Large Scale Integration of Inverter Based Resources in Nova Scotia Frequency Control and System Strength Assessment Initial Findings and Recommendations Report Number: 083-2023-TSMG October 23, 2023 Manitoba Hydro International Ltd. Nova S...
AI summary This report, titled 'Large Scale Integration of Inverter Based Resources in Nova Scotia,' focuses on assessing frequency control and system strength for integrating inverter-based resources into the grid. It is authored by Manitoba Hydro International Ltd. and Nova Scotia Power Inc., highlighting technical and operational considerations for grid reliability.
Executive Summary Nova Scotia is on a path to build a cleaner, greener future for the province, phasing out coal and working towards 80% renewable energy by 2030. Inverter-based generation will displace conventional synchronous machine-bas...
AI summary Nova Scotia aims for 80% renewable energy by 2030, transitioning from coal and conventional generation to inverter-based systems. This shift requires addressing technical challenges through system studies, including EMT analyses. Initial findings were released due to delays in plant models, with an updated report pending. Mitigation measures are emphasized to ensure grid reliability.
Recommendations Stable and Reliable Integration of Renewables - Verify network response for high Rate of Frequency (RoCoF) system disturbances through EMT simulations. Based on study to date, there are significant concerns for the ability...
AI summary The recommendations focus on ensuring stable integration of renewables by addressing RoCoF risks, upgrading grid interconnection standards, and conducting detailed studies. Concerns include existing RoCoF limits potentially causing cascade tripping, the need for IEEE 1547-2018 alignment, and MHI's proposals for grid study updates. NSPI is urged to review system guidelines and perform incremental studies for each generation/load wave.
Resource Planning for High IBR Penetration Update IBR and inertia constraints for resource planning based on the findings herein. At the present time, studies indicate that there is no hard limit on IBR penetration and dispatch if there is...
AI summary The document discusses updating resource planning for high IBR penetration, emphasizing the need for inertia and system strength metrics. It recommends a sliding scale for inertia/FFR, maintaining inertia requirements even with two tielines, and introducing SCMVA as a new metric for system strength in future grid planning.
Good Planning Practices to Integrate Renewables in Nova Scotia • Perform an annual assessment of NSPI System Inertia and Strength in the 10-year horizon to identify potential issues. See Section [2.2.](#page-18-0) Include FOR and planned m...
AI summary The document outlines planning practices for integrating renewables in Nova Scotia, emphasizing annual system inertia assessments, model requirements for grid connections, system studies for western Nova Scotia's load and hydro generation, and maintaining SCMVA levels to ensure grid reliability.
System Operator Support to Transition to High IBR Grid - Develop a methodology to estimate the minimum SCMVA and SCR online prior to the addition of additional IBR (WEC, BESS, HVDC etc.) to the NSPI grid. - Develop a methodology to estimat...
AI summary The document outlines the need to develop methodologies for estimating SCMVA, SCR, and inertia online to ensure grid stability before integrating additional IBR (e.g., WEC, BESS, HVDC) into the NSPI grid. It also emphasizes updating operating guidelines and conducting EMT studies to address fault ride-through, control interactions, and system oscillations from expanded IBR interconnections.
Acronyms Acronym Term BES Bulk Electric System BESS Battery Energy Storage System CI Control Interaction EMT Electromagnetic Transient FACTS Flexible AC Transmission System FFR Fast Frequency Response IBR Inverter Based Resource LVRT Low V...
AI summary The document outlines the acronyms and terminology used in the analysis of frequency control and system strength within the Bulk Electric System (BES), including terms related to power electronics, energy storage, and system impact studies.
[Appendix B: Sensitive SCMVA Buses](#page-58-0) - Table B 1: SCMVA Sensitive Buses, 2023 Typical SCMVA - Table B 2: SCMVA Sensitive Buses, 2023 Minimum SCMVA, 2 thermals, ML - Table B 3: SCMVA Sensitive Buses, 2030 SCMVA, RoCoF Case 511 -...
AI summary Appendix B presents tables analyzing Short Circuit MVA (SCMVA) sensitivity for critical buses in Nova Scotia's power system under various scenarios (2023/2030, thermal limits, tie lines, inertia levels). The data reflects system stability considerations for the Bulk Electric System (BES) under different operational conditions.
