_001. If there are any assumed differences in the measure characterization between this...
AI summary This section introduces a new measure and notes that its characterization is assumed to align with CUS-IND_001. Any differences will be flagged in subsequent sections, with references to CUS_IND_001 for further details.
3.1.6.2 Coincident Peak Demand Savings (kW) - Value: 100.79 kW - Source: Refer to CUS_IND_001 - Details: The peak demand savings for this measure are assumed to be consistent with CUS_IND_001.
AI summary The document specifies that the coincident peak demand savings for the measure is 100.79 kW, with the value derived from CUS_IND_001. The assumption is that the savings are consistent with the referenced document.
3.2 CUS-NC_001 CUSTOM – NEW CONSTRUCTION - Custom provides large business, non-profit, and institutional (BNI) participants with technical assistance, - financial incentives, and project financing to help reduce their electricity consumpti...
AI summary The Custom – New Construction program provides technical assistance, financial incentives, and project financing to large businesses, non-profits, and institutions to reduce electricity consumption and peak demand. Eligible projects must meet specific size and energy savings criteria, and EfficiencyOne claims savings based on phased project completion.
1 3.2.1 MEASURE IDENTIFIERS & DEFINING CHARACTERISTICS Measure ID (Plan) CUS-NC_001 Measure ID (Incremental Cost) BNI__CUS-NC_001 Common Measure Name Custom - New Construction Sector BNI Program Name Custom Incentives Program Component Cus...
AI summary This section outlines a measure related to custom incentives for new construction under the BNI program. It includes identifiers, sector, program name, and other defining characteristics of the measure.
- 5 Incentives Evaluation. This table is reproduced below. Partial Savings Claimed Final Savings for Projects Fully Claimed in 2024 Total Number of Projects 1 27 28 Energy Savings Tracked Gross Energy Savings – at the Meter (GWh) 6.273 13....
AI summary The table presents an evaluation of incentives, showing energy and peak demand savings from 28 projects, including 1 partially claimed and 27 fully claimed in 2024. It includes metrics such as gross energy savings, adjustment ratios, line loss factors, and effective useful life of the projects.
1 3.2.3 MEASURE LIFE - 2 Value: 19 Years - Source: Derived based on information in Table 19[2](#page-61-3) 3 from the Custom Incentives Evaluation 2024. - 4 Details: To estimate the EUL, E1 divided Total gross lifetime energy savings at th...
AI summary The document discusses the estimation of the Energy Unit Life (EUL) based on data from Table 19 and the Custom Incentives Evaluation 2024, with a value of 19 years derived from total gross lifetime energy savings at the generator divided by total annual energy savings.
3.2.6.2 Coincident Peak Demand Savings (kW) Value: 184.93
AI summary The Coincident Peak Demand Savings (kW) is reported as 184.93, indicating the amount of kilowatts saved during peak demand periods through demand-side management initiatives.
Source: Derived based on information in Table 19[4](#page-62-1) from the 2024 Custom Incentives Evaluation. Partial Savings Claimed Final Savings for Projects Fully Claimed in 2024 Total Number of Projects 1 27 28 Energy Savings Tracked Gr...
AI summary The table presents data on energy and peak demand savings from the 2024 Custom Incentives Evaluation. It includes metrics such as gross energy savings, adjustment ratios, line loss factors, and effective useful life for projects fully claimed in 2024. The data is used to evaluate the impact of energy efficiency initiatives.
2024 Gross Energy Savings - at the Meter. Input Description Total A Total Gross Energy Savings - at the Meter 20.17 B Total Gross Peak Demand Savings - at the Meter 3.73 C = B / A kW savings per 1,000,000 kWh 184.93 2024 Custom Incentive E...
AI summary The document presents 2024 Gross Energy Savings at the Meter, detailing total energy and peak demand savings. It references a table from the 2024 Custom Incentive Evaluation and mentions CUS-IND_001, an industrial retrofit program for large business and institutional participants.
1 3.3.1 MEASURE IDENTIFIERS & DEFINING CHARACTERISTICS Measure ID (Plan) CUS-IND_001 Measure ID (Incremental Cost) BNI__CUS-IND_001 Common Measure Name Custom - Industrial Retrofit Sector BNI Program Name Custom Incentives Program Componen...
AI summary This section defines a measure for a custom industrial retrofit program under the BNI program, specifying identifiers, sector, program name, and other attributes such as replacement type and unit basis.
- 6 reproduced below. Partial Savings Claimed Final Savings Claimed for Single- Year Projects Final Savings Claimed for Multiyear Projects Total Number of Projects 13 61 14 88 Energy Savings Tracked Gross Energy Savings – at the Meter (GWh...
AI summary The text presents a table summarizing energy and peak demand savings from various projects, including tracked gross energy savings, adjustment ratios, and line loss factors. It includes data for single-year and multiyear projects, and provides metrics such as effective useful life and gross lifetime energy savings.
12 3.3.5 INCREMENTAL COST - 13 Value: $382,537.50 (in $2025) - 14 Unit: per GWh of energy savings - 15 Source: Incremental Costs were developed by Apex Analytics in 2024. - 16 Details: The incremental cost of this measure is assumed to be...
AI summary The incremental cost for the measure is estimated at $382,537.50 per GWh of energy savings, based on an average incentive of 15 cents per kWh multiplied by 2.5. This multiplier was recommended due to insufficient program tracking data, with Apex Analytics citing the EmPOWER 2023 report as a reference. Future evaluations should collect more specific data for Nova Scotia.
11 3.3.6.2 Coincident Peak Demand Savings (kW) - 12 Value: 100.79 - 13 Source: Derived based on 2024 Custom Incentives Evaluation project level data. - 14 Details: This value was calculated by dividing the evaluation adjusted project-level...
AI summary This section provides the value of Coincident Peak Demand Savings (kW) as 100.79, derived from 2024 Custom Incentives Evaluation project-level data. The value was calculated by dividing the evaluation adjusted project-level 2024 Gross Peak Demand Savings at the Meter by the evaluation adjusted project-level 2024 Gross Energy Savings at the Meter for Custom Industrial Retrofit.
17 Input Description Adjusted Gross Energy Savings – at Adjusted Gross Demand Savings – at the Meter (GWh) the Meter (MW) A Final Single Year 6.982 0.658 B Final Multiyear 2.026 0.241 C Partial Single Year & Multiyear 11.952 1.213 D = A+B+...
AI summary The document includes tables with data on energy and demand savings across different scenarios, as well as a reference to a commercial retrofit program. The context suggests a regulatory analysis involving energy efficiency measures and their quantification.
7 3.4.6.2 Coincident Peak Demand Savings (kW) - 8 Value: 102.44 - Source: Derived based on information in Table 11[13](#page-72-1) 9 from the 2024 Custom Incentives Evaluation. - 10 Details: This value was calculated by dividing the 2024 G...
AI summary The value of 102.44 kW for Coincident Peak Demand Savings is derived from the 2024 Custom Incentives Evaluation. It was calculated by dividing the 2024 Gross Peak Demand Savings at the Meter by the 2024 Gross Energy Savings at the Meter.
12 Input Description Total A Total Gross Energy Savings - at the Meter 25.02 B Total Gross Peak Demand Savings - at the Meter 2.56 C = B / A kW savings per 1,000,000 kWh 102.44 13 13 2024 Custom Incentive Evaluation, Evaluated Gross Saving...
AI summary The text presents a table showing energy savings metrics, including total gross energy savings, total gross peak demand savings, and a calculated ratio of peak demand savings per million kWh. It also references a 2024 Custom Incentive Evaluation report on page 18 of a PDF document.
3.5 CUS-P4P_001 CUSTOM - PAY FOR PERFORMANCE - Custom provides large business, non-profit, and institutional (BNI) participants with technical assistance, - financial incentives, and project financing to help reduce their electricity consu...
AI summary The Pay-for-Performance (P4P) program provides financial support for energy efficiency upgrades to large businesses, non-profits, and institutions, with incentives based on verified energy savings. Eligibility requires annual electricity consumption of at least 1,000,000 kWh and a 10% reduction in consumption. EfficiencyOne (E1) claims savings over multiple years, and savings are normalized on a per GWh basis.
14 3.5.6.1 Energy Savings (kWh) 15 Value: 1,000,000 16 Source: By construction. 16 2025 Custom Incentive Evaluation, Net Savings, Table 20: Evaluated 2022 P4P NTGRs, page 25 (PDF 664/1087) - 1 Details: Due to the heterogenous nature of thi...
AI summary The text discusses energy savings measured in kWh, with a value of 1,000,000 derived by construction. It references a 2025 Custom Incentive Evaluation and uses a unit basis of 'per GWh of savings' to determine costs and incentives for achieving energy efficiency goals.
3 3.5.6.2 Coincident Peak Demand Savings (kW) 4 Value: 206.65 Source: Derived based on information in Table 21[17](#page-76-0) 5 from the 2022 Custom Incentives Evaluation. 6 Details: This value was calculated using the approach set out in...
AI summary The value of 206.65 kW for Coincident Peak Demand Savings is derived from Table 21 in the 2022 Custom Incentives Evaluation, using a specified calculation approach.
7 Input Description Total A Annual Gross Savings at the Generator (GWh) 1.00 B Hours per Year 8760.00 C = B (1000 1000)/A Average kW Demand Impact 114.16 D Annual Gross Savings at the Generator (GWh) 2.89 E Annual Gross Peak Demand Savings...
AI summary The text provides a table with calculations related to energy savings, including annual gross savings, average kW demand impact, and peak demand savings. It references a 2022 Custom Incentive Evaluation report, specifically Table 21 from page 32 of the PDF document.
3.6.6.2 Coincident Peak Demand Savings (kW) - Value: 46.07 - Source: Derived based on information in Table 24[21](#page-80-1) from the 2024 Custom Incentives Evaluation. - Details: This value was calculated by dividing the Gross Peak Deman...
AI summary This section discusses Coincident Peak Demand Savings (kW) with a value of 46.07, derived from Table 24 in the 2024 Custom Incentives Evaluation. The value is calculated by dividing the Gross Peak Demand Savings at the Meter by the Gross.
- Energy Savings at the Meter. Input Description Total A Total Gross Energy Savings - at the Meter 1.86 B Total Gross Peak Demand Savings - at the Meter 0.09 C = B / A kW savings per 1,000,000 kWh 46.07 2024 Custom Incentive Evaluation, Ev...
AI summary The document presents energy savings metrics at the meter, including total gross energy savings and peak demand savings, along with a calculation of kW savings per 1,000,000 kWh. It references a 2024 Custom Incentive Evaluation and mentions a section on strategic energy management.
1 3.7.1 MEASURE IDENTIFIERS & DEFINING CHARACTERISTICS Measure ID (Plan) SEM_001 Measure ID (Incremental Cost) BNI__SEM_001 Common Measure Name Custom - Strategic Energy Management Sector BNI Program Name Custom Incentives Program Componen...
AI summary The document outlines a measure identified as SEM_001 under the Strategic Energy Management (SEM) program, which is part of the BNI Custom Incentives program. It specifies the measure's sector, program component, replacement type, unit basis, and DI flag.
3 3.7.6.2 Coincident Peak Demand Savings (kW) 4 Value: 120.2 - Source: Derived based on information in Table 32[24](#page-84-0) 5 from the 2024 Custom Incentives Evaluation. - 6 Details: This value was calculated by dividing the Gross Peak...
AI summary The value of 120.2 for Coincident Peak Demand Savings (kW) is derived from Table 32 in the 2024 Custom Incentives Evaluation. It is calculated by dividing the Gross Peak Demand Savings at the Meter by the Gross Energy Savings at the Meter.
3.8 BER-AR__LGT_INHORT_001__0 AR - INDOOR - HORTICULTURAL LIGHTING - BER provides financial incentives in the form of prescriptive rebates or financing to business, non-profit, - and institutional (BNI) participants to foster reductions in...
AI summary The BER program provides rebates and financing to BNI participants in Nova Scotia to reduce electricity consumption and peak demand. The program includes Application Rebates and Instant Rebates, with different eligibility criteria and participant details tracking capabilities. Distributors play a key role in promoting and supporting the program.
3.8.2 KEY SOURCES FOR MEASURE INPUT DEVELOPMENT - The primary source of the values for measure input development is the Horticultural Lighting Measure[25](#page-86-2) - from the 2024-2025 DSM Commercial Measure Assessment. The measure summ...
AI summary The primary source for measure input development is the Horticultural Lighting Measure from the 2024-2025 DSM Commercial Measure Assessment, with reference to a measure summary table.
$$Unitary\ Energy\ Savings\ \left[\frac{kWh}{yr}\right] = \frac{(W_b[W] \times Qty_b[-] - W_b[W] \times Qty_b[-]) \times HOU\left[\frac{h}{yr}\right] \times IE}{1,000}$$ 2024 DSM Evaluation Reports, 2024-2025 DSM Measure Assessment, BNI, L...
AI summary The document discusses the calculation of unitary energy savings and provides a table with parameters and values related to lighting measures and horticultural lighting from the 2024 DSM Evaluation Reports and 2024-2025 DSM Measure Assessment. It includes baseline wattage, quantity, new wattage, hours of operation, and energy savings interactive effects factor.
$$Unitary\ Peak\ Demand\ Savings\ [kW] = \frac{(W_b[W] \times Qty_b[-] - W_e[W] \times Qty_e[-]) \times PCF \times IE_{PD}}{1.000}$$ ВЕ R-AR Parameter Symbol Retrofit New Construction Reference Peak Coincidence Factor [-] PCF Actual ctual...
AI summary The document presents a formula for calculating unitary peak demand savings, along with a table outlining parameters and their values. It references the 2024 DSM Evaluation Reports and mentions BER (Business Energy Rebates) providing financial incentives for energy-efficient measures, such as small ductless mini-split heat pumps.
4.1.3 MEASURE LIFE Value: 18 Years Source: The EUL value for this prescriptive measure was drawn from the 2024 DSM Program Evaluation
AI summary The Effective Useful Life (EUL) for the prescriptive measure is set at 18 years, derived from the 2024 DSM Program Evaluation.
4.1.4 NET TO GROSS Value: 1.0 Source: As set out in the 2024 DSM Program Evaluation Reports, [31](#page-93-6) free-ridership and spillover effects are nil since participants are non-profits or low-income housing owners with limited budgets...
AI summary The document discusses the Net to Gross (NTGR) value of 1.0 applied to the 2024 DSM Program Evaluation Reports due to nil free-ridership and spillover effects from participants in non-profit or low-income housing. It also outlines the direct installation cost, energy savings, and coincident peak demand savings associated with the program. The Efficient Product Installation (EPI) program is highlighted, focusing on the installation of energy-efficient products and its role in residential demand response.
4.2.2 KEY SOURCES FOR MEASURE INPUT DEVELOPMENT - The primary source of the values for measure input development is the Low-flow Showerhead Measure[32](#page-96-3) - from the 2024-2025 DSM Residential Measure Assessment. The measure summar...
AI summary The primary source for measure input development is the Low-flow Showerhead Measure from the 2024-2025 DSM Residential Measure Assessment. The measure summary table from this section is referenced.
Value: 0.99 2024 DSM Evaluation Reports, 2024-2025 DSM Measure Assessment, Residential, Water Heating Measures, Low-flow Showerheads, page 40 (PDF 1122/1442) 2024-2025 DSM Measure Assessment, Residential, Effective Useful Life, Other Measu...
AI summary The text references 2024 DSM Evaluation Reports and the 2024-2025 DSM Measure Assessment, focusing on residential water heating measures and non-LED lighting measures, including Effective Useful Life (EUL) values and sources.
1 4.2.6.2 Coincident Peak Demand Savings (kW) 2 Value: 0.061 6 - 3 Source: Average savings value calculated using recent tracked savings for this measure. - 4 Details: In practice, unitary peak demand savings are calculated by multiplying...
AI summary The value of 0.061 represents average savings for coincident peak demand in kW, calculated using recent tracked savings. It is derived by multiplying the unitary savings value by the peak demand-to-energy ratio (0.162 RES-Water Heat, Navigant 2016-2018 DSM Plan).
4.3.2 KEY SOURCES FOR MEASURE INPUT DEVELOPMENT - The primary source of the values for measure input development is the Humidity Sensor Measure[36](#page-101-2) from - the 2024-2025 DSM Residential Measure Assessment. The measure summary t...
AI summary The primary source for measure input development is the Humidity Sensor Measure from the 2024-2025 DSM Residential Measure Assessment, with a reference to a measure summary table.
Parameter Symbol EPI Reference Fan Efficiency [CFM/W] $\eta_{fan}$ 3.5 ENERGY STAR min standard, 2024 175 Savings Percentage % Savings 50% Demand controlled ventilation A case study for existing Swedish multifamily buildings, 2004 176 Fan...
AI summary This section discusses fan efficiency, savings percentage, fan exhaust rate, annual operating hours, and energy savings related to demand-controlled ventilation in multifamily buildings. The data is sourced from various standards and case studies, including ENERGY STAR and a 2004 Swedish study.
4.4.2 KEY SOURCES FOR MEASURE INPUT DEVELOPMENT - The primary source of the values for measure input development is the Smart Thermostat for Electrical - Heating Systems Measure[40](#page-105-1) from the 2024-2025 DSM Residential Measure A...
AI summary The primary source for measure input development is the Smart Thermostat for Electrical Heating Systems Measure from the 2024-2025 DSM Residential Measure Assessment.
- summary table from this section is reproduced below. Parameter Instant Sav MHEEP, A E PI Reference Measure Description and Identification Measure Smart thermos floor heating stats cont rolling electric ba aseboard s, MSHP or ele ctric in...
AI summary The table presents parameters for residential space heating measures, including smart thermostats and electric heating systems. It details installation rates, effective useful life, energy savings, and peak demand savings. The document is part of a 2024-2025 DSM Measure Assessment.
Source: This value was drawn from Table 135[41](#page-106-3) of the 2024 DSM Measure Assessment. MHEEP, ASFH programmable thermostats Smart Thermostats for Electrical Heating Systems Instant Savings, Various EUL values are used among juris...
AI summary The text discusses the use of various EUL values for smart thermostats in electrical heating systems, noting that the common practice is to use the same EUL value as for programmable thermostats. It references Table 135 from the 2024 DSM Measure Assessment.
Table 72: Non-learning Smart Thermostat for Electrical Heating System Measure Summary Parameter ASFH, Instant Savings EPI Reference Measure Description and I Measure Description and Identification Measure sensor-based heating for sin Non-l...
AI summary Table 72 outlines a measure summary for non-learning smart thermostats used in electrical heating systems. It includes details on installation rates, energy savings, and peak demand savings for various heating systems such as electric baseboards, MSHPs, and electric furnaces.
4.5.6.1 Energy Savings (kWh) - Value: 205 - Source: This is the deemed unitary energy savings value for the Smart Thermostat for Electrical Heating - Systems Measure in the 2025 Measure Assessment. - Details: Some models of smart thermosta...
AI summary The document discusses the calculation of energy savings (in kWh) for smart thermostats installed in electrical heating systems, using a formula that incorporates heating energy, savings percentage, and system efficiency. The percentage of savings is based on studies of central heating systems, as no specific studies were found for electric baseboards or in-floor systems.
4.6.2 KEY SOURCES FOR MEASURE INPUT DEVELOPMENT - The primary source of the values for measure input development is the Smart Thermostat for Electrical - Heating Systems Measure[48](#page-114-3) from the 025 DSM Residential Measure Assessm...
AI summary The primary source for measure input development is the Smart Thermostat for Electrical Heating Systems Measure from the 025 DSM Residential Measure Assessment. The measure summary table from this section is referenced.
4.6.6.1 Energy Savings (kWh) - Value: 265 - Source: This is the deemed unitary energy savings value for the Smart Thermostat for Electrical Heating - Systems Measure in the 2025 Measure Assessment. - Details: Some models of smart thermosta...
AI summary The document discusses the energy savings calculation for smart thermostats used in electrical heating systems, using a formula and referencing studies on Nest thermostats for central heating systems. The savings percentage is based on 12% for central air-source heat pumps, which are considered similar to electric baseboards and MSHPs.
4.7 EPI__WNDW_FLM_EPI_001__0 WINDOW FILM KITS - EPI provides participants with free-of-charge direct installations of energy efficient products. EPI has - played a pivotal role in transforming the residential lighting market by making ener...
AI summary EPI provides free direct installation of energy-efficient products, focusing on electrician-installed measures to support residential demand response. It is funded by electricity ratepayers and the Nova Scotia government's Green Fund. The program has evolved to phase out lighting measures as LEDs became standard.
4.7.2 KEY SOURCES FOR MEASURE INPUT DEVELOPMENT - The primary source of the values for measure input development is the Window Film Kit Measure[52](#page-118-2) from - the 2024-2025 DSM Residential Measure Assessment. The measure summary t...
AI summary The primary source for measure input development is the Window Film Kit Measure from the 2024-2025 DSM Residential Measure Assessment, with a reference to a measure summary table.
4.7.6.2 Coincident Peak Demand Savings (kW) - Value: 0.036 - Source: Value based on actual tracked savings from 2024. - Details: In practice, unitary peak demand savings are calculated by multiplying the unitary savings value - by the peak...
