Matter: Nova Scotia Power Inc. - CI C0083589 – IR751 Brooklyn Community Solar - $0 (U&U)2026 Q1 Capital Reports
5 passages 1 document

Distribution Planning across all matters →

N-1CI C0083589 – IR751 Brooklyn Community Solar - $0 - Redacted 5 passages
Preamble p. p. 2
CI Number: C0083589 Title: IR751 Brooklyn Community Solar Start Date: 2026/02 In-Service Date: 2027/06 Final Cost Date: 2027/12 Function: Distribution Forecast Amount: $0

AI summary The document outlines a project titled 'IR751 Brooklyn Community Solar' with a start date in 2026, an in-service date in 2027, and a final cost date in 2027. The forecast amount is listed as $0, indicating no anticipated financial impact.

INTERCONNECTION REQUEST #751 SYSTEM IMPACT STUDY p. p. 2
INTERCONNECTION REQUEST #751 SYSTEM IMPACT STUDY Community Solar program: Total 4.8 MW Capacity Site Address: Brooklyn Road, Annapolis County, NS Report Number: W-DSIS-2025-011

AI summary The document outlines an interconnection request for a 4.8 MW community solar project located on Brooklyn Road in Annapolis County, Nova Scotia. The report number is W-DSIS-2025-011, indicating it is a Distribution System Impact Study related to the project.

Prepared By: NSPI Date: November 17th, 2025 p. pp. 2-6
Prepared By: NSPI Date: November 17th, 2025 Rev Description Date Prepared Reviewed Approved 0 Issued for Release November 17, MA JH, BH, RD BH 2025

AI summary This document, prepared by NSPI on November 17, 2025, appears to be a version control table for a regulatory proceeding. It includes a distribution system impact study (DSIS) and other related procedures, but the content is limited to administrative information.

4.14.2 Voltage Dips p. p. 19
4.14.2 Voltage Dips The acceptable limits for voltage deviation are listed in Table 8. Operation of the Generating Facility at full load output, from on-line to off-line shall cause no more than a 2.5% step change in system voltage measure...

AI summary The acceptable limits for voltage deviation are specified in Table 8, with a requirement that operating the Generating Facility at full load output from on-line to off-line causes no more than a 2.5% step change in system voltage measured at the POI.

Table 9: Maximum Harmonic Current Distortion in Percent of Maximum Demand Current p. p. 20
Table 9: Maximum Harmonic Current Distortion in Percent of Maximum Demand Current Individual Harmonic Order h (Odd Harmonics) Total Demand 2 ≤ h < 11 11 ≤ h < 17 17 ≤ h < 23 23 ≤ h < 35 35 ≤ h ≤ 50 Distortion 4.0% 2.0% 1.5% 0.6% 0.3% 5.0%...

AI summary Table 9 outlines the maximum harmonic current distortion levels in percent of maximum demand current for various harmonic orders. The Generating Facility must be able to tolerate these levels, which may be present even without harmonics generated by the Interconnection Customer's facility.

Disclaimer: These summaries were generated by AI from the filings they describe. We take care to make them accurate, but errors are possible - and they aren't advice. Only the filings themselves are the record: if you're relying on something here, confirm it against the source documents or the Nova Scotia Energy Board's own record. Full disclaimer →