[Appendix C: SCR Sensitive Facilities](#page-59-0) - Table C 1: SCR Sensitive Sites, Existing Typical - Table C 2: SCR Sensitive Sites, Existing Minimum Transmission Level Voltage - Table C 3: SCR Sensitive Sites, 2030 RoCoF Case 511 - Tab...
AI summary Appendix C presents tables detailing SCR (Short Circuit Ratio) sensitive facilities under various scenarios, including existing transmission levels, 2030 RoCoF Case 511, and minimum SCMVA conditions. These tables assess system stability risks associated with low SCR values in the Nova Scotia power grid.
List of Tables and Figures Table 1: Minimum Inertia for Frequency Control, First Iteration15 Table 2: Minimum Inertia and FFR Required for Frequency Control 17 Table 3: Most Severe RoCoF, 2023 Grid18 Table 4: First Iteration for 2030 RoCoF...
AI summary The document provides a list of tables and figures related to frequency control, inertia requirements, and grid stability, including tables on minimum inertia, FFR support, and RoCoF, as well as figures illustrating voltage waveforms, simulation results, and frequency response. The introduction section is referenced but not detailed in this chunk.
1.1 Background Most power systems in North America, Europe, Australia, and the Middle East have seen increased penetration of renewable energy-based generation of from 10% to 30% over the past decade. In 2021, close to 30% of NSPI electric...
AI summary The document discusses the increasing penetration of renewable energy, particularly inverter-based generation, and its technical challenges on power systems. NSPI aims for 80% renewable electricity by 2030, but this may reduce system inertia, short circuit levels, and cause instability issues like fault recovery and torsional oscillations, requiring mitigation measures.
1.1.1 Frequency Control In an electrical system, generation and load must be balanced at all times to maintain system stability. Load is the demand for electricity at any instance in time. Generation is the electrical energy to supply the...
AI summary The text explains the importance of balancing generation and load to maintain system frequency (60Hz) in Nova Scotia. Traditional synchronous generators provide Synchronous Inertial Response (SIR) to stabilize frequency during disturbances, while Inverter-Based Resources (IBR) like wind and solar lack inherent inertia but can be programmed for fast frequency response. Effective RoCoF management is critical to prevent equipment trips and maintain stability.
1.1.2 System Strength In an electric system, to be able to transmit power to the customer load, the voltage level on the transmission grid must be maintained within a specific range. When there is a system disturbance,such as lightning str...
AI summary The document explains system strength in electric grids, emphasizing the role of Short Circuit MVA (SCMVA) and the impact of replacing synchronous generators with Inverter-Based Resources (IBRs). Synchronous machines historically provided high SCMVA, but IBRs offer only 10-20% of that support, weakening system stability and increasing voltage volatility during disturbances.
1.2 Scope The following scope will be investigated to ensure a stable NSPI system as it transitions to large scale integration of renewables:
AI summary The scope of the proceeding focuses on ensuring the stability of Nova Scotia Power Inc.'s (NSPI) system as it transitions to large-scale renewable energy integration, emphasizing system reliability and grid management challenges associated with renewable energy adoption.
1.2.1 Frequency Control - Perform an assessment to determine minimum inertia required to maintain frequency stability for the Nova Scotia system under existing and 2030 load and generation dispatch scenarios. - Perform detailed system simu...
AI summary The section outlines tasks related to assessing frequency stability in Nova Scotia's power system, identifying stability and RoCoF concerns through simulations, and recommending mitigation strategies for system design and plant ride-through capabilities under current and 2030 scenarios.
1.2.2 System Strength - Perform a screening level assessment to benchmark 2023 SCMVA levels at 69, 138 and 230 KV buses. - Document minimum SCMVA at load sensitive locations. - Document minimum SCR at all Wind Plants, SVC and HVDC location...
AI summary The document outlines a system strength assessment for Nova Scotia's grid, focusing on benchmarking SCMVA/SCR levels, identifying IBR connection issues, and recommending support measures like BESS or synchronous condensers to maintain reliability by 2030. Initial findings are published ahead of full EMT study results.
2 Assessment Metrics and Methodologies The metrics and methodologies described below are utilized for this study. The assessment is looking at 2030 and aims to identify any deficiencies in frequency and voltage control due to the changing...
AI summary The study assesses 2030 system challenges in frequency and voltage control due to evolving generation fleets, applying Nova Scotia UARB standards. Traditional methods like load flow and short circuit analysis are combined with new methodologies for IBR integration.