AI summary The value for Coincident Peak Demand Savings (kW) is 0.036, derived from actual tracked savings in 2024. The calculation uses a peak demand-to-energy ratio of 0.283 from the RES-Elec-Space Heat & Cool report by Navigant (2016-2018 DSM Plan).
Values, page 162 (PDF 336/1442). 2024-2025 DSM Measurement Assessment - Residential, Table 53: Mini-split Heat Pump Measure Summary, page 55 (PDF 72/159) Measure Free-ridership Participant Spillover NTGR Energy Efficiency Measures 17% 40/...
AI summary The document discusses the 2024-2025 DSM Measurement Assessment for residential energy efficiency, specifically focusing on Mini-split Heat Pump measures. It includes a table showing free-ridership, participant spillover, and NTGR values for Energy Efficiency and Solar PV measures. The section also introduces a discussion on incremental cost.
DSM Evaluation- Existing Residential Program, page 157 (PDF 183/229). Description Value Unit Source Energy Savings per Btu/h 0.076kWh/Btu/H pdf page 183/229 kW/ kWh Ratio 0.00159 Calculated from Table 21 Energy Savings per ton 912kWh/Ton C...
AI summary The document provides a table with calculated energy savings metrics for the DSM Evaluation- Existing Residential Program, including energy savings per Btu/h, kW/kWh ratio, energy savings per ton, and peak demand savings per ton. These values are derived from HOT2000 simulation results adjusted with HEA data.
- HomeWarming program. See Table 22[60](#page-140-0) of the 2024 Existing Residential Evaluation Report 2024-2025 DSM Measurement Assessment - Residential, Table 53: Mini-split Heat Pump Measure Summary, page 55 (PDF 72/159) Measure Catego...
AI summary The HomeWarming program is discussed in the context of the 2024-2025 DSM Measurement Assessment, with data on energy and peak demand savings from the Mini-split Heat Pump Measure. The table provides details on the number of participants, energy savings, and effective useful life of the measures.
1 4 Details: This value was calculated by multiplying the peak demand-to-energy ratio by the unitary energy
AI summary This value was calculated by multiplying the peak demand-to-energy ratio by the unitary energy. The calculation method is outlined in the details provided.
5 savings of 912 kWh. Input Description Total A Gross Energy Savings at the Meter for Non modelled Heat Pumps (GWh) 0.197 B Gross Peak Demand Savings at the Meter for Non modelled Heat Pumps (MW) 0.313 C = (B / A)/1000 Peak demand to energ...
AI summary The table provides energy savings data for non-modelled heat pumps, showing gross energy savings, peak demand savings, and a peak demand to energy ratio. It calculates coincident peak demand savings based on these figures.
- Source: This value was drawn from Table 53[61](#page-142-3) 8 of the 2024 Residential DSM Measure Assessment. 61 2024-2025 DSM Measurement Assessment - Residential, Table 53: Mini-split Heat Pump Measure Summary, page 55 (PDF 72/159) Tab...
AI summary The text discusses the assessment of mini-split heat pumps as a residential demand-side management (DSM) measure, including installation rates, energy savings parameters, and peak demand savings calculations. It references a table and subsections in the 2024 Residential DSM Measure Assessment.
12 4.14.1 MEASURE IDENTIFIERS & DEFINING CHARACTERISTICS Measure ID (Plan) IS__HVAC_TSTAT_001__0 Measure ID (Incremental Cost) RES__HVAC_TSTAT_001__0 Sector Residential Program Component Instant Savings Replacement Type RET Unit Basis Per...
AI summary This section outlines a measure for residential demand-side management, specifically the installation of smart thermostats for mini-split heat pumps under the Residential Efficient Product Rebates program.
14 4.14.2 KEY SOURCES FOR MEASURE INPUT DEVELOPMENT - 15 The primary sources of the values for measure input development are the Smart Thermostat for Electrical - Heating Systems Measure from the 2024 program evaluation[64](#page-148-3) 16...
AI summary The primary sources for measure input development are the Smart Thermostat for Electrical Heating Systems Measure from the 2024 program evaluation and the 2025 DSM Residential Measure Assessment. Summary tables from these sources are included.
18 Evaluated 2024 In netant Savings N let Energy and Peak Demand Savings (Continued) Product Category Smart Heavy-duty Outdoor Programmable Smart Thermostats Clotheslines Efficient Clothes Efficient Clothes Product Category Bars Timers The...
AI summary The table presents energy and peak demand savings for various product categories, including smart thermostats, efficient clothes washers, and dryers. It includes metrics such as gross and net energy savings, effective useful life, and peak demand savings, providing a detailed analysis of the performance of these products.
3 4.14.3 MEASURE LIFE 4 Value: 10 Years 5 Source: This value was drawn from Table 72 of the 2025 DSM Measure Assessment, shown above. 6 - 4.14.4 NET TO GROSS - Value: 1.0 - Source: This value was drawn from Table 32 of the 2024 Existing Re...
AI summary The document discusses the 10-year life value of a measure, energy savings calculations for smart thermostats in electrical heating systems, and the methodology used to determine heating consumption savings based on thermostat types. The savings calculation uses a formula and references the 2025 Illinois TRM for the 10.2% heating consumption savings value.
4.14.6.2 Coincident Peak Demand Savings (kW) Value: 0.000 Source: This is the deemed unitary peak demand savings value for the Smart Thermostat for Electrical - Heating Systems Measure[67](#page-151-1) in the 2025 Measure Assessment. - Det...
AI summary The deemed unitary peak demand savings value for the Smart Thermostat for Electrical Heating Systems Measure is 0.000, based on the 2025 Measure Assessment. This value is derived from a peak demand-to-energy ratio assumption from literature review findings.
14 4.15.2 KEY SOURCES FOR MEASURE INPUT DEVELOPMENT - 15 The primary sources of the values for measure input development are the Smart Thermostat for Electrical - Heating Systems Measure from the 2024 program evaluation[68](#page-152-3) 16...
AI summary The primary sources for measure input development are the 2024 program evaluation and the 2025 DSM Residential Measure Assessment, which provide values for measure input development.
3 4.15.3 MEASURE LIFE 4 Value: 10 Years 5 Source: This value was drawn from Table 72 of the 2025 DSM Measure Assessment, shown above. 6 - 4.15.4 NET TO GROSS - Value: 1.0 - Source: This value was drawn from Table 32 of the 2024 Existing Re...
AI summary The document discusses the 'Measure Life' for a DSM program, with a value of 10 years, sourced from Table 72 of the 2025 DSM Measure Assessment. It also outlines energy savings calculations for smart thermostats used in electrical heating systems, referencing the 2025 Illinois TRM for a 10.2% heating consumption savings estimate.
4.15.6.2 Coincident Peak Demand Savings (kW) Value: 0.000 Source: This is the deemed unitary peak demand savings value for the Smart Thermostat for Electrical Heating Systems Measure[71](#page-155-1) in the 2025 Measure Assessment. Details...
AI summary The document discusses the deemed unitary peak demand savings value of 0.000 for the Smart Thermostat for Electrical Heating Systems Measure in the 2025 Measure Assessment. It also outlines details about Outdoor Heavy Duty Timers under the Instant Savings program, including measure identifiers, program components, measure life, net-to-gross ratios, and incremental costs.
4.16.6.1 Energy Savings (kWh) Value: 122 kWh - Source: 2024-2025 DSM Measure Assessment, Residential, Plug Load Control Measures, Heavy-duty - Outdoor Timers, page 118. - Details: For heavy-duty outdoor timers, the electrical unitary energ...
AI summary The energy savings value of 122 kWh for heavy-duty outdoor timers is derived from the OPA 2012 Consumer Program Evaluation, which found these timers are used for outdoor lighting, pool pumps, and car block heaters.
- outdoor timers sold through Instant Savings. Parameter Instant Savings Reference Measure Description and Identification Measure Description Heavy-duty outdoor timers rebated in store - Baseline Outdoor outlets without timers General Para...
AI summary The text outlines parameters for outdoor timers sold through the Instant Savings program, including measure description, baseline, installation rates, effective useful life, and energy savings metrics. The data provides technical details relevant to energy efficiency and rebate programs.
4.16.6.2 Coincident Peak Demand Savings (kW) Value: 0 kW Source: 2024-2025 DSM Measure Assessment, Residential, Plug Load Control Measures, Heavy-duty Outdoor Timers, page 118. Details: Calculated by multiplying the unitary savings value b...
AI summary The Coincident Peak Demand Savings for the 2024-2025 DSM Measure Assessment, Residential, Plug Load Control Measures, Heavy-duty, Outdoor Timers is reported as 0 kW. The value is calculated by multiplying the unitary savings value by the peak demand-to-energy ratio, as detailed on page 118.
1 5.1.6.2 Coincident Peak Demand Savings (kW) 2 Value: kW 3 Source: 4 Details:
AI summary This section outlines the topic of Coincident Peak Demand Savings (kW), providing a value, source, and details. However, the content is minimal and lacks specific information or discussion.
5 1 Request IR-39: 2 3 Appendix A - Preferred Plan pp. 1-112 (Attach. 1-5) 4 5 (a) Regarding Section 2.2.2 "Residential Behaviour Program": 6 i) Pdf pg. 93 states: "In 2023, E1 collaborated with NS Power to address program 7 overlap betwee...
AI summary The document outlines requests for clarification regarding E1's Residential Behaviour Program, allocation of energy savings in the Preferred Plan, and the rationale for increasing DSM spending despite decreasing energy savings. It highlights concerns about program overlap, communication with NS Power, and the effectiveness of the DSM plan.
i) If required, please recalculate the Attachment 3 annual PAC score and payback period for each measure within each program for each year from 2027 to 2031, and provide a revised Appendix A, Attachment 3 in Excel format with all formulae...
AI summary The document requests a recalculation of the Attachment 3 annual PAC score and payback period for each measure within each program from 2027 to 2031, and asks whether Nova Scotia Power has considered reducing non-incentive related costs for programs that fail the PAC test.
E1 Responses to Nova Scotia Energy Board (NSEB) Information Requests NON-CONFIDENTIAL 1 • For the programs that fail the PAC test in Appendix A of Exhibit E-1 2 (pdf pgs. 117-121), please identify the reduction in "non-incentive" 3 related...
AI summary The document discusses Nova Scotia Power's (E1) response to information requests from the Nova Scotia Energy Board (NSEB), specifically addressing the Payback Analysis Criteria (PAC) test for programs that failed and the rationale for including heat pump cleanings as a Demand Side Management (DSM) measure.
1 (d) The higher per-unit cost of Residential sector programs reflects the structure of that 2 customer base, not an inefficient allocation of resources. Residential customers represent 3 approximately 519,000 customers, or 91 percent of N...
AI summary The Residential sector programs have higher per-unit costs due to the large customer base and the need for diverse and equitable program delivery. E1 emphasizes that the allocation of resources aligns with the Balanced Plan Principles and that shifting investment to BNI would not meet the needs of Residential customers or align with these principles.
- 26 Please refer to Attachment 1 of E1's response to IG IR-21. 1 (f) E1 confirms that the investment in Appendix A, Table 17 is correct. Please refer to 2 Attachment 1 of E1's response to NSEB IR-38. 3 (i) Please refer to E1's response to...
AI summary E1 confirms the correctness of investments in various appendices and tables, referencing attachments from their responses to NSEB information requests. They mention that certain low-income and equity programs did not pass the cost-effectiveness test but are fully funded or receive higher incentives, and reducing support for these programs could create barriers for low-income customers and Mi'kmaw communities.
Request IR-40: Appendix A - Preferred Plan pp. 1-112 (Attach. 1-5) Exhibit E-1, Appendix A, page 19 of 112 (pdf pg. 107): E1 notes that, for existing measures, measure-level inputs were developed using the most recently available program a...
AI summary Nova Scotia Power (E1) modified measure-level inputs for existing programs in the DSM Plan to reflect known or expected changes from 2027–2031, including updates to energy savings, effective useful life, and participation assumptions based on evaluation data and market developments.
5 Modifications were determined through application of evaluation results, analysis of recent 6 program data, consultant input, and professional judgement. Where future changes were known 7 or expected, these were incorporated through stag...
AI summary Modifications were determined based on evaluation results, recent program data, consultant input, and professional judgment. Future changes were incorporated through staged or time-dependent adjustments.
8 were subject to iterative review to ensure they reflect current and expected conditions. 1 Request IR-41: 2 3 Appendix A - Preferred Plan pp. 1-112 (Attach. 1-5) 4 5 Appendix A, page 92 of 112 (pdf pg.180), Table 54: 2027-2031 Outreach A...
AI summary The Nova Scotia Energy Board (NSEB) requested information from EfficiencyOne (E1) regarding the measurement of tools and content on its website and social media platforms, the definition of a 'total awareness score,' and the rationale for growing its preferred partner membership. E1 responded that it uses monthly measurement reports to track website performance and engagement.
16 assess E1's fulfillment of its legislative mandate. 1 Request IR-43: 2 3 Appendix A - Preferred Plan pp. 1-112 (Attach. 1-5) 4 5 Exhibit E-1, Appendix A, page 103 of 112 (pdf pg. 191): 6 7 E1 notes that the demand response program evalu...
AI summary E1 explains that demand response differs from energy efficiency programs by providing temporary load reduction during peak times, whereas energy efficiency measures like mini-split heat pumps provide ongoing energy and peak demand savings. E1's programs are evaluated based on both energy and peak demand savings metrics.
M12780 – EfficiencyOne (E1) 2027–2031 Demand Side Management (DSM) Resource Plan Application - 1 with NS Power's system operations and dispatch decisions. Available Demand Response - 2 Capacity is therefore the appropriate metric for asses...
AI summary The document discusses E1's 2027–2031 Demand Side Management (DSM) Resource Plan Application, highlighting the importance of Available Demand Response Capacity as a metric for assessing the performance of E1's DR program.
- 3 Please also refer to E1's response to part (a) of Synapse IR-70 for further detail. 1 Request IR-44: 2 3 Appendix A - Preferred Plan pp. 1-112 (Attach. 1-5) 4 5 Exhibit E-1, Appendix A, page 108 of 112 (pdf pg. 196): 6 7 E1 discusses e...
AI summary E1 (Nova Scotia Power) responds to the Nova Scotia Energy Board's information request regarding performance targets for estimation accuracy and program spending variances. E1 argues against establishing these as standalone targets, citing the need for flexibility in responding to market conditions and customer uptake, while emphasizing the importance of core performance targets such as energy savings and demand response capacity.
1 based accountability. Imposing input-level metrics such as estimation accuracy or spending 2 variances as binding performance targets would shift the regulatory framework toward a 3 prescriptive, compliance-oriented model, inconsistent w...
AI summary E1 argues that imposing input-level metrics as binding targets would create a prescriptive regulatory framework, conflicting with the flexibility needed for effective demand-side management. E1's mid-course adjustment process provides accountability while preserving optimization of program delivery, aligning with ratepayer interests.
E1 Responses to Nova Scotia Energy Board (NSEB) Information Requests NON-CONFIDENTIAL 1 Request IR-45: 2 3 Appendix A - Preferred Plan pp. 1-112 (Attach. 1-5) 4 5 Exhibit E-1, Appendix A, page 108 of 112 (pdf pg. 196): 6 7 E1 discusses fur...
AI summary Nova Scotia Power (E1) responds to information requests from the Nova Scotia Energy Board (NSEB) regarding mid-course adjustments to demand-side management plans and cost assumptions in the General Rate Application. E1 references prior responses and states it is not aware of required updates to avoided costs.
1 Request IR-49: 2 3 Appendix A - Preferred Plan pp. 1-112 (Attach. 1-5) 4 5 Reference Appendix A, Attachment 3 (Exhibit E-1-(ii)): 6 7 E1 provides justification for measures that do not pass the program administrator cost (PAC) 8 test. 9...
AI summary The Nova Scotia Energy Board (NSEB) has requested detailed justifications from E1 regarding its heat pump maintenance costs, investment degradation, and the cost-benefit analysis of specific measures in its demand-side management plan. E1 is being asked to explain why certain measures may not meet the program administrator cost (PAC) criteria and how they contribute to maintaining delivery costs and contractor engagement.
1 Request IR-50: 2 3 Appendix A - Preferred Plan pp. 1-112 (Attach. 1-5) 4 5 Regarding Appendix A, Attachment 5 of Exhibit E-1 – "Innovation Framework, Process and Plan 6 for 2027-2031": 7 8 (a) Pdf pg. 21 of the application: "E1 engaged w...
AI summary The document discusses E1's submission of an Innovation Framework, Process, and Plan for 2027–2031 as part of its application, and includes a request for feedback from DSMAG parties and an organizational chart of E1's Innovation team. The Innovation team is part of E1's Engineering and Planning team and is responsible for managing innovation initiatives.
1 Request IR-51: 2 3 Appendix A - Preferred Plan pp. 1-112 (Attach. 1-5) 4 5 Exhibit E-1, Appendix A, Attachment 5 - Innovation Framework, page 1 of 14 (pdf pg. 216): 6 7 E1 refers to its innovation activities but notes that this overview...
AI summary The document includes requests and responses related to E1's innovation activities, particularly non-DSM funded initiatives and its 2027 innovation plan. E1 notes that non-DSM innovation is supported by government funding aligned with specific objectives, and refers to an attachment for the innovation plan.
2.1 Lead with purpose This Innovation plan will do this by: - Setting direction for researching, developing, and piloting new programs, measures, and delivery models early. In doing so, E1 is better positioned to achieve its annual and mul...
AI summary This section outlines E1's Innovation plan, which focuses on researching, developing, and piloting new programs and delivery models to meet annual and multi-year targets. The plan also aims to identify emerging measures and services to support customers and partners in transforming energy use.
2.2 Build for the long term This Innovation plan will do this by: - Working with partners to increase capacity to accelerate the energy transition. For example, training contractors on new technologies being tested through projects in the...
AI summary The Innovation plan aims to build for the long term by increasing capacity through partnerships and training contractors on new technologies, and by exploring emerging measures and services to advance industry and market readiness.
Criterion 2 (CIO): Benefits to Nova Scotian electricity consumers through optimized electricity system costs Justification of selection: Activities that produce benefits to the electricity system through DSM and other agreements generally...
AI summary The document discusses how Demand Side Management (DSM) and related activities contribute to benefits for Nova Scotian electricity consumers by optimizing system costs. Energy efficiency is highlighted as central to E1's business, and the E&P team is encouraged to consider all system benefits when evaluating new DSM opportunities.
Long-term vision: Recognize all known electricity system benefits when evaluating potential projects Establish unknown system benefits, e.g. avoided costs for ancillary services Delivery of multiple forms of electricity DSM by E1
AI summary The long-term vision includes recognizing all known electricity system benefits, establishing unknown system benefits such as avoided costs for ancillary services, and delivering multiple forms of electricity demand-side management (DSM) by E1 (Nova Scotia Power).
3 Innovation Projects The ELT prioritized three subject areas that support the innovation objectives while aligning with the Strategic Plan. The subject areas are described in Section [3.1.](#page-196-1) The 2025 Innovation Roadmap focuses...
AI summary The 2025 Innovation Roadmap emphasizes completing active projects, transitioning completed pilots to programs, and starting new pilots. The R&D Engineering team found that the current portfolio is well-aligned with market trends, and feedback highlights the importance of project close-out and transitioning pilots to programs.
3.1 Subject Areas The innovation roadmap (section [3.2)](#page-199-0) categorizes projects by subject area. A jurisdictional scan of each subject area was conducted in 2023 to identify active programs in North America. Five subject areas w...
AI summary The document outlines the selection and revision of subject areas for the innovation roadmap, highlighting the focus on avoided costs such as carbon, transmission capacity, non-energy benefits, and ancillary services. These subject areas are periodically reviewed and adjusted based on new opportunities.
3.1.1 Subject Area 1: Market Transformation The R&D Engineering team sees substantial energy, demand and GHG savings potential through Market Transformation (MT) programs[3](#page-197-2) . In some jurisdictions (such as California, Arizona...
AI summary The R&D Engineering team highlights the potential of Market Transformation (MT) programs to drive energy, demand, and GHG savings, particularly as traditional programs lose effectiveness. MT programs in regions like California and Massachusetts have shown significant success. In 2025, the HPWH pilot will transition to PM, with ongoing efforts to expand MT program acceptance and planning for future initiatives in the 2027-2031 DSM plan.
3.1.2 Subject Area 2: Distributed Energy Resources (DERs) DERs are small-scale energy generation or storage systems that are located close to the point of use, such as in homes, businesses or communities. Typical technologies include solar...
AI summary The document discusses the role of Distributed Energy Resources (DERs) in Demand Side Management (DSM), focusing on the testing of Behind-The-Meter batteries (BTM) as part of a load flexibility pilot. It also mentions investigating commercial battery opportunities for integration into long-term load flexibility strategies.
3.4 Innovation Pilots Overview No. Technology Description 2025 Action Short-term Deliverables (1-3 years) Medium-term Deliverables (3-5 years) Long-term Deliverables (5+ years) Sector(s) Category / Categories 1 Domestic Hot Water Controlle...
