Matter: NSPI CI# 38819 - $7,452,511 - 51V Tremont Circuit Breaker & Bus
13 passages 6 documents

Infrastructure Planning across all matters →

N-1Redacted Work Order 8 passages
Why do this project? p. p. 7
Why do this project? The load on the 69kV system in the Annapolis Valley has increased to a level where a loss of selected elements (138kV line or 138-69kV transformer) in the area, under peak load conditions, causes the voltage on the 69k...

AI summary The project is necessary due to increased load on the 69kV system in the Annapolis Valley, which risks voltage drops below acceptable levels during peak conditions. The solution involves adding a new 138kV line and a 138kV-69kV autotransformer at the 51 V-Tremont Substation to ensure reliability.

Why do this project this way? p. p. 7
Why do this project this way? The new line terminal and second transformer addition at 51V-Tremont is required to terminate the new 138kV line and provide the additional source point on the 69kV system. This work will be completed by NSPI....

AI summary The project at 51V-Tremont involves adding a new line terminal and transformer to accommodate a 138kV line and provide an additional source point on the 69kV system. The increased cost is primarily due to the requirement for a new radio link.

Consulting – Design $386,500 p. p. 7
Consulting – Design $386,500 This estimate includes costs for protection and control design, substation design, and witnessing of tests.

AI summary The document outlines a consulting design cost of $386,500, which covers protection and control design, substation design, and test witnessing.

Surge Arresters - Station Class p. p. 7
Surge Arresters - Station Class Schedule of F Prices & Delivery 10 a) Please provide the planning studies and other relevant documents that justify the 11 construction of these three related projects. 12 13 b) Since these three projects, t...

AI summary The text contains a series of questions requesting information about the planning, design, engineering, and procurement processes for three related infrastructure projects totaling approximately $24 million. The questions focus on the justification for splitting the projects, the status of design and engineering phases, and the preparation of tender documents and Gantt charts.

4 p. p. 7
4 Tender Document Tender Amount Issue Date Close Date Comments Right-of–Way Clearing $500 K March 2010 March 2010 Tender awarded Site Development and Foundations – Canaan Rd. $350 K May 2010 July 2010 This tender has been issued, but not a...

AI summary The text presents a table of tender documents related to infrastructure projects, including details such as tender amounts, issue dates, close dates, and comments on the status of each tender. Some tenders have been awarded, while others are estimated or not yet issued.

7 Table 3 Breakdown of CI#11004 Canaan Rd. Circuit Breaker Additions p. pp. 7-19
7 Table 3 Breakdown of CI#11004 Canaan Rd. Circuit Breaker Additions Account 2010 Total 2011 Total Project Total Labour 161,831 0 161,831 Overtime Labour 7,420 0 7,420 Materials Contracts Other 24,893 0 24,893 Interest 29,521 0 29,521 AO 2...

AI summary The text discusses the breakdown of costs for the Canaan Rd. Circuit Breaker Additions project, including labor, materials, and interest, and outlines NSPI's plans for completing design and electrical work at the Canaan Road and Tremont Substations. It emphasizes the confidentiality of the study and material information due to system security concerns and competitive advantage considerations.

Section 169 p. p. 19
Canaan Road - Tremont Transmission Reinforcement

AI summary The document discusses the Canaan Road - Tremont Transmission Reinforcement project, which involves upgrading transmission infrastructure to enhance system reliability and accommodate increasing electricity demand.

Section 171 p. pp. 19-25
Test 4 43V- Canaan Rd. - 51V- Tremont 138kV System Expansion Project

AI summary The text references a 138kV System Expansion Project on Canaan Rd. and Tremont, indicating an infrastructure development initiative related to power distribution. The figures and project names suggest a discussion around grid modernization and infrastructure planning.

N-2NSPI Redacted Responses to Information Requests 1 passage
NON-CONFIDENTIAL p. p. 0
NON-CONFIDENTIAL 1 Request IR-2: 13 percentage overload is the contingency situation at 120 percent of the 65 degree Celsius 14 manufacturer nameplate MVA. 1 Request IR-5: 2 3 Reference Response to ACE Plan IR-T2, Attachment 1, page 4 of 3...

AI summary The text outlines requests and responses related to infrastructure changes, including the establishment of a 138 KV ring bus and reconfiguration of a 69 KV bus. NSPI explains that there is no incremental cost for establishing the ring bus as it requires the same number of components as an alternative configuration.

06178Board Decision and Order 1 passage
ORDER
ORDER WHEREAS Nova Scotia Power Incorporated ("NSPI") filed applications on July 27, 2010, with the Nova Scotia Utility and Review Board (the "Board") for approval of Work Orders CI# 38819 - 51V Tremont Circuit Breaker & Bus in the amount...

AI summary The Nova Scotia Utility and Review Board approved NSPI's applications for work orders related to electrical infrastructure upgrades, including transmission lines and circuit breaker additions, after considering stakeholder input and reviewing the affiliate transaction with Emera Utility Services.

05263Board Letter advising a forum for public review is required 1 passage
Section 1 p. p. 0
Nova Scotia Utility and Review Board Mailing address PO Box 1692, Unit "M" Halifax, Nova Scotia B3J 3S3 [email protected] Web www.nsuarb.ca Office 3rd Floor 1601 lower Water Street Halifax, Nova Scotia B3J 3P6 902 424-4448 t 902 424-391...

AI summary Nova Scotia Power Inc. (NSPI) submitted a request for review and approval of three Work Orders totaling $17,459,577 for the Canaan Road to Tremont Transmission Line and Associated Substation Additions in Kings County, Nova Scotia. The request was addressed in correspondence from the Nova Scotia Utility and Review Board (NSUARB) dated September 16, 2010.

05705Information Requests 1 passage
IR-5:
IR-5: - Reference Response to ACE Plan IR-T2, Attachment 1, page 4 of 35 - a) NSPI proposes to establish a 138 KV ring bus? What is the incremental cost to establish a ring bus? - b) Please describe more fully the reasons for establishing...

AI summary The document contains a series of questions posed by the regulatory body regarding proposed electrical infrastructure changes by NSPI, including the establishment of a 138 KV ring bus, reconfiguration of a 69 KV bus, and an alternative transmission route, focusing on costs and reliability impacts.

06178Board Decision and Order 1 passage
ORDER
ORDER WHEREAS Nova Scotia Power Incorporated ("NSPI") filed applications on July 27, 2010, with the Nova Scotia Utility and Review Board (the "Board") for approval of Work Orders CI# 38819 - 51V Tremont Circuit Breaker & Bus in the amount...

AI summary Nova Scotia Power Incorporated (NSPI) applied for approval of several electrical infrastructure projects. The Nova Scotia Utility and Review Board conducted a public review and received input from stakeholders, including the Consumer Advocate. After reviewing the applications and responses, the Board approved the projects, noting their necessity for improving service reliability and confirming the legitimacy of the affiliate transaction with Emera Utility Services.

Disclaimer: These summaries were generated by AI from the filings they describe. We take care to make them accurate, but errors are possible - and they aren't advice. Only the filings themselves are the record: if you're relying on something here, confirm it against the source documents or the Nova Scotia Energy Board's own record. Full disclaimer →