2.1 Frequency Control As noted in Section 1.1.1, SIR is an immediate response provided by conventional synchronous machines. It is not a synthesized response through control actions but rather the natural response of a synchronous machine....
AI summary The text discusses the importance of synchronous inertial response (SIR) for system stability and the risks posed by converter-based IBR generators lacking SIR. It highlights NSPI's concerns about future grid reliability with high renewable penetration, emphasizing the need for inertia and FFR to manage RoCoF and maintain frequency stability.
2.2 System Strength As noted in Section [1.1.2](#page-10-0), for the connection of additional IBR generation, the SCMVA is predominantly known to as System Strength in industry. Typically, the SCMVA is estimated by calculating the fault cu...
AI summary The document explains system strength in power grids using SCMVA and SCR metrics. Low SCR (short circuit ratio) indicates weak system strength, leading to potential issues like fault recovery challenges, unstable oscillations, and voltage control difficulties. SCR classifications (high >3, low 2-3, very low <2) are referenced for industry guidance.
2.3 Iterative Assessment The initial assessment and metrics used for these studies follow the traditional load flow and dynamics methodologies with the intent to then take critical cases into PSCADTM for EMT analysis. Upon examination of t...
AI summary The text discusses an iterative assessment process for grid stability, focusing on the challenges of maintaining system inertia and frequency response with the integration of inverter-based resources (IBR). It highlights the need to decouple frequency control requirements from system strength requirements and outlines a multi-step approach to ensure system reliability.
3 Frequency Control Assessment in PSS®E For frequency control assessment, the Nova Scotia grid will experience the greatest frequency deviation and potential high RoCoF when it separates from the North American grid. - The critical dynamic...
AI summary The Nova Scotia grid may experience significant frequency deviation and high RoCoF when it separates from the North American grid, with the loss of transmission lines L-8001 and L-6613 being a critical contingency. UFLS is expected under this scenario.
3.1 Frequency Excursion Damping Boundary cases for light load and peak load for the 2030 load conditions, with maximum renewables online, were run. Simulations were run iteratively to get the online synchronous generation dispatched to the...
AI summary Simulations were conducted to assess frequency excursion damping under light and peak load conditions for 2030, with maximum renewable energy online. Cases were iteratively evaluated, and ten cases met basic criteria for further assessment, focusing on grid requirements for frequency control.
- The light load cases were run with 6 variations. In light load, NSPI has sufficient wind and imports to serve load with 100% renewable energy. Hydro resources are offline. Variations of FFR and inertia were simulated with the goal of tak...
AI summary The text discusses simulations of light load and winter peak scenarios in Nova Scotia's power system, analyzing the use of wind, hydro, and battery energy storage systems (BESS) for stability and inertia. It also examines the impact of losing the New Brunswick tieline with high Nova Scotia imports.
o meet the load, while reducing the thermal units, new wind and BESS was added to the simulation cases. Load Flow and Dynamic assessment was performed for the loss of NB tieline with high NS imports. Case 5, with a low amount of inertia on...
AI summary The document discusses grid simulations analyzing the impact of reducing thermal units and adding renewable resources like wind and BESS. It highlights voltage issues under winter peak load conditions and the potential of FFR from IBRs to reduce reliance on synchronous resources for frequency control in the 2030 grid.
- System load 2145 MW (2030 peak as forecast in 2020), including PHP at 152 MW - ML at 152 MW with 50 MW FFR for case 101, ML at 150 MW without FFR for case 102, offline for case 103 - NB imports at 296 MW - Wind: approximately 474 MW exis...
AI summary The document discusses system load and generation capacity in Nova Scotia, including the impact of reduced inertia and the importance of RoCoF (Rate of Change of Frequency) in system studies. It highlights the planned wind additions and the role of FFR in maintaining system stability.
3.2 RoCoF Historically, there have been RoCoF requirements for generation facilities and some protection devices to ensure they function as expected during frequency swings. The requirements are as needed to stay online for a grid with goo...
AI summary The document discusses the Rate of Change of Frequency (RoCoF) requirements for the Nova Scotia Power Inc. (NSPI) grid, analyzing how changes in grid inertia due to the phasing out of synchronous generation and the increase of renewable generation affect RoCoF. Simulations show varying RoCoF values under different load and generation scenarios, with a 500ms sample time used for calculations.