AI summary This section outlines two innovation pilot programs: Domestic Hot Water Controllers and Smart Thermostats, both aimed at enhancing demand response capabilities. The pilots focus on load shifting and flexibility in residential and commercial sectors, with short-term, medium-term, and long-term deliverables outlined.
Definition of a pilot Pilots are small-scale experiments meant to test new ideas and prepare for eventual implementation of the idea being tested for permanent implementation at scale. The objective of a pilot is to: - Validate that the id...
AI summary Pilots are defined as small-scale experiments aimed at testing new ideas and preparing for their potential large-scale implementation. The purpose includes validating the idea, identifying gaps, collecting feedback, and assessing industry capacity.
3.4.1.1 DHW DLC direct install There are three strategic objectives of the DHW DLC direct install pilot, centered around demand response capability, as follows. The first objective is to work closely with services, business development man...
AI summary The DHW DLC direct install pilot has three strategic objectives: evaluating EPI DHW DLC delivery for MURBs, designing solutions for central hot water control in MURBs and other segments, and testing flexible load use cases for DHW controllers. The pilot aims to achieve significant demand response capacity by targeting MURBs and other customer segments.
3.4.1.2 DR Load flexibility The DR load flexibility pilot will launch in Q1 of 2025 and will focus on leveraging existing DR technologies/participants in new use cases beyond system peak curtailment. The new use cases may include cold load...
AI summary The DR load flexibility pilot will launch in Q1 2025, aiming to expand DR use cases beyond system peak curtailment, such as cold load pickup and renewable following, to improve program cost-effectiveness. The pilot seeks to increase DR value for ratepayers and enhance grid stability, with evaluation planned after the first DR season.
3.4.1.3 Value stacking The value stacking pilot will launch in Q2 of 2025 and will focus on how to best use behind the meter (BTM) Distributed Energy Resources (DERs) for the customer. For example, peak shaving the customer load vs. discha...
AI summary The value stacking pilot, launching in Q2 2025, will explore the optimal use of behind-the-meter distributed energy resources (DERs) for customers. It will evaluate methods such as peak shaving, net metering, and demand response participation to determine the most valuable combination.
3.4.2.1 Heat pump water heater MT pilot In 2022, R&D engineering and an expert consultant, Resource Innovations (RI), completed phase I of this project: a market characterisation study to identify an ideal candidate for E1's first MT pilot...
AI summary In 2022, phase I of the HPWH MT pilot project was completed, identifying HPWH as the most viable measure. Phase II followed with a baseline assessment, and phase III was completed in 2024. Market interventions for HPWHs continue into 2025 and beyond.
3.4.3 Closed pilots (2025) The Deep Retrofit Navigator pilot was undertaken together with Halifax Regional Municipality (HRM) from 2023-2025.
AI summary The Deep Retrofit Navigator pilot was a collaborative effort between the Halifax Regional Municipality (HRM) and other entities from 2023 to 2025.
1 Request IR-53: 2 3 Appendix A - Preferred Plan pp. 1-112 (Attach. 1-5) 4 5 Exhibit E-1, Appendix A, Attachment 5 - Innovation Framework, page 6 of 14: Table 1: Projected 6 Direct Expenditures by Focus Area: 7 8 (a) How are the budget amo...
AI summary The response to Request IR-53 outlines how budget amounts for focus areas in the 2027–2031 DSM Plan were determined based on EfficiencyOne's (E1) expectations for implementing the plan and aligning with 2026 approved amounts. Specific innovation projects have not yet been individually approved, as project selection will occur after the Nova Scotia Energy Board's decision on the DSM Plan.
E1 Responses to Nova Scotia Energy Board (NSEB) Information Requests NON-CONFIDENTIAL 1 Request IR-54: 2 3 Appendix A - Preferred Plan pp. 1-112 (Attach. 1-5) 4 5 Exhibit E-1, Appendix A, Attachment 5 - Table 4, 5, and Figure 2, pages 11-1...
AI summary Nova Scotia Power (E1) responds to the Nova Scotia Energy Board (NSEB) request regarding the criteria for transitioning DSM measures from the concept stage to the planning stage. The response outlines the use of readiness levels and thresholds for market, performance, and program readiness in evaluating innovation activities.
3 Appendix A - Preferred Plan pp. 1-112 (Attach. 1-5) 4 - 5 Board staff notes that in Appendix A Attachment 4 from E1's 2023-2025 DSM application - 6 (M10473), E1 included columns identifying the following: "Gross Per Unit One-Time - 7 Inc...
AI summary The Board staff notes that certain cost-related columns from E1's 2023-2025 DSM application (M10473) are missing in the current matter's Appendix A Attachment 3. A response (IR-55) refers to Table 1, explaining the absence of these metrics in the 2027–2031 DSM tables.
19 Table 1: Metrics in 2023-2025 DSM Plan Application Column in 2023-2025 DSM Plan Application Attachment 4 Explanation Gross Per Unit One-Time Incremental Measure Cost ($) Following the Nova Scotia Energy Board's Decision on the Benefit-C...
AI summary The document discusses changes in the cost-effectiveness test for demand-side management (DSM) programs, specifically the removal of the Total Resource Cost (TRC) test after the Nova Scotia Energy Board's decision on the Benefit-Cost Analysis (BCA) test. The new Program Administrator Cost (PAC) test does not include incremental costs, leading to the exclusion of the 'Gross Per Unit One-Time Incremental Measure Cost' column in the 2027–2031 DSM Plan Application.
M12780 – EfficiencyOne (E1) 2027–2031 Demand Side Management (DSM) Resource Plan Application
AI summary This document outlines E1's 2027–2031 Demand Side Management (DSM) Resource Plan Application, detailing their proposed energy efficiency and demand management initiatives for the upcoming period.
1 Table 1: Rate and Bill Impacts by Rate Class as a Result of 2027-2031 DSM Preferred Plan Activities (100% 2 Rate Class Cost Allocation) Rate Class Rate Codes Average Rate Impact (%) Average Rate Impact (cents/kWh) Participant Average Bil...
AI summary The table presents the rate and bill impacts by rate class as a result of the 2027-2031 DSM Preferred Plan Activities. It shows the average rate impact percentage and cents per kWh, as well as the average bill impact for participants and non-participants across various rate classes.
8 Table 2: Correction of Appendix B Table 1 - Rate and Bill Impacts by Rate Class as a Result of 2027-2031 DSM 9 Preferred Plan Activities Rate Class Rate Codes Average Rate Impact (%) Average Rate Impact (cents/kWh) Participant Average Bi...
AI summary The document presents a table analyzing the rate and bill impacts by rate class resulting from the 2027-2031 DSM 9 Preferred Plan Activities. It includes a request for clarification regarding the absence of rate impact in 2027 and the diminishing but positive rate impact from 2028 to 2046, specifically in column AQ.
12 Table 7: 2025 Free-ridership, Spillover, and NTGRs Program Component and Measure Type Spillover Levels NTGRs Residential Appliance Retirementa Refrigerators 43% 0% 0.57 Freezers 45% 0.55 Air Conditioners 47% 0.53 Small Refrigerators 32%...
AI summary Table 7 presents data on free-ridership, spillover, and NTGRs for various residential and appliance programs in 2025. It details percentages for different program components such as appliance retirement, instant savings, and energy-efficient appliances.
- 3 [mera\_Annual\_Report.pdf](https://s205.q4cdn.com/781121964/files/doc_financials/2024/ar/2024_Emera_Annual_Report.pdf) (last accessed January 15, 2026)." 1 Request IR-64: 2 3 Exhibits E-2 - 2025 DSM Annual Progress Report 4 5 In refere...
AI summary The document discusses an information request (IR-64) regarding the 2025 DSM Annual Progress Report, specifically the Net Realization Rate of 101% for Affordable Single-family Homes and the calculation of Lifetime Net Electrical Energy Savings. The response explains that the rate was influenced by non-modelled heat pump savings from 2024.
M12780, Exhibit E-3, 2025 DSM Programs Evaluation Reports, 2025 DSM Programs Evaluation, Overall Executive Summary, March 24, 2026, page 25. 1 Request IR-66: 2 3 Exhibits E-2 - 2025 DSM Annual Progress Report 4 5 Please provide the NTGR Ca...
AI summary The document discusses the calculation of the Net Total Grant Rate (NTGR) for 2025 DSM programs, which is determined using free-ridership and spillover values. The NTGR is applied at different levels, including measure, project, or program component, and is calculated with the formula NTGR = (1 – % Free-ridership + % Spillover). Table 7 provides specific free-ridership and spillover values for various residential programs.
E-16E1 (Synapse) RIRs 1-90
256 passages
Request IR-01: Please provide Appendix A - Attachment 3: 2027–2031 Preferred Plan Measure-level Energy Efficiency and Solar-PV Technical Tables and Appendix A – Attachment 4: 2027–2031 Preferred Plan Demand Response Technical Tables in Exc...
AI summary The document outlines responses to two information requests regarding the 2027–2031 DSM Plan. It directs the requester to specific attachments containing technical tables, modeling assumptions, and results, as well as BCA workbooks related to the plan's development.
1 o Attachment 2, Appendix F: Round 2 Measure Level Technical Tables 1Solar-PV 2 Base (excel) 3 o Attachment 2, Appendix G: Round 2 Measure Level Technical Tables 1SE-Base 4 (excel) 5 o Attachment 2, Appendix H: DSMAG Consideration of the...
AI summary EfficiencyOne (E1) has modified certain attachments in its IR response, replacing specific references to DSMAG members with general references to the DSMAG and removing DSMAG Round 1 comments. These materials and discussions are critical to the development of E1's DSM plans and are conducted confidentially and without prejudice.
Investment Level Some DSMAG members commented that the overall DSM investment modelled in Round 2 2026-2030 was too high. Based on this feedback, E1 reviewed and updated the DSM investment levels modelled for Round 1 of the 2027-2031 DSM P...
AI summary DSMAG members criticized the high DSM investment levels in Round 2 (2026-2030), prompting E1 to adjust Round 1 investment levels for the 2027-2031 DSM Plan. The revised model shows reduced investment compared to Round 2, as illustrated in Figure 1.
Demand Response Some DSMAG members commented that the Demand Response investment modelled in Round 2 2026- 2030 was too high. The Demand Response inputs and assumptions were updated for 2027-2031 DSM Plan modelling to reflect 2024-2025 Dem...
AI summary DSMAG members criticized the high Demand Response investment in Round 2 (2026-2030). E1 updated 2027-2031 DSM Plan modelling with 2024-2025 results, identifying cost-reduction opportunities. Investment levels in both base and high DR scenarios decreased compared to Round 2, as shown in Figure 2.
Investment Level As noted above, some DSMAG members raised concerns about the overall DSM investment level modelled in Round 2 2026-2030, including the investment in new resources. Inputs and assumptions for Strategic Electrification and S...
AI summary DSMAG members expressed concerns about the investment levels in Round 2's 2026-2030 DSM plan, leading to adjusted assumptions in Round 1 for 2027-2031. Strategic Electrification and Solar-PV investments were reduced compared to previous models, as illustrated in Figure 3.
Strategic Electrification Strategic Electrification, as modelled in Round 1 (2027-2031 DSM Plan) reflects participation that ramps up over the five-year period as implementation of the resource becomes more established. Strategic Electrifi...
AI summary Strategic Electrification is modeled in the 2027-2031 DSM Plan using existing program components (Instant Savings, BER, Custom), avoiding new resource deployment costs. Incentive levels are reviewed against E1's methodology and similar measures, though low-income/equity support is absent in current models. Section 3.5 provides further details.
Solar-PV Solar-PV, as modelled in Round 1 (2027-2031 DSM Plan) reflects participation that ramps up over the fiveyear period as implementation of the resource becomes more established. Solar-PV measures, as modelled, will specifically targ...
AI summary The 2027-2031 DSM Plan models Solar-PV participation increasing over five years, targeting low-income and equity groups. Incentive levels for Solar-PV remain under review and refinement. Details on modelling results are referenced in Section 3.4.
Measure Characterization During 2027-2031 DSM Plan development, measure characterizations were updated to reflect the most current available information, primarily drawing on the 2023 and 2024 DSM evaluation results, internal program data,...
AI summary The 2027-2031 DSM Plan development updated measure characterizations using 2023-2024 evaluations, internal data, and expert insights. Ongoing reviews with Guidehouse support the process, and technical tables will be shared with DSMAG post-Round 2 modelling. Key assumptions are detailed in section 2.4.
Table 2: Key Initiatives in Round 1 Program Program Component Initiative Description New Residential Advanced New Homes New program component to help Mi'kmaw communities build high performing homes Solar-PV Residential New DSM resource – t...
AI summary Table 2 outlines key initiatives in Round 1, including new program components for Mi'kmaw communities, non-profits, and new categories like Enabling Strategies. Section 2.3 discusses cost-effectiveness testing as a key consideration in the proceeding.
2.4 MODELLING Attachment 1 [(2027-2031 Round 1 Modelling Assumptions.xlsx)](https://efficiencyns.sharepoint.com/:x:/r/sites/DSMAdvisoryGroup/Shared%20Documents/2027-2031%20DSM%20Resource%20Plan/Round%201%20Modelling%20Assumptions%20and%20R...
AI summary Attachment 1 outlines the modelling assumptions for the 2027–2031 DSM Resource Plan, including considerations for low-income and equity factors.
3.1 DSM RESOURCE SCENARIOS – ROUND 1 MODELLING RESULTS [Table 3](#page-12-0) provides results for the DSM Resource scenarios modelled in Round 1. Round 1 Model Input Assumptions and Results
AI summary This section outlines the results of the DSM Resource scenarios modelled in Round 1, with Table 3 providing the input assumptions and outcomes of the modelling process.
Table 4: 2023-2025 DSM Resource Plan & 2026 DSM Extension 2023-2025 DSM Resource Plan (as Approved) 2026 DSM Extension (as Proposed) 2023-2026 DSM RESOURCE Investment Energy Savings (GWh) Demand Savings (MW) Available Capacity (MW) Investm...
AI summary Table 4 outlines the 2023-2025 DSM Resource Plan and the proposed 2026 DSM Extension, showing investments in energy efficiency and demand response programs, along with energy and demand savings, and available capacity. The total investment for 2023-2026 is $236.75 million, with an average annual investment of $59 million.
Scenarios 1EE-Base & 2EE-High - Base scenario investment is aligned with both the Base DSM investment in the current Integrated Resource Plan (IRP) and the Base EE scenario modelled in Round 2 2026-2030. - High scenario has higher particip...
AI summary The document outlines two scenarios, Base and High, for energy efficiency investments. The Base scenario aligns with current Integrated Resource Plan (IRP) and Base EE models, while the High scenario assumes higher participation driven by programs like Instant Savings and Efficient Product Installation, and a 5% annual increase in investment as per DSMAG feedback.
3.3 DEMAND RESPONSE ROUND 1 MODEL RESULTS [Table 8](#page-16-1) provides insights for the two DR scenarios modelled in Round 1.
AI summary This section presents the results of the Demand Response Round 1 model, with Table 8 providing insights into the two DR scenarios modelled.
Table 8: DR Scenarios - Round 1 Modelling Insights Round 1 Model - All DR Scenarios 2027-2031 Scenario 1DR-Base Scenario 2DR-High Capacity Impacts Capacity as a % of NSP Net System Peak (2031) 2,503 MW (2025 Load Forecast) 1.2% 1.6% Capaci...
AI summary Table 8 presents two demand response (DR) scenarios, DR-Base and DR-High, evaluating their capacity impacts and investment benefits. The DR-High scenario shows higher capacity contributions and greater lifetime utility benefits compared to the DR-Base scenario.
The five-year total program component and pathways Round 1 modelling results are provided in [Table 9](#page-16-2) for Scenario 1DR - Base.
AI summary The document references Round 1 modelling results for Scenario 1DR - Base, which outlines the five-year total program component and pathways as presented in Table 9.
Table 9: Scenario 1DR-Base – Round 1 Modelling Results TRC & PAC NS Cost Test Available Total Program Scenario 1DR-Base Investment1 Lifetime Lifetime Capacity2 Resource Cost Administrator NS Cost Test (2027-2031) ($ million) Benefits Benef...
AI summary Table 9 presents the results of the Scenario 1DR-Base – Round 1 Modelling, detailing various demand response and energy efficiency programs, their investments, benefits, and costs. The table includes data for residential demand response, smart thermostats, water heaters, battery control, EV charging control, and BNI programs, with total investments and cost test figures provided.
Available capacity represents the total capacity available in 2031 for E1 programs. Five-year (2027-2031) cost-effectiveness. Includes E1 programs and costs only. Round 1 Model Input Assumptions and Results The five-year total program comp...
AI summary The text discusses the available capacity for E1 programs in 2031 and mentions the five-year (2027-2031) cost-effectiveness analysis, which includes E1 programs and costs. It references a table containing modelling results for Scenario 2DR – High.
Table 10: Scenario 2DR-High – Round 1 Modelling Results Scenario 1DR-High TRC & PAC NS Cost Test Available Total Program Investment1 ($ million) Lifetime Lifetime Capacity2 Resource Cost Administrator NS Cost Test (2027-2031) Benefits Bene...
AI summary Table 10 presents the results of Scenario 2DR-High – Round 1 Modelling, which includes various demand response and energy efficiency programs with associated investment, benefits, and capacity metrics. The table outlines the costs and benefits of different initiatives such as residential demand response, smart thermostats, and battery control.
Scenarios 1DR-Base & 2DR-High - Base scenario aligns with a year over year average increase of 2.5 MW compared to the 2026 DSM Extension target of 16.3 MW. - High scenario aligns with achieving 90% of the Base DR in the IRP. - High scenari...
AI summary The Base scenario aligns with a 2.5 MW annual increase in demand response (DR) capacity, while the High scenario aims for 90% of the Base DR in the Integrated Resource Plan (IRP). The High scenario is driven by higher residential participation in Eco-Shift, particularly through DLC-smart thermostats and DLC-water heaters. These scenarios focus on demand-side management and capacity planning through 2031.
3.5 STRATEGIC ELECTRIFICATION ROUND 1 MODEL RESULTS [Table 13](#page-19-1) provides insights for the Strategic Electrification scenario modelled in Round 1.
AI summary This section presents the results of the Strategic Electrification Round 1 model, with Table 13 providing key insights into the scenario analysis.
Table 13: 1SE-Base Scenario - Round 1 Modelling Insights Scenario 1SE-Base RES BNI Total Carbon Emissions Avoided Five-Year Annual Total (kilotonne) 2 10 12 Cumulative Lifetime (kilotonne) 32 192 224 Energy & Demand Impacts Lifetime Net En...
AI summary Table 13 presents modeling insights from the 1SE-Base Scenario, including carbon emissions avoided, energy and demand impacts, investment splits, and unit costs for RES and BNI. The data highlights the distribution of energy savings and investment across different sectors.
Table 14: 1SE-Base – Round 1 Modelling Results Scenario 1SE - Base (2027-2031) Investment ($ million) Lifetime TRC & PAC Benefits ($ million) NS Cost Test Lifetime Benefits ($ million) First Year Electric Energy Savings (GWh) Peak Demand S...
AI summary Table 14 presents the Round 1 Modelling Results for the 1SE-Base scenario, analyzing investment, energy savings, and cost-benefit metrics for residential and BNI programs. The table highlights energy savings, net energy impacts, and cost tests, showing the economic and energy performance of various efficiency programs.
Scenario 1SE-Base - Residential strategic electrification is being delivered through the Instant Savings program component. - BNI strategic electrification is being delivered through both the BER and Custom program components. - The measur...
AI summary Residential and BNI strategic electrification is being delivered through various programs, primarily involving heat pumps. E1 conducted a Rate Impact Measure (RIM) analysis to assess the impact of electrification on electricity costs as defined in the Public Utilities Act, evaluating both benefits and costs associated with the program.
Table 16: Enabling Strategies – Overall investment by Category Category 2027-2031 Investment ($M) Education and Outreach 8.5 Development and Research 6.0 Other Enabling Strategies 14.1 Market Transformation 8.8 TOTAL 37.5 For comparison pu...
AI summary Table 16 outlines the investment in Enabling Strategies from 2027-2031, with a total of $37.5M allocated across categories such as Education and Outreach, Development and Research, Market Transformation, and Other Enabling Strategies. Table 17 compares this with average annual investments for previous plans, showing projected changes in investment levels.
6.1 REPORTING E1 will report on the implementation of the 2027-2031 Plan through quarterly reports (quarters one through three), annual progress reports, annual evaluation reports, and annual audited financial statements filed with the NSE...
AI summary E1 will provide regular reporting on the implementation of the 2027-2031 Plan, including quarterly and annual reports, evaluations, and audited financial statements, all to be submitted to the NSEB.
2. BACKGROUND On June 16, 2015, EfficiencyOne (E1), Nova Scotia Power Incorporated (NS Power), the Consumer Advocate, the Small Business Advocate, the Ecology Action Centre, the Affordable Energy Coalition, and the Industrial Group signed...
AI summary In 2015, EfficiencyOne and other stakeholders signed a Consensus Agreement to establish a Standardized Filing Framework for DSM applications, which was approved by the NSUARB in 2015 and implemented in 2016. The Framework was later reviewed and updated by the DSMAG in 2024 and 2025 following guidance from the NSUARB in the 2023-2025 DSM Plan Decision.
Table 1: STANDARDIZED FILING FRAMEWORK ITEM DESCRIPTION 3.1 Various Scenarios Based on the UARB's October 7, 2015 Order, EfficiencyOne will "provide one or more alternate scenarios of DSM budgets for the Board to consider, and NSPI is to p...
AI summary The standardized filing framework outlines that EfficiencyOne must present various scenarios of DSM budgets for the Board's consideration, along with rate impact analysis from NSPI. Portfolio-level metrics such as investment, energy savings, demand savings, and cost-effectiveness testing are required for each scenario.
Table 2: PROGRAM DESCRIPTION TEMPLATE ITEM DESCRIPTION 1. OVERVIEW A brief description of the program intent, target market, and type of service or rebate. 2. OBJECTIVES Long-term objectives for the program. 3. OPPORTUNITY A summary of the...
AI summary The document presents a program description template used in regulatory proceedings, outlining key sections such as program overview, objectives, market opportunity, design, performance indicators, and low-income equity considerations. It also includes a section for comparing program alternatives within the proposed DSM plan.
4.1 OBJECTIVES The objectives of this document are as follows: - To ensure consistency in the overall Demand Side Management (DSM) planning and evaluation process in Nova Scotia; - To consolidate important decisions made by the Nova Scotia...
AI summary This document outlines the objectives of ensuring consistency in Demand Side Management (DSM) planning and evaluation in Nova Scotia, consolidating key regulatory decisions, and balancing DSM Resource Plans' multiple objectives.
4.2.1 DSM BASELINE STUDY EfficiencyOne will commission a DSM baseline study in advance of each DSM Potential Study. The DSM Baseline Study will identify current stocks of electricity consuming devices in all market sectors.E1 will work wit...
AI summary EfficiencyOne will commission a DSM baseline study before each DSM Potential Study to identify current electricity-consuming devices across all market sectors and collaborate with NSIESO under the More Access to Energy Act for integrated resource planning.
4.2.2 DSM POTENTIAL STUDY EfficiencyOne will commission a DSM potential study in advance of each Integrated Resource Plan (IRP). The DSM Potential study will identify DSM resources that are achievable over the planning horizon, and will in...
AI summary EfficiencyOne will commission a DSM potential study prior to each Integrated Resource Plan (IRP). The study aims to identify achievable demand-side management (DSM) resources and inform the development of Candidate Resource Plans. The process is aligned with the More Access to Energy Act and involves collaboration with the NSIESO.
4.2.3 INTEGRATED RESOURCE PLAN Nova Scotia Power's IRP develops a long-term Preferred Resource Plan that establishes directional information for DSM that assists NS Power in meeting customer demand and energy requirements, and environmenta...
AI summary Nova Scotia Power's Integrated Resource Plan (IRP) outlines a long-term strategy for managing demand-side management (DSM) to meet customer demand and environmental obligations. The NSIESO is required to collaborate with the franchise holder to develop avoided cost calculations for DSM resources and file the results of IRP exercises with the Energy Board.
4.2.3.1 AVOIDED COSTS Nova Scotia Power will provide estimates of annual avoided costs of fuel on a per-MWh basis, and annual avoided costs of generation, transmission, and distribution on a per-kW basis to EfficiencyOne for use in the cos...
AI summary Nova Scotia Power will provide avoided cost estimates to EfficiencyOne for use in DSM planning processes. These estimates will be updated before each DSM Potential Study and when changes are needed. The NSIESO will take over responsibility for avoided cost calculations as part of the IRP process following the implementation of the More Access to Energy Act on April 1, 2025.
4.3.2 COST-EFFECTIVENESS TESTING EfficiencyOne will apply the UARB-approved cost-effectiveness test. E1 will apply the NSEB-approved cost-effectiveness test. Pursuant to Section 79H (2) of the Public Utilities Act, the NSEB, in evaluating...
AI summary EfficiencyOne will apply the UARB-approved cost-effectiveness test and also provide NSEB-approved results at the measure and program levels for informational purposes, as per Board direction.
Performance Targets consist of: 24 E1 will propose Performance Targets within each DSM Resource Plan. Proposed Performance Targets will be reflective of the DSM resources proposed for the upcoming Plan period (e.g., energy efficiency, dema...
AI summary E1 is required to propose Performance Targets within each DSM Resource Plan, reflecting the DSM resources proposed for the upcoming Plan period. Historically, these targets have included cumulative energy and peak demand savings, demand response capacity, and first-year energy savings for low-income and equity programs.
Performance Indicators consist of: 25 E1 will propose Performance Indicators within each DSM Resource Plan. These performance indicators will be specific to the DSM resources proposed within each future Plan (e.g. performance indicator met...
AI summary E1 will propose performance indicators within each DSM Resource Plan, focusing on energy efficiency, demand response, and other DSM resources. Historical performance indicators include energy savings, peak demand savings, ratepayer benefits, and customer satisfaction. These metrics are reported by program and rate class, with a focus on low-income and equity communities.
4.3.4 DSM PROGRAMS E1 will propose DSM programs within each DSM Resource Plan. Investments in DSM programs reduce energy consumption through technology replacements and behaviour change. DSM programs are offered to the Residential and the...
AI summary E1 will propose Demand Side Management (DSM) programs within each DSM Resource Plan. These programs aim to reduce energy consumption through technology replacements and behaviour change, targeting the Residential and Business, Not-for-Profit and Institutional (BNI) sectors.
Historically, DSM programs have included:as follows: - Residential Efficient Product Rebates - Residential Existing Residential - Residential New Residential - Residential Energy Savings Actions - Business, Not-for-Profit and Institutional...
AI summary Historically, DSM programs have included various initiatives targeting residential and commercial sectors, such as efficient product rebates, direct installation, and demand response programs, aimed at promoting energy efficiency and conservation.
NS Power Shareholder Charitable Contribution NS Power shareholders have indicated that they will provide up to $37 million dollars over ten years (2015-2024) to upgrade all electrically-heated homes owned by low-income Nova Scotians. In th...
AI summary NS Power shareholders are contributing up to $37 million over ten years to upgrade electrically-heated homes for low-income Nova Scotians. EfficiencyOne will avoid using DSM funds for these upgrades if they are already being covered by shareholder contributions.
4.4.1 TRACKING EfficiencyOne E1 will track the energy and capacity savings resulting from each program. Tracked results will be used in quarterly reports. 26 M07151, NSUARB Decision Letter, Nova Scotia Power Inc. – DSM Cost Allocation and...
AI summary EfficiencyOne E1 will track energy and capacity savings from each program, with results used in quarterly reports. A reference is made to a 2016 decision letter regarding DSM cost allocation and recovery.
4.4.2 EVALUATION EfficiencyOne E1 will retain the services of an independent DSM evaluation firm to conduct annual evaluations for each DSM program, as described in Sections 4.65.5 and 5.6.
AI summary EfficiencyOne E1 plans to retain an independent DSM evaluation firm to conduct annual evaluations for each DSM program, as outlined in Sections 4.65.5 and 5.6 of the document.
4.4.3 VERIFICATION The UARB's NSEB's savings verification consultant provides a verification review of the evaluated savings.
AI summary The UARB's NSEB's savings verification consultant conducts a verification review of the evaluated savings as part of the process.
4.5.14.6.1 ANNUAL PROGRESS REPORTS In the first quarter of the calendar year of each intervening year between multi-year filings, ENS E1 will file an Annual Progress Report (APR) with the UARBNSEB, which will include the following informat...
AI summary ENS E1 is required to submit an Annual Progress Report (APR) to the UARBNSEB every year between multi-year filings. The report must include a summary of prior year activities, milestones, and performance indicators, as well as a management discussion and analysis of discrepancies relative to the original plan.
4.5.44.6.4 IMPACT EVALUATION ENS E1 will file impact evaluations for each program annually, 31 produced by an independent third party DSM program evaluator.
AI summary ENS E1 is required to submit annual impact evaluations for each program, conducted by an independent third-party DSM program evaluator.
4.5.54.6.5 PROCESS EVALUATION ENS E1 will file process evaluations for individual programs, produced by an independent third party DSM program evaluator as necessary. 32 Examples of instances in which a program-level evaluation maywould oc...
AI summary ENS E1 will file process evaluations for individual programs when necessary, particularly for new or significantly changed program components, or those with large energy savings variances. These evaluations are conducted by an independent third-party DSM program evaluator.
4.64.7 DEMAND SIDE MANAGEMENT ADVISORY GROUP The DSM Advisory Group is a forum to provide strategic or directional advice and stakeholder perspectives on current or emerging DSM issues including, but not limited to, issues identified in UA...
AI summary The DSM Advisory Group serves as a forum to provide strategic and directional advice on demand side management issues, including those identified in UARB NSEB Orders related to DSM.
2. BACKGROUND On June 16, 2015, EfficiencyOne (E1), Nova Scotia Power Incorporated (NS Power), the Consumer Advocate, the Small Business Advocate, the Ecology Action Centre, the Affordable Energy Coalition, and the Industrial Group signed...
AI summary In 2015, EfficiencyOne, Nova Scotia Power, and various stakeholders signed a Consensus Agreement to establish a standardized filing framework for DSM applications. The NSUARB approved the agreement in 2015, and the framework was used in the 2016-2018 DSM Plan. The NSUARB encouraged updates to the framework in 2023, leading to a review and update by the DSMAG in 2024 and 2025.
Table 1: STANDARDIZED FILING FRAMEWORK ITEM DESCRIPTION ITEM DESCRIPTION - Cumulative energy and demand savings and investment (approved and actual) since 9 2012, and other additional approved and actual Performance Targets, as applicable.
AI summary The text presents a table item under the 'Standardized Filing Framework' that requests cumulative energy and demand savings and investment data since 2012, along with other performance targets. This relates to reporting on energy efficiency and demand-side management programs.
13 M10473, NSUARB Order, E1 2023-2025 DSM Plan, November 8, 2023, page 2, item 5. 14 Ibid., item 6.
AI summary The text references a document from the NSUARB Order related to the E1 2023-2025 DSM Plan, citing specific pages and items.
Table 2: PROGRAM DESCRIPTION TEMPLATE ITEM DESCRIPTION 1. OVERVIEW A brief description of the program intent, target market, and type of service or rebate. 2. OBJECTIVES Long-term objectives for the program. 3. OPPORTUNITY A summary of the...
AI summary This section provides a template for describing demand-side management (DSM) programs, including their objectives, market potential, implementation strategies, and performance indicators such as energy savings, demand response capacity, and cost-effectiveness. It also outlines specific considerations for low-income and equity performance.
4.1 OBJECTIVES The objectives of this document are as follows: - To ensure consistency in the overall Demand Side Management (DSM) planning and evaluation process in Nova Scotia; - To consolidate important decisions made by the Nova Scotia...
AI summary This document outlines the objectives of ensuring consistency in Demand Side Management (DSM) planning and evaluation in Nova Scotia, consolidating key decisions by the Nova Scotia Energy Board and the Nova Scotia Utility and Review Board, and ensuring DSM Resource Plans balance multiple objectives.
4.2.1 DSM BASELINE STUDY E1 will work with the Nova Scotia Independent Energy System Operator (NSIESO) in pursuit of the NSIESO's duties to carry out integrated resource planning exercises as outlined in the More Access to Energy Act. [16]...
AI summary E1 will collaborate with the NSIESO to conduct integrated resource planning as required by the More Access to Energy Act, potentially including the commission of a DSM baseline study prior to each DSM Potential Study.
4.2.2 DSM POTENTIAL STUDY E1 will work with the NSIESO in pursuit of the NSIESO's duties to carry out integrated resource planning (IRP) exercises as outlined in the More Access to Energy Act. [17](#page-62-3) This may include the commissi...
AI summary E1 will collaborate with the NSIESO to conduct a DSM Potential study as part of integrated resource planning under the More Access to Energy Act. This study will identify achievable DSM resources and inform Candidate Resource Plans for the IRP.
4.2.3 INTEGRATED RESOURCE PLAN Integrated resource planning establishes directional information for DSM planning. E1 will work with the NSIESO in the pursuit of their duties to carry out IRP exercises. [18](#page-63-0) As outlined in the M...
AI summary The Integrated Resource Plan (IRP) establishes a framework for demand-side management (DSM) planning. E1 will collaborate with the NSIESO to fulfill IRP duties under the More Access to Energy Act. The NSIESO must work with the franchise holder to develop avoided cost calculations and conduct cost-effective DSM, and file IRP results with the Energy Board.
4.2.3.1 AVOIDED COSTS As outlined in the More Access to Energy Act , the NSIESO will work with the DSM franchise holder to develop avoided cost calculations for demand-side management resources as part 18 Ibid. of its IRP exercises (see se...
AI summary The More Access to Energy Act mandates the NSIESO to develop avoided cost calculations for demand-side management resources as part of its IRP exercises, which will transition from NS Power to the NSIESO starting April 1, 2025.
4.3 DSM RESOURCE PLAN DEVELOPMENT Integrated resource planning establishes directional information for DSM that will inform the development of a preferred DSM Resource Plan by E1, including analysis of alternate scenarios of DSM activity,...
AI summary The Integrated Resource Plan (IRP) provides directional guidance for Demand Side Management (DSM) to support the development of a preferred DSM Resource Plan by EfficiencyOne (E1), including the analysis of alternate DSM scenarios in line with the Standardized Filing Framework.
4.3.1 BALANCED PLAN APPROACH E1 will produce DSM Resource Plans that balance multiple aspects of DSM for the benefit of customers, including: - Short-term and long-term energy and capacity avoidance; - Program delivery costs; - Avoided ene...
AI summary E1 will develop DSM Resource Plans that balance various aspects of demand-side management to benefit customers, including energy and capacity avoidance, program delivery costs, non-electric benefits, diversity of delivery, and rate impacts.
4.3.2 COST-EFFECTIVENESS TESTING E1 will apply the NSEB-approved cost-effectiveness test. Pursuant to Section 79H (2) of the Public Utilities Act , the NSEB, in evaluating a franchise holder's application, "shall evaluate the proposed cost...
AI summary E1 will apply the NSEB-approved cost-effectiveness test for demand-side management programs, as required by Section 79H (2) of the Public Utilities Act. The test is applied at the portfolio, measure, and program levels, with justification provided for measures that fall below the 1.0 threshold.
Performance Targets consist of:[22](#page-66-1) E1 will propose Performance Targets within each DSM Resource Plan. Proposed Performance Targets will be reflective of the DSM resources proposed for the upcoming Plan period (e.g., energy eff...
AI summary E1 is required to propose Performance Targets within each DSM Resource Plan, reflecting the DSM resources proposed for the upcoming Plan period. Historically, these targets have included cumulative energy and peak demand savings, demand response capacity, and first-year savings for low-income and equity programs.
Performance Indicators consist of:[23](#page-67-0) E1 will propose Performance Indicators within each DSM Resource Plan. These performance indicators will be specific to the DSM resources proposed within each future Plan (e.g. performance...
AI summary E1 will propose performance indicators within each DSM Resource Plan, focusing on metrics such as energy savings, demand response capacity, ratepayer benefits, and customer satisfaction. Historical performance indicators have included annual and cumulative energy and peak demand savings, as well as low-income program participation and expenditures.
4.3.4 DSM PROGRAMS E1 will propose DSM programs within each DSM Resource Plan. DSM programs are offered to the Residential and the Business, Not-for-Profit and Institutional (BNI) sectors. Historically, DSM programs have included:: - Resid...
AI summary E1 will propose DSM programs for residential and BNI sectors, including rebates, incentives, and demand response initiatives. These programs have historically included a variety of efficiency and energy-saving measures for both residential and business sectors.
4.3.5 ENABLING STRATEGIES E1 will propose Enabling Strategies and categories within each DSM Resource Plan. Historically, Enabling Strategies expenditures have included the following categories: - Education and Outreach - Development and R...
AI summary E1 will propose Enabling Strategies within each DSM Resource Plan. Historically, these strategies have included education, outreach, and research. Expenditures over $100,000 benefitting specific rate classes will have 75% of the investment allocated to those classes, while the remaining 25% is based on energy and demand requirements.
4.4.1 TRACKING E1 will track the energy and capacity savings resulting from each program. Tracked results will be used in quarterly reports.
AI summary E1 will track energy and capacity savings from each program, with the results used in quarterly reports to monitor program effectiveness.
4.4.2 EVALUATION E1 will retain the services of an independent DSM evaluation firm to conduct annual evaluations for each DSM program, as described in Section 4.6
AI summary E1 plans to retain an independent DSM evaluation firm to conduct annual evaluations for each DSM program, as outlined in Section 4.6 of the document.
4.4.3 VERIFICATION The NSEB's savings verification consultant provides a verification review of the evaluated savings.
AI summary The NSEB's savings verification consultant conducts a review of the evaluated savings as part of the verification process.
4.6.1 ANNUAL PROGRESS REPORTS In the first quarter of the calendar year, E1 will file an Annual Progress Report (APR) with the NSEB, which will include the following information:[26](#page-70-0) - A summary of the context, activities and m...
AI summary E1 is required to submit an Annual Progress Report (APR) to the NSEB, detailing prior year activities, performance indicators, and program costs and savings. The APR also serves as a means to notify the NSEB and stakeholders of any significant changes to the approved Plan, such as adding or terminating programs or altering budget targets.
4.6.2 QUARTERLY REPORTS E1 will file quarterly reports with the NSEB for quarters one through three of each year. The reports will provide quarterly status updates and service highlights, as well as communicate course adjustments within th...
AI summary E1 is required to submit quarterly reports to the NSEB, providing updates on the DSM Resource Plan and service highlights. The requirement is based on the DSM Settlement Agreement 2013-2015 DSM Plan.
4.6.4 IMPACT EVALUATION E1 will file impact evaluations for each program annually,[29](#page-71-0) produced by an independent third party DSM program evaluator.
AI summary E1 will submit annual impact evaluations for each program, conducted by an independent third-party DSM program evaluator.
4.6.5 PROCESS EVALUATION E1 will file process evaluations for individual programs, produced by an independent third party DSM program evaluator as necessary.[30](#page-71-1) Examples of instances in which a programlevel evaluation may occu...
AI summary E1 will submit process evaluations for individual programs conducted by an independent third-party DSM evaluator when necessary, such as for new program components, major changes, significant recommendations, or energy savings variances exceeding 25 percent.
4.7 DEMAND SIDE MANAGEMENT ADVISORY GROUP The DSM Advisory Group is a forum to provide strategic or directional advice and stakeholder perspectives on current or emerging DSM issues including, but not limited to, issues identified in NSEB...
AI summary The Demand Side Management Advisory Group serves as a forum for providing strategic advice and stakeholder perspectives on current and emerging DSM issues, including those outlined in NSEB Orders related to Demand Side Management.
EfficiencyOne 2027-2031 Demand Side Management Resource Plan Round 2 Model Input Assumptions and Results CIRCULATED: FEBRUARY 27, 2026
AI summary This document outlines the 2027-2031 Demand Side Management Resource Plan, including Round 2 Model Input Assumptions and Results, circulated on February 27, 2026.
1. INTRODUCTION The modelling phase for the 2027-2031 Resource Plan defines the Demand Side Management (DSM) resources and scenarios that EfficiencyOne (E1) explores through modelling in preparation for its Plan application filing with the...
AI summary The modelling phase for the 2027-2031 Resource Plan by EfficiencyOne (E1) has been completed, with this report detailing the results, key assumptions, and insights from the Round 2 modelling exercise in preparation for the Plan application filing with the Nova Scotia Energy Board (NSEB).
2. BACKGROUND AND OVERVIEW: ROUND 2 MODEL RESULTS E1 circulated its Round 1 model assumptions and results to the Demand-Side Management Advisory Group (DSMAG) on October 27, 2025. E1 received written comments from DSMAG members regarding t...
AI summary E1 updated its Round 2 model results for the DSM Plan, incorporating new avoided costs from NS Power and guidance from the NSEB. Strategic electrification was excluded due to its failure to reduce customer electricity costs. The Residential Behaviour program was removed, and the Residential DR program was modified based on feedback from the NSEB and DSMAG.
3.1 DESIGN CONSIDERATIONS In Round 1 comments from DSMAG members as well as in the 2026 DSM Extension proceeding, E1 heard that there was limited support for the three design objectives that E1 has been using to guide the development of re...
AI summary The document discusses feedback received from DSMAG members and the 2026 DSM Extension proceeding regarding the design objectives for recent DSM Plans. The feedback indicated limited support for the current 50/50 investment split, 40/60 energy savings split, and 15-20% low-income investment targets. In response, E1 has developed a new methodology for DSM resource scenario design.
Energy Efficiency Energy Efficiency (EE) continues to be a crucial resource for Nova Scotia's electricity system as demonstrated in integrated resource planning by reducing system load and peak, improving grid reliability and lowering elec...