Table 3: Most Severe RoCoF, 2023 Grid Case Load Total Inertia (MW s) ML FFR RoCoF 2 Light Load 2224 Offline 1.4 11 Summer Peak Load 2487 Offline 2.3 Case 2 is a light load case with three large units on as per the existing operating guidel...
AI summary Table 3 presents the most severe Rate of Change of Frequency (RoCoF) in the 2023 grid, showing values of 1.4 and 2.3 for two different load cases. Case 2 is described as a light load case with three large units operating according to existing guidelines.
Case 11 dispatch is the worst case achievable under existing transmission system configuration and operating guideline for 3 thermal units and ML on for inertia: - The maximum load that could be served with imports, wind and the minimum th...
AI summary The text discusses the worst-case scenario for Case 11 dispatch, analyzing the maximum load that can be served under existing transmission system configurations and operating guidelines. It highlights the need for sufficient inertia and Fast Frequency Response (FFR) to maintain a RoCoF of under 2.5 Hz/s on a 500ms sample time, aligning with 2023 dispatch conditions and recommending further study on appropriate RoCoF metrics for Nova Scotia.
ned with what could be experienced with 2023 dispatch conditions and operating guidelines. That said, it is recommended that further study on an appropriate RoCoF metric for Nova Scotia be undertaken. The GHD survey [12] found that of the...
AI summary The document discusses the need for further study on an appropriate RoCoF metric for Nova Scotia, referencing existing studies and guidelines. It highlights the importance of understanding RoCoF ride-through capabilities of legacy and DER generation sources and the implications of different RoCoF thresholds on transmission system design and grid stability.
Table 4: First Iteration for 2030 RoCoF Case Load Total Inertia (MW s) ML FFR RoCoF 51 Light Load 1044 50MW 2.65 52 Light Load 1102 0MW 3.41 53 Light Load 1603 offline 2.32 101 Peak Load 2404 50MW 3.02 102 Peak Load 2404 0MW 3.27 103 Peak...
AI summary The text discusses the analysis of RoCoF (Rate of Change of Frequency) under various load conditions and the impact of BESS (Battery Energy Storage System) FFR (Fast Frequency Response) support. Tables show the initial and revised inertia levels and RoCoF values, with BESS significantly reducing RoCoF. The study indicates that integrating BESS with FFR capabilities can reduce the inertia required for maintaining RoCoF below 2.5 Hz/s.
4 System Strength Assessment in PSS®E A minimum level of System Strength is required for the power system to remain stable during system disturbances. A minimum level is also required for inverter-based facilities to stay online during sys...
AI summary The document discusses the importance of system strength in maintaining power system stability during disturbances and the testing conducted on the NSPI grid using a full contingency set based on 2020 IRP studies. Six cases were analyzed for system strength under different load conditions.
4.1 Existing Fault Level Assessment To understand the System Strength of the 2023 Nova Scotia grid, an "average" day dispatch was taken as the benchmark for existing SCMVA. Dispatch for benchmarking SCMVA has 3 thermal units, ML, all hydro...
AI summary The document discusses the existing fault level assessment for the 2023 Nova Scotia grid, using an 'average' day dispatch as a benchmark for SCMVA. It notes that wind generation is excluded to avoid including legacy wind's fault current contribution. The assessment is a high-level screening metric, with detailed studies planned for future grid conditions.
4.2 Minimum SCMVA for Sensitive Facilities While the above metric will be a measure of overall SCMVA and a measure of change over time, it will be necessary to monitor the minimum SCMVA for sensitive facilities such as manufacturing plants...
AI summary This section discusses the importance of monitoring the minimum SCMVA for sensitive facilities like manufacturing plants and HVDC facilities to ensure continued grid reliability. If future reductions in SCMVA are anticipated, studies will be conducted, and mitigation measures will be taken to maintain reliability.
4.4 System Support Requirements System Strength requirements will be driven by the need to support existing facilities as the grid transitions to high renewables as well as to strengthen the grid to support the addition of significant quan...
AI summary System strength requirements are necessary to support existing grid facilities during the transition to high renewable energy integration and to strengthen the grid for the addition of significant Inverter-Based Resources (IBR) to meet Nova Scotia Power Inc. (NSPI), provincial, and federal targets.
4.4.1 Post Contingency Voltage Support To maintain post contingency voltage within the range required by NSPI, NPCC and NERC criteria, reactor and capacitor banks were added at several locations in the province. For the winter peak cases,...