AI summary Energy efficiency (EE) is a critical resource for Nova Scotia's electricity system, reducing load and peak demand, improving grid reliability, and lowering costs. Nova Scotia Power's 2022 IRP identified Base EE as the optimal level, resulting in significant energy savings and cost-effectiveness. E1 has modeled scenarios based on stakeholder input and third-party recommendations, including energy savings targets and sectoral allocations.
Demand Response Demand Response (DR) was introduced as an E1 program in the 2023-2025 DSM Plan and is a critical resource to support Nova Scotia's electricity system. E1 has heard and is responding to concerns from stakeholders regarding b...
AI summary Demand Response (DR) was introduced in the 2023-2025 DSM Plan and is a critical resource for Nova Scotia's electricity system. E1 addressed concerns about achievability and cost effectiveness in Round 2 DR modelling, leading to realistic performance targets for the 2027-2031 DSM Plan. The available capacity remains within optimal levels identified in Nova Scotia Power's 2022 IRP, and a cost-effectiveness target of 1.0 was applied for both Base and High scenarios.
Strategic Electrification The priority consideration for Strategic Electrification (SE) was to ensure alignment with the definition of strategic electrification as outlined in the Public Utilities Act , ("in a manner that reduces overall g...
AI summary The Strategic Electrification (SE) initiative must align with the Public Utilities Act , requiring reductions in both electricity costs and GHG emissions to be included in a DSM Plan. E1 is leveraging existing programs and partnerships, including input from the DSMAG, to model SE measures with a cautious approach to timelines and performance targets.
3.2 COST-EFFECTIVENESS TESTING E1 has provided Program Administrator Cost (PAC) test results for Round 2 modelling for all four of the DSM resources considered. Attachment 2 provides detail on the impact quantification used for Round 2 (Re...
AI summary E1 has submitted Program Administrator Cost (PAC) test results for Round 2 modelling of four DSM resources. Attachment 2 details the impact quantification used for Round 2, referenced in the 'CET Assumptions' tab.
3.3 MODELLING E1 shared its key model assumptions, cost effectiveness test (CET) assumptions, and low-income and equity assumptions in the Round 1 model results package circulated October 27, 2025. There have been no changes to E1's approa...
AI summary E1 updated its cost effectiveness test (CET) assumptions in Round 2 to align with the Board's decision in M12282, which required using the PAC test and NS Power's WACC as the discount rate. E1's key assumptions remain unchanged since Round 1, but ongoing refinement of model inputs is occurring, with finalization prior to the 2027-2031 DSM Plan Application.
Table 1: Energy Efficiency Insights - Scenario 1EE-Base and Scenario 2EE-High Scenario 1EE-Base Scenario 2EE-High EE Scenarios (2027-2031) RES BNI Total RES BNI Total Carbon Emissions Avoided Five-Year Annual Total (kilotonne) 20 51 71 26...
AI summary Table 1 presents energy efficiency insights comparing two scenarios, 1EE-Base and 2EE-High, focusing on carbon emissions avoided, energy and demand savings, investment distribution, and benefits. The 2EE-High scenario shows higher savings and a greater proportion of investment in low-income and equity programs.
4.1.1 SCENARIO 1EE: BASE The five-year total program and program component Round 2 modelling results are provided in [Table 2.](#page-82-0) Attachment 3 provides the measure level technical tables for Scenario 1EE-Base.
AI summary Scenario 1EE-Base outlines the five-year total program and program component modelling results from Round 2, with detailed technical tables provided in Attachment 3 for further analysis.
4.1.2 SCENARIO 2EE – HIGH The five-year total program and program component Round 2 modelling results are provided in [Table 3.](#page-83-0) Attachment 4 provides the measure level technical tables for Scenario 2EE-High.
AI summary This section presents the five-year total program and program component Round 2 modelling results for Scenario 2EE-High, with detailed measure-level technical tables provided in Attachment 4.
4.2 DEMAND RESPONSE ROUND 2 MODEL RESULTS [Table 4](#page-84-1) provides insights for the two DR scenarios modelled in Round 2.
AI summary The section discusses the results of the Demand Response Round 2 model, with Table 4 providing insights into the two DR scenarios modelled in this round.
Table 4: DR Scenarios - Round 2 Modelling Insights Round 2 Model - All DR Scenarios 2027-2031 Scenario 1DR-Base Scenario 2DR-High Capacity Impacts Capacity as a % of NSP Net System Peak (2031) 2,503 MW (2025 Load Forecast) 1.0% 1.4% Capaci...
AI summary Table 4 presents capacity impacts for two demand response (DR) scenarios (Scenario 1DR-Base and Scenario 2DR-High) from 2027 to 2031, showing percentages of capacity relative to various load forecasts and DR contributions.
Table 5: Scenario 1DR-Base – Round 2 Modelling Results PAC Lifetime Available Program Scenario 1DR-Base Investment Benefits Capacity1 Administrator (2027-2031) ($ million) ($ million) (MW) Cost (PAC) BNI Demand Response 18.8 40.5 25.5 2.4...
AI summary Table 5 presents the modelling results for Scenario 1DR-Base in Round 2, focusing on the BNI Demand Response and BNI Curtailment programs. It outlines investment, benefits, available capacity, and program administrator costs for the period 2027–2031.
The five-year total program component and pathways Round 2 modelling results for Scenario 2DR – High are provided in [Table 6.](#page-85-1) Round 2 Model Input Assumptions and Results
AI summary The document presents the five-year total program component and pathways Round 2 modelling results for Scenario 2DR – High, as outlined in Table 6. It includes input assumptions and results from the model.
Table 6: Scenario 2DR-High – Round 2 Modelling Results Scenario 1DR-High (2027-2031) Investment ($ million) PAC Lifetime Benefits ($ million) Available Capacity1 (MW) Program Administrator Cost (PAC) Residential Demand Response 10.3 7.2 3....
AI summary Table 6 presents the modelling results for Scenario 2DR-High in Round 2, showing investment amounts, program administrator costs, and available capacity for various demand response and efficiency programs, including Residential Demand Response, DLC Smart Thermostats, and BNI Demand Response.
Table 9: 1SE-Base Scenario - Round 2 Modelling Insights Scenario 1SE-Base RES BNI Total Carbon Emissions Avoided Five-Year Annual Total (kilotonne) 1 6 8 Cumulative Lifetime (kilotonne) 20 111 131 Energy & Demand Impacts Lifetime Net Energ...
AI summary Table 9 presents the 1SE-Base Scenario - Round 2 Modelling Insights, showing carbon emissions avoided, energy and demand impacts, investment splits, and benefits and costs associated with RES and BNI programs. Key metrics include carbon emissions, energy savings, investment distribution, and cost-benefit analysis.
Table 10: 1SE-Base – Round 2 Modelling Results Modified-PAC First Year Lifetime Scenario 1SE - Base (2027-2031) Investment ($ million) Lifetime PAC Benefits ($ million) Modified-PAC Lifetime Benefits ($ million) First Year Electric Energy...
AI summary Table 10 presents the Round 2 Modelling Results for the 1SE-Base scenario, highlighting investment amounts, energy savings, and Program Administrator Cost (PAC) metrics for various energy efficiency programs across residential and business sectors in Nova Scotia.
Table 13: Enabling Strategies –2027-2031 Category 2027-2031 Investment ($M) 2027-2031 Average Annual Investment ($M) Education and Outreach 8.5 1.7 Development and Research 7.3 1.5 Other Enabling Strategies 14.0 2.8 Market Transformation 8...
AI summary Table 13 outlines the investment in Enabling Strategies from 2027-2031, categorizing investments into Education and Outreach, Development and Research, Other Enabling Strategies, and Market Transformation, with a total investment of $38.5M over the period.
Table 15: 2027-2031 Enabling Strategies Categories and Activities Enabling Strategies Category Description of Activities Education and Outreach • Education and Outreach activities are designed to drive awareness of, and participation in, E...
AI summary Table 15 outlines enabling strategies for DSM (Demand-Side Management) from 2027 to 2031, including education and outreach, development and research, market transformation, and other enabling strategies. These activities aim to enhance participation in energy efficiency programs, adapt to market changes, and address barriers to adoption of energy-saving technologies.
9. UPDATE ON BOARD DIRECTIVES: 2027-2031 DSM PLAN E1 received several Board directives relating to the development of the 2027-2031 Plan and has provided an update on these items i[n Table 17,](#page-91-1) below. As always, E1 remains comm...
AI summary E1 has received several Board directives related to the development of the 2027-2031 DSM Plan and has provided an update on these items in Table 17. E1 is committed to complying with all Board directives.
Table 17: Update on Board Directives Relating to the 2027-2031 Plan Board Directives E1 Update Application for a new Benefit Cost Analysis (BCA) Test for evaluating DSM Plans (M12282)
AI summary The document references an application for a new Benefit Cost Analysis (BCA) Test for evaluating DSM Plans under matter number M12282, indicating a regulatory proceeding related to demand-side management evaluation.
Round 2 Model Input Assumptions and Results Board Directives E1 Update • E1 may include the energy savings related to its Residential Behaviour program and demand savings from its Residential Demand Response and BNI Demand Response program...
AI summary E1 is allowed to include energy savings from its Residential Behaviour, Residential Demand Response, and BNI Demand Response programs in its E1 Update but must address concerns in its five-year DSM Plan application. E1 has already addressed these concerns in its Round 2 modelled scenarios and will do so again in its 2027-2031 application.
10.1.1 MID-COURSE ADJUSTMENT PROCESS (MCA) [Some DSMAG members have] expressed concern that MCAs can lead to investment shifts between customer classes as compared to the DSM Plan as approved. The [DSMAG member] has specifically commented...
AI summary Some DSMAG members are concerned that mid-course adjustments (MCA) may lead to significant shifts in spending between customer classes compared to the approved DSM Plan. The IG has requested the Board to direct E1 to manage budgeted program spending within a reasonable range. E1 agrees that refinements to the MCA process are needed but believes the underlying principles remain valid and intends to collaborate with DSMAG to revise the process for the 2027-2031 DSM Plan.
Context for Discussion Mid-course adjustments give the DSM administrator flexibility to adjust program budgets and savings from those in the original approved Plan to respond to market conditions and program performance changes unknown at...
AI summary The document discusses mid-course adjustments in the DSM Plan, allowing E1 to modify program budgets and savings based on market conditions and performance changes. E1 has agreed to enhanced reporting and more stakeholder engagement. However, E1 maintains that the current process should remain, with proposed adjustments to address concerns around rate class spending and engagement.
10.1.2 MID-PLAN REVIEW PROCESS Stakeholders have expressed concerns about performance risk and the need for additional engagement following the 2022 amendment to the PUA which extended DSM Plans from a three-year to a five-year term. [Some...
AI summary Stakeholders are concerned about the performance risks associated with the five-year extension of DSM Plans following the 2022 amendment to the Public Utilities Act. Some DSMAG members propose a mid-plan review process, including stakeholder check-ins and one-on-one meetings, to ensure ongoing engagement and oversight during Plan implementation. E1 acknowledges these concerns and intends to collaborate with DSMAG members to define the mid-plan review process for the 2027-2031 DSM Plan.
10.2 PERFORMANCE TARGETS AND INDICATORS In each DSM Plan application, E1 proposes performance target metrics and indicators, to be considered and approved by the NSEB. Round 2 Model Input Assumptions and Results For the 2027-2031 DSM Plan,...
AI summary E1 proposes performance target metrics and indicators for the 2027-2031 DSM Plan, to be reviewed and approved by the NSEB. Metrics include energy savings, demand response capacity, and solar-PV generation. E1 invites comments from the DSMAG and anticipates consistency with past performance indicators, with adjustments for new DSM resources.
20 July 2016 1 TABLE OF CONTENTS 1. Objective 1 2. Background 1 3. Standardized Filing Framework 3 4. Demand Side Management Standards 16 LIST OF FIGURES Figure 1: Glossary of Terms 3 LIST OF TABLES Table 1: Standardized Filing Framework 6...
AI summary The document outlines the structure and content of a regulatory proceeding, including sections on objectives, background, and standardized filing frameworks, as well as demand-side management standards.
Figure 1: Glossary of Terms Term Definition Cumulative net demand savings The cumulative total (or sum) of the incremental net demand savings for the specific Plan period (i.e., total savings achieved across the multiple years of the Plan...
AI summary This glossary defines key terms related to demand response and energy savings. It explains cumulative net demand and energy savings, including the impact of free-ridership and spillover effects, and defines demand response and available capacity in the context of Nova Scotia Power's operations.
12 E1 submitted its first DSM Plan in 2012 as DSM Administrator. ITEM DESCRIPTION - the affordability of the proposed DSM Resource Plan; and - cost-efficiency opportunities; and - key global assumptions. 3. ALTERNATE SCENARIOS TO THE PROPO...
AI summary E1 submitted its first DSM Plan in 2012 as DSM Administrator. The document discusses alternate scenarios to the proposed DSM Plan, including cost-efficiency opportunities and key global assumptions. EfficiencyOne is required to provide alternate scenarios of DSM budgets, with NSPI providing rate impact analysis. The proposed DSM Resource Plan includes cost-effectiveness testing metrics.
Appendix 1 ITEM DESCRIPTION 4.2 Program-Level Savings and Investment A summary of program-level savings and investment for the upcoming period by individual Plan year and in total for the Plan period (e.g., annual and cumulative). Referenc...
AI summary This section outlines the requirements for reporting program-level savings and investment, including metrics like energy savings, demand response capacity, and cost-effectiveness testing. It also references program descriptions and enabling strategies for the upcoming period.
Appendix 1 ITEM DESCRIPTION Incremental net Energy Savings (First-year); - Incremental net Demand Savings (First-year); - Incremental net Energy Savings (Lifetime); - Demand Response Available Capacity; - Incremental net savings from other...
AI summary The document outlines the metrics and analysis required for the DSM Plan, including energy and demand savings, cost-effectiveness testing using the Program Administrator Cost (PAC) test, and the use of NS Power's Weighted Average Cost of Capital (WACC) as a discount rate. The Board also directed the use of a modified PAC to assess strategic electrification, which must reduce both GHG emissions and electricity costs.
19 M10830, NSUARB Letter, E1 2022 RBIA, February 24, 2023, page 5. 20 M06733, NSUARB Order, E1 2016-2018 DSM Plan, October 7, 2015, page 2, item 12. E1 will "provide one or more alternate scenarios of DSM budgets for the Board to consider,...
AI summary The text references several regulatory documents and orders related to demand-side management (DSM) plans and rate impact analyses. It includes references to NSUARB orders and a letter regarding the 2022 RBIA and DSM plans, including the requirement for E1 to provide alternate scenarios and rate impact analysis.
Standardized Filing Framework 11 (2) Prior to, or as part of, conducting an integrated resource planning exercise and subsequent competitive procurements of energy resources, the [NS]IESO shall: - (a) work with the holder of the franchise...
AI summary The NSIESO is required to collaborate with franchise holders to develop avoided cost calculations for demand-side management resources under the Public Utilities Act and to file the results of its integrated resource planning (IRP) exercises with the Energy Board once completed.
Performance Targets relevant to the DSM resources may include: - i. Cumulative annual energy savings; - ii. Cumulative annual peak demand savings; - iii. Demand Response Available Capacity; and - iv. Cumulative energy savings applicable to...
AI summary The document outlines performance targets relevant to demand-side management (DSM) resources, including cumulative energy and peak demand savings, demand response capacity, and savings from low-income and equity programs. The Board may also propose or order additional targets.
Performance Indicators consist of: 36 E1 will propose Performance Indicators within each DSM Resource Plan for consideration and approval by the NSEB. These performance indicators will be specific to the DSM resources proposed within each...
AI summary E1 will propose performance indicators for each DSM Resource Plan for approval by the NSEB. These indicators will be tailored to specific DSM resources such as energy efficiency, demand response, and solar-PV.
Performance Indicators may include: - i. Annual incremental energy savings (reported by program and rate class); - ii. Cumulative annual energy savings (reported by program and rate class); - iii. Annual lifetime energy savings (reported b...
AI summary The text outlines a list of performance indicators that may be included in regulatory proceedings, focusing on energy savings, demand response, customer satisfaction, and cost-effectiveness testing. These metrics are reported by program and rate class, and include both annual and cumulative data, as well as considerations for low-income communities and equity impacts.
DSM programs may include:as follows: - Residential Efficient Product Rebates - Residential Existing Residential - Residential New Residential - Residential Energy Savings Actions - Business, Not-for-Profit and Institutional Efficient Produ...
AI summary The text outlines various Demand Side Management (DSM) programs that may be included, such as residential and business rebate programs, direct installation initiatives, and demand response programs, along with the possibility of adding other proposed DSM programs.
2. BACKGROUND On June 16, 2015, EfficiencyOne (E1), Nova Scotia Power Incorporated (NS Power), the Consumer Advocate, the Small Business Advocate, the Ecology Action Centre, the Affordable Energy Coalition, and the Industrial Group signed...
AI summary In 2015, EfficiencyOne and other stakeholders signed a Consensus Agreement to establish a Standardized Filing Framework for DSM applications. The NSUARB approved the agreement, and the Framework was used in future DSM Plan applications. The NSUARB and its successor, the NSEB, have directed ongoing review and updates to the Framework through the DSMAG, including considerations for E1's 'balanced plan' and impact assessments.
Figure 1: Glossary of Terms Term Definition Cumulative net demand savings The cumulative total (or sum) of the incremental net demand savings for the specific Plan period (i.e., total savings achieved across the multiple years of the Plan...
AI summary The glossary defines key terms related to energy efficiency and demand response, including cumulative net demand and energy savings, and available capacity from demand response programs. These definitions account for factors like free-ridership and spillover effects.
16 M12282, Nova Scotia Energy Board Order, December 10, 2025. In the Board's Decision on the Benefit-Cost-Analysis Test (BCA), E1 was directed to use the Program Administrator Cost (PAC) test for screening the cost effectiveness of its pro...
AI summary The Nova Scotia Energy Board Order M12282 from December 10, 2025, directed E1 to use the Program Administrator Cost (PAC) test for evaluating the cost effectiveness of its proposed DSM Plan and to apply NS Power's Weighted Average Cost of Capital.
17 Supra note 1. 18 M10830, NSUARB Letter, E1 2022 RBIA, February 24, 2023, page 5. 19 M06733, NSUARB Order, E1 2016-2018 DSM Plan, October 7, 2015, page 2, item 12. E1 will "provide one or more alternate scenarios of DSM budgets for the B...
AI summary The text references a letter from the NSUARB dated February 24, 2023, and an order from October 7, 2015, both related to DSM plans and rate impact analyses. These documents outline the requirement for E1 to provide alternate DSM budget scenarios and for NS Power to conduct rate impact analysis.
Table 2: PROGRAM DESCRIPTION TEMPLATE ITEM DESCRIPTION 6.2 Payback Period & Considerations As per the NSUARB's 2023-2025 DSM Plan Order, E1 is directed "to include payback information in its measure level tables in future applications for...
AI summary The text outlines a program description template for a regulatory proceeding, focusing on payback period considerations, justifications for measure inclusion, and other items related to the 2023-2025 DSM Plan Order issued by the NSUARB. It emphasizes the need for detailed information and justification in future resource plan applications.
4.1 OBJECTIVES The objectives of this document are as follows: - To ensure consistency in the overall Demand Side Management (DSM) planning and evaluation process in Nova Scotia; - To consolidate important decisions made by the Nova Scotia...
AI summary This document outlines the objectives of ensuring consistency in Demand Side Management (DSM) planning and evaluation in Nova Scotia, consolidating key decisions by the Nova Scotia Energy Board (NSEB) and its predecessor, and ensuring DSM Resource Plans balance multiple objectives.
4.2.1 DSM BASELINE STUDY E1 will work with the Nova Scotia Independent Energy System Operator (NSIESO) in pursuit of the NSIESO's duties to carry out integrated resource planning exercises as outlined in the More Access to Energy Act. [23]...
AI summary E1 will collaborate with the Nova Scotia Independent Energy System Operator (NSIESO) to conduct a DSM baseline study as part of integrated resource planning under the More Access to Energy Act. The study will identify current electricity-consuming devices across all market sectors.
4.2.2 DSM POTENTIAL STUDY E1 will work with the NSIESO in pursuit of the NSIESO's duties to carry out integrated resource planning (IRP) exercises as outlined in the More Access to Energy Act. [24](#page-145-3) This may include the commiss...
AI summary E1 will collaborate with the NSIESO to conduct a DSM Potential study as part of integrated resource planning exercises required under the More Access to Energy Act. This study will identify achievable DSM resources and inform Candidate Resource Plans for the IRP.
4.2.3 INTEGRATED RESOURCE PLAN Integrated resource planning establishes directional information for DSM planning. The Preferred Resource Plan identified in the IRP will inform the development of a preferred DSM Resource Plan by E1, includi...
AI summary The Integrated Resource Plan (IRP) establishes directional information for Demand Side Management (DSM) planning. E1 will develop a preferred DSM Resource Plan in collaboration with the NSIESO, in accordance with the Standardized Filing Framework and the More Access to Energy Act . The NSIESO is required to file the results of its IRP exercises with the Energy Board.