AI summary To maintain post contingency voltage within required ranges, NSPI added reactor and capacitor banks at various locations in Nova Scotia. These additions were effective for many scenarios, but future load growth may necessitate dynamic reactive power support if growth exceeds current forecasts.
4.4.2 SCMVA for Sensitive Buses With all contingencies solving well for the 6 cases, a comparative look at the SCMVA for sensitive buses was run. See [Appendix B: Sensitive SCMVA Buses](#page-58-0) for the tables of values. As can be seen...
AI summary The analysis examines the Short Circuit MVA (SCMVA) for sensitive buses under different generation dispatch scenarios. It highlights the need for inertia support, particularly with a second 345kV tieline to New Brunswick, and notes that synchronous condensers are currently the preferred mechanism for grid support.
4.4.4 IBR SCR As noted in Section [4.4.3,](#page-31-0) SCR has limitations in its usefulness as a screening metric for the connection of additional IBR. However, it is still a measure of a wind facility's ability to ride through system eve...
AI summary The document discusses the Short Circuit Ratio (SCR) as a metric for assessing the ability of Inverter-Based Resources (IBR) to ride through system events. It outlines current SCR ranges, the intent to maintain SCR at the Point of Interconnection (POI) for legacy IBR plants, and the need for system studies to determine grid support requirements as the grid evolves.
4.4.5 Stability Requirement When sufficient inertia, FFR and reactive support was added to meet criteria (Frequency, Voltage, and RoCoF, SCMVA etc) as defined in this report there were no observed stability issues in PSS®E. Stability and C...
AI summary The document discusses the stability requirements for the power system, noting that sufficient inertia, fast frequency response (FFR), and reactive support were added to meet defined criteria. Stability and control interactions are best observed in EMT simulations and require further analysis in PSCADTM.
5 Frequency Control and System Strength Assessment in PSCADTM First Stage studies, RMS analysis in PSS®E, have been completed as detailed in the sections above. Stage Two focused on EMT analysis in PSCAD are ongoing. As there are significa...
AI summary First Stage studies using RMS analysis in PSS®E have been completed, with significant findings reported. Stage Two, focusing on EMT analysis in PSCAD, is ongoing, and an updated report will be issued upon completion.
5.3 Detailed PSCADTM Simulation Detailed PSCADTM simulations are used to identify stability and fault ride though concerns and further assess potential RoCoF concerns. EMT simulations have become critical when integrating PE inverter-based...
AI summary Detailed PSCADTM simulations are used to assess stability, fault ride-through, and RoCoF concerns when integrating inverter-based resources (IBR) into AC networks. Traditional RMS simulations may miss critical design considerations, and EMT simulations are essential for identifying system challenges. Increasing short circuit levels and using synchronous support are recommended solutions, though new transmission may not be economically viable. Future NSPI grid analysis will explore IBR controls for system inertia and strength.
5.4.1 Fault Ride-Through NERC Reliability Standard PRC-024-2 describes how generator protective relays should be set such that generating units remain connected during frequency and voltage excursions (see [Figure 5)](#page-37-2). The curv...
AI summary This section discusses the challenges of meeting Low Voltage Ride Through (LVRT) requirements under weak grid conditions for inverter-based plants. It highlights issues such as limitations in Phase Locked Loop response and the impact of plant tripping on voltage control and system stability.
5.4.2 Control Interactions Control Interactions (CI) is a specific issue that can impact the coordinated operation of Power Electronic devices in a local area. Control systems of dynamic devices can interact in an undesirable manner result...
AI summary Control Interactions (CI) can lead to unstable oscillations in power systems, especially with fast-acting reactive power controllers and dynamic devices like wind and solar. The Maritime Link HVDC is designed to avoid adverse interactions with thermal plants. Mitigation requires detailed studies and vendor collaboration.
5.4.3 Sub Synchronous Control Interaction When an IBR is connected to a network, the voltage and phase at the IBR terminals are each sensitive not only to the inverter output but also to the output from other nearby IBR projects or FACTS d...
AI summary The document discusses Sub-Synchronous Control Interaction (SSCI) when Inverter-Based Resources (IBRs) are connected to a network, particularly near series compensated lines. It highlights the potential for negative damping effects from IBRs, such as Type 3 wind units, and notes that Nova Scotia Power Inc. (NSPI) is considering series compensated lines in some studies, requiring SSCI analysis.