4.2.3.1 AVOIDED COSTS As outlined in the More Access to Energy Act , the NSIESO will work with the DSM franchise holder to develop avoided cost calculations for demand-side management resources as part of its IRP exercises (see section 4.2...
AI summary The More Access to Energy Act requires the NSIESO to collaborate with the DSM franchise holder to calculate avoided costs for demand-side management resources as part of IRP exercises. These calculations will be provided to E1 for use in the cost-effectiveness screening of DSM measures and programs during planning processes.
4.3.1 BALANCED PLAN APPROACH E1 will produce DSM Resource Plans that balance multiple aspects of DSM for the benefit of customers, including: - Short-term and long-term energy and capacity avoidance; - Program delivery costs; - Avoided ene...
AI summary E1 will develop DSM Resource Plans that balance various aspects of demand-side management to benefit customers, including energy and capacity avoidance, program delivery costs, non-electric benefits, and ensuring access across all market sectors.
4.3.2 COST-EFFECTIVENESS TESTING E1 will apply the NSEB-approved cost-effectiveness test. Pursuant to Section 79H (2) of the Public Utilities Act , the NSEB, in evaluating a franchise holder's application, "shall evaluate the proposed cost...
AI summary E1 is required to apply the NSEB-approved cost-effectiveness test for its DSM plan, using the PAC test and NS Power's WACC as the discount rate. The Board also directed the use of a modified PAC for assessing strategic electrification, which must reduce both GHG emissions and electricity costs. E1 will provide cost-effectiveness results at multiple levels, including individual measures that fail testing.
4.3.3.1 DEFINITIONS To provide clarity, the following definitions are used[:31](#page-148-4) Performance Metric: A quantifiable measure that is used to track and assess the status of a specific achievement. Performance Indicators: A set of...
AI summary The document defines key terms related to performance metrics, indicators, targets, and thresholds in the context of regulatory proceedings. It references NSEB orders and applications, including E1's 2023-2025 DSM Plan and a 2016 supply agreement application.
Performance Indicators consist of:[34](#page-150-0) E1 will propose Performance Indicators within each DSM Resource Plan for consideration and approval by the NSEB. These performance indicators will be specific to the DSM resources propose...
AI summary E1 will propose performance indicators for each DSM Resource Plan for NSEB approval. These indicators include energy savings, demand response capacity, customer satisfaction, and cost-effectiveness testing, with a focus on equity and low-income communities.
4.3.4 DSM PROGRAMS E1 will propose DSM programs within each DSM Resource Plan. DSM programs are offered to the Residential and the Business, Not-for-Profit and Institutional (BNI) sectors. DSM programs may include:: - Residential Efficient...
AI summary E1 will propose DSM programs for residential and BNI sectors, including rebates, custom incentives, direct installation, and demand response initiatives as part of the DSM Resource Plan.
Other Low Income and Equity Programming In accordance with Section 4.3.1, the Balanced Plan Approach, E1 will design and deliver programs and services that benefit low-income and equity customers. 35 M12249, NSEB Order, 2026 DSM Extension,...
AI summary E1 is required to design and deliver programs benefiting low-income and equity customers under the Balanced Plan Approach. It must include Program Administrator Cost (PAC) test results for 2023-2025 in its 2025 Annual Progress Report and report future results annually.
4.4.1 TRACKING E1 will track the energy and capacity savings resulting from each program. Tracked results will be used in quarterly reports.
AI summary E1 will track energy and capacity savings from each program, with results reported quarterly.
4.4.2 EVALUATION E1 will retain the services of an independent DSM evaluation firm to conduct annual evaluations for each DSM program, as described in Section 4.6 36 M07151, NSUARB Decision Letter, Nova Scotia Power Inc. – DSM Cost Allocat...
AI summary E1 will hire an independent DSM evaluation firm to perform annual evaluations for each DSM program, as outlined in Section 4.6. A reference is made to a 2016 decision letter by the NSUARB regarding Nova Scotia Power Inc.'s DSM cost allocation and recovery.
4.4.3 VERIFICATION The NSEB's savings verification consultant provides a verification review of the evaluated savings.
AI summary The NSEB's savings verification consultant is responsible for conducting a verification review of the evaluated savings within the proceeding.
4.6 REPORTING REQUIREMENTS E1 proposes its DSM reporting within each DSM Resource Plan. This includes the following DSM reporting:
AI summary E1 proposes to include its Demand Side Management (DSM) reporting within each DSM Resource Plan, outlining the specific reporting requirements.
4.6.1 ANNUAL PROGRESS REPORTS In the first quarter of the calendar year, E1 will file an Annual Progress Report (APR) with the NSEB, which will include the following information:[38](#page-153-1) - A summary of the context, activities and...
AI summary E1 is required to file an Annual Progress Report (APR) with the NSEB, including program performance, expenditures, and forecast information. Quarterly reports will also be filed, providing updates on savings targets, variances, and program activities. Significant changes to the DSM Plan must be reported in advance.
4.6.4 IMPACT EVALUATION E1 will file impact evaluations for each program annually,[41](#page-155-0) produced by an independent third party DSM program evaluator.
AI summary E1 will file annual impact evaluations for each program, produced by an independent third-party DSM program evaluator.
4.6.5 PROCESS EVALUATION E1 will file process evaluations for individual programs, produced by an independent third party DSM program evaluator as necessary.[42](#page-155-1) Examples of instances in which a programlevel evaluation may occ...
AI summary E1 will file process evaluations for individual programs, produced by an independent third party DSM program evaluator as necessary. Evaluations may be required for new program components, those with major changes, or those with significant variances in energy savings.
4.7 DEMAND SIDE MANAGEMENT ADVISORY GROUP The DSM Advisory Group is a forum to provide strategic or directional advice and stakeholder perspectives on current or emerging DSM issues including, but not limited to, issues identified in NSEB...
AI summary The Demand Side Management Advisory Group (DSMAG) serves as a forum for providing strategic advice and stakeholder perspectives on DSM issues, including those outlined in NSEB Orders. The text references a letter from the NSUARB and an RBIA prepared by EfficiencyOne.
2. BACKGROUND On June 16, 2015, EfficiencyOne (E1), Nova Scotia Power Incorporated (NS Power), the Consumer Advocate, the Small Business Advocate, the Ecology Action Centre, the Affordable Energy Coalition, and the Industrial Group signed...
AI summary The document outlines the history and evolution of the Standardized Filing Framework for DSM applications in Nova Scotia, including its approval by the NSUARB and ongoing updates guided by the DSMAG. Key stakeholders include EfficiencyOne, NS Power, and various advocacy groups.
3.1 Glossary of Terms Term Definition Cumulative net demand Sum of incremental net demand savings across the Plan period; net of free savings ridership and spillover. Cumulative net energy Sum of incremental net energy savings across the P...
AI summary This section defines key terms related to demand-side management (DSM) and energy efficiency, including cumulative net demand and energy savings, DSM resource plans, demand response, and effective useful life of measures. These definitions support the evaluation and approval of DSM activities and budgets.
Program description content is described in Table 3. Table 3: Program Description Template Item Description 1. Overview Intent, target market, and type of service or rebate. 2. Objectives Long-term objectives for the program. 3. Opportunit...
AI summary The document outlines a program description template used in regulatory proceedings, focusing on demand side management standards, including program objectives, design, performance indicators, and equity considerations.
4.1 Objectives - Ensure consistency in the overall Demand Side Management (DSM) planning, evaluation, reporting in Nova Scotia; - Consolidate Board decisions and directives as they pertain to DSM; and - • Ensure that DSM Resource Plans bal...
AI summary The objectives outlined focus on ensuring consistency in Demand Side Management (DSM) planning, consolidating Board decisions related to DSM, and ensuring that DSM Resource Plans balance multiple objectives.
4.2.2 DSM Potential Study E1 will work with the NSIESO on IRP activities, [6](#page-163-1) including the commission of a DSM Potential study in advance of each IRP exercise. The DSM Potential study identifies DSM resources that are achieva...
AI summary E1 will collaborate with the NSIESO on IRP activities, including conducting a DSM Potential study prior to each IRP exercise. This study will identify achievable DSM resources and inform the development of Candidate Resource Plans for the IRP.
4.2.4 Avoided Costs NSIESO will work with the DSM franchise holder to develop avoided cost calculations for demandside management resources[.6](#page-163-1)
AI summary NSIESO will collaborate with the DSM franchise holder to develop avoided cost calculations for demand-side management resources.
4.3.3 Performance Metrics The following performance metrics and requirements were established under the 2016-2018 DSM Plan. [1](#page-159-2)
AI summary This section outlines the performance metrics and requirements established under the 2016-2018 DSM Plan, providing a framework for evaluating demand-side management initiatives during that period.
Performance Indicators E1 will propose DSM resource specific performance indicators within each DSM Resource Plan filing for consideration and approval by the Board. Performance indicators may include annual incremental and cumulative ener...
AI summary E1 proposes to include specific performance indicators in each DSM Resource Plan filing for Board approval. These indicators cover energy and peak demand savings, customer satisfaction, equity impacts, and cost-effectiveness, among others.
4.3.4 DSM Programs E1 will propose DSM programs for Residential and the Business, Not-for-Profit and Institutional (BNI) sectors which may include Residential Efficient Product Rebates, Existing Residential, New Residential, BNI Efficient...
AI summary E1 is proposing a range of DSM programs targeting residential and BNI sectors, including rebates, direct installation, and demand response initiatives.
4.3.5 Enabling Strategies E1 will propose Enabling Strategies such as Education and Outreach, Development and Research, Other Enabling Strategies; and additional categories as proposed. For activities requiring an annual investment of $100...
AI summary E1 will propose Enabling Strategies including Education and Outreach, Development and Research, and other categories. Investments over $100,000 benefiting specific rate classes will have 75% of the participant benefit portion allocated to those classes, while investments under $100,000 or benefiting all classes will be allocated based on per-rate class expenditures. The system benefit portion (25%) is allocated based on class energy and demand requirements.
4.4.1 Tracking E1 will track the energy and capacity savings by program and report results in quarterly reports.
AI summary E1 will track energy and capacity savings by program and report results in quarterly reports.
4.4.2 Evaluation E1 will retain the services of an independent DSM evaluation firm to conduct annual impact evaluations for each DSM program or process evaluations as needed.
AI summary E1 plans to retain an independent DSM evaluation firm to conduct annual impact evaluations for each DSM program or process evaluations as needed.
4.4.3 Verification The Board's savings verification consultant provides a verification review of the evaluated savings.
AI summary The Board's savings verification consultant conducts a verification review of the evaluated savings as part of the verification process.
4.6.1 Annual Progress Reports Reporting requirements were established under the 2013–2015 DSM Plan Settlement Agreement and continue to evolve.[9](#page-168-9) In the first quarter of the calendar year, E1 will file an Annual Progress Repo...
AI summary Annual Progress Reports (APR) must be filed by E1 in the first quarter of each year, including performance indicators, discrepancies, expenditures, savings, and forecast data, as established under the 2013–2015 DSM Plan Settlement Agreement.
4.6.2 Quarterly Reports E1 will file quarterly reports with the Board for quarters one through three of each year. Reporting requirements were established under the 2013–2015 DSM Plan Settlement Agreement and continue to evolve: [9](#page-...
AI summary E1 is required to file quarterly reports with the Board, covering updates on the DSM Resource Plan, variances in savings and investment, incentive levels, and other program-related information, as established under the 2013–2015 DSM Plan Settlement Agreement.
4.6.4 Evaluation E1 will file annual impact evaluations for each program prepared by an independent third party DSM program evaluator. E1 will file process evaluations for individual programs, produced by an independent third party DSM pro...
AI summary E1 is required to submit annual impact evaluations and process evaluations for individual programs, prepared by independent third-party DSM program evaluators, particularly when there are significant changes or variances.
4.7 Demand Side Management Advisory Group The DSM Advisory Group provides strategic or directional advice and stakeholder perspectives on current or emerging DSM issues including Board Orders pertaining to Demand Side Management.
AI summary The Demand Side Management Advisory Group offers strategic advice and stakeholder perspectives on current and emerging DSM issues, including relevant Board Orders.
, Schedule B: More Access to Energy Act . Establishes NSIESO, including IRP and avoided‑cost duties (in force April 1, 2025). - 7. M07151 – Nova Scotia Power, DSM Cost Allocation and Recovery, NSUARB Decision Letter, (April 11, 2016), at p...
AI summary The text outlines regulatory references related to the More Access to Energy Act, DSM cost allocation, and the Public Utilities Act. It also includes a request for detailed cost-effectiveness analysis of E1's DSM Plans using specific metrics and scenarios.
18 Table 1: 2023-2026 DSM Plan Energy Savings, Demand Savings and Available Capacity Compared to 2022 19 Evergreen Integrated Resource Plan (IRP) Plan as Approved 2022 Evergreen IRP Reference Plan Variance Between Plan as Approved and 2022...
AI summary The table compares the 2023-2026 DSM Plan energy and demand savings with the 2022 Evergreen IRP Reference Plan, showing variances in energy savings, peak demand savings, and available capacity across the years.
3 Table 2: 2027-2031 Preferred DSM Plan Energy Savings, Demand Savings and Available Capacity Compared 4 to 2022 Evergreen Integrated Resource Plan (IRP) Plan as Proposed 2022 Evergreen IRP Reference Plan IRP Reference Plan Year Energy Sav...
AI summary Table 2 compares the 2027-2031 Preferred DSM Plan's energy savings, demand savings, and available capacity with the 2022 Evergreen Integrated Resource Plan (IRP). The data shows a decrease in energy and demand savings compared to the 2022 plan, with solar-PV installed capacity remaining low in the proposed plan.
The IRP Reference Scenario that avoided costs of DSM were developed from (CE1-E1-R2) has 203 MW of solar by 2031. The high DER IRP scenario (included higher levels of customer sited solar) which had favorable Revenue Requirement results wh...
AI summary The document discusses the Integrated Resource Plan (IRP) and the 2027–2031 DSM Plan, noting that the DSM Plan is consistent with the IRP despite achieving a significant portion of its energy savings. The IRP includes a reference scenario with 203 MW of solar by 2031 and a high DER scenario with favorable revenue results when customer costs are excluded.
he DSM Plan reflects a near-term implementation decision. The Plan explicitly uses the IRP as a benchmark and includes modelling of an IRP-aligned scenario, confirming those savings are achievable and cost-effective. However, the Preferred...
AI summary The DSM Plan prioritizes short-term affordability over long-term system optimization, acknowledging deferral risks but finding a balance. It identifies a 39 MW peak demand gap and a 15 MW demand response shortfall by 2031, which may require future DSM programming, demand response expansion, and alternative supply-side resources.
M Planning? (c) Does E1 anticipate updating the avoided costs in its 2027-2031 DSM Plan as a result of the updated avoided costs from NSIESO? If so, when would E1 make these updates? Response IR-11: (a) The development of Integrated Resour...
AI summary EfficiencyOne (E1) states that the development of Integrated Resource Plans (IRP) is now managed by the Nova Scotia Independent Energy System Operator (NSIESO). E1 anticipates that updated avoided costs for energy and capacity will be developed after the completion of the NSIESO's 2026 IRP, with finalization expected in 2027.
al of modifications to the approved DSM Plan. [2026-IRP-Draft-Terms-of-Reference.pdf](https://ieso-ns.ca/wp-content/uploads/2026/03/2026-IRP-Draft-Terms-of-Reference.pdf) Request IR-12: Page 17 of the Evidence states, "Fourth, with respect...
AI summary EfficiencyOne (E1) is requested to provide a BCA ratio for the 2027–2031 DSM Plan using the NS Test with the WACC from the PAC BCA and a societal discount rate of 2%. E1 acknowledges the request and notes that they have used modelling software to perform multiple cost-effectiveness tests, including the NS Test, TRC, RIM, PAC, and others.
odelling software capable of performing multiple cost-effectiveness tests, including the proposed NS Test as well as the Total Resource Cost (TRC) test, the Rate Impact Measure (RIM), the PAC and the modified-PAC. This functionality was us...
AI summary The document discusses the use of various cost-effectiveness tests for the 2027–2031 DSM Plan, including the PAC test, which was confirmed as the primary method by the Nova Scotia Energy Board's Decision (M12282). E1 provided multiple test results, but full results under the proposed NS Test and TRC were not produced due to the use of the PAC test.
R-12 Page 2 of 2 M12282, NSEB Decision, E1's Application for approval of a New Benefit-Cost Analysis Test for Evaluating Demand Side Management Plans, December 10, 2025. Request IR-13: Page 17 of the Evidence states, "E1 further notes that...
AI summary E1 has not received long-run marginal emissions rates from NS Power despite requests in 2025 and 2026, but expects the information to be developed by NSIESO. E1 does not anticipate updating the 2027–2031 DSM Plan even after receiving this information, as the current plan was developed using the best available data from NS Power's IRP and revisions may impose a regulatory burden.
(IRP) consistent with the approved 2023–2026 DSM Plan, revisions would not be warranted and may impose a disproportionate regulatory burden at this stage. Please refer to E1's response to NSEB IR-05. Request IR-14: Pages 18-19 of the Evide...
AI summary The response discusses E1's ongoing collaboration with NS Power on locational demand response and program stacking, with no anticipated resolution date but continuation into the 2027–2031 DSM Plan period. Updates to the DSM Plan are referenced in another response.
common understanding is reached in 2026, E1 expects collaboration and efforts will continue into the 2027–2031 DSM Plan period. (b) Please refer to E1's response to Synapse IR-72. Request IR-15: Page 25 of the Evidence states, "The Preferr...
AI summary E1 references a jurisdictional scan conducted by APEX to determine appropriate energy savings targets and sector allocations for the DSM Plan, aligning with 0.8–1.0% of load and a 30/70 split between residential and BNI sectors, as well as 11% low-income and equity programs within residential savings.
(c) Please compare the systems for the utilities identified in (b) with Nova Scotia's in terms of climate (including heating degree days and system peak) and DSM program mix. 1 (d) Given the mentioned affordability challenges, is there any...
AI summary The response discusses lower-than-expected enrollment in EV and battery pathways, attributing it to a smaller addressable market and customer behavior. It also references future census data to assess low-income trends in Nova Scotia.
eligible behind-the-meter battery systems, which remain low-penetration and high-cost so there are less devices bearing the cost of the battery pathway. EfficiencyOne's (E1) EV and battery incentive structures are shown in the 2025 DSM Eva...
AI summary The text discusses challenges with EfficiencyOne's (E1) EV and battery pathways in the Eco Shift program, including low enrollment, high costs, and compatibility issues. E1 plans to remove these pathways pending approval, citing cost-effectiveness and operational complexity. Peer jurisdictions and lessons learned are requested regarding residential demand response and grid management strategies.
Response IR-17: (a) The peer jurisdictions referenced in EfficiencyOne's (E1) Evidence are Ontario / IESO Peak Perks, Massachusetts / National Grid and Eversource Wi-Fi thermostat programs, and California / PG&E Smart Thermostat Control Pi...
AI summary EfficiencyOne references peer jurisdictions like Ontario, Massachusetts, and California to show that residential demand response programs improve in cost-effectiveness as they mature. The 2025 Evaluation also highlights variations in program design and operational practices across jurisdictions.
Eco Shift (Residential Demand Response) Date Duration (hours) Hour 1 (MW) Hour 2 (MW) Hour 3 (MW) Hour 4 (MW) Dec. 04 2024 17:00-21:00 4 0.063 0.587 0.053 0.039 Dec. 20 2024 07:00-11:00 4 0.239 0.175 0.144 0.091 Dec. 23 2024 17:00-21:00 4...
AI summary The document presents data from the Eco Shift (Residential Demand Response) program and Smart Synergy (BNI Demand Response) program, showing demand response performance across various dates and times. These tables highlight the participation and curtailment levels during specific periods, indicating the effectiveness of demand response initiatives in managing energy consumption.
Response IR-19: (a) EfficiencyOne (E1) included $165,975 over the five-year 2027–2031 DSM Plan application for innovation activities focused specifically on strategic electrification (Table 1, PDF p. 221). At this stage, the innovation inv...
AI summary EfficiencyOne (E1) has allocated $165,975 over the 2027–2031 DSM Plan for innovation activities focused on strategic electrification. The investment is intended to support research into market and technological barriers and will be used for expert consultation and planning. The initiative is subject to approval by the Nova Scotia Energy Board (NSEB).
1 • combination of heat Energy Storage Solutions and Electric Space Heating 2 pumps and battery energy storage or electric thermal storage solutions. 3 • Hybrid Heating Load Management automation and direct-load control of 4 hybrid heating...
AI summary The text discusses E1's approach to the 2027–2031 DSM Plan, including hybrid heating load management, collaboration with NSIESO, and exclusion of Strategic Electrification due to legislative requirements not being met. E1 notes uncertainty about future results and confirms that past measures did not achieve both GHG emission and electricity cost reductions.
The forward-looking information is based on reasonable assumptions and is subject to risks, uncertainties and other factors that could cause actual results to differ materially from historical results or results anticipated by the forward-...