SSTI due to interaction with power electronic converters: Power electronic converters and their controls can interact with the natural modes of generator shafts and give rise to poorly damped mechanical shaft oscillations. A main objective...
AI summary This section discusses the potential for Sub-synchronous Torsional Interaction (SSTI) caused by the interaction between power electronic converters and generator shafts, leading to poorly damped mechanical oscillations. The focus is on investigating these impacts through Electromagnetic Transient (EMT) studies, particularly in proximity to generating stations and transmission systems.
Torsional interactions due to network resonance conditions: In addition to SSTI due to interactions with power electronic converters, transient torque magnitude and damping can be negatively affected when series compensated transmission ar...
AI summary The text discusses how torsional interactions can occur due to network resonance conditions, particularly when series compensated transmission lines are near generators. These interactions can cause unstable resonant conditions that affect thermal generators and their mechanical systems, especially when the natural frequency of the mechanical system aligns with the complement of sub-synchronous network resonant frequencies.
5.4.5 IBR Low Frequency Oscillations According to field results and detailed simulation-based studies, the operation of many inverter-based devices in a weak network area can result in sustained low-frequency oscillations. The oscillation...
AI summary The document discusses the potential for low-frequency oscillations (8 Hz – 12 Hz) caused by inverter-based resources (IBRs) in weak network areas, a concern first observed in Australia around 2019. These oscillations, though small and stable, may cause visible flicker. Solutions such as SVC and STATCOM are suggested for system strength issues.
5.4.6 RoCoF The addition of IBR and the subsequent phasing out of conventional generation in Nova Scotia has potential to adversely impact the system RoCoF. This in turn will have impacts on the stable operation of IBRs that are based on g...
AI summary The integration of Inverter-Based Resources (IBR) in Nova Scotia's grid, along with the phase-out of traditional generation, may negatively impact the system's Rate of Change of Frequency (RoCoF). This could affect the stable operation of IBRs and legacy plants during frequency events. Manitoba Hydro International (MHI) recommends surveys and EMT simulations to better understand RoCoF impacts and ensure system reliability.
6.1.3 Fast Frequency Response [Figure 6](#page-49-0) in Section [7.1.2](#page-48-0) demonstrates the ability of FFR from an IBR in damping a frequency deviation for a system disturbance. FFR from HVDC, BESS and other fast acting devices wi...
AI summary This section discusses the role of Fast Frequency Response (FFR) from Inverter-Based Resources (IBR), HVDC, and Battery Energy Storage Systems (BESS) in stabilizing frequency deviations in Nova Scotia's power system during generation disturbances. These systems offer flexibility in rapidly adjusting power injection or consumption based on the state of charge.
6.2 BESS BESS can support the management of the energy supply in a renewable energy dominated NSPI system. Additionally, with appropriate specifications, the fast-acting nature of BESS inverters can also be used to mitigate stability relat...
AI summary Battery Energy Storage Systems (BESS) are highlighted for their ability to manage energy supply in a renewable energy-dominated Nova Scotia Power Inc. (NSPI) system and mitigate stability concerns through fast-acting inverters. They are considered a strong near-term candidate for providing grid-forming and virtual synchronous machine response.
6.3 Synchronous Condensers The addition of synchronous condensers at selected locations in an electrical system is an effective technical solution to facilitate high IBR penetration. It is expected that additional synchronous support will...
AI summary Synchronous condensers are being considered for installation in the NSPI grid to support system strength and accommodate high IBR penetration. Research is ongoing with vendors to understand design options, and EMT models are being assessed for their value in enhancing system stability and frequency response.
6.6 Transmission Connections New transmission paths will generally strengthen a power system. The more the ties between areas of a power system the stronger the ability of the system to withstand grid events. For Nova Scotia, additional tr...
AI summary New transmission connections can enhance power system resilience by reducing RoCoF and increasing SCMVA near tie line termini. Two areas in Nova Scotia are identified as having potential to improve grid stability and support IBR resources under various system conditions.
6.6.1 Second Tie with NB The addition of a second 345kV transmission line to New Brunswick would improve System Strength available from New Brunswick in the Onslow area and reduce the impact of the most critical contingency of the present...
AI summary Adding a second 345kV transmission line to New Brunswick would improve system strength in the Onslow area and reduce RoCoF during high imports. However, this may reduce system strength if synchronous units are offline, potentially affecting WEC facilities at lower voltage levels.