AI summary The forward-looking information includes various risks and uncertainties that could affect outcomes, such as regulatory changes, economic conditions, commodity prices, and technological developments. These factors may significantly impact actual results compared to historical or anticipated performance.
NSPI's electric revenues are affected by rates approved by the NSEB and electric sales volumes. NSPI's electric revenues include revenues related to the recovery of fuel costs and non-fuel costs. The FAM allows NSPI to recover all prudentl...
AI summary NSPI's electric revenues depend on approved rates by the NSEB and sales volumes, influenced by factors like weather, customer numbers, and DSM activities. Fuel costs are recovered through the FAM, which does not significantly affect net income. Customer types include residential, commercial, industrial, and other categories.
Q2 2025 compared to Q2 2024 Q2 2025 net income decreased by $12 million compared to Q2 2024. The decrease is due to higher OM&G expenses, and higher depreciation and amortization due to increased PP&E in service. OM&G expenses increased du...
AI summary Q2 2025 net income decreased by $12 million compared to Q2 2024 due to higher OM&G expenses and depreciation and amortization. The request IR-21 asks for detailed data on lighting measures in the Instant Savings and Efficiency Product Installation program components, including number of measures, investment, energy savings, costs, and benefits, categorized by measure type and plan year.
1 (d) Please see below for a list of key dates in the transition of the Residential lighting market. 2 EfficiencyOne (E1) discontinued all residential lighting support in 2025. E1 is unaware of 3 any associated building code implications....
AI summary The phase out of residential lighting measures by EfficiencyOne (E1) in 2025 has affected program components, particularly the Instant Savings program. Key dates include January 1, 2019, and January 1, 2025, which marked changes in evaluation baselines and the removal of LED lighting products from the program. This has reduced the effective useful life of products and diminished lifetime savings.
f energy savings as a percentage of load at 0.8 percent and the recommendation of the energy savings split between residential and business programs. (b) Please refer to part (a) of this IR response. Request IR-23: Page 48 of the Evidence...
AI summary The text discusses EfficiencyOne's (E1) cost management strategies, including competitive procurement practices and multi-year procurement arrangements used in its 2027-2031 DSM Plan to achieve best value and reduce transaction costs. It also requests detailed information on contracts up for competitive procurement and existing and new multi-year procurement arrangements.
Table 1: E1's Programs Delivered by Third Parties Affordable Multifamily Housing ✔ Efficient Product Installation ✔ Home Energy Assessment ✔ HomeWarming ✔ Instant Savings ✔ Mi'kmaw Home Energy Efficiency Project ✔ Strategic Energy Manageme...
AI summary Table 1 lists E1's programs delivered by third parties, including energy efficiency and demand response initiatives. E1's procurement activities are governed by a biennially reviewed procurement policy approved by E1's Board of Directors.
(a) DSM Investment restated in 2027 Dollars using 2 Percent Inflation Rate - Millions of Dollars 2027 2028 2029 2030 2031 DSM Plan $ 63.75 $ 63.75 $ 63.75 $ 63.75 $ 63.75 2027 Dollars $ 63.75 $ 62.50 $ 61.27 $ 60.07 $ 58.90 DSM Benefits Re...
AI summary The text presents a table showing the restated costs and benefits of the DSM Plan in 2027 dollars using a 2% inflation rate across the years 2027 to 2031. The values remain consistent for investment costs, while benefits decrease over time.
Aligns costs with multi-year benefits Upfront DR costs (e.g., program development, technology enablement, enrollment incentives) are incurred in a single year, but the benefits they enable accrue over future years. Levelizing these costs a...
AI summary Upfront Demand Response (DR) costs are incurred in one year, but their benefits are realized over multiple years. Levelizing these costs spreads them over the period of benefit realization, preventing a mismatch that could bias results.
Reflects program duration A ten-year horizon aligns with the typical assumed life of DR programs, during which ongoing system benefits are expected to be delivered, and reflects commonly observed program contract periods with third-party D...
AI summary A ten-year horizon for demand response programs aligns with their typical life and expected system benefits, as well as common contract periods with third-party providers, supporting long-term planning and continuation of demand response initiatives.
Improves comparability and clarity of results For the 2023–2025 DSM Plan and 2026 DSM Extension, Guidehouse applied a 10-year cost effectiveness framework to reflect the full expected duration of DR programs and capture all associated cost...
AI summary Guidehouse applied a 10-year cost effectiveness framework for the 2023–2025 DSM Plan and 2026 DSM Extension, but this approach introduced challenges such as reliance on long-term assumptions and post-modeling adjustments. Levelizing upfront costs over ten years improves comparability and clarity of benefit-cost ratios for DR programs within the PAC test.
1 Request IR-25: 2 3 Pages 63-64 of the Evidence state, "E1 is also proposing further enhancements including: 4 Reducing the threshold from 25 percent to 20 percent for program changes both spending and 5 savings that require explanations....
AI summary The text discusses a request (IR-25) related to EfficiencyOne's proposed changes to program-level budget and savings thresholds, asking for clarification and detailed explanations. The response refers to other parts of the document and an attachment for further information.
Request IR-28: - Please refer to page 9 of Appendix A – Preferred Plan, where E1 describes the "program design - and delivery changes [implemented] ahead of the 2026 season" including "ensuring installed - devices were event-ready" and "en...
AI summary The response to Request IR-28 provides data on the share of residential demand response devices deemed 'event-ready' in the 2025 and 2026 seasons, referencing an evaluation and internal tracking data. It also mentions the efficacy of providing BNI customers with 48 hours of advance notice for events, though it does not explicitly state whether this practice will continue in 2027.
Table 1: 2025 and 2026 Event-Ready Devices Year Smart Thermostats Domestic Hot Water Controllers (DHWC) Electric Vehicle (EV) Telematics Batteries 2025 10,200 1,002 191 12 2026 22,244 4,038 453 48 M12780, Exhibit 3, E1 2025 DSM Programs Ev...
AI summary The document presents data on event-ready devices for 2025 and 2026, including smart thermostats, domestic hot water controllers, EV telematics, and batteries. It also discusses EfficiencyOne's (E1) efforts to provide additional advance notice to BNI DR customers to improve participation during events.
on system needs and direction from NS Power. Request IR-29: Please refer to the statement on page 9 of Appendix A – Preferred Plan which states: "Throughout 2023–2025, several pathways modelled in the 2023–2026 DSM Plan were not pursued, i...
AI summary The response to Request IR-29 explains that EfficiencyOne (E1) did not pursue certain demand response pathways during the 2023–2026 period because they prioritized those with the highest available capacity potential, such as direct load control and battery control, and focused first on rolling out the newly introduced behavioural program component in the Residential Demand Response program.
ural program component (Residential Behaviour) in E1's energy efficiency programming was only being introduced in the 2023–2025 DSM Plan, so the roll-out of that behavioural program was pursued first. (b) In the BNI Demand Response program...
AI summary The response addresses the implementation of the residential behaviour program in E1's energy efficiency plan and the decision to focus on commercial and industrial curtailment in the BNI Demand Response program. It also references calculations related to the 2023–2026 Approved Rate Class Expenditures and Results.
- 22 - (b) The variances of 15 percent or more are identified in yellow in Table 1 in part (a). It is important to note that as part of efforts to enhance rate class spending reporting and monitoring, EfficiencyOne (E1) introduced a new ra...
AI summary EfficiencyOne introduced a new rate class allocation methodology in 2025 to improve reporting and monitoring of rate class spending, using three years of historical data instead of one year, as applied in the 2026 DSM Extension and the 2027–2031 DSM Resource Plan.
2027– 2031 DSM Plan application, and E1 forecasts in 2025 and 2026, are based on rate class percentages from three years of historical data. (c) Please refer to E1's response to part (c) of IG IR-14. Request IR-31: Pages 16-17 of Appendix...
AI summary The document discusses the 2027–2031 DSM Plan application and E1's use of historical data for rate class percentages. It also requests clarification on low-income customer estimates, stakeholder feedback on investment splits, and spending on low-income and equity initiatives.
4 Table 1: 2027-2031 Low-income & Equity Participants as a % of All Participants by Plan Year 2027 2028 2029 2030 2031 9.0% 8.5% 7.9% 8.1% 8.2% 6 Calculation: number of low-income & equity DSM participants divided by all participants in 7...
AI summary Table 1 shows the percentage of low-income and equity participants in the DSM program relative to all participants from 2027 to 2031. The calculation is based on the number of low-income and equity DSM participants divided by all DSM participants, with one participant representing one NS Power customer.
9 Table 2: 2027-2031 Low-income & Equity DSM Participants as a % of Residential DSM Participants by Plan Year 2027 2028 2029 2030 2031 9.7% 9.1% 8.4% 8.5% 8.6% Calculation: number of low-income & equity DSM participants divided by resident...
AI summary Table 2 presents the projected percentage of low-income and equity Demand Side Management (DSM) participants relative to total residential DSM participants from 2027 to 2031. The percentages decrease slightly over the years, with a slight increase in 2031.
• Assumptions for Tables 1 and 2: Participation eligibility assumptions reflect those of EfficiencyOne's (E1) rate and bill impact analysis (RBIA), found in E1's 2027–2031 DSM Plan Application, Appendix B, Attachment 5. • Each participant...
AI summary The text outlines assumptions and definitions used in EfficiencyOne's (E1) rate and bill impact analysis (RBIA) for the 2027–2031 DSM Plan Application. It includes details on participant definitions, exclusions, and references to other sections of the application.
1 Request IR-33: 2 - 3 Page 19 of Appendix A – Preferred Plan states, "For new measures, measure level inputs were - 4 developed, with support from Guidehouse, using a combination of engineering assumptions, - 5 evaluation results from com...
AI summary The document discusses a request (IR-33) asking about new measures in the 2027–2031 DSM Resource Plan and which programs offer them. The response directs the reader to Table 1 in the IR response for the full list of new measures.
15 Table 1: 2027-2031 Preferred Plan New Measures by Program Component New Measure (Measure Name) Program Component HW - Heat Pump Cleanings Affordable Single-family Homes MHEEP – Heat Pump Cleanings Affordable Single-family Homes Mi'kmaw...
AI summary The document includes a table listing new measures for the 2027-2031 Preferred Plan, focusing on heat pump cleanings and solar-PV systems in affordable and Mi'kmaw new home construction. It also includes a request for information regarding increased incentives in residential and BNI energy efficiency programs, with a response directing to specific attachments for detailed financial data.
Request IR-35: Please refer to Tables 9, 10, 11, 12, and 13: DSM Preferred Plan Savings and Investment by Program Component for 2027, 2028, 2029, 2030, and 2031 respectively starting on page 29 of Appendix A – Preferred Plan. (a) The Resid...
AI summary The response to IR-35 explains that E1's 2027–2031 DSM Preferred Plan focuses on affordability and cost-effectiveness. The Residential Instant Savings program has high cost-effectiveness and broad accessibility, while the Home Energy Assessment program is seeing increased investment to boost participation after the Canada Greener Homes Grant ended.
and savings. E1 is proposing higher incentives for customers to reduce participation barriers and cover a larger portion of total upgrade costs, as explained further in E1's response to Synapse IR-37. Request IR-36: Page 37 of Appendix A –...
AI summary E1 is proposing higher incentives to reduce participation barriers and cover more of the total upgrade costs. In response to a request about staff reductions in the DSM Preferred Plan, E1 notes that it will assess staffing needs during implementation to determine the specific operational requirements.
coverage that Apex Analytics suggested is typical in other jurisdictions during the development of the Preferred Plan. (e) E1 considered different incentive levels and how those changes would likely impact participant uptake, free-ridershi...
AI summary E1 has adjusted incentive levels for the Affordable Multifamily Housing program due to the end of provincial funding in May 2025. The response outlines that E1 considered various incentive levels and their impacts on participation, free-ridership, and cost effectiveness, and has proposed incentives that align with Apex Analytics' recommendations.
s a range of prescriptive and performance-based incentives. The estimated average incentive payments per project type are listed in Appendix A – Attachment 3 – 2027–2031 Energy Efficiency and Solar-PV - Technical Tables of E1's 2027–2031 D...
AI summary The document discusses proposed incentive levels for the 2027–2031 DSM Plan, noting that they are higher than previous levels but significantly lower than those when provincial top-up funding was available. E1 argues that the proposed incentives are reasonable and sustainable, aiming to increase customer participation and energy savings. However, the end of provincial top-up funding has led to a significant drop in customer pre-approval applications.
incentives have ended, monthly customer pre-approval applications have dipped by over 50 percent. (c) Please refer to part (b) of this IR response. (d) Please refer to part (b) of this IR response. Request IR-39: Page 40 of Appendix A – Pr...
AI summary EfficiencyOne (E1) used three years of historical data (2022–2024) to improve the accuracy of rate class allocations for the 2027–2031 DSM Preferred Plan. This approach was chosen to address concerns about spending variances and to enhance reporting accuracy. The methodology was also applied in the 2026 DSM Extension.
historical data to inform quarterly and annual (where applicable) rate class spending forecasts in 2025. This methodology was also used to calculate the 2026 DSM Extension rate class allocations, and the proposed 2027–2031 DSM Plan rate cl...
AI summary E1 used three-year historical data to improve the accuracy of rate class spending forecasts for the 2025 DSM Plan and future allocations up to 2031. This approach was deemed more effective than previous methods, which used only one or four years of data. E1 also aligned future customer commitments and program changes with these updated rate class allocations.
wed and considered alongside the rate class allocations that were calculated using three-year historical averages, and E1 determined that they were generally aligned with those rate class allocations. Request IR-40: Page 43 Appendix A – Pr...
AI summary The text discusses E1's use of data analytics in its DSM Plan, including segmentation data, website user behavior insights, and AMI data. It also asks whether E1 can identify homes with faulty equipment based on electricity use patterns and whether this data is used to target DSM programs.
eeper savings measures, does E1 see that customers benefit from more advance notice of equipment failure and the ability to prepare for a larger weatherization or heating system replacement project? (h) Does E1 see any opportunity to impro...
AI summary EfficiencyOne (E1) discusses its use of customer segmentation, website personalization, and AMI data to improve outreach and targeting of DSM programs. It notes that while AMI data is used for energy usage-based targeting, it has not explored using it for advance notice of equipment failure or outreach to customers with failing heating systems.
certain DSM programs (e.g., customers who participate in demand response programs). Please refer to part (a) of this IR response. (d) E1 has not explored that specific use case for AMI data for homes. (e) E1 has not used usage patterns to...
AI summary E1 has not used AMI data to promote DSM programs for customers with faulty equipment but plans to leverage usage patterns for DSM opportunities. E1 currently uses energy managers to identify faulty equipment and sees value and opportunity in using usage patterns for DSM.
3 Audit Name Description 2027 Cost per Audit Proposed Customer Co-pay D audit Initial home energy evaluation used to determine the current state of a home and develop an upgrade plan. $665.27 $0.00 E audit Final home energy evaluation used...
AI summary The document outlines the cost and customer co-pay for two types of home energy audits (D and E audits) and responds to a request regarding the implementation timeline for new energy efficiency measures in the Instant Savings Program. E1 explains that the 2028 start date for these measures is due to the anticipated late 2026 decision on the DSM Plan application.
- 1 (c) Electric thermal storage units are a technology that stores electricity in the form of thermal - 2 energy during off-peak hours when electricity is less expensive. The stored heat is gradually - 3 released to the room where it is i...
AI summary Electric thermal storage units store electricity as thermal energy during off-peak hours and release it gradually for heating purposes, either in the room where they are installed or by transferring heat to water in hydronic heating systems.
- 4 systems to provide less expensive heating and support grid load shifting. 1 Request IR-44: 2 3 Please refer to the Target Market section of Table 19: Existing Residential - Overview, 4 Objectives, Opportunity starting on Page 49 of App...
AI summary The document addresses a request for information about the number of property owners providing affordable housing and non-profit organizations offering support services in Nova Scotia, focusing on how many have been served and the DSM Plan's proposed coverage. The response refers to a 2025 evaluation report and a 2027–2031 DSM Resource Plan Application for further details.
- M12780, Exhibit 3, E1 2025 DSM Programs Evaluation Report, Existing Residential Program, March 13, 2026, Figure 2, page 4. DATE FILED: May 28, 2026 E1 (Synapse) IR-44 Page 2 of 2 Request IR-45: Please refer to the firstsection of Table 2...
AI summary The response to Request IR-45 explains that 2028 is the year of highest participation in the Affordable Multifamily Housing program because the baseline for BNI lighting projects is expected to shift to LED technology in 2029, making 2028 the last year for incentivizing such projects before the measure is retired. Participation is forecasted to decline afterward.
iciencyOne's (E1) independent third-party Evaluator. As such, 2028 is likely to be the final year that E1 can incentivize such projects and claim savings before this measure category will be retired. (b) As noted in the response to part (a...
AI summary EfficiencyOne (E1) is likely to retire a measure category by 2028, which impacts its ability to incentivize energy efficiency projects. The decline in participation from 2028–2031 is attributed to a change in the lighting baseline. Pre-weatherization barriers in older buildings may prevent customers in the Affordable Multifamily Housing program from proceeding with energy efficiency improvements, but no funding is included in the proposed 2027–2031 DSM Plan to address these barriers.
(d) Please refer to part (c) of this IR response. Where E1 does not have any recent statistics on the number of homes eligible for the program, we are unable to comment on current trends. (e) At the end of 2025, E1 had served roughly 9,500...
AI summary E1 reports serving approximately 9,500 homes through the program by the end of 2025, but challenges remain in quantifying the proportion of eligible customers served due to fluid eligibility numbers. Pre-weatherization barriers are a challenge for some participants, and E1 does not have specific funding in the 2027–2031 DSM Plan for addressing these barriers.
- 1 as part of building envelope upgrades where costs and risk are minimal. However, in many 2 cases, it is cost prohibitive, or the issues require the support and expertise of government - 3 agencies and other organizations who are in a b...
AI summary The response to IR-47 discusses the Affordable Single-family Homes program component, which includes heat pump installations as an eligible upgrade. It notes that 68% of participants in 2025 had both electric and non-electric heating systems and were considered for the Oil to Heat Pump Affordability grant.
1 Request IR-49: 2 3 Please refer to Table 36: 2027–2031 Custom Program Component on Page 69 of Appendix A – 4 Preferred Plan which states, "Enhancements in 2027-2031: Better support for E1's BNI Demand 5 Response program component by enco...
AI summary The response to Request IR-49 discusses the BNI Demand Response program, focusing on equipment compatibility, customer participation, and curtailment methods. It highlights that the program is technology-agnostic, plans to support residential customers with smart thermostats and heat pump water heaters, and primarily uses manual curtailment, with limited automatic control.
- 1 As a result, the automatically controlled portion is too small to support a meaningful - 2 comparison with manual curtailment. E1 will continue to monitor participation as the BNI - 3 DR portfolio develops. Request IR-50: Please refer...
AI summary E1 explains that it can claim savings for a portion of a project in the BNI DR portfolio due to low-income and equity impacts being treated as incidental. Participation rates for low-income and equity projects in the 2027–2031 DSM plan are estimated as 1, 0.4, 0.3, 0.3, and 0.2 for each year, respectively. These participants are apartment building owners, with benefits flowing to tenants.
DATE FILED: May 28, 2026 E1 (Synapse) IR-50 Page 2 of 2 1 M12249, E1 2026 DSM Extension, April 30, 2025, Appendix A, Attachment 2: Estimation of DSM Low-income and Equity Impacts, section 3.2: DSM Reporting Assumptions: Incidental Impacts,...
AI summary The document outlines a request and response regarding the definition of small businesses and their inclusion in the BNI demand response effort. It clarifies that small businesses are defined based on annual energy consumption and that while they may participate, they are not the primary focus of recruitment during the 2027–2031 DSM Plan period.
(c) E1 has not projected the portion of BNI demand response effort participants that are expected to be small business customers by year or in total across years. In Appendix A – Attachment 2: Program Savings and Investment by Rate Class,...
AI summary E1 has not provided projections on the participation of small businesses in BNI demand response efforts. The Small Business Energy Solutions program supports energy efficiency but does not provide additional equipment for demand response participation.
BNI demand response offer. If a small business customer participates in BNI demand response, the customer would receive the standard equipment or controls applicable to that demand response offering. Request IR-52: Please refer to the stat...
AI summary EfficiencyOne (E1) explains that it will not enroll new customers in the Residential Demand Response program from 2027 to 2031 due to current cost-effectiveness limitations. Instead, E1 will focus on optimizing the performance of existing equipment and managing program costs, with the expectation that future advancements will improve the program's cost-effectiveness and allow for renewed enrollment beyond 2031.
DATE FILED: May 28, 2026 E1 (Synapse) IR-52 Page 2 of 2 1 Request IR-53: 2 3 Page 76 of Appendix A – Preferred Plan states, "The level of available demand response 4 capacity proposed for 2027–2031 remains within, not exceeding, the optima...
AI summary The document includes a request for information regarding the optimal level of demand response capacity identified in NS Power's 2022 Integrated Resource Plan (IRP) and how the proposed capacity in the Preferred Plan remains within that level. The response refers to prior responses provided by EfficiencyOne (E1) to Synapse IR-10.