7 Findings and Recommendations This study scope includes full EMT assessment. Due to delay in getting adequate EMT generation and load facility models, it was determined that the initial findings and recommendation should be published imme...
AI summary The study scope includes a full EMT assessment, but due to delays in obtaining adequate models, initial findings and recommendations are being published immediately. An updated report will follow once EMT studies are complete. Findings are based on technical literature, industry expert discussions, and PSS®E studies on inertia and SCMVA for current and projected 2030 systems.
7.1 Findings NSPI can incorporate renewables, in particular IBR resources, limited only by the load to be served and the best economic dispatch to meet target metrics for renewables. There will be technical challenges and the grid will nee...
AI summary NSPI can integrate renewable energy sources, particularly inverter-based resources, up to the limits of load demand and economic dispatch. However, technical challenges and grid support requirements will increase as legacy plants are phased out or converted to alternate fuels, though the transition is deemed achievable with current and emerging technologies.
7.1.2 Minimum System Inertia and FFR The PSC study [23] performed for NSPI in 2019 documented the following: - A minimum of 3266 MW.sec of synchronous inertia will be required for steady state operation. - o Synchronous condensers generall...
AI summary The document discusses the minimum system inertia and Fast Frequency Response (FFR) requirements for Nova Scotia Power Inc. (NSPI), noting that a minimum of 3266 MW.sec of synchronous inertia is required for stable operation. It highlights various sources of inertia and FFR, including thermal units, hydro plants, biomass facilities, and the Maritime Link. The approach to maintaining inertia is based on RoCoF limits and current operating guidelines.
7.1.4 Operability As the grid moves to higher penetration of IBR, reduced SCMVA that occurs due to forced outages and planned maintenance will need an assessment for SCMVA and IBR stability. This may be in the form of updated guidelines or...
AI summary As the grid integrates more IBR, reduced SCMVA from forced outages and maintenance requires assessment for stability. This may involve updated guidelines or real-time studies, with increased need for real-time data visibility for inertia and SCMVA at critical buses for Transmission Operations staff.
7.2.1 Stable and Reliable Integration Recommendations to facilitate the integration of renewables on the timelines in place for Nova Scotia: - Based on study to date, there are significant concerns for the ability of the existing and futur...
AI summary The document outlines recommendations to ensure stable and reliable integration of renewable energy sources into Nova Scotia's grid. Key concerns include managing high RoCoF events, updating interconnection requirements, and addressing grid support needs as synchronous plants retire. Studies and system upgrades are recommended to mitigate risks of cascading tripping and maintain grid reliability.
7.2.2 Resource Planning for High IBR Penetration Recommendations to facilitate current and future economic generation dispatch for increased renewables on the timelines in place for Nova Scotia: - Update IBR and inertia constraints for Ple...
AI summary The document discusses resource planning for high Inverter-Based Resources (IBR) penetration in Nova Scotia, emphasizing the need to update models, incorporate frequency response, and maintain system strength through inertia or Frequency Response (FFR) as key metrics for stable grid operation.
7.2.3 Good Planning Practice Recommendations to implement good planning practices to the integration of renewables in Nova Scotia: - MHI recommends performing an annual assessment of NSPI System Inertia and Strength requirements in the 10-...
AI summary The text outlines recommendations for good planning practices in integrating renewables into Nova Scotia's grid, including annual assessments of system inertia, updated model requirements for load and generation, system studies for load growth and hydro availability, and maintaining SCMVA levels.
7.2.4 System Operator Transition to High IBR Grid Recommendations to support the System Operator transition to a grid with high IBR online. - Develop a methodology to estimate the minimum SCMVA and SCR online prior to the addition of addit...
AI summary The text outlines recommendations for the System Operator's transition to a grid with high Inverter-Based Resources (IBR). It suggests developing methodologies to estimate minimum Short Circuit MVA (SCMVA) and inertia, as well as reviewing and updating operating guidelines for the NSPI grid ahead of the next round of Transmission connected IBR integration.
8 References - [1] "Fast Frequency Response Concepts and Bulk Power System Reliability Needs", NERC Inverter-Based Resource Performance Task Force, March 2020 - [2] "Experiences with Wind Power Plants with Low SCR", Lessons learned from th...
AI summary The document provides a list of references related to power system reliability, renewable energy integration, and grid management, including studies on inverter-based resources, system strength, and high-voltage direct current (HVDC) systems.