Pages 77-78 of Appendix A – Preferred Plan states, "E1 understands that NS Power is currently developing a Distributed Energy Resource (DER) Integration Roadmap, expected to be filed in early 2026, which will outline locational planning st...
AI summary E1 is engaged in the development of NS Power's DER Integration Roadmap, expected to be filed in early 2026. E1 contributes demand response expertise and requests expanded AMI data feeds to better target constrained areas. E1 expects ongoing collaboration with NS Power on the roadmap.
g 6 the restoration of the AMI data transfer. - 8 Depending on the outcomes of the DER Integration Roadmap and AMI feeder ID 9 information, E1 would expect to assess the appropriate next steps. (g) 7 Request IR-55: Please refer to the disc...
AI summary The response discusses E1's awareness of NS Power's upcoming TVP 2024/25 EM&V report and the ongoing process for resolving cybersecurity and AMI data issues from the TVA pilot. E1 highlights the filing of Monthly Update 8 in matter M12273 regarding the cybersecurity incident.
ne and process for resolving these issues; however, E1 would note that NS Power filed Monthly Update 8 in matter M12273, Board Inquiry into Nova Scotia Power's Cybersecurity Incident, on May 14, 2026. Request IR-56: Please refer to Table 4...
AI summary The document discusses a request related to interruptible customers and their eligibility for the BNI Demand Response program, including how service interruptions are managed, differences between interruptible customers and BNI customers, and potential barriers to eligibility. E1 has committed to engaging with DSMAG members to assess the issue further.
of the engagement with DSMAG members on this topic? Would E1 need to modify the plan to take these actions? Response IR-56: (a) Part (a) of the following IR response has been provided by NS Power. NS Power manages the interruption of inter...
AI summary The response outlines how NS Power manages capacity shortfalls by interrupting interruptible customers, ensuring system reliability. It also addresses concerns about potential double counting of capacity value if BNI DR is applied to customers already providing system value. E1 plans to continue discussions with the DSMAG during the 2027–2031 Plan period.
remental value to ratepayers and does not compensate the same curtailable load twice. (d) E1 expects to continue discussions with DSM Advisory Group (DSMAG) members during the 2027–2031 Plan period. (e) Depending on the outcome of DSMAG en...
AI summary EfficiencyOne (E1) plans to continue engaging with the DSM Advisory Group (DSMAG) during the 2027–2031 Plan period to assess the potential for interruptible customers to provide incremental curtailable capacity through BNI DR. E1 explains that batteries, EV telematics, and EV charger devices are not included in the proposed 2027–2031 Plan, despite being supported in previous years.
2026 demand response seasons). Table 45 reflects the measures included in the proposed 2027–2031 Preferred DSM Plan (EV and battery pathways have not been included in the 2027–2031 proposed DSM Plan). Request IR-58: Please refer to the ava...
AI summary The response to Request IR-58 explains that the available demand response capacity estimates do not account for effective load carrying capability (ELCC) as estimated by NS Power. EfficiencyOne (E1) is awaiting the results of ongoing work by NSIESO and NS Power to assess ELCC treatment for demand response and will review findings to optimize program design and increase capacity value for ratepayers.
l review the findings to understand how program design, dispatch parameters, event timing, duration, and resource mix can be optimized to increase the capacity value of demand response for ratepayers. Request IR-59: Please refer to page 82...
AI summary The response to Request IR-59 discusses how past-season performance is factored into projected achievable demand response capacity, including adjustments to enrollment, retention, and per-device response rates based on observed results. It also addresses the increase in C&I Curtailment potential from 2026 to 2027 despite declining participation.
the participation and unitary capacity assumptions used in the proposed 2027–2031 DSM Plan. These assumptions were informed by evaluation results, observed program performance, and EfficiencyOne (E1) program experience. The attrition assum...
AI summary The proposed 2027–2031 DSM Plan uses participation and unitary capacity assumptions informed by EfficiencyOne's (E1) program experience and evaluation results. The attrition rate remains at 2% per year, and the increase in Commercial and Industrial (C&I) Curtailment potential is due to targeted recruitment and improved customer coordination, not just an increase in participant count.
additional advance notice from NS Power where feasible. These steps are intended to improve participation and reduce the likelihood that customers are unable to respond due to operational constraints. Request IR-60: Please refer to Table 4...
AI summary The response to Request IR-60 outlines the current Eco Shift participation incentives for residential customers and addresses whether E1 considered reducing incentives for new participants or expanding the program to new customers in constrained areas after NS Power provides AMI data feeds.
- i) Please refer to part (b) of this IR response. - ii) Please refer to part (b) of this IR response. - (c) No, E1 has not included any new enrollments in the proposed Eco Shift demand response program component during the 2027–2031 DSM P...
AI summary EfficiencyOne (E1) explains that the increase in participation in the BNI Demand Response Program from 2024 to 2025 was due to Smart Synergy recruitment and program maturation. E1 also notes that no new enrollments were added in the proposed Eco Shift demand response program component during the 2027–2031 DSM Plan period.
tment to build the program and support the higher capacity target, including recruiting customers with lower available capacity where appropriate. This helped increase participation from 2024 to 2025. After the 2025 season, E1 refined its...
AI summary EfficiencyOne (E1) is refining its recruitment strategy for the BNI Demand Response (DR) program, focusing on customers with higher curtailable capacity and reliability. Participation growth is expected to slow due to this targeted approach. Incentives include performance-based payments, and E1 is considering DER integration and AMI data for future planning.
tion where BNI DR can provide value and where customers with curtailable load are within those areas. i) Please refer to part (d) of this IR response. ii) Please refer to part (d) of this IR response. Request IR-62: Please refer to Table 4...
AI summary The response explains that the lower PAC for 2028 is due to significantly lower avoided costs in 2028 compared to other years, particularly the avoided cost of generation capacity being less than half of the 2027 value. Avoided cost of capacity is the main factor influencing PAC results for demand response programs.
3 Figure 1 shows how the annual variation in Residential Demand Response and BNI Demand 4 Response PAC results corresponds to the annual variation in the avoided cost of capacity. 5 6 Figure 1: Residential Demand Response and BNI Demand Re...
AI summary The text discusses the relationship between the annual variation in Residential Demand Response and BNI Demand Response Program Administrator Cost (PAC) results and the avoided cost of capacity. It references figures and tables that provide further details on program performance indicators.
1 Table 2: 2027–2031 Residential Demand Response Year Investment ($ million) Available Capacity (MW) Participation (devices) Participation (participants) Levelized Cost ($/kW year) Program Administrator Cost Test (PAC) 2027 2.2 4.2 22,940...
AI summary Table 2 outlines the projected investment, available capacity, and participation metrics for residential demand response programs from 2027 to 2031. The data shows a consistent investment of around $2 million annually, with a gradual decline in available capacity and participation devices, while the program administrator cost test (PAC) remains relatively stable.
4 Year Investment ($ million) Available Capacity (MW) Participation (devices) Participation (participants) Levelized Cost ($/kW year) Program Administrator Cost Test (PAC) 2027 3.1 17.0 0 169 - 2.9 2028 3.5 19.1 0 173 - 1.6 2029 3.8 21.2 0...
AI summary Table 4 estimates the Residential and BNI Demand Response Program Administrator Cost (PAC) results under a constrained area scenario, calculated manually by E1 using data from the DSM Plan and substituted avoided costs from Table 5. This method provides an approximation rather than a model-based result.
1 Table 4: Residential and BNI Demand Response PAC Results – Constrained Area Analysis PAC PAC Year Residential DR BNI DR 2027 1.1 3.5 2028 0.7 2.2 2029 1.0 3.3 2030 0.8 3.0 2031 0.8 3.1 Total 0.9 3.0 2
AI summary Table 4 presents the Program Administrator Cost (PAC) results for Residential and BNI Demand Response in a constrained area analysis, showing costs from 2027 to 2031 and total costs.
6 Table 5: Constrained Area Avoided Costs Avoided Cost Category 2027 2028 2029 2030 2031 T&D Capacity - Constrained ($/kW-yr) 186 190 194 198 202 Generation Capacity ($/kW-yr) 513 250 453 380 378 Energy Purchase On Peak ($/kWh) 155 40 84 1...
AI summary The document discusses a request for information regarding E1's engagement with Mi'kmaw communities related to its DSM Plan, including whether discussions affected previous and proposed DSM investments, and whether reliability concerns were raised. E1 responded that it has ongoing engagement and that solar-PV provides reliability benefits even without batteries.
Aligned with the Nova Scotia Energy Board's Decision on E1's Application for a New Benefit Cost Analysis Test for Evaluating Demand Side Management Plans (M12282), E1 has used the Program Administrator Cost test to assess the benefits of t...
AI summary E1 has used the Program Administrator Cost (PAC) test to evaluate the proposed 2027–2031 DSM Plan, aligning with the Nova Scotia Energy Board's decision on a new benefit cost analysis test. Non-energy benefits are not included in the assessment. E1 considered including batteries in the Solar-PV program, based on data from a previous Home Battery Pilot, which could lower the PAC ratio below 1.0.
DATE FILED: May 28, 2026 E1 (Synapse) IR-63 Page 3 of 3 1 Request IR-64: 2 3 Page 92 of Appendix A – Preferred Plan states, "The Roving Energy Manager facilitates 4 Mi'kmaw participation in E1's BNI programs throughout the 2027– 2031 DSM P...
AI summary The document outlines responses to requests regarding E1's Roving Energy Manager and a program harmonization initiative. The Roving Energy Manager facilitates Mi'kmaw participation in BNI programs through on-site audits and outreach. The harmonization initiative aims to streamline E1 operations, with implementation beginning in Q3 2026 and expected completion in Q2 2028. An evaluation will be conducted after the first phase.
1 HPWHs become industry standard. At each stage, it is the first time being conducted by 2 E1. 3 4 As demonstrated in other jurisdictions that deliver MT initiatives, including those for 5 HPWHssuch as Northwest Energy Efficiency Alliance...
AI summary The text discusses the long-term nature of Market Transformation (MT) initiatives, such as those for Heat Pump Water Heaters (HPWHs), and outlines the use of condensed impact evaluations for stable, mature programs. It references EfficiencyOne's (E1) approach to developing an evaluation framework with an independent consultant.
Request IR-69: Page 102 of Appendix A – Preferred Plan states, "E1 will work with the Evaluator to determine what program components should be evaluated based on the following criteria: • newly created program components that have not yet...
AI summary EfficiencyOne (E1) did not consider aligning the 25% evaluation variance threshold with the MCA's 20% threshold for program changes. E1 will review the matter but does not currently see a rationale for such alignment.
riance threshold with the MCA spending and savings threshold. E1 will review this matter to assess whether there is valid rationale for such a change. (b) Please refer to part (a) of this IR response. Request IR-70: Page 103 of Appendix A...
AI summary The response addresses whether the Evaluator can obtain information about the coincidence of load reduction with the utility peak period and whether the avoided capacity cost reflects this. It explains that the Evaluator's scope does not include collecting such information, as it is not required for evaluating total available demand response capacity.
collect and assess information regarding the coincidence of the load reduction with the utility peak period. This information is not required to evaluate the total available demand response capacity, which is EfficiencyOne's (E1) performan...
AI summary The document discusses how EfficiencyOne (E1) evaluates demand response capacity provided to NS Power, emphasizing that it does not require load reductions to coincide with the utility peak period. The avoided capacity cost is based on NS Power's planning value and reflects the broader value of DSM programs in avoiding generation investments.
d- side management (DSM) programs, including both energy efficiency and demand response. • For energy efficiency, avoided capacity costs are realized through reductions in overall system peak demand. • For demand response, avoided capacity...
AI summary The text discusses how demand side management (DSM) programs, particularly energy efficiency and demand response, help avoid capacity costs by reducing system peak demand. A study by the NSIESO on Effective Load Carrying Capability (ELCC) is evaluating the reliability of demand response resources during system need, which will inform future utility benefit calculations and avoided capacity cost estimations.
acity value. E1 expects the study to inform future discussions on avoided capacity cost estimation and utility benefit calculations. For additional detail, please refer to E1's response to NSEB IR-43. Request IR-71: Please refer to page 10...
AI summary E1 discusses the capacity cost estimation and utility benefit calculations, and responds to questions about BNI DR performance differences between morning and evening events, attributing stronger morning performance to higher available load in the morning. E1 also notes that residential performance varies based on device type and event conditions.
In general, residential heating loads are expected to be available during both morning and evening winter peaks, but performance can vary based on occupancy, weather, customer comfort settings, device connectivity, and whether the controll...
AI summary The text discusses the performance of residential heating loads during winter peaks, noting variability based on factors like occupancy and weather. EfficiencyOne (E1) does not control event timing, which is determined by NS Power, but collects customer preferences to ensure the portfolio can respond to both morning and evening events. References include the 2025 DSM Evaluation Report and M12780.
(g) recommended changes to respond to implementation challenges or opportunities; (h) the potential for additions and/or terminations of programs; and (i) the potential for a plan amendment and the cause(s), including but not limited to: s...
AI summary E1 proposes a mid-term check-in process for the DSM Plan to enhance transparency and stakeholder engagement. This includes advance notice, input opportunities, written materials, and one-on-one meetings with DSMAG members, with a session planned for the first quarter of 2029.
• Would an amendment to the DSM Plan be in the best interest of ratepayers? Consistent with a DSM Plan application, E1 would expect any amendment would require fulsome DSMAG member engagement prior to E1 filing an application seeking NSEB...
AI summary The document discusses potential amendments to the DSM Plan, emphasizing the need for engagement with the DSMAG and regulatory approval by the NSEB. It also considers the achievability of the plan and whether changes in the IRP would necessitate an amendment, noting that past changes in IRP outcomes have not automatically triggered amendments.
es - including updated avoided costs or revised resource adequacy findings – have not automatically triggered amendments to a DSM Plan in the past. E1 does additional regulatory burden unnecessarily. acknowledge that materially different a...
AI summary E1 acknowledges that changes in avoided costs or resource adequacy findings from a new IRP may be important but suggests that these should be evaluated on a case-by-case basis to determine if they warrant a DSM Plan amendment. E1 retains discretion in deciding whether to propose amendments and does not have a predefined threshold for what constitutes a material change.
(f) Please refer to part (a) of this IR response. (g) Please refer to part (a) of this IR response. (h) Please refer to part (a) of this IR response. (i) Please refer to part (a) of this IR response. DATE FILED: May 28, 2026 E1 (Synapse) I...
AI summary The request IR-73 asks whether E1 should align the 15 percent variance threshold for program changes with the MCA threshold of 20 percent. E1 refers to its response to NSEB IR-30 for an explanation of how these thresholds were determined.
lanations? Would it make sense to align these two thresholds? Why or why not? Response IR-73: Please refer to EfficiencyOne's response to NSEB IR-30 that explains how E1 determined these thresholds. Request IR-74: Page 2 of Appendix A – At...
AI summary The document includes responses to information requests regarding EfficiencyOne's (E1) threshold alignment, the composition of the Executive Leadership Team, and the definition of hybrid-heating solutions for households with high retrofit costs or structural barriers.
ncluding: - Air to water heat pumps with non-electric hydronic boiler - Roof top units with non-electric back up coil - Dual fuel systems (hybrid heat pumps with non-electric backup in a single unit) Request IR-76: Page 9 of Appendix A – A...
AI summary The discussion focuses on the integration of time-varying pricing rates with demand flexibility initiatives, emphasizing coordination between NS Power and E1 to align rate design and program participation. The response clarifies that demand flexibility includes both locational DSM and specific demand-response projects, ensuring alignment with rate signals and reducing market confusion.
DATE FILED: May 28, 2026 E1 (Synapse) IR-76 Page 2 of 2 Request IR-77: - Please refer to Figure 3: Average Rate Impacts (2027-2046) as a Result of 2027-2031 DSM - Preferred Plan Activities on page 8 of Appendix B - Rate and Bill Impact Ana...
AI summary The response explains that the Medium Industrial rate class has negative rate impacts due to reduced peak loads from high participation in the Demand Response program, which lowers the class's share of system peak costs. However, the inclusion of Renewable to Retail loads increases overall energy consumption, spreading DSM rider costs over more kWh and leading to negative rate impacts.
e "Renewable to Retail" adjustment is. Response IR-78: Please refer to Appendix B page 19, line 27 to page 20, line 23 for explanation of the Renewable to Retail adjustment. 1 Request IR-79: 2 Please refer to Table 1: Rate and Bill Impacts...
AI summary The document refers to the 'Renewable to Retail' adjustment and requests additional information on participant counts for the 2027-2031 DSM Preferred Plan, including how to present these counts over a five-year period.
4 Approach: - 5 Active Participants represents participants who experience savings in the specified year 6 as a result of participation in DSM at any time over the 2027–2031 DSM Plan. - 7 Non-Active Participants represents customers who do...
AI summary The document discusses the categorization of participants in the 2027–2031 DSM Plan, distinguishing between active and non-active participants. It references a request (IR-80) to add columns for active and non-active participants in a table analyzing rate and bill impacts over time.
5 Approach: - 6 Active Participants represents participants who experience savings in the specified year 7 as a result of participation in DSM at any time from 2011–2026. - 8 Non-Active Participants represents customers who do not experien...
AI summary The text explains the categorization of participants in the Demand Side Management (DSM) program, distinguishing between active and non-active participants, and outlines how the number of active participants decreases over time as energy savings expire.
1 Request IR-81: 2 3 Please refer to the table titled Rate and Bill Impacts of DSM on the Large General Class on page 4 4 of Appendix B - Attachment 2: Results by Rate Class (2027 - 2031 Preferred Plan), which shows 5 Active Participants a...
AI summary The response explains that Annual Participants refer to unique participants in a given year, while Active Participants refer to those currently experiencing savings from DSM programs. Active Participants are capped at the total number of NS Power participants by rate class, and annual participation declines over time based on the DSM Plan's program design.
volution - analysis. Outside of the annual program evaluations, it is anticipated that E1 may conduct a DSM - Potential Study during the 2027–2031 period subsequent to the 2026 Potential Study that is - 1 being conducted to inform the Nova...
AI summary E1 is planning a Potential Study during the 2027–2031 period to support the NSIESO's inaugural Integrated Resource Plan. Responses to requests regarding DSM performance targets and financial estimates refer to other documents and schedules within the Purchase Agreement.
ns current and aligned with regulatory requirements and stakeholder feedback. E1 will provide an updated version of the Framework, incorporating the approved changes, for future DSM Plan applications. (b) Please refer to Synapse IR-02, Att...
AI summary E1 will provide an updated version of the Framework aligned with regulatory requirements and stakeholder feedback. Definitions for terms like 'energy efficiency' and 'solar PV' are referenced in E1's 2027–2031 DSM Resource Plan Application.
pplication, page 83, lines 15-17; • Electricity Costs: Costs incurred by customers for electricity service, including supply, delivery, and consumption. The term is tied to statutory use: "the purpose - of the demand-side management provis...
AI summary The text discusses the definition of key terms related to demand-side management (DSM) programs, including 'program component' and 'program,' as outlined in E1's 2027–2031 DSM Resource Plan Application. It also references a decision (M12282) related to a new benefit-cost analysis test for evaluating DSM plans.
1 Table 1: 2027-2031 - Relationship between Portfolio, Resource, Sector, Program and Program Components 2027–2031 Portfolio Resource Sector Program Program Components Energy Efficiency Residential Residential Efficient Product Rebates Inst...
AI summary The text presents Table 1 outlining the 2027–2031 portfolio, resource, sector, program, and program components. It also includes a request (IR-88) for clarification on the metrics E1 will provide for the energy efficiency and demand-side management programs, including questions about the inclusion of the modified PAC, GHG emissions reductions, and solar PV generation.
: "Primary cost-effectiveness screen at the portfolio level, discount using NS Power's WACC. Strategic electrification is assessed using a modified PAC that includes the incremental utility revenues…" (d) E1 did include portfolio-level GHG...
AI summary The document discusses the evaluation of DSM Plans, including the inclusion of GHG savings and levelized cost of saved energy as performance indicators. E1 did not include GHG emissions reductions as a primary metric, but plans to update the Standardized Filing Framework based on the Board's recommendations.
1 Framework. This is because this performance metric does not directly measure the Plan's 2 resource acquisition objectives, cost-effectiveness, savings outcomes, or other quantifiable 3 results against which a DSM Plan is assessed. Instea...
AI summary The text discusses the limitations of a performance metric used to evaluate a DSM Plan, noting that it does not directly measure resource acquisition objectives, cost-effectiveness, or savings outcomes. Instead, it provides contextual information about customer experience and service delivery.
12 Process Timeframe 4.6 Mid-Course Adjustments Filed with E1's Q1 Report on May 25 each year, if applicable. Draft mid-course adjustments are provided to the DSMAG in advance for a two-week comment period and E1 responds to comments prior...
AI summary The document outlines various processes and timelines related to reporting and stakeholder engagement for demand-side management (DSM) in Nova Scotia. It includes mid-course adjustments, mid-term check-ins, and reporting requirements, as well as the role of the DSM Advisory Group (DSMAG) in the process.